Post by jp23 on Unable to Connect to Modbus RTU Device
CODESYS Forge
talk
(Post)
Hi all, I am attempting to use the Control Win V3 soft PLC to control a WAGO 750-315 remote I/O system via modbus RTU communication. I am struggling to connect to the device. I have been following this tutorial: https://www.youtube.com/watch?v=YlRfkESaNds I have setup my devices as shown in the images below. I have verified that my com port settings are correct as I am able to connect/control using modbus simulator software with these settings. I have also connected to a modbus master simulator program as instructed in the video, but the orange triangles will not go away. Additionally, I have updated my settings to 485 using the PLC shell. I have also set "always update variables" to enabled (1). Serial port, PCI-Bus, and modbus serial device status all show as "Not Running."
Last updated: 2024-08-26
Post by jp23 on Unable to Connect to Modbus RTU Device
CODESYS Forge
talk
(Post)
Hi all, I am attempting to use the Control Win V3 soft PLC to control a WAGO 750-315 remote I/O system via modbus RTU communication. I am struggling to connect to the device. I have been following this tutorial: https://www.youtube.com/watch?v=YlRfkESaNds I have setup my devices as shown in the images below. I have verified that my com port settings are correct as I am able to connect/control using modbus simulator software with these settings. I have also connected to a modbus master simulator program as instructed in the video, but the orange triangles will not go away. Additionally, I have updated my settings to 485 using the PLC shell. I have also set "always update variables" to enabled (1). Serial port, PCI-Bus, and modbus serial device status all show as "Not Running."
Last updated: 2024-08-26
Post by jp23 on Unable to Connect to Modbus RTU Device
CODESYS Forge
talk
(Post)
Hi all, I am attempting to use the Control Win V3 soft PLC to control a WAGO 750-315 remote I/O system via modbus RTU communication. I am struggling to connect to the device. I have been following this tutorial: https://www.youtube.com/watch?v=YlRfkESaNds I have setup my devices as shown in the images below. I have verified that my com port settings are correct as I am able to connect/control using modbus simulator software with these settings. I have also connected to a modbus master simulator program as instructed in the video, but the orange triangles will not go away. Additionally, I have updated my settings to 485 using the PLC shell. I have also set "always update variables" to enabled (1). Serial port, PCI-Bus, and modbus serial device status all show as "Not Running."
Last updated: 2024-08-26
Post by jp23 on Unable to Connect to Modbus RTU Device
CODESYS Forge
talk
(Post)
Hi all, I am attempting to use the Control Win V3 soft PLC to control a WAGO 750-315 remote I/O system via modbus RTU communication. I am struggling to connect to the device. I have been following this tutorial: https://www.youtube.com/watch?v=YlRfkESaNds I have setup my devices as shown in the images below. I have verified that my com port settings are correct as I am able to connect/control using modbus simulator software with these settings. I have also connected to a modbus master simulator program as instructed in the video, but the orange triangles will not go away. Additionally, I have updated my settings to 485 using the PLC shell. I have also set "always update variables" to enabled (1). Serial port, PCI-Bus, and modbus serial device status all show as "Not Running."
Last updated: 2024-08-26
Post by jp23 on Unable to Connect to Modbus RTU Device
CODESYS Forge
talk
(Post)
Hi all, I am attempting to use the Control Win V3 soft PLC to control a WAGO 750-315 remote I/O system via modbus RTU communication. I am struggling to connect to the device. I have been following this tutorial: https://www.youtube.com/watch?v=YlRfkESaNds I have setup my devices as shown in the images below. I have verified that my com port settings are correct as I am able to connect/control using modbus simulator software with these settings. I have also connected to a modbus master simulator program as instructed in the video, but the orange triangles will not go away. Additionally, I have updated my settings to 485 using the PLC shell. I have also set "always update variables" to enabled (1). Serial port, PCI-Bus, and modbus serial device status all show as "Not Running."
Last updated: 2024-08-26
Post by timvh on Dynamically enabling/disabling Modbus slave devices in runtime (performance issue with timeouts)
CODESYS Forge
talk
(Post)
As far as I remember, the Reconfigure functionality doesn't work for Modbus devices. But... Each Modbus device in your device tree has a name. You can set the property "Enable" of this device to FALSE to stop communicating with it. So if one of your Modbus Slave devices name is "MbSlave1" in the device tree, then in your code you can set the Enable to FALSE to let it stop communicating: MbSlave1.Enable := FALSE; Please let us know if this worked on your controller with your application and your CODESYS version. Alternatively you could use the ModbusFB library. See: https://forge.codesys.com/prj/codesys-example/modbus/home/Home/
Last updated: 2025-08-13
Post by expertplas on No connection to opc server from codesys opc client
CODESYS Forge
talk
(Post)
Hello, we have aproblen to connect our CODESYS OPC Client to the OPC Server. We installed the client according the CODESYS manual. We can browse the server and variables can be linked to the PLC. I created a self signed certificate for the CmpOPCUAClent as described. The server has a cerificate also. I copied the certificates to the trusted zone of server and client. But when it comes to data exchange we get an error message. "Communication error in data source OPC UA Library. Error ID : 7001 German : "Kommunikatinsfehler inder Datenquelle OPC UA -Bibiothek. Es wurde kein genauer Fehler angegeben. Fehler ID : 7001" It semms that there is no cerificate exchange. We are working with CODESYS 3.5 SP19 Patch 5. Can anyone here say something about this error or has an idea for a solution? Thanks.
