Post by niallel on CamBuilder and first boundary position not zero CODESYS Forge talk (Post)
Hi, I've read the CamBuilder documentation and it shows to use the left boundary of the first segment as SMCB.BoundImplicit(), so that the transition is as smooth as possible. With this it sets X and Y to 0. My first slave position is not 0 (say for example it's 100), so I would set it with SMCB.Bound(0,100). My question is that when the cam goes back to the start (Periodic := TRUE) , will it blend with the last position (360, 100) if I do this? I imagine it will, but the documentation isn't clear as the information in the Periodic Cams only says to set Smooth Transition in the cam properties - but when I'm defining it with code there isn't an option for Smooth Transition to be set. Hope this makes sense? Many thanks,
Last updated: 2024-10-23

Post by struccc on Problem Update new version Master ethercat CODESYS Forge talk (Post)
Hi, I had some issues as well migrating to the new version. What I have learnt: - Have to check all the libraries in the library manager, if they are the proper versions. - Some other parts of the application, maybe an old library referenced by another one can keep the old Ethercat libraries.... Use the "Placeholders" function on the library manager - See if there is a new version available of the slave "devices". Might just have to update them ... I had problems moving from 4.7 to with 4.8, especially with the 2nd adapter for redundancy - some devices failed to initialize properly.... So I have just downgraded those libraries now. P.
Last updated: 2024-10-28

Post by hardcoder on EtherCAT Mailbox Gateway CODESYS Forge talk (Post)
Hi all I found that in the last Ethercat master release (4.8.0.0) the Mailbox Gateway feature has been added. This would be useful for me to connect to a specific slave in my system, since its configuration software supports this type of gateway communication. Anyway I don't find usage information or examples. At the moment I tried to enable it in the ethercat master device settings and I configured with an IP address on the subnet of the ethercat adapter (i.e. ethercat nic configured with static ip 192.168.10.100 subnet 255.255.255.0, mailbox gateway configured to 192.168.10.30). I expected it would have responded to ping commands on the address but nothing happens. I am missing something?
Last updated: 2024-12-11

Post by imdatatas on MC_CamIn did not work properly with SMC_FreeEncoder on SoftMotion 4.17.0.0 CODESYS Forge talk (Post)
Hi @tk096, Thank you for your response. Here is example project file and some screenshot for your analysis regarding this matter. In order to reproduce the problem on your side and make it independent of the hardware, I simulated the encoder counter incrementally for the master in this example. I configured a virtual axis as the slave motion axis. The problem occurs in the same way in the real hardware configuration (servo drive connected to Ethercat and hardware incremental encoder) in MC_CamIn. I hope this example helps you see the problem on your side and understand and find the source of the problem with FreeEncoderAxis for Softmotion 4.17.0.0. Best Regards, Imdat
Last updated: 2024-12-19

Post by esave on Stepper Drive with Ethercat CODESYS Forge talk (Post)
Hello everybody I am new into Codesys. I have a stepper driver (EM3E-556E) from Leadshine. I want to controll the stepper driver via EtherCat to a ST programm but I dont have any function block or anything that i can use. I only have the XML-File wich I loaded. With it I implemented the drive as a Ethercat slave and now I see these variables. (See picture) I dont know how to controll the stepper drive. And the manufacturer doesnt provide support for me. Can anybody help me or atleast tell me how they would do it?
Last updated: 2024-03-14

Post by fugtwad on Automation Builder V2.5 EtherCAT CM579 Master Scan for devices - >No gateway selected CODESYS Forge talk (Post)
ABB Automation Builder v2.5.0.22 Premium CodeSys 2.3.9.62 Running on Win 10 VM x64 Goal: I have an EtherCAT topology issue which normally a "Scan for devices.." on the EtherCAT master would shed some light on. Issue: Upon trying such I get a "No gateway selected" error. Question: How might I point the the "scanner" at a gateway? What is working: Gateway is running in system tray. I can go online to PLC. A scan from the "Diagnostics live" tab of the EtherCAT master gives slave status. What I have tried: Restarting gateway in system tray. Exiting system tray gateway and reloading it. Turning off firewall. Contacting ABB support multiple times. Any help appreciated.
Last updated: 2024-05-20

