Post by kevinl on RevPi Connect RS485 CODESYS Forge talk (Post)
I figured this out on my own with this logic: usually the Serial port on a Raspberry pi is on /dev/ttyUSB0 then you need to set linux.DeviceFile=/dev/ttyUSB in codesys you then must set com port to 1 so i assumed codesys subtracts 1 from the number and adds this to the filename... (in code it would look like this: var comPort : byte := '1'; linuxDevice : string := '/dev/ttyUSB'; filename : string; end_var filename := concat(linuxDevice, (to_string(comPort-1)); filaname then is /dev/ttyUSB0 RevPi uses ttyRS485 as Serial port so you must remove the last number from the name and set the com port to this number +1 i hope this is understandable ;-)
Last updated: 2023-12-11

Post by struccc on Release SP20 - Changes in behaviour? CODESYS Forge talk (Post)
Dear all, I've just started to migrate some of my ancient projects to SP20. There is one strange error (?) I have noticed so far. In a method call, depending on the circumstances I would like to return reference to an object, or an invalid reference: METHOD Add_EVT_OUT : REFERENCE TO FB_MSG VAR END_VAR IF __ISVALIDREF(refMSG_Entry) THEN Add_EVT_OUT REF= MANAGER.AddMsg_EVT_OUT( refMSG_Entry, _Get_EVT_Message(MSG_EVENT.OUT), _Get_EVT_AddCode(MSG_EVENT.OUT) )^; ELSE Add_EVT_OUT := 0; END_IF So far setting a reference variable to 0, did this. But now, the expression Add_EVT_OUT := 0; gives an error: [ERROR] DB_WTP_370: Add_EVT_ACK MSG_TRIGGER_EXT: C0032: Cannot convert type 'BIT' to type 'REFERENCE TO FB_MSG' Naturally... I can write: Add_EVT_OUT := DWORD#0; But is this the correct way? Is there any constant I could use instead, like "NULL"? Or this is totally wrong and to be avoided?
Last updated: 2024-03-24

Post by paro on Modbus Client Request Not Processed CODESYS Forge talk (Post)
Hi, works in my case if I increase the timeout! to_udint(t#100ms) -> 100 -> 100us.. FUNCTION_BLOCK MODBUS_master_example_ST VAR initDone : BOOL := FALSE; aIPAddress : ARRAY [0..3] OF BYTE := [127,0,0,1]; clientTcp: ModbusFB.ClientTcp; // buffer to read input registers aDataInputRegisters : ARRAY[0..9] OF UINT; // some client requests clientRequestReadInputRegisters: ModbusFB.ClientRequestReadInputRegisters; xExecute: BOOL; uistart: UINT := 100; udiTimeout1: UDINT; END_VAR IF NOT initDone THEN initDone := TRUE; // configure clientTcp clientTcp(aIPaddr:=aIPAddress, uiPort:=502, udiLogOptions := ModbusFB.LoggingOptions.All); // configure clientRequestReadInputRegisters clientRequestReadInputRegisters(rClient:=clientTcp, uiUnitId:=1, udiTimeout:=1000000); // 1sec END_IF // call the client FB's clientTcp(); clientRequestReadInputRegisters(rClient:=clientTcp,xExecute := xExecute AND NOT clientRequestReadInputRegisters.xBusy ,uiStartItem:=uistart, uiQuantity:=3, pData:=ADR(aDataInputRegisters[0]));
Last updated: 2024-05-30

Post by zer0g on Modbus Client Request Not Processed CODESYS Forge talk (Post)
I'm using the code bellow which is based on the Codesys example: FUNCTION_BLOCK MODBUS_master_example_ST VAR initDone : BOOL := FALSE; aIPAddress : ARRAY [0..3] OF BYTE := [127,0,0,1]; clientTcp: ModbusFB.ClientTcp; // buffer to read input registers aDataInputRegisters : ARRAY[0..9] OF UINT; // some client requests clientRequestReadInputRegisters: ModbusFB.ClientRequestReadInputRegisters; xExecute: BOOL; END_VAR IF NOT initDone THEN initDone := TRUE; // configure clientTcp clientTcp(aIPaddr:=aIPAddress, uiPort:=502, udiLogOptions := ModbusFB.LoggingOptions.All); // configure clientRequestReadInputRegisters clientRequestReadInputRegisters(rClient:=clientTcp, uiUnitId:=1, udiTimeout:=TO_UDINT(T#1000MS)); END_IF // call the client FB's clientTcp(); clientRequestReadInputRegisters(rClient:=clientTcp,xExecute := xExecute AND NOT clientRequestReadInputRegisters.xBusy ,uiStartItem:=2, uiQuantity:=3, pData:=ADR(aDataInputRegisters[0])); As you can see the clientTCP is called cyclically with the same result.
Last updated: 2024-05-30

