Post by eschwellinger on EtherCAT drive not moving
CODESYS Forge
talk
(Post)
you need to switch to a realtime capable plc. Do not map variables, this will be done by the SoftMotion. And check the Ds402 parameters in the generic parameterview on the Softmotion Connector.
Last updated: 2024-03-05
Post by mandeepahujaifm on IFM CR711S Version Mismatch
CODESYS Forge
talk
(Post)
Please send an email to info.us@ifm.com and they shall provide you with the correct information. Alternatively you can check the website for latest packages. https://www.ifm.com/us/en/product/CR711S?tab=documents
Last updated: 2024-03-05
Post by john-robinson on Limiting Memory Access of an Array to Within its Bounds
CODESYS Forge
talk
(Post)
Thanks Tim! This was exactly the functionality we were looking for. We are already using implicit checks to check for divide by 0 errors, we will add implicit checking for array bounds.
Last updated: 2024-03-06
Post by xabier on No work Control Torque Codesys with Drivers M751 Control Techniques
CODESYS Forge
talk
(Post)
Please...can you help me???I don´t understand...Where check it that you tell me ??Where appear Pdf??? I need more support thanks
Last updated: 2024-03-14
Post by fraccaroli on New Codesys Library Dependencies
CODESYS Forge
talk
(Post)
Hello, you probably fixed in this meanwile, but I think your problem comes from dependencies of other libraries. I see in the Project column of errors the "caa types extern" and "caa fb factory", that both have dependencies. Try to check there. Regards, Francesco
Last updated: 2024-03-21
Post by valec on Connect local Asem HMI runtime to local Codesys Control Win V3 x64
CODESYS Forge
talk
(Post)
Solved: update all the software to the latest version, set optional user management, have a symbol configuration, check tasks priorities.
Last updated: 2024-03-28
Post by xabier on Remove white spaces in file .txt
CODESYS Forge
talk
(Post)
Hi, I want write a array with line break in file.txt (I attacehd the screen array) and when i check the file appear with white spaces (I attached file .txt ) Somepeople know how remove this white spaces?? Thanks you Regars XABI
Last updated: 2024-04-22
Post by dkugler on RecipeManCommands.ReloadRecipes
CODESYS Forge
talk
(Post)
Hi William, I struggled in the same way as you at the beginning with the recipe manager. This chapter helped me a lot to understand how it has to be used: https://content.helpme-codesys.com/en/CODESYS%20Recipes/_rec_start_page.html Check out the Methode LoadFromAndWriteRecipe / LoadAndWriteRecipe Good luck! Dave
Last updated: 2024-05-16
Post by dkugler on RecipeManCommands.ReloadRecipes
CODESYS Forge
talk
(Post)
Hi William, I struggled in the same way as you at the beginning with the recipe manager. This chapter helped me a lot to understand how it has to be used: https://content.helpme-codesys.com/en/CODESYS%20Recipes/_rec_start_page.html Check out the Methode LoadFromAndWriteRecipe / LoadAndWriteRecipe Good luck! Dave
Last updated: 2024-05-16
Post by timvh on Error: C0138: No matching 'FB_Init' method found for instantiation of VisuClientObjectMgr
CODESYS Forge
talk
(Post)
Maybe check: - The library manager, are you maybe missing some libraries - Tools - CODESYS installer: update the CODESYS Visualization and Visualization support - Project - Project environment: maybe you need to update the visualization profile
Last updated: 2025-11-27
Post by eschwellinger on Accessing parameters from a structure or function block with the web interface
CODESYS Forge
talk
(Post)
yes, but you could use a demo project in the analyzer to check other types: https://analyzer-eu.automation-server.com/help/en/tags this should work.
Last updated: 2025-12-02
Post by aniket-b on Scara3 kinematic robot error
CODESYS Forge
talk
(Post)
I am using Scara3 kinematic with EtherCAT PLC. The robot stops at the same place randomly after few cycles. Check attached image. I am getting SMC_ERROR.SMC_DI_FIELDBUS_LOST_SYNCRONICITY in all 3 axes.
