Post by gurkan on OPCUA array max length?
CODESYS Forge
talk
(Post)
2000 works. When testing with UA Expert there is a timeout from the OPCUA Server when trying to subscribe to the variable CPU do not seems to be to affected. The memory(RAM) however is building up
Last updated: 2024-02-19
Post by eschwellinger on OPC Da Server Code Meter Issues after Enabling License
CODESYS Forge
talk
(Post)
it is mandatory to activate the OPC DA license into the 32-xxxxxx legacy container (not UFC) you need a remove ticket -> contact CODESYS store - my question to move the license
Last updated: 2024-05-03
Post by bryandimino on OPC Da Server Code Meter Issues after Enabling License
CODESYS Forge
talk
(Post)
Additionally the license is loaded on the soft storage for my device but it shows up as invalid. I just activated it today.
Last updated: 2024-05-02
Post by hwopereis on How to use Application Trigger in Modbus TCP Server
CODESYS Forge
talk
(Post)
I'm now circumventing the problem by creating a separate TCP client for all Write actions. Upon registering a changed variable, I enable this client, until the change is processed.
Last updated: 2024-07-01
Post by shabroz-gill on Data Sources Manager causing exception due to float or double type in OPC server
CODESYS Forge
talk
(Post)
Was this ever resolved? I see the same issue with the version 3.5.19.5
Last updated: 2024-07-01
Post by elayaraj on Codesys Soft PLC OPC UA server
CODESYS Forge
talk
(Post)
Hi, You may refer to this below video link to get some idea.. hopefully it works https://www.youtube.com/watch?v=RBMff-IlPA4
Last updated: 2024-08-30
Post by reinier-geers on Syssockping hang up V3.5.9.2
CODESYS Forge
talk
(Post)
For data logging on a server i check the connection with Syssockping. When i do that it seems to hang uo the system once a while for 13 seconds. Why ??
Last updated: 2024-09-02
Post by arfoto on Gateway
CODESYS Forge
talk
(Post)
Merhaba Gateway config moda almak istediğimde BU hatayı alıyorum. maalesef bu sorunu çözemiyorum amacım softplc yi Automation Server a Bağlamak Ama maalesef config moda giremiyorum dosya yolumda C:\ProgramData\CODESYS\CODESYSGatewayV3 bu şekilde. Teşekkür ediyorum.
Last updated: 2024-09-17
Post by fmbrew-rob on Licensing info not available.
CODESYS Forge
talk
(Post)
I do have a license server installed. Can you point to a document or ANYTHING that shows how to configure this virtual control to properly do licensing?
Last updated: 2024-09-24
Post by astrum on OPC UA Client Zertifikate in "Vertrauenswürdige Zertifikate" verschieben
CODESYS Forge
talk
(Post)
Hallo zusammen, gebe es eine Möglichkeit die Client Zertifikate aus dem Quarantäne Bereich zu den Vertrauenswürdige Zertifikaten zu verschieben, und das ohne die Codesys-Umgebung ? Der OPC UA Server läuft über eine Delta Steuerung die über Codesys eingerichtet wurde.
Last updated: 2024-10-10
Post by mainak on OPC UA C# client connecting to OPC UA CODESYS server
CODESYS Forge
talk
(Post)
it could be due to security settings. In codesys IDE, go to device-> change run-time security policy, and click the checkbox that says "Allow anonymous login". try if this works.
Last updated: 2024-10-19
Post by banialuk on Modbus TCP Server
CODESYS Forge
talk
(Post)
Hello, I have poroblem with define input in function block modbusFB.serverTCP 'dataModel', in my aplication I need starting Input Registers from 3000, and I must define this in 'data Model' but I dont now how exacly to do it. Anybody now somethin about this?
Last updated: 2024-10-19
Post by tmo21 on Automation server - trends stop recording - need to manually reconnect
CODESYS Forge
talk
(Post)
Hi Edwin, Thanks for your message. Edge controller Version: 4.4.0.0 based on 3.5.17.30 PLC version: Device Identification Name CODESYS Control for Raspberry Pi MC SL Vendor 3S - Smart Software Solutions GmbH Device type Softmotion3S Firmware version 4.4.0.0
Last updated: 2024-10-23
Post by dogulas on OPC UA C# client connecting to OPC UA CODESYS server
CODESYS Forge
talk
(Post)
mainak, sorry, just saw your post. I have done that and I still get the same exception. the innerResult says "BadSecureChannelClosed 'Remote side closed connection'". Any other tips? Pointers are welcome.
