Post by nulltrace on Modbus TCP Server connection is ESTABLISHED but all holding registers are value 0?
CODESYS Forge
talk
(Post)
your case looks different, the first one was an codesys modbus tcp-slave, your's an Master-Application with gateway. I dont know this Unit, but i would say, from Point of Codesys it looks wrong configured. Just give us more detailed configuration and the please make a sketch of the topology you're trying to realise.
Last updated: 2026-04-08
Post by buczekj on ERROR: Calling the program "AlarmStorage_Prg" is not allowed from multiple tasks
CODESYS Forge
talk
(Post)
Many issues with the alarmmanager and alarmstorage can be solved by deleting the configuration, rebooting, and redownloading. I've found that the configurator doesn't always update when you make chanegs. For linux installations it is typically located in /var/opt/codesys/PlcLogic/alarms/ look for file Application.AlarmConfiguration.xml cd /var/opt/codesys/PlcLogic sudo rm -r alarms sudo reboot
Last updated: 2026-04-09
Post by grant32 on Codesys ARTI .XML file not creating but working.
CODESYS Forge
talk
(Post)
Hello, I am working on a project with a Beijer Nexto Xpress. I have done this a few times with no issues but for some reason this time when creating a Symbol Configuration the ARTI .xml file is not being created in the Project Folder. However when manually putting the ARTI tags in the HMI program they are connected and work. So I am just not getting the file to import all the tags. I can do it manually which is fine but no matter where the project folder is saved this occurs. Anyone experienced this? Did not see another forum on it.
Last updated: 2023-10-27
Post by orbis-tertius on 3.5 P20 hangs - no response
CODESYS Forge
talk
(Post)
Is there anybody can help me with the same problem? I have to migrate created project in ver.3.5.17.0 32BIT with runtime 4.7.0 to ver.3.5.20.0 64BIT with runtime 4.7.11.0 due to the new license. All the libraries and dependencies are updaded and there are no any errors. The first compilation and loading to the controller is being compleated well. After this being done and if I am forced to change any values or change any code in the current project, another compilation will be freezed. This problem can be solved if pressed Build/cleen or cleen all. There is another method to solve this; if project is loaded with excluded object (Alarm Configuration), repeated compilations will be done well.
Last updated: 2024-06-27
Post by rockallsue on Frustration-Fueled Feedback on Project File Management and Git Integration
CODESYS Forge
talk
(Post)
Some developers export ST code manually and edit it in VSCode, then copy it back. However, a more practical approach might be using automation scripts (PowerShell, Python) to extract and inject code into the CODESYS project. You could also check if CODESYS Automation Server or CODESYS API allows better ST access for external tools. https://www.codesys.com/the-system/releases-updates-lifecycle/release-plan-roadmap.html Network drive issues are particularly painful. As a mitigation, you could try using local project storage with periodic cloud sync instead of directly saving to a network drive. Using Rsync or Syncthing for automatic but safe synchronization might reduce risks of file corruption.
Last updated: 2025-06-03
Post by dkugler on Project loses 'Download time' information
CODESYS Forge
talk
(Post)
and if you copy or transfer a project to another place, copy not only the .project, copy .compileinfo .bootinfo and .bootinfo_guids then we figured out it is more often possible to go online without full download. If you build an archiv and extract it, some of this files are missing and login isn't possible without download. I work with V3.5 SP16 Patch 4. I don't know if this problem of the archiv is solved in newer Versions/SP's and I don't know what the problem of Codesys is to help out a lot of programers of this very annoying problem or at least help with a workaround
Last updated: 2025-09-18
Post by budd7566 on Text size suddenly changed
CODESYS Forge
talk
(Post)
Iv been working with a Deep Sea Electronics DSE840 for about 6 months. I have a development version of my program working with a state machine and a basic gui interface. I went to implement CAN and suddenly the text on the gui on the controller is much larger than before. I could flash old versions of my project and the text was the correct size, but if i renamed the project file, the text displayed would be large. The visualization in CODESYS always shows the expected size, but not the controller. I did a fresh install of CODESYS and even a new project with only one text box, I cant get the text size on the controller to match what is displayed in codesys to match. Any advice?
Last updated: 2023-12-09
Post by damian177 on CM4S GPIO's in Codesys
CODESYS Forge
talk
(Post)
Hi, I am running my application on device based on Compute Module 4S (Cortex-A72 (ARMv8) 64-bit ). On this device I installed RPi Runtime in 4.11.0.0 version. In my project I use device: Codesys Control for Raspberry Pi 64SL and my project works, but I actually do not have acces to all GPIO's , because GPIOs Compute Module is available only in 3.5.16.0 version and it doesn't work. Properly work GPIOs B+/Pi2 but using this device I do not have acces to all GPIO's in CM4S. Anyone of can tell me how add GPIOs Compute Module 4.11.0.0 to my project ?
