Post by kleeswi on SysFileOpen does not work after update to V3.5 SP19 Patch 5
CODESYS Forge
talk
(Post)
I use the function SysFile.SysFileOpen(sFileNamePara, SysFile.ACCESS_MODE.AM_WRITE, pErrorFileOpen); to open and write a file. Since the update from Codesys V3.5 SP17 to V3.5 SP19 Patch 5 it does not work anymore. I first had SysFile.SysFileOpen(sFileNamePara, SysFile.ACCESS_MODE.AM_APPEND_PLUS, pErrorFileOpen); in both versions. hFile_Test is a pointer to byte. It gives an exceptional error when dereferencing the hFile_Test pointer. Edit: I use Codesys on a Raspberry pi
Last updated: 2024-02-19
Post by andrej on POU - Access to runtime
CODESYS Forge
talk
(Post)
Hello all, when creating a POU, the Codesys IDE allows the setting "Enable System Call" (in the Settings, Property -> Build), see picture. The name suggest, that runtime functionalities i.e. functions of codesyscontrol such as "stop plc" etc. can be directly called. I tried various approches without success, the following does, unsurprisingly not work. FUNCTION accessRTE: BOOL; ****************************** codesyscontrol.stop(); Can you please tell me how I can make a system call to codesyscontrol from a POU. Or could you provide me with a use case for this setting. Many thanks for your feedback and kind regards Andrej
Last updated: 2024-03-02
Post by ofey on EtherCAT fieldbus
CODESYS Forge
talk
(Post)
Okey, thank you! Do you think it is something in this library, that makes it possible to do the configuration in a PRG? https://content.helpme-codesys.com/en/libs/IODrvEtherCATDriver/Current/IoDrvEtherCAT.html#id1 I think the codesys modbus libraries support configuration and connection to modbus slaves without having to add the slave devices in the device tree. Just do it from function blocks inside the program. I was hoping for something similar with EtherCAT.
Last updated: 2024-04-10
Post by joep on Custom robotics kinematics model debugging
CODESYS Forge
talk
(Post)
When trying to move my axis using any group move instruction I get the following error: SMC_CP_INVALID_PATH_ELEM and axisgroup goes into errorstop state. I tested my methods thoroughly which makes it hard for me to debug. Are there some hidden rules I need to abide to? How would one go about debugging a custom robotics model, since the information inside isn't accesible. Is it possible to find the source of where the function breaks? Any hint in the right direction would be appreciated. Best regards
Last updated: 2024-06-08
Post by timvh on OSCAT Scale_r function not working in LD 4.60 works in LAD2 on 3.5.21sp3
CODESYS Forge
talk
(Post)
It seems like a bug in FBD. Work-around: If you click on the small line between the box and the output variable and delete this, the variable is removed. When you then assign a variable again (Ctrl-A), then you will see that the line will be a bit longer. If you then select the previous variable, you will see that it works.
Last updated: 2025-10-26
Post by youness on CSVReaderInit returns error : INVALID_HANDLE
CODESYS Forge
talk
(Post)
I have Already the same problem when i'm trying to write data more than 10 times in the same file. In fact, i send my data periodicaly to a file that i configured to have permission of W/R in my CodesysContol.cfg. When the Error occurs, i must reboot my machine to success. It means that the problem isn't realted to a limitation of size, but a problem in the function supposed to handle the file. totorovic : allow me to know if you've found a solution to your problem. Thanks.
Last updated: 2025-11-26
Post by nxbp on About Compatibility
CODESYS Forge
talk
(Post)
Let's say I have a CODESYS controller (PLC) with a runtime version around 3.5.19. If I use development software version 3.5.21.40 or a later version that will be released in the future for programming, could there be any problems or malfunctions in the controller's program execution or in the execution of the new, updated function blocks from the newer software? I mostly work with servo-based motion applications, so please keep that in mind when answering, and provide a detailed answer so I don't have to email you again about this topic.
Last updated: 2025-12-11
Post by durallymax on VAR_INFO from inside of a FB to get info on the instance.
