Post by timvh on Profinet fault with codesys control V3 - Receive packet error
CODESYS Forge
talk
(Post)
Are you using the Control Win SL (installed together with the development environment of CODESYS)? If yes, you might want to consider using the CODESYS RTE instead. This has real-time capabilities (running on separate core(s)). But to be able to use this, you have to install the CODESYS Ethernet driver for your network interface to be able to let the RTE access the network port also in realtime. See: https://store.codesys.com/en/codesys-control-rte-sl-bundle.html https://content.helpme-codesys.com/en/CODESYS%20Control/_rtsl_windows_rts_v3.html PS, I haven't tested this myself yet, but you could try to use the SetCommunicationState method of the Profinet controller to see if you can reset and start the bus communication: result := PN_Controller.SetCommunicationState(eRequestedState := DED.DEVICE_TRANSITION_STATE.START); PS, if you are located in the Netherlands or Belgium, we could also provide the license(s) for you.
Last updated: 2024-02-28
Post by dhumphries on Not able to see input data coming from eip adapter on codesys
CODESYS Forge
talk
(Post)
Does the device have a green icon next to it when the PLC is running? If not you have some kind of communication problem, wireshark may be picking up some data but the scanner may not be configured correctly to receive the data. Check the T>O and O>T bytes and make sure they match on both the scanner and adapter. I've had very little success loading a .eds file and having the configuration work without some manual configuration. If you have a green icon, have you enabled the device to always update variables?
Last updated: 2024-03-02
Post by valec on Connect local Asem HMI runtime to local Codesys Control Win V3 x64
CODESYS Forge
talk
(Post)
I have a project made on a PL700 PLC with Codesys and an Asem Premium HMI panel. I don't have access to the physical PLC right now, so I'm trying to use Codesys Control Win V3 x64. I created the application and loaded "Codesys Control Win V3 x64" without errors, then I activate "Start PLC" from the tray. Asem cannot connect. I tried to use "localhost" or the local IP address and it doesn't work (it's the "CoDeSys Soft PLC Communication Driver"). I need to connect my local Asem runtime to a virtual Codesys application on my PC. How can I do it?
Last updated: 2024-03-26
Post by albzen on EtherCat Slaves diagnosis
CODESYS Forge
talk
(Post)
Hello everybody, I'm working on a RunTime Plc (Codesys 3.5.16/18.20) connected to an EtherCat bus with many devices. The bus has some communication fault but I don't know how understand which is the device or the cable that has the trouble. To understand the cause of the problem I would like to read the WKC (Working counter) of the devices (0x0300...0x030C), how is explained in EtherCat documents, but it seems that the read of the counter is disabled. Attached there is an extract of the Ethercat document. Can anyone give me some advice about how and with function can I read it. Thank you in advance!
Last updated: 2024-03-29
Post by albzen on EtherCat Slaves diagnosis
CODESYS Forge
talk
(Post)
Hello everybody, I'm working on a RunTime Plc (Codesys 3.5.16/18.20) connected to an EtherCat bus with many devices. The bus has some communication fault but I don't know how understand which is the device or the cable that has the trouble. To understand the cause of the problem I would like to read the WKC (Working counter) of the devices (0x0300...0x030C), how is explained in EtherCat documents, but it seems that the read of the counter is disabled. Attached there is an extract of the Ethercat document. Can anyone give me some advice about how and with function can I read it. Thank you in advance!
Last updated: 2024-03-29
Post by hafizapik99 on Webvisu not showing Codesys V3.5 SP13 Patch 4
CODESYS Forge
talk
(Post)
Hello, I am using a Hitachi Micro EHV+ for a small project, and I wanted to have a Web visu, done with Codesys V3.5 SP13 Patch 2. I test the Visu screen and it works well in Codesys, but I get a blank page when i enter the web visu in a browser. Here is the setting under web visualization: Update rate (ms): 5000 (previously set to 2500 also not working) Default communication size: 100000 (previously set to 50000 also not working) Under Visu_Task tab: Priority: 3 The Visu_Task interval is set to 2500ms (previously set to 200ms also not working) I'm using Google chrome with the latest update, the Javascript is enabled with HTML5. Any advice?
Last updated: 2024-04-06
Post by hafizapik99 on Webvisu not showing Codesys V3.5 SP13 Patch 2.