Last updated: 2025-12-19
Post by edvard-munch on How I can get "Done flag" for "Modbus Slave Channel"?
CODESYS Forge
talk
(Post)
This is from 10 years ago, I know. But I have been using (SLAVE_DEVICE.iChannelIndex = CHANNEL_NUMBER) AND (SLAVE_DEVICE.xDone) I suppose that it shows xDone for the channel that shows up in the iChannelIndex at the same cycle? It seems to be working properly for two devices that I have been using it before But now I have another device and using two write channels, for one register each. One channel works properly and returns DONE flag When another channel is triggered, I see that it shows up in iChannelIndex, but flag DONE not received, but no Error for the channel. Also, when i check the register in the device it's evident that data has been transferred. Is this could happen sometimes with CODESYS, so DONE flag not received? Or this is a problem with a given device? With this certain register
Last updated: 2024-12-19
Post by pistola on C0357: "GetNextClient" is obsolete, use VisuUtils instead
CODESYS Forge
talk
(Post)
I'm having some troubles with this same issue and I'm wondering if someone can help me out. On a settings visual I allow the operator to enter some values however if they activate the page change button it will change the change with the Numpad dialog open. Since I'm using Visuelems.CURRENTVISU to change the pages I came across this code noted below for determining if the Numpad dialog was active. This code worked great however now in 3.5.19 it's now obsolete. I've tried following the directions in the attached program above however I can't see to get it to work in my program. Can anyone provide some help to determine if a dialog is open? FUNCTION Check_Dialog_Open : Bool VAR_INPUT sDialogName : STRING; // Input variable for the name of the dialog END_VAR VAR pstClientData : POINTER TO VisuElems.VisuStructClientData; // Pointer to the client data structure itfDialogManager : VisuElems.IDialogManager; // Interface for the dialog manager itfMyDialog : VisuElems.IVisualisationDialog; // Interface for the specific visualisation dialog END_VAR // Begin the iteration over the client manager VisuElems.g_ClientManager.BeginIteration(); // Loop through each client until no more clients are found WHILE (pstClientData := VisuElems.VisuElemBase.g_ClientManager.GetNextClient()) <> 0 DO // Get the dialog manager interface itfDialogManager := VisuElems.g_VisuManager.GetDialogManager(); // Get the specific dialog interface using the dialog name itfMyDialog := itfDialogManager.GetDialog(sDialogName); // Check if the dialog is open for the current client Check_Dialog_Open := VisuDialogs.VisuDlgUtil_IsDialogOpen(itfMyDialog, pstClientData, itfDialogManager); // If the dialog is open, exit the loop IF Check_Dialog_Open THEN EXIT; END_IF END_WHILE
Last updated: 2025-03-27
Post by forest on SM Drive license error
CODESYS Forge
talk
(Post)
Hi, when it comes about license, I used INVTmatic Studio, which uses Codesys, for programming INVT plc. I bought Codesys Modbus license, it was not expensive, and then realised that INVT didn't have License Manager option (greyed out in program) which is needed for using of Codesys License. I contacted support from INVT, but developers told me that option is still not available. So depending on environment for programming Codesys, you can or not use Modbus license. Good thing about this version of Modbus TCP it works both direction. I could send commands and receive feedbacks from drive. But communication stops after 30 mins. So I used simple version of ethernet modbus which is somewhere in INVT or Condesys library (I can check tomorrow) which works only one way. I could send cmd to drive, and control it, but didn't have any feedback, like some readings back in PLC. which is bad, but at least I could start it and it didn't fail after 30 mins.
