Post by peterkcontrols on Codesys Network driver install for Codesys Control RTE x64 CODESYS Forge talk (Post)
Hello I am trying to download my project onto my Codesys Control RTE x64 soft PLC. and I have had an issue when downloading. [FATAL ERROR] Unresolved reference: 'SYSETHERNETADAPTEROPEN' [FATAL ERROR] Unresolved reference: 'SYSETHERNETADAPTERCLOSE' [FATAL ERROR] Unresolved reference: 'GETNUMBEROFADAPTERS' [FATAL ERROR] Unresolved reference: 'GETADAPTERINFO' [FATAL ERROR] Unresolved reference: 'SYSETHERNETIPFRAMERECEIVE' [FATAL ERROR] Unresolved reference: 'SYSETHERNETETHFRAMESEND' [FATAL ERROR] Unresolved reference: 'SYSETHERNETETHFRAMERECEIVE' [FATAL ERROR] Unresolved reference: 'SYSETHERNETIPFRAMESEND' [FATAL ERROR] Unresolved reference: 'SYSETHERNETFRAMERELEASE' Looking on the forum I have found other people had to install the network driver, which I have done following this youtube video by codesysGroup: https://youtu.be/10oj4wABaKc?si=664l83JXUGQSDlAe I have added the network driver, please see attached image. I have checked my BIOS to make sure my secure boot status is disabled, see attached image. when I go to component manager, the drop down menu doesnt have the new network adapter, see attached image. I have not yet purchased or installed any licenses is that what I am missing? What other reason is there that I can't download to the runtime. Thanks
Last updated: 2025-03-18

Post by razebones on sdo read write codesys 3.5 CODESYS Forge talk (Post)
ENG For some reason, I can't bind a variable to the data parameter. Also, why does only the sdo_read4 function work for me? I also can't write through sdo_write4. I can only view the received values via sdo_read4. Please help me with this task. Moreover, I tried to write the values through sdo write 4 and for a while the data stopped being written and I overwritten it manually and sdo read4 started working again and at the same time they do not want to work in the main task. RU Я не могу почему то привязать переменную к параметру data. Так же у меня почему работает только функция sdo_read4 так же не могу записать через sdo_write4. Могу только просматривать полученные значения через sdo_read4. Помогите пожалуйста с этой задачей. Причём я попытался записать значения через sdo write 4 и у меня на какое то время перестали записываться данные и перезаписал вручную и sdo read4 начал работать снова и одновременно они не хотят работать в main task.
Last updated: 2025-04-01

Post by macman on Codesys 3.5 OPC UA Client to Kepware OPC UA Server CODESYS Forge talk (Post)
Hi, I have problem with connecting Wago PLC WAGO 750-8212/0025-0002 configured as OPC UA client to Kepware OPC UA Server. I am using Codesys 3.5.19.70. What I did so far. To the Codesys project I added object Data Source Manager and configured connection OPC UA like below: pic 1 Then I can browse the OPC server tags in “Variables” tab after prior trust on the server side of the client certificate created in the “Communication” tab: pic 2 Additionally second certificate has been created in Codesys for runtime process in “Security screen” as well as the server certificate was approved here: pic 3 But when I compiled project, downloaded it to PLC and go to RUN I can’t read selected in “Variables” tab, OPC Server tags. I am getting such error (ID: 7001): pic 4 All two PLC certificates has been trusted in OPC server (Kepware) side: pic 5 and Kepware server configuration look like this: pic 6 I can easily connect using third party OPC UA client UaExpert to Kepware server without problem. In attachment I added also log from Kepware OPC UA server. pic # - this specifies the number of a concrete graphic from one of the collective in attachment
Last updated: 2025-04-02

