Post by kurtk on runtime dynamic modbus devices
CODESYS Forge
talk
(Post)
I am CODESYS neophyte getting my wheels on. My goal is to re-platform an existing PLC application written in 61131 ST I've got the majority of the code/variables in a compilable form - excluding all the IO and comms nuances I am not sure whether this the right forum An important functionality which I implemented on the other platform was totally dynamic modbus devices... Most configurations I have come across impose static MB configs in which all configured devices MUST be present and functional... I have monkeyed around with MB enough to know that herding a half dozen MB cats into a working config can be tricky. I just do them one at a time and dynamically turn them on/off in whatever combination is convenient with ID, IP, baud, parity etc being runtime tweakable. I am totally curious whether this is possible with codesys, or whether its device configuration corrals one into a static cage which requires re-building the code to support flexible variations. Best regards
Last updated: 2025-08-19
Post by ernesto881124 on ernesto881124
CODESYS Forge
talk
(Post)
Hello good morning everyone I would like to ask a question, is it possible to directly connect a device that only contains modbus RTU communication through an R-45 connector, directly to the PC? Or would you need an intermediate device to achieve communication? It would be of great help to me because I cannot achieve communication between the Codesys simulator plc and a Fuji Frenic mini VFD, please help me if anyone has had the same experience. Thank you so much
Last updated: 2023-09-13
Post by timvh on ernesto881124
CODESYS Forge
talk
(Post)
You will need a USB to RS485 converter to connect the PC to the Modbus RTU Slave Device. In Windows this converter will be recognized as Serial COM poort (e.g. COM2, or COM3, see the windows device manager to find this out). Select this port in your CODESYS application. On the PC you need to use the CODESYS Control Win (SoftPLC) to run your application. It will not work in simulation mode, because then the Modbus Communication will not be activated.
Last updated: 2023-09-14
Post by janderson on Ethercat scan for devices not picking up EL7041 as a softmotion axis
CODESYS Forge
talk
(Post)
it appears that the different revisions have different PDOs. I am currently trying to use the rev25. I have tried to use the rev24 (the device repository entry not from 'scan for devices') and i keep getting 'invalid output mapping' or 'invalid input mapping' in the ethercat log. I cant even get the bus to run from the device description that comes from 'scan for devices'...
Last updated: 2023-09-18
Post by janderson on Ethercat scan for devices not picking up EL7041 as a softmotion axis
CODESYS Forge
talk
(Post)
it appears that the different revisions have different PDOs. I am currently trying to use the rev25. I have tried to use the rev24 (the device repository entry not from 'scan for devices') and i keep getting 'invalid output mapping' or 'invalid input mapping' in the ethercat log. I cant even get the bus to run from the device description that comes from 'scan for devices'...
Last updated: 2023-09-18
Post by ofey on Device parameter - ‘ModbusTCP Configuration’
CODESYS Forge
talk
(Post)
Hi! Do anybody know how I can add and enable the parameter 'Default Modbus TCP slave' on a device? I am currently writing a program where the PLC shall be set up as a Modbus TCP client, but I dont know how to add parameters to devices in codesys. I'm pretty new to the codesys environment. The picture in the attachment is on a similar PLC project where I have not written the code. my goal is to add this parameter in another project.
Last updated: 2023-10-04
Post by naps on Welchen I-Port benötige ich?
CODESYS Forge
talk
(Post)
Hallo, ich versuche eine 750-653(konfiguriert per iocheck) über die Wago Modbus Lib einzusetzen. Ich scheitere im moment an dem Korrekten I-Port. Ich habe es mit 75x_653 und IoConfig_Globals.75x653 versucht, jedoch bekomme ich folgenden fehler: ------ Übersetzungslauf gestartet: Applikation: Device.Application ------- Code typisieren... Code erzeugen... [FEHLER] Unbenannt7: POU_1 Device: SPS-Logik: Application: C0032: Typ 'DED.CAADiagDeviceDefault(caa device diagnosis, 3.5.20.0 (caa technical workgroup))' kann nicht in Typ 'WagoTypesCom.I_WagoSysComBase(wagotypescom, 1.6.2.3 (wago))' konvertiert werden Übersetzung abgeschlossen -- 1 Fehler, 0 Warnungen : Kein Download möglich Wie kann ich den die Karte benutzen?