Post by installwhat on C0077 on one machine but not another CODESYS Forge talk (Post)
I have a version of codesys 3.5.16 on my local machine and a vm. The local machine has loads of codesys versions and libraries installed etc. I can open the FPosCR_Example_Project_SP16_patch1 project on my vm without any errors. On the local machine I get the error C0077: unknown type IoDrvEthercatLib.ETC_CO_SdoWrite. I can, on the local machine, declare a var of type IoDrvEthercatLib.ETC_CO_SdoWrite and include it in the code without adding an extra error. The problem only seems to affect the library. This is seems more an issue with my codesys set up rather than something with festo. I would like to know the possible causes. I understand most of the library manager features but it's not clear how to find the cause. Thanks
Last updated: 2024-06-11

Post by joschi2804 on Licensing info not available. CODESYS Forge talk (Post)
Hi, maybe this fixes your problem. At least this was our issue back then. We tried to run the codesys runtime environment on an embedded Linux system. The problem on our side was that we changed the WORKDIR directory in the /etc/init.d/codesyscontrol script to /home/user/codesys, but we forgot to copy all files (including the hidden files) from the initial WORKDIR (I am not sure but I guess the initial WORKDIR was /var/opt/codesys) to the new one. After copying those files and restarting codemeter and codesyscontrol, we were able to upload licenses. Hope this help BR Josef
Last updated: 2024-07-10

Post by ucconversions on displaying all incoming CAN bus messages CODESYS Forge talk (Post)
Hello Im using CAN API Im receiving CAN messages with no problem. below is my code. METHOD ProcessMessage VAR_IN_OUT ( Incoming message ) Message : CAN.RxMESSAGE; END_VAR VAR i: USINT; END_VAR recvCANid := Message.udiCanID; IF recvCANid = 16#18FF8247 THEN UserVarGlobal.g_countMsg_RPMset := UserVarGlobal.g_countMsg_RPMset + 1; FOR i := 0 TO 7 DO myDataFF82[i] := Message.abyData[i]; END_FOR END_IF but in this way I can only display CAN messages which I know its ID. I want to display all incoming CAN messages for example first incoming CAN message - I assign it into a variable Message1. second incoming CAN message - I assign it into a variable Message2. third incoming CAN message - I assign it into a variable Message3. Can you give me guidance? Thank you BR
Last updated: 2024-07-18

Post by askic on Generate FBs from source CODESYS Forge talk (Post)
Hello, I'm coming from Siemens (TIA) world and currently learning Codesys. I'd like to know if there is an option to add external txt file with ST code for creation of a function block and then use this file as a source file from which FB will be generated? For example, in TIA, there is an option add external source file to the project structure and then use option "Generate blocks from source". This would create a FB. Does Codesys have something similar? This external source file would look like this: FUNCTION_BLOCK Scaling VAR_INPUT x, k, n : REAL; END_VAR VAR_OUTPUT y : REAL; END_VAR VAR END_VAR y := k*x+n; END_FUNCTION_BLOCK
Last updated: 2024-07-31

Post by alimans on OPC-UA Server, Symbol Set: Raise an error: Object reference not set to an instance of an object. CODESYS Forge talk (Post)
Hi everyone, I just created a very simple library without any code and, added it to my very simple project. after adding this library, I get an error when I try to open "Symbol Set" in "OPC UA Server" in "Communication Manager". Here is the code of my POU in the library: FUNCTION_BLOCK POU VAR eCommand : (CMD_NONE:=0, CMD_RESET:=-1) INT := CMD_NONE; END_VAR Attached is the error that I get. I also noticed that by removing the enumeration variable above (eCommand), I can open the "Symbol Set" again. Anybody has any idea why this error is raised and how could I use enumeration variables without error in "OPC UA Symbol Set"?
Last updated: 2024-08-08

