Post by wind-11 on Problem with simulation Modbus
CODESYS Forge
talk
(Post)
Hello everyone, I encountered a problem in the simulation while working. In a test project we set up a Modbus connection. We wanted to simulate this with test values. The connection also worked, but unfortunately the values are frozen and do not report any “current data”. (Picture attached) Since these are my first points of contact with Codesys and my colleague continues to work elsewhere, I was hoping that someone here might have an idea. Kind regards and thanks in advance.
Last updated: 2024-03-22
Post by rossanoparis on RevPi CONNECT+, CODESYS, EtherCAT master "Filedbus lost synchronicity"
CODESYS Forge
talk
(Post)
Hello @rmaas I assume, you've already verified and tuned everything regarding the EtherCAT network. In my case the problem was due to a wrong core assignement. I suggest to not use the core #0 for your EtherCAT task. The OS realtime patch, which is present on RevPi OS, uses the core #0 for its porpouses and it mustn't be used by any other task which requires realtime and deterministic features. regards Rossano
Last updated: 2024-04-11
Post by esave on Stepper Drive with Ethercat
CODESYS Forge
talk
(Post)
I bought and installed SoftMotion Light now. When I try to add a SoftMotion Light Axis to my stepper drive and I go online it shows: "The license is missing or invalid". See picture What am I doing wrong? This is the right way right? First add your EtherCat XML-File from your stepper driver and then add the SoftMotion Light axis right? Thanks for your help esave
Last updated: 2024-04-25
Post by eschwellinger on License problem gateway
CODESYS Forge
talk
(Post)
I just try to help. Anyway it is a big difference if a Store SL runtime or an oem plc and licence is used. These licenses need to be activated on plc side - so you have dependencies to the version (CODESYS and Runtime Version) Did you ever ask Epis out for this situation? They should know which license fit to their device. Even they should know if the device is capable for Softmotion and see the requiremnts in the CODESYS store: Runtime 4.9.0.0 - how should this work with Epis 3.5.16.x? Anyway refund is not a problem.
Last updated: 2024-04-26
Post by yannick on Raspberry PI 5 not working
CODESYS Forge
talk
(Post)
Hello I'm using Codesys V3.5 SP19 Patch 6 and a Raspberry PI 5 4GB Bookworm 32bit with the Runtime 4.11.0.0 SL. I can install the runtime and download the software completly but after a few seconds the connection disconnects with the message no connection to device. Please scan network again. And the object reference was not set to an object instance. See screenshot. Can somebody help me with that? Thanks
Last updated: 2024-04-28
Post by corriibme on Setting array values with JSON Utilities SL
CODESYS Forge
talk
(Post)
It turns out that you can build JSON structures without ever calling the JSONBuilder function block directly. Instead, create a pointer to JSON.JSONData and invoke the necessary methods on its dereference. The parent object has a parent index of -1 (and an index of 0). EVERY other item (including keys, values, empty arrays and sub-objects) created by the setX methods needs the index to increase by 1. Then use the JSONByteArrayWriter FB to generate your JSON string
Last updated: 2024-05-23
Post by yofi on Raspberry PI change tag only responds after stopping PLC
CODESYS Forge
talk
(Post)
Using V19 Patch 7 and 4.11.0.0 for Pi 4 Model B, My problem is whenever I change a tag e.g bool from true to false it will change in software but the pin will only go high to low after pressing stop PLC in codesys and same if i want to bring it back to high, have to login start plc change it and stop plc in order to change. any insight ? thanks
Last updated: 2024-05-25
Post by plunje on Sensor not set
CODESYS Forge
talk
(Post)
A got a larger project but this very small example makes it clear. I have a button, and after it's clicked a lamp should flip on and stays on, and when the mouse-button is released it should stay on. When I try that in the PLC_PRG it works, but when I change it to a function block (seet attched demo proj) it isn't. I'm fairly new to PLC programming but are very experienced C# engineer, but this goes above my head...