Last updated: 2024-01-10
Post by thysonfury on OPTO22 Groov Epic PR2 Modbus Comms Dropping out every 2 hours and 4 Mins
CODESYS Forge
talk
(Post)
Hi after some assistance with an error on a Groov PR2 PLC. We have a few different communications set up as shown below: One Modbus TCP Slave Connection - ( Sending / Receiving Data from a PC ) Two Modbus TCP Master Connection - ( Reading Data from a UPS Panel and Reading Data Gas Chromatograph) One Modbus RTU Slave Connection 485 - (Reading Data from a fire and gas panel) One Modbus RTU Master Connection 485 - (Sending Data to a Telemetry Unit) All Licenses have been installed as per OPTO22 suggestions of the order below: Modbus TCP Master Modbus TCP Slave Modbus RTU Master Modbus RTU Slave When I check on License manager the RTU Master license seems to disappear on installing the RTU. (What ever reason I’ve been told this is “normal”). If I use Device License Read It will successfully read all the licenses correctly. Now the issue is every 2 hours and between 4. For what ever reason the communications seems to end and lock up for about 20 seconds. During this time even if I was logged into the PLC it would kick me off and I’d have to re type the password to enter. Most of the devices can handle this however the RTU flags up a communications failure at the SCADA and is raising alarms every 2 hours and 4 mins. We’ve had multiple people go through the code to check for anything obvious. Does anyone have any ideas?
Last updated: 2024-04-15
Post by thysonfury on OPTO22 Groov Epic PR2 Modbus Comms Dropping out every 2 hours and 4 Mins
CODESYS Forge
talk
(Post)
Hi after some assistance with an error on a Groov PR2 PLC. We have a few different communications set up as shown below: One Modbus TCP Slave Connection - ( Sending / Receiving Data from a PC ) Two Modbus TCP Master Connection - ( Reading Data from a UPS Panel and Reading Data Gas Chromatograph) One Modbus RTU Slave Connection 485 - (Reading Data from a fire and gas panel) One Modbus RTU Master Connection 485 - (Sending Data to a Telemetry Unit) All Licenses have been installed as per OPTO22 suggestions of the order below: Modbus TCP Master Modbus TCP Slave Modbus RTU Master Modbus RTU Slave When I check on License manager the RTU Master license seems to disappear on installing the RTU. (What ever reason I’ve been told this is “normal”). If I use Device License Read It will successfully read all the licenses correctly. Now the issue is every 2 hours and between 4. For what ever reason the communications seems to end and lock up for about 20 seconds. During this time even if I was logged into the PLC it would kick me off and I’d have to re type the password to enter. Most of the devices can handle this however the RTU flags up a communications failure at the SCADA and is raising alarms every 2 hours and 4 mins. We’ve had multiple people go through the code to check for anything obvious. Does anyone have any ideas?
Last updated: 2024-04-15
Post by thysonfury on OPTO22 Groov Epic PR2 Modbus Comms Dropping out every 2 hours and 4 Mins
CODESYS Forge
talk
(Post)
Hi after some assistance with an error on a Groov PR2 PLC. We have a few different communications set up as shown below: One Modbus TCP Slave Connection - ( Sending / Receiving Data from a PC ) Two Modbus TCP Master Connection - ( Reading Data from a UPS Panel and Reading Data Gas Chromatograph) One Modbus RTU Slave Connection 485 - (Reading Data from a fire and gas panel) One Modbus RTU Master Connection 485 - (Sending Data to a Telemetry Unit) All Licenses have been installed as per OPTO22 suggestions of the order below: Modbus TCP Master Modbus TCP Slave Modbus RTU Master Modbus RTU Slave When I check on License manager the RTU Master license seems to disappear on installing the RTU. (What ever reason I’ve been told this is “normal”). If I use Device License Read It will successfully read all the licenses correctly. Now the issue is every 2 hours and between 4. For what ever reason the communications seems to end and lock up for about 20 seconds. During this time even if I was logged into the PLC it would kick me off and I’d have to re type the password to enter. Most of the devices can handle this however the RTU flags up a communications failure at the SCADA and is raising alarms every 2 hours and 4 mins. We’ve had multiple people go through the code to check for anything obvious. Does anyone have any ideas?
