Search talk: Command ‘Source Upload’

 
<< < 1 .. 9 10 11 12 > >> (Page 11 of 12)

Post by mavitia on Application based license problem - Modbus TCP CODESYS Forge talk (Post)
I am running ubuntu on a raspberry pi, and installed an application based license Control Basic M on it, it runs a demo program fine, does not timeout etc. however, when I add a modbus TCP device, I start getting errors: <Entry severity="error" component="CmpApp" user="nobody" timestamp="12/18/2023 3:49:42 PM" infoId="24">Online change denied. Application Application is in exception state!</Entry> <Entry severity="error" component="CmpApp" user="nobody" timestamp="12/18/2023 3:49:42 PM" infoId="68">Download failed: Application=Application</Entry> <Entry severity="exception" component="CmpApp" user="nobody" timestamp="12/18/2023 3:49:41 PM" infoId="0">Application app=Application has invalid license metrics!</Entry> the modbus tcp slave runs, and the counter ticks up, however, when I call the variables on the %IX0.0 in my program, and try to upload the changes, I am getting the error messages which stop the program as far as I understand, the application based, M includes 2 fieldbus instances, but on the other side is fairly new, anything obvious I am missing out here?
Last updated: 2023-12-18

Post by dhumphries on No source code available CODESYS Forge talk (Post)
Try using an Ethernet/IP scanner instead of an adapter, I'm guessing the 2 devices you're trying to communicate with are adapters, you have to have a scanner somewhere and Codesys should be a scanner. I don't know why you're getting the error, you should be able to use your Ethernet port as an EthernetIP adapter (although I've never had a reason to try,) but it's probably not what you wanted to do, unless you're connecting to another PLC that is a scanner. Good luck configuring the devices you're trying to connect to, it will be a lot easier if you have an .EDS file instead of starting with a generic module, even with an .EDS it can be tricky getting the communication working.
Last updated: 2024-02-03

Post by tokamk on Dynamic setting of the modbus tcp/ip slave ip address CODESYS Forge talk (Post)
Hello, I'm working on a project which includes Panel-PC which communicates with a PLC through Modbus TCP/IP. On the PLC I have a CODESYS code which has Modbus slave objects. The Modbus slave objects have to have manually set IP address in order for them to work properly and the Ip address has to be the PC-Panels's IP. This project is going to a customer and they're using their own IP address realm. So, my question is that is it possible to configure these slaves in some other way, so that the customer doesn't need to modify the CODESYS project? I was thinking that would it be possible to set the IP address of these slaves from external source?
Last updated: 2024-02-15

Post by expertplas on No connection to opc server from codesys opc client CODESYS Forge talk (Post)
Hello, we have aproblen to connect our CODESYS OPC Client to the OPC Server. We installed the client according the CODESYS manual. We can browse the server and variables can be linked to the PLC. I created a self signed certificate for the CmpOPCUAClent as described. The server has a cerificate also. I copied the certificates to the trusted zone of server and client. But when it comes to data exchange we get an error message. "Communication error in data source OPC UA Library. Error ID : 7001 German : "Kommunikatinsfehler inder Datenquelle OPC UA -Bibiothek. Es wurde kein genauer Fehler angegeben. Fehler ID : 7001" It semms that there is no cerificate exchange. We are working with CODESYS 3.5 SP19 Patch 5. Can anyone here say something about this error or has an idea for a solution? Thanks.
Last updated: 2024-08-19

Post by pierre on difference between stub file and source file in scriptengine CODESYS Forge talk (Post)
I included the stub files of scriptengine (codesys python api) in a directory scriptengine of a project. I tried to include librarymanager like that: from scriptengine import librarymanager visual studio code detected an error. It said librarmanager could not be found. Indeed in the stub file, this was library_manager. But if I change it in my code, the plugin doesn t work anymore. I found an easy solution to this problem. I ve just changed the copied stub files.(library_manager -> librarymanager) But I think it would be better if you update it yourself in the future.
Last updated: 2024-09-20

Post by pierre on difference between stub file and source file in scriptengine CODESYS Forge talk (Post)
I included the stub files of scriptengine (codesys python api) in a directory scriptengine of a project. I tried to include librarymanager like that: from scriptengine import librarymanager visual studio code detected an error. It said librarmanager could not be found. Indeed in the stub file, this was library_manager. But if I change it in my code, the plugin doesn t work anymore. I found an easy solution to this problem. I ve just changed the copied stub files.(library_manager -> librarymanager) But I think it would be better if you update it yourself in the future.
Last updated: 2024-09-20