Last updated: 2024-05-26
Post by mozed on Bug Device login
CODESYS Forge
talk
(Post)
Good morning, The problem I encounter is very disturbing, when I try to connect to my project, it asks me to put in my username and password, which I do. However, I cannot connect and it restarts. the window to rewrite my identifiers. However it is the correct identifier and password I do not understand why. When I try to put false identifiers there strangely it tells me that these are not valid identifiers. There is something what can I do? Sincerely
Last updated: 2024-06-11
Post by ph0010421 on Windows 11 and SP17
CODESYS Forge
talk
(Post)
Hello New W11 machine. I've tried installing and the 'Codesys installer' appeared, which basically failed. This was the exe from the Store. I've now tried installing with an old copy of SP17, which didn't try and use the Codesys installer, but has hung at the 'Install all packages added to the setup' stage. Has the exe been updated to use the Codesys installer? What is the installer? Do we think it'll work on w11? thanks, Paul
Last updated: 2024-06-12
Post by ranadheer on Request to share documents about SoftPLC Extension SL
CODESYS Forge
talk
(Post)
Hello Everyone Our team is planning to begin an industrial automation project and we are currently evaluating the use of SoftPLC Extension SL as a potential solution. As we are in the early stages and have yet to start the implementation, we kindly request access to official reference documents, technical manuals, and datasheets relating to SoftPLC Extension SL. Thank you very much for your assistance. We look forward to your response.
Last updated: 2025-10-18
Post by imdatatas on SMC_ERROR.SMC_AXIS_NOT_READY_FOR_MOTION when using Drive Virtual
CODESYS Forge
talk
(Post)
@ducng, Another possible situation could be that normally there are 3 inputs for MC_Power. In your above images, I can't see the "bDriveStart" input activated. As Mr. @gseidel mentioned, you need to make sure MC_Power.Status output should be TRUE. Issuing any movement command without activating the axis would naturally result in an error. For MC_Power; You can set the Enable and bDriveStart inputs to TRUE and try turning the axis activation on and off using only the bRegulatorOn input. Regards, Imdat
Last updated: 2025-11-28
Post by gseidel on MC_Phasing state explenation
CODESYS Forge
talk
(Post)
Hi kenth1973, MC_Phasing has been improved in recent versions. I would recommend to install the latest version of SoftMotion (4.20.1.0) and test whether the problem still exists, and if so, what the error identifier is. (Also check the PLC log in this case, it might contain additional information.) Setting the internal state of the FB is not recommended, it could lead to malfunction of the FB and unintended movements of the drive. Best regards, Georg
Last updated: 2025-11-28
Post by marciohogenelst on stablish CAN communication through the PC's USB port
CODESYS Forge
talk
(Post)
I'm using Codesys v3.21SP4 on my PC via ControlWin to establish CAN communication through the PC's USB port. The software works fine. The CAN/USB converter works fine and is validated. However, there is no communication. Which folder and file should be modified to allow the CAN/USB converter to work and thus achieve the connection? Converter used: PCAN-View Information not yet processed: Access the folder: C:\Program Files (x86)\3S CODESYS\GatewayPLC\CODESYSControl.cfg Uncomment the line: Component.5=CmpPCANBasicDrv Any help would be appreciated.
Last updated: 2025-12-11
Post by marciohogenelst on stablish CAN communication through the PC's USB port
CODESYS Forge
talk
(Post)
I'm using Codesys v3.21SP4 on my PC via ControlWin to establish CAN communication through the PC's USB port. The software works fine. The CAN/USB converter works fine and is validated. However, there is no communication. Which folder and file should be modified to allow the CAN/USB converter to work and thus achieve the connection? Converter used: PCAN-View Information not yet processed: Access the folder: C:\Program Files (x86)\3S CODESYS\GatewayPLC\CODESYSControl.cfg Uncomment the line: Component.5=CmpPCANBasicDrv Any help would be appreciated.
Last updated: 2025-12-11
Post by seler on Custom button with output status
CODESYS Forge
talk
(Post)
Just to clarify. Output for lamp will have two inputs: from plc IN (wall switch) and from visu button. Until now I had separate object for visu button and separate for visu lamp. Now I want it to be one object, bulb icone which will change color on lamp status and yet by touching it will change visu button state. Tried "Switch Image" object but there is no way to assign switch var.
