Post by ben1 on How to write multiple coils (Modbus FC15)
CODESYS Forge
talk
(Post)
If I am understanding what you are saying, then yes that would be your problem. I would create an array of bools on the client side for the transfer and try that. Or if client can't be changed then use words on server and unpack. But I am not sure if you or I are mis interpreting but it sounds a bit jumbled. I don't know what you have control of, but, if you are turning on BITS in the server, you should write to BITS in the client with a Function 15. If you are writing to WORDS in the server, you should write to WORDS in the client with a Function 16.
Last updated: 2024-11-17
Post by milan-svarny on ModbusFB.ClientSerial Problem with Reply Timeout
CODESYS Forge
talk
(Post)
Hi All, I have problem with ModbusFB.ClientSerial. I'm using 4 different port for Modbus communication. After some time of running program ClientSerial stops to receive data to reply buffer and all request finish with Reply Timeout. The Device sent reply correctly,that it is visible on oscilloscope and it is possible to see that data( reply )are in the device. If the usbtty device is read over external app. then it is possible to see all data which were not taken by ModbusFB.ClientSerial. The stack does not overflow or something , program runs correctly forward and no exceptions or something. The main problem it is that when the error occur than it is not possible to reset port or something or maybe i'm doing it wrong way. please help me with this issue. Thank you for any help in advice Milan
Last updated: 2025-05-23
Post by ofey on EtherCAT fieldbus
CODESYS Forge
talk
(Post)
Hi, everyone! I'm trying to set up a PLC controller and a connection to an EtherCAT slave device in Codesys. I want to create a flexible program that I can upload to multiple controllers with different remote IO connected (same program). On one plant i may have 5 AI-cards and 3 DO-cards, and on another I may have 4 AI-cards and 2 DO-cards. For not needing to maintain several different programs wih different devices defined in the program (one for each set up) I thought that using a remote IO would make it easier having a single program. That way I could refer to different memory addresses instead of predefined slots/channels and IO's, that would give me errors if there was a different IO on the plant than what the program expected. When I tried setting up the etherCAT master, I saw that I had to define the etherCAT slave devices with the different IO'cards for me to be able to refer to the memory addresses in a PRG. Exactly what I was trying to avoid. My setup is something like a program that can handle 16 separate pump controls. In a year maybe 6 plans get deployed, and depending on how large the project is, the number of pumps can vary between 4 and 16. And the managers dont want to have IO's for all 16 pumps on every cabinet, and I dont want to maintain 16 separate projects files in case of updates etc. I thought the best way to tackle this was having a single project that read/write data to the different pump IO's by remote IO (fieldbus ethercat) addresses. And the number of pump controls are activated by an external GUI. If pump 1-6 is activated by the GUI, then the PLC-program tries to read/write input/outputs from predefined addresses for the expected IO's. My test setup is a PFC200 WAGO controller and a EtherCAT fieldbus coupler (750-354) with some IO. I hope I didn't explain this too horrible, and if there is a more easy and elegant solution for this challenge I appreciate a feedback on this.
Last updated: 2024-04-08
Post by dekelec on Codesys 2.3 & Peak PCAN
CODESYS Forge
talk
(Post)
I use Peak USB adapter daily to download from CoDeSys 2.3 and 3.5 to IFM, EPEC and other controllers. The process: - First you need to install the appropriate driver. Link: https://www.peak-system.com/Drivers.523.0.html?&L=1 - Restart the computer - Start the CoDeSys application - Change the name of the adapter in Communication parameters, as mentioned in previous comment. Write the name exactly as written "Peak_USB", as it could also be case sensitive (defines which .dll file to use). If this doesn't work I would contact the vendor of the controller to find out the procedure. In the attachment I've added a FAQ document from IFM regarding using PCAN USB. P.S. I've noticed in your picture of communication parameters a channel via TCP/IP is mentioned. In this case a USB to CAN connection is not being used. First you should change the channel/gateway to connect via CANbus or connect using an Ethernet cable.
Last updated: 2024-07-09
Post by simone on Cannot connect to webvisu on localhost
CODESYS Forge
talk
(Post)
As I wrote before on the title, I have difficulties to connect to see webvisu from localhost. The story: while waiting for the plc+hmi to arrive, I'm preparing the software, mainly the visual parts trough the control Win3 x64 (same version as the ide 3.5.20.10). The problem is that I can't see the webvisu with the installed webbrowser. I don't know if this is a problem, but I changed the port to 9001 (randomly "free") because 80, 8000, 8080, 8088, 3000 are all occupied by other projects (all on the Apache server). Is there something wrong with the config file? This is the url: localhost:9001/webvisu_app.htm and here the config file part "CmpWebServer". [CmpWebServer] ;The handling of startup/shutdown of the webserver: ;0->automatically start, shutdown only on shutdown of the runtime;1->automatically start, could be shutdown on demand ;2(default)->start/shutdown on demand;3->start on demand, shutdown only on shutdown of the runtime StartupType=0 ;The TCP port the webserver listens on WebServerPortNr=9001 LocalAddress=localhost ;LocalAdapterName=LAN-Connection LocalAdapterName=EthernetPCPLC ;LocalAdapterNameUnicode=L\00A\00N\00-\00C\00o\00n\00n\00e\00c\00t\00i\00o\00n\00 LocalAdapterNameUnicode=E\00t\00h\00e\00r\00n\00e\00t\00P\00C\00P\00L\00C\00 Thanks for all the help!