Last updated: 2024-10-01
Post by imdatatas on Remote to PLC device in City-B from City-A
CODESYS Forge
talk
(Post)
Hello, In an example scenario like below figure, can the developer in City-A connect to the device in City-B remotely using only "Codesys Automation Server" and "Edge Gateway" with the following structure? If no, what should be done with Automation Server for this remote connection requirement? If yes, how should it be configured for this remote connection requirement? Thank you in advance for your answers. Regards, Imdat
Last updated: 2025-02-04
Post by glutenaron on Safety drive EL6900 and mitsubishi
CODESYS Forge
talk
(Post)
Hi, Im wokring to get my servo mitsubishi mr-j5-g40-rnj1 working with my safety drive. I have as you can se in the picture Ek1100 koppler and EL6900 as safety plc. My questien is how do i connect the safety_drive to the SM3_Drive_ETC_Mitsubishi_MelServo_J5_Axis1 down below? I get the error ((Logical I/Os]: The logical device 'Safety_Drive' is not mapped to any physical device.)) but how do i map this? regard
Last updated: 2025-05-13
Post by marlutec on [ERROR] The PLCopenXML import is not possible because Device not found. Type: 89, Id: 0000 0005, Version: 3.5.10.0
CODESYS Forge
talk
(Post)
Hello every one. Now i'm instaling a Weintek cMT2108x2(v2) with IR-ETN40R. When I start to import the archive content the code of I/O remote IR-ETN40R, ocurred this error. [ERROR] The PLCopenXML import is not possible because Device not found. Type: 89, Id: 0000 0005, Version: 3.5.10.0 Can someone help me? Marcos Gentil, from Brazil.
Last updated: 2024-02-15
Post by martincapd on EWON
CODESYS Forge
talk
(Post)
I have the same problem in that I can connect to the eWon and ping the controller IP Address, however I cant connect through CodeSys. I'm using Gateway-1 which is configured to use "IP-Address: localhost" and "Port: 1217". Rather than scanning the network for devices, I enter the IP Address of the device, codesys returns a "No Device is repsonding..." message. See attached. I'm wondering if the IP-Address used Gateway-1 should be "localhost" or the WAN/LAN IP of the eWon? Thanks for the help MC
Last updated: 2024-02-21
Post by john-martin on Control SL Extension Package doubts
CODESYS Forge
talk
(Post)
Hello everybody, I'm trying to understand the SL control extension package, more specifically, the external IODriver example, because C integration is very easy and I just made my first C component successfully. Ther External IODriver has no documentation and it's not clear how to proceed. Furthermore, there is no information on how to modify the device descriptor, which is necessary to import the device into the Codesys repository. Any advice ? Thank you in advance and best regards.
Last updated: 2024-02-28
Post by nano on Is there any support for I2C on Raspberry Pi?
CODESYS Forge
talk
(Post)
hello jdj this question can be answered well with a pretty good forge documentation: https://forge.codesys.com/drv/io-drivers/doc/Generic/ u r also able to create in codesys directly an iec-code by using the i2c-interface as driver using the codesys ide and st depending on the stepperdriver, used in yöur hat, its possible that an driver is already available in the device-repository. which mcp-device is used on the hat?
