Post by adamrobotic on llcallback() iec exception caught cmpid=0x00000002, eventid=0x00010008
CODESYS Forge
talk
(Post)
Hi All, Recently I have been experiencing a issue in CodeSys SP16 Patch 3, with a exception which comes up after I have made several online changes. callcallback() iec exception caught cmpid=0x00000002, eventid=0x00010008, after I experience this fault then I receive a error message for any subsequent online change "online change failed, no task gap within 10000ms". To recover either the controller needs a orgin reset, which will allow online edits thereafter until falling back into the loop. I am using a TURCK TX707 product which is controlling robot trajectory, We have hard coded the coordinate data rather than using persistence variables so hence the need to do online changes consistently. I have read on the forum other people have experienced similar issue with the online task gap, but I have no task which have same priority and also monitored the CPU usage and have not seen it go above 13%. Anyones help would be much appreciated, thankyou.
Last updated: 2023-08-18
Post by egret on Issue with J1939, PGN 65267 (Vehicle Position)
CODESYS Forge
talk
(Post)
I have a J1939 network (ISOBUS) connected to my PLC. I can receive various PGNs such as 65256 (Vehicle Direction/Speed) and 65254 (Time/Date). However, I cannot receive 65267 (Vehicle Position). PGN 65267 (VP) contains SPN 584 (Latitude) and SPN 585 (Longitude). On the network both SPNs return a value of -210 (meaning the CAN message payload is zero in both cases). The conversion settings are the default values and appear to be correct (see attached screenshot). Using a CAN analyser I can see that PGN 65267 (Vehicle Position) is being transmitted over the network with valid (non-zero) data that matches the latitude and longitude coordinates I would expect. I've created a program to read the raw J1939 data and this also returns valid data. It seems that the Codesys J1939 database has a problem with reading PGN 65267 messages. Can anybody else confirm this? I'm using Codesys Version 3.5 SP16 Patch 5.
Last updated: 2023-09-13
Post by macman on Codesys 3.5 OPC UA Client to Kepware OPC UA Server
CODESYS Forge
talk
(Post)
Hi, I have problem with connecting Wago PLC WAGO 750-8212/0025-0002 configured as OPC UA client to Kepware OPC UA Server. I am using Codesys 3.5.19.70. What I did so far. To the Codesys project I added object Data Source Manager and configured connection OPC UA like below: pic 1 Then I can browse the OPC server tags in “Variables” tab after prior trust on the server side of the client certificate created in the “Communication” tab: pic 2 Additionally second certificate has been created in Codesys for runtime process in “Security screen” as well as the server certificate was approved here: pic 3 But when I compiled project, downloaded it to PLC and go to RUN I can’t read selected in “Variables” tab, OPC Server tags. I am getting such error (ID: 7001): pic 4 All two PLC certificates has been trusted in OPC server (Kepware) side: pic 5 and Kepware server configuration look like this: pic 6 I can easily connect using third party OPC UA client UaExpert to Kepware server without problem. In attachment I added also log from Kepware OPC UA server. pic # - this specifies the number of a concrete graphic from one of the collective in attachment
Last updated: 2025-04-02
Post by tomast on Codesys and Siemens SINAMICS 20 modbus RTU "Response CRC Fail"
CODESYS Forge
talk
(Post)
Hi everyone, I'm currently working on a project involving the control of 5 VFDs via Modbus RTU, this time using the WAGO 750-8212 CPU. So far, I've managed to make progress, but I've encountered an issue. While I can successfully read and write to all the registers I need, I consistently encounter a "Response CRC Fail" error when attempting to write the value 1151 to the STW register at address 40100. I'm able to set the frequency via register 40101 and adjust all other parameters using different registers. Setting STW to 1150 results in the drive ready boolean from the ZSW-bit being received instantly. However, the moment I attempt to send 1151 to register 40100, I immediately receive the "Response CRC Fail" error for all channels. I've also attempted to use combined control, employing Modbus for frequency control and starting from a digital input. Everything seems to function properly until I send the start command to the VFD. Interestingly, I consistently encounter the same error the moment I send the start command, regardless of whether I use register 40006 (high) or 40100 (1151). Could someone please assist me in resolving this issue?