Post by kuegerls on SysProcessExecuteCommand2 and CANopen Device CODESYS Forge talk (Post)
Hello, CODESYS Control is running on my RevPi, and my system communicates over a CANbus with a master using the ConnectCan module (Slave - CANopen Device). The communication works perfectly fine so far. However, as soon as I call a Python script with "SysProcessExecuteCommand2" that creates a CSV file and executes without errors, the master does not adopt any changes to the Transmission Process Data Objects (TPDOs). I don't quite understand what one has to do with the other, and perhaps someone can help me with this. Here is my script call: SysProcess.SysProcessExecuteCommand2(pszCommand:='python /home/pi/test.py', pszStdOut:=sCMDOutput, udiStdOutLen:= SIZEOF(sCMDOutput), pResult := ADR(eResult)); Thank you in advance! Best regards, Stefan
Last updated: 2024-06-20

Post by msirotkin on EtherCAT status errors CODESYS Forge talk (Post)
Hello, I'm trying to understand the reason for the many errors on the EtherCAT master status page. If we set the cycletime to 1ms we see a lot of rxerrors and lostframes, but the send and recive times are quite good (see attachement). And the status of the EtherCAT bus is good (no other errors, all is green, slave has no errors) But when we set 2ms cycletime the lostframe errors are gone, but periodically increses rxerror counter (see attachement). The questions is, what do these errors actually mean and what we can do to get gid of them? Linux RT, imx8, Codesys runtime for ARM 3.5.21.10, Ethercat 4.10 Thanks
Last updated: 2025-11-25

Post by mattkaree on Mapping values with etherCAT mailbox communication CODESYS Forge talk (Post)
I am using a WAGO PFC200 PLC as an etherCAT master and a Keyence IV3-G120 with DL-EC1A attached as an etherCAT slave. I am using CODESYS V3.5 SP21 Patch 3. I was able to set up mailbox communication and can see values changing accordingly, but I want to know how I can map these values and reference them in my program. I am able to map the process data objects in the 'EtherCAT I/O Mapping' tab, but there is no where to map the mailbox values in the 'CoE Online' tab. Is there a way I can reference one of these values in my code?
Last updated: 2026-01-27

Post by konstantin on CAM Motion Recover after STO CODESYS Forge talk (Post)
Hello, one of the projects I work on is about a racetrack collator with two independent belts on it - two different servo motors. Both motors share the same mechanical frame and there is a train on a belt that collects items from the input conveyor. The way the motion is performed is the following - there is a virutal master axis and both real axis are synchronised with different cam motion profiles. The problem is when an STO is triggered on any of the slave axis, the synchronization process starts from position 0 of the slaves. How can I force the slaves to retain their current position until the master passes their position? Then the slaves should catch up with the master according to the profile, the slaves should not start synchronization from 0 position. Best Regards Konstantin Kolev
Last updated: 2026-02-12

Post by kurt9 on ReadWriteEEprom FB question CODESYS Forge talk (Post)
I want to programmatically write the alias address to a new EtherCAT slave when I plug it into my IPC EtherCAT network. I am looking at the ReadWriteEEprom FB and see that one of the elements is "pbyData". which is the pointer to byte that is usually set to 2048 bytes. Since I am setting the alias address to the EEprom only (EEprom address 16#0012), I would assume that what I am writing is 2 bytes only. Does the pbyData have to be specified as ADR(myArray) where "myArray" is the 2 bytes of the alias address? How is the best way to set this element of the function block? Thanks in advance
Last updated: 2026-05-18

