Post by smeitink on Timeout Error in Modbus Communication with WAGO PFC200 and iEM2050 Meter using 750-652 Module
CODESYS Forge
talk
(Post)
Hi all, I'm looking for help with an issue I've come across while trying to facilitate Modbus communication between a WAGO PFC200 PLC using a 750-652 communication module and an iEM2050 Series Single Phase Energy Meter. I believe to have everything wired and setup correcty, but I keep running into a "Error time out" message, and by now I don't really know what else to try. My setup is as follows: A PFC200 Wago PLC, which has 2 750-652 Serial Interfaces extension modules connected to its field bus. I'm using one of these to talk to a Schneider iEM2050 - kWh-meter over modbus. I have connected terminal 23 (A) of the iEM2050 to connector 6 (A) on the 750-652. I have connected terminal 24 (B) of the iEM2050 to connector 2 (B) of the 750-652. I'm using 200mm of twisted together wires to connected them both, and I have placed a 120 ohm resistor between A and B at both ends. I've attached relevant pinout images to this post. I then wrote a simple program that configures the Mobus port, as per the datasheet of the iEM2050. You can find an image of the relavent page attached to this post too. This is my program: PROGRAM PLC_PRG VAR Master: FbMbMasterSerial; xIsConnected: BOOL; xError: BOOL; iIndex: INT := 1; xTrigger: BOOL; utQuery : typMbQuery := ( bUnitId := 1, // The Modbus unit or slave address bFunctionCode := 4, // Function code for reading input registers uiReadAddress := 1829, // adress for the Power on off counter uiReadQuantity := 1 // Quantity of registers to read ); iStep: INT; oStatusModbus: WagoSysErrorBase.FbResult; utResponseModbus: typMbResponse; xConnect: BOOL := FALSE; delayTimer: TON; END_VAR Master( xConnect:= xConnect, I_Port:= _750_652_24_1, udiBaudrate:= 9600, usiDataBits:= 8, eParity:= WagoTypesCom.eTTYParity.Even, eStopBits:= WagoTypesCom.eTTYStopBits.One, eHandshake:= WagoTypesCom.eTTYHandshake.None, ePhysical:= WagoTypesCom.eTTYPhysicalLayer.RS485_HalfDuplex, xIsConnected=> xIsConnected, xError=> xError, oStatus=> oStatusModbus, eFrameType:= WagoAppPlcModbus.eMbFrameType.RTU, tTimeOut:= T#5S, utQuery:= utQuery, xTrigger:= xTrigger, utResponse:= utResponseModbus); delayTimer(IN := TRUE, PT := T#3S); // Use the Q output of the timer to set xConnect after the delay IF delayTimer.Q THEN xConnect := TRUE; END_IF CASE iStep OF 0: //Wacht totdat de master de poort geopend heeft IF xIsConnected THEN iStep := 1; END_IF 1: //Stuur request naar de slave xTrigger := TRUE; iStep := 2; 2: //Wacht totdat de master klaar is met het afhandelen van de request IF NOT xTrigger THEN iStep := 3; END_IF END_CASE The TON delay before opening the port is due to a an error I encountered when opening it straight away. This seems to be a bug, as described here. However, the TON solved that particular issue. I tried reading multiple registers, but like I said, I still always end up with the "Error time out". What else can I test or try at this point?
Last updated: 2024-02-24
Post by alexgooi on Modbus writing on value change
CODESYS Forge
talk
(Post)
The way I usally tackle this is by syncing only words (then you are able to use the FB above). If you then want to write a Boolean simply type it like this. Value[1].0 := Bool1; Value[1].1 := Bool2; Value[1].2 := Bool3; Uints have the same number of bits than a INT/WORD so these ones will work as well (they are only represented diffrently). A Real will work but you will loose some infomration in the conversion. If you want to keep the information you can convert 2 words to a float with a function (for example with the IEEE-754 standard) . In this way the syncing to the server is very simple and in the Codesys Program you decide what part of the word you want to use.
