Post by tayhim on WAGO HMI Device not found
CODESYS Forge
talk
(Post)
Hello, I'm trying to connect with a Wago TP600 HMI but without success. I'm using codysis 3.5 SP19 patch 7 (SP20 block all the time) and the official wago package is installed. However, when I scan and select my device, I get a message saying that the device doesn't match the project's device object with the possibility to update the device (as shown in the attached picture). however, after choosing to update i got a message that the device is not found. I've tried with a new empty project but the same results. do you have any ideas? Thanks.
Last updated: 2024-06-25
Post by s1mon on Two OneWireMaster on one Raspberry PI 5
CODESYS Forge
talk
(Post)
I don't know why the EtherCat fails, but what happens is: First I have only one 1WireMaster running on my Raspberry Pi and EtherCat is running fine. Then I'd like to add a 2nd 1WireMaster. Therefore I enable a 2nd GPIO Pin on the raspberry in the file "/boot/firmware/config.txt". dtoverlay=w1-gpio,gpiopin=4,pullup=0 dtoverlay=w1-gpio,gpiopin=23,pullup=0 To be able to use this 2nd 1WireMaster in Codesys Runtime I Adjust the CODESYScontrol.cfg file and add there: PlaceholderFilePath.2=/sys/devices/w1_bus_master2, $OneWire2$ After a reboot the EtherCat Master is not working any more. I didn't even add a 2nd OneWire Master in Codesys, but still if I do the EtherCat does not work. Do you have an idea why?
Last updated: 2025-10-21
Post by malte on OPC UA multiple Endpoints
CODESYS Forge
talk
(Post)
My CODESYS OPC UA server provides endpoints using both the hostname and the IP address. Connecting via the IP address works fine, but connecting via the hostname does not. The endpoint list shows both opc.tcp://<hostname>:4840 and opc.tcp://<ip>:4840. When using the hostname, the OPC UA client (UA Expert) fails to connect. Using the IP address connects without issues. Main goal is to conect via Python but opcua-asyncio seems to prefer the hostname. How can I configure CODESYS or my system so that the OPC UA connection via hostname also works properly or disable it completly? Running Codesys for PFC200 sl 4.18.0.0
Last updated: 2025-10-28
Post by aria13 on Has anyone fed ESP32 sensor data into CODESYS (via MQTT/Modbus)?
CODESYS Forge
talk
(Post)
Has anyone tried sending live sensor data from an ESP32 into a CODESYS runtime (for example via MQTT gateway or a Modbus bridge) to trigger PLC logic? I was reading an ESP32 → MQTT tutorial (https://www.theengineeringprojects.com/2021/11/esp32-mqtt.html) that shows how easy it is to publish sensor data from an ESP32, and I’m wondering how practical that is when tying the stream into industrial control software like CODESYS. I’ve also seen Arduino forum threads where people relay sensor streams to MQTT brokers and Raspberry Pi projects that bridge MQTT→Modbus, so I’m mainly curious about real-world issues: reliability, message latency, and simple patterns you’d recommend for safe PLC integration. Any tips, examples, or gotchas from folks who’ve done this?
Last updated: 2025-10-29
Post by miltos on licensing question
CODESYS Forge
talk
(Post)
Greetings to all, I'm working on a webvisu project on control win V3 x64 runtime, and have purchased 3 licenses for my application. -Codesys Control Standard M -Codesys Visualization L -Codesys Communication M I have them installed on a Codesys usb dongle When I try to download the program, a login error window appears with the message "No valid license found for the webvisualization". The control win v3 communicates with 3 plc, and have enabled communication over codesys V3 communication by adding one datasource for every plc in the datamanager. If I remove the data manager from the project, the rest of the visualisation can be downloaded normally. Do I need to purchase another License and which one? Please find attached the software metrics and the error screen.
Last updated: 2025-10-31
Post by davidbo on How to stop dhcpcd and use SysSockSetIpAddressAndNetMask to set address?
CODESYS Forge
talk
(Post)
It is stated: "Dynamic ip address, provided by DHCP, BOOTP, etc. Cannot be changed by SysSockSetIpAddressAndNetMask()" Therefore I try to stop dhcpcd and flush the eth0 like this VAR CONSTANT flushIP:STRING:='sudo ip addr flush dev eth0'; stopDHCP:STRING:='sudo systemctl stop dhcpcd'; END_VAR SysProcessExecuteCommand2(pszCommand:=stopDHCP, pszStdOut:=stdout,udiStdOutLen:= SIZEOF(stdout),pResult := ADR(Result)); SysProcessExecuteCommand2(pszCommand:=flushIP, pszStdOut:=stdout,udiStdOutLen:= SIZEOF(stdout),pResult := ADR(Result)); Besides losing the connection when flush occurs the CODESYS halts, seen on the display and I cannot see why, because I have lost the connection from my IDE. Why does the flush command halt the execution of the application?