Last updated: 2024-05-28
Post by jorenbeyl on library inside library
CODESYS Forge
talk
(Post)
I am currently developing a library that contains real‑time data. To handle this real‑time data, I am using additional libraries called SysTime and SysTypes Interfaces. When I compile my library on its own, no errors occur. However, when I use this library in a project and compile the project, I get an error indicating that the SysTime data type is not recognized. This happens even though the SysTime library is visible as a dependency under my library. Does anyone know how to correctly include a library within another library so that the project recognizes the sub‑library without causing compilation errors?
Last updated: 2026-04-23
Post by ernesto881124 on ernesto881124
CODESYS Forge
talk
(Post)
Hello good morning everyone I would like to ask a question, is it possible to directly connect a device that only contains modbus RTU communication through an R-45 connector, directly to the PC? Or would you need an intermediate device to achieve communication? It would be of great help to me because I cannot achieve communication between the Codesys simulator plc and a Fuji Frenic mini VFD, please help me if anyone has had the same experience. Thank you so much
Last updated: 2023-09-13
Post by transmin01 on PCAN serial "No CAN driver found"
CODESYS Forge
talk
(Post)
Hi, I am using a PCAN mini CAN board which has the Windows drivers installed on the target PLC. PCAN board can be seen in device manager. However, I am getting "No CAN driver found" error. I have read the post https://forge.codesys.com/forge/talk/CODESYS-V2/thread/44aae19318/ and have uncommented the CmpPCANBasicDrv driver in the CodesysControl.cfg file in development PC and have copied it to the target PC. Current CodesysControl.cfg file attached. Is there anything else I am missing? Regards
Last updated: 2023-09-14
Post by eschwellinger on Persistence Manager Backup
CODESYS Forge
talk
(Post)
you need at them moment a download once (for the configuration files generated including addresses) then stop the plc - exchange the persistence file ( without the config file) This will be improved to 3.5.18.6 and 3.5.20.0. (possible then to generate offline bootproject including full persistenmanager files) - this is if you have not 100% the same bootapplication on the devices. In case you copy the whole Application (PLCLogic) directory it should work out of the box - but only with 100% same bootprojects as mentioned above. By the CODESYS Automation Server would help solve this too.
Last updated: 2023-10-19
Post by snhatton on Running webvisu with Codesys Control Win V3 in Simulation Mode
CODESYS Forge
talk
(Post)
Yes, you can use the CODESYS ControlWin V3 Soft PLC. However, if simulation is enabled on the device this will disable all communication, so you need to turn off simulation to view the visualization in a web browser. In simulation mode, all IO and communication is disabled for standalone testing. In addition, make sure to set the start visualization in the WebVisu object in the application tree. I hope this helps!
Last updated: 2023-12-04
Post by andre-luis on Check if Codesys runtime is on 'Running' or 'Stopped' state?
CODESYS Forge
talk
(Post)
Just to share, for those who as me are seeking for this and had found no information anywhere in this World: Every time I stop/start the PLC runtime ( turning into 'Stopped' or 'Running' state ) the 'CODESYSControlService' appears at the Taskmanager list, which could suggest a straight correlation. I was expecting a clever solution, but this one solves for while.
Last updated: 2024-07-02
Post by ralfki on User management
CODESYS Forge
talk
(Post)
Hello eschwellinger, at first thank you for your answer. So the only ways to activate the user management are CodeSys delevelopment enviroment and the Codesys Automation Server. So there is no function to activate the user management via code? Do you have an idea how to get back the users when somebody replaced the PLC. Our customers have only our own developed visualization and they also don't want to install further softwares. Do you maybe have a solution for this
Last updated: 2024-09-04
Post by elektron785 on Dongle von Linux-Modul (ARM64) nicht erkannt
CODESYS Forge
talk
(Post)
Die Ausgabe bei lsusb ist im ersten Post im Bild usb.png zu sehen - der Dongle wird als WIBU Systems CmStick erkannt. Um Codesys als Soft-PLC darauf zum laufen zu bekommen habe ich das Addon Codesys Control for Linux ARM SL installiert und mir einen Docker gebaut mit den Dateien: codesyscontrol_linuxarm64_4.10.0.0_arm64.deb und codemeter-lite_7.60.5625.503_arm64.deb Wenn ich den Docker ausführe sind die beiden Programme ja inbegriffen und Codemeter sollte eigentlich die Erkennung des Dongles sicherstellen. Gibt es eine Möglichkeit festzustellen, dass Codemeter korrekt ausgeführt wird?
