Post by andreag0 on How to access to variable value through symbolic string name
CODESYS Forge
talk
(Post)
Good to know. I am looking for some soluction to avoid PLC Handler and OPC-UA. Thank you.
Last updated: 2024-06-14
Post by fizzy-bubblech on 3.5 P20 hangs - no response
CODESYS Forge
talk
(Post)
Colleagues, i have the same problems. At the current time, I have to use the new version of the Codesys (3.5.20.10) + Control for Linux SL 4.11.0.0, but it works unstable : theree are a lot of freezes and not-respondings. I tested this on different projects: those that were created in the current version of the project, and those that were migrated from other versions of the development environment. Compiling a project without connecting to a controller is fast enough. The first downloading of the code into the controller, too. But as soon as you need to make edits and download a new code problems begin. Codesys "freezes" at the "Generation code" stage for 15-20 minutes. And only after that time loads the code into the controller. Previously, we used version 3.5.17.60 + Control for Linux SL 4.7.0.0. The process took 1-2 minutes. Do you have any ideas how can i fix it? I will be grateful for your answers.
Last updated: 2024-06-27
Post by eschwellinger on Two OneWireMaster on one Raspberry PI 5
CODESYS Forge
talk
(Post)
you need to have an own task for the one wire and io update these slaves in an own low prio task!
Last updated: 2025-10-18
Post by s1mon on Two OneWireMaster on one Raspberry PI 5
CODESYS Forge
talk
(Post)
yes sure. Thx for your support! This is the Codesys project stripped down only to my EtherCat and OneWire Configuration. The Project now contains only one OneWire Master on GPIO4.
Last updated: 2025-10-20
Post by timvh on Toradex and CODESYS and licensing
CODESYS Forge
talk
(Post)
For the Virtual Control you need to use a "Network license". The Virtual Control has parameters of which one is the reference to the license server. This can be the device itself, but you need to activate the license on the host system (not in the container). For this, CODESYS has a Network License server with WBM (web based management). See for the Network License configuration: https://content.helpme-codesys.com/en/CODESYS%20Control/_rtsl_license_controller_linux.html If it is only for evaluation, I would advise to use a CODESYS (USB) key and activate the license on the key. Then you still have to install the CODESYS Network License server on the host, but you don't have to activate the license as soft license on the device. The benefit is that you can easily move your license to another device when needed. Off course your device must have a free USB port available to be able to do this.
Last updated: 2025-10-20
Post by alimans on Unrecoverable SoftMotion state after switch to PreOp
CODESYS Forge
talk
(Post)
Hi Kim, Hi eschwellinger, how you could solve the problem? I am using Codesys V3.5.19.60 and I still have the same problem. It will work only after a warm/cold restart. Thank you in advance for your kind help.
Last updated: 2025-10-22
Post by eschwellinger on search runtime 4.9.0.0 for pi 3
CODESYS Forge
talk
(Post)
sorry I missed to say how to do this just update the runtime. (extract latest debian package out of the CODESYS package) but 8n this case an update all to the latest version including CODESYS is probably the easiest option now.
Last updated: 2025-10-26
Post by thoughtburnish on EThercat Dynamic configuration
CODESYS Forge
talk
(Post)
For the EL3632, you are using a dynamic EtherCAT configuration (oversampling, timestamped, analog input). You're accurately recognizing the slave and configuring DC settings, SMs, and FMMUs manually. https://forge.codesys.com/forge/talk/Engineering/thread/e42a7575e1 Sprunki
Last updated: 2025-11-04
Post by davidbo on What is the prerequisites for a Raspberry Pi to work with SysSockSetIpAddressAndNetMask()
CODESYS Forge
talk
(Post)
I have done: systemctl stop dhcpcd sudo ip addr flush dev eth0 sudo ip link set eth0 up but a call to SysSockSetIpAddressAndNetMask does not give the eth0 an IP address Why?
Last updated: 2025-11-04
Post by nano on What is the prerequisites for a Raspberry Pi to work with SysSockSetIpAddressAndNetMask()
CODESYS Forge
talk
(Post)
have u turned on the Ip-Setter in codesyscontrol.cfg? [SysSocket] Adapter.0.Name="eth0" Adapter.0.EnableSetIpAndMask=1
Last updated: 4 days ago
Post by davidbo on What is the prerequisites for a Raspberry Pi to work with SysSockSetIpAddressAndNetMask()
CODESYS Forge
talk
(Post)
I have now and it works. I had the idea that it had something to do with codesyscontrol.cfg, but where can I find a description of all the things you can set in codesyscontrol.cfg and its syntax?