Post by timvh on Communication between applications on same device/controller/runtime (Win RTE 3.5.20.20) CODESYS Forge talk (Post)
If you have a Windows system (RTE), then why not run the CODESYS HMI as separate controller. This could easily be moved to another PC if required. In the HMI you could also still use the Symbolic Var access as part of the Data Source Manager, although maybe OPC is the preferred way to make it more future proof. Or what about the Remote Target Visu. Then you can reduce the load of the main controller, while still only having to create one application including Visualization. This is now also supported for Linux systems. See: https://content.helpme-codesys.com/en/CODESYS%20Control/_rtsl_target_visu_for_linux.html https://content.helpme-codesys.com/en/CODESYS%20Visualization/_visu_execute_remote_target_visu.html
Last updated: 2024-09-28

Post by imdatatas on MC_CamIn did not work properly with SMC_FreeEncoder on SoftMotion 4.17.0.0 CODESYS Forge talk (Post)
Hi @tk096, Thank you for your response. Here is example project file and some screenshot for your analysis regarding this matter. In order to reproduce the problem on your side and make it independent of the hardware, I simulated the encoder counter incrementally for the master in this example. I configured a virtual axis as the slave motion axis. The problem occurs in the same way in the real hardware configuration (servo drive connected to Ethercat and hardware incremental encoder) in MC_CamIn. I hope this example helps you see the problem on your side and understand and find the source of the problem with FreeEncoderAxis for Softmotion 4.17.0.0. Best Regards, Imdat
Last updated: 2024-12-19

Post by dhumphries on Codesys device configuration CODESYS Forge talk (Post)
First make sure the programming laptop and HMI are both on the same subnet. For example if the IP address of the HMI is 192.168.1.125 with a subnet mask 255.255.255.0 set your laptop IP to 192.168.1.120 with a subnet mask of 255.255.255.0. Make sure the cables are fully connected (the ethernet port on my programming laptop will click once but the cable is not fully seated.) Make sure the HMI is powered on, try pinging the device from a command prompt, if you can't ping the HMI there is a network issue that has to be resolved first.
Last updated: 2023-12-30

Post by superjojo2002 on Licensing info not available. CODESYS Forge talk (Post)
I recognized that I have to start the two services "/etc/init.d/codemeter" and "/etc/init.d/codemeter-webadmin" in the docker container as well. If I do so, then the command "cmu -x" returns root@sensoredge-field-netfield-produktmanagment:/# cmu -x cmu - CodeMeter Universal Support Tool. Version 7.60c of 2023-Aug-09 (Build 5625) for Linux/ARMHF 64-Bit Copyright (C) 2007-2023 by WIBU-SYSTEMS AG. All rights reserved. So this time there is no indication any more that "Codemeter is not running". But still we are getting the error when using the license manager in CODESYS development system.
Last updated: 2024-03-21

Post by bschraud on Unerwünschte Username- und Passwortabfrage im Browserfenster CODESYS Forge talk (Post)
Hallo, nach der Portierung meiner Applikation von Codesys Version 3.5.18 auf 3.5.20 habe ich u.a. folgende Baustelle: Wenn in der Datei /etc/CODESYSControl_User.cfg die Einträge [SysProcess] Command=AllowAll und [CmpWebServerHandlerV3] AllowFileTransferServices=1 ergänzt werden, startet die Webvisu mit einer Login Abfrage. Die Webvisu soll aber (wie bisher auch) ohne Benutzeraktion starten. Den Browser für die Webvisu rufe ich mit dem Eintrag @firefox --kiosk --private-window localhost:8080/webvisu.htm in der autostart Datei auf. Wie kann man die Login-Abfrage wieder loswerden? Die Runtime läuft auf einem RPi mit Kernel Version 6.1.21 (aarch64) Vielen Dank für die Hilfe
Last updated: 2024-04-02

Post by i-campbell on build (F11) / generate code using a python script file CODESYS Forge talk (Post)
hello, please enjoy. # i-campbell 2024 import subprocess from scriptengine import * # with a project already open # save if not yet saved # check pool objects if it is a library # generate code only for the active application if it is a project # beep thanks to https://devblogs.microsoft.com/scripting/powertip-use-powershell-to-send-beep-to-console/ if projects.primary: # check project is open if projects.primary.dirty: # save projects.primary.save() if projects.primary.path.lower().endswith('.library'): projects.primary.check_all_pool_objects() # check all pool objects for lib else: projects.primary.active_application.generate_code() # generate if not lib # note, there could be more applications than the active application, # this script does not generate those else: system.write_message(Severity.Error,'no project open') ps_output = subprocess.check_output(["powershell", "-Command", "[console]::beep(500,300)"]) # beep
Last updated: 2024-04-10

