Post by rafa on MODBUS TCP SERVER DON'T AUTOMATIC STARTUP CODESYS Forge talk (Post)
Dear all, I have a project where I have two ModbusTCP communication drivers in the application. It's working normally until a power outage or the installation panel is restarted. As soon as the PLC CPU is restarted, the Ethernet port is OK, but the TCP Server displays an "UNDEFINED" error. I can't reset the error using the diagnostic confirmation or the "mbserver.xConfirmError" bit. I noticed that the error only appears in the "mbserver.byModbusError" memory and the description is "UNDEFINED." The "mbserver.xError" memory doesn't flag an error. When using the warm restart function and then START CPU, the devices return to normal operation. The following demonstration images; The main question is: How can I make devices boot automatically? Um using Codesys Version 3.5.20.30 Patch 3+ My CPU is a Weintek Cmtx Built-int - ( CMT3092x )
Last updated: 2025-07-15

Post by pernockham on Gateway in China - "Gateway not connected" CODESYS Forge talk (Post)
Trying to communicate (from Europe) with/to a unit located in china, the communication seems blocked/stopped. The edge gateway is installed in a linux environment and was possible to link to my Automation server account using the "Automation service tool". However it seems the unit cannot communicate with the Automation server (a Network scan will give the message "Gateway not connected"). (I have tested the eq. setup with units locally which works.) Anyone having experience situation similar to this and if its possible to make this work? Will a VPN be needed possibly? Other tips?
Last updated: 2025-09-04

Post by ranadheer on Implementation of IEC-104 CODESYS Forge talk (Post)
Hi Everyone, As we didn't have client for IEC - 104 - only server server is available , so because of that we are trying to make establish the communication between the external simulator as a Client and codesys itself as a server. We are looking for the variable behavior from CODESYS has to change according to the message triggered by the CLIENT (we are using simulator Application like Redisant). We are able to see the log data as the status of triggering the SCS from Client received to the Log data of the codesys device(attached screen shot of it) and in simulator panel we had set the details to trigger the data from Redisant to Codesys. Current Status: The project builds and runs successfully, but I need guidance on how to connect this to an external IEC-104 simulator for testing and visualization by using demo mode.
Last updated: 2025-10-14

Post by ranadheer on Implementation IEC-104 CODESYS Forge talk (Post)
Hi Everyone, As we didn't have client for IEC - 104 - only server server is available , so because of that we are trying to make establish the communication between the external simulator as a Client and codesys itself as a server. We are looking for the variable behavior from CODESYS has to change according to the message triggered by the CLIENT (we are using simulator Application like Redisant). We are able to see the log data as the status of triggering the SCS from Client received to the Log data of the codesys device(attached screen shot of it) and in simulator panel we had set the details to trigger the data from Redisant to Codesys. Current Status: The project builds and runs successfully, but I need guidance on how to connect this to an external IEC-104 simulator for testing and visualization by using demo mode.
Last updated: 2025-10-14

Post by sumit on Remote Ethernet/ip Adapter communication with scanner running on codesys CODESYS Forge talk (Post)
Hello there, I have my ethernet/ip adapter (from Texas Instrument) running on Texas Instrument Board and I have configured the scanner on codesys. I have mapped the I/Os and I can see (on wireshark) the frames coming from adapter but I don't see my input variables in scanner get updated, they just stay at 0. I wanted to see the real data that has been sent from adapter to scanner on codesys. I am not sure if the problem is in I/O mapping or there is a step/s that I have missed. I have attached the screenshot of my project for your ref. Thank you, Sumit
Last updated: 2023-12-15

Post by sumit on Remote Ethernet/ip Adapter communication with scanner running on codesys CODESYS Forge talk (Post)
Hello there, I have my ethernet/ip adapter (from Texas Instrument) running on Texas Instrument Board and I have configured the scanner on codesys. I have mapped the I/Os and I can see (on wireshark) the frames coming from adapter but I don't see my input variables in scanner get updated, they just stay at 0. I wanted to see the real data that has been sent from adapter to scanner on codesys. I am not sure if the problem is in I/O mapping or there is a step/s that I have missed. I have attached the screenshot of my project for your ref. Thank you, Sumit
Last updated: 2023-12-15