CODESYS Forge
talk
(Post)
The help link appears to be broken. When I implemented something similar I had to add {attribute 'reflection} above the declaration of the FB with {attribute 'instance-path'} above the string VAR that would contain the path. Then wrote a function to trim off however much I wanted removed by searching for periods, then formatting it with spaces at the periods and removing brackets on arrays while also breaking up the PascalCase to present it a bit nicer for the end-users.
Last updated: 2025-12-12
Post by pernockham on How to recognize licenses SMALL, MEDIUM, LARGE by CmpCodemeter
CODESYS Forge
talk
(Post)
Third update. I figured that even knowing the level of the license, it will not tell me if its level is enough for the current application. There must be some other way to find this out? I see a component CM write in the Log if starting without license-dongle. "License lost - time left.. " Can I access this CM to check status from inside the application? This function is essential, why is it so hard to find info about implementation?
Last updated: 2026-10-06
Post by antonz on OSCAT Scale_r function not working in LD 4.60 works in LAD2 on 3.5.21sp3
CODESYS Forge
talk
(Post)
That's what I found as well Shaun. I have seen it at least in versions 3.5.21.1 and 3.5.21.3. There seems to be an issue with the FBD/LD package v4.6.0.0. The workaround proposed by Tim works but needs to be done manually on every code change/addition. For now we manually downgrade the FBD/LD package from v4.6.0.0 down to v4.5.0.0 after installation of CoDeSys. Same as you did. I hope this gets fixed on a next patch.
Last updated: 2025-11-21
Post by timvh on KeyPad Function in Visualization to fill a table
CODESYS Forge
talk
(Post)
Create an array of STRING and 1 INT variable, e.g.: asMyString : ARRAY[0..9] OF STRING; iIndex : INT; Then place a "Table" object in the visualization: - link this to the string array variable. - Check the option "Use Template" - Then in the Input Configuration - add the "Write Variable" command Somewhere else add a "Combobox, array" - link this to the same array. - And link the index to the INT variable. In the Combobox, you can then select one of the strings from the array. The index variable will indicate which selection has been made.
Last updated: 2026-01-08
Post by josepmariarams on Limit Axis CNC Jerk using SMC_Polynomial_AbsMaxLocs
CODESYS Forge
talk
(Post)
Dears. Until now, I have been using CNC libraries with Codesys 3.5SP11. I was using SMC_Polynomial_AbsMaxLocs function, from CNC library, to calculate the axis jerks, interpolating splines, to limit it. Now I have passed to SP20, and the functions which calculates the zeros and the maximum-minimum and zeros of polynomials has been disapeared. Questions: -Exist any FB wich can limit the jerk of individual axis in CNC? -Exist any other functions which can calculate max-min and zeros of polynomials? Thanks
Last updated: 2026-05-22
Post by programmierer on UDB Block in Codesys V2.3 implementieren um Werte an bestimmte IP-Adresse zu senden
CODESYS Forge
talk
(Post)
Hallo zusammen, ich möchte mich hiermit an euch wenden, in der Hoffnung, dass ihr mir bei meinem Problem behilflich sein könnt. Ich bin neu in der Programmierung und arbeite aktuell mit einem Wago Controller in unserem Labor, der eine Wärmepumpe steuert. Mein Ziel ist es, vier spezifische Werte an eine bestimmte IP-Adresse zu senden. Dazu habe ich versucht, in das vorhandene CODESYS-Programm der Wärmepumpe zusätzliche UDP-Blöcke einzufügen, um die Datenübertragung zu ermöglichen. Leider hat das Senden der Daten bis jetzt nicht funktioniert. Ich habe auch Bilder der Blockkonfiguration beigefügt, um einen besseren Einblick in den Aufbau zu geben. Über jegliche Hilfestellung würde ich mich sehr freuen. Vielen Dank im Voraus!
Last updated: 2024-07-19
Post by andrebrandt on FB string and naming
CODESYS Forge
talk
(Post)
Hi Tim. Not quite correct. What i'd like, is when you place the FB in prog, i choose a block NTC10k, and name this RT401. What i'm trying to do, is to get the name RT401 automaticly into the FB, so i can put this into the string i pass in a struct. So in var in POU, i saw this a place i could do this, RT401: NTC10k(Tag:='RT401'), but i can't get this to work. I shurly must have had something like this in FB: FUNCTION_BLOCK NTC10k String TAG But it's here where I'm stuck...