Post by ppix on Establishing TLS Connection with MQTT Broker using MQTT Client SL Package CODESYS Forge talk (Post)
For anyone confused with the process visit this link (the bottom section about creating a .pfx file) https://content.helpme-codesys.com/en/LibDevSummary/certificate.html#import-of-client-certificates-with-private-key. I solved this problem by creating a .pfx file and importing it into the security store under 'Own Certificates'(must have SP18 or newer to import .pfx). I used a gitbash shell to enter the openssl command that created the .pfx file. Once you import the file, in your TLS context, set your 'sUseCaseName' to be the same as the name listed in the 'Information' column of your imported certificate. This did it for me
Last updated: 2024-06-20

Post by andre-luis on Check if Codesys runtime is on 'Running' or 'Stopped' state? CODESYS Forge talk (Post)
Hi there, I'm running the Codesys runtime on Windows 64 and I need to know if it is on "Running" or "Stopped" state just after a system crash. The following commands works perfectly well to (re)start it... net stop “CODESYS Control Win V3 - x64" net start “CODESYS Control Win V3 - x64" ...however I'm unable to determine when it is required to be call; I mean, by checking the System Tray icon, it is possible to know if it is on "Stopped" state, but I wanted to run a .BAT command to retrieve it. How can we do that?
Last updated: 2024-07-02

Post by davidbo on RPI can system operation like rm in a shell have an impact on a Task cycle time CODESYS Forge talk (Post)
I have noticed that a rm file1.txt command on a shell has an impact on the cycle time for a TASK writing to file2.txt. Seen in the Monitor fane of the Task configuration Furthermore if a TASK makes a system call like rm, its cycle time increases of course but it seems to have an invisible impact on other TASKs too. I have a TASK for handling communication over the CANbus (SPI) where it stops sending "Heartbeats" for many seconds when another TASK does a system rm. Why is that not seen on the Monitor fane? Is even codesyscontrol paused when system calls are made? The CPU load is about 30-40%
Last updated: 2024-09-23

Post by micik on Start Codesys project and then execute python script from command line CODESYS Forge talk (Post)
Hello, by searching the forum, I have found an example of batch script that can be used to start codesys projct by temporarily setting env variables. However, I'm not sure how to modify this to start Codesys 3.5.20 and whether or not I need to specify "profile" with Codesys version at all. @echo off SET PROJECT=D:\TestScripts\Data\OnlineTest.project SET VARIABLES=POU.testint,POU.testoutput start /wait CoDeSys.exe --profile="CoDeSys V3.4 SP3" --noUI --runscript="D:\TestScripts\Forum_Environment.py" I have tried the following just to open the test project: SET PROJECT=C:\TEST\Example.project start CODESYS.exe --profile="CODESYS V3.5 SP20 Patch 2" But I'm not sure how to specify this project to be open after py script is executed. The py script should first add required library to the project and then project should be open.
Last updated: 2024-09-30

Post by ricola on Change default node Id name on Raspberry Pi CODESYS Forge talk (Post)
EDIT : https://forge.codesys.com/forge/talk/Engineering/thread/cb5a492aa0/ hyplcmotion - 2022-12-16 Found out how! Needed to connect to PFC200 via Putty, and open CodesysControl.cfg with “sudo nano /etc/CODESYSControl.cfg”. Then adding following command to the end of file, and use the name you want, save/close CODESYSControl.cfg, and reboot your PLC. [CmpOPCUAProviderIecVarAccess] CustomNodeName= PFC200 Hi! , I'm digging up this issue cause we have still this long name within current versions on CodesysControl. Is it a lock for "demo" licences or can it be changed in some way ? This DeviceSet name is too way long with spaces inside, not easy to handle with string parsing... Cheers !
Last updated: 2024-10-10

