Post by trent on Automation server - trends stop recording - need to manually reconnect
CODESYS Forge
talk
(Post)
Hi All, I use the analysis page in automation server to capture historical trends from my PLC - i only sample one point per hour but it does the job (for now) One issue I have is I often log on to analysis page to find the system has stopped recording trends from my PLC. To fix this, I need to choose "state information" in the "List view" under PLC and click "Reconnect" When I do this I see my variables listed under "parameters" under "PLC Details" start updating again and the trend in Data analyzer continues to update. My Question, Why do I need to manually reconnect? Is there a way to get automation server to automatically reconnect to the PLC so I continue to capture data from the PLC? Regards, Trent
Last updated: 2024-10-22
Post by timvh on Modbus TCP & RTU with Control for Linux SL
CODESYS Forge
talk
(Post)
It seems you have 2 network interfaces. Did you try eth1? Did you already configure the IP address for this interface in Linux? If yes, then maybe undo this. - or only set eth0 in the Nic configuration without anything else (so no IP address, because this is already set in Linux). For more information about the Nic settings, see (probably already read it?): https://content.helpme-codesys.com/en/CODESYS%20Control/_rtsl_obj_deploy_control_sl_configuration.html PS, if you only want to run CODESYS Control SL, you don't necessarily need the Virtual PLC variant. You could also install and run the CODESYS Control SL Runtime in the Host operating system. This way you should also be able to access the serial port and directly access all ethernet ports. Maybe this is easier?
Last updated: 2024-10-23
Post by struccc on HTML5 Controls - string(>80) values
CODESYS Forge
talk
(Post)
Dear all, does anyone have experience with HTML5 controls recently? CODESYS 3.5.20.30 / Visualization 4.6.0.0 I'd like to create a simple lightweight text editor, with proper multiline handling, cut & paste, scrolling, etc. And it seems to work fine, just have problems with strings longer than 80 bytes.... Declaring a variable sText1 : STRING(8000) and referencing it in the HTML5 Controls corresponding value property works perfectly one way: the code receive the data as a string (See log1)... (Note TypeID 1000...) Also sending back the data (seems to work (See log2) except it doesn't change the value of the bound variable. Probably the issue is with using SendSimpleValue method... Naturally, I could do a workaround, but maybe there is a more standard way to implement this... Please let me know if you have any suggestions.
Last updated: 2024-10-23
Post by wistaro on How to use PLC_Open FBs with PROFINET servodrive (PROFIdrive layer)
CODESYS Forge
talk
(Post)
Hello, I would like to know if there is a PROFIdrive layer in CODESYS. I am already familliar with Codesys's SoftMotion on CANOpen/EtherCAT (to control PLC Open FBs), and I need the same kind of stuff for PROFINET-IO devices; In my configuration, I have a CIFX board from Hischer to enable IRT, the SoftPLC "Codesys Control RTE V3 x64", and a servo-drive from INFRANOR that implements PROFINET / PROFIdrive (with IRT) protocol. This drive works well with the Object Technology of Tia Portal, but some customers use Codesys. Do you have an idea how to do that? Thanks in advance. Regards, William ROMIGUIERES INFRANOR France
Last updated: 2024-10-29
Post by mabac on No file found
CODESYS Forge
talk
(Post)
CODESYS introduced many cyber security related changes over the last few years, one of them is to restrict file access. By default, file access is restricted to the PlcLogic folder and subfolders of the CODESYS control runtime of version 3.5.19.0 and newer. For Control Win this would be the folder C:\ProgramData\CODESYS\CODESYSControlWinV3x64\xxxxxxxx\PlcLogic\ To enable access to other folders, you can configure additional paths by adding them to the file CODESYSControl.cfg. For example: [SysFile] FilePath=C:/temp/test FilePath.1=C:/Users/Public You should now be able to access your file in C:\temp\test\ or in C:\Users\Public
Last updated: 2024-10-30
Post by sigurdrb on Codesys and error messages, warnings exceptions etc.
CODESYS Forge
talk
(Post)
Hi, I tried some different libraries (CmpApp etc.) to find some global variables that I could read out as a variable in the codesys environment. Do any one of you know which libraries are best suited for this, and how I can read it out? My goal is to send messages, warnings etc. to the system that communicates to the PLC. Currently if something goes wrong I need to see the logfiles, or go online with the controller. I think I could save a lot of time if I could read the errors from our user interface that is connected to the PLC by TCP/IP.