Last updated: 2024-07-11
Post by denkihitsuji on Content update through Data URI on Web Brower on Visualization Toolbox
CODESYS Forge
talk
(Post)
Objective: I want to dynamically update the content with strings and JPEG images received from a TCP/IP socket. For this purpose, I am exploring the possibility of utilizing the Web Browser feature of the Visualization toolbox. Example: In a standard web browser, entering data:text/plain;charset=utf-8;base64,SGVsbG8gc3RyYW5nZXI= in the URL window will display "Hello stranger" on the webpage. Issue: When attempting to use this method in the Web Browser of the Visualization toolbox, the content does not display as expected. Instead, it shows the error:'Navigation to the webpage was canceled.'. Request: I seek guidance on how to resolve this issue so that the Web Browser in the Visualization toolbox correctly interprets and displays the data URI content. Alternative Solution Welcomed: Or, if it is possible to directly use Codesys Structured Text (ST) variables within an HTML page, this approach would also meet my requirements. Thank you for your attention.
Last updated: 2024-07-30
Post by julianramirez on ModbusFB write update
CODESYS Forge
talk
(Post)
Hello everyone, I am testing the ModbusFB library tcp server and so far I am able to create holding registers successfully, however, I am trying to identify after each write which registers got updated (i.e. function code, write value). I can even see the var udiNumWriteRequests, which increases with every write. I noticed that there is logging with the LogStatusInfo method. After I call it I am able to read in the console stuff that I want. Nevertheless, this is only available at the logs and is not easy to decode because it consists on several messages, I would like to know if there is a way for me to retrieve this information from the function itself with pointers or if there is any way to copy the logs messages (assuming that I can filter them with the LoggingOptions to only show what I need) inside the runtime code and not in the console. Thanks for your help :)
Last updated: 2024-09-16
Post by timvh on STRING conversions to DWORD
CODESYS Forge
talk
(Post)
I guess that the printer expects to receive an array of byte values. So where it is described that it expects to receive: Hercules String : 1B4F513030311B7532626C61636B04 it actually expects to receive an array of bytes with the values 1B,4F,51,30,30, etc. So what you can do is create an array of bytes and assign the byte value to each item in the array: VAR abyToSend : ARRAY[0..99] OF BYTE; END_VAR abyToSend[0] := 16#1B; // ASCII Escape character, hexadecimal representation uses 16# as prefix abyToSend[1] := 16#4F; // ASCII 'O' abyToSend[2] := 16#51; // ASCII 'Q' abyToSend[3] := 16#30; // ASCII '0' // you can do the rest yourself // maybe could be created a lot smarter, but gives you an indication how to handle this. Then with the serial communication (or TCP/IP?) you can send a message with the reference to the array (abyToSend) and the number of bytes to send (15 bytes for the string you gave as example).
Last updated: 2025-02-02
Post by george32 on TCP Server
CODESYS Forge
talk
(Post)
Thank you for your advice Rinie, I have tried to follow this example but found one problem.When I disconnect with Hercules the system does not acknowledge the lost of its connection this could result in critical errors. Because of this error I am trying to implement the Syssocket library. With this library I am having a problem which I could not solve. I have the following code: ip_adres : STRING :='0.0.0.0'; port : WORD := 5000; iStep : INT := 1; // Socket information Socket_handler : SysSocket_Interfaces.RTS_IEC_HANDLE; Socket_handler_result : SysSocket_Interfaces.RTS_IEC_RESULT; Socket_adress : SysSocket_Interfaces.SOCKADDRESS; Addres_Convert : SysSocket_Implementation.RTS_IEC_RESULT; // Bind information Bind_handler : SysSocket_Interfaces.RTS_IEC_RESULT; // Listener Information Listener_handler : SysSocket_Interfaces.RTS_IEC_RESULT; Addres_Convert := SysSocket_Implementation.SysSockInetAddr(szIPAddress:= ip_adres,pInAddr:= ADR(Socket_adress.sin_addr)); Socket_adress.sin_family:= SysSocket_Interfaces.SOCKET_AF_INET; Socket_adress.sin_port := SysSocket_Implementation.SysSockHtons(usHost:= port); CASE iStep OF 1: // Create Socket Socket_handler :=SysSockCreate( iAddressFamily :=SysSocket_Interfaces.SOCKET_AF_INET, diType:=SysSocket_Interfaces.SOCKET_STREAM, diProtocol:=SysSocket_Interfaces.SOCKET_IPPROTO_TCP, pResult:=ADR(Socket_handler_result)); IF Socket_handler = SysSocket_Interfaces.RTS_INVALID_HANDLE THEN iStep := 1; ELSE iStep := 2; END_IF 2: Bind_handler := SysSocket_Implementation.SysSockBind( hSocket:=Socket_handler, pSockAddr :=ADR(Socket_adress), diSockAddrSize:=SIZEOF(Socket_adress) ); 3: Listener_handler := SysSocket_Implementation.SysSockListen( hSocket :=Socket_handler, diMaxConnections :=1); END_CASE When I am trying to get this working, the SysSockBind function gives a value of 16#207 which means adress already in use. I find this weird because of the IP-adress of 0.0.0.0. I think I am converting the Ip-adress in the wrong way, but the code does not give a error arround this. So therefore I cannot find the solution to this problem. I hope someone could help me with this problem. Thanks in advance George
Last updated: 2025-02-20
Post by latassan on RaspberryPi 5 gateway problem
CODESYS Forge
talk
(Post)
Hello, I'm trying to use a raspberryPi 5 as a PLC. I fixed its IP address, I can ping it. I've also installed the CODESYS Control for Raspberry Pi 64 SL runtime on it. So I've created a gateway (IP address of the Raspberry, TCP port 1217). I see the green dot next to this gateway. When I do a network scan, I can see my raspberry (see photo). When I try to connect to it, I have to define an administrator profile, which I do. On validation, I see a message: No device is responding to the scan request. I've checked that port 1217 is listening on the raspberry, I've uninstalled the runtime then installed it again, but I can't connect. Also, when I try to configure the user groups before connecting, I see that Offline mode is not supported by the device, even though I'm connected to it in the Deploy Control SL tab. When I try to refresh, I see: Gateway not configured properly. How can I connect to my Raspberry? Have I defined my gateway incorrectly?