Post by yang123 on EtherCAT Can't reconnect to servo drive CODESYS Forge talk (Post)
I am using Ethercat Master 4.6.0.0 and have use the automatic restart slaves feature. But we found of after the Ethercat communication normal and slave drive power-off and power-on the slave can't reconnect sucess. The PLC Log show the drive was al status "6#34 : Invalid DC Timeout Error" and its was reconnection sucess first but seconced later the drive will show the "16#2C : Fatal Sync error" and then drive will can't reconnection. Other slave are reconnect sucess which was link after the can't reconnect's drive the drive was OMRON R88D-1SN
Last updated: 2024-01-23

Post by dhumphries on No source code available CODESYS Forge talk (Post)
Try using an Ethernet/IP scanner instead of an adapter, I'm guessing the 2 devices you're trying to communicate with are adapters, you have to have a scanner somewhere and Codesys should be a scanner. I don't know why you're getting the error, you should be able to use your Ethernet port as an EthernetIP adapter (although I've never had a reason to try,) but it's probably not what you wanted to do, unless you're connecting to another PLC that is a scanner. Good luck configuring the devices you're trying to connect to, it will be a lot easier if you have an .EDS file instead of starting with a generic module, even with an .EDS it can be tricky getting the communication working.
Last updated: 2024-02-03

Post by alexgooi on Codesys licensing explanation CODESYS Forge talk (Post)
Dear Forum, We are currently switching to a native Codesys controller, and I'm currently trying to determine the correct license. I have a question regarding the Modbus instances. With the Standard S license this is set to 4 (See picture). In our projects we are using a lot of communications to Modbus servers using a Codesys Controller, for this communication I'm using the ModbusFB library (supplied by 3S) (see picture). In my project I would like to use more than 4 instances of the ClientTCP FB. My question is, is this now capped at 4 possible connections with the standard S license. Or do these function blocks have a different relation with the license? Some clarity on this topic would be very welcome. Thank you in advance
Last updated: 2024-02-15

Post by timvh on Profinet fault with codesys control V3 - Receive packet error CODESYS Forge talk (Post)
Are you using the Control Win SL (installed together with the development environment of CODESYS)? If yes, you might want to consider using the CODESYS RTE instead. This has real-time capabilities (running on separate core(s)). But to be able to use this, you have to install the CODESYS Ethernet driver for your network interface to be able to let the RTE access the network port also in realtime. See: https://store.codesys.com/en/codesys-control-rte-sl-bundle.html https://content.helpme-codesys.com/en/CODESYS%20Control/_rtsl_windows_rts_v3.html PS, I haven't tested this myself yet, but you could try to use the SetCommunicationState method of the Profinet controller to see if you can reset and start the bus communication: result := PN_Controller.SetCommunicationState(eRequestedState := DED.DEVICE_TRANSITION_STATE.START); PS, if you are located in the Netherlands or Belgium, we could also provide the license(s) for you.
Last updated: 2024-02-28

Post by timvh on Profinet fault with codesys control V3 - Receive packet error CODESYS Forge talk (Post)
Are you using the Control Win SL (installed together with the development environment of CODESYS)? If yes, you might want to consider using the CODESYS RTE instead. This has real-time capabilities (running on separate core(s)). But to be able to use this, you have to install the CODESYS Ethernet driver for your network interface to be able to let the RTE access the network port also in realtime. See: https://store.codesys.com/en/codesys-control-rte-sl-bundle.html https://content.helpme-codesys.com/en/CODESYS%20Control/_rtsl_windows_rts_v3.html PS, I haven't tested this myself yet, but you could try to use the SetCommunicationState method of the Profinet controller to see if you can reset and start the bus communication: result := PN_Controller.SetCommunicationState(eRequestedState := DED.DEVICE_TRANSITION_STATE.START); PS, if you are located in the Netherlands or Belgium, we could also provide the license(s) for you.
Last updated: 2024-02-28

Post by dhumphries on Not able to see input data coming from eip adapter on codesys CODESYS Forge talk (Post)
Does the device have a green icon next to it when the PLC is running? If not you have some kind of communication problem, wireshark may be picking up some data but the scanner may not be configured correctly to receive the data. Check the T>O and O>T bytes and make sure they match on both the scanner and adapter. I've had very little success loading a .eds file and having the configuration work without some manual configuration. If you have a green icon, have you enabled the device to always update variables?
Last updated: 2024-03-02

