Post by timvh on Modbus TCP & RTU with Control for Linux SL
CODESYS Forge
talk
(Post)
RS485 doesn't seem very logical to use in VPLC's in my opinion. I also don't know if this is supported.... But for TCP/IP, I think you still need to configure the Nic settings. See the attached png. In my case enp6s0. When changing this setting, restart the VPLC. What is really nice, is that you don't have to configure the IP address setting in Linux. By setting the Nic to a certain IP address in the CODESYS instance configuration, this is automatically done for you. I only tested this with EtherCAT, but I guess this works the same for Modbus TCP/IP.
Last updated: 2024-10-23
Post by dwpessoa on CNC Jumps G20 - SMC_NCInterpreter and long time to process
CODESYS Forge
talk
(Post)
I am studying and developing a Softmotion+CNC system for a machine that executes multiple pieces. The G code program is written by the machine operator and each cycle execute 1 piece. The programs are large, exceeding 1000 lines and using up to 8 axes (X, Y, Z, A, B, C, P and Q). The machine needs to run cyclically, executing N pieces (selected by the Operator)... so I tested it using Looping and counters (G36 G37 and G20) and it worked, but it takes a long time to process, and the more pieces I need, the longer the processing time and this is totally impracticable. I found this solution which was very good, and for a few cycles it works well, but for 99999 pieces of a program with 1000 lines, it doesn't work very well... Another solution I tested is to maintain the interpolator with an automatic restart, that is, I load the program without looping (without G20) and give it another start as soon as it finishes. This partially resolved it, but there is still a delay in processing SMC_NCInterpreter in each restart :(. Another solution I thought of is to manually create the SMC_GEOINFO structure and then reuse it, avoinding the Interpreter, but reading the documentation and checking the structure filled by standard blocks, I noticed that there doesn't seem to be a "JUMP" function in the structure! In other words, the SMC_NCInterpreter actually keeps copying and copying the program section for each jump (G20)... If I repeat a 10-line program 1000 times, I will have a structure with more than 10000 lines... possibly this is the cause of take so long to process. Has anyone ever had a problem like this? I believe the same thing happens with typical applications with manipulator robots using Codesys in continuous cycles, and I would like to know if there is any solution, or even if I am misinterpreting the G20 question in SMC_GEOINFO. Thanks!
Last updated: 2023-09-20
Post by dantheman on Connecting to SoftPLC Only Works By Turning Off Modbus Ethernet Port
CODESYS Forge
talk
(Post)
I have an IPC with 2 ethernet ports and 1 Wi-Fi. I'm using ModbusTCP with the ethernet port named "enp2s0" connected to my remote I/O. This works fine when testing with Python and also works with CODESYS, but CODESYS is only able to scan for the Linux SoftPLC when I turn off the "enp2s0" interface. In other words, I can't get online with the IDE if I want my ModbusTCP comms to run with CODESYS. I'm using a Linux SoftPLC that has the following entry in CODESYSControl.cfg, hoping that this will allow me to connect with "enp1s0" or "wlp3s0", and leave "enp2s0" for field comms, but this seems to only make the source IP of the ModbusTCP comms to be bound to "enp2s0". That last point is the case only if I don't restart the service, but if I do restart the service after changing the config file, the source IP for the ModbusTCP comms then becomes the one for "enp1s0", which is very confusing to me: [SysSocket] Adapter.0.Name="enp2s0" Adapter.0.EnableSetIpAndMask=1 On the device list, I only have "enp2s0" given as the ethernet device that has the ModbusTCP master & slave beneath it, shown in Screenshot 1. On the IPC, I can ping the ModbusTCP client (remote I/O) from "enp2s0", and I've attached a Wireshark capture of running ModbusTCP from the CODESYS runtime as Screenshot 2, 3 & 4 (again, I can't get online when this is running, I have to turn off "enp2s0" to connect even when it's idle and I don't have an active TCP session with my Python tests). Like I explained above, the source IP is "enp1s0", even though the ethernet device on the project is "enp2s0". I was lucky to catch the red message that showed the source IP that makes sense to me (the one for "enp2s0"), but for some reason that connection was reset and I never saw that packet again. I've also tried this with Auto-reconnect both enabled & disabled, for the ModbusTCP Master device. I also have to turn off "enp1s0" and then turn it on, just so that I can have the ModbusTCP comms running from "enp2s0" (which is not intuitive in any way to me, I'd love some help understanding that phenomenon as well) in the weird manner that I've described above. I would be very appreciative if someone can help me figure out this pickle. I'd love to just connect to CODESYS through my Wi-Fi interface and leave my ethernet ports for field comms.