Last updated: 2025-11-04
Post by jeindhoven on Deploying to raspberry pi 5 hangs
CODESYS Forge
talk
(Post)
Hi CoDeSys support forum, hope that this is the correct place to ask this. Might be double as i am new to Codesys and dont know all terminology. I am trying to test Codesys with a virtual plc on a raspberry pi 5. Already figured that i need Tools -> Deploy Control SL, enter Communication parameters. Codesys says "Connected". Then tab "Deployment", there i select "CODESYS Control for Raspberri Pi SL" and "4.16.0.0 (all)". Click "Install" and the gui turns grey and unresponsive. The titlebar says "Untitled1.project - CODESYS (Not Responding)" as well. Restarting Codesys and checking shows no package was installed. How to deploy the runtime? Thank you in advance for your time. Edit: After some patience, an error showed up: "Error when sending ssh heartbeat: Session operation has timed out" "Error installing codesyscontrol" Any pointers to what remote command might have failed, or log of some sort, would be welcome. Software versions: Codesys version 3.5.21.10 Raspberry pi 5 (deployment machine): $ uname -a Linux raspberrypi 6.1.21-v8+ #1642 SMP PREEMPT Mon Apr 3 17:24:16 BST 2023 aarch64 GNU/Linux $ lsb_release -a No LSB modules are available. Distributor ID: Debian Description: Debian GNU/Linux 11 (bullseye) Release: 11 Codename: bullseye $ apt list --installed | grep openssh-server openssh-server/oldstable,now 1:8.4p1-5+deb11u3 arm64 Development machine: $ uname -a Linux 2B 6.1.0-35-amd64 #1 SMP PREEMPT_DYNAMIC Debian 6.1.137-1 (2025-05-07) x86_64 GNU/Linux $ lsb_release -a No LSB modules are available. Distributor ID: Debian Description: Debian GNU/Linux 12 (bookworm) Release: 12 Codename: bookworm VirtualBox Version 7.0.26 r168464 (Qt5.15.8) Virtual OS: Windows 10 Pro 64-bit (10.0, Build 19045) .NET version 4.0.30319.42000
Last updated: 2025-06-22
Post by dnordenberg on BOOL variable in OPC UA and modbus simultaneously
CODESYS Forge
talk
(Post)
How can I have an BOOL variable that is read/write in both modbus TCP server and from OPC UA at the same time? Variables with %MX.n %QX.n addressing which is used for BOOL/coils in modbus server is not allowed in OPC UA symbol list on Schneider M251 controllers. I have already asked on Schneiders forum but there are not a lot of codesys experts over there :( So OPC symbols can't have a address and the modbus TCP server needs a address. So how should I do it then? It seems like an impossible combination. Since I want read/write access from both ways I can't just simply make a second variable and assign it the value of another since it would be a one way assignment. I also tried using VAR_CONFIG which then makes the address syntax %Q or %M in my main variable list and that fools OPC UA Symbol Configuration to allow it and then I add the complete %MX.n address of it in the VAR_CONFIG list. This semi works, I can toggle the BOOL from modbus but the OPC UA symbol seems to be read only. It displays symbol status but nothing happens when I toogle it. I think I need another way to have the variables and symbols pointing to the same bits in memory... My plan B is to write a BOOL array compare FB that saves a history bit from previous cycle and if that does not match current status at next cycle for either the OPC symbol or the modbus variable then it copies the new status over to the other. Maybe ugly but it's like my last alternative. Kind regards David
Last updated: 2025-07-14
Post by mondinmr on Why SysPipeWindows is not implemented in RTE?
