Runtime
Tiziano
2020-02-24
2020-02-24
  • Tiziano

    Tiziano - 2020-02-24

    Hi everyone, is it possible to connect a touch screen to the raspberry without using the codesysy internal web server and to see the same pages programmed inside the Codesys editor?
    Thank you

     
  • eschwellinger

    eschwellinger - 2020-02-24

    Hi,
    it is,
    you need to execute:
    "c:\Program Files\CODESYS 3.5.15.30\GatewayPLC\RemoteTargetVisu.exe"
    scan the PI/plc and then you have it.
    (Sure you need to cal this on an Windows PC) not on the PI.

    BR
    Edwin

     
  • Tiziano

    Tiziano - 2020-02-24

    Hello and thanks for the reply,
    Could I connect the raspberry with codesys to a weintec type operator panel without pointing to an IP address?

     
  • eschwellinger

    eschwellinger - 2020-02-24

    Hi,
    if on the weintec pc is on MS Windows (7 or 10), yes
    If you PI is 3.5.15.x you need to install the Edge Gateway and use then the Gateway in the PI to connect/scan the PI plc.
    BR
    Edwin

     