Post by timvh on Is it possible to use debug functions such as Step Execution while the PLC ladder is in Running? CODESYS Forge talk (Post)
Yes, it is possible to set breakpoints and use step into / step over (also in Ladder diagram). Yes, the PLC will actually stop, so be carefull with this. How a PLC works is that at the start of the execution of the Task, the Inputs are read, then the code is being executed and then the outputs are written. So if you set a breakpoint, you will not see your analog inputs changing, because the task cycle is interrupted and the inputs and outputs are not refreshed. For detailed information, see: https://content.helpme-codesys.com/en/CODESYS%20Development%20System/_cds_using_breakpoints.html
Last updated: 2024-01-16

Post by fdmartello on Unable to compare projects containing alarm manager 4.5.0.0 CODESYS Forge talk (Post)
Hello. In Codesys version 3.5.19.50 when comparing two projects that have an "Alarm Configuration" obj from the Alarm Manager library vers. 4.5.0.0 the attached error pops up. This originally happened with two projects that I converted from vers. 3.5.17.30 so, thinking it was some conversion issue, I created two clean projects directly in 3.5.19.50 using the Standard Project template and only added the Alarm Configuration objects in them. The result is the same and the only way I found that allowed me to compare them is by deleting the incriminated object in one of the two projects. Has anyone else encountered this issue? Best regards
Last updated: 2024-01-19

Post by arundara on OPC UA Server Stops after 5 consecutive disconnections of ethernet port CODESYS Forge talk (Post)
Hello Every one, During testing of OPC UA communication between UA Expert software and the CODESYS SoftPLC on a Linux environment, an observation was made. When the Ethernet cable was disconnected and reconnected with 2-minute intervals, on the 5th attempt, the OPC UA connection failed to establish in UA Expert software. At this juncture, restarting the CODESYS SoftPLC enabled the reestablishment of OPC UA communication. The same result was obtained when testing on a Raspberry Pi SoftPLC. What is the reason behind this phenomenon? and whether there are settings to stop this behavior? Please help. Thanks & Regards.
Last updated: 2024-02-13

Post by hafizapik99 on Webvisu not showing Codesys V3.5 SP13 Patch 2. CODESYS Forge talk (Post)
Hello, I am using a Hitachi Micro EHV+ for a small project, and I wanted to have a Web visu, done with Codesys V3.5 SP13 Patch 2. I test the Visu screen and it works well in Codesys, but I get a blank page when i enter the web visu in a browser. Here is the setting under web visualization: Update rate (ms): 5000 Default communication size: 100000 Under Visu_Task tab: Priority: 3 The Visu_Task interval is set to 2500ms I'm using Google chrome with the latest update, the Javascript is enabled with HTML5. Any advice?
Last updated: 2024-04-06

Post by saugat10 on Cannot install Codesys control Multicore in raspberry pi 4 CODESYS Forge talk (Post)
I have raspberry pi 4 with Raspbian 12 (bookworm). I want to install the latest version of codesys control 4.11.0.0 multicore for 32 bit. I cannot install multicore and it only gives me the option to install Standard. Here are some outputs from the pi pi@saugat:/usr $ uname -a Linux saugat 6.6.20+rpt-rpi-v7l #1 SMP Raspbian 1:6.6.20-1+rpt1 (2024-03-07) armv7l GNU/Linux pi@saugat:~ $ cat /etc/os-release PRETTY_NAME="Raspbian GNU/Linux 12 (bookworm)" NAME="Raspbian GNU/Linux" VERSION_ID="12" VERSION="12 (bookworm)" VERSION_CODENAME=bookworm ID=raspbian ID_LIKE=debian HOME_URL="http://www.raspbian.org/" SUPPORT_URL="http://www.raspbian.org/RaspbianForums" BUG_REPORT_URL="http://www.raspbian.org/RaspbianBugs" A
Last updated: 2024-04-22

Post by reinier-geers on License problem gateway CODESYS Forge talk (Post)
Epis doesnt want Softmotion. I thought it was about the price. If it was possible it would be working already and i dont need an extra licence. Thats the problem of codesys. The software is running but hangs on its license. Epis made it posible to see the stick. I can see the license. Softmotion is there from 3.5.14.Xx Like is said And Motion control is alrady posible 15 year ago. And i only need a Sync of 2 drives. I want a good solution not a refund. Dont point to the manufacturer. The software is made by 3s not by epis .
Last updated: 2024-04-29

