Post by youness on No source code available (cip object)
CODESYS Forge
talk
(Post)
Hi yotaro, hope your problem was resolved. I had the same, but with an other library title. This exception is not detected during compilation, but rather at a given position in the program (when switching to a given visualization). Although the exception is generated at this point, it does not involve the visualization in question. This error is due to one of 3 reasons: 1) A division by zero somewhere: The program is able to detect divisions by zero at compile time. But in the case of a variable, which takes a valid value at init and changes to 0 at a later stage. 2) An invalid pointer: (either because it has a value of 0, or because it points outside the memory reserved for the program) is being dereferenced. Locate any pointers or interfaces you have in the code and check them - you should also be wary of mixing inline modifications and pointers. 3) Array overflow: Generally when a processing operation is executed outside the array's definition range. Example: a write loop with n iterations is executed on an array of dimmension n-1. On the other hand, the error message may not appear. In the latter case, the error may have fatal consequences, as the overflow has induced writing to potentially forbidden memory areas. This problem can be explained by the fact that it's not always the adjacent memory areas of PLC_PRG that are overwritten, but the memory areas that are randomly allocated to the array during compilation. In this case, however, there is no entry in the log, so you need to integrate the "Implicit Check function", which checks the line of code generating the error. To integrate this functions, click on Application --> POU for implicit controls Regards,
Last updated: 2024-07-16
Post by mondinmr on Why SysPipeWindows is not implemented in RTE?
CODESYS Forge
talk
(Post)
This library would be very useful for IPC communications. Using a UDP socket on localhost is unpredictable, as with slightly loaded machines it does not even guarantee packet delivery locally. Using TCP creates a lot of overhead. Message named pipes would be an excellent solution for Windows RTE. On Linux, since the release of the extension package, there is no issue, as it is sufficient to develop a component. However, although now 90% of our clients understand that Linux runtimes are better in every way compared to Windows RTE, especially from the security aspect (Not in kernel space) and the issues with Windows updates, 10% stubbornly insist (sometimes for trivial commercial reasons) on using Windows. Managing IPC with circular buffers in shared memory is quite ugly, or rather really ugly and unaesthetic. In the manuals, I saw the SysPipeWindows libraries, so I decided to test them, but unfortunately, I noticed that they are not implemented for RTE devices. Technically, I could try to open them as regular files, but SysFileOpen returns 16#27 or 16#39 depending on how I set the name (direction of the slashes). Here is the code to create shared memory and named pipes. Shared memory work great, named pipes no! #ifdef Q_OS_WIN32 SECURITY_ATTRIBUTES sa; SECURITY_DESCRIPTOR sd; InitializeSecurityDescriptor(&sd, SECURITY_DESCRIPTOR_REVISION); SetSecurityDescriptorDacl(&sd, TRUE, NULL, FALSE); sa.nLength = sizeof(SECURITY_ATTRIBUTES); sa.lpSecurityDescriptor = &sd; sa.bInheritHandle = FALSE; const wchar_t* name = L"Global\\ShmTest"; HANDLE hMapFile = CreateFileMapping( INVALID_HANDLE_VALUE, NULL, PAGE_READWRITE, 0, sizeof(SharedData), name); if (hMapFile == NULL) { qCritical("Error creating shared memory"); return 1; } data = static_cast<SharedData*>(MapViewOfFile(hMapFile, FILE_MAP_ALL_ACCESS, 0, 0, sizeof(SharedData))); if (data == NULL) { qCritical("Error mapping shared memory"); return 1; } HANDLE hPipe = CreateNamedPipe( TEXT("\\\\.\\pipe\\MyPipe"), PIPE_ACCESS_DUPLEX, PIPE_TYPE_MESSAGE | PIPE_READMODE_MESSAGE | PIPE_WAIT, PIPE_UNLIMITED_INSTANCES, 1024 * 1024, 1024 * 1024, NMPWAIT_USE_DEFAULT_WAIT, &sa); if (hPipe == INVALID_HANDLE_VALUE) { qCritical("Error creating named pipe"); return -1; } if (!ConnectNamedPipe(hPipe, NULL)) { qCritical("Error connecting to named pipe"); return -1; } checkPipe(hPipe); #endif
Last updated: 2024-02-02
Post by felipemsgarcia on EtherCAT - Force Control Word
CODESYS Forge
talk
(Post)
What worked for me: Use SMC_SetControllerMode and set the nControllerMode to SMC_nocontrol. With that, you can control the drive via Modes of Operation(16#6060) and Controlword(16#6040) directly. Hope that helps, Cheers!