Post by rene-h on ClientFilter used the same Client ID 2 times - Bug? CODESYS Forge talk (Post)
Hello, like the topic name says, i have a problem on one Visu which i cannot reproduce on another Visu. We filter buttons with input locks and visible items with [CURRENTCLIENTID] on different WebVisu's with different ID's, and one time the itfClient used the same Client ID for 2 Clients, so the Visualization on the first ID was wrong, because that one which connected after did not have the same permissions like the first, so the first one was blocked. We read the Clients with the VisuClientIteration project: //count active clients gCli.iNumberOfClients:=gCli.iNumberOfClients+1; // if client is active write data to global struct IF gCli.iNumberOfClients > 0 THEN gCli.astClientInfo[gCli.iNumberOfClients-1].iClientID:=itfClient.ClientId ; gCli.astClientInfo[gCli.iNumberOfClients-1].stCurrentVisu:=itfClient.CurrentVisuName; gCli.astClientInfo[gCli.iNumberOfClients-1].wsUserName:=itfClient.UserName; gCli.astClientInfo[gCli.iNumberOfClients-1].sIpAddress:=itfClient.GetIPv4Address(); gCli.astClientInfo[gCli.iNumberOfClients-1].ClientType:=itfClient.ClientType; END_IF Runtime from the device: 3.5.19.20 Codesys we use: 3.5.20.10 I added a screenshot where the same ID exists 2 times. Thanks for your answers.
Last updated: 2025-05-14

Post by kuegerls on Programmatically clearing or syncing Data Source Manager cache? CODESYS Forge talk (Post)
Hi everyone, is there a way to programmatically clear the cache of the Data Source Manager in CODESYS so that variable values are re-synchronized from the OPC UA server (Symbol Configuration with OPCUA features)? Alternatively, is it possible to trigger a manual synchronization of data source variables from within the application code at runtime? Here’s the situation: A variable is first written by the OPC UA client to the server in one state of a state machine and changes to another state – so the initial communication works. Later, the server changes the variable value, but the client does not receive or reflect the updated value, unless the variable is actively written again. I’m looking for a way to force the client (data source manager) to re-read or refresh the variable state from the server, possibly by clearing the internal cache or triggering a sync. Any ideas or suggestions would be greatly appreciated! Thanks!
Last updated: 2025-05-23

Post by chris--o on ModbusTCP RaspberryPi zu Fronius Wechselrichter CODESYS Forge talk (Post)
Hallo zusammen, ich hab ein kleines Problem bei einer Modbus TCP-Verbindung von meinem RaspberryPi (ML) zu einem Fronius Wechselrichter. Ich habe mir die CodeSys Version 3.5SP20 heruntergeladen und die Runtime auf dem RaspberryPi mit aktualisiert. Gerät ist ein Fronius Symo 6.0-3-M Folgende Konfiguration habe ich im Wechselrichter (Siehe Bilder). Laut Registertabelle fangen die Daten bei Adresse 40001 an und gehen im Modus int+SF bis 40120 Ich habe mir also im Ethernet-Adapter einen Modubus Master und darunter einen ModbusSlave angelegt. Der Slave (Fronius) hat bei mir die IP 192.168.2.46 dazu UnitID und Port. Ich habe dann einen Kanal mit den 120 WORDS und dem OFFSET angelegt. Wenn ich nun die Konfiguration übertrage , scheint erst mal alles zu passen.. aber es flackert immer wieder ein Fehler beim Slave auf (kann nicht erkennen welcher und finde auch keine Diagnose). Es werden auch keine Daten übertragen. Alles bleibt auf 0. Ich muss dazu sagen, dass ich noch eine weiter Modbus TCP Verbindung zu einer anderen SPS habe. Die funktioniert wunderbar. Normalerweise sollten ja auch mehrere Verbindungen gleichzeitig möglich sein oder? Wäre top, wenn ihr mir helfen könntet, den Fehler zu finden. LG Chris
Last updated: 2025-06-30

