Post by mehakfatima on Need Help Configuring Energy Analyzers via Modbus TCP & RTU (RS-485) in CODESYS 3.5
CODESYS Forge
talk
(Post)
Hello everyone, I am currently working on reading data from energy analyzers using Modbus TCP and RTU (RS-485). In my previous software, I used the following method to add slave devices (i have attached the image) and configure registers: Add the Modbus slave device. Configure the communication parameters (baud rate, parity, etc.). Define the registers and their addresses for data retrieval. Now, I am trying to achieve the same in CODESYS 3.5, but I am not sure how to configure the Modbus master, add slave devices, and set up the registers properly. If anyone has experience with Modbus TCP/RTU setup in CODESYS 3.5, I would really appreciate your guidance! A step-by-step explanation or any references/tutorials would be extremely helpful.
Last updated: 2025-03-13
Post by benemenn on OPC UA Method - How to wait for result?
CODESYS Forge
talk
(Post)
so from what i've learned. Codesys OPCUA Server can only provide OPC UA Methods, when they are created in an XML Model beforehand. So you have to create the XML Model with OPC UA Methods. Then load that model into codesys and create the IEC Blocks. This is automated Code and will create all the variables and Methods from your XML Model. Then they will be displayed on discovery with an OPC UA Client. As far as I understood. There is no way for Methods to be shown in OPC UA when not using an external XML Informationmodel. Codesys can not yet create the informationmodel on itself. Regards
Last updated: 2025-04-02
Post by benemenn on OPC UA Method - How to wait for result?
CODESYS Forge
talk
(Post)
so from what i've learned. Codesys OPCUA Server can only provide OPC UA Methods, when they are created in an XML Model beforehand. So you have to create the XML Model with OPC UA Methods. Then load that model into codesys and create the IEC Blocks. This is automated Code and will create all the variables and Methods from your XML Model. Then they will be displayed on discovery with an OPC UA Client. As far as I understood. There is no way for Methods to be shown in OPC UA when not using an external XML Informationmodel. Codesys can not yet create the informationmodel on itself. Regards
Last updated: 2025-04-02
Post by rossanoparis on Internal Error (ARM): Unsupported conversion! With new version v3.5 SP21
CODESYS Forge
talk
(Post)
I have updated CODESYS development tool to the version v3.5 SP21 (64bit) The previous version was v3.5.20.40 Compiling an existing application with the new evelopment tool I get the following error. kunbusiodrvrevpibridge, 1.4.1.0 (kunbus gmbh): IoDrvScanModules [IoDrvRevPiBridge](Line 51, Column 1 (Impl)): Internal Error (ARM): Unsupported conversion! This error was not reported in the previous compiler version and is now highlighted in a third-party library, which I cannot change or modify. The error is due to the following conversion: m_udiError := TO_UDINT(excCode); . The excCode variable is a system type, declared as shown below, and should be converted to a UDINT excCode : __SYSTEM.ExceptionCode; m_udiError: UDINT; . I would appreciate it if someone could provide feedback on this issue.
Last updated: 2025-04-15
Post by alex2 on Error Highlighting Not Working in CODESYS v3.5 SP10 on Windows 11
CODESYS Forge
talk
(Post)
Hello everyone, I'm currently using CODESYS v3.5 SP10 on Windows 11, and I've noticed that syntax errors are not automatically underlined in red as they normally should be. Is there a specific setting that needs to be enabled for this feature to work? If so, could you please let me know where to find it? I’ve already tried uninstalling and reinstalling CODESYS, but that didn’t resolve the issue. Also, i have a teammate who have exactly the same computer as me and he didnt encounter any issue. Thank you in advance for your help!