Post by gilbertamine on Comparing Arrays of structure CODESYS Forge talk (Post)
Hi Everybody, I'm looking for a simple way of comparing two array of a structure. My structure is define like this : TYPE Positions_T : STRUCT PosX: DINT; PosY: DINT; PosZ: DINT; END_STRUCT END_TYPE I have multiples Var : ARRAY [0..220] OF Positions_T, that I need to compare quickly. I don't really want to do a Loop that goes by every 220 points and compare each one of them so I was wondering if there is another way. I came accross the MEM.Compare function, but it require to know the size in Bytes of the memory, and I don't know how to do that... Has anybody an idea on how to do the comparing easily ? Thanks in advance
Last updated: 2024-08-22

Post by dkugler on Webvisu client connection monitoring CODESYS Forge talk (Post)
you can give this code snippet a try. It's extracted and simplyfied from my code: Install VisuElemBase lib if not installed yet. Execute in visu task: VAR pClientData : ARRAY [-1..100] OF POINTER TO VisuElemBase.VisuStructClientData; END_VAR VisuElemBase.g_ClientManager.BeginIteration(); pClientData := VisuElemBase.g_ClientManager.GetNextClient(); WHILE pClientData <> 0 DO pClientData[pClientData^.GlobalData.GlobalClientID] := pClientData; END_WHILE You have to make shure every no longer updated pointers in the array have to be deleted and no longer used by your code! Usage of this pointer access at your own risk :-) Works with SP16. From SP17 and newer there will be warnigs etc. using this solution as I remember. It will be great, if Codesys publishes a example or give a hint how to accesse this client values with the VisuUtil lib or other future-proof way!
Last updated: 2024-09-09

Post by timvh on Communication between applications on same device/controller/runtime (Win RTE 3.5.20.20) CODESYS Forge talk (Post)
If you have a Windows system (RTE), then why not run the CODESYS HMI as separate controller. This could easily be moved to another PC if required. In the HMI you could also still use the Symbolic Var access as part of the Data Source Manager, although maybe OPC is the preferred way to make it more future proof. Or what about the Remote Target Visu. Then you can reduce the load of the main controller, while still only having to create one application including Visualization. This is now also supported for Linux systems. See: https://content.helpme-codesys.com/en/CODESYS%20Control/_rtsl_target_visu_for_linux.html https://content.helpme-codesys.com/en/CODESYS%20Visualization/_visu_execute_remote_target_visu.html
Last updated: 2024-09-28

Post by andrebrandt on FB string and naming CODESYS Forge talk (Post)
Hi Tim. Not quite correct. What i'd like, is when you place the FB in prog, i choose a block NTC10k, and name this RT401. What i'm trying to do, is to get the name RT401 automaticly into the FB, so i can put this into the string i pass in a struct. So in var in POU, i saw this a place i could do this, RT401: NTC10k(Tag:='RT401'), but i can't get this to work. I shurly must have had something like this in FB: FUNCTION_BLOCK NTC10k String TAG But it's here where I'm stuck...
Last updated: 2024-09-30

Post by pistola on Case Function - Multiple Conditions, Is it possible? CODESYS Forge talk (Post)
Looking at the help (https://content.helpme-codesys.com/en/CODESYS%20Development%20System/_cds_st_instruction_case.html). I don't think it is possible but I figured I'd ask. I'm looking at have a case that evaluates two variables, instead of having multiple If Else statements I was hoping I could just use a case. Example * Case Var1 & Var 2 of 10 & 10: Instruction Code 10 & 20: Instruction Code 20 & 20: Instruction Code End_Case Obviously I tried typing as noted above and Codesys threw an error. But I was wondering if there was a different way of programming to make something like this work? If not I'll just use a bunch of If Else Statements, Thanks.
Last updated: 2024-11-03