Last updated: 2024-08-01
Post by manuknecht on Persistence Manager does not save alphabetically first value
CODESYS Forge
talk
(Post)
I have several libraries which contain values that should be saved on a PLC. As apparently no Persistent Variable List is available within Libraries, I use the Persistence Manager to create a Persistence Channel in the Project which imports the library. I then specify the persistence channel in the library using the {attribute 'ac_persist':='PersistenceChannel_CT'} specifier. This generally works very well and gives me exactly the properties I require. However, it came to my attention that the (alphabetially) first value from the library is not saved in the created ASCII file. When checking the content of the Persistence Channel, it shows all the variables as defined in the library. But the created file does not contain the first value and it is not restored after restart or reset. (see attached picture) I disabled Periodic Saving and set xSaveOnChange to TRUE and so the file usually updates immediately after changing one of the values. When changing the first value, it does not update which is consistent with this value not being saved. I also created a sample project and library from scratch which shows the same issue both using a Raspberry Pi and using a Linux machine. Does someone know what the reason for this could be or did someone make similar experiences? Looking forward to hearing your suggestions. Thanks in advance and best wishes Manuel
Last updated: 2023-10-17
Post by ewi04 on Git with visu
CODESYS Forge
talk
(Post)
Hi, I have several problems with the git extension. Situation: I am working with Codesys v3.5 SP19 Patch 1 and Git V1.2.1.0. The remote repository is GitLab Community Edition v16.1.2. I am working on a project with one other person. Problems: 1: After each start of Codesys all of the visu pages are marked as modified. So we have to discard all changes first. Otherwise the history is not clean and the merge request becomes more complex. I tested it with a new project and only local. I made the observation, that a page is not marked as modified when it is committed a second time (after a restart of codesys). But this is necessary after every change of a page. However, since we are working in a team, it seems we are playing ping-pong and so all pages are marked as modified on each startup. 2: Each image pool causes a parent child conflict. Also in my local project. The only solution that I have found, is to ignore the issue. Does anyone have the same problems? I think it looks more like bugs. Thanks ewi04
Last updated: 2023-11-22
Post by tim-roelant on Profinet fault with codesys control V3 - Receive packet error
CODESYS Forge
talk
(Post)
I have set up a brandnew Beckhoff panel pc with a codesys control runtime V3. I configured it together with 2 profinet field devices: a 16in/16out IO module from Turck and an MTS linear encoder. The machine works fine untill all of a sudden the communication breaks and the profinet participants become unreachable. At that point I can still ping the device, but the profinet master does not find them anymore: When i do a scan they are not found. When i do a cold restart, the profinet master becomes active again and the devices are found again. In the log i get Ethercat packet receive error: sysethernet. I am a little confused, there is no ethercat device in the device tree. I already set the send clock and the reduction ratio to higher values, but without result. Can codesys be configured, so that the communication re-establishes without doing the cold reset? This is very annoying and is causing a lot of prodution losses. regards Tim
Last updated: 2024-02-27
Post by tim-roelant on Profinet fault with codesys control V3 - Receive packet error
CODESYS Forge
talk
(Post)
I have set up a brandnew Beckhoff panel pc with a codesys control runtime V3. I configured it together with 2 profinet field devices: a 16in/16out IO module from Turck and an MTS linear encoder. The machine works fine untill all of a sudden the communication breaks and the profinet participants become unreachable. At that point I can still ping the device, but the profinet master does not find them anymore: When i do a scan they are not found. When i do a cold restart, the profinet master becomes active again and the devices are found again. In the log i get Ethercat packet receive error: sysethernet. I am a little confused, there is no ethercat device in the device tree. I already set the send clock and the reduction ratio to higher values, but without result. Can codesys be configured, so that the communication re-establishes without doing the cold reset? This is very annoying and is causing a lot of prodution losses. regards Tim
Last updated: 2024-02-27
Post by tim-roelant on Profinet fault with codesys control V3 - Receive packet error
CODESYS Forge
talk
(Post)