Last updated: 2024-03-21
Post by kiranbsiddaiah on CodeSys OPC UA client Unable to Connect To OPC UA sever through Username and password
CODESYS Forge
talk
(Post)
Hi, I'm using codesys v3.5 sp21 software. I have downloaded the sample opc ua client project from https://content.helpme-codesys.com/en/CODESYS%20Examples/_ex_uacapi_example.html and i tested connecting to "prosys opc ua simulation server". Through Anonymous connection it is connecting to server and can read data. Later tried to connect using username and password. First got a SECURITY_CHECKS_FAILED error, trusted the client certificate in the server and this issue resolved. Next got an INVALID_CERTIFICATE error, trusted the server certificate in the client and this issue resolved. After these two error it is not establishing the connection and not giving any error messages. UAAsyncProp: UA.AsyncProperty := (tnTaskName:='UAClientTask', usiTaskPrio:=20, udiTaskInterval:=10000); UAPolicy: UA.SecurityPolicy := (sPolicy:=UA.OpcUa_SecurityPolicy.OpcUa_SecurityPolicy_Aes128Sha256RsaOaep, eSecurity:=UA.SECURITY_MODE.SIGN_AND_ENCRYPT); //UAPolicy: UA.SecurityPolicy := (sPolicy:=UA.OpcUa_SecurityPolicy.OpcUa_SecurityPolicy_None, eSecurity:=UA.SECURITY_MODE.NONE); UAAuth: UA.UserNameAuth := (sUserName:=UAVars.sUser, sPassword:=UAVars.sPass); UAClient: UA.Client := ( itfAsyncProperty:= UAAsyncProp, //sClientName:= 'MyOPC UA client name', //default: ‘CODESYS OPC UA Client’ sURL:= UAVars.sURL, sSession:= UAVars.sSession, itfPolicy:= UAPolicy, itfAuth:=UAAuth, udiTimeout:= 100000 //,itfNamespaceArray:= UAVars.itfNamespaceArray //optional use ); ----------------------------------------------------------------------------------------------------------------------- Please let me know if any additional information required. Thank you...
Last updated: 2026-05-07
Post by ellcap on Symbol Configuration, I'm doing it wrong
CODESYS Forge
talk
(Post)
if you're here because you are making the same mistake as me, I just resolved it. I mistakenly thought I didn't need to write the word attribute in the column labeled attribute. changed this 'symbol' := 'read' to this attribute 'symbol' := 'read' The last two in this clip are still wrong: I recongize this is probably a big "duh". That's ok. I like to fail out loud in hopes it helps someone else from looking silly.
Last updated: 2023-08-31
Post by bruno-roth on Read "Homed" status from EtherCAT drive
CODESYS Forge
talk
(Post)
Hello, the information if your axis is already homed you could only find out direct from your Slave. In DS402 status there is no Bit defined. But some manufacturer of Drives use some optional bits or status. E.g. if you have Schneider Electric LXM32 Servo you will find this information in Bit 15. You have to check the manual of your used Servo-Drive f this information is provided in any object and then read it out with SDO.
Last updated: 2025-01-08
Post by jvfred on Reading a negative number
CODESYS Forge
talk
(Post)
I have a Codesys-based Eurotherm E+PLC400 connected to Codesys HMI SL for visualization. I am also bringing in several Pressure Indicators via the Ethernet. Everything works; however, the Pressure indicators sometimes read a negative value. When they do, the displayed value on the screen reads "65532." While I know what it represents, the customer freaks out and wants it to read "0" or a negative number. The value comes in as an integer, just in case that matters. Does anyone have any ideas?
