Post by timvh on Version management CODESYS Forge talk (Post)
This depends on what you want to achieve with installing the latest version and how you manage your projects and repositories. Maybe you also want to update your device (right click on it to update) or maybe your device is depending on certain versions of libraries (go to the library manager in your project and download the missing libraries). An option is also to first create a projectarchive of the current project you have before you install a new version of CODESYS. Then you can open this projectarchive in the new CODESYS version. Especially if you install the latest version of CODESYS in a Sandbox.
Last updated: 2025-12-15

Post by eschwellinger on CmpCharDevice blocks gpiochip access on Raspberry Pi 5 since update from SP18 to SP21 CODESYS Forge talk (Post)
yes, this is a known issue which will be fixed with 3.5.23.0 .. soll will take some time. You need to switch back the runtime running not as dedicated user, like it was before 4.21.0.0 How to switch back you'll find here. ('Change service user' in the deploy tool) https://content.helpme-codesys.com/en/CODESYS%20Control/_rtsl_linux_dedicated_user.html to sumerize both problems: 1. missing entries in CODESYSControl_Usr.cfg was the problem on Raspberry PI Runtime 2. Arm64 SL is running rootless by default since 4.21.0.0 ( Pi not by default you need to switch manually if needed due this GPIO restriction)
Last updated: 2026-07-22

Post by ranadheer on Assistance for MQTT configure with external broker (Mosquitto) CODESYS Forge talk (Post)
Hi everyone Am trying to make establish MQTT connection , where am using IIOT example for this as a demo mode. where i had given IP-address of of local Linux application as a 172.31.239.67 and port number as 1883 in the PLC_PRG itself, and preparing the publish message by manually as " this is from published message", and this should receive at the subscriber side. Aim: To make communicate external publisher to the CODESYS by using MQTT protocol. By any chance having reference documents about this implementation please share here. and suggest the process to make it possible. I had uploaded reference project file after updating address in th PLG_PRG, kindly assist to configure with the broker
Last updated: 2025-12-03

Post by jroddball79 on PM556-TP-ETH — How to change IP address without overwriting the PLC program? CODESYS Forge talk (Post)
Still looking for a solution. I have gathered more information that might help: Device: ABB AC500 PM556-TP-ETH Firmware version: 2.4.2.14993 (dated 2014) Open ports confirmed: 502 (Modbus TCP), 1200 and 1201 (CODESYS runtime). SSH (22) and HTTP (80) are not reachable. No SD card in the PLC. I can connect via Automation Builder using the current IP and Online Login works, but I have no original source project available. Automation Builder requires a full PLC download to apply IP changes, which we want to avoid as it would overwrite the running program. Any guidance on how to change the IP without a full download would be greatly appreciated. I am also open to solutions using third party tools, DCP protocol, or scripts. Thank you
Last updated: 2026-05-22