Post by thommy54 on CODESYSControl_User cfg richtig konfigurieren CODESYS Forge talk (Post)
Hallo, nach Erwerb eines neueren Raspberry pi 4 (V1.5) musste ich zwangsläufig von Codesys 3.5.16 hochwechseln - ich habe auf 3.5.20.1 geupdated. Da schlugen mir plötzlich ne Menge Einschränkungen entgegen, deren Behebung einige Zeit dauerte. Eine davon ist, das ein SysFile.SysFileOpen nicht mehr funktioniert. Ich habe das Problem mit Einträgen in der /etc/CODESYSControl.cfg behoben: [SysFile] FilePath.1=/etc/, 3S.dat IecFilePath.1=/proc/, cpuinfo IecFilePath.2=/proc/, iomem PlaceholderFilePath.1=/sys/devices/w1_bus_master1, $OneWire$ PlcLogicPrefix=1 ; ; ---------------------- ; selbst eingefügt PlaceholderFilePath.2=/home/root, $my_home_root$ PlaceholderFilePath.3=/etc/init.d, $my_conf$ PlaceholderFilePath.4=/var/lib/mpd, $my_music$ PlaceholderFilePath.5=/root/Rasp_SPS_Filesystem, $my_Rasp$ Ob die Einträge sich etwas überlappen, kann mir gern jemand sagen, das ist aber nicht das Problem. Ich habe bei den vielen Versuchen, das Teil zum Laufen zu bringen, bemerkt, daß die Einträge auch ganz schnell mal verschwinden. Das ist ja auch so beschrieben, wenn die nächste Version kommt, sind meine Einträge weg. Da ich ähnliche Probleme mit dem Funktionieren von "SysProcessExecuteCommand2()" hatte, die ich ebenfalls mit Einträgen in die /etc/CODESYSControl.cfg hätte beheben können, habe ich gelesen, das man "private" Einträge lieber in die Datei /etc/CODESYSControl_User.cfg machen soll. Gesagt getan und "SysProcessExecuteCommand2()" lief: [SysProcess] Command=AllowAll Command.0=shutdown Aber auch irgendwo stand, das so ein Beteichner wie [SysFile] oder [SysProcess] nur einmal in den beiden Files /etc/CODESYSControl.cfg oder(!) /etc/CODESYSControl_User.cfg vorkommen darf. Das ist nun die eigentliche Frage! Ist das so ? Bei [SysProcess] ist das kein Problem, das gibt es in /etc/CODESYSControl.cfg nicht. Aber bei [SysFile] sieht das anders aus. Da sind 5 Zeilen schon in /etc/CODESYSControl.cfg drin. Würde ich diese in die User-Datei rüberschieben, könnte beim nächsten Update was fehlen oder, oder... Lasse ich es so wie es ist, sind meine Einträge beim Update weg - das sollte ja verhindert werden. Kann da jemand genaue Auskunft geben ?? Vielen Dank Thomas
Last updated: 2024-06-28

Post by westcountryewe on ac_persistence not working when creating a Boot Application but works with a Direct Download to the PLC CODESYS Forge talk (Post)
I am using V3.5 SP18 Patch 5. I have noticed that when I Create a Boot Application from CODESYS, and upload this to my PLC via a USB stick the AC_Persistence does not work and none of my values that are in my PersistenceChannel are retained. However, if I connect direct to my PLC and I perform a direct download of my CODESYS program, my values that are in my PersistenceChannel are retained and work as they should. This makes me wonder if there are files that are missing when a Boot Application is created. I have tried taking a backup of my configuration files after performing a direct download, which gives me the plclog.zip folder, and appears to have the ac_persistence folder present within the file structure, however when I replace the plclogic.zip with the same folder that was created when I created a Boot Application, it still does not work but I wonder whether this is because the ac_persistence folder isn't stored in the correct location for reading. The .app and .crc files are embedded within the plclogic.zip folder, which obviously when uploading need to be standalone files in the root directory of the USB, so the intention there is clearly to extract the .app and .crc files and put them into the correct location within the USB. I wonder if it could be the same for the ac_persistence folder? I have tried moving it to different locations but none have worked. Has anybody else discovered a fix for this? I know the short-term solution is to do a direct download to the PLC but there are some logistical reasons why this isn't neccesarily the best solution for us.
Last updated: 2024-02-27