Post by gmau on RS232 Communication in CODESYS Control RTE V3 CODESYS Forge talk (Post)
Hello, I would like to implement RS232 communication into CODESYS Control RTE V3. I was writing the program testing it on CODESYS Control Win V3, where it worked fine. When I changed it to RTE, the communication was on, but I cannot send the data between PLC and scale - there is no or little response from scale - mostly one time receive and that is it. On Win V3 it was working fine. I read that I am supposed to configure CODESYSControl file for a proper communication using RTE, but even after that I can not get a stable and working communication. I am attaching my CODESYSControl and CODESYSControlUser data below, as well as I am sending the code from communication function. The communication should be through COM1 port of PC. CODESYS Version: CODESYS V3.5 SP21 + (64-bit) Runtime + Version: CODESYS Control RTE V3 Version 3.5.21.0 / CODESYS Gateway V3 - x64 Version 2.5.21.0 I would be much gratefull for any help. Sincerely,
Last updated: 2025-07-16

Post by gvdb on Raspberry Pi 4 mod B icm codesys linking USB serial device (arduino) to com port CODESYS Forge talk (Post)
Raspberry Pi 4 Codesys 3.5.20 sp3 Codesyscontrol 4.15.0.0 based on sdk 3.5.21.0 Hi all, I have found a lot of topics but none of them get me on the right path, therfore i started a new post. Usually i work with plc based systems and codesys but now im trying to create an project where i read out a serial data stream from an arduino connected by an USB port. in the future this need to be more arduino's but first trying to make it work with one I had my program working but i needed to update my raspberry pu to the letest version to get the mimo screen working. Now i tried several rules in the CODESYSControl.cfg and/or CODESYSControl_User.cfg files but i never get the com port opened. At this moment i have an file CODESYSControl_User.cfg with entry: [SysCom] Linux.Devicefile.1=/dev/ttyUSB0 I tested the connection with minicom and the data runs fluently. Can somebody help me with what could be wrong? the com port states ERROR_UNKNOWN 5004 when i tried to open.
Last updated: 2025-07-17

Post by kurtk on dynamic modbus devices CODESYS Forge talk (Post)
I am CODESYS neophyte getting my wheels on. My goal is to re-platform an existing PLC application written in 61131 ST I've got the majority of the code/variables in a compilable form - excluding all the IO and comms nuances I am not sure whether this the right forum An important functionality which I implemented on the other platform was totally dynamic modbus devices... Most configurations I have come across impose static MB configs in which all configured devices MUST be present and functional... I have monkeyed around with MB enough to know that herding a half dozen MB cats into a working config can be tricky. I just do them one at a time and dynamically turn them on/off in whatever combination is convenient with ID, IP, baud, parity etc being runtime tweakable. I am totally curious whether this is possible with codesys, or whether its device configuration corrals one into a static cage which requires re-building the code to support flexible variations. Best regards
Last updated: 2025-08-19

Post by timvh on Codesys virtual control redundancy CODESYS Forge talk (Post)
I think it depends on what you consider as redundant. Is it allowed to plug the network cable in another device (server), move the USB key with license to the other device (server) and then start it up? Or should it automatically switch over within msec and take over the communication with the I/O flawlessly without noticing the switchover? We helped several customers setting up the CODESYS Redundancy functionality and the nice thing is that when you have it up and running, you can easily switchover from active to passive and when you download a new applicaiton, CODESYS handles the update of boot project on the passive controller automatically. Sure this will require an additional license and the license for redundancy, but if your installation is that critical it should be worth it. Please contact us (Extend Smart Coding) if you need any further information. We could help you setup the configuration and possibly provide the licenses for it (I noticed you are situated in the Netherlands).
Last updated: 2025-09-04