Last updated: 2024-04-03
Post by paro on Modbus Client Request Not Processed
CODESYS Forge
talk
(Post)
Hi, works in my case if I increase the timeout! to_udint(t#100ms) -> 100 -> 100us.. FUNCTION_BLOCK MODBUS_master_example_ST VAR initDone : BOOL := FALSE; aIPAddress : ARRAY [0..3] OF BYTE := [127,0,0,1]; clientTcp: ModbusFB.ClientTcp; // buffer to read input registers aDataInputRegisters : ARRAY[0..9] OF UINT; // some client requests clientRequestReadInputRegisters: ModbusFB.ClientRequestReadInputRegisters; xExecute: BOOL; uistart: UINT := 100; udiTimeout1: UDINT; END_VAR IF NOT initDone THEN initDone := TRUE; // configure clientTcp clientTcp(aIPaddr:=aIPAddress, uiPort:=502, udiLogOptions := ModbusFB.LoggingOptions.All); // configure clientRequestReadInputRegisters clientRequestReadInputRegisters(rClient:=clientTcp, uiUnitId:=1, udiTimeout:=1000000); // 1sec END_IF // call the client FB's clientTcp(); clientRequestReadInputRegisters(rClient:=clientTcp,xExecute := xExecute AND NOT clientRequestReadInputRegisters.xBusy ,uiStartItem:=uistart, uiQuantity:=3, pData:=ADR(aDataInputRegisters[0]));
Last updated: 2024-05-30
Post by zer0g on Modbus Client Request Not Processed
CODESYS Forge
talk
(Post)
I'm using the code bellow which is based on the Codesys example: FUNCTION_BLOCK MODBUS_master_example_ST VAR initDone : BOOL := FALSE; aIPAddress : ARRAY [0..3] OF BYTE := [127,0,0,1]; clientTcp: ModbusFB.ClientTcp; // buffer to read input registers aDataInputRegisters : ARRAY[0..9] OF UINT; // some client requests clientRequestReadInputRegisters: ModbusFB.ClientRequestReadInputRegisters; xExecute: BOOL; END_VAR IF NOT initDone THEN initDone := TRUE; // configure clientTcp clientTcp(aIPaddr:=aIPAddress, uiPort:=502, udiLogOptions := ModbusFB.LoggingOptions.All); // configure clientRequestReadInputRegisters clientRequestReadInputRegisters(rClient:=clientTcp, uiUnitId:=1, udiTimeout:=TO_UDINT(T#1000MS)); END_IF // call the client FB's clientTcp(); clientRequestReadInputRegisters(rClient:=clientTcp,xExecute := xExecute AND NOT clientRequestReadInputRegisters.xBusy ,uiStartItem:=2, uiQuantity:=3, pData:=ADR(aDataInputRegisters[0])); As you can see the clientTCP is called cyclically with the same result.
Last updated: 2024-05-30
Post by shrikantp007 on help to get codesys understand
CODESYS Forge
talk
(Post)
Hello , I need some help on how to start with , 1) how to get test license to test codesys , 2) how to take a configuration backup or running process back and post file on fourm so people can understand and deploy same file and get idea what is missing or configure wrong 3) where i can get pdf for codesys admin or programmer 4) what is hardware recommand ,i am running on windows guest on kvm server .is it ok ? 5) i am trying to get ardunio porject working ,using ardunio board as a modbus slave but its not working some how https://forge.codesys.com/forge/talk/Engineering/thread/bf832569b8/ Thanks in advance . shrikant pune -india
Last updated: 2024-07-22
Post by yannickasselin on codesys VLAN tagging
CODESYS Forge
talk
(Post)
I ordered a cheap managed switch and tested it as soon as I received the switch. It works great! I even went a bit further. As you can see in the screenshot, I created 2 Codesys containers. Each one having 2 fieldbuses. The first one has EtherCAT and EtherNet/IP and the second one has EtherCAT and Modbus/TCP. All going through the same ethernet port from the PC to the switch. The switch splits it up into 4 different networks. The hardest part was to figure out how to configure the switch. @eschwellinger, thank you very much.
