Welcome to our new forum
All users of the legacy CODESYS Forums, please create a new account at account.codesys.com. But make sure to use the same E-Mail address as in the old Forum. Then your posts will be matched. Close

Ethernet Adapter 3.5.9.0 Ethernet Link : 'IoDriver Utility' placeholder library not resolved

Anonymous
2016-09-02
2016-09-05
  • Anonymous - 2016-09-02

    Originally created by: vincent.devillers

    When I add an Ethernet device (3S- Smart Software Solution Gmbh 3.5.9.0 Ethernet Link.), I get an error from the library manager.
    In the library manager the library IoDrvEthernet uses the library IoDrvUtility with seems to be (not resolved).

    => Could not open library '#IoDriver Utility'. (Reason: The placeholder library 'IoDriver Utility' could not be resolved.)I am using Codesys V3.5 SP9 Patch 1 +

    When I look in the Library Repository this "IoDrvUtility' seems to be located in the 'IoDriverBase' library.

    Compiling fails wit at least 35 errors.

    How can I correct this problem?

    see screenshots attached.

    IMG: Library Repository.png

    IMG: Library Manager.png

     
  • eschwellinger

    eschwellinger - 2016-09-02

    Hi,
    which plc are you using and in which version?
    The Problem is that the placeholders for this new SP9 lib is not defined in the plc device.
    The workwround is to set it manually in the placeholders on the libraryManager.

    BR
    Edwin

    IMG: placehlders.jpg

     
  • Anonymous - 2016-09-05

    Originally created by: vincent.devillers

    Thanks, it works.
    The PLC I am using is a Macq P6
    codesys 3.5.9.10

     