Post by ranadheer on Codesys Control for PLCnext (PLC - AXL F 2152) CODESYS Forge talk (Post)
Hello Jaco Pretorius, I came across your post regarding CodeSys control for PLCnext. I’m currently working on a similar setup and had a quick question. Here am using the CODESYS V3.5 SP21 PATCH2 ,VERSION 3.5.21.20 , and Downloaded extension package 4.16.0.0 (old versions are not available in the extension CodeSys installer) Devices used here are: BUS COUPLER : 2403869 BK PN TPS Module carrier slot 1 : 1088127 AXL SE DI16/1 Module carrier slot 2 : 1088062 AXL SE AI4 | 4-20 Module carrier slot 3 : 1088129 AXL SE DO16/1 Module carrier slot 4 : 1088123 AXL SE AO4 | 4-20 -->Start a New Project Type: Standard Project Device: CODESYS Control Win V3 x64 Language: Structured Text -->Install GSDML File Navigate to: Tools > Device Repository > Install Select the GSDML file path (downloaded from Phoenix Contact for device coupler Part ID: BK PN TPS 2403869) Click Renew Device Repository Close the dialog -->Add Device to Project -->Right-click on Devices > Add Device Issue: Devices from the repository are not available to select or call into the project! I’d really appreciate any guidance or suggestions you can offer. Best Regards Ranadheer Reddy
Last updated: 2025-09-09

Post by ranadheer on Codesys Control for PLCnext (PLC - AXL F 2152) CODESYS Forge talk (Post)
Hello Jaco Pretorius, I came across your post regarding CodeSys control for PLCnext. I’m currently working on a similar setup and had a quick question. Here am using the CODESYS V3.5 SP21 PATCH2 ,VERSION 3.5.21.20 , and Downloaded extension package 4.16.0.0 (old versions are not available in the extension CodeSys installer) Devices used here are: BUS COUPLER : 2403869 BK PN TPS Module carrier slot 1 : 1088127 AXL SE DI16/1 Module carrier slot 2 : 1088062 AXL SE AI4 | 4-20 Module carrier slot 3 : 1088129 AXL SE DO16/1 Module carrier slot 4 : 1088123 AXL SE AO4 | 4-20 -->Start a New Project Type: Standard Project Device: CODESYS Control Win V3 x64 Language: Structured Text -->Install GSDML File Navigate to: Tools > Device Repository > Install Select the GSDML file path (downloaded from Phoenix Contact for device coupler Part ID: BK PN TPS 2403869) Click Renew Device Repository Close the dialog -->Add Device to Project -->Right-click on Devices > Add Device Issue: Devices from the repository are not available to select or call into the project! I’d really appreciate any guidance or suggestions you can offer. Best Regards Ranadheer Reddy
Last updated: 2025-09-09

Post by alexgooi on Licensing info not available. CODESYS Forge talk (Post)
Sorry for the question, but I'm not completely getting the idea here, could you be more specific, maybe give an example? I'm now in a state where I don't have a softcontainer on my license server anymore (even after reinstalling from the Codesys-IDE). I tried reaching the webserver of Codemeter but when I do that I get redirected to http://"IP":22352 This is not reachable, afterwards I installed lynx on my Debian machine (command line only). From here I could reach the webserver and toggle the network server setting, but unfortunately this did not help. I also tried to changed the remote read setting to 1 (in the Server.ini file). But after a Codemeter reboot this is overwritten to 0. I have the feeling that it should be much easier to get a license to work, am I missing some checkbox somewhere? Is there a tutorial (or manual) that explains the licensing sequence step by step, because I'm pretty stuck.
Last updated: 2025-10-01

Post by timvh on Licensing info not available. CODESYS Forge talk (Post)
In the VPLC configuration settings there is an entry for the IP address of the license server. In this setting fill in the IP address of your device (host IP address). Then when the virtual PLC starts up, it will get the license from the license container on the host. You can do this for all VPLC's running on your device. The VPLC will always take the smallest license which fits the required license. So if you have 2 licenses for VPLC's with small and large applications, then this will work fine if you start up one VPLC which requires the small license and the other which requires the large license. PS, personally I find it much easier, especially for testing and experimenting, to activate the licenses on a CODESYS (USB) key. This is easy to activate (on your development PC) and easier to move to another device. Addtionally you don't loose the license when you need to install a completely new image on the device.
Last updated: 2025-10-02