Post by jackbrady on Function Blocks and arrays of function blocks CODESYS Forge talk (Post)
Hello, I am new to Codesys and PLC programming in general (please go easy ha!) I'm not looking for code to be written for me just some help and pointing in the right direction. I am writing some code to send commands to a relay based on input values (to put it simply). Quite basic stuff. I have wrote a function block that takes a global variable (Open_command:BOOL) and outputs to another global variable (Opened : BOOL). The function block is simulating a device so I'll eventually get the globals from that. I now need to create multiple versions of this function block/ device (lets say 100) but I need each iteration of that function block to reference it's own relevant global variable. I think that the best way of doing this would be to use arrays, although I could be wrong. I am aware that for up to 100 instances I could very well manually assign everything but that seems rather time consuming and I want a fancier way of doing it. Here is a very basic example of what I am looking to do, please note I have not written this in proper code it's just to show what I mean. Global Variables V[0-100] int Open_command [0-100] Bool Opened [0-100] Bool Function Block var input x : BOOL Var output y : BOOL if x then y = TRUE ELSE y = FALSE The input to my function block will be Open_command, output will be Opened Example code. If V[x] > 10 then Open_command [x] = TRUE ELSE Open_command [x] = FALSE (So when V1 goes above 10 I need Open_command1 = TRUE therefore initiating FB1 output. V2 > 10, open_command2 = True > FB2 output V3 > 10, open_command3 = True > FB3 output ... ... ) What I can't seem to figure out is how to tie all this together, I have read through the codesys documentation and if anything it has confused me more! ha. Apologies for the poorly written post but hopefully you understand what I am trying to get at. Thanks, Jack
Last updated: 2024-02-14

Post by jari-koivuluoma on Problem trying Net Base Services 3.5.15.0 TCP connection CODESYS Forge talk (Post)
I have a need to send messages between 2 PLCs and I cant use network variables (because of size limit) so I tried writing this simple test program. This seems to work fine. I can send messages back and forth when a first "Start server" and then "Connect client". See the attached image. However, if I disconnect the client by setting ClientConnect to false and try to re-connect then the TCP_Client just gives me TIMEOUT error. When I stop and start the server again, then Im able to reconnect. How is this supposed to work? Why reconnecting wont work. There is not other way of disconnecting the client than setting xEnable of the TCP_Client to false. This is just a testing program and I will try it on 2 seperate devices once this works. PROGRAM PLC_PRG VAR CONSTANT mySize : UDINT := 255; END_VAR VAR Server: NBS.TCP_Server; ServerIpStr: STRING := '127.0.0.1'; ServerIP: NBS.IP_ADDR; ServerPort: UINT := 50000; ServerConnection: NBS.TCP_Connection; Client: NBS.TCP_Client; ServerRead: NBS.TCP_Read; ServerWrite: NBS.TCP_Write; ServerSend: STRING(mySize); ServerReceive: STRING(mySize); ServerConnect: BOOL; bServerSend: BOOL; IP: NBS.INADDR; ConnectedClientIP: STRING; ClientPort: UINT := 50000; ClientIpStr: STRING := '192.168.1.49'; ClientIP: NBS.IP_ADDR; ClientRead: NBS.TCP_Read; ClientWrite: NBS.TCP_Write; ClientSend: STRING(mySize); ClientReceive: STRING(mySize); ClientConnect: BOOL; bClientSend: BOOL; Error: BOOL; Message: BOOL; END_VAR // Server ServerIP.sAddr := ServerIpStr; Server( ipAddr := ServerIP, uiPort := ServerPort ); ServerConnection( xEnable := Server.xEnable, hServer := Server.hServer, ); IP := ServerConnection.IPAddress; ConnectedClientIP := F_Concat7( BYTE_TO_STRING(IP.S_un_b.s_b1),'.', BYTE_TO_STRING(IP.S_un_b.s_b2),'.', BYTE_TO_STRING(IP.S_un_b.s_b3),'.', BYTE_TO_STRING(IP.S_un_b.s_b4)); ServerRead( xEnable := ServerConnection.xActive, hConnection := ServerConnection.hConnection, szSize := SIZEOF(ServerReceive), pData := ADR(ServerReceive) ); IF ServerRead.xReady AND ServerRead.szCount > 0 THEN Message := TRUE; END_IF IF ServerRead.eError > 0 THEN Error := TRUE; END_IF ServerWrite( xExecute := ServerConnection.xActive AND bServerSend, hConnection := ServerConnection.hConnection, szSize := LEN(ServerSend)+1, pData := ADR(ServerSend) ); IF ServerWrite.xDone THEN bServerSend := FALSE; END_IF IF ServerWrite.eError > 0 THEN Error := TRUE; END_IF // Client ClientIP.sAddr := ClientIpStr; Client( xEnable := ClientConnect, ipAddr := ClientIP, uiPort := ServerPort, udiTimeOut := 10000000 ); ClientRead( xEnable := Client.xActive, hConnection := Client.hConnection, szSize := SIZEOF(ClientReceive), pData := ADR(ClientReceive) ); IF ClientRead.xReady AND ClientRead.szCount > 0 THEN Message := TRUE; END_IF IF ClientRead.eError > 0 THEN Error := TRUE; END_IF ClientWrite( xExecute := Client.xActive AND bClientSend, hConnection := Client.hConnection, szSize := LEN(ClientSend)+1, pData := ADR(ClientSend) ); IF ClientWrite.xDone THEN bClientSend := FALSE; END_IF IF ClientWrite.eError > 0 THEN Error := TRUE; END_IF
Last updated: 2024-10-03