Last updated: 2024-09-17
Post by timvh on Modbus TCP & RTU with Control for Linux SL
CODESYS Forge
talk
(Post)
It seems you have 2 network interfaces. Did you try eth1? Did you already configure the IP address for this interface in Linux? If yes, then maybe undo this. - or only set eth0 in the Nic configuration without anything else (so no IP address, because this is already set in Linux). For more information about the Nic settings, see (probably already read it?): https://content.helpme-codesys.com/en/CODESYS%20Control/_rtsl_obj_deploy_control_sl_configuration.html PS, if you only want to run CODESYS Control SL, you don't necessarily need the Virtual PLC variant. You could also install and run the CODESYS Control SL Runtime in the Host operating system. This way you should also be able to access the serial port and directly access all ethernet ports. Maybe this is easier?
Last updated: 2024-10-23
Post by ben1 on How to write multiple coils (Modbus FC15)
CODESYS Forge
talk
(Post)
If I am understanding what you are saying, then yes that would be your problem. I would create an array of bools on the client side for the transfer and try that. Or if client can't be changed then use words on server and unpack. But I am not sure if you or I are mis interpreting but it sounds a bit jumbled. I don't know what you have control of, but, if you are turning on BITS in the server, you should write to BITS in the client with a Function 15. If you are writing to WORDS in the server, you should write to WORDS in the client with a Function 16.
Last updated: 2024-11-17
Post by ihatemaryfisher on Sorting array of any-sized structure
CODESYS Forge
talk
(Post)
With that I could make an array of varying size, but would still have to define the array type in the function's declaration VAR_IN_OUT stArray: array [*..*] of <pre-defined data type> END_VAR I wanted a function that could take an array of any type (e.g., a structured VAR) as an input. That way I could call it in multiple POUs to handle different arrays structures.
Last updated: 2023-08-18
Post by docker on Canopen connection. Unknown node id.
CODESYS Forge
talk
(Post)
hi, i am currently trying to adapt an i/o device for a project. the node id is unknown and there is no eds file available. no data is being emitted from the device as a giveaway, the baudrate is known but useless without the node id. is there an sdo request available to determine the id? i cannot get the device to leave pre op status even with a global nmt request. please help. no hair left.
Last updated: 2023-09-25
Post by timvh on Specify Input Configuration "OnDialogClosed" Action to only react to certain Dialogs
CODESYS Forge
talk
(Post)
What maybe helps is the Visu Dialog ST demo project: https://store.codesys.com/en/visu-dialog-st.html This has an application IECOpenDialog where dialogs are opened using the VU.FbOpenDialogExtended function blocks. The fbOpenConfigurationDialog call has a reference (interface) to the "close listener" FB of which it's method is automatically called when the dialog is closed. This way you can create specific function blocks for each dialog when it is closed and do what you want with the data that might have been changed.
Last updated: 2023-09-28
Post by voffi on Converting UINT into bytes and converting 2Bytes into UINT
CODESYS Forge
talk
(Post)
There are some ways. One is to use SHR and SHL and it depends on your byte order in the data array. For Motorola byte order: PROGRAM PLC_PRG VAR u : UINT; byte_array_in : ARRAY [1..8] OF BYTE := [16#11, 16#12, 16#13, 16#14, 16#15, 16#16, 16#17]; byte_array_out : ARRAY [1..8] OF BYTE; END_VAR u := SHL(TO_UINT(byte_array_in[2]), 8) + TO_UINT(byte_array_in[1]); byte_array_out[1] := TO_BYTE(u); byte_array_out[2] := TO_BYTE(SHR(u, 8)); If it's Intel byte order just change 1 and 2 in the array indexes.
Last updated: 2023-12-07
Post by tvm on VisuFbFrameBase.SetInputPositionData: The element id for the input position cannot be determined
CODESYS Forge
talk
(Post)
I'm getting this error on one of my projects. Searching for it I came across this https://www.codesys.com/fileadmin/data/Images/System/Releaseinformation/Patch-Note-CODESYS-Visualization-4300.html which says it was a bug VIS-1394, fixed in Visualization 4.3.0.0. I'm using a previous visu version, what is the cause of this error, and what can be done to work around it?