CODESYS Forge
talk
(Post)
Hello, I am using a Hitachi Micro EHV+ for a small project, and I wanted to have a Web visu, done with Codesys V3.5 SP13 Patch 2. I test the Visu screen and it works well in Codesys, but I get a blank page when i enter the web visu in a browser. Here is the setting under web visualization: Update rate (ms): 5000 Default communication size: 100000 Under Visu_Task tab: Priority: 3 The Visu_Task interval is set to 2500ms I'm using Google chrome with the latest update, the Javascript is enabled with HTML5. Any advice?
Last updated: 2024-04-06
Post by sachem on Problem retain values Weidmuller UC20-WL2000
CODESYS Forge
talk
(Post)
Good afternoon. I am working with a weidmuller uc20-wl2000 controller, using a codesys license. We made a ladder code to control a process, and it works well, but we want some variables to remain stored even when the controller is turned off. We tried to use retain variables, but at the time of loading the program, when we went offline from the controller, the program was deleted, it did not remain in the controller, and in the same way if we turned off the controller. In addition to this, when we tried to program it again, the program would not stay loaded and began to present errors with the opc-ua communication. What could be causing this problem? How can we maintain the values of the variables without damaging the program or affecting the controller? thank you
Last updated: 2024-04-10
Post by kuegerls on SysProcessExecuteCommand2 and CANopen Device
CODESYS Forge
talk
(Post)
Hello, CODESYS Control is running on my RevPi, and my system communicates over a CANbus with a master using the ConnectCan module (Slave - CANopen Device). The communication works perfectly fine so far. However, as soon as I call a Python script with "SysProcessExecuteCommand2" that creates a CSV file and executes without errors, the master does not adopt any changes to the Transmission Process Data Objects (TPDOs). I don't quite understand what one has to do with the other, and perhaps someone can help me with this. Here is my script call: SysProcess.SysProcessExecuteCommand2(pszCommand:='python /home/pi/test.py', pszStdOut:=sCMDOutput, udiStdOutLen:= SIZEOF(sCMDOutput), pResult := ADR(eResult)); Thank you in advance! Best regards, Stefan
Last updated: 2024-06-20
Post by rohan on Child Application Alarm
CODESYS Forge
talk
(Post)
Hi All, I'm trying to develop a multi-application project that allows me to switch between applications. I currently have a parent application and several child applications, as this is the only way for them to share CAN/Ethernet communication. I've noticed that I am only able to create an Alarm Configuration for the parent application. But the children application do not seem to be displaying alarms on the Alarm Table in the visualisation for when an alarm is raised. Does anyone know of a fix, solution or a way around this? I am utilising Codesys v3.5 SP16 Patch 5 64Bit
Last updated: 2024-06-21
Post by kthomas on Cant login to Rpi4 but can see it in codesys communications settings.
CODESYS Forge
talk
(Post)
I have been struggling for over a week to program my rapspberry pi 4 with codesys. I purchased the license. I installed the runtime and the gateway, and I can see the pi in the communication settings. But cannot log in. I have checked the status of the pi with sudo systemctl status codesyscontrol and it is running. I have enabled traffic to and from the pi with iptables and checked the logs and all looks good. I just cannot connect through the codesys ide. Can anyone help me before I lose my mind?
Last updated: 2024-06-22
Post by kthomas on Cant login to Rpi4 but can see it in codesys communications settings.
CODESYS Forge
talk
(Post)
I have been struggling for over a week to program my rapspberry pi 4 with codesys. I purchased the license. I installed the runtime and the gateway, and I can see the pi in the communication settings. But cannot log in. I have checked the status of the pi with sudo systemctl status codesyscontrol and it is running. I have enabled traffic to and from the pi with iptables and checked the logs and all looks good. I just cannot connect through the codesys ide. Can anyone help me before I lose my mind?
Last updated: 2024-06-22
Post by pazderai on CanOpen write issue
CODESYS Forge
talk
(Post)
Thank you for an answer. Unfortunatelly, it doesn't work. The slave needs command byte as follows 0x22. It means expedited transfer where s-bit is not set, therefore data length is not specified. If I use segmented mode by CiA405.SDO_WRITE_DATA it produce command byte as follows 0x21 which is unfortunately supported by the slave and it returns with error 0x05040001 - SDO Abort Code -Client/server command specifier not valid or unknown. I can use CAN API low level to overcome this problem where it is possible to set 0x22 as a command byte, but than I can use user interface to set the communication probably, because I thing that machine expert uses library CiA405.SDO_WRITE for setting the slave. Or am I wrong?
Last updated: 2024-07-16
Post by toffeebonbon on EL7041-0052 - does it run with EL7041 SoftMotion?