Post by cdutz on Problems connecting to Codesys 4.9.0.0 runtime on my Wago PFC200 CODESYS Forge talk (Post)
Turns out I managed to get a connection to my PLC. It seems that a few weeks ago Wago released something with version 4.3.3(25). So I reset my PLC to Factory-Reset, set it to the 192.168.1.17 IP and changed the IP to the one I wanted with the Wago EthernetSettings tool. Then updated the latest firmware using the WAGOupload tool. Now the PLC came back up without a PLC runtime running, so in the Web-tool I wen't to the "Configuration"/"PLC Runtime" and selected the runtime version "CODESYS V3". I uninstalled all Codesys versions and installed the version from the download package of Wago together with all the packages the bundle provided. After creating a new project I didn't select the old PFC200 runtime, but one of the dozens of new device profiles, that it now listed. With these settings I was then able to connect to my PLC. Now I hope I'll get the existing project that I had ported to this new structure. Sorry for the noise. Chris
Last updated: 2023-08-26

Post by ofey on Codesys Soft PLC OPC UA server CODESYS Forge talk (Post)
Hi! I'm sorry if this has been asked before. I have tried looking up previous topics regaring this, but even though I'm following tutorials and other posts I cant seem to get this to work consistently. I actually got the connection established on a test project after some trial and error. I only got it to work with the "Anonymous login". But after i deleted the test project and tried to get the same thing to work on another project I cant get it to work anymore. What I'm trying to do: Set up and OPC UA Server using CODESYS with the free soft PLC. I then try to connect to the OPC UA Server with the program "UaExpert". What happens: I get the error Error "'BadUserAccessDenied' was returned during ActivateSession". What I have done in CODESYS: - Added the object "Symbol configuration" and checked some test variables - Checked "Support OPC UA features - In "Communication settings -> device -> Change runtime security policy" I have checked "Allow anonymous login" What I have done in UAExpert: - Found the OPC UA server under "local". (It is showing two servers though, I do not know why. It showed the same when it worked yesterday). Se attachment - Checked "Anonymous" under "Authentication settings in the OPC UA server. I'm new to CODESYS, so it could be something elementary wrong in my settings. Maybe something in the user settings in CODESYS regarding user rights or something?
Last updated: 2023-09-14

Post by sturmghost on Visualization using methods and cyclic ST-calls CODESYS Forge talk (Post)
Im looking for a way to implement ST-code into the visualization element without creating a helper POU or method in my device/application tree. Like visualization properties are evaluated at each VISU_TASK cycle I want to be able to create own ST code which interacts with the visualization interface variables. To be more specific I want to have a property which executes user defined ST-code at each VISU_TASK cycle exactly like its already possible for Input Configuration on various mouse and dialog events. Also a property for initialization (so only executed once) and a timed property would be nice. With the situation right now I'll have to create a POU function which handles the ST-code and misuse a property, like the text variable, to execute this POU function at each VISU_TASK cycle. Or does it exist and I don't know it?
Last updated: 2023-10-02