Last updated: 2024-03-01
Post by mp9876 on Device User Logon
CODESYS Forge
talk
(Post)
Hi everyone, Had that problem before where I could not create another user but used the method just above and it worked great. My problem now is that I get this message when attempting to logon to the device: invalid user authentication on the target dev5, the new user created is pretty much a copy of the user 'Owner' except for the password. Any idea as to why I am always getting this "invalid user authetication on the target" message ? Using Codesys V3.5 SP19 Patch 6 + (64 bit) Regards
Last updated: 2024-03-16
Post by alez on CANOpen SDO to write VISIBLE STRING
CODESYS Forge
talk
(Post)
Hello, I am experiencing difficulties in configuring a CANopen device by sending SDOs. In particular I am attempting to write an Object Dictionary that has VISIBLE STRING as the Data Type. When I try to configure the sending of an SDO from Codesys to configure this parameter I am not allowed to enter a string value. In my particular case I am trying to change the Manufacturer Device Name ( Index 0x1008 ). Could it be that Codesys doesn't manage these types of variables?
Last updated: 2024-04-29
Post by svdpoint on Raspberry Pi Zero 2W with external Ethernet adapter
CODESYS Forge
talk
(Post)
Hello all, Somebody try to run the CodeSys at RPi Zero 2W with external ETHx device? I need to more information how youi do it, what need to it, ...etc. It is interesting to use it together with EtherCat-interface. For example I had try to connect W5500 over SPI. The eth0 is present, but does not found any EtherCat IO-device. BR
Last updated: 2024-05-25
Post by lmarmonti on Login problem with FileTransfer on Raspberry Pi 5
CODESYS Forge
talk
(Post)
Hello everyone, I have the same problem. I have a Linux-based system with CODESYS 3.6.22.20, and I need to download some files from the external web panel. I have enabled: [CmpWebServerHandlerV3] AllowFileTransferServices=1 In this case, I can see the login page when the web panel connects to the device. I can't disable the device user management access because I need to prevent software modifications. Do you have any ideas? Regards,
Last updated: 2026-08-14
Post by ph0010421 on ModbusTCP_FunctionCode06
CODESYS Forge
talk
(Post)
Hi You can add a channel to the standard Modbus TCP library with FC06. From the device tree, add Ethernet device, ModbusTCP master then finally a ModbusTCP slave (your power meter). You can add read/write channels (for any FC) in here. As you add these devices, the necessary libraries will be inserted for you. Alternatively, I have a ModbusTCP client/server library if your RT doesn't have Modbus (I think they all do these days?)
Last updated: 2026-05-18
Post by wold on CodeMeter Network Server: Keep runtime dongle local-only and export only a second CmStick
CODESYS Forge
talk
(Post)
Hello, I am running a CODESYS Control Runtime on a Raspberry Pi. Two CmSticks are connected to the same system: CmStick A - Runtime license - MultiCore license - KNX license CmStick B - Engineering / Developer licenses My goal is: The runtime on the Raspberry Pi shall use CmStick A locally. Licenses from CmStick A shall NOT be provided by the CodeMeter Network Server. Only licenses from CmStick B shall be available to remote network clients. During troubleshooting I observed that the CodeMeter Network Server collects licenses from both CmSticks. The KNX license appears to be local-only, but the runtime and multicore licenses of the same dongle are still visible through the server. I would like to know if a supported configuration exists for the following scenario: One CmStick remains strictly local to the runtime. A second CmStick on the same machine is exported through the CodeMeter Network Server. Questions: Is it possible to exclude a specific CmStick from being exported by the CodeMeter Network Server? Can this be configured via License Access Permissions (ACL), WebAdmin, or another mechanism? Can export rules be applied per CmStick, per Firm Code, or per Product Code? If supported, could you provide a configuration example or a reference to the relevant documentation? The reason for asking is that after removing a separately installed CodeMeter server component and returning to a local-only setup, the runtime licensing behaviour became stable again. Therefore I am looking for the officially supported way to keep the runtime dongle local while still providing engineering licenses from a second dongle over the network. Thank you.
