Post by otbeka on CAA File Handling: "Read only" error
CODESYS Forge
talk
(Post)
Hi, sorry for the late reply. After some investigation, the read-only error was being triggered by a FAT-fs filesystem panic on the kernel end, probably caused by unfinished write/reads causing corruption. I found this thread https://forge.codesys.com/forge/talk/Engineering/thread/e637d252b7/ which seems to give a solution of using SysProcess to send the 'sync' command to the console immediately following a write to prevent issues if power is lost or, in my case, if the unit is harshly power cycled. Indeed this seems to resolve the issue bar the worst possible edge cases.
Last updated: 2025-05-02
Post by rockallsue on Frustration-Fueled Feedback on Project File Management and Git Integration
CODESYS Forge
talk
(Post)
Some developers export ST code manually and edit it in VSCode, then copy it back. However, a more practical approach might be using automation scripts (PowerShell, Python) to extract and inject code into the CODESYS project. You could also check if CODESYS Automation Server or CODESYS API allows better ST access for external tools. https://www.codesys.com/the-system/releases-updates-lifecycle/release-plan-roadmap.html Network drive issues are particularly painful. As a mitigation, you could try using local project storage with periodic cloud sync instead of directly saving to a network drive. Using Rsync or Syncthing for automatic but safe synchronization might reduce risks of file corruption.
Last updated: 2025-06-03
Post by tk096 on Max lines of code, codesys CNC ?
CODESYS Forge
talk
(Post)
Hi, this is a bug in CODESYS Softmotion. Due to this bug the size is limited to a maximum of 32767 elements. However, we recommend to use way smaller buffer sizes. You could use a small buffer (it should be big enough so that it does not run empty when the interpolator processes the elements). In the beginning you fill the buffer in PLC_PRG until it is full. Afterwards, you start the interpolator. The interpolator processes the elements and removes them as soon as it travels past them. In PLC_PRG you check whether new elements can be stored in the buffer (NOT QUEUE.bFull). If the buffer has space, you generate the next elements and add them to the buffer (SMC_AppendObj()). I hope this helps you.
Last updated: 2025-06-04
Post by timvh on Codesys 3.5.18.60 β Application Loss and Persistent Data Corruption
CODESYS Forge
talk
(Post)
Which device do you use? Does this have persistent memory (e.g. NVRAM) available? Maybe first ask your PLC vendor about the possibilities and how they advice to use persistent variables? If you have no NVRAM available, CODESYS will store the variables in a file when the device gracefully shuts down. But on an abrupt power failure, this is not possible. If you have no NVRAM and you want to use persistent variables, then consider using a UPS. In this case when the power is lost, the UPS can keep the power on the PLC which then can gracefully shut down. Alternatively use the Persistence Manager to store the variable values in a file e.g. only on change. See: https://content.helpme-codesys.com/en/CODESYS%20Application%20Composer/ac_pm_overview.html
Last updated: 2025-08-26
Post by antonz on CoDeSys v3.5: creating libraries for both 32-bit and 64-bit controllers
CODESYS Forge
talk
(Post)
Follow up question: in the Project Settings, under Library Development, there is an option related to this: Check all Pool Objects -> Pointer size to use Options are: * 32 Bit * 64 Bit * 32 and 64 Bit The descriptions and online help suggest to me this is only relevant for checking and showing any incorrect pointer types as an error in the IDE. E.g. using a DWORD to store a pointer value on a 64-bit controller. It would not control the creation of either 32-bit or 64-bit compiled libraries. Is that correct?
Last updated: 2025-09-01
Post by pernockham on Control for linux SL, 4.14.0.0 -> 4.15.0.0 breaks web page access. URL requires authentication
CODESYS Forge
talk
(Post)
I have a problem which I have identified with a device-update from 4.14.0.0 to (4.15.0.0-4.17.0.0) where the newer versions will stop any local access to the internal web page with the browser responding "The requested URL requires authentication". Setting the device back to 4.14.0.0. the web page will respond. Access to web page through Automation server is possible also for the newer version, but not "local" access. Runtime (Codesys control for linux SL) is on 4.17.0.0. I have tried to manipulate settings for 'Access-Control-Allow-Origin' '*' always; through nginx (normally a proxy_pass to localhost:8080). Also tested bypassing nginx by accessing 8080 directly with the same result.