Last updated: 2024-09-05
Post by veneto on OPC UA Client
CODESYS Forge
talk
(Post)
Ciao damian177, provo a chiederti un'informazione. Sul mio progetto Codesys(ver.3.5 SP17) non è visibile l'oggetto "Data Source Manager". Il PC con il progetto Codesys(client) è collegato via rete TCP ad un PLC Siemens1200(server). Sul PC con Codesys ho installato UAexpert(client) e riesco a vedere le variabili del PLC1200. Riesci ad aiutarmi a capire come mai non è visibile l'oggetto "Data Source Manager"? Molte grazie
Last updated: 2024-09-06
Post by trprsmn on "Scan Network" doesn't find CR1140 device (ifm)
CODESYS Forge
talk
(Post)
Hi, I'm watching an ifm tutorial on how to setup an industrial controller in CODESYS. I'm using an 'ecomatDisplay43inch_64bit) controller. CODESYS Gateway and PLC are both runngin (systray). However if I click "Scan Network" I can't find my controller. The only thing it finds is a "desktop" it seems (I'm using a Windows 10 on a Mac Book using VMWare, so maybe it has something to do with that?). How can I fix this? Thanks in advance!
Last updated: 2024-09-11
Post by dkugler on TargetVisu Freezing
CODESYS Forge
talk
(Post)
The only weird situation i remeber with particular or complete frozen target visu was after the rtc clock was fallen or set back to the past. It looked like after running a while the alarm history database crashed during writing entries at a date lot of years in the past. After setting the rtc clock to actual date/time and deleting the alarm db every thing worked fine. I don't know, if this is/was a problem of our PLC hardware/firmware? Maybe check date/time at your system?
Last updated: 2024-09-13
Post by ellocco on Kann mich nicht am Gerät anmelden
CODESYS Forge
talk
(Post)
Ich benutze das virtuelle Gerät "CODESYS Control Win V3 x64" und schaffe es nicht, mich am Gerät anzumelden, CODESYS v3.41p18 meldet: "Ungültige Benutzerauthentifizierung auf dem Gerät". Gibt es die Möglichkeit vorhandene Benutzer zu löschen? Ich habe das Gerät / die PLC bereits über das externe Programm: "CODESYS Control Win V3 x64" gestartet, beendet und erneut gestartet. Aber es hilft nichts, leider ist die Sicherheitsverwaltung ausgegraut und ich weis nicht, wie ich die freigeschalten kann.
Last updated: 2024-10-15
Post by bzzz on Connect WS2812B Light Strip to CodeSys via RasPi
CODESYS Forge
talk
(Post)
Hey guys, I have a RasPi and can control my WS2812B (addressable light strip) via Python. The lightstrip is this one: https://core-electronics.com.au/1m-rgb-led-strip-ws2812b-144-per-meter-white-strip-weatherproof.html What I would like to do is to control it directly via CodeSys through the plc on my RasPi. I know I can run a python script on CodeSys, but I'd like to avoid doing that. Is it possible, and how do I do it? Is there a library that does this?
Last updated: 2024-10-16
Post by mtnkyr on Ethercat Master
CODESYS Forge
talk
(Post)
Hi everyone, I am working on a 3 axes Cartesian robot. I take control of all the axes. In the Ethercat connection, the drive sequence is the same as in the program. For example, in the current program the order is as follows. 1. Axis_Z 2. Axis_X 3. Axis_Y Communication Diagram PLC->Drive_Z->Drive_X->Drive_Y When I try to change the order in the program while keeping the communication diagram the same, there is an axis drive mismatch. How can I fix this?
Last updated: 2024-10-22
Post by winki on Modbus TCP & RTU with Control for Linux SL
CODESYS Forge
talk
(Post)
Hello, Today I am able to test ma industrial computer in my test bench. I am able to do all the configuration throught my VPN, 100% remote. I can see the gateway & the Virtual PLC. Now I would like to do some Modbus TCP Client & Modbus RS485. But I am lost due to docker ! When I go to modbus TCP it only gave me the docker network, but not my eth0 & eth01 When I go to modbus rtu, how can I create the link between Com number & my /dev/ttyRS485 Loic,
Last updated: 2024-10-23
Post by mascara on TouchScreen does not work in Webvisualization.
CODESYS Forge
talk
(Post)
I am configuring a Lenovo M900 computer with CODESYS Control RTE SL 3.5.20.30. I use an Aoc E2272pwut LED 21.5 monitor. The touchscreen works perfectly in the Windows 10 PRO environment but does not work in the WebVisualization environment (Window opened at PLC startup). Does anyone know if it is necessary to configure any drivers in Win RTE? I am at your disposal for any questions. Thank you.
Last updated: 2024-11-11
Post by mubeta on Strange problem with the ‘MC_SetPosition’ function
CODESYS Forge
talk
(Post)
No errors in any condition. The function terminate correctly with the 'done' bit. Now I leave the machine and I don't know when I will be there again. The assumption you made I had considered. The operational limits of the axis are all fit for purpose, and this function should operate virtually without even noticing the motion limits. In fact in practice with the axis at low speed the function corrects any numerical value of the position in the range 0 ... 360° without any problem whatsoever in a single PLC scan cycle.
Last updated: 2025-01-10