CODESYS Forge
talk
(Post)
This library would be very useful for IPC communications. Using a UDP socket on localhost is unpredictable, as with slightly loaded machines it does not even guarantee packet delivery locally. Using TCP creates a lot of overhead. Message named pipes would be an excellent solution for Windows RTE. On Linux, since the release of the extension package, there is no issue, as it is sufficient to develop a component. However, although now 90% of our clients understand that Linux runtimes are better in every way compared to Windows RTE, especially from the security aspect (Not in kernel space) and the issues with Windows updates, 10% stubbornly insist (sometimes for trivial commercial reasons) on using Windows. Managing IPC with circular buffers in shared memory is quite ugly, or rather really ugly and unaesthetic. In the manuals, I saw the SysPipeWindows libraries, so I decided to test them, but unfortunately, I noticed that they are not implemented for RTE devices. Technically, I could try to open them as regular files, but SysFileOpen returns 16#27 or 16#39 depending on how I set the name (direction of the slashes). Here is the code to create shared memory and named pipes. Shared memory work great, named pipes no! #ifdef Q_OS_WIN32 SECURITY_ATTRIBUTES sa; SECURITY_DESCRIPTOR sd; InitializeSecurityDescriptor(&sd, SECURITY_DESCRIPTOR_REVISION); SetSecurityDescriptorDacl(&sd, TRUE, NULL, FALSE); sa.nLength = sizeof(SECURITY_ATTRIBUTES); sa.lpSecurityDescriptor = &sd; sa.bInheritHandle = FALSE; const wchar_t* name = L"Global\\ShmTest"; HANDLE hMapFile = CreateFileMapping( INVALID_HANDLE_VALUE, NULL, PAGE_READWRITE, 0, sizeof(SharedData), name); if (hMapFile == NULL) { qCritical("Error creating shared memory"); return 1; } data = static_cast<SharedData*>(MapViewOfFile(hMapFile, FILE_MAP_ALL_ACCESS, 0, 0, sizeof(SharedData))); if (data == NULL) { qCritical("Error mapping shared memory"); return 1; } HANDLE hPipe = CreateNamedPipe( TEXT("\\\\.\\pipe\\MyPipe"), PIPE_ACCESS_DUPLEX, PIPE_TYPE_MESSAGE | PIPE_READMODE_MESSAGE | PIPE_WAIT, PIPE_UNLIMITED_INSTANCES, 1024 * 1024, 1024 * 1024, NMPWAIT_USE_DEFAULT_WAIT, &sa); if (hPipe == INVALID_HANDLE_VALUE) { qCritical("Error creating named pipe"); return -1; } if (!ConnectNamedPipe(hPipe, NULL)) { qCritical("Error connecting to named pipe"); return -1; } checkPipe(hPipe); #endif
Last updated: 2024-02-02
Post by thysonfury on OPTO22 Groov Epic PR2 Modbus Comms Dropping out every 2 hours and 4 Mins
CODESYS Forge
talk
(Post)
Hi after some assistance with an error on a Groov PR2 PLC. We have a few different communications set up as shown below: One Modbus TCP Slave Connection - ( Sending / Receiving Data from a PC ) Two Modbus TCP Master Connection - ( Reading Data from a UPS Panel and Reading Data Gas Chromatograph) One Modbus RTU Slave Connection 485 - (Reading Data from a fire and gas panel) One Modbus RTU Master Connection 485 - (Sending Data to a Telemetry Unit) All Licenses have been installed as per OPTO22 suggestions of the order below: Modbus TCP Master Modbus TCP Slave Modbus RTU Master Modbus RTU Slave When I check on License manager the RTU Master license seems to disappear on installing the RTU. (What ever reason I’ve been told this is “normal”). If I use Device License Read It will successfully read all the licenses correctly. Now the issue is every 2 hours and between 4. For what ever reason the communications seems to end and lock up for about 20 seconds. During this time even if I was logged into the PLC it would kick me off and I’d have to re type the password to enter. Most of the devices can handle this however the RTU flags up a communications failure at the SCADA and is raising alarms every 2 hours and 4 mins. We’ve had multiple people go through the code to check for anything obvious. Does anyone have any ideas?
Last updated: 2024-04-15
Post by thysonfury on OPTO22 Groov Epic PR2 Modbus Comms Dropping out every 2 hours and 4 Mins
CODESYS Forge
talk
(Post)
Hi after some assistance with an error on a Groov PR2 PLC. We have a few different communications set up as shown below: One Modbus TCP Slave Connection - ( Sending / Receiving Data from a PC ) Two Modbus TCP Master Connection - ( Reading Data from a UPS Panel and Reading Data Gas Chromatograph) One Modbus RTU Slave Connection 485 - (Reading Data from a fire and gas panel) One Modbus RTU Master Connection 485 - (Sending Data to a Telemetry Unit) All Licenses have been installed as per OPTO22 suggestions of the order below: Modbus TCP Master Modbus TCP Slave Modbus RTU Master Modbus RTU Slave When I check on License manager the RTU Master license seems to disappear on installing the RTU. (What ever reason I’ve been told this is “normal”). If I use Device License Read It will successfully read all the licenses correctly. Now the issue is every 2 hours and between 4. For what ever reason the communications seems to end and lock up for about 20 seconds. During this time even if I was logged into the PLC it would kick me off and I’d have to re type the password to enter. Most of the devices can handle this however the RTU flags up a communications failure at the SCADA and is raising alarms every 2 hours and 4 mins. We’ve had multiple people go through the code to check for anything obvious. Does anyone have any ideas?
