Post by alexgooi on Codesys KNX implementation
CODESYS Forge
talk
(Post)
Dear forum, We are currently doing some research on the Codesys KNX implementation (https://store.codesys.com/en/codesys-knx-sl.html). We almost have it working but we are missing the last part. The setup: We have a Codesys virtual control container running on docker (4.17.0.0), the I/O is running over an Ethernet IP coupler (Weidmüller), and this is running fine. As far as I’m concerned this tells me that the ethernet device is working properly (the container has access to the outside world, including multicast). Underneath this ethernet adapter the KNX module is added (see picture). In the KNX device (Codesys) 2 input variables are added (see picture), and these are exported to ETS (ETS 5). In ETS A Codesys KNX device has been imported and the Codesys export was imported, afterwards the group addresses are attached to the variables (see picture). Afterwards this configuration is downloaded to the Codesys controller (Container) via ETS. ETS asks for the pressing of the programming button, when the virtual programming button is pressed the download starts and finishes without any errors. This tells me that ETS is communicating with the Codesys controller, and that the download process is ok (so far so good). Now the part where we are struggling with, somehow we need to convert the KNX TP to KNX IP. For this we have the following interface: Zenio KIPI SC (https://www.zennio.com/product/kipi-sc/) this is a KNX TP to IP interface. We have the following setup for this device (see picture) (an IP in the same subnet is used). We tried multiple combinations of IP addresses but the TP devices are simply not communicating to the Codesys container. Does anyone has any advice on what to try next. To make the question more explicit how can we link the TP bus to the Codesys device? Kind Regards Alex
Last updated: 2026-01-05
Post by jasonhogan on Login problem with FileTransfer on Raspberry Pi 5
CODESYS Forge
talk
(Post)
That’s a classic CODESYS quirk. As soon as you enable AllowFileTransferServices=1, the web server locks down and demands authentication for everything, including WebVisu sessions. Since you're on a Raspberry Pi / Linux, trying to make the built-in CODESYS web server do both secure file handling and unauthenticated kiosk visu is usually a losing battle. A couple of ways to get around this: The cleaner route (separate the jobs): Turn AllowFileTransferServices back off in the config so your kiosk WebVisu opens freely without any login prompts. Then, handle the file download outside of CODESYS — just run a dead-simple Nginx/lighttpd file server or a tiny Python script on the Pi pointed at your export folder (/var/opt/codesys/...). That way your PLC security stays intact, and the kiosk screen just works. If you really want it through CODESYS: Check your Device -> Users and Groups in the IDE. Make sure the Everyone / Anonymous user group actually has explicit view permissions checked for the Visualization. Sometimes when file services are toggled, anonymous users lose the default visu-read rights and get booted straight to the login dialog. URL / Browser trick for kiosk: If the Pi is just opening a local browser on startup, you can sometimes pass the basic credentials in the browser launch script or use a small reverse proxy on localhost to inject the headers automatically so you don't see the popup. Honestly, running a lightweight HTTP/FTP endpoint on Linux (option 1) is by far the least headache.