Post by nicetuxedo on Can not activate license on Raspberry pi CODESYS Forge talk (Post)
Hello everyone, I'm hoping for some assistance with a license activation issue: a software crash has left my license in a strange state. Here is the sequence of events: I purchased a new license for the Raspberry PI from the official CODESYS web store. I opened the CODESYS and started the online activation process using the ticket number I received. During the activation, the CODESYS software threw an exception and crashed. I was not able to see if the activation completed. After restarting CODESYS, I attempted to run the activation process again with the same ticket number. The License Manager now gives me an error stating that the ticket has already been activated/used. I am now stuck because my installation is not licensed, but the activation server believes my ticket has been consumed. Has anyone encountered this before? Is there a way to have the ticket status reset?
Last updated: 2025-10-08

Post by mavitia on Application based license problem - Modbus TCP CODESYS Forge talk (Post)
I am running ubuntu on a raspberry pi, and installed an application based license Control Basic M on it, it runs a demo program fine, does not timeout etc. however, when I add a modbus TCP device, I start getting errors: <Entry severity="error" component="CmpApp" user="nobody" timestamp="12/18/2023 3:49:42 PM" infoId="24">Online change denied. Application Application is in exception state!</Entry> <Entry severity="error" component="CmpApp" user="nobody" timestamp="12/18/2023 3:49:42 PM" infoId="68">Download failed: Application=Application</Entry> <Entry severity="exception" component="CmpApp" user="nobody" timestamp="12/18/2023 3:49:41 PM" infoId="0">Application app=Application has invalid license metrics!</Entry> the modbus tcp slave runs, and the counter ticks up, however, when I call the variables on the %IX0.0 in my program, and try to upload the changes, I am getting the error messages which stop the program as far as I understand, the application based, M includes 2 fieldbus instances, but on the other side is fairly new, anything obvious I am missing out here?
Last updated: 2023-12-18

Post by giackanto on Eoe issues with Windows and Linux CODESYS Forge talk (Post)
Hello, I've been trying to use EoE for communication between a Windows PC and an M753 drive from Control Technique. Despite following some online guides (https://content.helpme-codesys.com/en/libs/EtherCATStack/4.3.0.0/Ethernet_over_EtherCAT/fld-Ethernet_over_EtherCAT.html) I haven’t had any success. Both are connected to a Debian device where RTE is running: The PC is connected via the Ethernet port. The drive is connected via the EtherCAT port. I'm unable to ping the drive from my Windows PC. Here is my configuration: On Debian: (See attachments 1, 2, 3) enp1s0 = Ethernet port enp2s0 = EtherCAT port tap2 = TAP device IP forwarding and routes are both configured. On Windows: (See attachments 4, 5) On Codesys: (See attachments 6, 7) Version: Windows 11 Debian GNU/Linux 11 Codesys 3.5.17 Control for Linux SL 4.7.0 EtherCAT 4.4.0 With this configuration, I can ping the TAP device, but not the drive (See attachment 8). Could someone explain how to properly configure all these settings? Thank you, GA
Last updated: 2023-12-19

Post by chalk on No source code available CODESYS Forge talk (Post)
Hello, This is my first time using Codesys, I am trying to add EtherNetIP communication to a Raspberry PI. I’ve added the EtherNetIP Adapter configured the network setting and added some modules to the pi but when I download the project it generates the following error: “There is no source code available for the object because it is in the compiled library ‘cip object, 4.5.1.0 (3s – smart software solution gmbh)’. Do you want to browse for the original library in order to display the source code? There are 2 errors in the log which are: SOURCEPOSITION App=[Application] area=3, offset=332760 EXCEPTION [Application] occurred: App=[Application], Task=[ENIPAdapterServiceTask] I can’t for the life of me work out how to get around this. I can’t find the source code anywhere or any information regarding this error. I’m using Codesys V3.5 SP19 Patch 3, the version of the Ethernet adapter is 4.5.1.0 and the version of the modules is 4.1.0.0. Any help on this will be greatly appreciated. Thanks
Last updated: 2024-02-02