Post by solidlogicguy on Little endian to Float from Modbus RTU CODESYS Forge talk (Post)
Hello, I got a device from which I require to read values from I am using a WAGO PLC 750-8212 and I am communicating through Modbus Master FUNCTION BLOCK from library WagoAppPLCModbus in Codesys 3.5 to this device. I already receive data from the device that is a CVM to monitor voltage from a fuel cell. The technical support of the company that makes these devices says that the data is sent in little endian form. And I want to convert it to a float value. The tech support sent me the next instructions of how to do it but I am new using codesys, so any advice or help I will really appreciate so much. Message from tech support: The process is complicated, better to do it with already implemented library in the language/program you use. Basically the process should be next: To convert the two Modbus registers containing parts of a 32-bit float in little-endian byte order to a floating-point number using mathematical operations, you first need to combine the two 16-bit integers (assuming reg1 is the lower word and reg2 is the higher word) and then interpret the result according to the IEEE 754 standard. Given: - Register 192 (reg1) = 4096 - Register 193 (reg2) = 14884 Step 1: Combine the two registers. Since we are dealing with little-endian byte order, reg2 is the high word, and reg1 is the low word: combined = reg2 * 2^16 + reg1 combined = 14884 * 65536 + 4096 combined = 975175680 + 4096 combined = 975179776 Step 2: Convert the combined value to binary: combined_binary = '1110101101011100000000000000000' Step 3: Split the binary into IEEE 754 components: Sign bit (1 bit): 0 Exponent (8 bits): 11101011 Mantissa (23 bits): 01011100000000000000000 Step 4: Convert the binary exponent to decimal and subtract the bias (127 for 32-bit floats): exponent = int('11101011', 2) - 127 exponent = 235 - 127 exponent = 108 Step 5: Calculate the mantissa as a fraction: The mantissa in IEEE 754 format is the fractional part after the leading 1 (which is implicit). Therefore, we need to convert the binary mantissa to decimal and add the implicit leading 1: mantissa_fractional = 1 + int('01011100000000000000000', 2) / 2^23 mantissa_fractional = 1 + 18688 / 8388608 mantissa_fractional = 1 + 0.002227783203125 mantissa_fractional β‰ˆ 1.002227783203125 Step 6: Combine the sign, exponent, and mantissa to get the float value: float_value = (-1)^0 * mantissa_fractional * 2^exponent float_value = 1 * 1.002227783203125 * 2^108 Because the exponent is quite large, the resulting float value is a very large number.
Last updated: 2023-12-15

Post by risele on dynamic modbus devices CODESYS Forge talk (Post)
Have the same issue: I'm making a test setup for modbus devices testing and calibration. One is run for every possible address, and it starts with minimal request: if the device is found, it continue to work with it, otherwise it's set to Disabled temporary. Those state machines are running under FOR cycle, and disabled are just skipped. Every instance have its own timer for not running too frequently and a start delay, so the actual requests are separate in time. I also check not for a single error, but have some timer to allow one-two timeouts. The small program disables and re-enables devices temporary (manually, since i could not iterate over MB devices). VAR Reset:ARRAY[1..GVL_MB.MD_COUNT] OF R_TRIG; i:INT; END_VAR {IF hasconstantvalue(GVL_MB.MD_COUNT, 1, >= )} i:=1; MD_1.Enable:=GVL_MB.MDPortsEnable[i]; Reset[i](CLK:=GVL_MB.MDPortsEnable[i]); MD_1.xReset:=Reset[i].Q; {END_IF} {IF hasconstantvalue(GVL_MB.MD_COUNT, 2, >= )} i:=2; MD_2.Enable:=GVL_MB.MDPortsEnable[i]; Reset[i](CLK:=GVL_MB.MDPortsEnable[i]); MD_2.xReset:=Reset[i].Q; {END_IF} There is also program to re-enable devices periodically. METHOD ScanBus VAR_INPUT END_VAR VAR j:INT; (*block auto scanning if calibration is running for any device since it's data-reach process that should not be interrupted with modbus timeouts *) CalibrationBusy:BOOL:=FALSE; END_VAR CalibrationBusy:=FALSE; FOR j:=1 TO GVL_MB.MD_COUNT DO CalibrationBusy:=CalibrationBusy OR MD_Calibrate.AutoTesters[j].xBusy; END_FOR; IF CalibrationBusy THEN RETURN; END_IF tBusScanSchedule(IN:=(NOT tBusScanSchedule.Q), PT:=tBusScanPeriod); IF (NOT tBusScanDelayer.Q) AND (tBusScanSchedule.Q OR (NOT xFirstScanPerforemed)) THEN xBusScanBusy:=TRUE; MissingCounter:=0; xFirstScanPerforemed:=TRUE; FOR j:=1 TO GVL_MB.MD_COUNT DO (* MD_Calibrate is main calibration program. Identifiers - is array of State machines mentioned above Phase_Faulted is a state of Identifiers where I'm sure device is missing on the bus *) IF MD_Calibrate.Identifiers[j].state=eStateMDIdentifier.Phase_Faulted THEN MD_Calibrate.Identifiers[j].Rescan(); MissingCounter:=MissingCounter+1; END_IF END_FOR END_IF tBusScanPauser(IN:=tBusScanDelayer.Q AND (MissingCounter>0),PT:=tBusScanDelay*MissingCounter); xBusScanBusy:=tBusScanPauser.Q; xFirstScanPerforemed:=xFirstScanPerforemed OR tBusScanPauser.ET>=tBusScanPauser.PT; Also the GUI have buttons for each address possible that re-enables the device if required.
Last updated: 2026-02-13