Last updated: 2024-04-15
Post by mubeta on Some 'pathetic' errors in SoftMotion program
CODESYS Forge
talk
(Post)
Hello everyone, I have a very simple program for the process, but it's driving me crazy and I can't see the problems I'm left with: Short topological description: Dual Core Berghof controller with softmotion runtime version 3.5.19.30; Two axes with servodrive on canopen bus, clocked distributed from master; Ethercat I/O node; 2 ms ethercat task, 2 ms canopen bus cycle time; I/O objects of the canopen master and canopen drives connected to the ethercat task cycle; Problem 1: Two separate programs each manage their own axis and drive, with separate state machines. A first axis moves primarily in velocity, except having to position itself absolutely at a predetermined point at the end of the job; the second axis, on the other hand, is a paper unwinder that changes, for each job cycle, from actions in absolute, relative, and cam displacement with the master axis. Well, the state machine of both axes was written in such a way as to call running the useful FB and change it on state change in this way: CASE i_stateMachine OF 0: o_Power(Enable := TRUE, bRegulatorOn := FALSE, bDriveStart := FALSE, Axis := o_PaperUnwinderAxis); o_MoveAbs(Execute := FALSE, Axis := o_PaperUnwinderAxis); o_MoveRel(Execute := FALSE, Axis := o_PaperUnwinderAxis); o_CamSelect(Execute := FALSE, Master := o_MachineAxis, Slave := o_PaperUnwinderAxis, CamTable := cam_PaperUnwinder); o_CamIn(Execute := FALSE, Master := MachineEncoder, Slave := o_PaperUnwinderAxis); o_CamOut(Execute := FALSE, Slave := o_PaperUnwinderAxis); o_SetPosition(Execute := FALSE, Axis := o_PaperUnwinderAxis); IF ... THEN i_StateMachine := 10; END_IF; 10: o_Power( Enable := TRUE, bRegulatorOn := TRUE, bDriveStart := TRUE, Axis := o_PaperUnwinderAxis ); IF o_Power.Status THEN i_StateMachine := 20; END_IF; 20: (* Avanzamento carta *) o_MoveAbs( Execute := TRUE, Position := o_Somewhere, Velocity := 25.0, Acceleration := 3666.7, Deceleration := 3666.7, Jerk := 48000.0, Direction := MC_DIRECTION.positive, Axis := o_PaperUnwinderAxis ); IF o_MoveAbs.Done THEN o_MoveAbs(Execute := FALSE, Axis := o_PaperUnwinderAxis); i_StateMachine := 30; END_IF 30: d_HomingPosition := ...; o_SetPosition( Execute := TRUE, Position := d_HomingPosition, Mode := FALSE, Axis := o_PaperUnwinderAxis ); (* ... *) IF o_SetPosition.Done = TRUE THEN o_SetPosition(Execute := FALSE, Axis := o_PaperUnwinderAxis ); o_LogServer.Append(sMessage := '...', lscClass := LOGSERVER_CLASS.ALWAYS, sdt := o_CommonsMgrData.systime.sdtLocal); i_StateMachine := 40; END_IF; 50: ... The code above is a sketchy example of what I wanted to write. But it gives me a spot problem: in some, the state change results in a drive error, which is unrecoverable except with a reinitialization via SM3_ReinitDrive(). Things are improved a little if in the program I always run the call of all softmotion blocks in this way: o_Power(Axis := o_PaperUnwinderAxis); o_Jog(Axis := o_PaperUnwinderAxis); o_Halt(Axis := o_PaperUnwinderAxis); o_MoveAbs(Axis := o_PaperUnwinderAxis); o_MoveRel(Axis := o_PaperUnwinderAxis); o_CamIn(Master := MachineEncoder, Slave := o_PaperUnwinderAxis); o_CamOut(Slave := o_PaperUnwinderAxis); If I don't execute all the calls of all the motion FBs used, when exchanging machine state often (but not always), the axis goes into error with event id THE_FB_WASNT_CALL... Done a little diagnostics it seems that the FBs return the bDone, before they are completely terminated. I tried doing the machine state exchange not with the bDone bit of the FBs, but with the 'standstill' state of the axis. It didn't seem to change anything. Problem 2: During the use SM3_ReinitDrive() I get the erro in the log: "NetID 0: SDO read error for object 16#607C..." Assuming that the device involved it's one of the two servodrive, (no others device are present in the network), I don't found any object 0x607C in the 'possible object list in/out' of the two drive, and I don't understand where this object can be listed. So any ideas and suggestions regarding these two issues will be very, very welcome. If you need the source project, I am willing to send it.