Post by hammer on Cartesian XY Chart — 2-D array binding: "Element to use" enumerates the wrong dimension CODESYS Forge talk (Post)
Title: Cartesian XY Chart — 2-D array binding: "Element to use" enumerates the wrong dimension; documented example (Dialog: XY Chart Configuration, "Two-dimensional array of base type REAL") appears transposed Product / version: CODESYS Development System V3.5 SP21 Patch 40 (3.5.21.40). Cartesian XY Chart visualization element (System_VisuElemXYChart / VisuElemXYChart). Summary: When a curve's Data X/Data Y is bound to a two-dimensional array, the element treats the last array dimension as the per-point record (the one selected by "Element to use") and iterates the first dimension as the sequence of curve points. The online documentation's worked example has the dimensions in the opposite order, so following it produces a non-functional curve and a nonsensical "Element to use" list. Steps to reproduce (fails — matches the documented layout): 1. Declare aData : ARRAY[0..1, 0..4095] OF LREAL; (2 data sets × 4096 points, i.e. first dimension = set, second = point). 2. In XY Chart Configuration, bind a curve's Data X (and Y) Variable to this array. 3. Observe the "Element to use" combobox. Actual result: The "Element to use" combobox lists 4096 entries (the indices of the second dimension) instead of 2 (the data sets in the first dimension). Selecting a row does not produce the expected curve; at most a single/degenerate point is plotted. Steps to reproduce (works — transposed): 1. Declare aData : ARRAY[0..4095, 0..1] OF LREAL; (points first, set second). 2. Bind Data X/Y to this array; "Element to use" now correctly lists [0] and [1]. 3. Populate aData[point, set] and the curve plots as expected. Expected result: Either the documented example should select the data set from the first dimension (as its [1]/[2] "Element to use" implies), or the documentation should state that the last dimension is the record dimension (stride) and the first dimension is the point sequence — consistent with how the element actually behaves. Analysis: The behavior is self-consistent if the element always walks a single array by a fixed byte stride, reading one element per point — the same mechanism as the documented "one-dimensional array of a DUT" case, where it strides by SIZEOF(DUT) and "Element to use" picks the member offset. For a 2-D array the record is the last dimension: to plot column/set c it starts at [0, c] and strides by the last-dimension length to reach [1, c], [2, c], … (row-major layout makes this a contiguous column walk). Under that rule, ARRAY[0..N, 0..1] is correct (record length 2 → "Element to use" [0]/[1]), and the documented ARRAY[1..2, 1..50] with "Element to use" [1]/[2] is transposed. Documentation reference: Dialog: XY Chart Configuration → Data X / Data Y → "Example: Two-dimensional array of the base type REAL" (ARRAY[1..2, 1..50], Element to use [1]/[2], "100 array values are displayed"). This example does not plot as described in 3.5.21.40; transposing to ARRAY[1..50, 1..2] does. Request: Please confirm whether this is (a) a documentation error (example dimensions reversed) or (b) an element defect (combobox enumerates the wrong dimension). Either way, a corrected example plus an explicit statement of which dimension is the point sequence vs. the record/stride dimension would prevent others from hitting this. Two separate 1-D arrays for Data X and Data Y work correctly and are unaffected.
Last updated: 2026-08-14

Post by jari-koivuluoma on Comparing between SP19 patch 5 and patch 7 CODESYS Forge talk (Post)
Hello. Has anyone here used project compare tool across different versions of Codesys? I tried the compare of the title but it does not seem to do much. It lets me choose the project files and then seems to be comparing but no results are ever shown. If the compare tool cannot be used how else would I keep 2 nearly identical projects in sync when the versions differ? On the other hand it might be possible to just have one project but then I would need to use the older codesys with older target device description to develop for devices that have newer device description. Codesys will let me do that but its not recommending it. Any advice?
Last updated: 2026-08-20

Post by timvh on EXCEPTION [watchdog] how to find position cause CODESYS Forge talk (Post)
Monitor what your current cycle time is (in the Task Configuration when you are online). If this is sometimes close to 200ms, then change your code (e.g. limit the loops, or prevent copying a lot of data between objects). Or just set the Watchdog time (or sensitivity) higher if you don't care that it sometimes takes longer than 200ms. If you want to find out which objects in your application consume the most time, then buy a PDE (Professional Developer Edition) license. With this you get a license for the Profiler. This can help you a lot to find the root cause, because it will create a nice overview of all objects, their calls and the time (percentage) it takes to execute it.
Last updated: 2026-02-09

Post by dat422 on CODESYS crashes when adding standard OPC UA Information Model to Communication Manager CODESYS Forge talk (Post)
Hi all, I am experiencing a problem when trying to add a standard OPC UA Information Model to the Communication Manager. When I try to add the following standard information models to a new or existing project http://opcfoundation.org/UA (15.07.2020) http://opcfoundation.org/UA/DI (02.06.2020) CODESYS crashes every time during the process. Adding an OPC UA Server itself works without any problem. The crash only happens when adding the standard OPC UA Information Model. CODESYS version: CODESYS V3.5 SP20 Patch 4 (64 bit) Has anyone experienced the same issue or knows a possible workaround? Thank you in advance.
Last updated: 2026-03-19

Post by vstrom on Codesys v3.5.22.10 - Fail to create a project Archive CODESYS Forge talk (Post)
Hi to all, I've created a project using the File->New Project-> Standard Project command. Then I've add the object "Visualization Manager" and then tried to create a project archive (File->Project Archive->Save Archive), but it fails with the error "Access to the path 'C:\Program Files\CODESYS 3.5.22.10\CODESYS\Common\3hxi4iod.put' is denied". The idicated file don't exist. First time of use of the new Codesys versionù, I've reinstalled the developement software but nothing change. If I don't add the Visualization part, the archive is created, it's seems to be a problem with the HMI part. Any ideas? Thanks
Last updated: 2026-04-22