Last updated: 3 days ago
Post by emmieturner on Which Lib to use, connect to a socket with URL instead of IP address
CODESYS Forge
talk
(Post)
hi, maybe Net Base Services https://forge.codesys.com/prj/codesys-example/nbs/home/Home/ Thank for sharing
Last updated: 3 days ago
Post by alex-at-xana on EThercat Dynamic configuration
CODESYS Forge
talk
(Post)
Hi Everyone, For a fast monitoring system I am using Ethercat oversampling and timestamping inputs. As the customers has a lot of different configurations out in the field, we went for a dynamic Ethercat configuration. Already got the whole detection chain working but now I am stuck since two days in debugging the configuration. Here are my quesitons: I extended the dynamic config example for the EL3632 16#0E303052: //EL3632 pSlave^.SetDCSettings(TRUE,TRUE,80,80,TRUE,4000,0,0); pSlave^.AddSyncManager(16#1000,128,16#26,TRUE,3); pSlave^.AddSyncManager(16#1080,128,16#22,TRUE,2); pSlave^.AddSyncManager(16#1100,0,16#4,TRUE,1); pSlave^.AddSyncManager(16#1110,214,16#20,TRUE,0); pSlave^.AddFMMU(0,214,0,7,16#1110,0,1,1); pSlave^.AddFMMU(0,1,0,0,16#80D,0,1,1); xKnown := TRUE; This leads to a PLL Error for these devices. I double and triple checked the configuraton, but cannot find the issue. There seems to be one difference: the config dialog creates a startup parameter: 16#10F3:16#05, Name: Command_0, Value:0. Bitlen: 16, Stop on fault: false, jumpt at fault: false: next line: 0 a) I do not find information on how to set this in my code. Can you help me there? b) Without trying to set the value, I get a PLL error for these devices in the master log. Is the config wrong? c) Do I need to set the Master to Autoconfigure or Manual? I used autoconfigure for my tests. The stack creates input data addresses for the slaves input data range (pSlaves[i].InputData) which are different from those created when I use the Engineering tools dialogs to configure Ethercat. Specifically, the addresses seem to be aligned at 16 byte boundaries when they are created using the engineering tool, but may appear at uneven addresses when I use the script in dynamic config. I did not try to access ULINT at uneven addresses yet, but I am suspecting this may be a problem. Do I need to manually align the addresses ? Any help is appreciated...
Last updated: 2024-09-10
Post by mubeta on Some 'pathetic' errors in SoftMotion program
CODESYS Forge
talk
(Post)
Thank you for your interest. Your answers are in line with what I knew, so at least it comforts me that I did not misinterpret the situation. However, I don't have an exact match as, for this project over the past few days I have: 1) I have gone back to leaving the various FBs of the motion always called, all of them, and in the state machine I use a boolean to activate the various useful Execute. (But in the future I want to go back and try the programming technique with which I wanted to develop this project); 2) For the occasional error: SMC_FB_WASNT_CALLED_DURING_MOTION perhaps it was due to the fact that I had set the Ethercat bus synchronism only at the CAN master level, but not at the level of individual drives. I have now also activated it for the individual drives and it does indeed seem to have been resolved, but having also adopted the programming technique mentioned in point 1), I cannot say whether this was the solution to the problem, or instead the previous point. Is there an error ‘regulator or start not set’ in the device log before the error ‘motion generating FB wasn't called for at least one cycle’? I can't answer that right now. By now the machine is running and I am no longer there, at this one. Also, I seem to remember that the 'fbeFBerror' drive structure (5-element array), does not cycle, BUT ONCE THE 5 EVENTS AFTER SWITCHING ON, IT DOES NOT UPDATE ANYMORE (but that's another issue), so diagnostics were not easy.