Last updated: 2024-04-15
Post by thysonfury on OPTO22 Groov Epic PR2 Modbus Comms Dropping out every 2 hours and 4 Mins
CODESYS Forge
talk
(Post)
Hi after some assistance with an error on a Groov PR2 PLC. We have a few different communications set up as shown below: One Modbus TCP Slave Connection - ( Sending / Receiving Data from a PC ) Two Modbus TCP Master Connection - ( Reading Data from a UPS Panel and Reading Data Gas Chromatograph) One Modbus RTU Slave Connection 485 - (Reading Data from a fire and gas panel) One Modbus RTU Master Connection 485 - (Sending Data to a Telemetry Unit) All Licenses have been installed as per OPTO22 suggestions of the order below: Modbus TCP Master Modbus TCP Slave Modbus RTU Master Modbus RTU Slave When I check on License manager the RTU Master license seems to disappear on installing the RTU. (What ever reason I’ve been told this is “normal”). If I use Device License Read It will successfully read all the licenses correctly. Now the issue is every 2 hours and between 4. For what ever reason the communications seems to end and lock up for about 20 seconds. During this time even if I was logged into the PLC it would kick me off and I’d have to re type the password to enter. Most of the devices can handle this however the RTU flags up a communications failure at the SCADA and is raising alarms every 2 hours and 4 mins. We’ve had multiple people go through the code to check for anything obvious. Does anyone have any ideas?
Last updated: 2024-04-15
Post by e13740e on Parameterized Property syntax for array element processing
CODESYS Forge
talk
(Post)
Since parameterized (indexed) properties are not possible, I decided to use architectural approach "Indexing Property Adapter" to achieve the intended goal — avoiding code duplication for validated access to array elements. Essence: Create a Function Block Adapter (FB_PropertyAdapter) that encapsulates the logic for working with a single element of the target array (e.g., with one settings structure). Declare Properties inside the adapter block for accessing each individual field of the data structure. All validation logic is implemented within the Set accessors of these properties. Data Binding via VAR_IN_OUT: The adapter block receives a reference to a specific data element from the global array through its VAR_IN_OUT section, which ensures direct work with the original data without copying. Create an Array of Adapters: In the parent POU (e.g., FB_SettingsManager), an array of these adapter blocks is created — one for each element of the global array that needs to be managed. Initialize Bindings: In a FOR loop, each adapter instance from the array is given a reference to the corresponding data element. Result: This approach allows accessing the data via the index of the adapter array, and then through the property name, which simulates the behavior of an indexed property: MyAdapterArray[Index].MyProperty Thus, the validation and data access logic is written only once inside the adapter block and is then reused multiple times by creating instances of it in an array. This completely solves the problem of code duplication while providing a clean, scalable, and object-oriented architecture compatible with standard CODESYS features. Question closed.
Last updated: 2025-10-19
Post by ihatemaryfisher on Sorting array of any-sized structure
CODESYS Forge
talk
(Post)
With that I could make an array of varying size, but would still have to define the array type in the function's declaration VAR_IN_OUT stArray: array [*..*] of <pre-defined data type> END_VAR I wanted a function that could take an array of any type (e.g., a structured VAR) as an input. That way I could call it in multiple POUs to handle different arrays structures.
Last updated: 2023-08-18
Post by martinlithlith on Relay board / relays for raspberry pi 3 b+
CODESYS Forge
talk
(Post)
hi! im planning a project on a raspberry with Codesys. For this I'll need a number of relays to control heating and fans, all a max of 24v and about 2a. How would i know if the board / relays i buy will be working with Codesys? Does every hat work or does it need a library/driver? is there a list of drivers/libraries created? as this is a hobby project all tips on a relay board or single boards that works with codesys and not to expensive are very welcome.