Post by damian177 on Codesys and SMS in RPi CODESYS Forge talk (Post)
I tried initialize my GSM modem by write simple application in C, and GSM modem works, below used AT commands: AtChat: T : "AT" AtChat: F : "OK" AtChat: T : "AT+CMEE=1" AtChat: F : "OK" AtChat: T : "AT+CMGF=0" AtChat: F : "OK" AtChat: T : "AT+CGMI" AtChat: F : "WH_Ltd" AtChat: F : "WH_GM35" AtChat: F : "Revision: RDA BV5" AtChat: F : "OK" AtChat: T : "AT+CGMM" AtChat: F : "WH_GM35" AtChat: F : "OK" AtChat: T : "AT+CGMR" AtChat: F : "Revision: GM35-D_B5_R05_A01_D170914" AtChat: F : "OK" AtChat: T : "AT+CGSN" AtChat: F : "868221045990218" AtChat: F : "OK" AtChat: T : "AT+CNMI=2,1,0,1,0" AtChat: F : "OK" AtChat: T : "AT+CLIP=1" AtChat: F : "OK" AtChat: T : "AT+COPS?" AtChat: F : "+COPS: 0,2,\"26002\"" AtChat: F : "OK" operator name: "26002" AtChat: T : "AT+CREG?" AtChat: F : "+CREG: 1,1" AtChat: F : "OK" at+creg Modem is initialized I do not understand why Codesys SMS library send AT+CPIN? command ?
Last updated: 2023-09-29

Post by wmoon on Licensing info not available. CODESYS Forge talk (Post)
That command can't excute on my device. I installed CODESYS into Hilscher's product using container Here is the Docker file what I used. I'm not sure if this docker file have a problem. If it have a problem, please let me know how to download the files into my device using ftp server. FROM arm64v8/debian:11.6 RUN apt-get update RUN apt-get install -y wget sudo unzip libusb-1.0-0-dev procps ENV CDS_VERSION "4.10.0.0" ENV EDGE_VERSION "4.10.0.0" ENV URL "https://store-archive.codesys.com/ftp_download/3S/LinuxARM64/2302000039/$CDS_VERSION/CODESYS%20Control%20for%20Linux%20ARM64%20SL%20$CDS_VERSION.package" ENV EDGE_URL "https://store-archive.codesys.com/ftp_download/3S/EdgeGatewayLinux/000120/$EDGE_VERSION/CODESYS%20Edge%20Gateway%20for%20Linux%20$EDGE_VERSION.package" RUN wget --output-document=/tmp/codesys.package $URL && \ unzip -p /tmp/codesys.package 'codemeter.deb' > /tmp/codemeter.deb && dpkg -i /tmp/codemeter.deb && \ unzip -p /tmp/codesys.package 'codesyscontrol.deb' > /tmp/codesys.deb && dpkg -i /tmp/codesys.deb RUN wget --output-document=/tmp/edge.package $EDGE_URL && \ unzip -p /tmp/edge.package '*arm64.deb' > /tmp/edge.deb && dpkg -i /tmp/edge.deb EXPOSE 11740 1217 11743 ENTRYPOINT ["/bin/sh", "-c" , "/etc/init.d/codesyscontrol start && /etc/init.d/codesysedge start && tail -f /dev/null"]
Last updated: 2024-03-20

Post by salvadegianluca on How to use TON inside an FB that is instanced within a Visu page CODESYS Forge talk (Post)
Hi everyone; I'm building a project in which the drag of the mouse over some controls (or the click event) changes the background color of the control items; this change of color is made with an FB that assignes a color code to the background with MUX command based on the value of an enumerator, this part is perfectly working but, when I'm using a touchpanel instead of a web visu (controlled by a mouse) I get into some issues as it seems that the touch operations are not triggering the MouseEnter and MouseLeave properties as it's done with the mouse.... For this reason I'm trying to add a TON to my FB and, if the enum that changes color remains at the same state for more then 3s I'm automatically resetting it to it's "0" so the item gets back the not selected color. Anyhow it looks like the TON function from library is not working in these FB that are instanced in the various visualizations, as instead they do if I create some instances within the POUS. Anyone has ideas of how to make them work?
Last updated: 2024-04-15

Post by salvadegianluca on How to use TON inside an FB that is instanced within a Visu page CODESYS Forge talk (Post)
Hi everyone; I'm building a project in which the drag of the mouse over some controls (or the click event) changes the background color of the control items; this change of color is made with an FB that assignes a color code to the background with MUX command based on the value of an enumerator, this part is perfectly working but, when I'm using a touchpanel instead of a web visu (controlled by a mouse) I get into some issues as it seems that the touch operations are not triggering the MouseEnter and MouseLeave properties as it's done with the mouse.... For this reason I'm trying to add a TON to my FB and, if the enum that changes color remains at the same state for more then 3s I'm automatically resetting it to it's "0" so the item gets back the not selected color. Anyhow it looks like the TON function from library is not working in these FB that are instanced in the various visualizations, as instead they do if I create some instances within the POUS. Anyone has ideas of how to make them work?
Last updated: 2024-04-15

