Post by timvh on Device logon problem following fresh install
CODESYS Forge
talk
(Post)
In your project you selected the "CODESYS Control Win V3" as device, but the device you want to connect to is a "CODESYS Control Win V3 x64". Those are not the same. If you double click on the device during the network scan, you will get information that these are not the same, but that you can change the type in your project to the x64 bit type. Another option is to "right-click" on the device in the device tree of your project and select "update device" then select the x64 type.
Last updated: 2024-03-19
Post by wind-11 on Problem with simulation Modbus
CODESYS Forge
talk
(Post)
Hello everyone, I encountered a problem in the simulation while working. In a test project we set up a Modbus connection. We wanted to simulate this with test values. The connection also worked, but unfortunately the values are frozen and do not report any “current data”. (Picture attached) Since these are my first points of contact with Codesys and my colleague continues to work elsewhere, I was hoping that someone here might have an idea. Kind regards and thanks in advance.
Last updated: 2024-03-22
Post by ofey on EtherCAT fieldbus
CODESYS Forge
talk
(Post)
Okey, thank you! Do you think it is something in this library, that makes it possible to do the configuration in a PRG? https://content.helpme-codesys.com/en/libs/IODrvEtherCATDriver/Current/IoDrvEtherCAT.html#id1 I think the codesys modbus libraries support configuration and connection to modbus slaves without having to add the slave devices in the device tree. Just do it from function blocks inside the program. I was hoping for something similar with EtherCAT.
Last updated: 2024-04-10
Post by syjoo on Recipe Manager in PRG (3.05.13.XX)
CODESYS Forge
talk
(Post)
I'm using version 3.5.13. Is it possible to handle Recipe Manager in PRG in this environment? Can you give me a simple example? Although it has been confirmed that the functions work on Recipe Manager, they do not work properly when implemented through FB within a simple PRG. I would like to save the current value as a recipe or load the recipe's value as the current value. And I want to save the recipe as a file or load the recipe saved as a file. somebody help me. (TT)
Last updated: 2024-04-15
Post by dkugler on Codesys SVN
CODESYS Forge
talk
(Post)
Don't set on SVN. The service phase has started in March 2024 and will be discontinued in 2027. We actually use SVN and have to switch to GIT in the future. As I informed, there is no way of getting a single SVN or GIT licence. I' dont understand, why Codesys forces us customers to pay for an expensive Professional Edition paket from year to year using only one part of it! If you find a way to buy a single licence, let me know.
Last updated: 2024-04-29
Post by alez on CANOpen SDO to write VISIBLE STRING
CODESYS Forge
talk
(Post)
Hello, I am experiencing difficulties in configuring a CANopen device by sending SDOs. In particular I am attempting to write an Object Dictionary that has VISIBLE STRING as the Data Type. When I try to configure the sending of an SDO from Codesys to configure this parameter I am not allowed to enter a string value. In my particular case I am trying to change the Manufacturer Device Name ( Index 0x1008 ). Could it be that Codesys doesn't manage these types of variables?
Last updated: 2024-04-29
Post by gseidel on CNC - system goes to X=0 Y=0 before CNC file execution starts, how to avoid that?
CODESYS Forge
talk
(Post)
Hi peterned, the start position given in the CNC properties is only used if you use the compile mode OutQueue. With compile mode SMC_CNC_REF, you need to provide the start position in the IEC application. The function block SMC_NCInterpreter has an input piStartPosition. You can initialize it with the output of the forward kinematic transormation FB for your machine. In your case probably SMC_TRAFOF_Gantry2. Best regards, Georg
Last updated: 2024-04-30
Post by yannickasselin on How to sort JSON object in codesys
CODESYS Forge
talk
(Post)
Just adding: sSubscriberdata := ''; Right before your memcopy should fix the extra characters. It is because your are copying 36 characters into a string which can contain more than 36 characters and there is garbage left in the extra characters. Regarding the parsing of json, I usually build a structure that mirrors the json data and use the available methods in the IIoT library to parse the data and fill the structure.