Last updated: 2023-09-03
Post by damian177 on Codesys MQTT subscribe
CODESYS Forge
talk
(Post)
Hi, In my project I have MQTT Client like below: //mqtt client mqttClient( xEnable:=connect_to_broker, sHostname :=sHostname, uiPort:= uiPort, xUseTLS:=FALSE, wsUsername:="", wsPassword:="", xCleanSession:=TRUE, sClientId:='694d45587761676f4b6f6e74656e6572', pbWillMessage := ADR(sWillMessage), uiWillMessageSize:=DINT_TO_UINT(Stu.StrLenA(ADR(sWillMessage))), xWillRetain:=FALSE, udiTimeOut:= 10000000); And ten subscriber's , one of those is below: //subscribe a topic1 mqttSubscriber_S1(xEnable:=subscribe, eSubscribeQoS := 0, pbPayload:=ADR(sSubscribeMessage_S1), udiMaxPayloadSize :=SIZEOF(sSubscribeMessage_S1), mqttClient:=mqttClient, wsTopicFilter:=wsSubcribeTopic_S1); TerminateString(ADR(sSubscribeMessage_S1), mqttSubscriber_S1.udiPayloadSize); After connected to broker I set subscribe to TRUE in alls subscribers and my mqttclient recive error : ACKNOWLEDGE_TIMEOUT what can be wrong ?
Last updated: 2023-10-11
Post by davidbo on RPI How to login for a copy of the SD image
CODESYS Forge
talk
(Post)
I had one RPI device where I could login. I copied the SD-flash over to another SC-flash. This new SD-flash was inserted in the new device. I can boot the new device but I cannot login why? How can I install an application on this new device? Control 4.4.0.0 cat os-release PRETTY_NAME="Raspbian GNU/Linux 11 (bullseye)" NAME="Raspbian GNU/Linux" VERSION_ID="11" VERSION="11 (bullseye)" VERSION_CODENAME=bullseye ID=raspbian ID_LIKE=debian HOME_URL="http://www.raspbian.org/" SUPPORT_URL="http://www.raspbian.org/RaspbianForums" BUG_REPORT_URL="http://www.raspbian.org/RaspbianBugs"
Last updated: 2023-10-18
Post by eschwellinger on Persistence Manager Backup
CODESYS Forge
talk
(Post)
you need at them moment a download once (for the configuration files generated including addresses) then stop the plc - exchange the persistence file ( without the config file) This will be improved to 3.5.18.6 and 3.5.20.0. (possible then to generate offline bootproject including full persistenmanager files) - this is if you have not 100% the same bootapplication on the devices. In case you copy the whole Application (PLCLogic) directory it should work out of the box - but only with 100% same bootprojects as mentioned above. By the CODESYS Automation Server would help solve this too.
Last updated: 2023-10-19
Post by rcaponi on Codesys 3.5 SP19 Patch 4. Trace context menu does not work
CODESYS Forge
talk
(Post)
Hello, I'm using the new Codesys 3.5 SP19 Patch 4 version with CODESYS Control for Raspberry Pi MC SL v4.8. Compared to the Codesys 3.5 SP19 Patch 1 version, the context menu on a Trace object no longer works. So I can no longer run the Downloader Trace command. Do any options need to be enabled with the new version? Best regards Roberto Caponi
Last updated: 2023-10-24
Post by tehthoams on Find Function: Object reference not set to an instance of an object.
CODESYS Forge
talk
(Post)
Hey, Sorry this isn't super helpful, but i had this problem once and was able to resolve it. I can't recall how I solved it and whether it was a problem with my codesys installation or the project itself. If it is the codesys installation, make sure all your required libraries and plugins are installed and available. compare with a colleagues installation if possible. I vaguely recall saving a copy of my project and deleting things one by one until the error went away...
Last updated: 2023-10-30
Post by tehthoams on Find Function: Object reference not set to an instance of an object.
CODESYS Forge
talk
(Post)
Hey, Sorry this isn't super helpful, but i had this problem once and was able to resolve it. I can't recall how I solved it and whether it was a problem with my codesys installation or the project itself. If it is the codesys installation, make sure all your required libraries and plugins are installed and available. compare with a colleagues installation if possible. I vaguely recall saving a copy of my project and deleting things one by one until the error went away...