Last updated: 2024-11-06
Post by simone on Collapse all
CODESYS Forge
talk
(Post)
Hi, I'm wondering if it exist a button or a keyboard shortcut (much much better) for "collapse all" the open folder on a codesys project. It would really be nice to have. Also: Are there some options or configuration for set a default zoom for the different editor (or even one global), for example I would like to have 100% on ST, LD editor and have 80% on Visualization Editor; and also have a button to set all the zooms to default, now it seems that every file mantain the one previously set. I'm working with the 3.5.20.10 right now Thanks!
Last updated: 2024-11-21
Post by arcadium on Library ENUM text representation in visualization
CODESYS Forge
talk
(Post)
Hello, Maybe someone could help with this. When I add ENUM to a text field I get the number instead of the text. For my own ENUM variable I have declared and enabled text list value is displayed as text, but I need enum text displayed from softMotion and other internal FB's. In the picture I have one of desired ENUM variable setup, but in the visu I have number, but in the watch window it's text. There is probably some checkbox to tick, but was looking for an hour, can't find a solution. Would apreciate some help
Last updated: 2024-12-24
Post by arcadium on Library ENUM text representation in visualization
CODESYS Forge
talk
(Post)
Hello, Maybe someone could help with this. When I add ENUM to a text field I get the number instead of the text. For my own ENUM variable I have declared and enabled text list value is displayed as text, but I need enum text displayed from softMotion and other internal FB's. In the picture I have one of desired ENUM variable setup, but in the visu I have number, but in the watch window it's text. There is probably some checkbox to tick, but was looking for an hour, can't find a solution. Would apreciate some help
Last updated: 2024-12-24
Post by trusty-squire on Read "Homed" status from EtherCAT drive
CODESYS Forge
talk
(Post)
@imdatatas, thanks for the info, I increased DSP402.uiHomingMinCycles to 10 and have a good feeling that will solve the issue of "false" homings. It's an intermittent issue so I'll report back once it's confirmed. @bruno-roth, also good info. According to my documentation, bit 14 is used to indicate the homed status. I did a test and the bit always stays true after it's been homed once (eg. even if I initiate a new homing procedure then hit the the e-stop mid homing), so I need to take that into consideration, but I can work with that. Thanks!
Last updated: 2025-01-09
Post by mkintegration on Reading Absolute Encoder Position From Yasakawa Drive
CODESYS Forge
talk
(Post)
I am looking to read in the absolute position of a yaskawa servo drive Sigma 7 that is using absolute encoder. It looks like yaskawa outputs this across there CN1 I/O connecter and during operation just outputs encoder pulses. But at boot up transmits the Multiturn data position and the Position within one rotation (pulse train) on two different wires. Once the drives are enabled it just uses incremental pulses. Does any one have experience with what IEC blocks to use to read this information in. I attached the Yaskawa Manual section that talks about the format.
Last updated: 2025-02-26
Post by mkintegration on Reading Absolute Encoder Position From Yasakawa Drive
CODESYS Forge
talk
(Post)
I am looking to read in the absolute position of a yaskawa servo drive Sigma 7 that is using absolute encoder. It looks like yaskawa outputs this across there CN1 I/O connecter and during operation just outputs encoder pulses. But at boot up transmits the Multiturn data position and the Position within one rotation (pulse train) on two different wires. Once the drives are enabled it just uses incremental pulses. Does any one have experience with what IEC blocks to use to read this information in. I attached the Yaskawa Manual section that talks about the format.
Last updated: 2025-02-26
Post by peterkcontrols on Copying 2 byte word to output
CODESYS Forge
talk
(Post)
Hello. I am using codesys 3.5. I would like to know if it is possible to set a variable to an output without declaring in. I have defined a STRUCT and within this struct I have a Struct for inputs called I and a struct for outputs called O. I have declared a variable of the type of this Struct, I would like to set or alias the value in this variable to an input/output value of an IO block that has a module on the ethernet tree. Is it possible to copy the contents of %IW0 -> STRUCT.I ? The size of both of these is 2 bytes. I understand that I can declare a variable with the input like Input01 AT %IX0.0 : BOOL; However how can I make STRUCT.I.D00 AT %IX0.0? Is this possible? Thanks
Last updated: 2025-03-03
Post by clarenced on Multiple applications on one device sharing variables.