Last updated: 2026-08-02
Post by jeffg on ERROR: GetNetLinkSockAndInfoByMac(): could not open netlink socket: Too many open files
CODESYS Forge
talk
(Post)
I just installed codesys runtime on a raspberry pi Cortex-A72 (ARM v8) 64-bit SoC @ 1.5GHz (Compute Module 4) I am running on Codesys control for raspberry pi 64 SL ver 4.13.0 and I keep getting a crash after about five to ten minutes. This program was running fine on a 32bit system with runtime 4.8 previously but they upgraded the panel PC cause it got smashed. Looking at the logs I see this error "ERROR: GetNetLinkSockAndInfoByMac(): could not open netlink socket: Too many open files" at the time of crash. I do have a UDP socket open for a serial to ethernet adapter and im wondering if maybe its opening a bunch of sockets and while receiving messages, Im not sending anything to the device only receiving. Below is the code used for the UDP VAR // Scale Comm fbPeerServer : NBS.UDP_Peer; ipAddress : NBS.IPv4Address; fbReceive : NBS.UDP_Receive; xPeerActiv : BOOL := TRUE; abyReceive : ARRAY [0..255] OF BYTE; sLastValidReceive : STRING(255); udiIndex : UDINT; END_VAR IF xPeerActiv AND NOT fbPeerServer.xBusy THEN ipAddress.SetInitialValue(ipAddress := gvlSettings.sIPAddres); fbPeerServer(xEnable := TRUE, itfIPAddress := ipAddress, uiPort := gvlSettings.uiPort); END_IF fbPeerServer(); fbReceive(xEnable := fbPeerServer.xBusy, itfPeer := fbPeerServer, pData := ADR(abyReceive), udiSize := SIZEOF(abyReceive)); IF fbReceive.udiCount > 0 THEN IF fbReceive.udiCount < SIZEOF(sLastValidReceive) THEN SysMem.SysMemCpy(pDest := ADR(sLastValidReceive), pSrc := ADR(abyReceive), udiCount := fbReceive.udiCount); // Set End of String sLastValidReceive[fbReceive.udiCount] := 0; END_IF END_IF If anyone as seen this I could really use some help figuring it out. I included the Log report
Last updated: 2024-09-19
Post by kuegerls on PROFINET Controller SL: WRREC remains BUSY forever, no DCE/RPC packets transmitted (RevPi Connect 5 + NORD SK205E)
CODESYS Forge
talk
(Post)
Hello , I am currently evaluating the CODESYS PROFINET Controller SL on a Revolution Pi Connect 5 and have encountered a problem with acyclic PROFINET Record Access (WRREC/RDREC). System Hardware: Revolution Pi Connect 5 Runtime: CODESYS Control 4.16.0.0 (SDK 3.5.21.10) Development System: CODESYS V3.5 SP21 (64-bit) CommFB: 3.5.17.10 ProfinetCommon: 4.6.0.0 PROFINET Controller Device: PN-Controller 4.6.0.0 PROFINET Device: NORD DRIVESYSTEMS SK205E with SK TU4-PNT GSDML: GSDML-V2.46-NORDDRIVESYSTEMS-PNT-20251016.xml Network The PROFINET network is completely separated from the office network. RevPi: eth0 → Office network eth1 → PROFINET wlan0 → Visualization The PN Controller is configured to use eth1. IP configuration: RevPi (eth1): 192.168.100.1/24 NORD Drive: 192.168.100.3 Connection is established successfully. Current Status The PN Controller reports: Controller Status = Run Online = TRUE IP Active = TRUE Connections = 1 Cyclic PROFINET IO communication works correctly. Problem I am trying to access PKW parameters via WRREC (Record Index 100). The request buffer contains: 01 14 00 04 92 00 00 00 00 00 00 which corresponds to Reference = 0x01 Request = Read Axis = 0 Parameter = 170 + 1000 Subindex = 0 Value = 0 The WRREC call is fbWRREC( REQ := xWrReq, ID := ConnectionID, INDEX := 100, LEN := 11, RECORD := ADR(TxBuffer) ); REQ is pulsed for one PLC cycle only. Observed Behaviour WRREC enters BUSY state and never finishes. Observed values: BUSY = TRUE DONE = FALSE ERROR = FALSE STATUS = 16#FFFFFFFF indefinitely. Packet Capture A Wireshark capture was taken on the PROFINET network. Observed traffic: PROFINET