Last updated: 2025-05-22
Post by rmaas on TargetVisu for Linux SL not starting
CODESYS Forge
talk
(Post)
Hello, I am trying to get TargetVisu for Linux working but i am having some troubles. The problem is that after installation it is not starting automatically on boot and i cannot start it from the update Targetvisu tool. When i try i get the following error (see attached screenshot) The file /opt/codesysvisualization/scripts/codesysvisualization_start.sh is missing... Steps performed: - installed fresh Debian 12.7 on virtual machine - installed all required libraries as described here: https://content.helpme-codesys.com/en/CODESYS%20Control/_rtsl_target_visu_for_linux.html - then installed the TargetVisu for Linux SL 4.13.0.0 using the Codesys IDE Does someone know how i can fix this? Best Regards, Rinie
Last updated: 2024-10-02
Post by pernockham on How to manage soft container licenses for (remote) multi units?
CODESYS Forge
talk
(Post)
Using Codesys runtime for Linux and thinking of the process of preparing multiple such systems for my customer. I don't necessarily have physical access to these units, they can be (very) remote. The idea so far is to use an image to install the Linux OS and codesys runtime. Application updates can be done by distribution of the PlcLogic/Application/application.app and application.crc files. But whats the most practical way of managing the license for these units? Do each controller need to be physically connected to a License Manager instance or can licenses be distributed by means of a license file for each unit? I believe that the license should be stored in soft containers for each unit. Help and insights appreciated! Per
Last updated: 2025-04-04
Post by dhumphries on No source code available
CODESYS Forge
talk
(Post)
Try using an Ethernet/IP scanner instead of an adapter, I'm guessing the 2 devices you're trying to communicate with are adapters, you have to have a scanner somewhere and Codesys should be a scanner. I don't know why you're getting the error, you should be able to use your Ethernet port as an EthernetIP adapter (although I've never had a reason to try,) but it's probably not what you wanted to do, unless you're connecting to another PLC that is a scanner. Good luck configuring the devices you're trying to connect to, it will be a lot easier if you have an .EDS file instead of starting with a generic module, even with an .EDS it can be tricky getting the communication working.
Last updated: 2024-02-03
Post by nmcc on Viewing PDF in WebBrowser Visual Element
CODESYS Forge
talk
(Post)
I am trying to show a PDF in a WebBrowser element. I have the file saved to the drive of the HMI/PLC. I am linking it in the URL parameter of the WebBrowser using the following directory link. 'http://localhost:8080/$$sdcard$$/FileName.pdf'. This allows for the program to download without any errors. When I navigate to that screen it is just a white box and nothing shows. I attempted putting the same link in the show parameter and I get a loading icon on my cursor when monitoring the HMI with my PC. Any help is appreciated. Thank you.
Last updated: 2024-02-29
Post by tecnocons on Trouble Writing Files to External Paths in CODESYS
CODESYS Forge
talk
(Post)
Hello everyone, I'm encountering an issue in CODESYS regarding writing files to external paths. Despite correctly configuring the placeholder in the CODESYSControl_User.cfg file to allow access to an external folder, CODESYS doesn't seem to write any files, and no errors are reported. The issue on the older versions was absent with no placeholders. I've checked the operating system permissions, and they seem to be in order, but the issue remains. Has anyone faced a similar situation or has any suggestions on how I might resolve this problem? Any help would be greatly appreciated. Thank you in advance for your support. I'm using raspberry PI as a logger. RPI3 Buster Codesys 32bit SL V4.11 Codesys Win64 3.5.20 [SysFile] PlaceholderFilePath.1=/home/pi/scan, $SCAN$
Last updated: 2024-04-09
Post by i-campbell on build (F11) / generate code using a python script file
CODESYS Forge
talk
(Post)
hello, please enjoy. # i-campbell 2024 import subprocess from scriptengine import * # with a project already open # save if not yet saved # check pool objects if it is a library # generate code only for the active application if it is a project # beep thanks to https://devblogs.microsoft.com/scripting/powertip-use-powershell-to-send-beep-to-console/ if projects.primary: # check project is open if projects.primary.dirty: # save projects.primary.save() if projects.primary.path.lower().endswith('.library'): projects.primary.check_all_pool_objects() # check all pool objects for lib else: projects.primary.active_application.generate_code() # generate if not lib # note, there could be more applications than the active application, # this script does not generate those else: system.write_message(Severity.Error,'no project open') ps_output = subprocess.check_output(["powershell", "-Command", "[console]::beep(500,300)"]) # beep
Last updated: 2024-04-10
Post by dkugler on build (F11) / generate code using a python script file
CODESYS Forge
talk
(Post)
thank you very much! I found the generate_code methode, but struggled with the primary and active_application. With this expample I will be able to play around. If the code generation takes a minute or more I often switch to other programs and don't notify the process is finished. So now I'll get an alert and will switch back immediately. My next little project will be, to beep different if there are errors and a seperate script to do the download incl. the user management data base without stopping at the dialogs asking for onlinechange/complete download and overwriting an existing database and as goody, play a beep/sound again.