Last updated: 2026-08-15
Post by thn-power on Updating OPC UA Core Nodeset on PLS
CODESYS Forge
talk
(Post)
Hi After much trail and error I think I found the root cause to my OPC UA problem. The problem is that I cannot manage to build and download a program with a a custom OPC UA Information model. We use a Weidmueller WL2000 PLS, but the problem also exsist on the Win V3 PLC. Our custom information model is based on the latest versions of the OPC UA Core Nodeset v 1.05.03 (2023-09-20) and UA/DI nodeset 1.04.0 (2022-11-03) Those nodesets are installed in the Codesys Information Model Repository (3.5.19.6) However, when trying to build I get the following error. [ERROR] Untitled1: Communication Manager [Device: PLC Logic: Application]: The information model http://opcfoundation.org/UA/ is required by http://bos.org/ with a minimal publication date from 15.12.2023 but the device has only a model from 15.09.2021 installed. Probably the information model from 15.09.2021 is missing in the information model repository. [ERROR] Untitled1: Communication Manager [Device: PLC Logic: Application]: The information model http://opcfoundation.org/UA/DI/ is required by http://bos.org/ with a minimal publication date from 03.11.2022 but the device has only a model from 09.03.2021 installed. Probably the information model from 09.03.2021 is missing in the information model repository. Build complete -- 2 errors, 1 warnings : No download possible I think the problem is that the UA Core nodeset is implemented in the PLC firmware (at least that in Siemens S7), and that only includes the "old" nodeset from 2021-09-21 etc. So the question is, how (or if?) can I transfer the new nodeset to the PLS? I have created separate Information models under Communication manager with the newer code nodesets (UA and DI). But it seems that the compiler does not recognize them being excising, neither in the Codesys IDE or on the PLC. Would have guessed that this is a common issue, sine many manufacturers use the latest versions of the OPC UA standard, and that it would be a solution to the problem.
Last updated: 2024-09-20
Post by pppn on Issue with Forward Open Connections in Ethernet/IP Protocol Stack in Codesys
CODESYS Forge
talk
(Post)
Hello, I am facing an issue with my Ethernet-based project in Codesys. My product was functioning well until I modified the protocol stack and uploaded it to my device. Here are the details of my problem: Project Setup: I am working on an Ethernet-based project to test my product. The project was running without issues before modifying the protocol stack. Issue: After modifying the protocol stack and uploading it to my device, I am encountering an error in Codesys related to the forward open connections. Error status: connection failure, extended: connection in use or duplicate forward open. According to the Ethernet/IP protocol in codesys, there are three forward open connections that need to be established. The first two connections are opening without any issues. The third connection, which is an input-only connection, is causing problems. The error message indicates that the connection is already open. Debugging Attempts: I have extensively debugged the protocol stack and found no issues. The product works well when tested with EIP tools but not with Codesys. Exclusive owner connections are working correctly, and only the input-only connection is problematic. Wireshark Traces: Wireshark traces show that the third connection attempts to open but reports that it is already open. Steps to Reproduce: Modify the protocol stack and upload it to the device. Attempt to establish three forward open connections in Codesys. Observe the error on the third connection (input-only). Request: I would appreciate any suggestions or guidance on how to resolve this issue. If there are specific settings or configurations in Codesys that I need to check, please let me know. Additionally, if there are known issues or workarounds related to this problem, I would be grateful for the information. Attachments: Wireshark traces showing the connection attempts and errors Screenshots of the error messages in Codesys codesys version: CODESYS V3.5 SP16 Patch 3 + 64 bit
Last updated: 2024-06-25
Post by pppn on Issue with Forward Open Connections in Ethernet/IP Protocol Stack in Codesys
CODESYS Forge
talk
(Post)