Last updated: 2025-09-08
Post by durallymax on Persistent Vars
CODESYS Forge
talk
(Post)
Looking for a better way to manage Persistent Variables. We tend to have local vars in our FBs that need persistence through downloads as the systems are updated/altered on a regular basis. Retain would suffice if we had an easy mechanism to backup and restore like we can with Persistent variables and recipes. Although not having to remember that step with Persistent variables is preferred. We're running into issues with persistent storage capacity (WAGO PFC200) using the Persistent variable list (and adding all instances). It appears there are many ways to handle this, some with recipes, some with files, others with application manager. Is there a solution that exists that is as simple as declaring as Persistent and managing elsewhere? Or do we need to move onto periodically writing CSVs?
Last updated: 2025-09-22
Post by reinholdgaylord on CAA File Handling: "Read only" error
CODESYS Forge
talk
(Post)
Hi, sorry for the late reply. After some investigation, the read-only error was being triggered by a FAT-fs filesystem panic on the kernel end, probably caused by unfinished write/reads causing corruption. I found this thread https://forge.codesys.com/forge/talk/Engineering/thread/e637d252b7/geometry dash lite which seems to give a solution of using SysProcess to send the 'sync' command to the console immediately following a write to prevent issues if power is lost or, in my case, if the unit is harshly power cycled. Indeed this seems to resolve the issue bar the worst possible edge cases. Thank you so much!
Last updated: 2025-09-25
Post by bbmussatto on Connetion with Topcon Opus B3 ECO Full display
CODESYS Forge
talk
(Post)
I have a Topcon Opus B3 ECO Full display and i wanna program it with codesys, but i cant connect it to the display. After creating a new project, i choose the device "Opus B3-B4-B6-3.5.19.50" that is already available in my version of codesys, but i think the problem is that my version of codesys or something else is not the same as the codesys runtime version running on my display. Can anyone tell me how i can see the codesys runtime version on my display? i tried looking in the settings (Daemon > CDS) on the display, but all i see is "N/A" for "Customer Number", "Customer Part Number" and "Customer Serial Number". Can anyone help me make this connection?
Last updated: 2025-10-07
Post by manuknecht on Using SMC_MOVTYP.INITPOS without specifying the start position
CODESYS Forge
talk
(Post)
I am using the object SMC_GEOINFO to generate a trajectory and move a system accordingly using the SMC_INTERPOLATOR function block similar to the sample project CNC10_DynamicPath.project. According to the documentation, the movement type INITPOS does not require a start position in the SMC_GEOINFO object, which is confirmed in the documentation of the SMC_GEOINFO object. When using the movement type INITPOS however, the motion will still start from the starting point defined in the SMC_GEOINFO object (0,0,0 if not specified otherwise). Does someone know how to resolve this or is there an example project that makes use of the INITPOS movement type without specifying the starting point? Thanks in advance!
Last updated: 2023-12-15
Post by sean-barton on Function block method default arguments
CODESYS Forge
talk
(Post)
I have default arguments specified for function block methods but when calling a method, an error is produced requiring me to supply all the arguments despite there being default values. According to the online documentation, under section "Calling a Method" and subsection "argument passing" of the following link: https://content.helpme-codesys.com/en/CODESYS%20Development%20System/_cds_obj_method.html "Passing an argument for an input ... can be omitted ... for which a default or initial value was specified in the declaration..." I have found this to be the case for all Codesys IDEs I've used, 3.5.11, 3.5.16, 3.5.17, 3.5.19. Am I missing something?
Last updated: 2023-12-21
Post by jmohre on External file with relative path
CODESYS Forge
talk
(Post)
I try to add a simple text file to my PLC application, so that is download everytime the application is downloaded to the target. What I did is to add an external file to the application and this works perfect as long as the external file location does not change. It looks like the external file path is stored absolute in project. But if different users work on the project they may have different locations where for their working directory. Is there an option to store the external file path relative e.g. to the project file? Or does s.o. know a different solution to add a text file to application in order to download automatically with the application? Thanks
Last updated: 2024-01-04
Post by anderson on function block output
CODESYS Forge
talk
(Post)
I'm trying to make a CNC machine, but I'm having problems because the drive I'm using only has the option of communicating through digital inputs. In this case, I should use the CLP's digital outputs to communicate with it, correct? However, in the function blocks it seems that they are already pre-programmed and I didn't find the pulse output options, for example, so that I could associate a digital output from the PLC to connect this to the drive's pulse input. My question is: is it possible to associate the pulse output of the function block with a digital output of the PLC? and how to do this?