Last updated: 2025-06-12
Post by mondinmr on Direct Pointers in IOMapping for EtherCAT with IoDrvEthercatLib.ETCSlave_Dia
CODESYS Forge
talk
(Post)
Using SDO, I can read the EtherCAT mappings and offsets from various registers like 0x1c12, 0x1c13, etc. When I obtain registers mapped in the PDOs and various offsets, I could technically access directly to the statusword, controlword, etc., if they are mapped. I have noticed that on IoDrvEthercatLib.ETCSlave_Diag I can find pointers to the input and output buffers. However, although the input buffer can be easily read by referring to what has been obtained from the SDOs, it is not possible to write to the output buffer, as it is overwritten in each cycle by the data from the IOMapping task. Is there a way, knowing an instance of IoDrvEthercatLib.ETCSlave_Diag, to obtain the pointer to the first data in the IOMapping? The offsets are identical to those of the PDOs, but obviously the data is a copy. For me, the cleanest thing would be to access the pointers on IOMapping, for DS402a devices to retrieve the key data and point them to internal references. I need to know this as, having developed our own motion library, I would like to simplify the initial setup by eliminating unnecessary and nonsensical mappings that can lead users to unnecessary errors. In the current version that we have been using for years, we have to map everything manually. I would like to pass only the slave reference to the FB_init constructors and eliminate the mapping.
Last updated: 2024-02-12
Post by tama00 on GPIOs not running with Raspberry Pi 4 (and SPI connection)
CODESYS Forge
talk
(Post)
Hello everyone, I have a working SPI connection (with transferExt) between a Raspberry master with Codesys and an ESP32 slave. I would also like to use a few GPIO pins. Is there a problem with using SPI AND GPIOs? Environment: Raspberry Pi 4+ with Raspian from Oct 23 Codesys V3.4 SP19 Patch 5 with Runtime Version 4.10.0.0 Device: GPIOs B+/Pi2 My problem: The status is displayed as “GPIOs : not running”. And also during mapping the message “The bus is not running. The values shown are perhaps not actual”. However, the variable changes that I make in my program are displayed under “Current Value”. In the Logic Analyzer, the pin toggles during transmission with small intervals of +-4us (seems to be a cyclical disorder, but I don't know where exactly it could be coming from). This applies to pins that I actually use (output) but also to the other GPIOs (not used). With GPIO 4, the line remains permanently high. Attached is a screenshot from the Logic Analyzer. Channel 1,3,5 were GPIO pin 26, 22, 17 Would be very grateful for help. Best regards
Last updated: 2024-05-06
Post by wbj0t on System libs and I/O Drivers
CODESYS Forge
talk
(Post)
Hi everyone. My question about: where I can learn (read or watch) an info about codesys workflow through the system IO libs? I want to know how to implement I/O drivers by my self. In the system libs I see many interfaces, methods etc... But there is no explanation about them, just names of methods and fields of the FBs. I know about this page: https://forge.codesys.com/drv/io-drivers/doc/Generic/ There is so BIG the device description file and not so clear explaining of the attributes and elements, also some elements or attributes missed at it all. Yes, there are code examples on this page, but, so shortly and, for example, code about Modbus drivers is absent. And even if I try to add the IoDrvFB with lib, I get and error, something like: "failed to load IoDrvFB driver". And what about the book of codesys that written by Gary Pratt? Is there information about system libs and drivers in this book more clearly? Thank you :)
Last updated: 2024-02-02
Post by alexgooi on Modbus writing on value change
CODESYS Forge
talk
(Post)
Hi Duvan, You could make this in 1 single object (FB), Indeed don't use a function for this beacuse you need some memory to keep the old value. For i := 0 TO 200 BY 1 DO //Check if the value has been changed IF Old_Value[i] <> Value[i] THEN //Set the trigger to TRUE Trigger[i] := TRUE; Old_Value[i] := Value[i]; END_IF END_FOR If you define the Value array as an In_Out and the Trigger as an In_Out you arn't claiming any aditional memory to your system. You ofcourse then need to add some code arround it that does something with the trigger and writes it back to FALSE again. If you want more flexability you also could use pointers instead of using the IN_OUT FOR i := 0 TO 200 BY 1 DO address := address_Input + i * SIZEOF(*Put type here); IF Address^ <> Old_Value[i] THEN Trigger[i] := TRUE; Old_Value[i] := Address^; END_IF END_FOR
Last updated: 2024-04-02