Post by dhumphries on Rounding error in simple addition CODESYS Forge talk (Post)
Thanks for the response, as I've thought about this problem over the last month I began to suspect this was a problem with not being able to exactly represent .1 as a 32 bit binary number. I think I've found a work around by making the number an integer, then dividing it by 10 and storing that value as a floating point number. There is still an issue with the value not being exact somewhere in the 8th or 9th decimal place, but because I'm incrementing an integer value then dividing it, the error doesn't compound.
Last updated: 2024-05-25

Post by jaspergain on Non-existing identifiers CODESYS Forge talk (Post)
Hello, I got a bit of a weird issue going on which is kind of annoying. So recently we switched a lot of Modbus IO to EtherCAT, as we were having issues with stability. All works fine, which is great. But sometimes when I change the program I get errors claiming that identifiers are not defined. Meaning I can't go online. See the picture below. I believe this is because some of these identifiers were used with Modbus, and they weren't properly removed/deleted? A clean all temporary fixes the issue, but it comes back again after a while of changing the code, and building. Any way to fix these non-existing required identifiers, or even find out where they are required? Thanks for the help in advance. Jasper.
Last updated: 2024-05-29

Post by kuegerls on SysProcessExecuteCommand2 and CANopen Device CODESYS Forge talk (Post)
Hello, CODESYS Control is running on my RevPi, and my system communicates over a CANbus with a master using the ConnectCan module (Slave - CANopen Device). The communication works perfectly fine so far. However, as soon as I call a Python script with "SysProcessExecuteCommand2" that creates a CSV file and executes without errors, the master does not adopt any changes to the Transmission Process Data Objects (TPDOs). I don't quite understand what one has to do with the other, and perhaps someone can help me with this. Here is my script call: SysProcess.SysProcessExecuteCommand2(pszCommand:='python /home/pi/test.py', pszStdOut:=sCMDOutput, udiStdOutLen:= SIZEOF(sCMDOutput), pResult := ADR(eResult)); Thank you in advance! Best regards, Stefan
Last updated: 2024-06-20

Post by wchin on Passing EtheNetIP adapter device into a Function Block to access it's IO CODESYS Forge talk (Post)
We are creating helper function blocks for our VFD(EtherNetIP). How should I set it up so that I can pass the device into and out of the Function Block so that ideally I can access the IO of the device by devicename.channelname. So something like for example we have a VFD with a start bit that is in the ControlWord channel and a SetVelocity that is a channel. And we want to create a Function Block called StartVFD. So I declare something like: FUNCTION_BLOCK StartVFD VAR_IN_OUT device: ioDrvEthernetIP.RemoteAdapter; END_VAR VAR_INPUT velocity : REAL; So in the code it would look something like device.SetVelocity := velocity; device.ControlWord.6 := True; We have a pretty basic eds file for our VFD and can update it if necessary. Thanks in advance.
Last updated: 2025-10-28

Post by wchin on Passing EtheNetIP adapter device into a Function Block to access it's IO CODESYS Forge talk (Post)
We are creating helper function blocks for our VFD(EtherNetIP). How should I set it up so that I can pass the device into and out of the Function Block so that ideally I can access the IO of the device by devicename.channelname. So something like for example we have a VFD with a start bit that is in the ControlWord channel and a SetVelocity that is a channel. And we want to create a Function Block called StartVFD. So I declare something like: FUNCTION_BLOCK StartVFD VAR_IN_OUT device: ioDrvEthernetIP.RemoteAdapter; END_VAR VAR_INPUT velocity : REAL; So in the code it would look something like device.SetVelocity := velocity; device.ControlWord.6 := True; We have a pretty basic eds file for our VFD and can update it if necessary. Thanks in advance.
Last updated: 2025-10-28

Post by wchin on Passing EtheNetIP adapter device into a Function Block to access it's IO CODESYS Forge talk (Post)
We are creating helper function blocks for our VFD(EtherNetIP). How should I set it up so that I can pass the device into and out of the Function Block so that ideally I can access the IO of the device by devicename.channelname. So something like for example we have a VFD with a start bit that is in the ControlWord channel and a SetVelocity that is a channel. And we want to create a Function Block called StartVFD. So I declare something like: FUNCTION_BLOCK StartVFD VAR_IN_OUT device: ioDrvEthernetIP.RemoteAdapter; END_VAR VAR_INPUT velocity : REAL; So in the code it would look something like device.SetVelocity := velocity; device.ControlWord.6 := True; We have a pretty basic eds file for our VFD and can update it if necessary. Thanks in advance.
Last updated: 2025-10-28