Last updated: 2025-05-13
Post by kut69 on Retain / Persistent Variables in Codesys for Raspberry Pi
CODESYS Forge
talk
(Post)
Hi, I am interested in details about the .ret file in the filesystem. I have already a project where the file is used (write on demand, read by start) and I want to share it as 'default input' for test devices using the identical application. Opening the .ret file content in a hex editor (I only use a single string retain var) I asked myself what the meaning of the first 24 bytes is. It neither contains a handle to the application nor a reference to the variable. Is this maybe a timestamp? Or a CRC/checksum? Regards, Thomas
Last updated: 2025-05-19
Post by edson-bueno on IFM Controller Connection Issue
CODESYS Forge
talk
(Post)
Hi, Could you please send an print of your ethernet adapter info? Ip addr Subnet Mask Default Gateway Also, check if the gateway service is active in your windows. Win+R > services.msc > Look in the list CODESYS Control Win V3 x64 Gateway OR CODESYS Gateway V3 Hook up the M12 code D into the ETH port, supply the controller, it should apperars to you. Make sure when you try to connect with the controller, the target of your project has to match with the controller. Otherwise, click on the device in the devices tree > Communications Settings tab > Device > Options > And disable "Filter Network Scans by Target ID". Good luck.
Last updated: 2025-05-29
Post by durallymax on Dynamical scaling of bar graph without the bar itself
CODESYS Forge
talk
(Post)
I'm a fan of the analog indicators from ISA101. To recreate these, I use a number of rectangles that are dynamically sized and colored based on the input configuration. To keep it standard and easy, everything is built around 100px height. Then when instantiated in a frame, it can be resized as needed with the math remaining the same. The math logic is in a METHOD called by the rear most rectangle. These indicators do not use a "filling" bar graph, rather a fixed bar graph with a carrot to track the current value.
Last updated: 2025-06-06
Post by kareem-pt on Velocity is too low even though correct value is reported
CODESYS Forge
talk
(Post)
Hello, I'm playing around with a single axis. I've setup scaling and set the drive to move 360 degrees in the commissioning tab. The axis does move 360 degrees, but it moves much slower than the 360 degrees per second that I set for the velocity. It seems to be about 3 times slower (taking about 3 seconds instead of 1). This is despite the set and actual velocity both being displayed as 360. The acceleration, deceleration and jerk are all set to very high values. I'm just running this on my PC, using demo mode (no license purchased yet). I've attached a video showing the problem. Does anyone know what the problem could be? Thanks
Last updated: 2025-06-06
Post by pauloricardoss on Codesys Control Raspberry PI 4.10.0 - missing 'Update Raspberry PI' option
CODESYS Forge
talk
(Post)
I am having the same problem. 'Update Raspberry PI' disappeared from the 'Tools' menu. Using RaspberryPI 3B+, Codesys V3.5 Sp21 + RaspberryPI Package 4.16. I installed the package as Administrator, executed Codesys as Administrator I also tried to connect using the deploy (even with ssh and everything enabled on the RaspberryPi I received password denied). I used in the past the same equipment with Codesys V3.5 Sp18 and RaspberryPI Package 4.08, it was really easy. (I also did a brand new RaspbianOs installation to make sure that nothing affect the connection). Anyone, knows how to fix it? Thanks,
Last updated: 2025-06-13
Post by mondinmr on Why SysPipeWindows is not implemented in RTE?
CODESYS Forge
talk
(Post)
This library would be very useful for IPC communications. Using a UDP socket on localhost is unpredictable, as with slightly loaded machines it does not even guarantee packet delivery locally. Using TCP creates a lot of overhead. Message named pipes would be an excellent solution for Windows RTE. On Linux, since the release of the extension package, there is no issue, as it is sufficient to develop a component. However, although now 90% of our clients understand that Linux runtimes are better in every way compared to Windows RTE, especially from the security aspect (Not in kernel space) and the issues with Windows updates, 10% stubbornly insist (sometimes for trivial commercial reasons) on using Windows. Managing IPC with circular buffers in shared memory is quite ugly, or rather really ugly and unaesthetic. In