CODESYS Forge
talk
(Post)
I let this project rest for a while and picked it up last week. I have been in contact with the support from beckhoff and got the information that the terminals were identical (communication wise). As the Log of the Axis (not the drive's log) shows the error when trying to write into the register 0x8012 and set the value for an encoder to a value that is the default - at least according to the manual - I was wondering if it is possible to "not write that value" to skip that part? Or am I misunderstanding the way the library communicates with the drive?
Last updated: 2024-07-24
Post by alimans on OPC-UA Server, Symbol Set: Raise an error: Object reference not set to an instance of an object.
CODESYS Forge
talk
(Post)
Hi everyone, I just created a very simple library without any code and, added it to my very simple project. after adding this library, I get an error when I try to open "Symbol Set" in "OPC UA Server" in "Communication Manager". Here is the code of my POU in the library: FUNCTION_BLOCK POU VAR eCommand : (CMD_NONE:=0, CMD_RESET:=-1) INT := CMD_NONE; END_VAR Attached is the error that I get. I also noticed that by removing the enumeration variable above (eCommand), I can open the "Symbol Set" again. Anybody has any idea why this error is raised and how could I use enumeration variables without error in "OPC UA Symbol Set"?
Last updated: 2024-08-08
Post by expertplas on No connection to opc server from codesys opc client
CODESYS Forge
talk
(Post)
Hello, we have aproblen to connect our CODESYS OPC Client to the OPC Server. We installed the client according the CODESYS manual. We can browse the server and variables can be linked to the PLC. I created a self signed certificate for the CmpOPCUAClent as described. The server has a cerificate also. I copied the certificates to the trusted zone of server and client. But when it comes to data exchange we get an error message. "Communication error in data source OPC UA Library. Error ID : 7001 German : "Kommunikatinsfehler inder Datenquelle OPC UA -Bibiothek. Es wurde kein genauer Fehler angegeben. Fehler ID : 7001" It semms that there is no cerificate exchange. We are working with CODESYS 3.5 SP19 Patch 5. Can anyone here say something about this error or has an idea for a solution? Thanks.
Last updated: 2024-08-19
Post by jp23 on Unable to Connect to Modbus RTU Device
CODESYS Forge
talk
(Post)
Hi all, I am attempting to use the Control Win V3 soft PLC to control a WAGO 750-315 remote I/O system via modbus RTU communication. I am struggling to connect to the device. I have been following this tutorial: https://www.youtube.com/watch?v=YlRfkESaNds I have setup my devices as shown in the images below. I have verified that my com port settings are correct as I am able to connect/control using modbus simulator software with these settings. I have also connected to a modbus master simulator program as instructed in the video, but the orange triangles will not go away. Additionally, I have updated my settings to 485 using the PLC shell. I have also set "always update variables" to enabled (1). Serial port, PCI-Bus, and modbus serial device status all show as "Not Running."
Last updated: 2024-08-26
Post by jp23 on Unable to Connect to Modbus RTU Device
CODESYS Forge
talk
(Post)
Hi all, I am attempting to use the Control Win V3 soft PLC to control a WAGO 750-315 remote I/O system via modbus RTU communication. I am struggling to connect to the device. I have been following this tutorial: https://www.youtube.com/watch?v=YlRfkESaNds I have setup my devices as shown in the images below. I have verified that my com port settings are correct as I am able to connect/control using modbus simulator software with these settings. I have also connected to a modbus master simulator program as instructed in the video, but the orange triangles will not go away. Additionally, I have updated my settings to 485 using the PLC shell. I have also set "always update variables" to enabled (1). Serial port, PCI-Bus, and modbus serial device status all show as "Not Running."
Last updated: 2024-08-26
Post by jp23 on Unable to Connect to Modbus RTU Device
CODESYS Forge
talk
(Post)
Hi all, I am attempting to use the Control Win V3 soft PLC to control a WAGO 750-315 remote I/O system via modbus RTU communication. I am struggling to connect to the device. I have been following this tutorial: https://www.youtube.com/watch?v=YlRfkESaNds I have setup my devices as shown in the images below. I have verified that my com port settings are correct as I am able to connect/control using modbus simulator software with these settings. I have also connected to a modbus master simulator program as instructed in the video, but the orange triangles will not go away. Additionally, I have updated my settings to 485 using the PLC shell. I have also set "always update variables" to enabled (1). Serial port, PCI-Bus, and modbus serial device status all show as "Not Running."