Post by mr-ege on Error: C0138: No matching 'FB_Init' method found for instantiation of VisuClientObjectMgr CODESYS Forge talk (Post)
Hi all! I'm trying to learn PLC Programing. Today I was making a simple PLC program, as you can see. When I compile the program without the visualization, there are no errors. However, when I add the visualization and then compile it, I get this error. I don’t know how to solve the problem. I have tried the following solutions: rebooting the PC and updating the software. Error Code: C0138: No matching 'FB_Init' method found for instantiation of VisuClientObjectMgr Compile complete -- 1 errors, 0 warnings Build complete -- 1 errors, 0 warnings : No download possible Version: CODESYS V3.5 SP21 Patch 3
Last updated: 2025-11-25

Post by imdatatas on Codesys IDE initialization error from a new Sandbox image CODESYS Forge talk (Post)
Hello everyone, I created a new sandbox image on the D drive with Codesys Installer. However, when I launch the IDE from this image, it gives the error shown in the attached image. -- Codesys V3.5 SP19 Patch7. -- The installer is the latest (2.5.0). -- All packages in the installer were updated to the latest version as of today when creating the sandbox. -- The originally installed IDE on the C drive does not give this error when launched. -- I last upgraded it to Softmotion 4.20.1.0 through the installer. Has anyone encountered the same or a similar issue? Will this issue be fixed in the next update? Best regards, Imdat
Last updated: 2025-12-05

Post by harryc on Soft Container License issue with ARM64 Linux CODESYS Forge talk (Post)
Hi, We are working to provide our customers with CODESYS operation on our hardware product ( https://elprotech.com/product/el-qe-e-quantum-edge-series/ ). I'm trying to enable a CODESYS license (Soft container) on our product running ARM64 linux. This problem am having looks similar to here: https://forge.codesys.com/forge/talk/Runtime/thread/6d29b6b4de/ and here: https://forge.codesys.com/forge/talk/Runtime/thread/a2d0c63375/; but I am not running docker, and I am not re-installing a license. This is first time install. I have CODESYS Control SL running on my device, as well as CodeMeter. I purchased a license, and installed it to the CODESYS Development system, (Tools >> License Repository) then tried to install to the device (Tools >> License Manager >> o Device >> o Soft container >> Remote [0001] >> OK. This gives me the "License Manager - Overview" dialog, and the message "Licensing info not available. There is no dongle attached to the device." Below shows the running applications, installed packages, and current content of /var/opt/codesys Also attached screenshots of the Development software as I go through the steps to install the license. # # ps | grep -e "code" -e "CodeMeter" 1391 daemon /usr/sbin/CodeMeterLin 1407 root /opt/codesys/bin/codesyscontrol.bin /etc/codesyscontrol/CODESYSControl.cfg 1442 root /opt/codesysedge/bin/codesysedge.bin /etc/codesysedge/Gateway.cfg 29229 root grep -e code -e CodeMeter # dpkg -l Desired=Unknown/Install/Remove/Purge/Hold | Status=Not/Inst/Conf-files/Unpacked/halF-conf/Half-inst/trig-aWait/Trig-pend |/ Err?=(none)/Reinst-required (Status,Err: uppercase=bad) ||/ Name Version Architecture Description +++-==============-=============-============-============================================================================================== ii codemeter-lite 8.20.6539.500 arm64 WIBU CodeMeter minimal runtime ii codesyscontrol 4.14.0.0 arm64 codesyscontrol based on SDK 3.5.20.40 , from Fri Nov 29 08:35:37 CET 2024 [265], Release build ii codesysedge 4.14.0.0 arm64 codesysedge based on SDK 3.5.20.40 , from Fri Nov 29 08:34:19 CET 2024 [265], Release build # ls -la /var/opt/codesys total 208 drwxr-xr-x 6 root root 4096 Nov 7 05:31 . drwxr-xr-x 1 root root 4096 Nov 6 08:33 .. -rw-r--r-- 1 root root 23515 Nov 7 07:26 .Audit.log -rw-r--r-- 1 root root 160 Nov 7 05:31 .GroupDatabase.csv -rw-r--r-- 1 root root 160 Nov 7 04:37 .GroupDatabase.csv_ -rw-r--r-- 1 root root 20736 Nov 29 2024 .SoftContainer_CmRuntime.wbb -rw-r--r-- 1 root root 1982 Nov 29 2024 .UFC_SoftContainer_CmRuntime.WibuCmLif -rw-r--r-- 1 root root 229 Nov 7 04:35 .UserDatabase.csv -rw-r--r-- 1 root root 229 Nov 7 04:35 .UserDatabase.csv_ -rw-r--r-- 1 root root 11807 Nov 7 05:30 .UserMgmtRightsDB.csv drwxr-xr-x 6 root root 4096 Nov 6 08:30 .pki drwxr-xr-x 3 root root 4096 Nov 6 08:30 OPCUAServer drwxr-xr-x 7 root root 4096 Nov 6 08:30 PlcLogic -rw-r--r-- 1 root root 13 Nov 6 08:30 SysFileMap.cfg -rw-r--r-- 1 root root 2640 Nov 29 2024 bacstac.ini drwxr-xr-x 4 root root 4096 Nov 6 08:30 cert -rw-r--r-- 1 root root 94105 Nov 7 07:25 codesyscontrol.log # # uname -a Linux Remote 6.1.22 #5 SMP PREEMPT Tue Nov 18 11:35:46 AEST 2025 aarch64 GNU/Linux #
Last updated: 2025-12-04