I have set up a brandnew Beckhoff panel pc with a codesys control runtime V3. I configured it together with 2 profinet field devices: a 16in/16out IO module from Turck and an MTS linear encoder. The machine works fine untill all of a sudden the communication breaks and the profinet participants become unreachable. At that point I can still ping the device, but the profinet master does not find them anymore: When i do a scan they are not found. When i do a cold restart, the profinet master becomes active again and the devices are found again. In the log i get Ethercat packet receive error: sysethernet. I am a little confused, there is no ethercat device in the device tree. I already set the send clock and the reduction ratio to higher values, but without result. Can codesys be configured, so that the communication re-establishes without doing the cold reset? This is very annoying and is causing a lot of prodution losses. regards Tim
Last updated: 2024-02-27
Post by tim-roelant on Profinet fault with codesys control V3 - Receive packet error
CODESYS Forge
talk
(Post)
I have set up a brandnew Beckhoff panel pc with a codesys control runtime V3. I configured it together with 2 profinet field devices: a 16in/16out IO module from Turck and an MTS linear encoder. The machine works fine untill all of a sudden the communication breaks and the profinet participants become unreachable. At that point I can still ping the device, but the profinet master does not find them anymore: When i do a scan they are not found. When i do a cold restart, the profinet master becomes active again and the devices are found again. In the log i get Ethercat packet receive error: sysethernet. I am a little confused, there is no ethercat device in the device tree. I already set the send clock and the reduction ratio to higher values, but without result. Can codesys be configured, so that the communication re-establishes without doing the cold reset? This is very annoying and is causing a lot of prodution losses. regards Tim
Last updated: 2024-02-27
Post by markushunter on Different behavior between the "Start" button in the IDE and the Cmp function "AppStartApplication()"
CODESYS Forge
talk
(Post)
In our application with CODESYS V3.5 SP19 Patch 5 and the Soft-PLC Name: CODESYS Control Win V3 x64 Typ: 4096 ID: 0000 0004 Version: 3.5.19.50 the application behaves differently when we start the application via Cmp.AppStartApplication(pApp) than when we press the "Start" button in online mode in the IDE. Unfortunately, it looks like the AppStartApplication() function, which is called in the "StopDone" system event, is not able to restart the fieldbus driver correctly, in our case the EtherNet_IP_Scanner: Name: EtherNet/IP Scanner Hersteller: 3S - Smart Software Solutions GmbH Kategorien: EtherNet/IP Scanner Typ: 100 ID: 0000 100B Version: 4.5.1.0 Bestellnummer: 1 And one EtherNet/IP adapter Name: FANUC Robot R30iB Plus Hersteller: FANUC Robotics America Kategorien: EtherNet/IP Remote Adapter Typ: 101 ID: 356_12_4_3 Version: Major Revision=16#3, Minor Revision = 16#1 Beschreibung: EtherNet/IP Target imported from EDS File: fanucrobot0301_r30ibp.eds Device: FANUC Robot R30iB Plus Version Konfiguration 3.5.6.0 The application was cold reset in both cases via CmpApp.AppReset(pApp := pApp, usResetOption := CmpApp.RTS_RESET_COLD. Does anyone know the difference between the functions or services executed by the "START" button in online mode and Cmp.AppStartApplication()? Thanks and best regards, markushunter
Last updated: 2024-03-20
Post by markushunter on Different behavior between the "Start" button in the IDE and the Cmp function "AppStartApplication()"
CODESYS Forge
talk
(Post)
In our application with CODESYS V3.5 SP19 Patch 5 and the Soft-PLC Name: CODESYS Control Win V3 x64 Typ: 4096 ID: 0000 0004 Version: 3.5.19.50 the application behaves differently when we start the application via CmpApp.AppStartApplication(pApp) than when we press the "Start" button in online mode in the IDE. Unfortunately, it looks like the AppStartApplication() function, which is called in the "StopDone" system event, is not able to restart the fieldbus driver correctly, in our case the EtherNet_IP_Scanner: Name: EtherNet/IP Scanner Hersteller: 3S - Smart Software Solutions GmbH Kategorien: EtherNet/IP Scanner Typ: 100 ID: 0000 100B Version: 4.5.1.0 Bestellnummer: 1 And one EtherNet/IP adapter Name: FANUC Robot R30iB Plus Hersteller: FANUC Robotics America Kategorien: EtherNet/IP Remote Adapter Typ: 101 ID: 356_12_4_3 Version: Major Revision=16#3, Minor Revision = 16#1 Beschreibung: EtherNet/IP Target imported from EDS File: fanucrobot0301_r30ibp.eds Device: FANUC Robot R30iB Plus Version Konfiguration 3.5.6.0 The application was cold reset in both cases via CmpApp.AppReset(pApp := pApp, usResetOption := CmpApp.RTS_RESET_COLD. Does anyone know the difference between the functions or services executed by the "START" button in online mode and Cmp.AppStartApplication()? Thanks and best regards, markushunter
Last updated: 2024-03-20
Post by markushunter on Different behavior between the "Start" button in the IDE and the Cmp function "AppStartApplication()"
CODESYS Forge
talk
(Post)
