I am able to add the internal bus and the device is shown as active, but when I go to the bus it's status says PFC200Bus: Not running.
I seem to be able to compile and download programs, but IO interactions wont work.
When scanning for connected devices i get a kbus error.
There also a could not create directory /var/run/codesyscontrol/ error.
Update:
I removed some of my IO modules, so that i was left with only a 750-1506 and and the end-terminal.
This got the program running. Will do some more testing to see if one of the modules are faulty.
I do however still get the could not create the directory error.
If you would like to refer to this comment somewhere else in this project, copy and paste the following link:
never seen this error - could you check if enough space is left on your PFC ... login by ssh and 'df'.
and check if the eCockpit runtime is disabled by WBM
If you would like to refer to this comment somewhere else in this project, copy and paste the following link:
So i got all IO modules connected and PLC online. PLC might have some conflict with e!cockpit since it was running that, before i switched. At least it works now.
Not able to see anything about e!Cockpit in wbm, since swaping to codesys 3.5.
I am trying to get a PFC200 to run on codesys.
I am able to add the internal bus and the device is shown as active, but when I go to the bus it's status says PFC200Bus: Not running.
I seem to be able to compile and download programs, but IO interactions wont work.
When scanning for connected devices i get a kbus error.
There also a could not create directory /var/run/codesyscontrol/ error.
Setup:
pfc200 8212 fw 03.07.14(19) runtime V4.3.0.0
CODESYS Sp17 Patch 2
Any suggestions on how to solve this?
Is it possible that you are missing the end terminal on k-bus?
740-600 is mandatory to have connected
Last edit: eschwellinger 2022-01-05
Can confirm that i have a 750-600 end module connected. I had everything running fine with e!Cockpit before i decided to try codesys.
Update:
I removed some of my IO modules, so that i was left with only a 750-1506 and and the end-terminal.
This got the program running. Will do some more testing to see if one of the modules are faulty.
I do however still get the could not create the directory error.
never seen this error - could you check if enough space is left on your PFC ... login by ssh and 'df'.
and check if the eCockpit runtime is disabled by WBM
So i got all IO modules connected and PLC online. PLC might have some conflict with e!cockpit since it was running that, before i switched. At least it works now.
Not able to see anything about e!Cockpit in wbm, since swaping to codesys 3.5.
Storage does not seem to be full.
df returns:
Should i try to create the folder manually as root?
Last edit: DCJarle 2022-01-06
hm..you still see this message in the logger?
Yes the error is still there.