Last updated: 2024-05-08
Post by yofi on Raspberry PI change tag only responds after stopping PLC
CODESYS Forge
talk
(Post)
Using V19 Patch 7 and 4.11.0.0 for Pi 4 Model B, My problem is whenever I change a tag e.g bool from true to false it will change in software but the pin will only go high to low after pressing stop PLC in codesys and same if i want to bring it back to high, have to login start plc change it and stop plc in order to change. any insight ? thanks
Last updated: 2024-05-25
Post by dekelec on Request for IFM ecoPlus21 installation package
CODESYS Forge
talk
(Post)
Hello, I’m looking for the ecoPlus21 development environment used with early IFM controllers (e.g., CR0020_Q firmware). We have an old project created in ecoPlus21 that cannot be opened in CoDeSys 2.3, and IFM no longer provides this software. If anyone still has the ecoPlus21 installer or knows where it can be downloaded, please let me know. It’s needed only for recovery and migration of an existing project. Thanks in advance,
Last updated: 2025-10-17
Post by timvh on OSCAT Scale_r function not working in LD 4.60 works in LAD2 on 3.5.21sp3
CODESYS Forge
talk
(Post)
It seems like a bug in FBD. Work-around: If you click on the small line between the box and the output variable and delete this, the variable is removed. When you then assign a variable again (Ctrl-A), then you will see that the line will be a bit longer. If you then select the previous variable, you will see that it works.
Last updated: 2025-10-26
Post by larboardinner on Alarm Table Issues
CODESYS Forge
talk
(Post)
Variable for Selected Alarm ID only updates when the visualization is actually configured to send the alarm’s ID back to the control. On some devices/visualization profiles this isn’t enabled by default. Make sure your Alarm Table element has “Send Selected Alarm ID” activated in the visualization properties. you could check this example: https://store.codesys.com/alarm-manager.html Geometry Dash Lite If that option isn’t available in your version, then unfortunately the “Selected Alarm Group” is the only one that updates reliably in older 3.5.x builds.
Last updated: 2025-11-17
Post by kenth1973 on MC_Phasing state explenation
CODESYS Forge
talk
(Post)
My MC_Phasing FB was stuck in iPhasingState=1 and error output HIGH on one axis. I could manually overwrite the state to 0 in the instance data. During normal run I see the state change from 0 to 10 to 100 back to 0 (maybe more states that I couldnt catch with the naked eye) But - what are the states numbers and their different explenations? This is not explained in the FB guide on codesys. (the pictures show state = 0 after I reset)
Last updated: 2025-11-22
Post by antonz on OSCAT Scale_r function not working in LD 4.60 works in LAD2 on 3.5.21sp3
CODESYS Forge
talk
(Post)
That's what I found as well Shaun. I have seen it at least in versions 3.5.21.1 and 3.5.21.3. There seems to be an issue with the FBD/LD package v4.6.0.0. The workaround proposed by Tim works but needs to be done manually on every code change/addition. For now we manually downgrade the FBD/LD package from v4.6.0.0 down to v4.5.0.0 after installation of CoDeSys. Same as you did. I hope this gets fixed on a next patch.
Last updated: 2025-11-21
Post by bschraud on Speicherbegrenzung für lokale Variablen
CODESYS Forge
talk
(Post)
Aufgrund einer Schnittstellenänderung muss ich meine Messagebuffer erheblich vergrößern. U.g. Konstante bestimmt die Größe einer Byte-Array-Definition, die in einer Struktur für 9 Botschaften verwendet wird. Ich benötige also 177372byte zusätzlichen Speicher in dem Modul in dem die Struktur als lokale Variable angelegt wird. Dynamisches Allokieren zur Laufzeit möchte ich vermeiden, damit ich nicht während des Betriebes Fehler aus dem Allokieren behandeln muss. Für ein Reservieren des Speicherbereiches habe ich in Codesys keine Einstellmöglichkeiten gefunden. Die Applikation läßt sich ohne weitere Modifikation kopilieren, scheitert aber bei der Ausführung. Welche Lösungs- oder Einstellmöglichkeiten gibt es? Bei c_w_process_result_content_len_max: WORD := 292; [INFORMATION] Größe des