Last updated: 2024-02-08
Post by dagsupport on CAA SerialCOM - hCom Reset max value 1023
CODESYS Forge
talk
(Post)
Hi everybody We are currently working on a project with an RS232 serial COM interface and using the CAA SerialCOM library. We have it working fine reading and writing data, although we have found an issue we cannot resolve and any suggestions would be helpful. We have noticed that after a while the RS232 stops working. We have tracked this down to the HANDLE hCom keeps increasing and when this reaches 1023 the COM returns an unknown error "5003". Is there a way to reset this hCom reference? Thanks Richard
Last updated: 2024-03-22
Post by alez on CANOpen SDO to write VISIBLE STRING
CODESYS Forge
talk
(Post)
Hello, I am experiencing difficulties in configuring a CANopen device by sending SDOs. In particular I am attempting to write an Object Dictionary that has VISIBLE STRING as the Data Type. When I try to configure the sending of an SDO from Codesys to configure this parameter I am not allowed to enter a string value. In my particular case I am trying to change the Manufacturer Device Name ( Index 0x1008 ). Could it be that Codesys doesn't manage these types of variables?
Last updated: 2024-04-29
Post by hjohnson123 on Automatically selecting a visualization element
CODESYS Forge
talk
(Post)
I'm looking to automatically select a text field element in my visualization. I'm not sure if this is possible, as I don't know how to get the data on specific elements. I am wanting automatic selection of the text field, as I am using a keyboard-input barcode scanner, which should always input the barcode into the text field whenever a barcode is scanned. Does anyone know if this can be done?
Last updated: 2024-05-21
Post by ndzied2 on Rounding error in simple addition
CODESYS Forge
talk
(Post)
This is a consequence of how computers store floating point numbers. 0.1 cannot be exactly represented in a computer. This is not a CoDeSys thing. Here is a link to a converter to show you the exact value that is represented when you use a REAL data type (which is a 32 bit float). https://baseconvert.com/ieee-754-floating-point If you really need to keep track of 0.1 increments. use INT OR DINT and then add 1 each time and assume that there is one decimal place.
Last updated: 2024-05-24
Post by liamb on Converting CANbus to Decimal from signed 2's complement
CODESYS Forge
talk
(Post)
I need to combine two 8 bit CANbus messages to 16 bits signed int then convert to decimal Decimal from signed 2's complement. I've been using the below code to read for new messages, combine them then assign them to a variable What is the best way to do this for from signed 2's complement? fbRxMessage351(Data := RxMessage351Data); IF fbRxMessage351.NewMessage THEN ChargeVoltage := (WORD_TO_REAL((RxMessage351Data[0]) + ((RxMessage351Data[1]) * 256))) * 0.1; END_IF
Last updated: 2024-08-16
Post by egau on Mutate Hash table value
CODESYS Forge
talk
(Post)
Hi, using the ElementCollections Library, why isn't it possible to mutate a value found within a HashTable? From what I understand, the only way to change a value would be to use the RemoveByKey(), followed by AddKeyValuePair(). My goal is to use a Data Structure that works like a Dictionary in Python. The HashTable seems to come close to this, except that the values themselves seem to be immutable... In python, we can mutate a dict easily (see attached picture).