Last updated: 2024-08-19
Post by sigurdrb on OPC server in "Communication manager"
CODESYS Forge
talk
(Post)
Hi! I was thinking of switching the OPC server config from "Symbol Configuration" to the "Communication manager" in the device tree. I Have a lot of arrays of structs that I have previously declared in the "Persistent Variable" object in the device tree. It seems as it is not supported to directly expose persistant variables to the OPC server like the "older" way of doing it in the symbol config. Is this correct? Do you recommend to just do it the old fashioned way, or should I edit the structure of the global variable list / persistant data / OPC server and set up the OPC server from the "Communication manager" object?
Last updated: 2025-01-20
Post by alexgooi on Codesys virtual control redundancy
CODESYS Forge
talk
(Post)
Dear Forum, I’m currently investigating the possibilities of Codesys virtual control (Linux). The research rig consists of a PC (Debian with real time kernel) with a docker server installed on it. The PC is communicating with a Remote I/O and I have to say the performance is great. The process in the container is running (soft) real time. Currently I’m checking if it is possible to replace physical controllers by remote I/O’s and run the Codesys applications on a docker server. If I’m going into this route the reliability of the server is very important (server down, complete installation down), is it possible to make the server redundant without needing 2 separate containers (including licenses), and maintaining the real time behavior? I’m not only expecting direct answers, if you have any idea or thought they are very welcome. Kind regards Alex
Last updated: 2025-09-03
Post by snhatton on OpC UA server on Raspberry Pi 64 SL runtime
CODESYS Forge
talk
(Post)
Good afternoon, After changing the security settings to: CommunicationPolicy: POLICY_BASICSHA256SHA256 CommunicationMode: ALL Activation: Activated UserAuthentication: ENABLED Then generate a new certificate on the device for the OPC-UA server from Security Agent->Device->OPC UA Server. Restart the runtime using tools->Update Raspberry Pi->Stop->Start for the changes to take effect. It may take a minute for the runtime to start. Initiate the connection from the UA server side. You should see a pop-up asking you to trust the certificate. Click on the button 'Trust Server Certificate'. Next, you should see a certificate in the quarantined folder of the security agent in CODESYS. Click and drag this from quarantined to trusted and then try connecting from UA expert to the device. These steps worked for me and my setup and I hope they can help you!
Last updated: 2023-12-11
Post by simover on TCP/IP client
CODESYS Forge
talk
(Post)
HELLO thank for you answer!! I'm a beginner can you give me an example?
Last updated: 2023-12-19
Post by kuegerls on OpC UA server on Raspberry Pi MC SL - Certificate Issue
CODESYS Forge
talk
(Post)
Hello, I have set up an OPC UA server following several guides, including this one: https://revolutionpi.com/documentation/tutorials/opc-ua-codesys-nodered/. The license for the runtime is installed on the device. However, I am unable to create a certificate for the OPC UA server in the security screen. I always get the error message: "The certificate has not been created by the device." Does anyone have an idea what might be causing this issue? Any help would be greatly appreciated! Thanks in advance! Best regards, Stefan
Last updated: 2025-04-02
Post by timl on BacNet Server
CODESYS Forge
talk
(Post)
Hallo, für einen BacNet2 Server lassen sich mit zwei Ethernet Schnittstellen auch zwei Bacnet 2 IP Datalinks anlegen. Einen Datalink nutze ich für den UDP Port 47808 und einen für den UDP Port 47809. Dadurch ist der Server aus beiden Netzwerken erreichbar, was so gewollt ist. Allerdings verbindet er die beiden Netze auch miteinander, was zu Kommunikationsproblemen führt, da in beiden Netzwerken bereits gleiche Device ID's vergeben sind und diese sich dann doppeln. Lässt sich diese Verbindung der beiden Netze abschalten? Gruß Tim
Last updated: 2024-02-20
Post by miodusy on File transfer via visu and codesys automation server
CODESYS Forge
talk
(Post)
I have a problem with the file transfer library. Namely, it does not work via the codesys server. (error 5; overtime, and visualization resets). They operate mostly in local chains. I tested different browsers and VPN from the router. It works everywhere, except through access from the codesys automation server. The client, having many machines under one account, prefers to keep it that way rather than use an individual VPN just to download a backup. Does anyone have an idea what the problem is? Sylwester M.