Hello, I am facing an issue with my Ethernet-based project in Codesys. My product was functioning well until I modified the protocol stack and uploaded it to my device. Here are the details of my problem: Project Setup: I am working on an Ethernet-based project to test my product. The project was running without issues before modifying the protocol stack. Issue: After modifying the protocol stack and uploading it to my device, I am encountering an error in Codesys related to the forward open connections. Error status: connection failure, extended: connection in use or duplicate forward open. According to the Ethernet/IP protocol, there are three forward open connections that need to be established. The first two connections are opening without any issues. The third connection, which is an input-only connection, is causing problems. The error message indicates that the connection is already open. Debugging Attempts: I have extensively debugged the protocol stack and found no issues. The product works well when tested with EIP tools but not with Codesys. Exclusive owner connections are working correctly, and only the input-only connection is problematic. Wireshark Traces: Wireshark traces show that the third connection attempts to open but reports that it is already open. Steps to Reproduce: Modify the protocol stack and upload it to the device. Attempt to establish three forward open connections in Codesys. Observe the error on the third connection (input-only). Request: I would appreciate any suggestions or guidance on how to resolve this issue. If there are specific settings or configurations in Codesys that I need to check, please let me know. Additionally, if there are known issues or workarounds related to this problem, I would be grateful for the information. Attachments: Wireshark traces showing the connection attempts and errors Screenshots of the error messages in Codesys codesys version: CODESYS V3.5 SP16 Patch 3 + 64 bit
Last updated: 2024-06-25
Post by winki on ModbusFB ClientRequest: never recovers after a single ReplyTimeout (requires full download)
CODESYS Forge
talk
(Post)
Library: ModbusFB (CODESYS Modbus package) IDE / Runtime: CODESYS V3.5 SP___ / Control runtime ___ Target: ___ (e.g. gateway, Linux ARM64 / Debian) Slave: Modbus TCP inverter Summary I poll a Modbus TCP slave with a permanent connection: one ClientTCP (kept connected, xConnect:=TRUE) and one ClientRequestReadHoldingRegisters, triggered cyclically. Everything works fine after a fresh application download. But as soon as one single ReplyTimeout occurs (slave temporarily not answering), the request never recovers. It stays stuck and no further messages are sent, even though the TCP connection is still reported as alive. Only a full application download brings it back — an online change or a runtime reset is not enough / not what I want in production. State observed when stuck So the connection is alive, the request finished in ReplyTimeout, the FB is back to _state = None, but udiNumMsgSent no longer increases — as if a new rising edge on xExecute is no longer accepted / no longer produces a new message. My trigger logic (simplified) Each PLC cycle, in this order: If the request is fully at rest (NOT xExecute AND NOT xBusy AND NOT xDone AND NOT xError) and a read is pending, I set xExecute := TRUE. I call clientTcp() then clientRequest(rClient := clientTcp) once each, per cycle. On xDone or xError, I set xExecute := FALSE. I made sure to insert at least one full cycle with xExecute = FALSE (seen by the FB call) before re-triggering, so the falling edge is processed. Questions After a ReplyTimeout (xError = TRUE), what is the exact, correct sequence to re-trigger the same ClientRequest so a new message is actually sent again? Is a full cycle with xExecute = FALSE between two executions mandatory? Is there a known condition where, after ReplyTimeout, the ClientTCP keeps xConnected = TRUE but silently stops sending new requests (e.g. an internal request queue / _udiRequestId that gets out of sync)? udiNumMsgSent freezing at 23 while the FB shows _state = None is what puzzles me. Is the recommended pattern to drop the connection (ClientTCP.xConnect := FALSE for one cycle, then TRUE) on a request error, rather than keeping it alive? The docs state a request error does not close the connection, so I kept it open — but maybe that is the issue here. Could the large uiStartItem (50514) be relevant? It works right after download, so addressing seems correct, but I want to rule it out. Any guidance on the canonical recovery pattern after a request timeout would be greatly appreciated. Thanks!
