According to the website CODESYS supports OPC UA profile βMicro Embedded Device Serverβ. I like to know if the CODESYS OPC UA server also supports client/server communication security according to the OPC UA specifications.
If you would like to refer to this comment somewhere else in this project, copy and paste the following link:
Hi,
if you think on encrypted communiation between OPCUA Server and Client yes.
But depends in which Version your plc is.
You need to install the security agent from the CODESYS store. https://help.codesys.com/webapp/_cds_ru ... -ua-server
BR
Edwin
If you would like to refer to this comment somewhere else in this project, copy and paste the following link:
We are using CODESYS 3.5.X runtime toolkit for ARM-LINUX. What is the minimum runtime version that we need to support OPC-UA including encrypted communication between Server and Client?
If you would like to refer to this comment somewhere else in this project, copy and paste the following link:
According to the website CODESYS supports OPC UA profile βMicro Embedded Device Serverβ. I like to know if the CODESYS OPC UA server also supports client/server communication security according to the OPC UA specifications.
Hi,
if you think on encrypted communiation between OPCUA Server and Client yes.
But depends in which Version your plc is.
You need to install the security agent from the CODESYS store.
https://help.codesys.com/webapp/_cds_ru ... -ua-server
BR
Edwin
We are using CODESYS 3.5.X runtime toolkit for ARM-LINUX. What is the minimum runtime version that we need to support OPC-UA including encrypted communication between Server and Client?
Hi,
I think this should be 3.5SP12 and you need the security agent from store to have it easy to use.
BR
Edwin