Post by willbechel on Errors about PLC configuration in CoDeSYs software CODESYS Forge talk (Post)
I saved it as the same project but in a different location. I opened this "new project". I clicked on the "Direct Login from Automation Builder" button. It automatically directed me to CODESYS, where I was able to create the "Create Boot Project" but first I also clicked login again but inside CODESYS keeping the automation builder login online. Additional Information: The "Create Boot Project" function in CODESYS is used to create a project that will automatically start when the controller is booted up. To create a boot project, you must first create a new project in CODESYS. Once you have created a new project, you can then use the "Create Boot Project" function to create a boot application. The "Create Boot Project" function will create a new application that is based on the current project. The new application will be saved in the same location as the current project. You can then download the new application to the controller.
Last updated: 2024-02-01

Post by timl on BacNet "Unaufgelöste Referenz" CODESYS Forge talk (Post)
Hallo, ich habe Probleme beim nachbauen des BacNet2 Tutorials "Erste Schritte" aus der CODESYS Online Help. https://content.helpme-codesys.com/de/CODESYS%20BACnet/_bacnet_first_steps.html Das Anlegen des BacNet2 Servers und der danach folgenden BacNet Datenpunkte erfolgt ohne Probleme. Der Code lässt sich mit F11 auch Fehlerfrei generieren. Beim Download auf die SPS tritt dann der Fehler auf dem Bild auf. Anbei auch ein Bild des Logs nach dem Download. CODESYS BACnet 2.0.0.0 ist über den Installer runtergeladen. Device: CODESYS Control Win V3 x64 Version 3.5.19.40 CODESYS 3.5.19.40 Im Bibliotheksverwalter ist BACnet2 2.0.0.0 aufgeführt Die Konfigurationsdatei habe ich mit folgenden anpassungen abgespeichert: [ComponentManager] Component.1=CmpTargetVisuStub Component.2=CmpWebServer Component.3=CmpWebServerHandlerV3 Component.4=SysCpuMultiCore Component.5=SysReadWriteLock Component.6=SysCpuBreakpoints Component.7=SysPipeWindows ;Component.8=CmpHilscherCIFX ;Component.9=CmpPCANBasicDrv ;Component.10=CmpCANFoxDrv ;Component.11=CmpIxxatCANDrv ;Component.12=CmpBlkDrvCanServer ;Component.13=CmpBACnet Component.14=CmpBACnet2 [CmpBACnet2] ;configuration file of the BACnet stack IniFile=$PlcLogic$/bacstac2.ini ;task priority of the BACstack process task, default: TASKPRIO_NORMAL_END (159) TaskPrio=128 ;name of the named pipe for the communication with the BACstack AppName=/tmp/BACnetServer Habe ich etwas vergessen?
Last updated: 2024-02-16

Post by dtamm on How to read string from CharBufferPtr? CODESYS Forge talk (Post)
I am trying to implement a mechanism to send alarm SMS. For this, I have created an Alarm Class with a Notification Action which calls a POU. This POU implements IAlarmNotifiable making it selectable in the Alarm Class configuration. IAlarmNotifiable has an Execute method which is called by the alarm class. Now, I want to extract the alarm message of the triggered alarm. The Execute method comes with a VAR_INPUT itfAlarm: AlarmManager.IAlarm which supplies a method called GetMessage. The help text says: Returns the message text, that has been configured for the alarm. The result is a pointer to the buffer, where the message text is stored The type of the result is CharBufferPtr, and at some place I read that it can be interpreted as a pointer to string. But I cannot manage to extract the alarm message, all I get are numbers. I have tried the following: psAlarmText := itfAlarm.GetMessage(__SYSTEM.TYPE_CLASS.TYPE_STRING)^; sAlarmText := TO_STRING( itfAlarm.GetMessage(__SYSTEM.TYPE_CLASS.TYPE_STRING)^ ); So how do I get access to the alarm message as clear text? (In this case, "Larm 1")
Last updated: 2024-02-21