Last updated: 2024-03-07
Post by yannickasselin on codesys VLAN tagging
CODESYS Forge
talk
(Post)
I ordered a cheap managed switch and tested it as soon as I received the switch. It works great! I even went a bit further. As you can see in the screenshot, I created 2 Codesys containers. Each one having 2 fieldbuses. The first one has EtherCAT and EtherNet/IP and the second one has EtherCAT and Modbus/TCP. All going through the same ethernet port from the PC to the switch. The switch splits it up into 4 different networks. The hardest part was to figure out how to configure the switch. @eschwellinger, thank you very much.
Last updated: 2024-09-17
Post by timvh on Modbus TCP & RTU with Control for Linux SL
CODESYS Forge
talk
(Post)
It seems you have 2 network interfaces. Did you try eth1? Did you already configure the IP address for this interface in Linux? If yes, then maybe undo this. - or only set eth0 in the Nic configuration without anything else (so no IP address, because this is already set in Linux). For more information about the Nic settings, see (probably already read it?): https://content.helpme-codesys.com/en/CODESYS%20Control/_rtsl_obj_deploy_control_sl_configuration.html PS, if you only want to run CODESYS Control SL, you don't necessarily need the Virtual PLC variant. You could also install and run the CODESYS Control SL Runtime in the Host operating system. This way you should also be able to access the serial port and directly access all ethernet ports. Maybe this is easier?
Last updated: 2024-10-23
Post by brell on Automatic xExecute NBS.TCP_write
CODESYS Forge
talk
(Post)
I've recently started experimenting with CODESYS for a project and am fairly new to it. I'm currently working with Function Block Diagrams (FBD) to set up TCP communication between a server and a client, where the client is implemented as a Python script. Once the communication is established, my connection status changes to True, which is the expected behavior. My challenge arises with the TCP write module, which requires the xEnable_write flag to toggle between True and False. If xEnable_write remains True, the module only performs a single write operation. To address this, I introduced a falling edge trigger (F_TRIG), expecting it to help in toggling xEnable_write and it does, However, I've encountered an issue where in the beginning after connxion established I need to manually set xEnable_write to True for the system to work as intended. I'm looking for a way to automate this process so that xEnable_write becomes True automatically upon establishing a connection . Initially, I tried setting xEnable_write to True from the start, but this approach didn't work well since it left the flag permanently True, preventing further toggling. I also experimented with using a TON timer, but I faced similar issues. I am seeking a solution that automatically toggles xEnable_write between True and False after a connection is established, ensuring continuous write operations without manual intervention. Any advice or guidance on how to achieve this would be greatly appreciated."
Last updated: 2024-03-05
Post by shrikantp007 on new to codesys help on modbus with ardunio modbus rtu
CODESYS Forge
talk
(Post)
Hello , I am new to codesys ,working with it for just 15-17 days so ,i think i am able to installed it and configure it ,not i want to use ardunio program (smart dustbin ,college project using motor and Ultrasonic Module HC-SR04 and servo motor). i use ardunio program to write code with chatgpt to work ardunio as a modbus rtu as i dont have ethernet or wifi shild ,i wrote program in ariduno but now don have idea what change i have to make in codesys to comunicate as modbus slave it give error with bus error ,where i can get all errors ? Thanks in advance :)
Last updated: 2024-07-21
Post by mystx on Timeout Error in Modbus Communication with WAGO PFC200 and iEM2050 Meter using 750-652 Module
CODESYS Forge
talk
(Post)
Hello I have the same problem, anyone have some idea?? Regards
Last updated: 2024-07-30
Post by mystx on Timeout Error in Modbus Communication with WAGO PFC200 and iEM2050 Meter using 750-652 Module
CODESYS Forge
talk
(Post)
Hello I have the same problem, anyone have some idea?? Regards
Last updated: 2024-07-30
Post by mystx on Timeout Error in Modbus Communication with WAGO PFC200 and iEM2050 Meter using 750-652 Module
CODESYS Forge
talk
(Post)
Hello I have the same problem, anyone have some idea?? Regards
Last updated: 2024-07-30
Post by thysonfury on OPTO22 Groov Epic PR2 Modbus Comms Dropping out every 2 hours and 4 Mins
CODESYS Forge
talk
(Post)
OPTO22 Codesys Activation license not active.
Last updated: 2024-09-11
Post by zdenekkrejci on Issues with Modbus Slave with Raspberry Pi
CODESYS Forge
talk
(Post)
Did you find out what was wrong? I have the same issue
Last updated: 2025-03-09
Post by zdenekkrejci on Issues with Modbus Slave with Raspberry Pi
CODESYS Forge
talk
(Post)
Did you find out what was wrong? I have the same issue
Last updated: 2025-03-09
Post by eschwellinger on ModbusTCP RaspberryPi zu Fronius Wechselrichter
CODESYS Forge
talk
(Post)
Schreibe den Slavename(der vom Gerätebaum) in ein Watchfenster dann siehst du Instanz des Modbus Slave Fb's und hast dadurch Diagnose Info
Last updated: 2025-07-04