Post by williamcorlin on The future and proper use of CAA.BOLT, CAA.SEMA,.. CODESYS Forge talk (Post)
I've been moving in the same direction. For new libraries, I'm trying to minimize dependencies on APIs that look like they're being phased out unless the documentation explicitly recommends them. For synchronization primitives like CAA.BOLT and CAA.SEMA, I'd love to see an official replacement or abstraction layer that's guaranteed to remain stable across runtimes. That would make library development much cleaner than relying on platform-specific SysLib* implementations or conditional compilation everywhere. Until there's clearer guidance, my approach has been to isolate the locking mechanism behind a small wrapper interface. If CODESYS changes the recommended API in the future, only that wrapper needs to be updated instead of every library that uses it. It isn't perfect, but it's made maintenance much easier. https://forge.codesys.com/forge/talk/Engineering/thread/e6c20a740e/ https://zapgames.io/
Last updated: 2026-07-14

Post by rossanoparis on Upgrading CODESYS runtime from v4.7 to v4.9 using a bash script leads to lose the licences stored in the soft container CODESYS Forge talk (Post)
System information - Controller: KUNBUS RevPi CONNECT-S - OS: Linux buster 32bit 5.10.103-rt62-v7l #1 SMP PREEMPT_RT armv7l GNU/Linux - CODESYS v3.5 SP19 Patch 2 I'm facing a problem related to codesys licences using a procedure based on a bash script. Such bash script detect the presence of new .deb files and install them on system. My automation solution don't allow to be maintained by dedicated personal, thus even the CODESYS runtime SW must be installed using an "automatic" procedure instead of using the CODESYS tool. remark I've been using the following procedure since the runtime v4.5 without any issue. Before installing the new runtime packages, I need to copy the file CODESYSControl_User.cfg (here attached) because of new section which is necessary to add in order to allow some folders to be written by CODESYS runtime v4.9 Up to now, this has been unnecessary, this is the main difference between my previos bash file and the new one. remark If I skip this action, everythings goes fine, but my CODESYS application can't work as it needs to access some folders on controller's file system. Process - Before the procedure: the licenses are OK (see attached file lic-01.png) - After the procedure: the new CODESYS runtime version is correctly installed, but the software container with v1.19 and all licences disappear (see attached file lic-02.png) This is the synthetic content of bash script I'm using. # Stop runtime sudo service codesyscontrol stop sudo service codesysedge stop # Move the new CODESYSControl_User.cfg file # New configuraton with folders declared sudo mv -f CODESYSControl_User.cfg /etc # Install runtime package echo N | sudo apt-get install -y --allow-downgrades codesyscontrol_raspberry_4.9.0.0_armhf.deb # Install edge gateway package echo N | sudo apt-get install -y --allow-downgrades codesysedge_edgearmhf_4.9.0.0_armhf.deb # Reboot controller sudo reboot Thanks in advance
Last updated: 2023-09-19

Post by manuknecht on Opening a Dialog on a specific Client from ST CODESYS Forge talk (Post)
I managed to find a solution that seems to work reliably. As the VU.Globals.CurrentClient-filter accesses the CURRENTCLIENTID or at least a similar, internal variable it can only be used if called from a certain client (e.g. from a button in a visualization). My solution works by implementing a new client filter that compares the client ID of all clients to the ID of the last client that was used. The variable containing the data of the last client is defined as: G_LastClient : VU.IVisualizationClient; // Copy of last client that detected click This last client is then updated every time a button is pressed using the Execute ST-Code input configuration of the button: G_LastClient := VU.PublicVariables.Clients.Current; Next, I created a function block that implements the client filter interface as so: FUNCTION_BLOCK FB_LastClientFilter IMPLEMENTS VU.IVisualizationClientFilter VAR_INPUT END_VAR VAR_OUTPUT END_VAR VAR END_VAR Then i added a method to the FB called IsAccepted which is used to filter out the client. When creating the method, it should automatically be filled with the according variable declaration, as it is defined in the interface: (* For every client can be desided, if it is accepted. ``TRUE``: Client is accepted*) METHOD IsAccepted : BOOL VAR_INPUT (* The client, to check*) itfClient : VU.IVisualizationClient; END_VAR Now the client can be compared to the last used client as such: // check if clientID corresponds to clientID of last recorderd client IF itfCLient.ClientId = G_LastClient.ClientId THEN IsAccepted := TRUE; ELSE IsAccepted := FALSE; END_IF To make use of this custom client filter, initialize a variable with the client filter: LastClient : FB_LastClientFilter; // Client filter to find last used client Then use this client filter when opening or closing a dialog from ST: fbOpenMyDialog(itfClientFilter:=LastClient,xExecute:=TRUE,sDialogName:='VIS_MyDialog_DLG');
Last updated: 2023-09-27

