Welcome to our new forum
All users of the legacy CODESYS Forums, please create a new account at account.codesys.com. But make sure to use the same E-Mail address as in the old Forum. Then your posts will be matched. Close

unresolved references during login to Control RTE SL

2021-07-06
2021-07-13
  • captaincookie - 2021-07-06

    Hello,
    I installed the latest version of the softmotion runtime Control RTE SL for Windows from Codesys store. The Windows 10 Version is 10.0.19043. I allocated 1 core for RTE of 4 cores in total. Then I setup a simple Softmotion Project in SP17, with nothing more inside than the standard settings. Without any Softmotion Master the Project can connect to the runtime and everything seems to be fine, but when I add the Softmotion Master and try to connect to the runtime, I get some errors of unresolved references. The communication connection to the device is succesfull in both cases. The MAC adress should be correct. I tried every proposed one in the settings of the master. The PLC_PRG is empty. In the attachement you can find some screenshots. How can I solve this problem? Thanks for any suggestions that might be helpful. Please tell me, if you need more informations.

     
  • captaincookie - 2021-07-07

    thanks for your answer. I configured the connection as written in the link, but I still get the same errors. The driver describtion is Codesys EtherExpress GBit PCI Ethernet Adapter. I got it from the RTE folder.

     
  • captaincookie - 2021-07-13

    I found now a solution and it is working. Everything in the upper posts was right, the last thing you have to do is to check the PLC configuration if the driver is found by the PLC. Therefore right click on the PLC icon and open the PLC configuration. In the upper menu select Component Manager. In the table additional components the driver should be listet. If not, you have to add it. That's it.

     

Log in to post a comment.