Post by ben1 on How to write multiple coils (Modbus FC15) CODESYS Forge talk (Post)
If I am understanding what you are saying, then yes that would be your problem. I would create an array of bools on the client side for the transfer and try that. Or if client can't be changed then use words on server and unpack. But I am not sure if you or I are mis interpreting but it sounds a bit jumbled. I don't know what you have control of, but, if you are turning on BITS in the server, you should write to BITS in the client with a Function 15. If you are writing to WORDS in the server, you should write to WORDS in the client with a Function 16.
Last updated: 2024-11-17

Post by milan-svarny on ModbusFB.ClientSerial Problem with Reply Timeout CODESYS Forge talk (Post)
Hi All, I have problem with ModbusFB.ClientSerial. I'm using 4 different port for Modbus communication. After some time of running program ClientSerial stops to receive data to reply buffer and all request finish with Reply Timeout. The Device sent reply correctly,that it is visible on oscilloscope and it is possible to see that data( reply )are in the device. If the usbtty device is read over external app. then it is possible to see all data which were not taken by ModbusFB.ClientSerial. The stack does not overflow or something , program runs correctly forward and no exceptions or something. The main problem it is that when the error occur than it is not possible to reset port or something or maybe i'm doing it wrong way. please help me with this issue. Thank you for any help in advice Milan
Last updated: 2025-05-23

Post by alexgooi on Modbus writing on value change CODESYS Forge talk (Post)
The way I usally tackle this is by syncing only words (then you are able to use the FB above). If you then want to write a Boolean simply type it like this. Value[1].0 := Bool1; Value[1].1 := Bool2; Value[1].2 := Bool3; Uints have the same number of bits than a INT/WORD so these ones will work as well (they are only represented diffrently). A Real will work but you will loose some infomration in the conversion. If you want to keep the information you can convert 2 words to a float with a function (for example with the IEEE-754 standard) . In this way the syncing to the server is very simple and in the Codesys Program you decide what part of the word you want to use.
Last updated: 2024-04-03

