I am working on a CAN diagnostic software tool that uses a PEAK PCAN USB network monitor as the interface into the CAN network. The software builds and compiles and I am able to login to the PLC (using the computer as a PLC for now). Im using 'CoDeSys_Control_Win_V3' runtime and have added a CANbus Device to my project. Upon logging in and selecting the Status Tab on the CANbus device, I see 'No driver found'. I'm guessing this is some sort of configuration issue or setting within my project that has to point to the PCAN USB driver installed on my computer. Can somebody tell me where the driver should be placed so that CoDeSys 3.5 could use it?
Things I have done:
Confirmed the PCAN module is working correctly (read, write, and filter functions work as intended)
Added a CANbus deivce in CoDeSys
Started the PLC Control in the windows taskbar
Modified the CODESYSControl.cfg file in the installation directory\GatewayPLC (uncommented Componenet.6=CmPUSBCanDrv)
Added the PCAN_USB.SYS file into \GatewayPLC\Driver Folder. (was already there, but I over wrote it again)
Checked for no conflicting baud rates or node ids
CANbus Device Information Tab:
Type 15
ID 181015
Version 3.5.4.0
What am I missing?
Thank You,
Vadim B.
If you would like to refer to this comment somewhere else in this project, copy and paste the following link:
to the "c:\Program Files\3S CODESYS\GatewayPLC\CODESYSControl.cfg"
it will work like a charm
Even using several Peak-USB adapter connected (several CAN bus) are possible and doing CAN View at the same time while the runtime is running will work.
BR
Edwin
PS: this is a CODESYS V3 question... will be moved to the CODESYSV3 section
If you would like to refer to this comment somewhere else in this project, copy and paste the following link:
Anonymous
-
2015-09-29
Originally created by: OW_RPi
Hello,
I want to use my PEAK CAN USB dongle with 'CoDeSys Control Win V3'.
I followed Edwin's instructions and added 'Component.5=CmpPCANBasicDrv' to '\\GatewayPLC\CODESYSControl.cfg'.
But when start my application, CANBus Status shows ' No driver found'.
Is there anything I forgot?
Next question: Is it possible to use PEAK CAN USB dongle with 'Condesys Control for Raspberry Pi'?
Please help!
Best regards,
Oleg
If you would like to refer to this comment somewhere else in this project, copy and paste the following link:
please check on runtime startup (in the plc logger) if
CmpPCANBasicDrv component is loaded without error.
PeakUSB with Pi:
If you compile the Pi Linux kernel with socket can and enabled Peak USB modules, this should work.
Maybe the Peak System Forum give here more details: http://www.peak-system.com/forum/viewto ... a&start=60
BR
Edwin
If you would like to refer to this comment somewhere else in this project, copy and paste the following link:
Hi,
No should even work with demo version!
Could you give us the whole logger
Start Control Win by console (run as admin) and /debug option for a test.
BR
Edwin
If you would like to refer to this comment somewhere else in this project, copy and paste the following link:
Hello,
I have "No CAN driver found! (error code: 16#27E2)"
I have added "
[ComponentManager]
Component.1=CmpPCANBasicDrv
" to my CODESYSControl.cfg in GatewayPLC folder.
I have Control Win V3 Version 3.5.17.0 running and when I scan, I find my local PC and am able to login and download.
I have PCAN-View running, I've tried without it running as well. I also contacted Peak and they mentioned drivers, I have them installed, I use PCAN-View and PCANApi almost every single day.
What else could I be missing? I have also attached a log.
What other steps are needed? I have now added CmpPCANBasicDrv to C:\ProgramData\CodeSys\CODESYSControlWinV3\F05D572C as well as in the GatewayPLC folder as mentioned above.
I also tried uncommenting net 0 in CmpBlkDrvCanServer.
Hi Edwin, could you please post an example.projectarchive and a CODESYSControl.cfg with the location/path to place it? Then we could simply open the archive and compare the CODESYSControl.cfg to our own/replace ours to get this working. In this example project that runs on a Windows machine, could you please have it sending and receiving a CAN message?
