Multiple connections to CoDeSysOPC-Server

2019-06-13
2019-09-01
  • edmorrissey

    edmorrissey - 2019-06-13

    We are currently trying to connect the OSIsoft PI System to a CoDeSysOPC-Server using the PI OPC DA interface.
    There is also an Stange ECS application connected to this CoDeSysOPC-Server.
    When the Stange ECS application is connected to the CoDeSysOPC-Server, we are unable to connect with the PI system.
    Has anyone experienced something like this or would have any suggestions for me?

     
  • eschwellinger

    eschwellinger - 2019-06-21

    Hi,

    sounds like the max Client is exeeded ( Default is 4)
    If i understand it, you do not get values from the CODESYS PI to your OPC DA server connected Client, right?

    You could extend the Client by adding to the

    /etc/CODESYSControl_User.cfg

    [CmpChannelServer]Buffersize=1600000MaxChannels=8

    do not forget to restart the Pi after this change.

    BR
    Edwin

     
  • e.kislov

    e.kislov - 2019-06-21

    Edwin, can you explain "Buffersize=1600000"? What the buffer, which dimension of value (bytes?).
    "Channel" represents only CODESYS OPC connection to PLC? Or any connection like IDE connection, web-visu connection, etc.

     
  • eschwellinger

    eschwellinger - 2019-06-22

    Hi,

    BUFFERSIZE is the overall amount of memory to be used by all channels
    MAXCHANNELS defines the number of channels that may be handled
     concurrently.

    Since each channel needs separate send and receive channels
    the available communication buffer is BUFFERSIZE / (2*MAXCHANNELS)
    - Webvisu
    - OPC UA
    - OPC DA
    - CODESYS
    each occupy one channel...

    BR
    Edwin

     
  • e.kislov

    e.kislov - 2019-06-22

    Thank you for explanations.

     
  • edmorrissey

    edmorrissey - 2019-06-28

    Hi Edwin

    Thanks for your response. I have searched the etc folder an it does not contain the config file or any files from CODESYS.
    Could you please tell me where exactly I can locate this file?
    /etc/CODESYSControl_User.cfg

    Regards
    Ed

     
  • eschwellinger

    eschwellinger - 2019-09-01

    Hi,
    which version do you have installed on the PI?
    (CODESYS runtime 3.5.x.x)

    BR
    Edwin

     