Post by paro on Modbus Client Request Not Processed CODESYS Forge talk (Post)
Hi, works in my case if I increase the timeout! to_udint(t#100ms) -> 100 -> 100us.. FUNCTION_BLOCK MODBUS_master_example_ST VAR initDone : BOOL := FALSE; aIPAddress : ARRAY [0..3] OF BYTE := [127,0,0,1]; clientTcp: ModbusFB.ClientTcp; // buffer to read input registers aDataInputRegisters : ARRAY[0..9] OF UINT; // some client requests clientRequestReadInputRegisters: ModbusFB.ClientRequestReadInputRegisters; xExecute: BOOL; uistart: UINT := 100; udiTimeout1: UDINT; END_VAR IF NOT initDone THEN initDone := TRUE; // configure clientTcp clientTcp(aIPaddr:=aIPAddress, uiPort:=502, udiLogOptions := ModbusFB.LoggingOptions.All); // configure clientRequestReadInputRegisters clientRequestReadInputRegisters(rClient:=clientTcp, uiUnitId:=1, udiTimeout:=1000000); // 1sec END_IF // call the client FB's clientTcp(); clientRequestReadInputRegisters(rClient:=clientTcp,xExecute := xExecute AND NOT clientRequestReadInputRegisters.xBusy ,uiStartItem:=uistart, uiQuantity:=3, pData:=ADR(aDataInputRegisters[0]));
Last updated: 2024-05-30

Post by zer0g on Modbus Client Request Not Processed CODESYS Forge talk (Post)
I'm using the code bellow which is based on the Codesys example: FUNCTION_BLOCK MODBUS_master_example_ST VAR initDone : BOOL := FALSE; aIPAddress : ARRAY [0..3] OF BYTE := [127,0,0,1]; clientTcp: ModbusFB.ClientTcp; // buffer to read input registers aDataInputRegisters : ARRAY[0..9] OF UINT; // some client requests clientRequestReadInputRegisters: ModbusFB.ClientRequestReadInputRegisters; xExecute: BOOL; END_VAR IF NOT initDone THEN initDone := TRUE; // configure clientTcp clientTcp(aIPaddr:=aIPAddress, uiPort:=502, udiLogOptions := ModbusFB.LoggingOptions.All); // configure clientRequestReadInputRegisters clientRequestReadInputRegisters(rClient:=clientTcp, uiUnitId:=1, udiTimeout:=TO_UDINT(T#1000MS)); END_IF // call the client FB's clientTcp(); clientRequestReadInputRegisters(rClient:=clientTcp,xExecute := xExecute AND NOT clientRequestReadInputRegisters.xBusy ,uiStartItem:=2, uiQuantity:=3, pData:=ADR(aDataInputRegisters[0])); As you can see the clientTCP is called cyclically with the same result.
Last updated: 2024-05-30

Post by ofey on EtherCAT fieldbus CODESYS Forge talk (Post)
Hi, everyone! I'm trying to set up a PLC controller and a connection to an EtherCAT slave device in Codesys. I want to create a flexible program that I can upload to multiple controllers with different remote IO connected (same program). On one plant i may have 5 AI-cards and 3 DO-cards, and on another I may have 4 AI-cards and 2 DO-cards. For not needing to maintain several different programs wih different devices defined in the program (one for each set up) I thought that using a remote IO would make it easier having a single program. That way I could refer to different memory addresses instead of predefined slots/channels and IO's, that would give me errors if there was a different IO on the plant than what the program expected. When I tried setting up the etherCAT master, I saw that I had to define the etherCAT slave devices with the different IO'cards for me to be able to refer to the memory addresses in a PRG. Exactly what I was trying to avoid. My setup is something like a program that can handle 16 separate pump controls. In a year maybe 6 plans get deployed, and depending on how large the project is, the number of pumps can vary between 4 and 16. And the managers dont want to have IO's for all 16 pumps on every cabinet, and I dont want to maintain 16 separate projects files in case of updates etc. I thought the best way to tackle this was having a single project that read/write data to the different pump IO's by remote IO (fieldbus ethercat) addresses. And the number of pump controls are activated by an external GUI. If pump 1-6 is activated by the GUI, then the PLC-program tries to read/write input/outputs from predefined addresses for the expected IO's. My test setup is a PFC200 WAGO controller and a EtherCAT fieldbus coupler (750-354) with some IO. I hope I didn't explain this too horrible, and if there is a more easy and elegant solution for this challenge I appreciate a feedback on this.
Last updated: 2024-04-08