In our application with CODESYS V3.5 SP19 Patch 5 and the Soft-PLC Name: CODESYS Control Win V3 x64 Typ: 4096 ID: 0000 0004 Version: 3.5.19.50 the application behaves differently when we start the application via Cmp.AppStartApplication(pApp) than when we press the "Start" button in online mode in the IDE. Unfortunately, it looks like the AppStartApplication() function, which is called in the "StopDone" system event, is not able to restart the fieldbus driver correctly, in our case the EtherNet_IP_Scanner: Name: EtherNet/IP Scanner Hersteller: 3S - Smart Software Solutions GmbH Kategorien: EtherNet/IP Scanner Typ: 100 ID: 0000 100B Version: 4.5.1.0 Bestellnummer: 1 And one EtherNet/IP adapter Name: FANUC Robot R30iB Plus Hersteller: FANUC Robotics America Kategorien: EtherNet/IP Remote Adapter Typ: 101 ID: 356_12_4_3 Version: Major Revision=16#3, Minor Revision = 16#1 Beschreibung: EtherNet/IP Target imported from EDS File: fanucrobot0301_r30ibp.eds Device: FANUC Robot R30iB Plus Version Konfiguration 3.5.6.0 The application was cold reset in both cases via CmpApp.AppReset(pApp := pApp, usResetOption := CmpApp.RTS_RESET_COLD. Does anyone know the difference between the functions or services executed by the "START" button in online mode and Cmp.AppStartApplication()? Thanks and best regards, markushunter
Last updated: 2024-03-20
Post by caprez95 on Trace Restart Visuelement
CODESYS Forge
talk
(Post)
Hallo zusammen. Ich habe schon länger mit dem Problem zu kämpfen, dass ich einen Trend (Visuelement) nicht resetten (neustarten) kann. Ich habe es jetzt mit dem Beispiel hinbekommen, die Trace-Aufzeichnung über die CmpTraceMgr Bibliothek zu steuern. Aber wie bekomme ich diese Trace-Aufzeichnung in ein Visuelement? Der Code sieht wie folgt aus: // Configure trace IF xInit THEN // Create a trace packet PacketConfig.pszName := ADR('IECTraceConfiguration.Trace1'); // Name of trace PacketConfig.pszApplicationName := ADR('IECTraceConfiguration'); // Name of the application PacketConfig.pszIecTaskName := ADR('Task'); // Name of the task PacketConfig.pszComment := ADR('Demo packet'); PacketConfig.ulEveryNCycles := 1; PacketConfig.ulBufferEntries := 1000; PacketConfig.ulFlags := TRACE_PACKET_FLAGS.TRACE_PACKET_FLAGS_TIMESTAMP_MS AND TRACE_PACKET_FLAGS.TRACE_PACKET_FLAGS_AUTOSTART; IF (NOT fbTraceManager.CreatePacket(PacketConfig := PacketConfig, hPacket=>hPacket1)) THEN xError := TRUE; END_IF // Create a trace record RecordConfig.pszVariable := ADR('iSignal'); // This is the name of variable to record RecordConfig.tcClass := INT_TO_UDINT(TypeClass.TYPE_INT); // Type of the recording variable RecordConfig.ulSize := SIZEOF(iSignal); // Size of the recording variable pApp := AppFindApplicationByName('IECTraceConfiguration', 0); AppGetAreaOffsetByAddress(pApp, ADR(iSignal), ADR(RecordConfig.tvaAddress.taAddress.Area.usArea), ADR(RecordConfig.tvaAddress.taAddress.Area.ulOffset)); // Get and set area offsets RecordConfig.tvaAddress.ulAddressFlags := TRACE_VAR_ADDRESS_FLAGS_IEC OR TRACE_VAR_ADDRESS_FLAGS_AREA_OFFSET; RecordConfig.ulGraphColor := 16#FF00FF00; // green RecordConfig.ulGraphType := 1; // Line with points IF (NOT fbTraceManager.AddRecord(RecordConfig := RecordConfig, hPacket := hPacket1, hRecord => hRecord1)) THEN xError := TRUE; END_IF xInit := FALSE; END_IF // Starts the recording IF xStart THEN IF (NOT fbTraceManager.StartPacket(hPacket := hPacket1)) THEN xError := TRUE; END_IF xStart := FALSE; END_IF // Stop the recording IF xStop THEN IF (NOT fbTraceManager.StopPacket(hPacket := hPacket1)) THEN xError := TRUE; END_IF xStop := FALSE; END_IF // Reset the recording IF xReset THEN IF (NOT fbTraceManager.ResetPacket(hPacket := hPacket1)) THEN xError := TRUE; END_IF xReset := FALSE; END_IF
Last updated: 2024-06-04
Post by fajean on CODESYS control on RPi starts, shortly runs, then exits
CODESYS Forge
talk
(Post)
I have a Raspberry Pi 4 we have been using for years to run CODESYS for development purposes. I recently have had to re-install the OS (Raspberry OS lite). The only change to the default configuration is not creating the "pi" user during install. I (apparently successfully) installed the 4.10.0.0 control on the Raspberry Pi. We have licences on a dongle. I am able to start the control. systemctl status shows it as running for a little while (exactly, precisely 30 seconds as per my tests, every time), then it becomes exited. I can restart the control, and the same thing happens again. Every time. In the brief moments it is running, I can log in to the PLC. Working fast and restarting the control many times, I have been able to configure users. I have been able to download my application. I have been able to run the application, and stop on a breakpoint. I have been able to connect with the licence manager and confirm the dongle is detected and licences are listed as OK. I see nothing wrong until the service just exits. I have found nothing in the logs. It is like the runtime just terminates with no error code or message after exactly 30 seconds. Any help would be appreciated.