CODESYS Forge
talk
(Post)
I got this working using OPC UA. In the logic application I just added a Symbol Configuration. In the HMI application I added a Data Sources Manager and OPC UA Data Source. The one thing I don't like is the way the tags end up being named in the HMI application. In the logic application I have a program named PLC_PRG. It has a variable named testDINT. In the logic application the name I get for this variable is DeviceSet.CODESYS_Control_Win_V3_x64.Resources.Logic.Programs.PLC_PRG.testDINT. This is very long and looks like it could change if I used this on a different device type. Any ideas how I could get this name shortened down to just PLC_PRG.testDINT like it is on the Logic application?
Last updated: 2025-03-06
Post by clarenced on Multiple applications on one device sharing variables.
CODESYS Forge
talk
(Post)
I got this working using OPC UA. In the logic application I just added a Symbol Configuration. In the HMI application I added a Data Sources Manager and OPC UA Data Source. The one thing I don't like is the way the tags end up being named in the HMI application. In the logic application I have a program named PLC_PRG. It has a variable named testDINT. In the HMI application the name I get for this variable is DeviceSet.CODESYS_Control_Win_V3_x64.Resources.Logic.Programs.PLC_PRG.testDINT. This is very long and looks like it could change if I used this on a different device type. Any ideas how I could get this name shortened down to just PLC_PRG.testDINT like it is on the Logic application?
Last updated: 2025-03-06
Post by agentcousto on [Bug report] Issue with Importing XML Files Containing "POINTER TO" Variables in Codesys Platform Plugins Versions 2.7 and 2.8
CODESYS Forge
talk
(Post)
Hello, I have developed a Python script that I run to import XML files into my project. For this, I use the Python function import_xml(). Everything was working fine when I was using Codesys platform plugins version 2.6.1.2320, but since I upgraded to versions 2.7 and even 2.8, some files are no longer imported correctly. After some research, I identified that all the files containing variables of the type "POINTER TO" are affected. I have attached a screenshot of the error I am encountering. Do you know about this bug? Do you plan to fix it?
Last updated: 2025-03-26
Post by imdatatas on Programmatically change Tappet on a cam
CODESYS Forge
talk
(Post)
Yes, There is. As explained "Manual creation of CAM structure" on below section. Likewise tappet structure also can be create manual and value of the switching point can be change during IEC program running. https://content.helpme-codesys.com/en/CODESYS%20SoftMotion/_sm_basic_cam_programmatic_creation.html Just create a cam table and define some tapped points as sample for your project. Then on project compile, the created cam tapped data is converted internally into a global variable list. By clicking "Display generated code" in the "cam editor", you can display the automatically created global variables for both cam & tappets. Regards, Imdat
Last updated: 2025-04-02
Post by elsmart on Sequential read and triggering of Modbs RTU channels in application
CODESYS Forge
talk
(Post)
Hello I need some help understanding how to use Modbus RTU (COM port) in Codesys enviroment. I defined a Modbus Server device (slave) in device tree and added some channels to read from (function 3). Also I set trigering mode to Application. I have a POU in which I want to trigger each channel one after the other something like this (C code for better visualisation): for (int i = 0; i < channelsCount; i++) { triggerChannel(channelsArray[i]); // Start transmission while(channel.xBusy); // Wait for transmission to complete } I have found ModbusChannel function block documentation but examples are scarce. I don't understand how rising edge triggering works. What would be the best solution for achieving sequntial channel triggering? What is the common way to read multiple Modbus channels once every time a specified POU is executed?
Last updated: 2025-05-16
Post by abuckie on Getting raw value as full resolution for ADS1115
CODESYS Forge
talk
(Post)
I just found this and I am getting a value larger than 16 bit, around 81000 something. I am reading a 5 volt value and I am using level shifters for the i2c bus. This is how I have the channel configured: ADS1115.usiAddress := 16#48; ADS1115.ChannelConfigs[0].Active := TRUE; ADS1115.ChannelConfigs[0].PGA := FSR_6144mV; ADS1115.ChannelConfigs[0].InputMux := Single_0; RawAnalogValue := ADS1115.Channels[0].Value; It looks like every value is a multiple of 3. Any idea where to look to fix this? I think i found what I want to change in UpdateChannels Channels[FChannelNo].Value := INT_TO_REAL(WORD_TO_INT(LValue) * GetFullScaleRange(ChannelConfigs[FChannelNo].PGA)) / 2048.0; I try to edit it but I can't, sorry if this is a basic question, I am new to CODESYS.
Last updated: 2025-05-22
Post by george32 on Learning ST in an object-oriented way.