Post by jkessler on IoDrvModbusTCP_Diag not defined when using MODBUS
CODESYS Forge
talk
(Post)
Hi, Same for me ! Works in Codesys 3.5.19 but not in 3.5.20. I'm currenly using with a WAGO PLC200 [ERREUR] EmPlcProgram: Application [Device: Logique API]: C0046: Identificateur 'IoDrvModbusTCP_Diag' non défini [ERREUR] EmPlcProgram: Application [Device: Logique API]: C0080: Le bloc fonctionnel 'IoDrvModbusTCP' doit être instancié pour permettre l’accès [ERREUR] EmPlcProgram: Application [Device: Logique API]: C0004: 'IoDrvModbusTCP_Diag' n’est pas un composant de 'IoDrvModbusTCP' [ERREUR] EmPlcProgram: Application [Device: Logique API]: C0046: Identificateur 'ModbusTCPSlave_Diag' non défini [ERREUR] EmPlcProgram: Application [Device: Logique API]: C0080: Le bloc fonctionnel 'IoDrvModbusTCP' doit être instancié pour permettre l’accès [ERREUR] EmPlcProgram: Application [Device: Logique API]: C0004: 'ModbusTCPSlave_Diag' n’est pas un composant de 'IoDrvModbusTCP' [ERREUR] EmPlcProgram: Application [Device: Logique API]: C0046: Identificateur 'ModbusTCPSlaveUnit_Diag' non défini [ERREUR] EmPlcProgram: Application [Device: Logique API]: C0080: Le bloc fonctionnel 'IoDrvModbusTCP' doit être instancié pour permettre l’accès [ERREUR] EmPlcProgram: Application [Device: Logique API]: C0004: 'ModbusTCPSlaveUnit_Diag' n’est pas un composant de 'IoDrvModbusTCP' Thanks in advance
Last updated: 2024-05-29
Post by jkessler on IoDrvModbusTCP_Diag not defined when using MODBUS
CODESYS Forge
talk
(Post)
Hi, Same for me ! Works in Codesys 3.5.19 but not in 3.5.20. I'm currenly using with a WAGO PLC200 [ERREUR] EmPlcProgram: Application [Device: Logique API]: C0046: Identificateur 'IoDrvModbusTCP_Diag' non défini [ERREUR] EmPlcProgram: Application [Device: Logique API]: C0080: Le bloc fonctionnel 'IoDrvModbusTCP' doit être instancié pour permettre l’accès [ERREUR] EmPlcProgram: Application [Device: Logique API]: C0004: 'IoDrvModbusTCP_Diag' n’est pas un composant de 'IoDrvModbusTCP' [ERREUR] EmPlcProgram: Application [Device: Logique API]: C0046: Identificateur 'ModbusTCPSlave_Diag' non défini [ERREUR] EmPlcProgram: Application [Device: Logique API]: C0080: Le bloc fonctionnel 'IoDrvModbusTCP' doit être instancié pour permettre l’accès [ERREUR] EmPlcProgram: Application [Device: Logique API]: C0004: 'ModbusTCPSlave_Diag' n’est pas un composant de 'IoDrvModbusTCP' [ERREUR] EmPlcProgram: Application [Device: Logique API]: C0046: Identificateur 'ModbusTCPSlaveUnit_Diag' non défini [ERREUR] EmPlcProgram: Application [Device: Logique API]: C0080: Le bloc fonctionnel 'IoDrvModbusTCP' doit être instancié pour permettre l’accès [ERREUR] EmPlcProgram: Application [Device: Logique API]: C0004: 'ModbusTCPSlaveUnit_Diag' n’est pas un composant de 'IoDrvModbusTCP' Thanks in advance
Last updated: 2024-05-29
Post by jkessler on IoDrvModbusTCP_Diag not defined when using MODBUS
CODESYS Forge
talk
(Post)
Hi, Same for me ! Works in Codesys 3.5.19 but not in 3.5.20. I'm currenly using with a WAGO PLC200 [ERREUR] EmPlcProgram: Application [Device: Logique API]: C0046: Identificateur 'IoDrvModbusTCP_Diag' non défini [ERREUR] EmPlcProgram: Application [Device: Logique API]: C0080: Le bloc fonctionnel 'IoDrvModbusTCP' doit être instancié pour permettre l’accès [ERREUR] EmPlcProgram: Application [Device: Logique API]: C0004: 'IoDrvModbusTCP_Diag' n’est pas un composant de 'IoDrvModbusTCP' [ERREUR] EmPlcProgram: Application [Device: Logique API]: C0046: Identificateur 'ModbusTCPSlave_Diag' non défini [ERREUR] EmPlcProgram: Application [Device: Logique API]: C0080: Le bloc fonctionnel 'IoDrvModbusTCP' doit être instancié pour permettre l’accès [ERREUR] EmPlcProgram: Application [Device: Logique API]: C0004: 'ModbusTCPSlave_Diag' n’est pas un composant de 'IoDrvModbusTCP' [ERREUR] EmPlcProgram: Application [Device: Logique API]: C0046: Identificateur 'ModbusTCPSlaveUnit_Diag' non défini [ERREUR] EmPlcProgram: Application [Device: Logique API]: C0080: Le bloc fonctionnel 'IoDrvModbusTCP' doit être instancié pour permettre l’accès [ERREUR] EmPlcProgram: Application [Device: Logique API]: C0004: 'ModbusTCPSlaveUnit_Diag' n’est pas un composant de 'IoDrvModbusTCP' Thanks in advance
Last updated: 2024-05-29
Post by jkessler on IoDrvModbusTCP_Diag not defined when using MODBUS
CODESYS Forge
talk
(Post)