Post by artplc on 3.5 P20 hangs - no response CODESYS Forge talk (Post)
Subject: Solution: CODESYS Freezes Linked to Large Symbol Configuration (OPC UA) Hello everyone, I was experiencing the same problem as many here: CODESYS (v3.5 SP20+) freezing during compilation and download, especially on projects that use OPC UA for SCADA. The only workaround was to run Build > Clean all before every download. I believe I have found the root cause and a permanent solution. The Problem: The issue is directly related to a large Symbol Configuration. In my project, I only need about 700 tags for OPC UA, but the Symbol Configuration list was showing over 250,000 tags. This is because it automatically includes all variables from Global Variable Lists (GVLs) and other memory areas. When any static variable is changed, the IDE tries to rebuild this enormous list, causing it to freeze for several minutes. The Solution: Instead of letting CODESYS export every variable by default, you can use a pragma to tell it which variables or GVLs to exclude from the symbol export process. Place the following pragma at the top of any GVL or data structure that you do not want to be part of the symbol configuration: 1 {attribute 'symbol' := 'none'} 2 VAR_GLOBAL 3 // All variables in this GVL will now be excluded from the 4 // Symbol Configuration by default. 5 InternalVariable1 : INT; 6 InternalVariable2 : BOOL; 7 END_VAR After adding this pragma to all the GVLs that were not needed for OPC UA, the number of tags in my Symbol Configuration dropped to the correct amount. The compilation and download process is now fast again, with no freezing. This method is much more efficient than manually managing the symbol list in the editor. I hope this helps others who are facing this frustrating issue. Best regards.
Last updated: 2025-08-10

Post by full0pullpolen on Device User Logon CODESYS Forge talk (Post)
The following guide describes how you can adapt the user management for the first time in a project. It deals with the definition of a user and a group to which he belongs. Requirement: the project for which the user management is to be set up is opened. There is no adapted user configuration yet. Select Project Settings ‣ Users and Groups and then the Users tab. The user Owner is already created by default. Click on Add. ⇒ The dialog box Add User appears. Enter a login name, for example ‘Dev1’, and a password. Leave the option Activated activated. Click on OK. ⇒ On creating a group for the first time, CODESYS now requests you to authenticate yourself to perform this action. In this case, enter ‘Owner’ as the current user. Do not enter a password, just click on OK. The user Dev1 appears in the list and is automatically a member of the group 'Everyone'. Change to the tab Groups, in order to add the user to a new group. ⇒ The groups Everyone and Owner have already been created. Click on Add in order to open the dialog box Add Group. Specify at least one name for the new group, for example ‘Developers’. Activate the checkbox next to the entry User ‘Dev1’ in the field Members. Click on OK. ⇒ The group Developers now appears with has user member 'Dev1'. Switch to the Users tab. ⇒ The user Dev1 now appears as a member of the groups ‘Everyone’ and ‘Developers’.
Last updated: 2024-01-24

Post by full0pullpolen on Device User Logon CODESYS Forge talk (Post)
The following guide describes how you can adapt the user management for the first time in a project. It deals with the definition of a user and a group to which he belongs. Requirement: the project for which the user management is to be set up is opened. There is no adapted user configuration yet. Select Project Settings ‣ Users and Groups and then the Users tab. The user Owner is already created by default. Click on Add. ⇒ The dialog box Add User appears. Enter a login name, for example ‘Dev1’, and a password. Leave the option Activated activated. Click on OK. ⇒ On creating a group for the first time, CODESYS now requests you to authenticate yourself to perform this action. In this case, enter ‘Owner’ as the current user. Do not enter a password, just click on OK. The user Dev1 appears in the list and is automatically a member of the group 'Everyone'. Change to the tab Groups, in order to add the user to a new group. ⇒ The groups Everyone and Owner have already been created. Click on Add in order to open the dialog box Add Group. Specify at least one name for the new group, for example ‘Developers’. Activate the checkbox next to the entry User ‘Dev1’ in the field Members. Click on OK. ⇒ The group Developers now appears with has user member 'Dev1'. Switch to the Users tab. ⇒ The user Dev1 now appears as a member of the groups ‘Everyone’ and ‘Developers’.
Last updated: 2024-01-24