Last updated: 2026-06-19
Post by jari-koivuluoma on JSON_Utilities_SL JSONFileWriter error NULL_POINTER
CODESYS Forge
talk
(Post)
FB jsonFileWriter gives a NULL_POINTER error, why? JSONByteArrayWriter works fine so the JSONData FB should be fine. The device is CODESYS Control Win V3 x64 in simulation mode. Codesys version is V3.5 SP16 Patch 5 JSON_Utilities_SL version is 1.3.0.0 Src: ST_TestStruct1a; TXT: WSTRING(10000); MakeJSON : BOOL := TRUE; SrcJSONData: JSON.JSONData; jsonFileWriter : JSON.JSONFileWriter; IF MakeJSON THEN MakeJSON := FALSE; // Struct data to JSONData FB F_TestStructToJSON(ADR(Src),ADR(SrcJSONData)); // Writing to file jsonFileWriter( xExecute := TRUE, sFileName := 'c:\JSONTEST\JSON.txt', eEncoding := JSON.Encoding.UTF_16, xAsyncMode := TRUE, jsonData := SrcJSONData ); // Waiting to finish WHILE jsonFileWriter.xBusy DO ; END_WHILE // To text jsonArrayWriter( xExecute := TRUE, pwData := ADR(TXT), udiSize := SIZEOF(TXT), jsonData := SrcJSONData, xAsyncMode := FALSE, ); END_IF
Last updated: 2023-09-08
Post by timvh on Communication between applications on same device/controller/runtime (Win RTE 3.5.20.20)
CODESYS Forge
talk
(Post)
If you have a Windows system (RTE), then why not run the CODESYS HMI as separate controller. This could easily be moved to another PC if required. In the HMI you could also still use the Symbolic Var access as part of the Data Source Manager, although maybe OPC is the preferred way to make it more future proof. Or what about the Remote Target Visu. Then you can reduce the load of the main controller, while still only having to create one application including Visualization. This is now also supported for Linux systems. See: https://content.helpme-codesys.com/en/CODESYS%20Control/_rtsl_target_visu_for_linux.html https://content.helpme-codesys.com/en/CODESYS%20Visualization/_visu_execute_remote_target_visu.html
Last updated: 2024-09-28
Post by msegon on OPC UA Client failed to connect
CODESYS Forge
talk
(Post)
Hi everyone, I would appreciate your help with a problem I've been working on for a few days but haven't been able to resolve. I'm trying to read data from Tridium Niagara 4.15 OPC UA Server, but I get the error BadCertificateInvalid. As far as I understand, you need to add a CA certificate somewhere to establish a secure connection, but I don't know where. 2025-10-27T09:06:43.247Z, 0x0000008d, 4, 0, 0, * ERROR: OpcUa_Channel_BeginConnect: Cannot create secure channel without certificates! 2025-10-27T09:06:43.247Z, 0x00001090, 4, 0, 0, * ERROR: Datasource: Error Failed (268468242) in state Connecting I tried communicating without encryption, but it doesn't find the point. Has anyone managed to establish encrypted OPC UA communication?
Last updated: 2025-10-28
Post by mozed on Connection to device closed
CODESYS Forge
talk
(Post)
Hello I am using an OpusA3 with version 3.5 SP17 Patch 3 as part of a project. I had no real problem before I encountered a problem that blocked me. The detection of the OpusA3 from Codesys is done correctly. The gateway is well configured and if I ping the gateway or the OpusA3 I receive the response correctly. The problem is that when I try to connect, the Opus screen freezes and a few moments later Codesys displays an error message ("connection to device closed"). I tried to change PC, to update the runtime, to change OpusA3 but the problem remains the same. I'm a little lost knowing that before it worked without problem. I went back to a previous version of the project (where it worked correctly) but the message still appears. Do you have any clues to solve the problem? Sincerely,
Last updated: 2023-08-23
Post by rossanoparis on How to configure CODESYSControl_User.cfg in order to use a specific network card for OPCUA Server
CODESYS Forge
talk
(Post)
Hello at all I'd like to know how to configure CODESYSControl_User.cfg in order to use a specific network card for OPCUA Server. In the past, I tried to ask in "Forge" about this topic, but I could find neither help nor document informations about it. Reading the file "codesyscontrol.log" I see these logs OPC UA Server Started: Hostname: NTLRPICTRL01, Port: 4840 URL: opc.tcp://NTLRPICTRL01:4840 Loopbackadapter activated. **All available networkadapters are used.** Multithreading activated. 3 workers used. My controller, which is a Linux PC, has got two network cards eth0 and eth1 I whant to use the card with name "eth0" as a server for OPCUA and keep the "eth1" free for other stuffs. Is it possible ? Best regards Rossano
Last updated: 2023-08-25
Post by tvm on Web Client (HMI) Disconnects from Webvisu (Weidmuller u-OS)
CODESYS Forge
talk
(Post)
ok, that's different than our issue then. We're using Schneider Electric M262 PLCs, and we've had it where certain web browsers cause the web server to only allow https connections, but it's not recoverable with a refresh. It usually requires a power cycle or even a full firmware flash. Your issue might have more to do with the timing. I don't know if it helps you, but we normally run our visu task at 200mS, with an update rate of 200mS. Seems to work. I went through this: https://faq.codesys.com/pages/viewpage.action?pageId=112525371 but it really seems like trial and error.