Hi, Same for me ! Works in Codesys 3.5.19 but not in 3.5.20. I'm currenly using with a WAGO PLC200 [ERREUR] EmPlcProgram: Application [Device: Logique API]: C0046: Identificateur 'IoDrvModbusTCP_Diag' non défini [ERREUR] EmPlcProgram: Application [Device: Logique API]: C0080: Le bloc fonctionnel 'IoDrvModbusTCP' doit être instancié pour permettre l’accès [ERREUR] EmPlcProgram: Application [Device: Logique API]: C0004: 'IoDrvModbusTCP_Diag' n’est pas un composant de 'IoDrvModbusTCP' [ERREUR] EmPlcProgram: Application [Device: Logique API]: C0046: Identificateur 'ModbusTCPSlave_Diag' non défini [ERREUR] EmPlcProgram: Application [Device: Logique API]: C0080: Le bloc fonctionnel 'IoDrvModbusTCP' doit être instancié pour permettre l’accès [ERREUR] EmPlcProgram: Application [Device: Logique API]: C0004: 'ModbusTCPSlave_Diag' n’est pas un composant de 'IoDrvModbusTCP' [ERREUR] EmPlcProgram: Application [Device: Logique API]: C0046: Identificateur 'ModbusTCPSlaveUnit_Diag' non défini [ERREUR] EmPlcProgram: Application [Device: Logique API]: C0080: Le bloc fonctionnel 'IoDrvModbusTCP' doit être instancié pour permettre l’accès [ERREUR] EmPlcProgram: Application [Device: Logique API]: C0004: 'ModbusTCPSlaveUnit_Diag' n’est pas un composant de 'IoDrvModbusTCP' Thanks in advance
Last updated: 2024-05-29
Post by jkessler on IoDrvModbusTCP_Diag not defined when using MODBUS
CODESYS Forge
talk
(Post)
Hi, Same for me ! Works in Codesys 3.5.19 but not in 3.5.20. I'm currenly using with a WAGO PLC200 [ERREUR] EmPlcProgram: Application [Device: Logique API]: C0046: Identificateur 'IoDrvModbusTCP_Diag' non défini [ERREUR] EmPlcProgram: Application [Device: Logique API]: C0080: Le bloc fonctionnel 'IoDrvModbusTCP' doit être instancié pour permettre l’accès [ERREUR] EmPlcProgram: Application [Device: Logique API]: C0004: 'IoDrvModbusTCP_Diag' n’est pas un composant de 'IoDrvModbusTCP' [ERREUR] EmPlcProgram: Application [Device: Logique API]: C0046: Identificateur 'ModbusTCPSlave_Diag' non défini [ERREUR] EmPlcProgram: Application [Device: Logique API]: C0080: Le bloc fonctionnel 'IoDrvModbusTCP' doit être instancié pour permettre l’accès [ERREUR] EmPlcProgram: Application [Device: Logique API]: C0004: 'ModbusTCPSlave_Diag' n’est pas un composant de 'IoDrvModbusTCP' [ERREUR] EmPlcProgram: Application [Device: Logique API]: C0046: Identificateur 'ModbusTCPSlaveUnit_Diag' non défini [ERREUR] EmPlcProgram: Application [Device: Logique API]: C0080: Le bloc fonctionnel 'IoDrvModbusTCP' doit être instancié pour permettre l’accès [ERREUR] EmPlcProgram: Application [Device: Logique API]: C0004: 'ModbusTCPSlaveUnit_Diag' n’est pas un composant de 'IoDrvModbusTCP' Thanks in advance
Last updated: 2024-05-29
Post by mondinmr on Why SysPipeWindows is not implemented in RTE?
CODESYS Forge
talk
(Post)
This library would be very useful for IPC communications. Using a UDP socket on localhost is unpredictable, as with slightly loaded machines it does not even guarantee packet delivery locally. Using TCP creates a lot of overhead. Message named pipes would be an excellent solution for Windows RTE. On Linux, since the release of the extension package, there is no issue, as it is sufficient to develop a component. However, although now 90% of our clients understand that Linux runtimes are better in every way compared to Windows RTE, especially from the security aspect (Not in kernel space) and the issues with Windows updates, 10% stubbornly insist (sometimes for trivial commercial reasons) on using Windows. Managing IPC with circular buffers in shared memory is quite ugly, or rather really ugly and unaesthetic. In the manuals, I saw the SysPipeWindows libraries, so I decided to test them, but unfortunately, I noticed that they are not implemented for RTE devices. Technically, I could try to open them as regular files, but SysFileOpen returns 16#27 or 16#39 depending on how I set the name (direction of the slashes). Here is the code to create shared memory and named pipes. Shared memory work great, named pipes no! #ifdef Q_OS_WIN32 SECURITY_ATTRIBUTES sa; SECURITY_DESCRIPTOR sd; InitializeSecurityDescriptor(&sd, SECURITY_DESCRIPTOR_REVISION); SetSecurityDescriptorDacl(&sd, TRUE, NULL, FALSE); sa.nLength = sizeof(SECURITY_ATTRIBUTES); sa.lpSecurityDescriptor = &sd; sa.bInheritHandle = FALSE; const wchar_t* name = L"Global\\ShmTest"; HANDLE hMapFile = CreateFileMapping( INVALID_HANDLE_VALUE, NULL, PAGE_READWRITE, 0, sizeof(SharedData), name); if (hMapFile == NULL) { qCritical("Error creating shared memory"); return 1; } data = static_cast<SharedData*>(MapViewOfFile(hMapFile, FILE_MAP_ALL_ACCESS, 0, 0, sizeof(SharedData))); if (data == NULL) { qCritical("Error mapping shared memory"); return 1; } HANDLE hPipe = CreateNamedPipe( TEXT("\\\\.\\pipe\\MyPipe"), PIPE_ACCESS_DUPLEX, PIPE_TYPE_MESSAGE | PIPE_READMODE_MESSAGE | PIPE_WAIT, PIPE_UNLIMITED_INSTANCES, 1024 * 1024, 1024 * 1024, NMPWAIT_USE_DEFAULT_WAIT, &sa); if (hPipe == INVALID_HANDLE_VALUE) { qCritical("Error creating named pipe"); return -1; } if (!ConnectNamedPipe(hPipe, NULL)) { qCritical("Error connecting to named pipe"); return -1; } checkPipe(hPipe); #endif