Last updated: 2025-11-19
Post by leag on Reset device password Festo PLC
CODESYS Forge
talk
(Post)
Hi, I am new to CODESYS, and I want to program a new FESTO, but I am getting this authentication screen. I don't remember the password. I tried with Administrator/Administrator and some other defaults I found online but nothing works. I also tried searching for CODESYSControl_User.cfg and many other recommended directories but I dont seem to have any of them (like CODESYSControlWinV3x64) Could you please help me understand what I need to reset? Thanks a lot
Last updated: 2026-08-12
Post by nehaltrivedi96 on Modbus connection via Qronox PCD3 M6893
CODESYS Forge
talk
(Post)
Hello, I am currently scaling 4-20mA signals and the scaled output (temperature) has to be sent via modbus protocol to a tool like doctor modbus or modbus poll. I have defined my inputs as real as and the output is also real, but to send this output via modbus it has to be of word. So how will i convert real into word and then send the generated output via modbus?
Last updated: 2026-02-18
Post by fefefede on Get the numer of day
CODESYS Forge
talk
(Post)
Hello i tro to create a program to turn on or off the air condition in relationship temperature and numer of day. I can't get the number of day. I try this after installing SysTime library but this not work and have this error on debug ------ Build started: Application: Device.Sim.Device.Application ------- Typify code... Generate code... [ERROR] giorno_accensione_aria: PLC_PRG Device: PLC Logic: Application: C0032: Cannot convert type 'Unknown type: 'SysTimeCore(TRUE)'' to type 'TIME' [ERROR] giorno_accensione_aria: PLC_PRG Device: PLC Logic: Application: C0035: Program name, function or function block instance expected instead of 'SysTimeCore' [ERROR] giorno_accensione_aria: PLC_PRG Device: PLC Logic: Application: C0032: Cannot convert type 'Unknown type: 'DayOfWeek(CurrentTime)'' to type 'INT' [ERROR] giorno_accensione_aria: PLC_PRG Device: PLC Logic: Application: C0035: Program name, function or function block instance expected instead of 'DayOfWeek' [INFORMATION] giorno_accensione_aria: PLC_PRG Device: PLC Logic: Application: C0181: Related position Build complete -- 4 errors, 0 warnings : No download possible PROGRAM PLC_PRG VAR Temperatura: UDINT; AriaCondizionata: BOOL := FALSE; CurrentDayOfWeek: INT; //Variabile Giorno CurrentTime: TIME; GiornoDellaSettimana: INT; DayOfWeek: INT; END_VAR CurrentTime := SysTimeCore(TRUE); // Ottieni l'ora corrente CurrentDayOfWeek := DayOfWeek(CurrentTime); CASE GiornoDellaSettimana OF 1: // Azioni per Lunedì 2: // Martedì se più 10° accend altrimenti spegni IF Temperatura >= 10 THEN AriaCondizionata := TRUE; ELSE AriaCondizionata := FALSE; END_IF 3: // Mercoledì se più di 50° accendi altrimenti spegni IF Temperatura >=50 THEN AriaCondizionata := TRUE; ELSE AriaCondizionata := FALSE; END_IF 4: // Giovedì se più di 40° accendi altrimenti spegni IF Temperatura >=40 THEN AriaCondizionata := TRUE; ELSE AriaCondizionata := FALSE; END_IF 5: // Venerdì se più di 50° accendi altrimenti spegni IF Temperatura >=50 THEN AriaCondizionata := TRUE; ELSE AriaCondizionata := FALSE; END_IF 6: // Sabato se più di 25° accendi altrimenti spegni IF Temperatura >=25 THEN AriaCondizionata := TRUE; ELSE AriaCondizionata := FALSE; END_IF 7: // Domenica sempre spenta AriaCondizionata := FALSE; END_CASE
Last updated: 2023-09-14
Post by matteodigani on Error using function block "Write alias address"
CODESYS Forge
talk
(Post)