lizenzierten Benutzercodes: 363304 Bytes [INFORMATION] Speicherverbrauch auf dem Gerät, nicht für Lizenzierung verwendet: [INFORMATION] Speicherbereich 0 enthält Daten, Eingang, Ausgang, Speicher und Nicht-sichere Daten: Größe: 2807632 Bytes , höchste verwendete Adresse: 2159712, größte zusammenhängende Speicherlücke: 647920 Bytes (23 %) [INFORMATION] Speicherbereich 3 enthält Code: Größe: 7267784 Bytes , höchste verwendete Adresse: 5590600, größte zusammenhängende Speicherlücke: 1677184 Bytes (23 %) Übersetzung abgeschlossen -- 0 Fehler, 10 Warnungen : Bereit für Download Speicherprüfung: [WARNUNG] PAC: MC0006: Pointeradresse außerhalb des verwalteten Speichers für Eintrag GVL.htFactory._itfInstList.__Interface in Area 0, Offset 0x000033BC (0x71C15414) [WARNUNG] PAC: MC0006: Pointeradresse außerhalb des verwalteten Speichers für Eintrag __datasourcesInstancesGVL.__datasourcesInstances.dsInst._allItemsHashtable._ht.__Interface in Area 0, Offset 0x00128904 (0x71D3A95C) [WARNUNG] PAC: MC0009: Pointer to Interface zeigt nicht auf die erwartete Schnittstelle in einer FB-Instanz für Eintrag IoConfig_Globals.PiXtend_V2_L_Instance._IIoDrv.__Interface in Area 0, Offset 0x0018EC00 (0x71DA0C58) [WARNUNG] PAC: MC0009: Pointer to Interface zeigt nicht auf die erwartete Schnittstelle in einer FB-Instanz für Eintrag IoConfig_Globals.PiXtend_V2_S_DAC_Instance._IIoDrv.__Interface in Area 0, Offset 0x0018F090 (0x71DA10E8) [INFORMATION] PAC: Überprüfter Speicher für 21336 Objekte. 4 Prüfung(en) fehlgeschlagen. [INFORMATION] PAC: Check took 00:00:13.9743220. Applikation lässt sich downloaden und funktioniert auf dem Gerät. Nach der Vergrößerung: c_w_process_result_content_len_max: WORD := 20000; [INFORMATION] Größe des lizenzierten Benutzercodes: 363304 Bytes [INFORMATION] Speicherverbrauch auf dem Gerät, nicht für Lizenzierung verwendet: [INFORMATION] Speicherbereich 0 enthält Daten, Eingang, Ausgang, Speicher und Nicht-sichere Daten: Größe: 4114264 Bytes , höchste verwendete Adresse: 3164816, größte zusammenhängende Speicherlücke: 949448 Bytes (23 %) [INFORMATION] Speicherbereich 3 enthält Code: Größe: 7267832 Bytes , höchste verwendete Adresse: 5590640, größte zusammenhängende Speicherlücke: 1677192 Bytes (23 %) Übersetzung abgeschlossen -- 0 Fehler, 10 Warnungen : Bereit für Download Speicherprüfung: (gleiches Ergebnis wie vorher) [WARNUNG] PAC: MC0006: Pointeradresse außerhalb des verwalteten Speichers für Eintrag GVL.htFactory._itfInstList.__Interface in Area 0, Offset 0x000033BC (0x71C15414) [WARNUNG] PAC: MC0006: Pointeradresse außerhalb des verwalteten Speichers für Eintrag __datasourcesInstancesGVL.__datasourcesInstances.dsInst._allItemsHashtable._ht.__Interface in Area 0, Offset 0x0021DF38 (0x71E2FF90) [WARNUNG] PAC: MC0009: Pointer to Interface zeigt nicht auf die erwartete Schnittstelle in einer FB-Instanz für Eintrag IoConfig_Globals.PiXtend_V2_L_Instance._IIoDrv.__Interface in Area 0, Offset 0x00284238 (0x71E96290) [WARNUNG] PAC: MC0009: Pointer to Interface zeigt nicht auf die erwartete Schnittstelle in einer FB-Instanz für Eintrag IoConfig_Globals.PiXtend_V2_S_DAC_Instance._IIoDrv.__Interface in Area 0, Offset 0x002846C8 (0x71E96720) [INFORMATION] PAC: Überprüfter Speicher für 21336 Objekte. 4 Prüfung(en) fehlgeschlagen. [INFORMATION] PAC: Check took 00:00:14.0491831. Applikation lässt sich downloaden. Ausführen mündet in Ausnahmefehler Die Applikation läuft auf der Runtime CODESYS Control for Raspberry Pi MC SL. Die Codesys Version ist 3.5 SP20 mit allen Updates. Kennt jemand eine Speichergrenze für lokale Variablen bzw. eventuelle Einstellmöglichkeiten? Vielen Dank
Last updated: 2024-05-06
Post by smeitink on Timeout Error in Modbus Communication with WAGO PFC200 and iEM2050 Meter using 750-652 Module
CODESYS Forge
talk
(Post)