Last updated: 2024-04-11
Post by stewnguth on New License not working.
CODESYS Forge
talk
(Post)
Hey there, I am pretty new to the codesys space, but I got a codesys control basic M license for my raspberry pi that isntalled with no problem yesterday. Today, I went to install the visualization M locense as well because I went over the variable limit and am getting a "servernotfound" error in codesys when attempting to activate. I also tried to follow the advice in some other threads and install using a license request file on the web interface but am getting a message saying "An internal error occured" when attempting to install the license. Can anyone help me get this up and running? Thanks for your time.
Last updated: 2024-05-23
Post by kronlundo on Licensing info not available (WAGO PFC200 + Codesys V3)
CODESYS Forge
talk
(Post)
Hi! We're using a WAGO PFC200 for several projects towards the energy sector, and recently upgraded to CODESYS V3. We have the "IEC 60870-5-104 Server" package in a test program, and it works well with the package in DEMO mode. However, when we acquired a license for the "IEC 60870-5-104 Server" package and tried to add the license on the PFC200 through the license manager, we get an error (see attached file). It seems like there is no CmContainer on the device, does anyone have an idea on how to fix this? We've also contacted WAGO on this issue a while back with no feedback yet.
Last updated: 2024-06-10
Post by kuegerls on SysProcessExecuteCommand2 and CANopen Device
CODESYS Forge
talk
(Post)
Hello, CODESYS Control is running on my RevPi, and my system communicates over a CANbus with a master using the ConnectCan module (Slave - CANopen Device). The communication works perfectly fine so far. However, as soon as I call a Python script with "SysProcessExecuteCommand2" that creates a CSV file and executes without errors, the master does not adopt any changes to the Transmission Process Data Objects (TPDOs). I don't quite understand what one has to do with the other, and perhaps someone can help me with this. Here is my script call: SysProcess.SysProcessExecuteCommand2(pszCommand:='python /home/pi/test.py', pszStdOut:=sCMDOutput, udiStdOutLen:= SIZEOF(sCMDOutput), pResult := ADR(eResult)); Thank you in advance! Best regards, Stefan
Last updated: 2024-06-20
Post by arwie on Frustration-Fueled Feedback on Project File Management and Git Integration
CODESYS Forge
talk
(Post)
An other approach is to split the application into a hard real-time part running in CODESYS and the business logic running in Python asyncio. The business logic part is usually bigger and changes more often. As Python code is pure text, vscode and git are your friends. A performance example on YouTube (CODESYS SoftMotion + Python): https://www.youtube.com/watch?v=BT-L0H_4Aic Docs and code on GitHub: https://github.com/arwie/controlOS_demo/blob/main/docs/codesys_python_link.md Real-time variable exchange between a CODESYS application and a Python application running in parallel, using POSIX shared memory.