Post by francescoc on Custom log CmpLog CODESYS Forge talk (Post)
Hi, I am trying to create a log in my application. Since I cannot find any documentation regarding modifying the codesys configuration file to be able to log in ms, i tried to create a new log via CmpLog.LogCreate. Below is the part of the code where I create the logger and write a test string. In the log tab of codesys I actually see the new log that was created, but it is empty, and in the folder I cannot find any files. I can't find any detailed documentation. Can you guys give me support? Are there any examples? Thank you IF NOT FirstCycle THEN LogName:= 'LOGS/TestLog'; LogOptions.bEnable:= 1; LogOptions.iMaxEntries:= 5000; LogOptions.iMaxFiles:= 100; LogOptions.iMaxFileSize:= 5000; LogOptions.szName:= LogName; LogOptions.uiType:= CmpLog.LogTypes.LT_TIMESTAMP_RTC_HIGHRES; LogOptions.uiFilter:= CmpLog.LogClass.LOG_ALL; LogHandle:= CmpLog.LogCreate(pOptions := ADR(LogOptions), pResult:= ADR(Result)); LogHandle:= CmpLog.LogOpen(pszName:= LogName, pResult:= Result); Component_Manager.CMAddComponent2('TestLogNEW', 16#00000001, ADR(udiCmpIdNEW), 0); CmpLog.LogAdd2(LogHandle, udiCmpIdNEW, CmpLog.LogClass.LOG_INFO, 1, 1, 'Logger started...'); END_IF IF TestWrite THEN TestWrite:= FALSE; CmpLog.LogAdd2(LogHandle, udiCmpIdNEW, CmpLog.LogClass.LOG_INFO, 1, 1, 'Write test'); END_IF
Last updated: 2024-03-16

Post by thewizard8 on Raspberry PI4 Serial Port CODESYS Forge talk (Post)
Hi Dear All, I'm using my raspberry PI4 as a CoDeSyS PLC (Build from scratch with custom electronics). I was able to implement all fieldbuses with the exception of Modbus Serial. I'm using the internal Port (GPIO) and I configured it in /etc/Codesyscontrol_user.cfg the following away: [SysCom] Linux.Devicefile.1=/dev/ttyUSB0 Linux.Devicefile.2=/dev/ttyS0 I'm using COM2 on Master configuration. I'm using a interface board from TTL/RS485 (bidirectional board), and it's works perfectly with other devices but not in CoDeSyS. I'm able to send data with python script and read it on my pc using putty, but when I use a modbus slave simulator to interface with codesys I always get red icons on master and slave. (Please find image attached). I'm pretty shure that this might be a bad parameter on my CoDeSyS runtime configurstion file. Can someone help me? I'm stuck and this is for my master degree certification.
Last updated: 2024-03-18

Post by umdee on Error when monitoring LAD programs CODESYS Forge talk (Post)
System Information from the computer being used: OS Name Microsoft Windows 11 Pro Version 10.0.22631 Build 22631 Other OS Description Not Available OS Manufacturer Microsoft Corporation System Manufacturer Dell Inc. System Model Latitude 5500 System Type x64-based PC System SKU 08B9 Processor Intel(R) Core(TM) i7-8665U CPU @ 1.90GHz, 2112 Mhz, 4 Core(s), 8 Logical Processor(s) BIOS Version/Date Dell Inc. 1.3.11, 6/11/2019 SMBIOS Version 3.2 Embedded Controller Version 255.255 BIOS Mode UEFI BaseBoard Manufacturer Dell Inc. BaseBoard Product 0M14W7 BaseBoard Version A00 Platform Role Mobile Secure Boot State On PCR7 Configuration Elevation Required to View Windows Directory C:\WINDOWS System Directory C:\WINDOWS\system32 Boot Device \Device\HarddiskVolume1 Locale United States Hardware Abstraction Layer Version = "10.0.22621.2506" User Name CARDASSIA-IX\Engineer Time Zone Eastern Daylight Time Installed Physical Memory (RAM) 16.0 GB Total Physical Memory 15.8 GB Available Physical Memory 4.67 GB Total Virtual Memory 18.5 GB Available Virtual Memory 2.52 GB Page File Space 2.63 GB Page File C:\pagefile.sys Kernel DMA Protection Off Virtualization-based security Not enabled Windows Defender Application Control policy Enforced Windows Defender Application Control user mode policy Off Device Encryption Support Elevation Required to View Hyper-V - VM Monitor Mode Extensions Yes Hyper-V - Second Level Address Translation Extensions Yes Hyper-V - Virtualization Enabled in Firmware Yes Hyper-V - Data Execution Protection Yes
Last updated: 2024-03-19