Post by reinier-geers on wEBCLIENT Post data api CODESYS Forge talk (Post)
Ive got the webclient axample. If i put https://reversed.notion.site/Marktprijzen-API-89ce600a88ac4abe8c2ad89d3167a83e example to https://reqbin.com/post-online then i get data. If i do the same in Webclient example i get " not a valid graphql request. Why ? sUrl := 'https://graphql.frankenergie.nl/' Request_type_post Contenttype = 1 (json ) Postvalue := '{"query":{"query":"query MarketPrices {\n marketPrices(date:\"2025-12-25\") {\n electricityPrices {\n from\n till\n marketPrice\n marketPriceTax\n sourcingMarkupPrice\n energyTaxPrice\n perUnit\n }\n gasPrices {\n from\n till\n marketPrice\n marketPriceTax\n sourcingMarkupPrice\n energyTaxPrice\n perUnit\n }\n }\n}' I tranfer the postvalue from String to WSTRING
Last updated: 2025-12-25

Post by julianramirez on Visu 4.9.1 auto-logon/login CODESYS Forge talk (Post)
Hello everyone, I have been trying to test the auto-login feature that is advertised on the Release Notes since Visu 4.8: *Version: 4.8.0.0 Besides some bug fixes and improvements this version contains the following new functionality: Alarmmanagement: Possibility to raise alarms programmatically Use real time clock of IEC context Automatic login for WebVisu using Chrome "Sign in automatically"* I am using a personalized login Visualization, the User Management works, however, when ticking the checkbox that keeps the credentials stored, after I reload the page I still see that the user and password details are not filled in. I tried with the default Login Visu (Blue one), and still see the same behavior - VisuUserManagement.VUM_LoginVisualization - I've tried with Chrome and Edge. Thanks for your help
Last updated: 2026-01-12

Post by baotthitawat on Why Structured SCADA Documentation Matters in Modern Industrial Systems CODESYS Forge talk (Post)
Modern SCADA development is no longer limited to monitoring dashboards and PLC communication. Today’s industrial systems often require: Cloud architecture Web & mobile SCADA API integration IIoT communication Alarm management Scalable deployment workflows One challenge in many projects is that deployment knowledge is usually scattered across multiple documents, configuration guides, and troubleshooting references. As systems become more connected, engineers need a more structured learning approach to reduce deployment time and improve maintainability. The ATSCADA Training Book is an interesting example because it organizes the ecosystem into a clearer roadmap covering: SCADA architecture Driver & OPC communication Web visualization Mobile applications Cloud & IIoT systems Troubleshooting & maintenance I think structured technical documentation will become increasingly important as industrial automation systems continue evolving toward larger and more connected environments.
Last updated: 2026-05-27

Post by egerobotics on [New Hardware] EtherCAT Digital & Analog IO Board – CODESYS Compatible, All Channels Isolated CODESYS Forge talk (Post)
Hi everyone, I'd like to share a new EtherCAT slave I/O board I've developed — the EtherCAT Digital & Analog IO Board by EGEROBOTICS. Key specs: 12x isolated digital outputs (24VDC) 12x isolated digital inputs (24VDC) 4x isolated 0–10V analog outputs (12-bit DAC) 4x isolated 0–10V analog inputs (12-bit ADC) All channels galvanically isolated 24VDC powered EtherCAT CoE protocol Typical use cases: Analog servo drive speed reference (0–10V) via EtherCAT Frequency inverter reference signal Proportional valve control Industrial sensor data acquisition Compatible with CODESYS SoftMotion, Beckhoff TwinCAT 2/3, LinuxCNC + EtherCAT HAL, and SOEM. Here's a quick demo video showing it running under CODESYS: 👉 https://www.youtube.com/watch?v=bUuo9reK29s ESI file, PDF manual and AutoCAD drawings available. Available on Tindie: https://www.tindie.com/products/emresensoy/ethercat-digan-io/ Happy to answer any technical questions!
Last updated: 2026-06-13