CODESYS Forge
talk
(Post)
Dear all, I am currently creating a program in the ST language. Because the program is starting to grow nicely I would like to switch to a more object-oriented way of programming. (Like for example in Python). By surfing the internet I found out that Function Blocks is the best method for this. Now I would like to delve further into this, with all the possibilities that Function Blocks have only I cannot find a clear course, explanation of what everything is around the function block thing and how to approach everything. I find the standard documentation around Function Blocks rather abstract and the examples are minimal. Therefore I am looking for a page/course/document explaining object oriented programming in Codesys (or other PLC programming environment). Do you have any recommendations on this?
Last updated: 2025-06-10
Post by pauloricardoss on Codesys Control Raspberry PI 4.10.0 - missing 'Update Raspberry PI' option
CODESYS Forge
talk
(Post)
I am having the same problem. 'Update Raspberry PI' disappeared from the 'Tools' menu. Using RaspberryPI 3B+, Codesys V3.5 Sp21 + RaspberryPI Package 4.16. I installed the package as Administrator, executed Codesys as Administrator I also tried to connect using the deploy (even with ssh and everything enabled on the RaspberryPi I received password denied). I used in the past the same equipment with Codesys V3.5 Sp18 and RaspberryPI Package 4.08, it was really easy. (I also did a brand new RaspbianOs installation to make sure that nothing affect the connection). Anyone, knows how to fix it? Thanks,
Last updated: 2025-06-13
Post by levih on FbHTTPs_Get how to get data from a website and use it in codesys
CODESYS Forge
talk
(Post)
You get an array of DWORD into your receive buffer. You need to process this into usable data, before you can fit it into your DUT. I've made it work using FbWrite_ToIEC_ByRule in stead of Fb_JSON_ParseAndModify. I've attached images of the code. You receive the data into ARRAY[0..1023] OF DWORD. Then you use that array as the input for fbWrite_ToIEC_ByRule. To get the output from this you define a rule to fit the expected data structure including nesting levels. The you feed the rule into FbWrite_ToIEC_ByRule and then you can set the output to be of your DUT type.
Last updated: 2025-06-16
Post by buczekj on About CPU Loading
CODESYS Forge
talk
(Post)
This is a phenomenon that I have seen myself and with others. Texas instruments wrote an application note with this same issue. They noted with Codesys 3.5.19.10, that selecting CPU 1 as the EtherCAT task showed CPU spiking improvements over the performance of cores 0, 2, and 3. It appears to be linked to EtherCAT, are you configuring for use with distributed clocks? If so, I recommend choosing the 'Based on Input Reference' option. I have found it to reduce the CPU usage spike maximum slightly (see attached). See link to TI (also attached in case link breaks) https://www.ti.com/lit/an/spradh0/spradh0.pdf?ts=1723546111357
Last updated: 2025-07-01
Post by rafa on MODBUS TCP SERVER DONT AUTO-STARTUP
CODESYS Forge
talk
(Post)
Dear all, I have a project where I have two ModbusTCP communication drivers in the application. It's working normally until a power outage or the installation panel is restarted. As soon as the PLC CPU is restarted, the Ethernet port is OK, but the TCP Server displays an "UNDEFINED" error. I can't reset the error using the diagnostic confirmation or the "mbserver.xConfirmError" bit. I noticed that the error only appears in the "mbserver.byModbusError" memory and the description is "UNDEFINED." The "mbserver.xError" memory doesn't flag an error. When using the warm restart function and then START CPU, the devices return to normal operation. The following demonstration images; The main question is: How can I make devices boot automatically?
Last updated: 2025-07-15
Post by rafa on MODBUS TCP SERVER DON'T AUTOMATIC STARTUP
CODESYS Forge
talk
(Post)
Dear all, I have a project where I have two ModbusTCP communication drivers in the application. It's working normally until a power outage or the installation panel is restarted. As soon as the PLC CPU is restarted, the Ethernet port is OK, but the TCP Server displays an "UNDEFINED" error. I can't reset the error using the diagnostic confirmation or the "mbserver.xConfirmError" bit. I noticed that the error only appears in the "mbserver.byModbusError" memory and the description is "UNDEFINED." The "mbserver.xError" memory doesn't flag an error. When using the warm restart function and then START CPU, the devices return to normal operation. The following demonstration images; The main question is: How can I make devices boot automatically? Um using Codesys Version 3.5.20.30 Patch 3+ My CPU is a Weintek Cmtx Built-int - ( CMT3092x )
Last updated: 2025-07-15