Last updated: 2023-08-31
Post by eschwellinger on Device User Logon and No device is responding.. Pi4b codesys 3.5 SP19 2 + (64-bit)
CODESYS Forge
talk
(Post)
please use latest version 4.9.0.0 and it is mandatory to have a user pi on your device.
Last updated: 2023-09-11
Post by timvh on Troubles with using CAN API
CODESYS Forge
talk
(Post)
In the example project, you can see that a CAN.CANAreaReceiver is used which has an VAR_IN_OUT reference to a RECEIVER_AREA structure. This structure has a dwIdStart and dwIdEnd to filter a range of ID's and process them through the referenced msgProcessor.
Last updated: 2023-09-19
Post by derpaul on Official MQTT-Client: MAX_RECEIVE_BUFFER_SIZE_EXCEEDED
CODESYS Forge
talk
(Post)
That doesn't help at all: ---- plcload PLC load average: 20% CoreID: 0 --------------------------- PLC Core load: 20% And in taskconfiguration it says that the cycle time is about 5000us with MQTT enabled FBs and about 2800us whitout
Last updated: 2023-09-27
Post by derpaul on Official MQTT-Client: MAX_RECEIVE_BUFFER_SIZE_EXCEEDED
CODESYS Forge
talk
(Post)
Thank you very much so far - As I finaly decided to make an update on the PFC200 - as I've to get it up and running again. But something failed there and no I'm having an other Problem :-( I'll come back to this, when the error comes back!
Last updated: 2023-09-28
Post by tomas111 on Help with error C0142
CODESYS Forge
talk
(Post)
There was an exact mistake. I did as they wrote. I created a visualization and transferred it from the old one and everything works. CS 3.5 SP 19. Thank you.
Last updated: 2023-10-04
Post by davidbo on Is OPC communication possible with server certificate but no client certificate
CODESYS Forge
talk
(Post)
I was just wondering is the following option possible and what the settings should be. Is OPC communication possible with only and mandatory server certificate but no client certificate?
Last updated: 2023-10-06
Post by anhkdv on Motion FB Error
CODESYS Forge
talk
(Post)
Hi! I'm a newbie. I'm doing a project for Delta Robot using Codesys and got this error when trying to move in a dynamic coordinate system. This error occurs when I use FB MC_MoveLinearRelative and FB SMC_GroupWait
Last updated: 2023-10-08
Post by gurke258 on Codesys Safety EtherCAT with Beckhoff
CODESYS Forge
talk
(Post)
Okay, the solution was so simple... In my case, you first have to add the EL1918 and then the EL2904... then the connection is made automatically. I probably had something else before and then added the EL1918... then it doesn't catch the connection :/
Last updated: 2023-11-08
Post by baldeep on Codesys Raspberry Runtime 4.10.0.0 and RSM Utility 3.5.19.0
CODESYS Forge
talk
(Post)
I had been using Codesys Raspberry 4.9.0.0 Runtime for a Project with CAA File 3.5.19.0. But now with Update 4.10.0.0 and Raspberry pi 64 Bit.....i cannot compile my code as RSM Utility 3.5.19.0 is not recognised. Any help? Regards
Last updated: 2023-11-20
Post by ahuckphin on Issues with Modbus Slave with Raspberry Pi
CODESYS Forge
talk
(Post)
I have a DFRobot RS485 temperature & humidity sensor (SEN0438) connected to my Raspberry Pi via a USB to RS485 adapter. I am able to connect and read the sensor data when running a python code locally. However in Codesys, I encounter this error "A bus error has occurred." and "There was no response in time". Could this be because of Modbus Server Channel and Modbus Server Init configuration on my part? Admittedly I am new to Codesys. To get to this stage, I: 1. added some lines to CODESYSControl_User.cfg 2. added "Modbus_COM" in Codesys and set "Serial Port Configuration" under "General" 3. added "Modbus_Master_COM_Port" in Codesys and checked transmission mode is set to "RTU" 4. added "Modbus_Slave_COM_Port" in Codesys and checked server address is set to 1 (also set 1 in my sensor) 5. added 1 channel and 1 init for "Modbus_Slave_COM_Port" under "Modbus Server Channel" and "Modbus Server Init"
Last updated: 2024-07-10
Post by robert-o on Converting hex bytes to float
CODESYS Forge
talk
(Post)
Try OSCAT_BASIC and Function DW_TO_REAL. DWORD_OF_BYTE my although help. The Lib is open and free. It is not necessary to add this Lib, you can use/copy the source code just to get an idea.