Post by timvh on CPU + EtherCAT redundancy CODESYS Forge talk (Post)
It works well with two Wago 750-8210's. I helped a few customers setting this up. But it should work with any device which can control EtherCAT I/O, is real-time and has sufficient network interfaces. Two network adapters can be used to create a redundant EtherCAT network (you need 2 additional switches for this). The other network adapters can be used to interconnect the 2 PLC's (synchronization). We noticed that if you exchange variable lists that there could be some issues if you have long lists. So what we did is use a SoftPLC on a server that contains all the settings which continuously sends network packages (GVL sender) and which is received by both PLC's (network receiver). Switching over is done in milliseconds. The bus doesn't notice the change-over. EtherCAT communication works flawlessly.
Last updated: 2026-01-30

Post by konstantin on CAM Motion Recover after STO CODESYS Forge talk (Post)
Hello, one of the projects I work on is about a racetrack collator with two independent belts on it - two different servo motors. Both motors share the same mechanical frame and there is a train on a belt that collects items from the input conveyor. The way the motion is performed is the following - there is a virutal master axis and both real axis are synchronised with different cam motion profiles. The problem is when an STO is triggered on any of the slave axis, the synchronization process starts from position 0 of the slaves. How can I force the slaves to retain their current position until the master passes their position? Then the slaves should catch up with the master according to the profile, the slaves should not start synchronization from 0 position. Best Regards Konstantin Kolev
Last updated: 2026-02-12

Post by jorenbeyl on library inside library CODESYS Forge talk (Post)
I am currently developing a library that contains real‑time data. To handle this real‑time data, I am using additional libraries called SysTime and SysTypes Interfaces. When I compile my library on its own, no errors occur. However, when I use this library in a project and compile the project, I get an error indicating that the SysTime data type is not recognized. This happens even though the SysTime library is visible as a dependency under my library. Does anyone know how to correctly include a library within another library so that the project recognizes the sub‑library without causing compilation errors?
Last updated: 2026-04-23

Post by timvh on library inside library CODESYS Forge talk (Post)
1) it should be possible to access the type SysTime in the project as A_Lib.SysTime. 2) you could add the SysTimeCore library to the library manager of your library (POU Pool). This might seem as a double library, but because of the placeholder resolution only one will be used. Then, in your library manager of your library, select the SysTimeCore library, right-click, select "Properties" and enable the option "Publish all IEC symbols ...." For more information about library development, you could follow our advanced training course in Ridderkerk. The next is scheduled for 24 and 25 June 2026 https://www.extendsmartcoding.nl/codesys-training/
Last updated: 2026-04-25

Post by jroddball79 on PM556-TP-ETH — How to change IP address without overwriting the PLC program? CODESYS Forge talk (Post)
We have checked open ports. SSH (22) and HTTP (80) are not reachable. The only open ports are: 502 (Modbus TCP — used for lighting control) 1200 (CODESYS runtime) 1201 (CODESYS runtime) We can connect via Automation Builder using the current IP, but we don't have the original project source — only an empty project. This is why we are afraid of doing a full download, as it would overwrite the running application. Is there any way to change the IP through the CODESYS runtime protocol on ports 1200/1201 without affecting the running program?"
Last updated: 2026-05-20

Post by gseidel on Limit Axis CNC Jerk using SMC_Polynomial_AbsMaxLocs CODESYS Forge talk (Post)
Dear josepmariarams, this (internal) function has been removed with SoftMotion 4.17.0.0. We do not have public functions to compute the extrema of a polynomial. On which polynomials exactly did you call SMC_Polynomial_AbsMaxLocs? (Maybe if I understand better how you limit the jerk I can come up with an alternative.) There is no functionality to limit the jerk of individual axes in the CNC. With SMC_LimitDynamics, you can limit the velocity and acceleration of cartesian (X/Y/Z) and additional (P/Q/U/V/W/A/B/C) axes, but not the jerk. And with a quadratic ramp type you can limit the jerk on the path. Best regards, Georg