RT LLDP DCP Observed: successful cyclic IO Not observed: DCE/RPC Record Write Record Read RPC Bind No RPC packets are transmitted at all. Diagnostic Messages The controller repeatedly reports AR alarm.ind(err) AR CMI timeout although cyclic IO communication continues to work. Already Verified The following points have already been checked: correct Ethernet interface (eth1) correct CREATE_ID result correct Device ID correct Slot/Subslot correct GSDML correct REQ pulse RECORD buffer is larger than LEN cyclic IO communication works different Record Indices (100...104) tested Question Is there any known issue or limitation where WRREC/RDREC requests remain permanently BUSY and no RPC Record Access packets are generated? Could this behaviour be related to Runtime 4.16.0.0, PN Controller 4.6.0.0, the missing runtime license (currently running in demo mode), or any known issue with the PROFINET Controller SL? I am currently evaluating the PROFINET Controller SL and therefore the runtime is operating in demo mode. Could you please confirm whether WRREC/RDREC (acyclic Record Data services) are fully supported in demo mode, or whether a valid license is required for these services? If required, I can provide: complete project archive Wireshark capture (.pcap) GSDML online screenshots diagnostic log Thank you very much for your help. Best regards, Stefan
Last updated: 2026-07-17
Post by andre-luis on Check if Codesys runtime is on 'Running' or 'Stopped' state?
CODESYS Forge
talk
(Post)
It's already there, the service get started as default. I missed to say that sometimes it happens w/o even the system get restarted. Anyway, the main issue here is to know the state of the runtime. We collect a lot of informations about the whole system, and it would be nice to have a way to detect the runtime state.
Last updated: 2024-07-02
Post by tcarlbom on codesys sp20 opcua not working
CODESYS Forge
talk
(Post)
hi, anyone else having trouble with opc ua in codesys sp20? i get Error 'BadIdentityTokenInvalid' was returned during ActivateSession i have tried both windows x64 runtime and linux runtime. i have created a completely new codesys project for this. in each of them i have only added the symbol configuration and selected one tag. i have tried several opc ua client, like ua expert, nodejs and python. all return Error 'BadIdentityTokenInvalid' was returned during ActivateSession so the problem must be the opc ua server.
Last updated: 2024-07-03
Post by paulpotat on Can't open license manager with raspberry CM4
CODESYS Forge
talk
(Post)
Hello eschwellinger, Thanks for your answer, with this I was finally able to make it work by doing the following : install CODESYS Control for Linux ARM SL v4.13.0 uninstall CODESYS Control for Linux ARM SL v4.13.0 and make sure to select "yes" when prompted to uninstall WIBU CodeMeter Lite Runtime (v8.10.6230.501) re-install "CODESYS Control for Raspberry Pi SL" v4.13.0 It looks like the issue was probably related to the CodeMeter Runtime ? Best regards
Last updated: 2024-10-16
Post by timvh on Codesys Runtime Devie Password
CODESYS Forge
talk
(Post)
This has been moved because of security reasons. But it depends on how you start CODESYS where the project files are located (at least for Control Win from SP20). 1) If you start it through the sys tray icon, you start it as a service and the files will be located in: C:\Windows*System32\config\systemprofile\AppData\Roaming\CODESYS... (or C:\Windows*SysWOW64**\config...) 2) If you start it as a user, e.g. with a shortcut to the runtime, you can find it in: C:\Users\<your user="" name="">\AppData\Roaming\CODESYS...</your>
Last updated: 2025-02-11