Last updated: 2024-07-24
Post by gunstr on CODESYS control on RPi starts, shortly runs, then exits
CODESYS Forge
talk
(Post)
Thank you very much for the quick answer! The RPi hw were delivered last week so it's probably a resent version. I found an old scrapped board (2 years or so) with a broken GPIO that I tested with the same SD card image and with that board Codeys can run for the full 2h demo period without issues. Then I went back the the new board to test the 4.17.0.0 release but the installation fails... [INFORMATION] Standard output: create and install daemon [INFORMATION] Standard output: codesyscontrol started [WARNING] Unable to detect Raspberry Pi Architecture. Setting armv6l as default, you can change this through the settings panel. [INFORMATION] Standard output: codesyscontrol stopped [ERROR] Expected exit value of command failed: expected 0, received 1 [WARNING] Error setting the Raspberry Pi Architecture [ERROR] Error installing codesyscontrol Do you have any idea what could be the reason? I'm using an OS image including Python drivers for LCD and some I/O:s from last year to keep things stable, but also after upgrading with sudo apt update && sudo apt upgrade I still get the same error Reverting back to 4.15.00 works fine: [INFORMATION] Standard output: create and install daemon [INFORMATION] Standard output: codesysedge started [INFORMATION] Successfully installed codesyscontrol [INFORMATION] Successfully started CODESYS Edge Gateway for Linux [INFORMATION] Successfully started CODESYS Control for Raspberry Pi SL but as before the Codesys services stops after 30 seconds. And I noticed that the Codesys control stops and is not reachable also if I have no application loaded.
Last updated: 2025-09-02
Post by tk096 on High Cycle Times for SoftMotion_PlanningTask when using AxisGroup
CODESYS Forge
talk
(Post)
Hi, under this circumstances the performance of a Raspberry Pi 4 should be sufficient to run a Softmotion robotics application. A closer look at the project would be required. Maybe you could contact the codesys support? Usually it is recommended to run the planning task cyclically every 2ms with task priority of 0 on a dedicated core. In the task configuration you can have a look at the average and maximum execution time of the planning task. You could use the function block SMC_TuneCPKernel (https://content.helpme-codesys.com/en/libs/SM3_Robotics/Current/SM3_Robotics/POUs/AdministrativeConfiguration/Computation/SMC_TuneCPKernel.html) to define suitable values for the parameters 'fSyncBufferDuration' and 'fPlanningInterval'. However, as previously mentioned, the performance of a Raspberry Pi 4 with realtime patch should be sufficient. The 'fPlanningInterval' parameter specifies the maximum planning step width in seconds. The cycle time of the planning task should not permanently exceed this value. A higher value reduces the computational effort, but can lead to a violation or no full utilization of the set limit values for velocity, acceleration and jerk. From a starting value of 0.016 seconds, the value should be increased gradually until the performance is acceptable. The parameter 'fSyncBufferDuration' specifies the size (in seconds) of the buffer between the planning and fieldbus task. The cycle time of the planning task must not exceed this value at peak times (this will lead to the error SMC_CP_QUEUE_UNDERRUN). A higher value can compensate for peaks in the cycle time of the planning task. At the same time, however, this also increases the latency for executing interrupts and aborting movements.