Last updated: 2024-08-26
Post by jp23 on Unable to Connect to Modbus RTU Device
CODESYS Forge
talk
(Post)
Hi all, I am attempting to use the Control Win V3 soft PLC to control a WAGO 750-315 remote I/O system via modbus RTU communication. I am struggling to connect to the device. I have been following this tutorial: https://www.youtube.com/watch?v=YlRfkESaNds I have setup my devices as shown in the images below. I have verified that my com port settings are correct as I am able to connect/control using modbus simulator software with these settings. I have also connected to a modbus master simulator program as instructed in the video, but the orange triangles will not go away. Additionally, I have updated my settings to 485 using the PLC shell. I have also set "always update variables" to enabled (1). Serial port, PCI-Bus, and modbus serial device status all show as "Not Running."
Last updated: 2024-08-26
Post by jp23 on Unable to Connect to Modbus RTU Device
CODESYS Forge
talk
(Post)
Hi all, I am attempting to use the Control Win V3 soft PLC to control a WAGO 750-315 remote I/O system via modbus RTU communication. I am struggling to connect to the device. I have been following this tutorial: https://www.youtube.com/watch?v=YlRfkESaNds I have setup my devices as shown in the images below. I have verified that my com port settings are correct as I am able to connect/control using modbus simulator software with these settings. I have also connected to a modbus master simulator program as instructed in the video, but the orange triangles will not go away. Additionally, I have updated my settings to 485 using the PLC shell. I have also set "always update variables" to enabled (1). Serial port, PCI-Bus, and modbus serial device status all show as "Not Running."
Last updated: 2024-08-26
Post by jp23 on Unable to Connect to Modbus RTU Device
CODESYS Forge
talk
(Post)
Hi all, I am attempting to use the Control Win V3 soft PLC to control a WAGO 750-315 remote I/O system via modbus RTU communication. I am struggling to connect to the device. I have been following this tutorial: https://www.youtube.com/watch?v=YlRfkESaNds I have setup my devices as shown in the images below. I have verified that my com port settings are correct as I am able to connect/control using modbus simulator software with these settings. I have also connected to a modbus master simulator program as instructed in the video, but the orange triangles will not go away. Additionally, I have updated my settings to 485 using the PLC shell. I have also set "always update variables" to enabled (1). Serial port, PCI-Bus, and modbus serial device status all show as "Not Running."
Last updated: 2024-08-26
Post by jp23 on Unable to Connect to Modbus RTU Device
CODESYS Forge
talk
(Post)
Hi all, I am attempting to use the Control Win V3 soft PLC to control a WAGO 750-315 remote I/O system via modbus RTU communication. I am struggling to connect to the device. I have been following this tutorial: https://www.youtube.com/watch?v=YlRfkESaNds I have setup my devices as shown in the images below. I have verified that my com port settings are correct as I am able to connect/control using modbus simulator software with these settings. I have also connected to a modbus master simulator program as instructed in the video, but the orange triangles will not go away. Additionally, I have updated my settings to 485 using the PLC shell. I have also set "always update variables" to enabled (1). Serial port, PCI-Bus, and modbus serial device status all show as "Not Running."
Last updated: 2024-08-26
Post by shabroz-gill on Exception when OPCUA datasource disconnects from Server
CODESYS Forge
talk
(Post)
If i loose the network and the opcua data source suddenly looses connection with the server, i get an exception and my application stops working. I am using the latest version of the communication add v4.5.2.0 Is this a known issue? This makes the datasource unusable because it is inevitable that we will loose connectivity at some point, and the datasource crashing everything due to that seems to be a deal breaker. I can provide more details is someone from codesys is reading this. You can recreate is by just shutting off the Opc server after the codesys data source is connected and reading data from it. The codesys app does not crash everytime and sometimes it is able to reconnect without crashing, so you may have to try this a few times to see the exception. Best regards
Last updated: 2024-09-16
Post by davidbo on RPI can system operation like rm in a shell have an impact on a Task cycle time
CODESYS Forge
talk
(Post)
I have noticed that a rm file1.txt command on a shell has an impact on the cycle time for a TASK writing to file2.txt. Seen in the Monitor fane of the Task configuration Furthermore if a TASK makes a system call like rm, its cycle time increases of course but it seems to have an invisible impact on other TASKs too. I have a TASK for handling communication over the CANbus (SPI) where it stops sending "Heartbeats" for many seconds when another TASK does a system rm. Why is that not seen on the Monitor fane? Is even codesyscontrol paused when system calls are made? The CPU load is about 30-40%
Last updated: 2024-09-23