the manuals, I saw the SysPipeWindows libraries, so I decided to test them, but unfortunately, I noticed that they are not implemented for RTE devices. Technically, I could try to open them as regular files, but SysFileOpen returns 16#27 or 16#39 depending on how I set the name (direction of the slashes). Here is the code to create shared memory and named pipes. Shared memory work great, named pipes no! #ifdef Q_OS_WIN32 SECURITY_ATTRIBUTES sa; SECURITY_DESCRIPTOR sd; InitializeSecurityDescriptor(&sd, SECURITY_DESCRIPTOR_REVISION); SetSecurityDescriptorDacl(&sd, TRUE, NULL, FALSE); sa.nLength = sizeof(SECURITY_ATTRIBUTES); sa.lpSecurityDescriptor = &sd; sa.bInheritHandle = FALSE; const wchar_t* name = L"Global\\ShmTest"; HANDLE hMapFile = CreateFileMapping( INVALID_HANDLE_VALUE, NULL, PAGE_READWRITE, 0, sizeof(SharedData), name); if (hMapFile == NULL) { qCritical("Error creating shared memory"); return 1; } data = static_cast<SharedData*>(MapViewOfFile(hMapFile, FILE_MAP_ALL_ACCESS, 0, 0, sizeof(SharedData))); if (data == NULL) { qCritical("Error mapping shared memory"); return 1; } HANDLE hPipe = CreateNamedPipe( TEXT("\\\\.\\pipe\\MyPipe"), PIPE_ACCESS_DUPLEX, PIPE_TYPE_MESSAGE | PIPE_READMODE_MESSAGE | PIPE_WAIT, PIPE_UNLIMITED_INSTANCES, 1024 * 1024, 1024 * 1024, NMPWAIT_USE_DEFAULT_WAIT, &sa); if (hPipe == INVALID_HANDLE_VALUE) { qCritical("Error creating named pipe"); return -1; } if (!ConnectNamedPipe(hPipe, NULL)) { qCritical("Error connecting to named pipe"); return -1; } checkPipe(hPipe); #endif
Last updated: 2024-02-02
Post by thysonfury on OPTO22 Groov Epic PR2 Modbus Comms Dropping out every 2 hours and 4 Mins
CODESYS Forge
talk
(Post)
Hi after some assistance with an error on a Groov PR2 PLC. We have a few different communications set up as shown below: One Modbus TCP Slave Connection - ( Sending / Receiving Data from a PC ) Two Modbus TCP Master Connection - ( Reading Data from a UPS Panel and Reading Data Gas Chromatograph) One Modbus RTU Slave Connection 485 - (Reading Data from a fire and gas panel) One Modbus RTU Master Connection 485 - (Sending Data to a Telemetry Unit) All Licenses have been installed as per OPTO22 suggestions of the order below: Modbus TCP Master Modbus TCP Slave Modbus RTU Master Modbus RTU Slave When I check on License manager the RTU Master license seems to disappear on installing the RTU. (What ever reason I’ve been told this is “normal”). If I use Device License Read It will successfully read all the licenses correctly. Now the issue is every 2 hours and between 4. For what ever reason the communications seems to end and lock up for about 20 seconds. During this time even if I was logged into the PLC it would kick me off and I’d have to re type the password to enter. Most of the devices can handle this however the RTU flags up a communications failure at the SCADA and is raising alarms every 2 hours and 4 mins. We’ve had multiple people go through the code to check for anything obvious. Does anyone have any ideas?
Last updated: 2024-04-15
Post by thysonfury on OPTO22 Groov Epic PR2 Modbus Comms Dropping out every 2 hours and 4 Mins
CODESYS Forge
talk
(Post)
Hi after some assistance with an error on a Groov PR2 PLC. We have a few different communications set up as shown below: One Modbus TCP Slave Connection - ( Sending / Receiving Data from a PC ) Two Modbus TCP Master Connection - ( Reading Data from a UPS Panel and Reading Data Gas Chromatograph) One Modbus RTU Slave Connection 485 - (Reading Data from a fire and gas panel) One Modbus RTU Master Connection 485 - (Sending Data to a Telemetry Unit) All Licenses have been installed as per OPTO22 suggestions of the order below: Modbus TCP Master Modbus TCP Slave Modbus RTU Master Modbus RTU Slave When I check on License manager the RTU Master license seems to disappear on installing the RTU. (What ever reason I’ve been told this is “normal”). If I use Device License Read It will successfully read all the licenses correctly. Now the issue is every 2 hours and between 4. For what ever reason the communications seems to end and lock up for about 20 seconds. During this time even if I was logged into the PLC it would kick me off and I’d have to re type the password to enter. Most of the devices can handle this however the RTU flags up a communications failure at the SCADA and is raising alarms every 2 hours and 4 mins. We’ve had multiple people go through the code to check for anything obvious. Does anyone have any ideas?
