Post by gabor-n on PNIO Connect Parameter Error
CODESYS Forge
talk
(Post)
It's a bit confusing, the two RPI is the same (board, OS, runtime, programing with Codesys V3.5 SP20 P2) but the one has a codesyscontrol.cfg file and the other has a codesyscontrol_user.cfg file. Shouldn't be the same? And because I over Codesys 3.5 SP 12 this would be the '_user.cfg' for both. Attached...
Last updated: 2024-10-11
Post by spoun on Problem with edge gateway config mode
CODESYS Forge
talk
(Post)
I installed patch 3 now and i get a new message, although i located and modified the files in system32 and sysWOW64 still doesn't work. One thing i noticed is thta in system32 folder CODESYSGatewayV3 now i have two different XXXXXXXX files with the latest being created today at the time of installation
Last updated: 2024-10-21
Post by acc00 on Main Task cycle too long leading to PLC Fail
CODESYS Forge
talk
(Post)
I have 2 Wago PFC200 PLC, running with Runtime SP19 Patch 5, with the Redundant application. The PLC communicates as Modbus Master with at this moment 15 Modbus Slaves -later there will be 28 in total- (Drives, Power management units,...). These devices are connected in 2 rings (1 ring of Drives, 1 ring of Power Management units), with 2 Managed Moxa Switches being part of the ring. Each PLC is connected to one of these switches. The issue I'm encountering is that the Cycle time of the Active PLC goes very high when I'm closing the Drive ring (simulating an issue on one Cabinet supply, resulting in that one Drive shut down, which can happen on field quite often). As a result of this long cycle, the PLC fails and goes to Exception, and the Passive PLC does not take control of the system. A normal cycle is around 30ms for the Main task, and a few ms for the Ethercat task. When I monitor with Profiler, I see that in this Maximum Cycle, the main Task is only taking 13ms, so I'm not sure where the PLC is hanging for so long. Is the remaining cycle time the Redundant management/sync or something else? Thank you in advance.
Last updated: 2024-03-08
Post by rabaggett on Reading Named Pipes in Linux Is there a better way?
CODESYS Forge
talk
(Post)
I have a Python program that will handle things in my application such as VISA over IP and Telnet control of instruments. I want the main control and HMI in Codesys. My problem is communication between the two. I have looked at several ways to accomplish this, and settled on having the Python program create two named pipes, one to send information to Codesys, and one for Codesys to send information to Python. The information would be packetized with \n for end of packet.. Seems simple. I think the named pipes method should work, but file reading in Codesys using the CAA file library starts to get difficult when the file is never ending, as in this case. Before I spend too much time making something that may be fundamentally flawed I want to ask. Is there a better way? Is there a way to read the file 'one line at a time' which might solve my never ending file problem? Thanks!
Last updated: 2024-05-09
Post by egau on Hard shutdown: no code on device after power on
CODESYS Forge
talk
(Post)
This explanation aligns with the issues we’re experiencing with our machines. The scenario I described is happening with one of them (let’s call it Machine A). This machine is identical to another one (Machine B), except for some custom code that facilitates communication with an external Beckhoff PLC for MES integration in the production line. Machine B has been powered on and off daily for at least three months and has never had this problem. Given that, I highly doubt the MES custom code is the cause of the code corruption. This being said, your explanation does seem plausible. However, if faulty EtherCAT cables were the issue, why wouldn't the error occur during normal operation? Why would bad cables only cause problems during a hard shutdown? One last question: When you encountered this behavior, did you see a similar error in your logs? i.e, an "AccessViolation" exception in the EtherCAT Task?
Last updated: 2024-10-03
Post by riccardo on VisuElems.CurrentUserGroupId is not stable
CODESYS Forge
talk
(Post)
Goodmorning TimvH, Thanks for the reply. I don't know if your solution solve my trouble yet, I am going to see the link you sent me. In the mean time I try to explane better what I need to do. I have a turbine system that get in alarm under some condition (E.g low speed of turbine) and block the itself. When the system is stoped there is no speed turbine and the system cannot start. To give to the operetor the possibility to bypass the alarms, there is an acknoledgement alarm pushbutton. This bypass must not work for everyone but only for those client that perform the login by (User Management). Furthermore, if the user perform the (manual or automatic) logout in alarm conditions, the acknowlegment must be annulled and block the system again. To do this, I need to know if an operator is logged in the page and is working to fix the problem; otherwise the syste must autoturn off again. Now I go to study your solution, if I have explaned better and you have another idea tell me please.