Last updated: 2024-01-05
Post by riccardo on Error while processing the visualization: Client id not present or no longer valid
CODESYS Forge
talk
(Post)
Hallo goodmorning, I am using codesys 3.5 sp19 with Weidmueller PLC. I created a page with several checkbox to manage an array of bool. When I build the project the system doesn't signal any error, when I go in simulation mode everything works until I click on checkbox to toggle the variables. Other visu elements works proprerly (e.g. bottons, lights, ect, ect) but the check boxes cause a crash giving the following error: Error while processing the visualization: Client id not present or no longer valid I serched to figure the problem out and to search a solution on the web but nothing. Can someone help? Thanks and Regards, Scanu
Last updated: 2024-01-23
Post by dhumphries on Ethernet/IP Issue
CODESYS Forge
talk
(Post)
Make sure the O->T and T->O bytes required by the remote device match the configuration in Codesys. Most of the EDS files I've imported have not worked by default. See the attached images for the connections and assemblies tabs. Note that the connections are in Bytes and the assemblies are in bits, you have to have enough bits to equal the bytes. Either mismatch will give a red/orange triangle. Page 343 of the manual (assuming the STF10-IP is an applied motion microstep driver) has some recommended connection settings, you should be able to confirm the input and output bits somehow, some devices have a web GUI, some require a software tool.
Last updated: 2024-02-03
Post by alexgooi on Is it possible in the log to see previous shutdown
CODESYS Forge
talk
(Post)
Hi DavidBo, In general Codesys is used to control equipment and an exception is the worst thing that can happen in your installation. If you cannot prevent the exception from triggering, you could implement a Try catch statement, with this solution your controller keeps on running and you are able to handle the exception. __TRY //This statement will trigger an exception Result := 4/0; __CATCH(exc) //Handle the exception HandleException(exc, strExceptionText => strExceptionText); // From the Codesys help file //Create a log file //-------------------------------------------------------- __ENDTRY What you also could do is implement implicit checks, these functions cover most of the exceptions (like dividing by zero) See picture But in general avoid a complete controller shutdown!
Last updated: 2024-02-09
Post by valenting on Runtime not working on raspberry pi Bullseye
CODESYS Forge
talk
(Post)
Hello I have a problem with Codesys on Raspberry pi with Bullseye The device is not recognized as a Raspberry pi, as I get this error : ooops... this runtime was built for RASPBERRYPI. Hardware version or firmware version not supported! (-18, 0x00000BB8, 0xFFFFFFFB) I'm running Codesys on a compute module 4S with Raspbian GNU/Linux 11 (bullseye), my kernel version is Linux 5.10.90-v7l+ Codesys version is the latest, released last week (4.11.0.0, CODESYS Control V3.5.19.61 for ARM-32Bit - build Feb 22 2024) I know it works on the same device if I use Raspbian 10 (Buster) with Linux 5.4.81-v7l+ kernel, but for some other reasons I have to use Bullseye. What can I do ?
Last updated: 2024-03-01
Post by dhumphries on Not able to see input data coming from eip adapter on codesys
CODESYS Forge
talk
(Post)
Does the device have a green icon next to it when the PLC is running? If not you have some kind of communication problem, wireshark may be picking up some data but the scanner may not be configured correctly to receive the data. Check the T>O and O>T bytes and make sure they match on both the scanner and adapter. I've had very little success loading a .eds file and having the configuration work without some manual configuration. If you have a green icon, have you enabled the device to always update variables?