Last updated: 2023-09-06
Post by lraja on Codesys Programming with phyBOARD®-Pollux i.MX8M Plus
CODESYS Forge
talk
(Post)
Dear All, I am trying to Developing a PLC using phyBOARD®-Pollux i.MX 8M Plus. It is very difficult to find the suitable Codesys control for i.MX8M. I have tried to install CODESYS Control for Linux ARM SL , but unable install it and I am getting the following error, [INFORMATION] Executing SSH command on root@192.168.0.10: Retrieving architecture from package management [ERROR] Expected exit value of command failed: expected 0, received 127 [INFORMATION] Standard output: sh: line 1: dpkg: command not found Kindly check and help phyBOARD®-Pollux i.MX 8M Plus Link : https://www.phytec.eu/en/produkte/single-board-computer/phyboard-pollux/
Last updated: 2023-09-23
Post by andrej on Threads and TID created by CODESYSControl Win V3
CODESYS Forge
talk
(Post)
Hi all, for a deeper understanding of the Codesys RTE - I created a simple application with 3 IEC tasks (Ta,Tb,Tc) each with different priorities, and different cycle times. The application runs on Windows 10 in the Soft PLC CODESYS Control Win V3. If my understanding is correct, the RTE i.e. the Process CodesysControlService should spawn 3 threads (Th_a,Th_b,Th_c) which are executed with the defined cycle times, the priority of the threads should reflect the priority of the task set in the Codesys IDE. Does somebody have an idea, how I could identify the respective threads in Windows? Kind regards Andrej
Last updated: 2023-10-02
Post by benediktenger on Access project information of references library by script
CODESYS Forge
talk
(Post)
Hi, I need to accesss to project information of a referenced library in the project. At least I need the "Released" flag from these information to check that no project gets shipped with unreleased libraries. Unfortunally, I do not get this information by script. I archieved to get the library reference object and the managed library object but both won't give me this flag but only basic information like company, name, version, etc. Here is my code: # get the library refernces proj = projects.primary objects = proj.get_children(recursive=True) for object in objects: if object.is_libman: for libref in iter(object): if libref.is_placeholder and isinstance(libref.effective_resolution,str): print(libref) print(libref.name) # get the managed libraries libs = librarymanager.get_all_libraries() for lib in libs: print(lib.displayname) print(lib.version) Does somebody know how do get these information?
Last updated: 2023-10-23
Post by jerry-sorrells on Find Function: Object reference not set to an instance of an object.
CODESYS Forge
talk
(Post)
Build: CODESYS 3.5 SP19 Patch 1 (64-bit) Host OS: Windows 10 Target: Linux SL I have a project with programs in Structured Text and Ladder Diagram. When I try to use the Find function, it works for the Active Editor; however, when I try to use Find for the Entire Project, I get the error "Object reference not set to the instance of an object." I know what this error means in the context of the program, but I have no idea why the find function is returning this error. The variable I am searching does not matter: it happens with all variables. Any help with this will be greatly appreciated. I generally use the Find function quite often as I am developing and not having it is really slowing me down.
Last updated: 2023-10-23
Post by gurke258 on Codesys Safety EtherCAT with Beckhoff
CODESYS Forge
talk
(Post)
Hello :) We are currently configuring a system with Codesys as SoftPLC on a Linux system and with Beckhoff terminals. I have already gained some experience with Codesys and also with TwinCat incl. TwinCAT Safety. What is new to me now is Codesys in conjunction with Beckhoff safety terminals. We are currently using an EL1918 & EL2904 here. I have been able to integrate both terminals into my project, but I don't know how to interconnect them so that they communicate. That's a bit easier with Twincat ^^ Can any of you help me? I would also prefer a Codesys EtherCAT Safety training or webinar if anyone knows of one. Unfortunately I can't find such an event on the internet.