Last updated: 2024-08-29
Post by gustavocsw on MQTT memory leak problem
CODESYS Forge
talk
(Post)
Hello everyone, I'm using the IoT Library to implement the MQTT communication with my local broker server in order to publish and subscribe at specifics topics to share and consume information about my application. But, it seems that are occurring some memory leak problem in a "high" frequency (more than 10 Hz) subscribe process. I follow the same method as in IoT Lib exemples, and at first looks perfect but my PLC was rebooting frequently and when I check its memory usage that was increasing as fast as the subscribe massage was sent. I'm using a WEG PLC410 and a WEG PLC500, and this error occurred in both of them (including in CODESYS Control Win x64). The application sends to the system a message JSON with the float payload Ex. {"data" : 0.8500}, but this happens with a INT, or BOL as well. I use the follow code in my application to find the value: //FindFirstValueByKey VARs PROGRAM JSON_VELO VAR //------Setting the JSON Subscriber to Set the Relay Value jsonDataVelo : JSON.JSONData; jsonByteArrayReaderVelo : JSON.JSONByteArrayReader; xST1okVelo : BOOL; FindFirstValueByKeyVelo : JSON.FindFirstValueByKey; jsonElementVelo : JSON.JSONElement; xDoneReaderVelo : BOOL; xDoneFindVelo : BOOL; //STRING and WSTRING for Subscribe the massage sPayloadJsonVelo : STRING := 'opa'; psPayloadJsonVelo : POINTER TO BYTE := ADR(sPayloadJsonVelo); //wsPayloadJsonRelaySet : WSTRING := "opa"; wsPayloadJsonVelo : WSTRING := STRING_TO_WSTRING('opa'); pwsPayloadJsonVelo : POINTER TO WORD := ADR(wsPayloadJsonVelo); lrVelo : LREAL; xKeepAliveVelo : BOOL; xSetVelo : BOOL; RSSet : RS; LIMPAR : STRING; //Find the msg end sFindVelo : STRING := '}'; psFindVelo : POINTER TO STRING := ADR(sFindVelo); iLenVelo : INT; iSizeVelo : INT := 12; udiContMsg : UDINT; END_VAR // FindFirstValueByKey CODE // Relay Set configuration xSetVelo := MQTT_SUBSCRIBER.RSVelo.Q1; IF xSetVelo THEN xKeepAliveVelo := TRUE; END_IF IF xKeepAliveVelo THEN udiContMsg := udiContMsg + 1; iLenVelo := TO_INT(StrLenA(psPayloadJsonVelo)); iSizeVelo := iLenVelo - TO_INT(MQTT_SUBSCRIBER.udiPayloadSizeVelo); StrDeleteA(psPayloadJsonVelo,iSizeVelo,iLenVelo); wsPayloadJsonVelo := STRING_TO_WSTRING(sPayloadJsonVelo); pwsPayloadJsonVelo := ADR(wsPayloadJsonVelo); //MQTT.ConvertUTF8toUTF16(sourceStart:= ADR(sPayloadJsonVelo), targetStart:= ADR(wsPayloadJsonVelo), dwTargetBufferSize:= TAM, bStrictConversion:= 1); //Reset jsonByteArrayReader jsonByteArrayReaderVelo ( xExecute := TRUE, pwData := pwsPayloadJsonVelo, jsonData := jsonDataVelo, xDone => xDoneReaderVelo ); FindFirstValueByKeyVelo( xExecute := xDoneReaderVelo, wsKey := "data", diStartIndex:= 0, jsonData := jsonDataVelo, jsonElement => jsonElementVelo, xDone => xDoneFindVelo ); IF xDoneFindVelo THEN lrVelo := jsonElementVelo.value.lrValue; //Reset jsonByteArrayReader jsonByteArrayReaderVelo ( xExecute := FALSE, pwData := pwsPayloadJsonVelo, jsonData := jsonDataVelo, xDone => xDoneReaderVelo ); FindFirstValueByKeyVelo( xExecute := FALSE, wsKey := "data", diStartIndex:= 1, jsonData := jsonDataVelo, jsonElement => jsonElementVelo, xDone => xDoneFindVelo ); xKeepAliveVelo := FALSE; GVL.xSetVeloRead := TRUE; END_IF END_IF And this to subscribe at the topic: //SUBSCRIBE VAR: //----------------- Subscribe Velocity ----------------------- MQTTSubscribeVelo : MQTT.MQTTSubscribe;//Variable MQTTSubscriber block -X - function-X wsTopicSubscribeVelo : WSTRING(1024) := "CORE/odometry/GET/data/simp"; // Topic