Last updated: 6 days ago
Post by toffeebonbon on EL7041-0052 - does it run with EL7041 SoftMotion?
CODESYS Forge
talk
(Post)
Good morning everyone. In my setup I am trying to use a couple of EL7041-0052 (the EL7041 variant without terminals for an encoder) to run stepper motors without feedback. When using the softmotion drivers for the EL7041 (Rev22 and Rev24, even selecting external feedback type doesn't work) the device log shows warnings for the corresponding hardware: "SDO write error 0x1 -> 0x8012:0x08 eError 0x1 AbortCode 0x6090011". 0x8012:0x08 is the register for the Feedback Type. My best guess was setting the the register value in the start parameters to zero, but the result is the same. What else can I try to get the hardware to work? I have screenshots attatched showing the running fieldbus and the log messages. EDIT: One clarification: the "device log" that shows the error is the PLC, not the ethercat terminal. The log of the terminal itself shows neither errors nor warnings. BR Robert
Last updated: 2023-11-29
Post by tomast on Codesys and Siemens SINAMICS 20 modbus RTU "Response CRC Fail"
CODESYS Forge
talk
(Post)
Hi everyone, I'm currently working on a project involving the control of 5 VFDs via Modbus RTU, this time using the WAGO 750-8212 CPU. So far, I've managed to make progress, but I've encountered an issue. While I can successfully read and write to all the registers I need, I consistently encounter a "Response CRC Fail" error when attempting to write the value 1151 to the STW register at address 40100. I'm able to set the frequency via register 40101 and adjust all other parameters using different registers. Setting STW to 1150 results in the drive ready boolean from the ZSW-bit being received instantly. However, the moment I attempt to send 1151 to register 40100, I immediately receive the "Response CRC Fail" error for all channels. I've also attempted to use combined control, employing Modbus for frequency control and starting from a digital input. Everything seems to function properly until I send the start command to the VFD. Interestingly, I consistently encounter the same error the moment I send the start command, regardless of whether I use register 40006 (high) or 40100 (1151). Could someone please assist me in resolving this issue?
Last updated: 2024-03-21
Post by trusty-squire on CNC - How to manipulate SMC_GeoInfo objects
CODESYS Forge
talk
(Post)
I have an application using CNC GCode interpolation, but I need to modify the GCode provided to the PLC based on certain parameters. I am currently attempting to modify the SMC_GeoInfo objects in the SMC_OutQueue using the code below. Note that all the other code is pretty standard and works fine, but when I add the below it errors. PROGRAM TEST VAR fbReadCncFile : SMC_ReadNCFile2; fbCncInterpreter : SMC_NCInterpreter; arrCncInterpreter : ARRAY[1..99] OF SMC_GeoInfo; pGeoInfo: POINTER TO SMC_GeoInfo; giGeoInfo: SMC_GeoInfo; // ... END_VAR // ... Some code here in order to read CNC file using SMC_ReadNCFile2 and provide to SMC_NCInterpreter pGeoInfo := SMC_GetObj(poq:=ADR(fbCncInterpreter.poqDataOut), n:=1); IF pGeoInfo <> 0 THEN giGeoInfo := pGeoInfo^; // Do some manipulation here, then update the queue at the same position MC_SetObj(poq:=ADR(fbCncInterpreter.poqDataOut) , n:=0 , pgi:=ADR(giGeoInfo) ); END_IF It throws an error when I get to the line giGeoInfo := pGeoInfo^; Error: EXCEPTION [AccessViolation] occured: App=[Sim.Device.Application], Task=[PathTask] How do I use SMC_GetObj and access the data? It creates a pointer with the value as shown in the photo, but all the dereferenced values say dereference of invalid pointer.