Last updated: 2023-11-16
Post by solidlogicguy on Little endian to Float from Modbus RTU
CODESYS Forge
talk
(Post)
Hello, I got a device from which I require to read values from I am using a WAGO PLC 750-8212 and I am communicating through Modbus Master FUNCTION BLOCK from library WagoAppPLCModbus in Codesys 3.5 to this device. I already receive data from the device that is a CVM to monitor voltage from a fuel cell. The technical support of the company that makes these devices says that the data is sent in little endian form. And I want to convert it to a float value. The tech support sent me the next instructions of how to do it but I am new using codesys, so any advice or help I will really appreciate so much. Message from tech support: The process is complicated, better to do it with already implemented library in the language/program you use. Basically the process should be next: To convert the two Modbus registers containing parts of a 32-bit float in little-endian byte order to a floating-point number using mathematical operations, you first need to combine the two 16-bit integers (assuming reg1 is the lower word and reg2 is the higher word) and then interpret the result according to the IEEE 754 standard. Given: - Register 192 (reg1) = 4096 - Register 193 (reg2) = 14884 Step 1: Combine the two registers. Since we are dealing with little-endian byte order, reg2 is the high word, and reg1 is the low word: combined = reg2 * 2^16 + reg1 combined = 14884 * 65536 + 4096 combined = 975175680 + 4096 combined = 975179776 Step 2: Convert the combined value to binary: combined_binary = '1110101101011100000000000000000' Step 3: Split the binary into IEEE 754 components: Sign bit (1 bit): 0 Exponent (8 bits): 11101011 Mantissa (23 bits): 01011100000000000000000 Step 4: Convert the binary exponent to decimal and subtract the bias (127 for 32-bit floats): exponent = int('11101011', 2) - 127 exponent = 235 - 127 exponent = 108 Step 5: Calculate the mantissa as a fraction: The mantissa in IEEE 754 format is the fractional part after the leading 1 (which is implicit). Therefore, we need to convert the binary mantissa to decimal and add the implicit leading 1: mantissa_fractional = 1 + int('01011100000000000000000', 2) / 2^23 mantissa_fractional = 1 + 18688 / 8388608 mantissa_fractional = 1 + 0.002227783203125 mantissa_fractional ≈ 1.002227783203125 Step 6: Combine the sign, exponent, and mantissa to get the float value: float_value = (-1)^0 * mantissa_fractional * 2^exponent float_value = 1 * 1.002227783203125 * 2^108 Because the exponent is quite large, the resulting float value is a very large number.
Last updated: 2023-12-15
Post by gustavocsw on MQTT memory leak problem
CODESYS Forge
talk
(Post)
Hello everyone, I'm using the IoT Library to implement the MQTT communication with my local broker server in order to publish and subscribe at specifics topics to share and consume information about my application. But, it seems that are occurring some memory leak problem in a "high" frequency (more than 10 Hz) subscribe process. I follow the same method as in IoT Lib exemples, and at first looks perfect but my PLC was rebooting frequently and when I check its memory usage that was increasing as fast as the subscribe massage was sent. I'm using a WEG PLC410 and a WEG PLC500, and this error occurred in both of them (including in CODESYS Control Win x64). The application sends to the system a message JSON with the float payload Ex. {"data" : 0.8500}, but this happens with a INT, or BOL as well. I use the follow code in my application to find the value: //FindFirstValueByKey VARs PROGRAM JSON_VELO VAR //------Setting the JSON Subscriber to Set the Relay