If you would like to refer to this comment somewhere else in this project, copy and paste the following link:
Dear Friends I managed to activate the driver by removing semicolon from component 8 and 9, I assume, components must increment by 1 to be activated. Leaving semicolon at component 8 did not work for me.
In SP18 Control Win configuration:
c:\ProgramData\CODESYS\CODESYSControlWinV3x64\<uniquenumber>\CODESYSControl.cfg </uniquenumber>
Hello,
I am working on a CAN diagnostic software tool that uses a PEAK PCAN USB network monitor as the interface into the CAN network. The software builds and compiles and I am able to login to the PLC (using the computer as a PLC for now). Im using 'CoDeSys_Control_Win_V3' runtime and have added a CANbus Device to my project. Upon logging in and selecting the Status Tab on the CANbus device, I see 'No driver found'. I'm guessing this is some sort of configuration issue or setting within my project that has to point to the PCAN USB driver installed on my computer. Can somebody tell me where the driver should be placed so that CoDeSys 3.5 could use it?
Things I have done:
Confirmed the PCAN module is working correctly (read, write, and filter functions work as intended)
Added a CANbus deivce in CoDeSys
Started the PLC Control in the windows taskbar
Modified the CODESYSControl.cfg file in the installation directory\GatewayPLC (uncommented Componenet.6=CmPUSBCanDrv)
Added the PCAN_USB.SYS file into \GatewayPLC\Driver Folder. (was already there, but I over wrote it again)
Checked for no conflicting baud rates or node ids
CANbus Device Information Tab:
Type 15
ID 181015
Version 3.5.4.0
What am I missing?
Thank You,
Vadim B.
Hi,
if you use current CODESYS Version (V3.5.6.x) and you add
[ComponentManager]
Component.1=CmpTargetVisuStub
Component.2=CmpCodeMeter
Component.3=CmpWebServer
Component.4=CmpWebServerHandlerV3
Component.5=CmpPCANBasicDrv
to the "c:\Program Files\3S CODESYS\GatewayPLC\CODESYSControl.cfg"
it will work like a charm
Even using several Peak-USB adapter connected (several CAN bus) are possible and doing CAN View at the same time while the runtime is running will work.
BR
Edwin
PS: this is a CODESYS V3 question... will be moved to the CODESYSV3 section
Originally created by: OW_RPi
Hello,
I want to use my PEAK CAN USB dongle with 'CoDeSys Control Win V3'.
I followed Edwin's instructions and added 'Component.5=CmpPCANBasicDrv' to '\\GatewayPLC\CODESYSControl.cfg'.
But when start my application, CANBus Status shows ' No driver found'.
Is there anything I forgot?
Next question: Is it possible to use PEAK CAN USB dongle with 'Condesys Control for Raspberry Pi'?
Please help!
Best regards,
Oleg
Hi Oleg,
please check on runtime startup (in the plc logger) if
CmpPCANBasicDrv component is loaded without error.
PeakUSB with Pi:
If you compile the Pi Linux kernel with socket can and enabled Peak USB modules, this should work.
Maybe the Peak System Forum give here more details:
http://www.peak-system.com/forum/viewto ... a&start=60
BR
Edwin
I can't get this to work either using Codesys V3.5 SP9 Patch 2 (US) + for Control Win V3.
Here is my CodesysControl.cfg
[ComponentManager]
Component.1=CmpTargetVisuStub
Component.2=CmpDynamicTextUS
Component.3=SysCpuMultiCore
Component.4=CmpHilscherCIFX
Component.5=CmpPCANBasicDrv
;Component.4=CmpBlkDrvCanServer
The log shows CAN0 (DEVICE_NUMBER = 0): NetID = 0 CmpPCANBasicDrv
When I go online, the CANBus Status says "No driver found"
This is just using the demo version, could this be why?