Last updated: 2024-07-26
Post by programmierer on Implementing UDP Communication
CODESYS Forge
talk
(Post)
Hello everyone, I hope you can help me with my problem. I am new to programming and am currently working with a WAGO controller in our lab, which controls a heat pump. My goal is to send the electrical power of the heat pump (Pel_WP) via a UDP connection to a specific IP address. I am using Codesys version 2.3 and following the guide I found here: https://forge.codesys.com/forum/de/396/genmed-Konfiguration%20der%20UDP%20Kommunikation%20Cosesys%20S7.pdf. I have adapted the guide to suit my needs. The data sending works since I can force the reception value Pel_WP and the data is sent accordingly. However, I am having trouble with the receiving part. The reception value is not being correctly received, and the diSocket variable shows -1. The connection between the heat pump and the WAGO controller seems to be set up correctly, as the heat pump is listed under the communication parameters with the correct IP address. I have also attached images to provide a better view of the setup. I would greatly appreciate any support or suggestions for a solution. Thank you in advance!
Last updated: 2024-08-02
Post by paulg on RasPi CAA Serial example - unexpected behavior during debug
CODESYS Forge
talk
(Post)
I've trimmed down the CAA Serial Codesys example to only listen on one port but, when stepping through the Case structure in debug mode, it jumps out of the structure during a specific point in every scan (I'll point it out below after describing the setup and listing the code). I'm using a Pi 4 Model B, and I have an Arduino Nano Every plugged in via USB which is streaming the following serial message at 1 Hz: Time since opening connection: 1 s Time since opening connection: 2 s ...and so on. The Pi shows the Nano at /dev/ttyACM0 so I edited CODESYSControl_User.cfg to read: Linux.Devicefile=/dev/ttyACM The code in my PLC_PRG is (ignore some of the comments, I hadn't deleted them out from the original example): PROGRAM PLC_PRG VAR xStartTest : BOOL:= TRUE; iState : INT; xTestDone : BOOL;(* True, when the test was done succesfully *) (* Settings to communicate with the COM Port *) aCom1Params : ARRAY [1..7] OF COM.PARAMETER; como1 : COM.Open; comc1 : COM.Close; comw1 : COM.Write; comr1 : COM.Read; //sWrite : STRING := 'Test String!'; sRead : STRING(25); szRead : CAA.SIZE; xCom1OpenError : BOOL; xCom1CloseError : BOOL; xCom1WriteError : BOOL; xCom1ReadError : BOOL; END_VAR //This example shows the communication of two COM Ports with each other. //The first one writes a string of characters, which is read by the second one. //After successful execution, the two COM Ports are closed and the test is done. IF xStartTest THEN CASE iState OF 0: //The parameters are set for the COM Port aCom1Params[1].udiParameterId := COM.CAA_Parameter_Constants.udiPort; aCom1Params[1].udiValue := 1; // the correct Port should be adapted aCom1Params[2].udiParameterId := COM.CAA_Parameter_Constants.udiBaudrate; aCom1Params[2].udiValue := 115200; aCom1Params[3].udiParameterId := COM.CAA_Parameter_Constants.udiParity; aCom1Params[3].udiValue := INT_TO_UDINT(COM.PARITY.NONE); aCom1Params[4].udiParameterId := COM.CAA_Parameter_Constants.udiStopBits; aCom1Params[4].udiValue := INT_TO_UDINT(COM.STOPBIT.ONESTOPBIT); aCom1Params[5].udiParameterId := COM.CAA_Parameter_Constants.udiTimeout; aCom1Params[5].udiValue := 0; aCom1Params[6].udiParameterId := COM.CAA_Parameter_Constants.udiByteSize; aCom1Params[6].udiValue := 8; aCom1Params[7].udiParameterId := COM.CAA_Parameter_Constants.udiBinary; aCom1Params[7].udiValue := 0; //The first Port is opened with the given parameters como1(xExecute := TRUE, usiListLength:=SIZEOF(aCom1Params)/SIZEOF(COM.PARAMETER),pParameterList:= ADR(aCom1Params)); IF como1.xError THEN xCom1OpenError := TRUE; iState := 1000; END_IF //After a successful opening, the next state is reached IF como1.xDone THEN iState := 15; END_IF 15: // the reading process is started comr1(xExecute := TRUE,hCom:= como1.hCom, pBuffer:= ADR(sRead), szBuffer:= SIZEOF(sRead)); IF comr1.xError THEN xCom1ReadError := TRUE; END_IF //After completion the size of the written bytes are saved IF comr1.xDone OR comr1.xError THEN szRead := comr1.szSize; iState := 20; END_IF 20: // If everything was successful the ports are closed and the handles are released