Last updated: 2024-03-22
Post by cfam on Codesys Control for PLCnext (PLC - AXL F 2152)
CODESYS Forge
talk
(Post)
Good day All I would like to share some information on this site for the Codesys team as well for the future members using Codesys Control for PLCnext if it is allowed. I hope that i Post it in the correct spot. Subject: Codesys, Codesys Control for PLCnext Objective: Using the following Phoenix components to built a PLC Rack and run it on Codesys: Hardware and Software used 1. 2404267, AXC F 2152 - Controller 2. 1088136, AXL F BP SE6 - Module carrier 3. 1088129, AXL SE DO16/1 - Digital module 4. 1337224, AXL SE PD16 GND - Potential distributors 5. 1088127, AXL SE DI16/1 - Digital module 6. 1337223, AXL SE PD16 24V - Potential distributors 7. 1088123, AXL SE AO4 I 4-20 - Analog module 8. 1088134, AXL SE SC-A - Cover 9. Codesys v3.5 SP19 Patch 4 10. Codesys Control for PLCnext V4.10.0.0 Process: Firstly I built the Rack according to the Phoenix Project+ Software tool. Where I rebuilt it onto my test bench . I used the PLCnext Engineer IDE from Phoenix and all Communications where up and running and my PLC program executed successfully. THEN I tried the same PLC Layout with Codesys and Codesys Control for PLCnext. It was not successful and gave me the "Error: Local Bus not Running". I searched the web for answers but was unsuccessful in finding a solution. So I tried to change my configuration and found that the following Modules COULD NOT be recognized by Codesys Control. The result was that the Local Bus Failed to run. 1337224, AXL SE PD16 GND - Potential distributors 1337223, AXL SE PD16 24V - Potential distributors Example 1, Resulted in "Error: Local Bus Not Running": Module carrier slot 1: 1088129, AXL SE DO16/1 - Digital module Module carrier slot 2: 1337224, AXL SE PD16 GND - Potential distributors Module carrier slot 3: 1088127, AXL SE DI16/1 - Digital module Module carrier slot 4: 1337223, AXL SE PD16 24V - Potential distributors Module carrier slot 5: 1088123, AXL SE AO4 I 4-20 - Analog module Module carrier slot 6: 1088134, AXL SE SC-A - Cover Example 2, Result "Successful": Module carrier slot 1: 1088129, AXL SE DO16/1 - Digital module Module carrier slot 2: 1088127, AXL SE DI16/1 - Digital module Module carrier slot 3: 1088123, AXL SE AO4 I 4-20 - Analog module Module carrier slot 4: 1088134, AXL SE SC-A - Cover Module carrier slot 5: 1088134, AXL SE SC-A - Cover Module carrier slot 6: 1088134, AXL SE SC-A - Cover Result: Codesys or Codesys Control for PLCnext, has a PROBLEM to identify the following Modules. 1. AXL SE PD16 24V - Potential distributors 2. AXL SE PD16 GND - Potential distributors Hope that this information could be useful in future. Best regards Jaco Pretorius
Last updated: 2023-12-06
Post by ofey on EtherCAT fieldbus
CODESYS Forge
talk
(Post)
Hi, everyone! I'm trying to set up a PLC controller and a connection to an EtherCAT slave device in Codesys. I want to create a flexible program that I can upload to multiple controllers with different remote IO connected (same program). On one plant i may have 5 AI-cards and 3 DO-cards, and on another I may have 4 AI-cards and 2 DO-cards. For not needing to maintain several different programs wih different devices defined in the program (one for each set up) I thought that using a remote IO would make it easier having a single program. That way I could refer to different memory addresses instead of predefined slots/channels and IO's, that would give me errors if there was a different IO on the plant than what the program expected. When I tried setting up the etherCAT master, I saw that I had to define the etherCAT slave devices with the different IO'cards for me to be able to refer to the memory addresses in a PRG. Exactly what I was trying to avoid. My setup is something like a program that can handle 16 separate pump controls. In a year maybe 6 plans get deployed, and depending on how large the project is, the number of pumps can vary between 4 and 16. And the managers dont want to have IO's for all 16 pumps on every cabinet, and I dont want to maintain 16 separate projects files in case of updates etc. I thought the best way to tackle this was having a single project that read/write data to the different pump IO's by remote IO (fieldbus ethercat) addresses. And the number of pump controls are activated by an external GUI. If pump 1-6 is activated by the GUI, then the PLC-program tries to read/write input/outputs from predefined addresses for the expected IO's. My test setup is a PFC200 WAGO controller and a EtherCAT fieldbus coupler (750-354) with some IO. I hope I didn't explain this too horrible, and if there is a more easy and elegant solution for this challenge I appreciate a feedback on this.
Last updated: 2024-04-08
Post by joschi2804 on Licensing info not available.
CODESYS Forge
talk
(Post)
Hi, maybe this fixes your problem. At least this was our issue back then. We tried to run the codesys runtime environment on an embedded Linux system. The problem on our side was that we changed the WORKDIR directory in the /etc/init.d/codesyscontrol script to /home/user/codesys, but we forgot to copy all files (including the hidden files) from the initial WORKDIR (I am not sure but I guess the initial WORKDIR was /var/opt/codesys) to the new one. After copying those files and restarting codemeter and codesyscontrol, we were able to upload licenses. Hope this help BR Josef
Last updated: 2024-07-10
Post by askic on Library Documentation Export Error
CODESYS Forge
talk
(Post)
Hello, I have encountered a very strange and non descriptive error when creating libraries. Basically, when user just create a new CODESYS library, and then just add Text List, save build with no errors and then try to save as compiled library, the following error would be generated: "The library documentation export error" and nothing more, just like shown in the attachment. Of course I have installed package CODESYS Library Documentation Support v 4.6.0.0 I'm Using Codesys 3.5.20 Patch 2 Does anybody have any suggestion about the cause of this error or any advice on how to troubleshoot further?