Last updated: 2023-11-07
Post by bahrt on Raspberry Pi GPIO mapping
CODESYS Forge
talk
(Post)
Hi I am about to configure ALL GPIOs on a Raspberry Pi 3 model B V1.2. It seems that I have limited understanding of why not all the IO’s become available with the corresponding mapped IO’s – the 'dwInUse' contains mapping of the inputs from GPIO0 to GPIO27. But 'dwInputs' are only showing GPIO0 to GPIO8 and GPIO15 as available inputs. These mentioned inputs work fine You will be able to watch the limited mapped IO activity here: https://drive.google.com/file/d/1zz4PBNBfRZBF2YkiJ2VQxw6L9MBVji7R/view?usp=sharing Can you please bring your best idea on why GPIO09 to GPIO14 and GPIO16 to GPIO27 state are not active (at a fixed zero state) in the dwInputs register? Thanks in advance. Best regards Andreas Bahrt
Last updated: 2023-11-21
Post by tomgr on Codesys 3.5.19 Control Win x64 - network adapter for EtherCAT master not working
CODESYS Forge
talk
(Post)
Hi guys I am trying to run on my laptop Codesys 3.5.19 Control Win x64 where I created a EtherCAT master. I have defined the controler, specified network adapter (my docking station) and everything worked as expected. Later I needed to test it on site (without docking station) so I changed the network adapter by EC master to my laptop network card. After that it shows "Network adapter opened" but no device can be found by scanning and in LOG is saying "SysEthernet: packet could not be sent, error code: -1". Same error with USB network card, but if I switch back to docking station, all is working again... Any idea what I'm doing wrong?
Last updated: 2023-11-22
Post by riccardo on Codesys SP19 patch 4
CODESYS Forge
talk
(Post)
Hallo everyone, I am working on new PLC of Weidmueller that uses Codesys SP19. I made the upgrade at the Patch 4 coming from patch 0. Unce made the upgrade everything is working well in the progect except the web visu user menagent. In the new version, when I perfom the login, I cannot use the keyboard of the device; the window where to digit the user name and password opens, the buttons "OK" and "Cancel" work but the system doesn't allow to put input from the device keybord, the mouse behaves as it is an image. If I active the virtual keypad or numpad it works otherwise nothing. I am wondering if it is a bug of the new package or if I must set something else. Thanks in advance, Riccardo.
Last updated: 2023-11-27
Post by jmorit on CAM Table - Quadratic velocity ramp with jerk limitation
CODESYS Forge
talk
(Post)
Hello, I'm working on setup a CAM table by using the Codesys CAM Editor. My purpouse is to obtain a quadratic velocity ramp with jerk limitation motion profile, for which i define the accel/decel phases with Poly5 segment type, but the problem is that due to the fact i can "only" adjust until the acceleration, and the jerk is always setup to 0, and i cannot change the jerk values, i cannot achieve the desired results, as i need to generate jerk steps. Is there any way it can be achieved with the editor, or maybe by using PLC runtime code? Thank you in advance for your help BR, Jordi Morito
Last updated: 2023-12-02
Post by cfam on Codesys Control for PLCnext (PLC - AXL F 2152)
CODESYS Forge
talk
(Post)