Post by valec on Connect local Asem HMI runtime to local Codesys Control Win V3 x64 CODESYS Forge talk (Post)
I have a project made on a PL700 PLC with Codesys and an Asem Premium HMI panel. I don't have access to the physical PLC right now, so I'm trying to use Codesys Control Win V3 x64. I created the application and loaded "Codesys Control Win V3 x64" without errors, then I activate "Start PLC" from the tray. Asem cannot connect. I tried to use "localhost" or the local IP address and it doesn't work (it's the "CoDeSys Soft PLC Communication Driver"). I need to connect my local Asem runtime to a virtual Codesys application on my PC. How can I do it?
Last updated: 2024-03-26

Post by albzen on EtherCat Slaves diagnosis CODESYS Forge talk (Post)
Hello everybody, I'm working on a RunTime Plc (Codesys 3.5.16/18.20) connected to an EtherCat bus with many devices. The bus has some communication fault but I don't know how understand which is the device or the cable that has the trouble. To understand the cause of the problem I would like to read the WKC (Working counter) of the devices (0x0300...0x030C), how is explained in EtherCat documents, but it seems that the read of the counter is disabled. Attached there is an extract of the Ethercat document. Can anyone give me some advice about how and with function can I read it. Thank you in advance!
Last updated: 2024-03-29

Post by albzen on EtherCat Slaves diagnosis CODESYS Forge talk (Post)
Hello everybody, I'm working on a RunTime Plc (Codesys 3.5.16/18.20) connected to an EtherCat bus with many devices. The bus has some communication fault but I don't know how understand which is the device or the cable that has the trouble. To understand the cause of the problem I would like to read the WKC (Working counter) of the devices (0x0300...0x030C), how is explained in EtherCat documents, but it seems that the read of the counter is disabled. Attached there is an extract of the Ethercat document. Can anyone give me some advice about how and with function can I read it. Thank you in advance!
Last updated: 2024-03-29

Post by hafizapik99 on Webvisu not showing Codesys V3.5 SP13 Patch 4 CODESYS Forge talk (Post)
Hello, I am using a Hitachi Micro EHV+ for a small project, and I wanted to have a Web visu, done with Codesys V3.5 SP13 Patch 2. I test the Visu screen and it works well in Codesys, but I get a blank page when i enter the web visu in a browser. Here is the setting under web visualization: Update rate (ms): 5000 (previously set to 2500 also not working) Default communication size: 100000 (previously set to 50000 also not working) Under Visu_Task tab: Priority: 3 The Visu_Task interval is set to 2500ms (previously set to 200ms also not working) I'm using Google chrome with the latest update, the Javascript is enabled with HTML5. Any advice?
Last updated: 2024-04-06

Post by hafizapik99 on Webvisu not showing Codesys V3.5 SP13 Patch 2. CODESYS Forge talk (Post)
Hello, I am using a Hitachi Micro EHV+ for a small project, and I wanted to have a Web visu, done with Codesys V3.5 SP13 Patch 2. I test the Visu screen and it works well in Codesys, but I get a blank page when i enter the web visu in a browser. Here is the setting under web visualization: Update rate (ms): 5000 Default communication size: 100000 Under Visu_Task tab: Priority: 3 The Visu_Task interval is set to 2500ms I'm using Google chrome with the latest update, the Javascript is enabled with HTML5. Any advice?
Last updated: 2024-04-06

Post by sachem on Problem retain values Weidmuller UC20-WL2000 CODESYS Forge talk (Post)
Good afternoon. I am working with a weidmuller uc20-wl2000 controller, using a codesys license. We made a ladder code to control a process, and it works well, but we want some variables to remain stored even when the controller is turned off. We tried to use retain variables, but at the time of loading the program, when we went offline from the controller, the program was deleted, it did not remain in the controller, and in the same way if we turned off the controller. In addition to this, when we tried to program it again, the program would not stay loaded and began to present errors with the opc-ua communication. What could be causing this problem? How can we maintain the values of the variables without damaging the program or affecting the controller? thank you
Last updated: 2024-04-10

Post by kuegerls on SysProcessExecuteCommand2 and CANopen Device CODESYS Forge talk (Post)
Hello, CODESYS Control is running on my RevPi, and my system communicates over a CANbus with a master using the ConnectCan module (Slave - CANopen Device). The communication works perfectly fine so far. However, as soon as I call a Python script with "SysProcessExecuteCommand2" that creates a CSV file and executes without errors, the master does not adopt any changes to the Transmission Process Data Objects (TPDOs). I don't quite understand what one has to do with the other, and perhaps someone can help me with this. Here is my script call: SysProcess.SysProcessExecuteCommand2(pszCommand:='python /home/pi/test.py', pszStdOut:=sCMDOutput, udiStdOutLen:= SIZEOF(sCMDOutput), pResult := ADR(eResult)); Thank you in advance! Best regards, Stefan
Last updated: 2024-06-20