Thanks,
Travis
Hi,
No should even work with demo version!
Could you give us the whole logger
Start Control Win by console (run as admin) and /debug option for a test.
BR
Edwin
Hello,
I have "No CAN driver found! (error code: 16#27E2)"
I have added "
[ComponentManager]
Component.1=CmpPCANBasicDrv
" to my CODESYSControl.cfg in GatewayPLC folder.
I have Control Win V3 Version 3.5.17.0 running and when I scan, I find my local PC and am able to login and download.
I have PCAN-View running, I've tried without it running as well. I also contacted Peak and they mentioned drivers, I have them installed, I use PCAN-View and PCANApi almost every single day.
What else could I be missing? I have also attached a log.
Last edit: cole 2022-03-28
I could not see that the CmpPCANBasicDrv is loaded on startup of the plc:
In SP17 Control Win configuration should be this:
c:\ProgramData\CODESYS\CODESYSControlWinV3x64\<uniquenumber>\CODESYSControl.cfg </uniquenumber>
[ComponentManager]
Component.1=CmpTargetVisuStub
Component.2=CmpWebServer
Component.3=CmpWebServerHandlerV3
Component.4=SysCpuMultiCore
Component.5=SysReadWriteLock
Component.6=SysCpuBreakpoints
Component.7=SysPipeWindows
Component.8=CmpPCANBasicDrv
Last edit: eschwellinger 2022-03-29
What other steps are needed? I have now added CmpPCANBasicDrv to C:\ProgramData\CodeSys\CODESYSControlWinV3\F05D572C as well as in the GatewayPLC folder as mentioned above.
I also tried uncommenting net 0 in CmpBlkDrvCanServer.
I have the same problem but , even if I modified the CODESYSControl.cfg with Component.X=CmpPCANBasicDrv , in log file doesn't appear CmpPCANBasicDrv.
Is there something wrong in my configuration?
Is sure that you are in the correct CODESYSControl.cfg file could you add it?
I had added my CODESYSControl.cfg. Is it the right file? Correct contents? Do you need a license or something else to make this work?
no licenses needed, but where is the CODESYSControl.cfg is located?
this is the path of CODESYSControl.cfg file : C:\Program Files\CODESYS 3.5.17.10 (64bit)\GatewayPLC\tempCFG
the file is attached
Hi Edwin, could you please post an example.projectarchive and a CODESYSControl.cfg with the location/path to place it? Then we could simply open the archive and compare the CODESYSControl.cfg to our own/replace ours to get this working. In this example project that runs on a Windows machine, could you please have it sending and receiving a CAN message?
Can example is here in forge or store: https://store.codesys.com/de/catalogsearch/result/?q=can+example
the location of your config file on using Control Win 64Bit is:
c:\ProgramData\CODESYS\CODESYSControlWinV3x64\xxxxxxxx\CODESYSControl.cfg
Last edit: eschwellinger 2022-05-13
Dear Friends I managed to activate the driver by removing semicolon from component 8 and 9, I assume, components must increment by 1 to be activated. Leaving semicolon at component 8 did not work for me.
In SP18 Control Win configuration:
c:\ProgramData\CODESYS\CODESYSControlWinV3x64\<uniquenumber>\CODESYSControl.cfg </uniquenumber>
[ComponentManager]
Component.1=CmpTargetVisuStub
Component.2=CmpWebServer
Component.3=CmpWebServerHandlerV3
Component.4=SysCpuMultiCore
Component.5=SysReadWriteLock
Component.6=SysCpuBreakpoints
Component.7=SysPipeWindows
;Component.8=CmpHilscherCIFX
;Component.9=CmpPCANBasicDrv
;Component.10=CmpCANFoxDrv
;Component.11=CmpIxxatCANDrv
;Component.12=CmpBlkDrvCanServer
;Component.13=CmpBACnet
Now I try to make a local J1939 device. It seems it stuck at address claim process