Post by yannickasselin on Connect to remote PLC via local pc and teamviewer CODESYS Forge talk (Post)
Yes it is possible. I did it a lot of times using TeamViewer VPN. Unfortunately, TeamViewer VPN only works on Windows. If the remote PLC is a Codesys runtime running on Windows, you should be able to login directly using TeamViewer VPN if it is installed on the PC/PLC. If it is not Windows based, you can still do it but you need to have a Windows based PC acting as a gateway in the middle. In this case you need to enable IP Forwarding on the Windows remote PC (the gateway) and you need to setup the gateway IP address on the PLC to be the address of the Windows PC. Then you need to add a route on your local PC to point to the gateway PC for Codesys communication. I know it may not be detailed enough but I did not want to make a whole tutorial on how to do it. Bottom line, it is possible. I do it all the time.
Last updated: 2024-02-02

Post by tim-roelant on Profinet fault with codesys control V3 - Receive packet error CODESYS Forge talk (Post)
I have set up a brandnew Beckhoff panel pc with a codesys control runtime V3. I configured it together with 2 profinet field devices: a 16in/16out IO module from Turck and an MTS linear encoder. The machine works fine untill all of a sudden the communication breaks and the profinet participants become unreachable. At that point I can still ping the device, but the profinet master does not find them anymore: When i do a scan they are not found. When i do a cold restart, the profinet master becomes active again and the devices are found again. In the log i get Ethercat packet receive error: sysethernet. I am a little confused, there is no ethercat device in the device tree. I already set the send clock and the reduction ratio to higher values, but without result. Can codesys be configured, so that the communication re-establishes without doing the cold reset? This is very annoying and is causing a lot of prodution losses. regards Tim
Last updated: 2024-02-27

Post by tim-roelant on Profinet fault with codesys control V3 - Receive packet error CODESYS Forge talk (Post)
I have set up a brandnew Beckhoff panel pc with a codesys control runtime V3. I configured it together with 2 profinet field devices: a 16in/16out IO module from Turck and an MTS linear encoder. The machine works fine untill all of a sudden the communication breaks and the profinet participants become unreachable. At that point I can still ping the device, but the profinet master does not find them anymore: When i do a scan they are not found. When i do a cold restart, the profinet master becomes active again and the devices are found again. In the log i get Ethercat packet receive error: sysethernet. I am a little confused, there is no ethercat device in the device tree. I already set the send clock and the reduction ratio to higher values, but without result. Can codesys be configured, so that the communication re-establishes without doing the cold reset? This is very annoying and is causing a lot of prodution losses. regards Tim
Last updated: 2024-02-27

Post by tim-roelant on Profinet fault with codesys control V3 - Receive packet error CODESYS Forge talk (Post)
I have set up a brandnew Beckhoff panel pc with a codesys control runtime V3. I configured it together with 2 profinet field devices: a 16in/16out IO module from Turck and an MTS linear encoder. The machine works fine untill all of a sudden the communication breaks and the profinet participants become unreachable. At that point I can still ping the device, but the profinet master does not find them anymore: When i do a scan they are not found. When i do a cold restart, the profinet master becomes active again and the devices are found again. In the log i get Ethercat packet receive error: sysethernet. I am a little confused, there is no ethercat device in the device tree. I already set the send clock and the reduction ratio to higher values, but without result. Can codesys be configured, so that the communication re-establishes without doing the cold reset? This is very annoying and is causing a lot of prodution losses. regards Tim
Last updated: 2024-02-27