Last updated: 2024-07-17
Post by imdatatas on The default ramp type selection in SoftMotion V4.18.0.0 is Quadratic
CODESYS Forge
talk
(Post)
Dear @gseidel, Thank you for your clarification. I fully agree that the quadratic ramp type may have certain technical advantages. However, the main problem is backward compatibility and consistency across projects. In many automation projects, application developers rely on the fact that creating a new axis object will behave exactly the same way as in previous versions. With SoftMotion V4.18.0.0 and later, if an application developer adds an axis and overlooks the changed default, the motion function blocks behave differently than expected. In particular, since the Jerk value in SM3_Basic function blocks is ineffective in trapezoid ramp type, users are accustomed to leaving this parameter empty in their projects. In many existing projects, this variable has not even been assigned. When the default is changed to quadratic, the Jerk parameter suddenly becomes relevant, which can cause errors or unexpected behaviour in the field. From a user perspective, a default setting should always be the “safe” and “expected” option, while alternative options (like quadratic) can be selected manually if desired. Keeping the default as trapezoid ensures compatibility with existing projects and prevents unexpected issues, while still allowing users to benefit from quadratic ramps if they explicitly choose so. For these reasons, I kindly ask you to reconsider making trapezoid the default again. This would significantly reduce the risk of unexpected behaviour in future projects while still preserving the advantages of the quadratic ramp type for those who actively select it. Of course, the final decision is entirely at your discretion. Best Regards, imdatatas
Last updated: 2025-09-26
Post by e13740e on Parameterized Property syntax for array element processing
CODESYS Forge
talk
(Post)
Since parameterized (indexed) properties are not possible, I decided to use architectural approach "Indexing Property Adapter" to achieve the intended goal — avoiding code duplication for validated access to array elements. Essence: Create a Function Block Adapter (FB_PropertyAdapter) that encapsulates the logic for working with a single element of the target array (e.g., with one settings structure). Declare Properties inside the adapter block for accessing each individual field of the data structure. All validation logic is implemented within the Set accessors of these properties. Data Binding via VAR_IN_OUT: The adapter block receives a reference to a specific data element from the global array through its VAR_IN_OUT section, which ensures direct work with the original data without copying. Create an Array of Adapters: In the parent POU (e.g., FB_SettingsManager), an array of these adapter blocks is created — one for each element of the global array that needs to be managed. Initialize Bindings: In a FOR loop, each adapter instance from the array is given a reference to the corresponding data element. Result: This approach allows accessing the data via the index of the adapter array, and then through the property name, which simulates the behavior of an indexed property: MyAdapterArray[Index].MyProperty Thus, the validation and data access logic is written only once inside the adapter block and is then reused multiple times by creating instances of it in an array. This completely solves the problem of code duplication while providing a clean, scalable, and object-oriented architecture compatible with standard CODESYS features. Question closed.
Last updated: 2025-10-19
Post by eschwellinger on RPI Zero w - Edge gateway cant install
CODESYS Forge
talk
(Post)
ok now it is clear - this is a single core Pi Zero W. For this device there is no edge device available. But just for working with CODESYS it is not really needed and yes plc runs only for 2h unlicensed.
Last updated: 2023-09-13
Post by nickelwater on Fix compiler version in SP18+
CODESYS Forge
talk
(Post)
Is is possible to use the compiler "Fix Version" in SP18+? I have noticed that in SP17 and below, the option is available in the compiler options under project settings, but in versions 18+ it is unselectable. The help topic does not provide any information.
Last updated: 2024-07-21
Post by wagokurt on CODESYS Visualization M License Fails to activate on Linux SL
CODESYS Forge
talk
(Post)
This is what is on the device, is this correct? I did not see an option to install TargetVisu, is this needed?
Last updated: 2025-08-21
Post by flyingsheep on download project via codesys is slow but tftp/ftp/iperf is fast ??
CODESYS Forge
talk
(Post)
Setup description CODESYS is running on an embedded RTOS. For testing, I use a local debugging environment where my PC is connected directly to the embedded SoC via an Ethernet cable (no switch or router in between).