Post by rohan on Child Application Alarm CODESYS Forge talk (Post)
Hi All, I'm trying to develop a multi-application project that allows me to switch between applications. I currently have a parent application and several child applications, as this is the only way for them to share CAN/Ethernet communication. I've noticed that I am only able to create an Alarm Configuration for the parent application. But the children application do not seem to be displaying alarms on the Alarm Table in the visualisation for when an alarm is raised. Does anyone know of a fix, solution or a way around this? I am utilising Codesys v3.5 SP16 Patch 5 64Bit
Last updated: 2024-06-21

Post by kthomas on Cant login to Rpi4 but can see it in codesys communications settings. CODESYS Forge talk (Post)
I have been struggling for over a week to program my rapspberry pi 4 with codesys. I purchased the license. I installed the runtime and the gateway, and I can see the pi in the communication settings. But cannot log in. I have checked the status of the pi with sudo systemctl status codesyscontrol and it is running. I have enabled traffic to and from the pi with iptables and checked the logs and all looks good. I just cannot connect through the codesys ide. Can anyone help me before I lose my mind?
Last updated: 2024-06-22

Post by kthomas on Cant login to Rpi4 but can see it in codesys communications settings. CODESYS Forge talk (Post)
I have been struggling for over a week to program my rapspberry pi 4 with codesys. I purchased the license. I installed the runtime and the gateway, and I can see the pi in the communication settings. But cannot log in. I have checked the status of the pi with sudo systemctl status codesyscontrol and it is running. I have enabled traffic to and from the pi with iptables and checked the logs and all looks good. I just cannot connect through the codesys ide. Can anyone help me before I lose my mind?
Last updated: 2024-06-22

Post by msegon on OPC UA Client failed to connect CODESYS Forge talk (Post)
Hi everyone, I would appreciate your help with a problem I've been working on for a few days but haven't been able to resolve. I'm trying to read data from Tridium Niagara 4.15 OPC UA Server, but I get the error BadCertificateInvalid. As far as I understand, you need to add a CA certificate somewhere to establish a secure connection, but I don't know where. 2025-10-27T09:06:43.247Z, 0x0000008d, 4, 0, 0, * ERROR: OpcUa_Channel_BeginConnect: Cannot create secure channel without certificates! 2025-10-27T09:06:43.247Z, 0x00001090, 4, 0, 0, * ERROR: Datasource: Error Failed (268468242) in state Connecting I tried communicating without encryption, but it doesn't find the point. Has anyone managed to establish encrypted OPC UA communication?
Last updated: 2025-10-28

Post by timvh on CPU + EtherCAT redundancy CODESYS Forge talk (Post)
It works well with two Wago 750-8210's. I helped a few customers setting this up. But it should work with any device which can control EtherCAT I/O, is real-time and has sufficient network interfaces. Two network adapters can be used to create a redundant EtherCAT network (you need 2 additional switches for this). The other network adapters can be used to interconnect the 2 PLC's (synchronization). We noticed that if you exchange variable lists that there could be some issues if you have long lists. So what we did is use a SoftPLC on a server that contains all the settings which continuously sends network packages (GVL sender) and which is received by both PLC's (network receiver). Switching over is done in milliseconds. The bus doesn't notice the change-over. EtherCAT communication works flawlessly.
Last updated: 2026-01-30

Post by yannickasselin on Question about Demo License limitations for Modbus TCP communication and Fieldbus Instances CODESYS Forge talk (Post)
As far as I know, there is no other limitations than the 2 hours limit. The demo mode should be plenty enough for testing purposes. Regarding instances. In the device tree, 1 master = 1 instance, no matter how many slaves the master is communicating with. But it is also possible that your Codesys runtime act as a slave. In this case, each slave in the device tree is one instance. You can also use the license metric tool in the IDE. This will tell you exactly how many instances you have in your project. https://content.helpme-codesys.com/en/CODESYS%20Development%20System/_cds_edt_device_licensed_software_metrics.html
Last updated: 2026-02-28