Last updated: 2024-09-30
Post by ben1 on Help understanding analog in-/outputs
CODESYS Forge
talk
(Post)
Hi there mate Most PLC's have a very similar concept with AI/AO - have you used any other software before? I have not used a Wago before myself, but I assume the concept would very much be: 1. Add the analog in & out cards to your hardware config. 2. Setup the raw input scaling on the hardware (eg. 4 - 20mA = 4000 - 20000) 3. Use a built in or homemade scaling block to scale your input as needed (eg. 4000 - 20000 = -100 - 2000kPa. 4. Write code as required 5. Scale output as needed (eg. 0 - 100% = 0-10000 = 0 - 10V) Is this the information you require?
Last updated: 2024-12-15
Post by peterkcontrols on Copying 2 byte word to output
CODESYS Forge
talk
(Post)
Hello. I am using codesys 3.5. I would like to know if it is possible to set a variable to an output without declaring in. I have defined a STRUCT and within this struct I have a Struct for inputs called I and a struct for outputs called O. I have declared a variable of the type of this Struct, I would like to set or alias the value in this variable to an input/output value of an IO block that has a module on the ethernet tree. Is it possible to copy the contents of %IW0 -> STRUCT.I ? The size of both of these is 2 bytes. I understand that I can declare a variable with the input like Input01 AT %IX0.0 : BOOL; However how can I make STRUCT.I.D00 AT %IX0.0? Is this possible? Thanks
Last updated: 2025-03-03
Post by amy123 on codesys mqtt publish serialization
CODESYS Forge
talk
(Post)
Hello, I am using the CODESYS IIoT Libraries SL MQTT Publish. Does this publish block only support publishing STRINGS as a readable format? I can publish ENUM, STRUCT, BOOL; however, MQTT Explorer will only display strings. When I use Wireshark, I can see that it is publishing something, but it looks to be publishing a serialized version which is a bunch of 0s or random text. If so, is there any way to deserialize this information back into a readable format? See pictures, where I have a BOOL TRUE that gets published as 001. Then see where I publish a STRUCT and it's an incomprehensible combination of 0s - only the string variable is displayed. Or, is it expected that you convert everything to a string before publishing? Any help is greatly appreciated! :)
Last updated: 2024-02-16
Post by esave on OPC UA Server with on Codesys + OPC UA Client on Labview
CODESYS Forge
talk
(Post)
Hello everyone I want a communication between my PLC as an OPC UA Server and Labview on my PC as the OPC UA Client. I have an Festo CPX-E-CEC-C1-PN PLC and I have the OPC UA Toolkit from Labview. I created some Variables for testing (see picture 1) on Codesys. I tried to use this Labview block diagram (see picture 2) but I cant connect the PLC to it. What do I have to type in the Server Endpoint URL and what in the Node ID? Is this a good way for communication with a PLC to a PC? If not is there another way?
Last updated: 2024-04-12
Post by tayhim on WAGO HMI Device not found
CODESYS Forge
talk
(Post)
Hello, I'm trying to connect with a Wago TP600 HMI but without success. I'm using codysis 3.5 SP19 patch 7 (SP20 block all the time) and the official wago package is installed. However, when I scan and select my device, I get a message saying that the device doesn't match the project's device object with the possibility to update the device (as shown in the attached picture). however, after choosing to update i got a message that the device is not found. I've tried with a new empty project but the same results. do you have any ideas? Thanks.
Last updated: 2024-06-25
Post by pernockham on How to recognize licenses SMALL, MEDIUM, LARGE by CmpCodemeter
CODESYS Forge
talk
(Post)
I think google has fooled me here, the only thing I can conclude so far is what i now from reading the licenseManager, which tells me that my valid license have the following product-code CONTROL - 16#3000 VISU - 16#3003, feature map: 1000 COM - 16#3004, feature map: 0200 Will different level of license give different product codes or will I see the active license level by other means? What I am trying to achieve is block Starting a machine with time limited operation should the application be larger than what the license permits (DEMO-mode). And give this information to the user by an alarm/information.