Post by dekelec on Codesys 2.3 & Peak PCAN CODESYS Forge talk (Post)
I use Peak USB adapter daily to download from CoDeSys 2.3 and 3.5 to IFM, EPEC and other controllers. The process: - First you need to install the appropriate driver. Link: https://www.peak-system.com/Drivers.523.0.html?&L=1 - Restart the computer - Start the CoDeSys application - Change the name of the adapter in Communication parameters, as mentioned in previous comment. Write the name exactly as written "Peak_USB", as it could also be case sensitive (defines which .dll file to use). If this doesn't work I would contact the vendor of the controller to find out the procedure. In the attachment I've added a FAQ document from IFM regarding using PCAN USB. P.S. I've noticed in your picture of communication parameters a channel via TCP/IP is mentioned. In this case a USB to CAN connection is not being used. First you should change the channel/gateway to connect via CANbus or connect using an Ethernet cable.
Last updated: 2024-07-09

Post by simone on Cannot connect to webvisu on localhost CODESYS Forge talk (Post)
As I wrote before on the title, I have difficulties to connect to see webvisu from localhost. The story: while waiting for the plc+hmi to arrive, I'm preparing the software, mainly the visual parts trough the control Win3 x64 (same version as the ide 3.5.20.10). The problem is that I can't see the webvisu with the installed webbrowser. I don't know if this is a problem, but I changed the port to 9001 (randomly "free") because 80, 8000, 8080, 8088, 3000 are all occupied by other projects (all on the Apache server). Is there something wrong with the config file? This is the url: localhost:9001/webvisu_app.htm and here the config file part "CmpWebServer". [CmpWebServer] ;The handling of startup/shutdown of the webserver: ;0->automatically start, shutdown only on shutdown of the runtime;1->automatically start, could be shutdown on demand ;2(default)->start/shutdown on demand;3->start on demand, shutdown only on shutdown of the runtime StartupType=0 ;The TCP port the webserver listens on WebServerPortNr=9001 LocalAddress=localhost ;LocalAdapterName=LAN-Connection LocalAdapterName=EthernetPCPLC ;LocalAdapterNameUnicode=L\00A\00N\00-\00C\00o\00n\00n\00e\00c\00t\00i\00o\00n\00 LocalAdapterNameUnicode=E\00t\00h\00e\00r\00n\00e\00t\00P\00C\00P\00L\00C\00 Thanks for all the help!
Last updated: 2024-07-11

Post by denkihitsuji on Content update through Data URI on Web Brower on Visualization Toolbox CODESYS Forge talk (Post)
Objective: I want to dynamically update the content with strings and JPEG images received from a TCP/IP socket. For this purpose, I am exploring the possibility of utilizing the Web Browser feature of the Visualization toolbox. Example: In a standard web browser, entering data:text/plain;charset=utf-8;base64,SGVsbG8gc3RyYW5nZXI= in the URL window will display "Hello stranger" on the webpage. Issue: When attempting to use this method in the Web Browser of the Visualization toolbox, the content does not display as expected. Instead, it shows the error:'Navigation to the webpage was canceled.'. Request: I seek guidance on how to resolve this issue so that the Web Browser in the Visualization toolbox correctly interprets and displays the data URI content. Alternative Solution Welcomed: Or, if it is possible to directly use Codesys Structured Text (ST) variables within an HTML page, this approach would also meet my requirements. Thank you for your attention.
Last updated: 2024-07-30