Hi, I've got a problem using the function block "Write alias address" (ETCStack library 4.9.0.0). this is the code: EtherCAT_1(); IF EtherCAT_1.ConfigRead AND enable THEN CASE seq OF 0: exec := FALSE; T.IN := TRUE; T.PT := T#10S; T(); IF T.Q THEN seq := 1; T.IN := FALSE; END_IF ; 1: T.IN := FALSE; T(); //THIS ONE WORK CORRECTLY! WrAliasAdd.xAbort := FALSE; WrAliasAdd.usiCom := DWORD_TO_USINT(EtherCAT_1.InstanceNumber); WrAliasAdd.wSlaveAddress := 1002; WrAliasAdd.xAutoIncAdr := FALSE; WrAliasAdd.uiAliasAddress := 19; WrAliasAdd.udiTimeOut := 3000; IF start THEN exec := TRUE; ELSE IF NOT error THEN start := TRUE; END_IF END_IF IF WrAliasAdd.xDone THEN start := FALSE; done := TRUE; error := FALSE; exec := FALSE; seq := 5; END_IF IF WrAliasAdd.xError THEN start := FALSE; done := FALSE; error := TRUE; exec := FALSE; END_IF ; 5: exec := FALSE; T.IN := TRUE; T.PT := T#1S; T(); IF T.Q THEN seq := 10; END_IF ; 10: T.IN := FALSE; T(); //THIS ONE GIVES ME AN ERROR! WrAliasAdd.xAbort := FALSE; WrAliasAdd.usiCom := DWORD_TO_USINT(EtherCAT_1.InstanceNumber); WrAliasAdd.wSlaveAddress := 1006; WrAliasAdd.xAutoIncAdr := FALSE; WrAliasAdd.uiAliasAddress := 25; WrAliasAdd.udiTimeOut := 1000; IF start THEN exec := TRUE; ELSE IF NOT error THEN start := TRUE; END_IF END_IF IF WrAliasAdd.xDone THEN start := FALSE; done := TRUE; error := FALSE; exec := FALSE; seq := 99; END_IF IF WrAliasAdd.xError THEN start := FALSE; done := FALSE; error := TRUE; exec := FALSE; END_IF ; ELSE ; END_CASE WrAliasAdd(xExecute := exec); END_IF The first one slave ethercat works correctly, but the other one gives me an error. Attached the ethercat configuration of the devices. All the devices are set "Optional". So my idea is to enable only the first one (1002) and the fifth one (1006).
Last updated: 2025-10-01
Post by arundara on Variable Sync Issue In Soft Plc Redundancy
CODESYS Forge
talk
(Post)
Hello, I was trying to create a redundancy POC for our application where we read data from few modbus tcp devices. As there is a limitaion that modbus tcp device support only for single master device, we wanted to test how the variable sync happens in redundancy mode. For that i have used the redundancy sample code added a variable "b" under a condition. What i observed was while active controller is running, if passive controller is powerup, passive controller is able to sync all the data configured for redundacny. But after that the variable data which resided under a condition is not synching from active to passive controller. I have attached the image where i have highlighter the variable. Can some help me to understand how redundacny work in codesys soft plc and if there is a solution to sync variable which are under condition, please explain the same or suggestion to achieve the same. Hardware - Raspberry Pi (2 qty) Redundancy licence used - yes in both controllers. Codesys runtime - 4.9.0.0 Codesys software version - V3.5 SP19 if i have posted this question in wrong section, please do let me know in whcih section i have to post this question.
Last updated: 2023-12-01
Post by animesh on SoftPLC (CODESYS Control x86 RTE V3 x64) OPC UA binds only to 127.0.0.1 — Not binding to LAN IP
CODESYS Forge
talk
(Post)
Hello everyone, I am facing a persistent issue with the OPC UA Server on Advantech Soft PLC with hard realtime for Win64 (V3_5_2010_3) and need help from the community. Device Information Name: Advantech Control x86 RTE V3 x64 Vendor: Advantech Co., Ltd. Categories: PLCs Version: 3.5.20.10 Description: Advantech Soft PLC with hard realtime for Win64 (V3_5_2010_3) Problem Summary The OPC UA Server works perfectly when accessed via: opc.tcp://localhost:4842 opc.tcp://<hostname>:4842</hostname> But it does NOT work when using the LAN IP: opc.tcp://192.168.0.XX:4842 In UAExpert I get: Discovery FindServers on opc.tcp://192.168.0.XX:4842 failed (BadCommunicationError) Port is LISTENING in windows Firewall.. Tried with turning off the firewall completely. System Information Windows 10 x64 Advantech CODESYS RTE Soft-PLC (hard real-time) Network IP: 192.168.0.XX Hostname: WINDOWS-XXXXX Need your Support
Last updated: 2025-11-24
Post by ryusoup on JSONByteArrayWriter problem?
