Modbus TCP Device data not reading

2021-08-24
2021-08-26
  • nareshroyal - 2021-08-24

    Hello Team,

    I have tried to communicate Modbus TCP/IP device (Versadac Controller by Eurotherm) to codesys, but i could not read the Modbus registers data in Codesys.

    • Other Modbus devices is communicating to codesys but Versadac controller only not communication.
    • Communication status is healthy and there is no error count.
    • Codesys Version is V3.5 SP16 Patch 1
    • Check below screenshot for your reference.

    Pl check and let me the solution.

     
  • Chris.O - 2021-08-24

    Hi,

    do you use your %IW in the Programm?

    If not you will not receive the current values. For that you have to activate it in your controller settings:

     
    πŸ‘
    1
    • nareshroyal - 2021-08-26

      Hello Chris,

      Thanks for the solution..

      I have checked at my end those setting and it's working fine now... Thanks..:)

       