Last updated: 2025-02-15
Post by george32 on TCP Server
CODESYS Forge
talk
(Post)
Dear people, I would like to create a TCP server in my PLC program. The TCP server needs to communicate with an external device. I have been searching the internet and found that the libraries Syssocket or CAA NetBaseSrv are two possible solutions to create a TCP server. From what I have read, CAA NetBaseSrv is more user-friendly to implement than the Syssocket variant. However, I am still struggling to actually implement this library. Foremost is my little knowledge about creating a TCP server and how to read/understand each function block, especially the outputs of some blocks and the types, e.g. server has an output CAA.Handle, but I cannot find the explanation of CAA.Handle. I tried to find a good document that can help me understand how to implement a TCP server, but I could not find it. Thank you in advance, George
Last updated: 2025-02-20
Post by jinlee on Dynamic I/Os Mapping
CODESYS Forge
talk
(Post)
Hi guys, Recently, I am working at the Dynamic I/Os mapping feature in Ecockpit or Codesys v3.5. I have been trying the libraries. However, it looks like it will not work as I wanted. I want to build the PLC which can detect all the I/Os itself and from there, I can do something on these channels. For example, the current setup is one digital input card, one digital output card and one analogue input card. Then, I want to add one more card into the setup e.g. one more digital input. Then, wago screen can detect this and we can assign them to tasks for example to control digital output. May I know is it possible ? Kind regards
Last updated: 2023-08-18
Post by lraja on Codesys Programming with phyBOARD®-Pollux i.MX8M Plus
CODESYS Forge
talk
(Post)
Dear All, I am trying to Developing a PLC using phyBOARD®-Pollux i.MX 8M Plus. It is very difficult to find the suitable Codesys control for i.MX8M. I have tried to install CODESYS Control for Linux ARM SL , but unable install it and I am getting the following error, [INFORMATION] Executing SSH command on root@192.168.0.10: Retrieving architecture from package management [ERROR] Expected exit value of command failed: expected 0, received 127 [INFORMATION] Standard output: sh: line 1: dpkg: command not found Kindly check and help phyBOARD®-Pollux i.MX 8M Plus Link : https://www.phytec.eu/en/produkte/single-board-computer/phyboard-pollux/
Last updated: 2023-09-23
Post by ggarcia94 on CANOPEN SDO configuration
CODESYS Forge
talk
(Post)
Hello, I´m connected to two drives via CANOPEN. The connection seems to be ok. However, I´m not able to get the PDOs to work even tho they are configured as in the manual of the drives. Looking at the SDOs I´ve seen that for each PDO there is a "Disable PDO" SDO that does not exist in the manual or in the EDS file of the drives. This "Disable PDO" signal has the same Index and Subindex as another SDO used to set and enable the COB-ID of the PDO. I´m assuming this is normal but why is Codesys creating a "Disable PDO" SDO for each PDO and could that be the reason the PDOs are not working?
Last updated: 2023-09-25
Post by damian177 on Codesys V3.5 + Pixtend v1.3 + RaspberryPi
CODESYS Forge
talk
(Post)
Hi, I use Pixtend v1.3 with my RaspberryPi with Codesys V3.5 SP15 Patch1. Actually in my project I used two packages: - CODESYS Contro for Raspberry PI 3.5.15.10 - PiXtend for CODESYS 1.3.8.0 Now I would like to extend my project about the IIot Libraries SL package, I installed them. Next I added SMS_Service_SL 1.0.0.8 version library and I have problem with compile my project because I get error: [ERROR] PiXtend_DemoProject_q: Library Manager [Device: PLC Logic: Application]: Could not open library '#CAADTUtil'. (Reason: The placeholder library 'CAADTUtil' could not be resolved.) Any have idea what can I do to properly add SMS library to my project?