Post by tim-roelant on Profinet fault with codesys control V3 - Receive packet error CODESYS Forge talk (Post)
I have set up a brandnew Beckhoff panel pc with a codesys control runtime V3. I configured it together with 2 profinet field devices: a 16in/16out IO module from Turck and an MTS linear encoder. The machine works fine untill all of a sudden the communication breaks and the profinet participants become unreachable. At that point I can still ping the device, but the profinet master does not find them anymore: When i do a scan they are not found. When i do a cold restart, the profinet master becomes active again and the devices are found again. In the log i get Ethercat packet receive error: sysethernet. I am a little confused, there is no ethercat device in the device tree. I already set the send clock and the reduction ratio to higher values, but without result. Can codesys be configured, so that the communication re-establishes without doing the cold reset? This is very annoying and is causing a lot of prodution losses. regards Tim
Last updated: 2024-02-27

Post by dominggus on when going online, stuck on "Syncing file "visuelemsdatetime.tl_datetime.txt" CODESYS Forge talk (Post)
Hi, We are currently using a Raspberry Pi 4 CM4 module in a EdgeBox RPI 200 - Industrial Edge Controller running the latest CODESYS Runtime Package 4.11.0.0. On the PC (actually an Intel Macbook Pro running Windows 10 in Parallels) we run CODESYS V3.5.19.50. Yesterday end of day when I was about to logoff and head home, I wanted to send the latest build to the Raspberry I clicked the Login button to compile a new version and then sync the application and all the files, it get's stuck on the last file to sync (see attached screenshot). This takes eternally, although sometimes, when I use my SFTP client (Cyberduck) and go into the raspberry and refresh the directory /var/opt/codesys/PlcLogic/visu/, or when I open the actual file visuelemsdatetime.tl_datetime.txt, it gets un-stuck (forcing a refresh, which might fix the syncing issue) and CODESYS continues and I can click the Start button to start the application. But this SFTP force refresh trick does not always help either... What could be the issue here? network connectivity? Can someone please help me out?
Last updated: 2024-03-02

Post by wmoon on Licensing info not available. CODESYS Forge talk (Post)
That command can't excute on my device. I installed CODESYS into Hilscher's product using container Here is the Docker file what I used. I'm not sure if this docker file have a problem. If it have a problem, please let me know how to download the files into my device using ftp server. FROM arm64v8/debian:11.6 RUN apt-get update RUN apt-get install -y wget sudo unzip libusb-1.0-0-dev procps ENV CDS_VERSION "4.10.0.0" ENV EDGE_VERSION "4.10.0.0" ENV URL "https://store-archive.codesys.com/ftp_download/3S/LinuxARM64/2302000039/$CDS_VERSION/CODESYS%20Control%20for%20Linux%20ARM64%20SL%20$CDS_VERSION.package" ENV EDGE_URL "https://store-archive.codesys.com/ftp_download/3S/EdgeGatewayLinux/000120/$EDGE_VERSION/CODESYS%20Edge%20Gateway%20for%20Linux%20$EDGE_VERSION.package" RUN wget --output-document=/tmp/codesys.package $URL && \ unzip -p /tmp/codesys.package 'codemeter.deb' > /tmp/codemeter.deb && dpkg -i /tmp/codemeter.deb && \ unzip -p /tmp/codesys.package 'codesyscontrol.deb' > /tmp/codesys.deb && dpkg -i /tmp/codesys.deb RUN wget --output-document=/tmp/edge.package $EDGE_URL && \ unzip -p /tmp/edge.package '*arm64.deb' > /tmp/edge.deb && dpkg -i /tmp/edge.deb EXPOSE 11740 1217 11743 ENTRYPOINT ["/bin/sh", "-c" , "/etc/init.d/codesyscontrol start && /etc/init.d/codesysedge start && tail -f /dev/null"]
Last updated: 2024-03-20