CODESYS Forge
talk
(Post)
Hello, I am trying to implement a FB to make JSON formatted WSTRING type message using JSON Utilities 1.9.0.0 included in the IIoT library. In my case, I want to set some objects or arrays and set values to them later. But when I wrote as the sample below, // init builder builder(pJsonData:=pJsonData, diRootObj=>diRootObj); // set the 1st key to root diKey1 := builder.SetKeyWithArray(wsKey:="key1", diParentIndex:=diRootObj, eError=>eError); // set a value to the 1st key wsValue:="value01"; builder.SetValue(Value:=wsValue, diParentIndex:=diKey1, eError=>eError); // set the 2nd key to root diKey2 := builder.SetKeyWithArray(wsKey:="key2", diParentIndex:=diRootObj, eError=>eError); // set a value to the 2nd key wsValue:="value02"; builder.SetValue(Value:=wsValue, diParentIndex:=diKey2, eError=>eError); // set a value to the 1st key again wsValue:="value03"; builder.SetValue(Value:=wsValue, diParentIndex:=diKey1, eError=>eError); // set a value to the 2nd key again wsValue:="value04"; builder.SetValue(Value:=wsValue, diParentIndex:=diKey2, eError=>eError); // write build result writer(xExecute:=TRUE, pwData:=ADR(wsResult), udiSize:=SIZEOF(wsResult), xAsyncMode:=FALSE, jsonData:=pJsonData^); the result was: { "key1": ["value01"], "key2": ["value02", "value03", "value04"] } while my expection was: { "key1": ["value01", "value03"], "key2": ["value02", "value04"] } Inspecting pJsonData^, JSONData itself seems to be ok, so I believe the issue is something caused by the writer FB. Does anyone know how to fix it? Thanks,
Last updated: 2023-10-04
Post by to-ke on Errors with VisuUserManagement library
CODESYS Forge
talk
(Post)
Hallo zusammen, hi all, ich habe den gleichen Fehler. Auf einem Raspberry Pi geht der Fehler weg, wenn ich alles bereinige und dann vollständig übersetze. Wenn das Projekt im Codesys Development System wieder neu geladen wird ist der Fehler aber wieder da. Mit eine Win V3 x64 PLC kann ich den Fehler nur unterbinden wenn ich auf der HMI das VUM_Login einbinde. Dieses brauche ich aber nicht, da ich die HMI für das User Management selbst gestaltet habe. Das funktioniert auch. I have the same error. On a Raspberry Pi the error goes away if I clean everything and then compile completely. When the project is reloaded in the Codesys Development System, the error returns. With a Win V3 x64 PLC I can only prevent the error if I integrate the VUM_Login on the HMI. But I don't need this because I designed the HMI for user management myself. That works too. Anyone have an idea to fix this problem. Many thanks
Last updated: 2024-07-09
Post by breiter on Frustration-Fueled Feedback on Project File Management and Git Integration
CODESYS Forge
talk
(Post)
Hi, supporting a text based storage format is on our roadmap, see https://www.codesys.com/the-system/releases-updates-lifecycle/release-plan-roadmap.html It will be an Add-On feature called "File Based Storage" for the professional developer edition. Structured text POUs will be stored as plain text. Other graphical languages will remain in an xml format. You will be able to switch the storage type for projects. Certain workflows will become easier this way. Nevertheless restrictions will remain because of CODESYS specific storage logic (for example how methods below function blocks are stored as file). So merging using our Git Integration Add-On remains the recommended workflow. A workflow involving Visual Studio Code as the main IDE is not supported. Simply because many topics like library management, task configuration or fieldbus configurators are not available for VS Code. A PLC project is a lot more than just some ST POUs. Best Regards
Last updated: 2024-10-16