Last updated: 2024-04-15
Post by thysonfury on OPTO22 Groov Epic PR2 Modbus Comms Dropping out every 2 hours and 4 Mins
CODESYS Forge
talk
(Post)
Hi after some assistance with an error on a Groov PR2 PLC. We have a few different communications set up as shown below: One Modbus TCP Slave Connection - ( Sending / Receiving Data from a PC ) Two Modbus TCP Master Connection - ( Reading Data from a UPS Panel and Reading Data Gas Chromatograph) One Modbus RTU Slave Connection 485 - (Reading Data from a fire and gas panel) One Modbus RTU Master Connection 485 - (Sending Data to a Telemetry Unit) All Licenses have been installed as per OPTO22 suggestions of the order below: Modbus TCP Master Modbus TCP Slave Modbus RTU Master Modbus RTU Slave When I check on License manager the RTU Master license seems to disappear on installing the RTU. (What ever reason I’ve been told this is “normal”). If I use Device License Read It will successfully read all the licenses correctly. Now the issue is every 2 hours and between 4. For what ever reason the communications seems to end and lock up for about 20 seconds. During this time even if I was logged into the PLC it would kick me off and I’d have to re type the password to enter. Most of the devices can handle this however the RTU flags up a communications failure at the SCADA and is raising alarms every 2 hours and 4 mins. We’ve had multiple people go through the code to check for anything obvious. Does anyone have any ideas?
Last updated: 2024-04-15
Post by jeindhoven on Deploying to raspberry pi 5 hangs
CODESYS Forge
talk
(Post)
Hi CoDeSys support forum, hope that this is the correct place to ask this. Might be double as i am new to Codesys and dont know all terminology. I am trying to test Codesys with a virtual plc on a raspberry pi 5. Already figured that i need Tools -> Deploy Control SL, enter Communication parameters. Codesys says "Connected". Then tab "Deployment", there i select "CODESYS Control for Raspberri Pi SL" and "4.16.0.0 (all)". Click "Install" and the gui turns grey and unresponsive. The titlebar says "Untitled1.project - CODESYS (Not Responding)" as well. Restarting Codesys and checking shows no package was installed. How to deploy the runtime? Thank you in advance for your time. Edit: After some patience, an error showed up: "Error when sending ssh heartbeat: Session operation has timed out" "Error installing codesyscontrol" Any pointers to what remote command might have failed, or log of some sort, would be welcome. Software versions: Codesys version 3.5.21.10 Raspberry pi 5 (deployment machine): $ uname -a Linux raspberrypi 6.1.21-v8+ #1642 SMP PREEMPT Mon Apr 3 17:24:16 BST 2023 aarch64 GNU/Linux $ lsb_release -a No LSB modules are available. Distributor ID: Debian Description: Debian GNU/Linux 11 (bullseye) Release: 11 Codename: bullseye $ apt list --installed | grep openssh-server openssh-server/oldstable,now 1:8.4p1-5+deb11u3 arm64 Development machine: $ uname -a Linux 2B 6.1.0-35-amd64 #1 SMP PREEMPT_DYNAMIC Debian 6.1.137-1 (2025-05-07) x86_64 GNU/Linux $ lsb_release -a No LSB modules are available. Distributor ID: Debian Description: Debian GNU/Linux 12 (bookworm) Release: 12 Codename: bookworm VirtualBox Version 7.0.26 r168464 (Qt5.15.8) Virtual OS: Windows 10 Pro 64-bit (10.0, Build 19045) .NET version 4.0.30319.42000
Last updated: 2025-06-22
Post by martinlithlith on Relay board / relays for raspberry pi 3 b+
CODESYS Forge
talk
(Post)
hi! im planning a project on a raspberry with Codesys. For this I'll need a number of relays to control heating and fans, all a max of 24v and about 2a. How would i know if the board / relays i buy will be working with Codesys? Does every hat work or does it need a library/driver? is there a list of drivers/libraries created? as this is a hobby project all tips on a relay board or single boards that works with codesys and not to expensive are very welcome.