Post by julianramirez on ModbusFB write update CODESYS Forge talk (Post)
Hello everyone, I am testing the ModbusFB library tcp server and so far I am able to create holding registers successfully, however, I am trying to identify after each write which registers got updated (i.e. function code, write value). I can even see the var udiNumWriteRequests, which increases with every write. I noticed that there is logging with the LogStatusInfo method. After I call it I am able to read in the console stuff that I want. Nevertheless, this is only available at the logs and is not easy to decode because it consists on several messages, I would like to know if there is a way for me to retrieve this information from the function itself with pointers or if there is any way to copy the logs messages (assuming that I can filter them with the LoggingOptions to only show what I need) inside the runtime code and not in the console. Thanks for your help :)
Last updated: 2024-09-16

Post by timvh on STRING conversions to DWORD CODESYS Forge talk (Post)
I guess that the printer expects to receive an array of byte values. So where it is described that it expects to receive: Hercules String : 1B4F513030311B7532626C61636B04 it actually expects to receive an array of bytes with the values 1B,4F,51,30,30, etc. So what you can do is create an array of bytes and assign the byte value to each item in the array: VAR abyToSend : ARRAY[0..99] OF BYTE; END_VAR abyToSend[0] := 16#1B; // ASCII Escape character, hexadecimal representation uses 16# as prefix abyToSend[1] := 16#4F; // ASCII 'O' abyToSend[2] := 16#51; // ASCII 'Q' abyToSend[3] := 16#30; // ASCII '0' // you can do the rest yourself // maybe could be created a lot smarter, but gives you an indication how to handle this. Then with the serial communication (or TCP/IP?) you can send a message with the reference to the array (abyToSend) and the number of bytes to send (15 bytes for the string you gave as example).
Last updated: 2025-02-02

Post by george32 on TCP Server CODESYS Forge talk (Post)
Thank you for your advice Rinie, I have tried to follow this example but found one problem.When I disconnect with Hercules the system does not acknowledge the lost of its connection this could result in critical errors. Because of this error I am trying to implement the Syssocket library. With this library I am having a problem which I could not solve. I have the following code: ip_adres : STRING :='0.0.0.0'; port : WORD := 5000; iStep : INT := 1; // Socket information Socket_handler : SysSocket_Interfaces.RTS_IEC_HANDLE; Socket_handler_result : SysSocket_Interfaces.RTS_IEC_RESULT; Socket_adress : SysSocket_Interfaces.SOCKADDRESS; Addres_Convert : SysSocket_Implementation.RTS_IEC_RESULT; // Bind information Bind_handler : SysSocket_Interfaces.RTS_IEC_RESULT; // Listener Information Listener_handler : SysSocket_Interfaces.RTS_IEC_RESULT; Addres_Convert := SysSocket_Implementation.SysSockInetAddr(szIPAddress:= ip_adres,pInAddr:= ADR(Socket_adress.sin_addr)); Socket_adress.sin_family:= SysSocket_Interfaces.SOCKET_AF_INET; Socket_adress.sin_port := SysSocket_Implementation.SysSockHtons(usHost:= port); CASE iStep OF 1: // Create Socket Socket_handler :=SysSockCreate( iAddressFamily :=SysSocket_Interfaces.SOCKET_AF_INET, diType:=SysSocket_Interfaces.SOCKET_STREAM, diProtocol:=SysSocket_Interfaces.SOCKET_IPPROTO_TCP, pResult:=ADR(Socket_handler_result)); IF Socket_handler = SysSocket_Interfaces.RTS_INVALID_HANDLE THEN iStep := 1; ELSE iStep := 2; END_IF 2: Bind_handler := SysSocket_Implementation.SysSockBind( hSocket:=Socket_handler, pSockAddr :=ADR(Socket_adress), diSockAddrSize:=SIZEOF(Socket_adress) ); 3: Listener_handler := SysSocket_Implementation.SysSockListen( hSocket :=Socket_handler, diMaxConnections :=1); END_CASE When I am trying to get this working, the SysSockBind function gives a value of 16#207 which means adress already in use. I find this weird because of the IP-adress of 0.0.0.0. I think I am converting the Ip-adress in the wrong way, but the code does not give a error arround this. So therefore I cannot find the solution to this problem. I hope someone could help me with this problem. Thanks in advance George