Value jsonDataVelo : JSON.JSONData; jsonByteArrayReaderVelo : JSON.JSONByteArrayReader; xST1okVelo : BOOL; FindFirstValueByKeyVelo : JSON.FindFirstValueByKey; jsonElementVelo : JSON.JSONElement; xDoneReaderVelo : BOOL; xDoneFindVelo : BOOL; //STRING and WSTRING for Subscribe the massage sPayloadJsonVelo : STRING := 'opa'; psPayloadJsonVelo : POINTER TO BYTE := ADR(sPayloadJsonVelo); //wsPayloadJsonRelaySet : WSTRING := "opa"; wsPayloadJsonVelo : WSTRING := STRING_TO_WSTRING('opa'); pwsPayloadJsonVelo : POINTER TO WORD := ADR(wsPayloadJsonVelo); lrVelo : LREAL; xKeepAliveVelo : BOOL; xSetVelo : BOOL; RSSet : RS; LIMPAR : STRING; //Find the msg end sFindVelo : STRING := '}'; psFindVelo : POINTER TO STRING := ADR(sFindVelo); iLenVelo : INT; iSizeVelo : INT := 12; udiContMsg : UDINT; END_VAR // FindFirstValueByKey CODE // Relay Set configuration xSetVelo := MQTT_SUBSCRIBER.RSVelo.Q1; IF xSetVelo THEN xKeepAliveVelo := TRUE; END_IF IF xKeepAliveVelo THEN udiContMsg := udiContMsg + 1; iLenVelo := TO_INT(StrLenA(psPayloadJsonVelo)); iSizeVelo := iLenVelo - TO_INT(MQTT_SUBSCRIBER.udiPayloadSizeVelo); StrDeleteA(psPayloadJsonVelo,iSizeVelo,iLenVelo); wsPayloadJsonVelo := STRING_TO_WSTRING(sPayloadJsonVelo); pwsPayloadJsonVelo := ADR(wsPayloadJsonVelo); //MQTT.ConvertUTF8toUTF16(sourceStart:= ADR(sPayloadJsonVelo), targetStart:= ADR(wsPayloadJsonVelo), dwTargetBufferSize:= TAM, bStrictConversion:= 1); //Reset jsonByteArrayReader jsonByteArrayReaderVelo ( xExecute := TRUE, pwData := pwsPayloadJsonVelo, jsonData := jsonDataVelo, xDone => xDoneReaderVelo ); FindFirstValueByKeyVelo( xExecute := xDoneReaderVelo, wsKey := "data", diStartIndex:= 0, jsonData := jsonDataVelo, jsonElement => jsonElementVelo, xDone => xDoneFindVelo ); IF xDoneFindVelo THEN lrVelo := jsonElementVelo.value.lrValue; //Reset jsonByteArrayReader jsonByteArrayReaderVelo ( xExecute := FALSE, pwData := pwsPayloadJsonVelo, jsonData := jsonDataVelo, xDone => xDoneReaderVelo ); FindFirstValueByKeyVelo( xExecute := FALSE, wsKey := "data", diStartIndex:= 1, jsonData := jsonDataVelo, jsonElement => jsonElementVelo, xDone => xDoneFindVelo ); xKeepAliveVelo := FALSE; GVL.xSetVeloRead := TRUE; END_IF END_IF And this to subscribe at the topic: //SUBSCRIBE VAR: //----------------- Subscribe Velocity ----------------------- MQTTSubscribeVelo : MQTT.MQTTSubscribe;//Variable MQTTSubscriber block -X - function-X wsTopicSubscribeVelo : WSTRING(1024) := "CORE/odometry/GET/data/simp"; // Topic to publish a message sSubscribeMassageVelo : STRING; udiPayloadSizeVelo : UDINT; xSDoneVelo : BOOL; xSErrorVelo : BOOL; xReceiveVelo : BOOL; eSTypeVelo : MQTT.MQTT_ERROR; eSMQTTErrorVelo : MQTT.MQTT_ERROR; RSVelo : RS; udiCont : UDINT; //SUBSCRIBE CODE: MQTTSubscribeVelo( xEnable:= MQTT_CLIENT.xConnection_Broker AND NOT xSErrorVelo AND NOT JSON_VELO.xKeepAliveVelo, pbPayload:= JSON_VELO.psPayloadJsonVelo, udiMaxPayloadSize:= SIZEOF(JSON_VELO.sPayloadJsonVelo), udiPayloadSize => udiPayloadSizeVelo, mqttClient:= MQTT_CLIENT.ClientMQTT, wsTopicFilter:=wsTopicSubscribeVelo, xDone => xSDoneVelo, xError=> xSErrorVelo, xReceived => xReceiveVelo, eMQTTError=> eSMQTTErrorVelo ); RSVelo(SET := xReceiveVelo, RESET1 := JSON_VELO.xKeepAliveVelo);
Last updated: 2024-09-09
Post by ihatemaryfisher on Sorting array of any-sized structure
CODESYS Forge
talk
(Post)
With that I could make an array of varying size, but would still have to define the array type in the function's declaration VAR_IN_OUT stArray: array [*..*] of <pre-defined data type> END_VAR I wanted a function that could take an array of any type (e.g., a structured VAR) as an input. That way I could call it in multiple POUs to handle different arrays structures.