Last updated: 2023-09-03
Post by nico01 on Integer with comma in visualization
CODESYS Forge
talk
(Post)
Hello everyone, I created a visualization with a lot of REAL, with one or two digits after the decimal point. This causes me problems in terms of rounding and memory... is it possible to display an integer with a comma, like with PROFACE or SIEMENS? It's just an "abuse" of display, the comma is just on the visualization. This limits the memory (16 versus 64 bytes) and rounding is easier to manage... See print screen on proface software THANKS
Last updated: 2023-09-20
Post by damian177 on Codesys MQTT subscribe
CODESYS Forge
talk
(Post)
Hi, In my project I have MQTT Client like below: //mqtt client mqttClient( xEnable:=connect_to_broker, sHostname :=sHostname, uiPort:= uiPort, xUseTLS:=FALSE, wsUsername:="", wsPassword:="", xCleanSession:=TRUE, sClientId:='694d45587761676f4b6f6e74656e6572', pbWillMessage := ADR(sWillMessage), uiWillMessageSize:=DINT_TO_UINT(Stu.StrLenA(ADR(sWillMessage))), xWillRetain:=FALSE, udiTimeOut:= 10000000); And ten subscriber's , one of those is below: //subscribe a topic1 mqttSubscriber_S1(xEnable:=subscribe, eSubscribeQoS := 0, pbPayload:=ADR(sSubscribeMessage_S1), udiMaxPayloadSize :=SIZEOF(sSubscribeMessage_S1), mqttClient:=mqttClient, wsTopicFilter:=wsSubcribeTopic_S1); TerminateString(ADR(sSubscribeMessage_S1), mqttSubscriber_S1.udiPayloadSize); After connected to broker I set subscribe to TRUE in alls subscribers and my mqttclient recive error : ACKNOWLEDGE_TIMEOUT what can be wrong ?
Last updated: 2023-10-11
Post by davidbo on RPI How to login for a copy of the SD image
CODESYS Forge
talk
(Post)
I had one RPI device where I could login. I copied the SD-flash over to another SC-flash. This new SD-flash was inserted in the new device. I can boot the new device but I cannot login why? How can I install an application on this new device? Control 4.4.0.0 cat os-release PRETTY_NAME="Raspbian GNU/Linux 11 (bullseye)" NAME="Raspbian GNU/Linux" VERSION_ID="11" VERSION="11 (bullseye)" VERSION_CODENAME=bullseye ID=raspbian ID_LIKE=debian HOME_URL="http://www.raspbian.org/" SUPPORT_URL="http://www.raspbian.org/RaspbianForums" BUG_REPORT_URL="http://www.raspbian.org/RaspbianBugs"
Last updated: 2023-10-18
Post by eschwellinger on Persistence Manager Backup
CODESYS Forge
talk
(Post)
you need at them moment a download once (for the configuration files generated including addresses) then stop the plc - exchange the persistence file ( without the config file) This will be improved to 3.5.18.6 and 3.5.20.0. (possible then to generate offline bootproject including full persistenmanager files) - this is if you have not 100% the same bootapplication on the devices. In case you copy the whole Application (PLCLogic) directory it should work out of the box - but only with 100% same bootprojects as mentioned above. By the CODESYS Automation Server would help solve this too.
Last updated: 2023-10-19
Post by rcaponi on Codesys 3.5 SP19 Patch 4. Trace context menu does not work
CODESYS Forge
talk
(Post)
Hello, I'm using the new Codesys 3.5 SP19 Patch 4 version with CODESYS Control for Raspberry Pi MC SL v4.8. Compared to the Codesys 3.5 SP19 Patch 1 version, the context menu on a Trace object no longer works. So I can no longer run the Downloader Trace command. Do any options need to be enabled with the new version? Best regards Roberto Caponi
Last updated: 2023-10-24
Post by tehthoams on Find Function: Object reference not set to an instance of an object.
CODESYS Forge
talk
(Post)
Hey, Sorry this isn't super helpful, but i had this problem once and was able to resolve it. I can't recall how I solved it and whether it was a problem with my codesys installation or the project itself. If it is the codesys installation, make sure all your required libraries and plugins are installed and available. compare with a colleagues installation if possible. I vaguely recall saving a copy of my project and deleting things one by one until the error went away...