Last updated: 2024-06-13
Post by dekelec on Codesys 2.3 & Peak PCAN
CODESYS Forge
talk
(Post)
I use Peak USB adapter daily to download from CoDeSys 2.3 and 3.5 to IFM, EPEC and other controllers. The process: - First you need to install the appropriate driver. Link: https://www.peak-system.com/Drivers.523.0.html?&L=1 - Restart the computer - Start the CoDeSys application - Change the name of the adapter in Communication parameters, as mentioned in previous comment. Write the name exactly as written "Peak_USB", as it could also be case sensitive (defines which .dll file to use). If this doesn't work I would contact the vendor of the controller to find out the procedure. In the attachment I've added a FAQ document from IFM regarding using PCAN USB. P.S. I've noticed in your picture of communication parameters a channel via TCP/IP is mentioned. In this case a USB to CAN connection is not being used. First you should change the channel/gateway to connect via CANbus or connect using an Ethernet cable.
Last updated: 2024-07-09
Post by gallusrrr on usb2can in Codeysy 3.5 Can Gateway
CODESYS Forge
talk
(Post)
Hallo und guten Morgen, Ich danke für die Rückmeldung. ich habe das oben geschriebene durchgeführt und auch festgestellt das mit die Commandos für die Can befehle noch fehlen. (Google angeschmissen und geschaut auch gefunden) sudo apt-get install can-utils (damit auch jemanden anders der Post hilft) Anschließend habe ich das CAN System komplett aufgebaut so das ich mit einen anderen CAN Adapter schauen konnte ob die Nachricht auch ankommt. die Nachricht kommt an :) danach habe ich follgende Ausgabe: pi@Codesys:~ $ sudo ip -s -d link show can0 3: can0: <noarp,up,lower_up,echo> mtu 16 qdisc pfifo_fast state UP mode DEFAULT group default qlen 10 link/can promiscuity 0 allmulti 0 minmtu 0 maxmtu 0 can state ERROR-ACTIVE restart-ms 0 bitrate 250000 sample-point 0.875 tq 250 prop-seg 6 phase-seg1 7 phase-seg2 2 sjw 1 brp 12 gs_usb: tseg1 1..16 tseg2 1..8 sjw 1..4 brp 1..1024 brp_inc 1 clock 48000000 re-started bus-errors arbit-lost error-warn error-pass bus-off 0 0 0 0 0 0 numtxqueues 1 numrxqueues 1 gso_max_size 65536 gso_max_segs 65535 tso_max_size 65536 tso_max_segs 65535 gro_max_size 65536 parentbus usb parentdev 1-1.4:1.0 RX: bytes packets errors dropped missed mcast 3549 819 0 0 0 0 TX: bytes packets errors dropped carrier collsns 32 4 0 0 0 0</noarp,up,lower_up,echo> (Sorry habe kein Speicherplatz im Web um Bilder anzuzeigen..) man kan sehen das die Nachricht abgeht und auch 32 Byte Empfangen worden sind. Die nachricht ist auch am anderen CAN Adapter sichtbar gewesen. Wie bekomem ich den einrichteten Adapter in Codesys rein? das ich den Befehl sudo ip link set can0 up type can bitrate 500000 das ich die Einrichtungs des Can Adapters noch in die Rasperry Start rutine nehmen muss ist mir klar. Ich bedanke mich .
Last updated: 2024-01-18