Post by full0pullpolen on Device User Logon CODESYS Forge talk (Post)
The following guide describes how you can adapt the user management for the first time in a project. It deals with the definition of a user and a group to which he belongs. Requirement: the project for which the user management is to be set up is opened. There is no adapted user configuration yet. Select Project Settings ‣ Users and Groups and then the Users tab. The user Owner is already created by default. Click on Add. ⇒ The dialog box Add User appears. Enter a login name, for example ‘Dev1’, and a password. Leave the option Activated activated. Click on OK. ⇒ On creating a group for the first time, CODESYS now requests you to authenticate yourself to perform this action. In this case, enter ‘Owner’ as the current user. Do not enter a password, just click on OK. The user Dev1 appears in the list and is automatically a member of the group 'Everyone'. Change to the tab Groups, in order to add the user to a new group. ⇒ The groups Everyone and Owner have already been created. Click on Add in order to open the dialog box Add Group. Specify at least one name for the new group, for example ‘Developers’. Activate the checkbox next to the entry User ‘Dev1’ in the field Members. Click on OK. ⇒ The group Developers now appears with has user member 'Dev1'. Switch to the Users tab. ⇒ The user Dev1 now appears as a member of the groups ‘Everyone’ and ‘Developers’.
Last updated: 2024-01-24

Post by mp9876 on Device logon problem following fresh install CODESYS Forge talk (Post)
All screenshots are enclosed in MS Word document. NOTE; 4 questions features at the end. Any assistance would be greatly appreciated! Hi everyone, I am still having device logon problem following a fresh install Here are the STEPS I went through following a FRESH CODESYS Win 64 3.5.19.60 install on a different computer. ‘Gateway not configured properly’ when attempting to REFRESH from the Users and Groups. Then did Gateway manage and confirmed it was ok: This message popped out as it was a fresh install: YES then: Initially went with Administrator twice (user & password) but it did not like it. No device is responding to …: Continued by setting a new user Pressed OK and obtained the following message: Stopped and Restarted PLC at that point: Obtained the following: Attempted to login a 2nd time without success. Then I scanned the network to see if matching device can be detected: Only way to get it detected was to remove the tick in the ‘Hide non-matching devices…’ Attempted a WINK but got a return like this one: REFRESH either @ Users and Groups or @ Access Rights returns: Then created user ‘mp’ at Project level ang logged in: Understandably device user mp9876 was not valid for the Project. Device information A few questions comes to my mind following these connection attempts: 1- Gateway not configured properly message pops out because of a non-compatible device ? 2- Why would the device not be compatible ? 3- Any way to make the device compatible ? 4- Any ideas on how to get this connectivity problem to the device solved ?
Last updated: 2024-03-17

Post by yannickasselin on Lenze i950 Servo and WAGO PFC200 CODESYS Forge talk (Post)
I don't have time to go through the whole manual but as I said earlier, the servo drive does not support any of the modes needed for SoftMotion Light to work. If you want to use the full SoftMotion, you could use SMC_Homing function block to do the homing. This function block does not use the Homing Mode. It still uses the CSP mode and does the logic in Codesys runtime instead of in the servo drive. Read the documentation about it to see if it fits your needs. But if your controller only supports SoftMotion Light, I am afraid you will not be able to use the i950. I do a lot of motion stuff with different servo brands. Some support all the modes needed for SoftMotion Light and some don't. You really need to make sure the modes are supported before choosing a brand over another. I tend not to use brand specific controllers in order not to be limited by their supported features. I usually choose a PC (Linux or Windows) and install the Codesys runtime and licences myself. This is the most flexible way to use Codesys in my opinion. Depending on how many axes are needed in your project, a full SoftMotion license may not be more expensive than SoftMotion Light because SoftMotion is available as Application based license whereas SoftMotion Light is not. But of course, SoftMotion is harder on the CPU than SoftMotion Light.
Last updated: 2026-02-13