Last updated: 2024-02-02
Post by tcarlbom on Read tag values using external program
CODESYS Forge
talk
(Post)
This is my first time posting in this forum and I am new to codesys. I am a fullstack developer and I am trying to figure out how the following. What would be the best approach to create a own/custom tag browser? Either directly in codesys ide or using a separate custom program (perhaps a winforms application). 1.a. Shall I parse the .project xml file to get a list of all tags in the project? 1b. Shall I use python scripting in codesys ide to get a list of tags? Once one have selected some tags. These tags shall be exposed to a python program which will be acting as a edge computer. It’s fine to be able to import a file. 2a. I found a library called codesys plchandler which (as I understand) acts a rest api server. Is this correct? If so, can I query the api from a custom python script, ie can query what tags exist in project and or read tag values? My research so far. From earlier projects I know that using opc ua would be perfect for this but from my opinion it’s bloating the plc since it’s resource intensive. So opc ua is not an option. Codesys automation server is neat. But I don’t want to rely on some cloud services and subscription based pricing. There seem to be several interesting codesys libraries like mqtt, tcp server and NVL sender which would help me expose plc tags. But all have a common problem. One have to manually write what tags which will be used in these function blocks. I want a similar experience like “selecting” tags in the opc ua or the codesys tracing, ie a tag browser.
Last updated: 2024-06-28
Post by s1ack on Wago PFC200 Ethernet / IoDrvEthernet Issue?
CODESYS Forge
talk
(Post)
CODESYS Control for PFC200 4.13.00 CODESYS IIoT Libraries SL 1.11.0.0 Application Based License: CODESYS Control Standard M I have (2) projects with similar code base and both using Wago PFC200. On the second project I am seeing 2 things that I have not been able to resolve: 1) Errors in the log under the Ethernet Item: IoDrvEthernet: [PCI\E1Q51CE62] Could not be found on target! Please check the Ethernet settings. 2) Exception for CPU Load. "Processorload watchdog: plcload=100, maxplcload=95" I have slowed down cyclic tasks on this project, even though on the first project there is actually more code - and it does not exhibit this behavior. In looking at the CPU loading via Linux 'TOP' command there appears to be 20% idle. So plenty of headroom (my opinion). In an effort to troubleshoot I have duplicated the target hardware on my bench. It ran overnight without a CPU load exception. On the test system, I have tried (3) version of the ethernet device. 3.5.16.0 3.5.17.0 and 4.2.0.0 Presently the log does not show the error, but status says the module reports an error. I really do not know if this issue is related to the CPU load exception. The issue does not appear to effect ethernet communications (ModbusTCP or SNMP or Webvisu or PuTTy into Linux Shell). On my test bench I have ModbusTCP slave simulators for all ModbusTCP slaves, but only (1) of the (5) SNMP devices present.
Last updated: 2025-01-21
Post by mondinmr on Direct Pointers in IOMapping for EtherCAT with IoDrvEthercatLib.ETCSlave_Dia
CODESYS Forge
talk
(Post)
I have found a very interesting solution using: IoConfigTaskMap IoConfigConnectorMap IoConfigChannelMap The first is the list of IO tasks. The second is the connector for each IO module in the IOMap. The third is the individual input or output on the IOMap. One of the properties of the connector is another pointer to a connector, which corresponds with the connector of the EtherCAT slave. Through this information, it is possible to understand to which EtherCAT slave an IO connectormap corresponds. I am attaching an FB that allows for the construction of an IO map and finding the pointer to the actual IOs in the IOMap based on the bitoffset. FUNCTION_BLOCK IOExplorer VAR_INPUT END_VAR VAR_OUTPUT END_VAR VAR inputChannels: COL.LinkedList; outputChannels: COL.LinkedList; ulintFactory: COL.UlintElementFactory; END_VAR METHOD inputAtBitOffsetOfConnector : POINTER TO BYTE VAR_INPUT conn: POINTER TO IoConfigConnectorMap; bitOffset: UDINT; END_VAR VAR it: COL.LinkedListIterator; itf: COL.IElement; elem: COL.iUlintElement; channelInfo: POINTER TO ADVChannelInfo; bitOffsetR: UDINT; END_VAR inputChannels.ElementIterator(it); WHILE it.HasNext() DO it.Next(itfElement => itf); __QUERYINTERFACE(itf, elem); {warning disable C0033} channelInfo := TO___UXINT(elem.UlintValue); {warning restire C0033} IF