Last updated: 2023-08-18
Post by rossanoparis on After un upgrade of "CODESYS Control for Raspberry Pi MC SL" from v4.7 to v4.9 SysFileOpen function stopped working
CODESYS Forge
talk
(Post)
For those who will step on this thread. Everything is fine, I had only to increase by 1 my place holders number. For sure the system is occupying the number 1 without being declared ... Below the modification I made to get my code working. [SysFile] PlaceholderFilePath.2=/home/pi/hpca/bin, $hpcabin$ PlaceholderFilePath.3=/home/pi/hpca/cfg, $hpcacfg$ PlaceholderFilePath.4=/home/pi/hpca/logs, $hpcalogs$ PlaceholderFilePath.5=/home/pi/hpca/resources, $hpcares$
Last updated: 2023-08-22
Post by ofey on Symbol configuration / GVL
CODESYS Forge
talk
(Post)
Hi! I have som variables that I communicate to a Modbus Master. These variables are declared in a "Global Variable List" where I have assigned them memory addresses. To organize this mapping I want to make a MODBUS list where I show all the variable names together with the memory address. Is there an easy way to export this list from CODESYS? Either through script or some export function maybe?
Last updated: 2023-10-11
Post by ofey on Symbol configuration / GVL
CODESYS Forge
talk
(Post)
Hi! I have som variables that I communicate to a Modbus Master. These variables are declared in a "Global Variable List" where I have assigned them memory addresses. To organize this mapping I want to make a MODBUS list where I show all the variable names together with the memory address. Is there an easy way to export this list from CODESYS? Either through script or some export function maybe?
Last updated: 2023-10-11
Post by nathant on Some visualization objects disappear when user is logged in?
CODESYS Forge
talk
(Post)
I am deploying a webvisu on Codesys 3.5 SP 19.2 with legacy user management. I noticed that when a user logs in, some text and a rectangle I have (for aesthetics) both disappear. I made sure that none of the objects in question are linked to a state variable. Anyone know the cause/solution to this? Nothing crucial to the machine's function is lost, but it is a little annoying.
Last updated: 2023-12-15
Post by paro on Client Independent Visualization Switching
CODESYS Forge
talk
(Post)
Hi, can you please provide a new example for the topic at CODESYS "Client Independent Visualization Switching" https://forge.codesys.com/prj/codesys-example/client-independ/home/Home/ Since a few versions, the functions used cause warning messages. Examples for the use of all function blocks from the Visu Utils would generally be very helpful! Several people have put together an example here: https://forum-de.codesys.com//download/file.php?id=2240 BR Patrick
Last updated: 2023-12-20
Post by wiresplus on INT_TO_WORD function not working
CODESYS Forge
talk
(Post)
Hello, I need to take an INT input, and convert it to a WORD value. VAR DRV2Speed : WORD; //IO card takes a WORD where 16000 = full 10V output (equivalent to 50Hz) PumpFillSpeed : INT; //Users enter a value between 0 and 50 END_VAR IF <conditions> THEN DRV2Speed :=INT_TO_WORD((PumpFillSpeed/50)*16000); END_IF </conditions> According to me this should work - but it stays at 0, no matter what. What am I doing wrong?
Last updated: 2024-01-26
Post by ojz0r on INT_TO_WORD function not working
CODESYS Forge
talk
(Post)
That calculation will not work the way you expect it to. If PumpFillSpeed is limitied to 0-50 then the only whole number would be 50/50 = 1 everything else is 0.0-0.9999... and since you are using word and integer only 50 would work since there is no representation for mantissa in integer values. Declare a temporary real variable and do the calculation and then do a REAL_TO_WORD in the DRV2Speed assignment.
Last updated: 2024-01-26
Post by thomas-moba on "sudo"-Befehle über die Funktion "SysProcessExecuteCommand2"
CODESYS Forge
talk
(Post)
Hello, I need to execute "sudo" commands via CoDeSys 3.5 SP 19 P5 using the "SysProcessExecuteCommand2" function. Commands without sudo are no problem, but as soon as sudo is used in a .sh or a single command, it does not work. Command=AllowAll is entered under "SysProcess" in CODESYSControl.cfg. Nevertheless it does not work. Does anyone know what the problem could be? Greetings, Thomas
Last updated: 2024-02-01
Post by otdeveloper on IEC 61499
CODESYS Forge
talk
(Post)
It is being worked on by many companies and its even-driven function blocks seem like a natural evolution of the object oriented industrial programming I have seen Gary Pratt (author of the Book of CODESYS and much more) so expertly implement and explain. I would expect CODESYS to have this front and center on their sights and, if they do not, I would be very interested in learning why.