Last updated: 2026-10-06
Post by charly29160 on CmpCharDevice blocks gpiochip access on Raspberry Pi 5 since update from SP18 to SP21
CODESYS Forge
talk
(Post)
Hallo Herr Schwellinger - Danke für die Info. Der Fehler besteht weiterhin: Follow-up: Rootless mode is not the cause here — verified with ps aux, the runtime binary runs as root: root 1974 48.9 0.7 854852 62140 ? SLl 13:00 0:04 /opt/codesys/bin/codesyscontrol.bin /etc/codesyscontrol/CODESYSControl.cfg gpioinfo gpiochip0 as root also works flawlessly (all 54 lines listed correctly, no permission errors at the kernel level). So the block is happening purely inside CmpCharDevice's own sandboxing, not at the Linux/kernel permission level and not due to a dedicated unprivileged user. The correct config key to whitelist /dev/gpiochip0 for CmpCharDevice is still what I'm looking for. Im Voraus herzlichen Dank für Ihre Hilfe Karl Schuler
Last updated: 2026-07-20
Post by charly29160 on CmpCharDevice blocks gpiochip access on Raspberry Pi 5 since update from SP18 to SP21
CODESYS Forge
talk
(Post)
Hallo Herr Schwellinger - Danke für die Info. Der Fehler besteht weiterhin: Follow-up: Rootless mode is not the cause here — verified with ps aux, the runtime binary runs as root: root 1974 48.9 0.7 854852 62140 ? SLl 13:00 0:04 /opt/codesys/bin/codesyscontrol.bin /etc/codesyscontrol/CODESYSControl.cfg gpioinfo gpiochip0 as root also works flawlessly (all 54 lines listed correctly, no permission errors at the kernel level). So the block is happening purely inside CmpCharDevice's own sandboxing, not at the Linux/kernel permission level and not due to a dedicated unprivileged user. The correct config key to whitelist /dev/gpiochip0 for CmpCharDevice is still what I'm looking for. Im Voraus herzlichen Dank für Ihre Hilfe Karl Schuler
Last updated: 2026-07-20
Post by rik123456 on Alarmmanagement – Dynamic Alarm List
CODESYS Forge
talk
(Post)
Hi, I had a question about alarm management in the CODESYS visualization. I am currently investigating to what extent the alarm visualization can be built dynamically. In my program, I have developed a motor block that is used for multiple motors. When the emergency stop of one or more motors is activated, the corresponding motors are displayed in the alarm list (see image). This works quite well. I achieved this by linking variables to a latch, after which a piece of code displays the motors that are in emergency stop. My question is: do I need to create a separate latch for each motor or can I use a single latch to display multiple alarms of a motor underneath each other? This would then look like this: Time…: M1 Emergency Stop Active Time…: M4 Emergency Stop Active
Last updated: 2026-04-20
Post by alexgooi on Network variable stops sending
CODESYS Forge
talk
(Post)
Hi Reinier, What usually works for me is settings it up in the following way: In the sender block make sure that the list identifier is unique for the whole installation (this is only relevant when you have multiple senders in 1 network). When you are linking the NVL to a file make sure that the path to this file doesn't change. In my experience the NVL stops working when you change the working directory and afterwards open the NVL in de Codesys IDE. If this doesn’t apply to you application, you could also try to change the port number, maybe there is an other process making use of port 1202. Kind regards Alex
Last updated: 2026-04-22
Post by imdatatas on Read "Homed" status from EtherCAT drive
CODESYS Forge
talk
(Post)
Hello, I have experienced such situations with some servo drive devices in the past. The home completion information is reported to the upper controller by the slave drive with the states of the relevant bits in the StatusWord (for example; 6041h Bit10, Bit12 in Home mode). If the states of these bits are correct in terms of number and state but the motor does not actually perform the action; You can contact the slave drive manufacturer. There may be a problem with the device firmware. Another area you can play around with is looking at the settings in the "Advanced configuration" for Softmotion axis on the page the link to below, and trying it out and using the one that works for you. https://content.helpme-codesys.com/en/CODESYS%20SoftMotion/_sm_cmd_add_softmotion_cia402_axis.html A method I recommended worked for a user as in below message. https://forge.codesys.com/forge/talk/Engineering/thread/40bc82454d/ I hope your problem will be solved as soon as possible and by sharing the result here, you will help others to know and overcome it. Good luck. Best regards, Imdat