Last updated: 2023-10-30
Post by bbm1995 on Camera RTSP Feed
CODESYS Forge
talk
(Post)
Hi dgrard, I had the same issue for a long time, but on a WAGO webvisu. Now I'm glad that I can share my solution. I don't know if you are trying to use the webvisu or the target visu, but this works on webvisu: Get "go2rtc" and set it up according to the documentation. I'm running the Windows binary. Here's my example of the go2rtc.yaml config file (contains working example streams): api: listen: ":1984" # default ":1984", HTTP API port ("" - disabled) origin: "*" # default "", allow CORS requests (only * supported) static_dir: "www" # default "", folder for static files (custom web interface) tls_listen: ":443" # default "", enable HTTPS server tls_cert: "./SSL/fullchain.pem" tls_key: "./SSL/privatekey.pem" streams: # Streams with multiple links will fall back on the next link. ABUS TVIP48511: - rtsp://<username>:<password>@<hostname>:<port>/ch1/main - rtsp://<username>:<password>@<hostname>:<port>/ch1/sub # Diagnostic connections Kirchhoff Institute for Physics - Germany: http://pendelcam.kip.uni-heidelberg.de/mjpg/video.mjpg Blanton Bottling, Kentucky - USA: http://camera.buffalotrace.com/mjpg/video.mjpg Tokyo - Japan: http://61.211.241.239/nphMotionJpeg?Resolution=320x240&Quality=Standard Tampere Hacklab - Finland: http://tamperehacklab.tunk.org:38001/nphMotionJpeg?Resolution=640x480&Quality=Clarity Soltorget Pajala - Sweden: http://195.196.36.242/mjpg/video.mjpg Kaiskuru Skistadion - Norway: http://77.222.181.11:8080/mjpg/video.mjpg webrtc: listen: ":8555" #ice_servers: # - urls: [ "stun:localhost:3478" ] # username: "" # credential: "" Access the webinterface of go2rtc and get the link of your stream. Use the link as for your browser frame in the visualization. Depending on your device, you need to be able to access the file /etc/lighttpd/lighttpd.conf or /etc/lighttpd/webvisu.conf and change the contents similar to this one, otherwise you'll get CORS and CSP errors in the browser and you won't be able to view the stream on the webvisu: # Webvisu specific settings $SERVER["socket"] =~ port_webvisu_used_any { url.redirect += ( "^/webvisu/?$" => "/webvisu/webvisu.htm" ) $HTTP["url"] =~ "^/webvisu/?" { var.response_header_policy_webvisu = ( # CSP for WebVisu, allowing inline sources. "Content-Security-Policy" => "default-src 'self' 'unsafe-inline'; media-src *; frame-src *", # CORS for WebVisu, allowing any origin to access. "Access-Control-Allow-Origin" => "*", # Tell older browsers that this page can only be displayed if all ancestor # frames are same origin to the page itself. "X-Frame-Options" => "SAMEORIGIN" ) # Response header policy for WebVisu setenv.set-response-header = var.response_header_policy_webvisu setenv.set-response-header += var.response_header_policy_common }
Last updated: 2023-11-14
Post by rafael on Access to user group IDs
CODESYS Forge
talk
(Post)
Hello, I'm trying to access the group IDs of the connected user. "CurrentUserGroupId" var shows only the first group ID that the user is assigned, I need the other group IDs that the user is in. I find some structs but I can't find where they are used, like "VUM_User" scruct from visuusermgmt, where can I find this vars? https://content.helpme-codesys.com/en/libs/VisuUserMgmt2%20Interfaces/Current/VUM_User.html abyUserGroupIDs seens perfect but I can't find a GVL where it is used.
Last updated: 2024-07-08
Post by srouse on PFC200BUS not running
CODESYS Forge
talk
(Post)
I started a project in codesys for a WAGO 750-8212 PLC and I am working on getting online with the controller. I can log in to the controller and I can see and control all of the fieldbus couplers that I have. I am unable to get the internal bus working. It just says that the bus is not running and when I scan or devices nothing shows up. Am I missing something important in my device tree?
Last updated: 2024-07-10
Post by mikek10 on Error IoDrvEthernetIP: Connection Failure. (16#1) How to solve
CODESYS Forge
talk
(Post)
Your connection configuration should look something like the attachment. Consuming assembly O->T will be the hex of the assembly you want to reference for output data - I want 102 (DO Data Only) shown in the Wago web page 102 = 16#66. Producing assembly (T->O) is the assembly you require for input data - again shown in the Wago web page - I want 108 (DI Data Only) or 16#6C Then set the number of bytes as per the data in the Wago web page too (both 2 in my case)
Last updated: 2024-07-22