Last updated: 2024-02-09
Post by kleeswi on SysFileOpen does not work after update to V3.5 SP19 Patch 5
CODESYS Forge
talk
(Post)
I use the function SysFile.SysFileOpen(sFileNamePara, SysFile.ACCESS_MODE.AM_WRITE, pErrorFileOpen); to open and write a file. Since the update from Codesys V3.5 SP17 to V3.5 SP19 Patch 5 it does not work anymore. I first had SysFile.SysFileOpen(sFileNamePara, SysFile.ACCESS_MODE.AM_APPEND_PLUS, pErrorFileOpen); in both versions. hFile_Test is a pointer to byte. It gives an exceptional error when dereferencing the hFile_Test pointer. Edit: I use Codesys on a Raspberry pi
Last updated: 2024-02-19
Post by andrej on POU - Access to runtime
CODESYS Forge
talk
(Post)
Hello all, when creating a POU, the Codesys IDE allows the setting "Enable System Call" (in the Settings, Property -> Build), see picture. The name suggest, that runtime functionalities i.e. functions of codesyscontrol such as "stop plc" etc. can be directly called. I tried various approches without success, the following does, unsurprisingly not work. FUNCTION accessRTE: BOOL; ****************************** codesyscontrol.stop(); Can you please tell me how I can make a system call to codesyscontrol from a POU. Or could you provide me with a use case for this setting. Many thanks for your feedback and kind regards Andrej
Last updated: 2024-03-02
Post by ofey on EtherCAT fieldbus
CODESYS Forge
talk
(Post)
Okey, thank you! Do you think it is something in this library, that makes it possible to do the configuration in a PRG? https://content.helpme-codesys.com/en/libs/IODrvEtherCATDriver/Current/IoDrvEtherCAT.html#id1 I think the codesys modbus libraries support configuration and connection to modbus slaves without having to add the slave devices in the device tree. Just do it from function blocks inside the program. I was hoping for something similar with EtherCAT.
Last updated: 2024-04-10
Post by installwhat on Initialization of POUs (FB_Init)
CODESYS Forge
talk
(Post)
Hi I was wondering if there's a pattern I can employ to acheive what you're doing but with a "reference to" and also allowing for online changes? Someone told me that the new beckhoff keeps references safe during online changes but all the documentation I've found suggests that's not the case. The easiest thing is to use fb_init for normal vars and pointers and references can be added in the function body every cycle and this allows for method calls after so far as I can tell.
Last updated: 2024-07-29
Post by joep on overruling kinematic limits of [-90°, 90°] in bipod_rotary
CODESYS Forge
talk
(Post)
Hi All, for my robotics application we are building a 2-axis parallel scara using the kin_bipod_rotary kinematics. Codesys implemented limits of [-90°, 90°] according to the documentation: https://content.helpme-codesys.com/en/libs/SM3_Transformation/Current/SM3_Transformation/Function-Blocks/Positioning-Kinematics/Parallel-Systems/Kin_Bipod_Rotary.html Would it be possible to overrule these limits somehow, our mechanical limits are more in the range of [-110°, 135°] In this range we also don't encounter point where singularity is an issue. Hopeful someone knows a solution, Best regards, Joep
Last updated: 2024-09-04
Post by ralfki on User management
CODESYS Forge
talk
(Post)
Hello eschwellinger, at first thank you for your answer. So the only ways to activate the user management are CodeSys delevelopment enviroment and the Codesys Automation Server. So there is no function to activate the user management via code? Do you have an idea how to get back the users when somebody replaced the PLC. Our customers have only our own developed visualization and they also don't want to install further softwares. Do you maybe have a solution for this
Last updated: 2024-09-04
Post by mani-i4point0 on Codesys (Ethernet IP Scanner ) and Python (Ethernet IP Adapter)
CODESYS Forge
talk
(Post)
Hi, I am currently developing the software to establish the communication and data transfer between Python Module as a Ethernet IP - Adapter coding is running my laptop and Codesys as a Ethernet IP scanner in the resperry PI hardware. I am trying to look for some available recourses online, Can anyone suggest me to develop this function in Codesys and Python ? Best Regards, Mani
Last updated: 2024-09-24