Last updated: 2024-08-05
Post by trycyclepower on How to set unit in Axis
CODESYS Forge
talk
(Post)
I am very new to Motion in Codesys. I have linear axis and would like to setup as mm, I want to move axis and control axis in mm, mm/s. How do I do that? I know my electronic gearing is 200000.
Last updated: 2024-08-29
Post by dkugler on Webvisu client connection monitoring
CODESYS Forge
talk
(Post)
is your pointer set to the correct visu client? set a breakpoint in your client iteration and step through the active visu clients like programming system, targetvisu, webvisu,... and check the last usage value of each client
Last updated: 2024-08-30
Post by rmaas on CSV file and string manipulation.
CODESYS Forge
talk
(Post)
the $N stands for newline and $R stands for line break. maybe these combinations are considered as 1 character/position? Not sure, just a thought... see also: https://content.helpme-codesys.com/en/CODESYS%20Development%20System/_cds_operands_constant_string.html#:~:text=A%20string%20constant%20is%20a,belong%20to%20this%20character%20set.
Last updated: 2024-09-27
Post by nano on FB string and naming
CODESYS Forge
talk
(Post)
inside the fb, use the reflection-attribute and get the instancename includibg whole path.when im right, the applicationname will also reflected, if yes. you have to trim it. https://content.helpme-codesys.com/en/CODESYS%20Development%20System/_cds_pragma_attribute_instance_path.html
Last updated: 2024-10-02
Post by arwie on Shared memory between Python and Codesys
CODESYS Forge
talk
(Post)
Hi, I wrote a tutorial how to do this. Fast variable exchange between CODESYS and PYTHON via shared memory: https://gist.github.com/arwie/ff56783d9a2fff52940de82ae1bc1a22
Last updated: 2024-10-04
Post by arwie on Read bytes from Codesys runtime into external Python script
CODESYS Forge
talk
(Post)
Hi, I wrote a howto setup shared memory between CODESYS and Python. Working example code is linked. Fast variable exchange between CODESYS and PYTHON via shared memory: https://gist.github.com/arwie/ff56783d9a2fff52940de82ae1bc1a22
Last updated: 2024-10-04
Post by salvadegianluca on Eoe issues with Windows and Linux
CODESYS Forge
talk
(Post)
Is there any way to have EoE working with Tap names different from tap0? My PLC manufacturer uses Tap0 for the remote assistance service and it's not avvailable for other uses.
Last updated: 2024-10-07
Post by i-campbell on MODBUS TCP REGISTERS CODESYS V3.5
CODESYS Forge
talk
(Post)
codesys is in hex and starts at 0 your other program is set to decimal and maybe starts at 0 or 1, I can't tell.
Last updated: 2024-10-12
Post by thomas-moba on TrueType font problem
CODESYS Forge
talk
(Post)
Thanks for your answers! Close and Open CoDeSys has no effect. I already tried the original Roboto and this is working. But I think our marketing compartment changed it.
Last updated: 2024-10-23
Post by lsislsis on Alarm Table rows font size not change
CODESYS Forge
talk
(Post)
When we try to change the font size of alarm table headers change as excpected but timestamps and messages not change and keep one small size from the begining. Is there any solution for that? Regards
Last updated: 2024-10-23
Post by banialuk on CAN Open Manager - varible of SYNC
CODESYS Forge
talk
(Post)
Hello, were I have find varaible of SYNC "Cycle Period" , or variable that informs about the start of a new cycle SYNC. I want to use this variable in program code. I need to for communication beetween Mster and slave, and send PDO informations.
Last updated: 2024-10-26
To search for an exact phrase, put it in quotes. Example: "getting started docs"
To exclude a word or phrase, put a dash in front of it. Example: docs -help
To search on specific fields, use these field names instead of a general text search. You can group with AND or OR.