channelInfo^.connectorField = conn THEN IF bitOffsetR = bitOffset THEN inputAtBitOffsetOfConnector := channelInfo^.addr; RETURN; END_IF bitOffsetR := bitOffsetR + channelInfo^.size; ELSE bitOffsetR := 0; END_IF END_WHILE inputAtBitOffsetOfConnector := 0; END_METHOD METHOD outputAtBitOffsetOfConnector : POINTER TO BYTE VAR_INPUT conn: POINTER TO IoConfigConnectorMap; bitOffset: UDINT; END_VAR VAR it: COL.LinkedListIterator; itf: COL.IElement; elem: COL.iUlintElement; channelInfo: POINTER TO ADVChannelInfo; bitOffsetR: UDINT; END_VAR outputChannels.ElementIterator(it); WHILE it.HasNext() DO it.Next(itfElement => itf); __QUERYINTERFACE(itf, elem); {warning disable C0033} channelInfo := TO___UXINT(elem.UlintValue); {warning restire C0033} IF channelInfo^.connectorField = conn THEN IF bitOffsetR = bitOffset THEN outputAtBitOffsetOfConnector := channelInfo^.addr; RETURN; END_IF bitOffsetR := bitOffsetR + channelInfo^.size; ELSE bitOffsetR := 0; END_IF END_WHILE outputAtBitOffsetOfConnector := 0; END_METHOD METHOD scanIO VAR_INPUT END_VAR VAR numTasks: DINT := IoConfig_Globals.nIoConfigTaskMapCount; tType: WORD; ioTask: POINTER TO IoConfigTaskMap; numCon: WORD; connector: POINTER TO IoConfigConnectorMap; numCh: DWORD; channelInfo: POINTER TO ADVChannelInfo; iTsk: DINT; iCon: WORD; iCh: DWORD; i: DINT; _tmpConnList: COL.IList; elem: COL.IUlintElement; itf: COL.IElement; tmpCh: POINTER TO ADVChannelInfo; lastE: DINT; e: COL.COLLECTION_ERROR; e1: Error; END_VAR VAR_INST lF: COL.ListFactory; END_VAR IF outputChannels.CountElements() > 0 OR inputChannels.CountElements() > 0 THEN RETURN; END_IF _tmpConnList := lF.CreateDynamicList(16, 16); //Iterate through all IO tasks FOR iTsk := 0 TO numTasks - 1 DO ioTask := ADR(IoConfig_Globals.pIoConfigTaskMap[iTsk]); //Store the type of the task (Input or Output) tType := ioTask^.wType; numCon := ioTask^.wNumOfConnectorMap; //Iterate through all connectors of the task FOR iCon := 0 TO numCon - 1 DO connector := ADR(ioTask^.pConnectorMapList[iCon]); numCh := connector^.dwNumOfChannels; //Iterate through all channels of the connector FOR iCh := 0 TO numCh - 1 DO //Create a new channel info object and fill it with the address, connector and size of the channel //Connectors is address of field connector in this case like EtherCAT slave //Address is the address of the IOMap //Size is the size of channel data in bits in IOMap channelInfo := __NEW(ADVChannelInfo); channelInfo^.addr := connector^.pChannelMapList[iCh].pbyIecAddress; channelInfo^.connectorField := connector^.pConnector; channelInfo^.size := connector^.pChannelMapList[iCh].wSize; //We put the channel info a temporary ordered list //Order is based on the address of IOMap lastE := TO_DINT(_tmpConnList.CountElements()) - 1; FOR i := 0 TO lastE DO _tmpConnList.GetElementAt(udiPosition := TO_UDINT(i), itfElement => itf); __QUERYINTERFACE(itf, elem); {warning disable C0033} tmpCh := TO___UXINT(elem.UlintValue); {warning restire C0033} //If the address of the channel is smaller than the address of the channel in the list IF tmpCh^.addr > channelInfo^.addr THEN //Insert the channel in the list at the current position _tmpConnList.InsertElementAt(TO_UDINT(i), ulintFactory.Create(TO_ULINT(channelInfo))); //Clear the channel info pointer channelInfo := 0; //Exit the loop i := lastE + 1; END_IF END_FOR //If the channel info is not 0, it means that the channel was not inserted in the list IF channelInfo <> 0 THEN //Add the channel to the end of the list elem := ulintFactory.Create(TO_ULINT(channelInfo)); _tmpConnList.AddElement(elem); END_IF END_FOR //Iterate temporary list and add the channels to the input or output list lastE := TO_DINT(_tmpConnList.CountElements()) - 1; FOR i := 0 TO lastE DO _tmpConnList.GetElementAt(udiPosition := TO_UDINT(i), itfElement => itf); __QUERYINTERFACE(itf, elem); {warning disable C0033} tmpCh := TO___UXINT(elem.UlintValue); {warning restire C0033} //If type is input, add the channel to the input list IF tType = TaskMapTypes.TMT_INPUTS THEN e := inputChannels.AddElement(ulintFactory.Create(TO_ULINT(tmpCh))); //If type is output, add the channel to the output list ELSIF tType = TaskMapTypes.TMT_OUTPUTS THEN e := outputChannels.AddElement(ulintFactory.Create(TO_ULINT(tmpCh))); ELSE __DELETE(tmpCh); END_IF END_FOR //Clear the temporary list _tmpConnList.RemoveAllElements(); END_FOR END_FOR END_METHOD
Last updated: 2024-02-13
Post by george32 on Readable IO names
CODESYS Forge
talk
(Post)