Last updated: 2026-06-21
Post by afrazeh2026 on Curtis 1226BL Drive
CODESYS Forge
talk
(Post)
Subject: Curtis 1229-4105 CANopen (CiA 301 / CiA 402) Hello everyone, I am developing a battery-powered industry vehicle using a Curtis 1229-4105 motor controller together with a Siemens S7-1200 PLC and an HMS (Ixxat) CANopen Master. I am looking for someone who has practical experience with the Curtis 1229-4105 CANopen implementation. I would appreciate your help with the following questions: Does the Curtis 1229-4105 support only CANopen CiA 301, or does it also support CiA 402? Is an EDS file available for this controller? Is the CANopen Object Dictionary available? Has anyone successfully communicated with the Curtis 1229-4105 from a Siemens S7 PLC or another CANopen master? Are the CANopen PDOs and Object Dictionary based on the standard CiA profile, or are they Curtis-specific? Any documentation, examples, or practical experience would be greatly appreciated. Thank you very much.
Last updated: 2026-07-15
Post by brouwyka on JSON Utilities - JSON file written with invalid structure
CODESYS Forge
talk
(Post)
Hey there! I am currently running into the exact same issue (and have also posted to a similar post here: https://forge.codesys.com/forge/talk/Engineering/thread/c45929e2f1/#e27f). The JsonData object has all inexes & parent indexes in the way I expect, everything is correctly "linked". It purely seems that the writer is incorrectly parsing said JsonData, not based on parent & child index, but on something else that breaks it and puts things at the root, instead of the specified parent index. Did you ever manage to find a solution, or another way of achieving your JSON composing? I'm currently working on Codesys V3.5 SP19 Patch 7 with IIOT Libraries SL 1.13.0.0, specifically JSON Utilities SL 1.13.0.0 (to send requests to APIs with JSON bodies using Web Client SL 1.13.0.0).
Last updated: 2026-06-08
Post by vformanek on No source code available for profinet library
CODESYS Forge
talk
(Post)
Hello, I have been using CODESYS for a while and after updating to version 3.5.18.50 the code randomly stops with this fault. Why is that ? I have tried to locate the fault in the Call Stack but I dont know what to do now... I have updated the projects properly for the version I am using. This fault started happening after like 14 days of using the new version of CODESYS.
Last updated: 2023-08-23
Post by trprsmn on "Scan Network" doesn't find CR1140 device (ifm)
CODESYS Forge
talk
(Post)
Hi, I'm watching an ifm tutorial on how to setup an industrial controller in CODESYS. I'm using an 'ecomatDisplay43inch_64bit) controller. CODESYS Gateway and PLC are both runngin (systray). However if I click "Scan Network" I can't find my controller. The only thing it finds is a "desktop" it seems (I'm using a Windows 10 on a Mac Book using VMWare, so maybe it has something to do with that?). How can I fix this? Thanks in advance!
Last updated: 2024-09-11
Post by josepmariarams on Limit Axis CNC Jerk using SMC_Polynomial_AbsMaxLocs
CODESYS Forge
talk
(Post)
Dears. Until now, I have been using CNC libraries with Codesys 3.5SP11. I was using SMC_Polynomial_AbsMaxLocs function, from CNC library, to calculate the axis jerks, interpolating splines, to limit it. Now I have passed to SP20, and the functions which calculates the zeros and the maximum-minimum and zeros of polynomials has been disapeared. Questions: -Exist any FB wich can limit the jerk of individual axis in CNC? -Exist any other functions which can calculate max-min and zeros of polynomials? Thanks
Last updated: 2026-05-22
Post by dom4u on Using PEAK CAN PCIe card (IPEH-004040) with Codesys Control RTE V3
CODESYS Forge
talk
(Post)
Some findings on this issue: PEAK CAN Driver is the same as in every PCI card from PEAK. I updated the inf file. Here are my steps: 1. Include right VendorID into the *.inf file 2. Disable Windows driver check (Disable WHQL check). This you need because 3S driver is not certified. You will find steps via google or ask chatgpt :) 3. Select: Select driver from a list and navigate to the folder. Say yes to install an uncertified driver. 4. Driver installed and device without errors I did the same with CAN Card from ESD, but here you dont need to include the vendor ID. In ANY CASE it was not successful. The RTIOwdmgeneric is not available in Codesys or anyhow accassable :( I wonder that it fails in two cases, two suppliers, two driver in the same way. How can RTIOwdmgeneric implemented into the project?
Last updated: 2024-12-20