to publish a message sSubscribeMassageVelo : STRING; udiPayloadSizeVelo : UDINT; xSDoneVelo : BOOL; xSErrorVelo : BOOL; xReceiveVelo : BOOL; eSTypeVelo : MQTT.MQTT_ERROR; eSMQTTErrorVelo : MQTT.MQTT_ERROR; RSVelo : RS; udiCont : UDINT; //SUBSCRIBE CODE: MQTTSubscribeVelo( xEnable:= MQTT_CLIENT.xConnection_Broker AND NOT xSErrorVelo AND NOT JSON_VELO.xKeepAliveVelo, pbPayload:= JSON_VELO.psPayloadJsonVelo, udiMaxPayloadSize:= SIZEOF(JSON_VELO.sPayloadJsonVelo), udiPayloadSize => udiPayloadSizeVelo, mqttClient:= MQTT_CLIENT.ClientMQTT, wsTopicFilter:=wsTopicSubscribeVelo, xDone => xSDoneVelo, xError=> xSErrorVelo, xReceived => xReceiveVelo, eMQTTError=> eSMQTTErrorVelo ); RSVelo(SET := xReceiveVelo, RESET1 := JSON_VELO.xKeepAliveVelo);
Last updated: 2024-09-09
Post by docker on Webvisu client connection monitoring
CODESYS Forge
talk
(Post)
Hi mate, With this snippet i was able to see the lastusage variable count, but it would not iterate between clients? i was only able to access the data of the target visu. it threw an error with the array of pointers stating it was not able to convert etc. also when i tried it with the while loop it created an endless loop and crashed the program. any ideas? Thankyou
Last updated: 2024-09-10
Post by mani-i4point0 on Codesys (Ethernet IP Scanner ) and Python (Ethernet IP Adapter)
CODESYS Forge
talk
(Post)
Hi, I am currently developing the software to establish the communication and data transfer between Python Module as a Ethernet IP - Adapter coding is running my laptop and Codesys as a Ethernet IP scanner in the resperry PI hardware. I am trying to look for some available recourses online, Can anyone suggest me to develop this function in Codesys and Python ? Best Regards, Mani
Last updated: 2024-09-24
Post by andrebrandt on FB string and naming
CODESYS Forge
talk
(Post)
Hi all. I have a FB written in ST. FUNCTION_BLOCK NTC10k VAR_INPUT Syst:STRING; In:REAL; END_VAR VAR_OUTPUT Out:REAL; OTag:STRING; Out_St:Struct_NTC10K; END_VAR VAR Tag:STRING; InstanceName: STRING; Structure:Struct_NTC10K; END_VAR What i'm trying to do, is to pass data to structure. In structure i want to add a tag with systemnumber and sensorname. '320.001-RT401' In pou i use this RT401: NTC10k;, and tried this RT401: NTC10k(Tag:='RT401'); Anyone done this?
Last updated: 2024-09-26
Post by mubeta on Profibus DP master with EL6731 and automatic restart of slaves
CODESYS Forge
talk
(Post)
The problem is looking for a bug somewhere in CoDeSys in that, when the slave returns, the cyclic data exchange resumes, but the diagnostics do not update and the node continues to resulting off-line. it is not a problem with the PB master, but with its 3S/CoDeSys management. CoDeSys 3.5.19.20 runtime. Any ideas on how to fix it? Thank you.
Last updated: 2025-02-03
Post by trusty-squire on Which database to use?
CODESYS Forge
talk
(Post)
How large and how complex? It's tough to make a recommendation without additional details. The simplest thing is to just use data arrays (or even arrays of arrays). Not knowing your requirements, it might be sufficient and the simplest option is often the best. https://content.helpme-codesys.com/en/CODESYS%20Development%20System/_cds_datatype_array.html You might also look into using Recipes? https://forge.codesys.com/prj/codesys-example/recipe-manageme/home/Home/ Some more complex options below. https://forge.codesys.com/prj/codesys-example/element-collect/home/Home/ https://store.codesys.com/en/mysql-library-sl.html