Last updated: 2024-03-02
Post by esave on Stepper Drive with Ethercat
CODESYS Forge
talk
(Post)
Hello everybody I am new into Codesys. I have a stepper driver (EM3E-556E) from Leadshine. I want to controll the stepper driver via EtherCat to a ST programm but I dont have any function block or anything that i can use. I only have the XML-File wich I loaded. With it I implemented the drive as a Ethercat slave and now I see these variables. (See picture) I dont know how to controll the stepper drive. And the manufacturer doesnt provide support for me. Can anybody help me or atleast tell me how they would do it?
Last updated: 2024-03-14
Post by valec on Connect local Asem HMI runtime to local Codesys Control Win V3 x64
CODESYS Forge
talk
(Post)
I have a project made on a PL700 PLC with Codesys and an Asem Premium HMI panel. I don't have access to the physical PLC right now, so I'm trying to use Codesys Control Win V3 x64. I created the application and loaded "Codesys Control Win V3 x64" without errors, then I activate "Start PLC" from the tray. Asem cannot connect. I tried to use "localhost" or the local IP address and it doesn't work (it's the "CoDeSys Soft PLC Communication Driver"). I need to connect my local Asem runtime to a virtual Codesys application on my PC. How can I do it?
Last updated: 2024-03-26
Post by dhumphries on How to determine code size
CODESYS Forge
talk
(Post)
I'm trying to determine which Codesys Control license I need, the Control Standard S has all the features I think I'll need, but the code size is limited to 3mb, I created a simple program with only 1 line of ladder logic and a simple visualization with a button and an indicator. When I generate code I get some messages, one indicates that the total allocated memory size for code and data is 2.1mb. Is this metric the correct size of the code? I question the size because it exceeds the allowable code size for the Basic S and Basic M licenses and consumes 2/3 of the available memory for the Basic L or Standard S license. What tool can I use to estimate the size of code as it relates to the runtime license limit?
Last updated: 2024-04-05
Post by r-niedermayer on Issue with WebVisu on Raspberry PI
CODESYS Forge
talk
(Post)
Regarding to your application: When clicking in the web visualization, the boolean variable will be tapped for both buttons. The LED in the web visualization lights up as long as the variable is true The used variables should come from the GVL, ad/or thePLC_Prg. We see no difference or problem in both projects: You have created a visuelement Push button a a tapper, that is supposed to control the variable in this way as expected. This is also reflected (switching Bool from false to true) in the program code, as well as in the (GVL declared) variables. Wherever the misunderstanding comes from: no, this is not memory or license related. Our best guess: it is probably more of an applicative/conceptual implementation.
Last updated: 2024-04-11
Post by reinier-geers on License problem gateway
CODESYS Forge
talk
(Post)
Epis doesnt want Softmotion. I thought it was about the price. If it was possible it would be working already and i dont need an extra licence. Thats the problem of codesys. The software is running but hangs on its license. Epis made it posible to see the stick. I can see the license. Softmotion is there from 3.5.14.Xx Like is said And Motion control is alrady posible 15 year ago. And i only need a Sync of 2 drives. I want a good solution not a refund. Dont point to the manufacturer. The software is made by 3s not by epis .
Last updated: 2024-04-29
Post by robpqs on Program from one PLC to other WAGO 750-8204
CODESYS Forge
talk
(Post)
Hello, You use the WAGOUpload tool. You can download it on the download center of WAGO. Make a backup and restore it on the new device. (if can check the remanent data to copy the persistent variables if necessary) You can also use a SD card, go to the WBM copy it the image to the SD card and restart the other controller on the SD card. In the WBM, copy it back to the internal flash. If you contact your local Wago office, they will more than probably help you. There is also a WAGO forum. RP,
Last updated: 2024-05-27
Post by miltos on licensing question
CODESYS Forge
talk
(Post)
Greetings to all, I'm working on a webvisu project on control win V3 x64 runtime, and have purchased 3 licenses for my application. -Codesys Control Standard M -Codesys Visualization L -Codesys Communication M I have them installed on a Codesys usb dongle When I try to download the program, a login error window appears with the message "No valid license found for the webvisualization". The control win v3 communicates with 3 plc, and have enabled communication over codesys V3 communication by adding one datasource for every plc in the datamanager. If I remove the data manager from the project, the rest of the visualisation can be downloaded normally. Do I need to purchase another License and which one? Please find attached the software metrics and the error screen.
Last updated: 2025-10-31