comc1(xExecute := TRUE,hCom:= como1.hCom); IF comc1.xError THEN xCom1CloseError := TRUE; END_IF IF comc1.xDone OR comc1.xError THEN iState := 25; END_IF 25: // The first port is closed and the used handle released xTestDone := TRUE; xStartTest := FALSE; iState := 0; como1(xExecute := FALSE); comw1(xExecute := FALSE); comc1(xExecute := FALSE); ELSE iState := 0; END_CASE END_IF I realize as I write this that the .udiPort should be 0 and not 1, but that shouldn't be causing the issue I'm seeing. I'm forcing xStartTest:=TRUE every scan so that I can step into each line and observe what's happening. What I see is that the port parameters are set and the port is opened with no errors, but the code jumps out of the case structure to the last line every time it reaches (and I step into) the iState:=15 line (at the end of the iState:=0 block). So every scan cycle it goes through the block for iState=0 and jumps out at the same spot. I'm a little new to PLC programming so I may be misunderstanding the flow, but shouldn't this case structure keep moving down in the same scan? If it only handles one case per scan, why doesn't the value of iState persist? Thanks! Update: I restarted the Codesys control today and I was then able to see an error for como1.eError of "WRONG_PARAMETER". I tried doing some digging and another post made me think I should add another line to CODESYSControl_User.cfg, so I now have: [SysCom] Linux.Devicefile=/dev/ttyACM portnum := COM.SysCom.SYS_COMPORT1 So now when I set .udiPort to 1, I get "NO_ERROR" but I also don't read anything from the port (i.e. szRead = 0 always). If I try setting the port to 0 (which I'm confused about, because I added a COMPORT1 line but the device shows on the Pi as ACM0), I get the "WRONG_PARAMETER" error again. Is there an easier way to troubleshoot the Pi and view what ports the Codesys runtime is actually able to see while the Pi is running?
Last updated: 2024-06-06
Post by dogulas on OPC UA C# client connecting to OPC UA CODESYS server
CODESYS Forge
talk
(Post)
Noob alert! I’m just getting my feet wet with CODESYS. I have a “Hello World” project in the CODESYS IDE. I’m using the Win SoftPLC on the same computer. I’ve added a Communication Manager under the Application node. Under that is “OPC UA Server -> IEC Symbol Publishing 01”. I also added “OPC_UA_Symbols -> Information Model”. I’m not sure I need the second thing. I was grasping at straws. I also set up several dummy symbols in the IEC Symbol Publishing 01 node. In my C# application, I am trying to get an instance of EndpointDescription from CoreClientUtils.SelectEndpoint(“opc.tcp://localhost:1217/Gateway-1”, useSecurity: false, 15000). I wasn’t sure about the “Gateway-1”. I found that in the CODESYS IDE under the project -> Communication Settings. When I execute the previous method call in C#, I get: “BadSecureChannelClosed”. I have no idea what that means. Any pointers to documentation are welcome.
Last updated: 2024-08-16
Post by tvm on Web Client (HMI) Disconnects from Webvisu (Weidmuller u-OS)
CODESYS Forge
talk
(Post)
ok, that's different than our issue then. We're using Schneider Electric M262 PLCs, and we've had it where certain web browsers cause the web server to only allow https connections, but it's not recoverable with a refresh. It usually requires a power cycle or even a full firmware flash. Your issue might have more to do with the timing. I don't know if it helps you, but we normally run our visu task at 200mS, with an update rate of 200mS. Seems to work. I went through this: https://faq.codesys.com/pages/viewpage.action?pageId=112525371 but it really seems like trial and error.
Last updated: 2023-09-06
Transparency of element rectangle works only in simulation not in WebVisu
CODESYS Forge
talk
(Thread)
Transparency of element rectangle works only in simulation not in WebVisu
Last updated: 2023-05-25
What is the best way to upgrade a project to a new version of Codesys?
CODESYS Forge
talk
(Thread)
What is the best way to upgrade a project to a new version of Codesys?
Last updated: 2022-03-01
I want to use the function of PVT to realize move
CODESYS Forge
talk
(Thread)
I want to use the function of PVT to realize move
Last updated: 2013-05-14
Which kinds of data is transferred with 'Scan for devices' command?
CODESYS Forge
talk
(Thread)
Which kinds of data is transferred with 'Scan for devices' command?