Hello Folks, I have a quite basic understanding of how PLC programming works. However I keep getting stuck on 1 problem I could not get my head around. The problem is as follow: I have a PLC with 60 IO (20 inputs, 40 outputs). Each IO is defined as a function block. Furthermore I have an external IO card connected trough a CanBus connection. This IO card has 4 analog input channels (USINT), 4 digital inputs (Bool) and 4, digital outputs (Bool) Because I have 2 different components which both has data have I made 4 arrays to store the data off every component in one variable. PLC_Input: Array [1..20] of BOOL; PLC_Output: Array [1..40] of BOOL IOCard_Input: Array [1..8] of BOOL IOCard_Output: Array [1..4] of BOOL Because the control and reading of the different in and outputs is done by a TCP connection I want to use some kind of enumeration or struct to give each index a name so that my main would be a little bit more readable instead of all the magic numbers. Also this would make my program more dynamic for the furter in case I need to changes some in the IO nummers. For example: pump is placed on the fysical terminal strip number place 54, which is the 3th output of the IO card in the program: if I am sending a message with value 54 I would like to control IOCard_Output[3]. If there is a solution or methode to get this done, I can eventually do the following in my main program: IOCard_Output[Pump]. I have tried the following: IOCard_Output[Pump - 51] with an enumration but this keeps raising an error I hope some of you could help me further with this problem. In gross lines: I want to couple all the different IO to a more readable name and this readable name should control the right Array index Thanks in advance, George
Last updated: 2024-09-26
Post by jari-koivuluoma on Problem trying Net Base Services 3.5.15.0 TCP connection
CODESYS Forge
talk
(Post)
I have a need to send messages between 2 PLCs and I cant use network variables (because of size limit) so I tried writing this simple test program. This seems to work fine. I can send messages back and forth when a first "Start server" and then "Connect client". See the attached image. However, if I disconnect the client by setting ClientConnect to false and try to re-connect then the TCP_Client just gives me TIMEOUT error. When I stop and start the server again, then Im able to reconnect. How is this supposed to work? Why reconnecting wont work. There is not other way of disconnecting the client than setting xEnable of the TCP_Client to false. This is just a testing program and I will try it on 2 seperate devices once this works. PROGRAM PLC_PRG VAR CONSTANT mySize : UDINT := 255; END_VAR VAR Server: NBS.TCP_Server; ServerIpStr: STRING := '127.0.0.1'; ServerIP: NBS.IP_ADDR; ServerPort: UINT := 50000; ServerConnection: NBS.TCP_Connection; Client: NBS.TCP_Client; ServerRead: NBS.TCP_Read; ServerWrite: NBS.TCP_Write; ServerSend: STRING(mySize); ServerReceive: STRING(mySize); ServerConnect: BOOL; bServerSend: BOOL; IP: NBS.INADDR; ConnectedClientIP: STRING; ClientPort: UINT := 50000; ClientIpStr: STRING := '192.168.1.49'; ClientIP: NBS.IP_ADDR; ClientRead: NBS.TCP_Read; ClientWrite: NBS.TCP_Write; ClientSend: STRING(mySize); ClientReceive: STRING(mySize); ClientConnect: BOOL; bClientSend: BOOL; Error: BOOL; Message: BOOL; END_VAR // Server ServerIP.sAddr := ServerIpStr; Server( ipAddr := ServerIP, uiPort := ServerPort ); ServerConnection( xEnable := Server.xEnable, hServer := Server.hServer, ); IP := ServerConnection.IPAddress; ConnectedClientIP := F_Concat7( BYTE_TO_STRING(IP.S_un_b.s_b1),'.', BYTE_TO_STRING(IP.S_un_b.s_b2),'.', BYTE_TO_STRING(IP.S_un_b.s_b3),'.', BYTE_TO_STRING(IP.S_un_b.s_b4)); ServerRead( xEnable := ServerConnection.xActive, hConnection := ServerConnection.hConnection, szSize := SIZEOF(ServerReceive), pData := ADR(ServerReceive) ); IF ServerRead.xReady AND ServerRead.szCount > 0 THEN Message := TRUE; END_IF IF ServerRead.eError > 0 THEN Error := TRUE; END_IF ServerWrite( xExecute := ServerConnection.xActive AND bServerSend, hConnection := ServerConnection.hConnection, szSize := LEN(ServerSend)+1, pData := ADR(ServerSend) ); IF ServerWrite.xDone THEN bServerSend := FALSE; END_IF IF ServerWrite.eError > 0 THEN Error := TRUE; END_IF // Client ClientIP.sAddr := ClientIpStr; Client( xEnable := ClientConnect, ipAddr := ClientIP, uiPort := ServerPort, udiTimeOut := 10000000 ); ClientRead( xEnable := Client.xActive, hConnection := Client.hConnection, szSize := SIZEOF(ClientReceive), pData := ADR(ClientReceive) ); IF ClientRead.xReady AND ClientRead.szCount > 0 THEN Message := TRUE; END_IF IF ClientRead.eError > 0 THEN Error := TRUE; END_IF ClientWrite( xExecute := Client.xActive AND bClientSend, hConnection := Client.hConnection, szSize := LEN(ClientSend)+1, pData := ADR(ClientSend) ); IF ClientWrite.xDone THEN bClientSend := FALSE; END_IF IF ClientWrite.eError > 0 THEN Error := TRUE; END_IF