Post by gilbert-mh on CAA net base TCP client cause PLC to crash - Kernel message : N0HZ_local_softirq_pending 80 CODESYS Forge talk (Post)
Hello all, I have been trying to implement a TCP client on a Festo PLC (CPX-E-CEC-M1) and it looks like it works well except that after some time (greatly varies between a few hours to more than 100h) my PLC crash. When I look into the log file the only thing I see is that before the crash happens a few kernel warnings : N0HZ_local_softirq_pending 80 and then the crash. I've looked into this warning and from what I could find on the net it seems that this is warning is triggered when the ethernet link is down. I've tried to correct this bug for quite some time and what I know is that : - The crash is caused by my TCP client, when I remove it from my code I see no crash - The crash happens more quickly the more the TCP client is used. - The time before the crash is not directly proportional to the number of communications or their size. But it looks like it is just more likely to happen if the client connect to the server at a higher frequency. - The precedent observation makes it seem unlikely that the crash is caused by some memory overflow because then the crash speed would be more proportional to the amount of data exchanged. SO from these observations, I believe that the crash could be caused by the PLC trying to connect to a server while there is some kind of issue with the ethernet link resulting in the PLC getting stuck in some indefinite state and making it crash. This still seems a bit unlikely to me because if the ethernet is down it simply shouldn't be able to contact the server and the communication would just fail which doesn't cause my PLC to crash. Has anyone encountered the same kind of problem (with the same kernel message) ? I am pretty sure the warning is not the direct cause of the crash but just an indicator that something is wrong with my PLC. Thanks in advance
Last updated: 2024-01-12

Post by pppn on Issue with Forward Open Connections in Ethernet/IP Protocol Stack in Codesys CODESYS Forge talk (Post)
Hello, I am facing an issue with my Ethernet-based project in Codesys. My product was functioning well until I modified the protocol stack and uploaded it to my device. Here are the details of my problem: Project Setup: I am working on an Ethernet-based project to test my product. The project was running without issues before modifying the protocol stack. Issue: After modifying the protocol stack and uploading it to my device, I am encountering an error in Codesys related to the forward open connections. Error status: connection failure, extended: connection in use or duplicate forward open. According to the Ethernet/IP protocol in codesys, there are three forward open connections that need to be established. The first two connections are opening without any issues. The third connection, which is an input-only connection, is causing problems. The error message indicates that the connection is already open. Debugging Attempts: I have extensively debugged the protocol stack and found no issues. The product works well when tested with EIP tools but not with Codesys. Exclusive owner connections are working correctly, and only the input-only connection is problematic. Wireshark Traces: Wireshark traces show that the third connection attempts to open but reports that it is already open. Steps to Reproduce: Modify the protocol stack and upload it to the device. Attempt to establish three forward open connections in Codesys. Observe the error on the third connection (input-only). Request: I would appreciate any suggestions or guidance on how to resolve this issue. If there are specific settings or configurations in Codesys that I need to check, please let me know. Additionally, if there are known issues or workarounds related to this problem, I would be grateful for the information. Attachments: Wireshark traces showing the connection attempts and errors Screenshots of the error messages in Codesys codesys version: CODESYS V3.5 SP16 Patch 3 + 64 bit
Last updated: 2024-06-25

Post by pppn on Issue with Forward Open Connections in Ethernet/IP Protocol Stack in Codesys CODESYS Forge talk (Post)
Hello, I am facing an issue with my Ethernet-based project in Codesys. My product was functioning well until I modified the protocol stack and uploaded it to my device. Here are the details of my problem: Project Setup: I am working on an Ethernet-based project to test my product. The project was running without issues before modifying the protocol stack. Issue: After modifying the protocol stack and uploading it to my device, I am encountering an error in Codesys related to the forward open connections. Error status: connection failure, extended: connection in use or duplicate forward open. According to the Ethernet/IP protocol, there are three forward open connections that need to be established. The first two connections are opening without any issues. The third connection, which is an input-only connection, is causing problems. The error message indicates that the connection is already open. Debugging Attempts: I have extensively debugged the protocol stack and found no issues. The product works well when tested with EIP tools but not with Codesys. Exclusive owner connections are working correctly, and only the input-only connection is problematic. Wireshark Traces: Wireshark traces show that the third connection attempts to open but reports that it is already open. Steps to Reproduce: Modify the protocol stack and upload it to the device. Attempt to establish three forward open connections in Codesys. Observe the error on the third connection (input-only). Request: I would appreciate any suggestions or guidance on how to resolve this issue. If there are specific settings or configurations in Codesys that I need to check, please let me know. Additionally, if there are known issues or workarounds related to this problem, I would be grateful for the information. Attachments: Wireshark traces showing the connection attempts and errors Screenshots of the error messages in Codesys codesys version: CODESYS V3.5 SP16 Patch 3 + 64 bit
Last updated: 2024-06-25