Good day All I would like to share some information on this site for the Codesys team as well for the future members using Codesys Control for PLCnext if it is allowed. I hope that i Post it in the correct spot. Subject: Codesys, Codesys Control for PLCnext Objective: Using the following Phoenix components to built a PLC Rack and run it on Codesys: Hardware and Software used 1. 2404267, AXC F 2152 - Controller 2. 1088136, AXL F BP SE6 - Module carrier 3. 1088129, AXL SE DO16/1 - Digital module 4. 1337224, AXL SE PD16 GND - Potential distributors 5. 1088127, AXL SE DI16/1 - Digital module 6. 1337223, AXL SE PD16 24V - Potential distributors 7. 1088123, AXL SE AO4 I 4-20 - Analog module 8. 1088134, AXL SE SC-A - Cover 9. Codesys v3.5 SP19 Patch 4 10. Codesys Control for PLCnext V4.10.0.0 Process: Firstly I built the Rack according to the Phoenix Project+ Software tool. Where I rebuilt it onto my test bench . I used the PLCnext Engineer IDE from Phoenix and all Communications where up and running and my PLC program executed successfully. THEN I tried the same PLC Layout with Codesys and Codesys Control for PLCnext. It was not successful and gave me the "Error: Local Bus not Running". I searched the web for answers but was unsuccessful in finding a solution. So I tried to change my configuration and found that the following Modules COULD NOT be recognized by Codesys Control. The result was that the Local Bus Failed to run. 1337224, AXL SE PD16 GND - Potential distributors 1337223, AXL SE PD16 24V - Potential distributors Example 1, Resulted in "Error: Local Bus Not Running": Module carrier slot 1: 1088129, AXL SE DO16/1 - Digital module Module carrier slot 2: 1337224, AXL SE PD16 GND - Potential distributors Module carrier slot 3: 1088127, AXL SE DI16/1 - Digital module Module carrier slot 4: 1337223, AXL SE PD16 24V - Potential distributors Module carrier slot 5: 1088123, AXL SE AO4 I 4-20 - Analog module Module carrier slot 6: 1088134, AXL SE SC-A - Cover Example 2, Result "Successful": Module carrier slot 1: 1088129, AXL SE DO16/1 - Digital module Module carrier slot 2: 1088127, AXL SE DI16/1 - Digital module Module carrier slot 3: 1088123, AXL SE AO4 I 4-20 - Analog module Module carrier slot 4: 1088134, AXL SE SC-A - Cover Module carrier slot 5: 1088134, AXL SE SC-A - Cover Module carrier slot 6: 1088134, AXL SE SC-A - Cover Result: Codesys or Codesys Control for PLCnext, has a PROBLEM to identify the following Modules. 1. AXL SE PD16 24V - Potential distributors 2. AXL SE PD16 GND - Potential distributors Hope that this information could be useful in future. Best regards Jaco Pretorius
Last updated: 2023-12-06
Post by hwopereis on How to use Application Trigger in Modbus TCP Server
CODESYS Forge
talk
(Post)
Hi, I'm currently reading and writing several registers with a Modbus TCP server as a subdevice of a Modbus TCP Client. If I read and write cyclically, there are no issues. The problem is this: I see there is also the option to write by "Application", which I would like to use. However, I don't know With the Modbus RTU client, I see there is a trigger variable, xTrigger, to trigger the writing tasks. However, I can't find any such trigger for the Modbus TCP Client. Does anybody know how to implement the trigger behavior for the Modbus TCP client? In particular, I struggle to find the exact "trigger" variable. I'm running Modbus Client version 4.4.0.0 Thanks in advance!
Last updated: 2024-07-01
Post by joschi2804 on Licensing info not available.
CODESYS Forge
talk
(Post)
Hi, maybe this fixes your problem. At least this was our issue back then. We tried to run the codesys runtime environment on an embedded Linux system. The problem on our side was that we changed the WORKDIR directory in the /etc/init.d/codesyscontrol script to /home/user/codesys, but we forgot to copy all files (including the hidden files) from the initial WORKDIR (I am not sure but I guess the initial WORKDIR was /var/opt/codesys) to the new one. After copying those files and restarting codemeter and codesyscontrol, we were able to upload licenses. Hope this help BR Josef
Last updated: 2024-07-10