Last updated: 2023-10-30
Post by tehthoams on Find Function: Object reference not set to an instance of an object.
CODESYS Forge
talk
(Post)
Hey, Sorry this isn't super helpful, but i had this problem once and was able to resolve it. I can't recall how I solved it and whether it was a problem with my codesys installation or the project itself. If it is the codesys installation, make sure all your required libraries and plugins are installed and available. compare with a colleagues installation if possible. I vaguely recall saving a copy of my project and deleting things one by one until the error went away...
Last updated: 2023-10-30
Post by bbm1995 on Camera RTSP Feed
CODESYS Forge
talk
(Post)
Hi dgrard, I had the same issue for a long time, but on a WAGO webvisu. Now I'm glad that I can share my solution. I don't know if you are trying to use the webvisu or the target visu, but this works on webvisu: Get "go2rtc" and set it up according to the documentation. I'm running the Windows binary. Here's my example of the go2rtc.yaml config file (contains working example streams): api: listen: ":1984" # default ":1984", HTTP API port ("" - disabled) origin: "*" # default "", allow CORS requests (only * supported) static_dir: "www" # default "", folder for static files (custom web interface) tls_listen: ":443" # default "", enable HTTPS server tls_cert: "./SSL/fullchain.pem" tls_key: "./SSL/privatekey.pem" streams: # Streams with multiple links will fall back on the next link. ABUS TVIP48511: - rtsp://<username>:<password>@<hostname>:<port>/ch1/main - rtsp://<username>:<password>@<hostname>:<port>/ch1/sub # Diagnostic connections Kirchhoff Institute for Physics - Germany: http://pendelcam.kip.uni-heidelberg.de/mjpg/video.mjpg Blanton Bottling, Kentucky - USA: http://camera.buffalotrace.com/mjpg/video.mjpg Tokyo - Japan: http://61.211.241.239/nphMotionJpeg?Resolution=320x240&Quality=Standard Tampere Hacklab - Finland: http://tamperehacklab.tunk.org:38001/nphMotionJpeg?Resolution=640x480&Quality=Clarity Soltorget Pajala - Sweden: http://195.196.36.242/mjpg/video.mjpg Kaiskuru Skistadion - Norway: http://77.222.181.11:8080/mjpg/video.mjpg webrtc: listen: ":8555" #ice_servers: # - urls: [ "stun:localhost:3478" ] # username: "" # credential: "" Access the webinterface of go2rtc and get the link of your stream. Use the link as for your browser frame in the visualization. Depending on your device, you need to be able to access the file /etc/lighttpd/lighttpd.conf or /etc/lighttpd/webvisu.conf and change the contents similar to this one, otherwise you'll get CORS and CSP errors in the browser and you won't be able to view the stream on the webvisu: # Webvisu specific settings $SERVER["socket"] =~ port_webvisu_used_any { url.redirect += ( "^/webvisu/?$" => "/webvisu/webvisu.htm" ) $HTTP["url"] =~ "^/webvisu/?" { var.response_header_policy_webvisu = ( # CSP for WebVisu, allowing inline sources. "Content-Security-Policy" => "default-src 'self' 'unsafe-inline'; media-src *; frame-src *", # CORS for WebVisu, allowing any origin to access. "Access-Control-Allow-Origin" => "*", # Tell older browsers that this page can only be displayed if all ancestor # frames are same origin to the page itself. "X-Frame-Options" => "SAMEORIGIN" ) # Response header policy for WebVisu setenv.set-response-header = var.response_header_policy_webvisu setenv.set-response-header += var.response_header_policy_common }
Last updated: 2023-11-14
Post by svn123 on Can V3.5.19 and V2.3.9 be installed on same Windows10 PC without affecting each other?
CODESYS Forge
talk
(Post)
Hi All, Seasons Greetings! I have Codesys V3.5.19 patch 5 installed on a Windows 10 PC. I have received a program which is for Codesys V2.3.9. First I tried to convert it but had many conversion errors. I am wondering if it is possible to install Codesys V2.3.9 on same PC without affecting the V2.5.19 installations. Is this possible? SVN123
Last updated: 2023-12-28