Hi all, I'm looking for help with an issue I've come across while trying to facilitate Modbus communication between a WAGO PFC200 PLC using a 750-652 communication module and an iEM2050 Series Single Phase Energy Meter. I believe to have everything wired and setup correcty, but I keep running into a "Error time out" message, and by now I don't really know what else to try. My setup is as follows: A PFC200 Wago PLC, which has 2 750-652 Serial Interfaces extension modules connected to its field bus. I'm using one of these to talk to a Schneider iEM2050 - kWh-meter over modbus. I have connected terminal 23 (A) of the iEM2050 to connector 6 (A) on the 750-652. I have connected terminal 24 (B) of the iEM2050 to connector 2 (B) of the 750-652. I'm using 200mm of twisted together wires to connected them both, and I have placed a 120 ohm resistor between A and B at both ends. I've attached relevant pinout images to this post. I then wrote a simple program that configures the Mobus port, as per the datasheet of the iEM2050. You can find an image of the relavent page attached to this post too. This is my program: PROGRAM PLC_PRG VAR Master: FbMbMasterSerial; xIsConnected: BOOL; xError: BOOL; iIndex: INT := 1; xTrigger: BOOL; utQuery : typMbQuery := ( bUnitId := 1, // The Modbus unit or slave address bFunctionCode := 4, // Function code for reading input registers uiReadAddress := 1829, // adress for the Power on off counter uiReadQuantity := 1 // Quantity of registers to read ); iStep: INT; oStatusModbus: WagoSysErrorBase.FbResult; utResponseModbus: typMbResponse; xConnect: BOOL := FALSE; delayTimer: TON; END_VAR Master( xConnect:= xConnect, I_Port:= _750_652_24_1, udiBaudrate:= 9600, usiDataBits:= 8, eParity:= WagoTypesCom.eTTYParity.Even, eStopBits:= WagoTypesCom.eTTYStopBits.One, eHandshake:= WagoTypesCom.eTTYHandshake.None, ePhysical:= WagoTypesCom.eTTYPhysicalLayer.RS485_HalfDuplex, xIsConnected=> xIsConnected, xError=> xError, oStatus=> oStatusModbus, eFrameType:= WagoAppPlcModbus.eMbFrameType.RTU, tTimeOut:= T#5S, utQuery:= utQuery, xTrigger:= xTrigger, utResponse:= utResponseModbus); delayTimer(IN := TRUE, PT := T#3S); // Use the Q output of the timer to set xConnect after the delay IF delayTimer.Q THEN xConnect := TRUE; END_IF CASE iStep OF 0: //Wacht totdat de master de poort geopend heeft IF xIsConnected THEN iStep := 1; END_IF 1: //Stuur request naar de slave xTrigger := TRUE; iStep := 2; 2: //Wacht totdat de master klaar is met het afhandelen van de request IF NOT xTrigger THEN iStep := 3; END_IF END_CASE The TON delay before opening the port is due to a an error I encountered when opening it straight away. This seems to be a bug, as described here. However, the TON solved that particular issue. I tried reading multiple registers, but like I said, I still always end up with the "Error time out". What else can I test or try at this point?
Last updated: 2024-02-24
Post by denizerm on Deploy Control SL cant find Podman
CODESYS Forge
talk
(Post)
Hello, CODESYS seems to have problems finding the container engine. In the "Deploy Control SL" window, after connecting via ssh, it simply says: [INFORMATION] Connected successfully! [INFORMATION] Successfully connected to target (192.168.4.199) [WARNING] Error detecting container architecture running podman info yields normal results. My podman info output is as follows: home/Admin$ podman info host: arch: amd64 buildahVersion: 1.35.3 cgroupControllers: - cpu - memory - pids cgroupManager: systemd cgroupVersion: v2 conmon: package: Unknown path: /usr/bin/conmon version: 'conmon version 2.1.10, commit: affab49967eb62f75d2a47398344ab053326289f' cpuUtilization: idlePercent: 99.36 systemPercent: 0.3 userPercent: 0.34 cpus: 4 databaseBackend: sqlite distribution: codename: scarthgap distribution: redagv version: 1.0.0 eventLogger: journald freeLocks: 2040 hostname: secure-automation-os idMappings: gidmap: - container_id: 0 host_id: 1000 size: 1 - container_id: 1 host_id: 100000 size: 65536 uidmap: - container_id: 0 host_id: 1100 size: 1 - container_id: 1 host_id: 100000 size: 65536 kernel: 6.6.65-intel-pk-standard linkmode: dynamic logDriver: journald memFree: 6115598336 memTotal: 8086278144 networkBackend: cni networkBackendInfo: backend: cni dns: {} ociRuntime: name: crun package: Unknown path: /usr/bin/crun version: |- crun version 1.14.3.0.0.0.8-89d44-dirty commit: 89d44467e3b410b73f2065756a12789be45b855b rundir: /run/user/1100/crun spec: 1.0.0 +SYSTEMD +SELINUX +APPARMOR +CAP +SECCOMP +EBPF +YAJL os: linux pasta: executable: /usr/bin/pasta package: Unknown version: "" remoteSocket: exists: true path: /run/podman-shared/podman.sock security: apparmorEnabled: false capabilities: CAP_CHOWN,CAP_DAC_OVERRIDE,CAP_FOWNER,CAP_FSETID,CAP_KILL,CAP_NET_BIND_SERVICE,CAP_SETFCAP,CAP_SETGID,CAP_SETPCAP,CAP_SETUID,CAP_SYS_CHROOT rootless: true seccompEnabled: true seccompProfilePath: "" selinuxEnabled: false serviceIsRemote: true slirp4netns: executable: /usr/bin/slirp4netns package: Unknown version: |- slirp4netns version 1.2.0-beta.0+dev commit: unknown libslirp: 4.7.0 SLIRP_CONFIG_VERSION_MAX: 4 libseccomp: 2.5.5 swapFree: 0 swapTotal: 0 uptime: 1h 36m 10.00s (Approximately 0.04 days) variant: "" plugins: authorization: null log: - k8s-file - none - passthrough - journald network: - bridge - macvlan - ipvlan volume: - local registries: localhost:5000: Blocked: false Insecure: true Location: localhost:5000 MirrorByDigestOnly: false Mirrors: null Prefix: localhost:5000 PullFromMirror: "" search: - localhost store: configFile: /home/serviceuser/.config/containers/storage.conf containerStore: number: 2 paused: 0 running: 2 stopped: 0 graphDriverName: overlay graphOptions: {} graphRoot: /data/containerfiles graphRootAllocated: 119952025600 graphRootUsed: 13801246720 graphStatus: Backing Filesystem: extfs Native Overlay Diff: "true" Supports d_type: "true" Supports shifting: "false" Supports volatile: "true" Using metacopy: "false" imageCopyTmpDir: /var/tmp imageStore: number: 4 runRoot: /run/user/1100/containers transientStore: false volumePath: /data/containerfiles/volumes version: APIVersion: 5.0.2-dev Built: 1711987427 BuiltTime: Mon Apr 1 16:03:47 2024 GitCommit: bb81e85a430fa95d23a15b77c717fd68bf06ebf2 GoVersion: go1.22.12 Os: linux
Last updated: 2025-10-22
Post by sunfloweeerrry on Edgelogix-rpi-1000-cm4102032 SPI port connection to PiFace I/O Driver in CodeSys.
CODESYS Forge
talk
(Post)
Please anyone help there is not a lot reference about this.
Last updated: 2023-08-21
Post by eschwellinger on Raspberry Pi Control SL MC - Restoring License not working anymore!
CODESYS Forge
talk
(Post)
you need to use 'my question ' in the CODESYS store
Last updated: 2023-08-24
Post by rossanoparis on How to configure CODESYSControl_User.cfg in order to use a specific network card for OPCUA Server
CODESYS Forge
talk
(Post)
Hello at all I'd like to know how to configure CODESYSControl_User.cfg in order to use a specific network card for OPCUA Server. In the past, I tried to ask in "Forge" about this topic, but I could find neither help nor document informations about it. Reading the file "codesyscontrol.log" I see these logs OPC UA Server Started: Hostname: NTLRPICTRL01, Port: 4840 URL: opc.tcp://NTLRPICTRL01:4840 Loopbackadapter activated. **All available networkadapters are used.** Multithreading activated. 3 workers used. My controller, which is a Linux PC, has got two network cards eth0 and eth1 I whant to use the card with name "eth0" as a server for OPCUA and keep the "eth1" free for other stuffs. Is it possible ? Best regards Rossano
Last updated: 2023-08-25
Post by marekxc on Trun off webvisu
CODESYS Forge
talk
(Post)
Click Visualisation with the left mouse button. Next click right mosue button Select Properties In window select TAB Build and Select "Exclude from Build"
Last updated: 2023-09-01
Post by eschwellinger on Project compiling error in Simulation mode
CODESYS Forge
talk
(Post)
I fear you need to update if you need a solution for this.
Last updated: 2023-09-08
Post by necatibilgin on How to access files correctly in Linux
CODESYS Forge
talk
(Post)
This may help you. https://forge.codesys.com/forge/talk/Engineering/thread/3da9ded84e/?limit=250#62b3
Last updated: 2023-09-12
Post by transmin01 on EL6751 Canopen_Manager issue
CODESYS Forge
talk
(Post)
Fixed, in the end it just required the target to be rebooted. DOH! Regards Trevor
Last updated: 2023-09-12
Post by danwoodlock on RPI zero W - cant install edge gateway
CODESYS Forge
talk
(Post)
I see now this is the wrong section. Please close this thread, and I'll repost in the runtime section.
Last updated: 2023-09-13