Post by jrsantab on Remote connection to ifm PLC & HMI CODESYS Forge talk (Post)
We have finally solved the problem. The version of the Gateway in the computer that worked (3.5.11.0) and the one that didn't (3.5.17.30) was different. We have three different Codesys 3.5 versions installed because we work with different controllers. I believe that, depending on the sequence you follow to install the versions you get a different Gateway version. To solve the problem you first have to disable the "obsolete" services. Open services, serach for (in our case) CODESYS Gateway V3 Version 3.5.11.0 CODESYS ServiceControl Version 3.5.11.0 I stopped the services and changed to Manual Start. Then you have to create the new services. In our case, from a Command Prompt session (cmd): SC CREATE "Codesys GatewayService Rigual" binpath="C:\Program Files\CODESYS 3.5.17.30\GatewayPLC\GatewayService.exe" and then SC CREATE "CODESYS ServiceControl Version 3.5.17.30" binpath="C:\Program Files\CODESYS 3.5.17.30\GatewayPLC\CODESYSControlService.exe" remember also to set them as Automatic Start!
Last updated: 2024-04-22

Post by solve-it on SysFileOpenAsync CODESYS Forge talk (Post)
Just realized that it is the /dev/input/js0 file. Don't think this is a prob either. Found the ConfigFile. Where and how to add /dev/input/js0? raspberry [SysFile] FilePath.1=/etc/, 3S.dat PlcLogicPrefix=1 [SysTarget] TargetVersionMask=0 TargetVersionCompatibilityMask=0xFFFF0000 [CmpLog] Logger.0.Name=/tmp/codesyscontrol.log Logger.0.Filter=0x0000000F Logger.0.Enable=1 Logger.0.MaxEntries=1000 Logger.0.MaxFileSize=1000000 Logger.0.MaxFiles=1 Logger.0.Backend.0.ClassId=0x00000104 ;writes logger messages in a file Logger.0.Type=0x314 ;Set the timestamp to RTC [CmpSettings] FileReference.0=SysFileMap.cfg, SysFileMap FileReference.1=/etc/CODESYSControl_User.cfg [SysExcept] Linux.DisableFpuOverflowException=1 Linux.DisableFpuUnderflowException=1 Linux.DisableFpuInvalidOperationException=1 [CmpWebServer] ConnectionType=0 [CmpOpenSSL] WebServer.Cert=server.cer WebServer.PrivateKey=server.key WebServer.CipherList=HIGH [SysMem] Linux.Memlock=0 [CmpCodeMeter] InitLicenseFile.0=3SLicense.wbb [SysEthernet] Linux.ProtocolFilter=3 [CmpSchedule] ProcessorLoad.Enable=1 ProcessorLoad.Maximum=95 ProcessorLoad.Interval=5000 DisableOmittedCycleWatchdog=1 [CmpUserMgr] AsymmetricAuthKey=6873d655ac1f166f3743feea42d2f3dd1b39ae40 [CmpSecureChannel] CertificateHash=09fd8d52be4ddd45a709bc9c95e2aa093b3f5695 [SysSocket] Adapter.0.Name="eth0" Adapter.0.EnableSetIpMask=1 ;raspberry [ComponentManager] ;Component.1=CmpGateway ;Component.2=CmpGwCommDrvTcp ;Component.3=CmpGwCommDrvShm [SysCom] ;Linux.Devicefile=/dev/ttyS [CmpBlkDrvCom] ;Com.0.Name=MyCom ;Com.0.Baudrate=115200 ;Com.0.Port=3 ;Com.0.EnableAutoAddressing=1 [SysProcess] Command.0=shutdown [CmpApp] Bootproject.RetainMismatch.Init=1 ;Application.1=Application ;Application.1=Application ;Application.1=Application Application.1=Application [CmpRasPi] Architecture=armv6l [CmpRedundancyConnectionIP] [CmpRedundancy] [CmpSrv] [IoDrvEtherCAT]
Last updated: 2024-07-16

<< < 1 .. 9 10 11 12 > >> (Page 11 of 12)

Showing results of 294

Sort by relevance or date