Hi,
sure stucks in Communication state 80 which means - no stable distributed clock sync - due the fact taht Control Win is not capable to do this (no hard realtime)
You need to switch to Control RTE as plc.
BR
Edwin
If you would like to refer to this comment somewhere else in this project, copy and paste the following link:
Thanks for you reply, just like the attached screenshot, there is only a control win PLC started, do I have another way to do a test on my PC? thank you~
Hello,I get the communication error when I tried to connect my servo motor,
Hi,
sure stucks in Communication state 80 which means - no stable distributed clock sync - due the fact taht Control Win is not capable to do this (no hard realtime)
You need to switch to Control RTE as plc.
BR
Edwin
Thanks for you reply, just like the attached screenshot, there is only a control win PLC started, do I have another way to do a test on my PC? thank you~
yes download Control RTE from CODESYS store. Maybe install it on an different pc, because it needs an exclusive CPU core to run.