Post by manuknecht on High Cycle Times for SoftMotion_PlanningTask when using AxisGroup
CODESYS Forge
talk
(Post)
Hi, thanks a lot for the response. I did check all these parameters, but if the PlanningTask takes up to 60 ms, I can't increase the Buffer to such values. I contacted the Codesys support with a projectarchive. Let's see if they can help. Thanks again for your great support!
Last updated: 2024-03-22
Post by calviniscoding on Publish a JSON payload via MQTT Publish (using IIot Libraries)
CODESYS Forge
talk
(Post)
Are you able to dynamically change the JSON message? As in, if wsValue or iValue is linked to some real telemetry that varies over time, will the JSON message reflect these changes? I am only able to send the values that I initialize the JSON message to
Last updated: 2024-06-18
Post by stiller on OPC UA RPI 4.8.0.0 Status Code / "out of range"
CODESYS Forge
talk
(Post)
Hello, I have an OPC-UA server with an information model. For many values, there is a defined range (e.g., 0 to 100). If a client enters a value outside this range (e.g., 120), the StatusCode should change to Bad. How can I accomplish this? Any help is appreciated! Thank you in advance. Best regards, Christian Stiller
Last updated: 2024-07-10
Post by talhaali on Persistent variables not working for Control Win
CODESYS Forge
talk
(Post)
Hi everyone, I am facing issues with persistent retain variables. It was working fine. I added a few new Persistent variables and it stopped working. If I do cold reset it holds persistent variable values. But when I close control win gracefully, and opens it again then it does not. Even, it is not saving ret file in application.
Last updated: 2024-09-10
Post by timvh on Configuring a 2's compliment
CODESYS Forge
talk
(Post)
You could create a DUT of the Type Union and add an array of 2 bytes + an Int. Then write the byte values in the array of the Union and read the Int. Or VAR iInt : INT; byHigh : BYTE := 2#1111_1111; byLow : BYTE := 2#1111_1111; END_VAR iInt := TO_INT(byHigh*16#100 + byLow);
Last updated: 2024-09-28
Post by pietrobalint on Persistent variables are not read after initialization
CODESYS Forge
talk
(Post)
Hi, I realized that if I replug the power supply the persistent variables lost their value with the new software too. Cold reset do not affect the variables value but hardware reboot still reset the values. Application Composer can't be activated. What is the solution?
Last updated: 2024-10-11
Post by andrax on CodeSys Raspberry pi I2C driver not found
CODESYS Forge
talk
(Post)
Ok, this is a test programme with ADS1115. It is currently configured for the TCA9548 muxboard. If you want to run the ADS1115 single, then change the settings to the default values: ‘Is Multiplex:’ False ‘Stage mux channel numbers:’ [0,0,0,0,0,0,0,0,0] It is also important that the libraries are installed correctly here. But should be in this project
Last updated: 2024-11-07
Post by sawicpx on CANbus Remapping PDOs During Runtime
CODESYS Forge
talk
(Post)
Hello, I am working on an application where I need to remap PDOs to a different CANopen object during runtime depending on what value is at a specific register. I have gotten to the point where I put the device into Preoperational State using the CIA405.NMT function. I then reconfigure the PDO 180x and 1a0x obejcts usings SDOs to point to a new canopen object on the device however when I go to restart the Device from PREOP to OP using the CIA405.NMT function the device is reset back to the original configuration as per the initial setup. I am wondering is there any way to change the PDOs at runtime is there some more functionaility I can access to do this. Any direction is appreciated!
Last updated: 2023-12-22
Post by fontrap on cmDongle Raspberry Pi issue
CODESYS Forge
talk
(Post)
Good morning @eschwellinger, After some research I found out that the problem is the preinstalled CodeMeter on Raspberry Pi. As I mentioned the CodeMeter was installed on the Raspberry because I use a license from other vendor that needs the CodeMeter to be installed. The problem is that when I uninstall the CodeMeter from Raspberry I am able to detect the dongle from CODESYS and everything works as it should be but now the other product can not detect its own license. When I reinstall the CodeMeter I am back to the initial problem. Is there a way to overcome this conflict through CODESYS?
Last updated: 2024-04-24
Post by timvh on FB string and naming
CODESYS Forge
talk
(Post)
I see, you want to initialize the FB. To be able to initialise it like you described, you need to add the FB_Init method to your FB. (right click on the FB, select add object --> method). Then press the arrow down, to select the FB_Init (overwrite default implementation). In the VAR_INPUT section of this method, add the variable --> Tag : STRING; Then in the code section of this method add: THIS^.Tag := Tag; // copy initial value to local variable in FB Search Google if you want to know more about FB_Init. PS, reflection + instance path, is also an option if you want to get the full name of the instance (path) of the Function Block. See: https://content.helpme-codesys.com/en/CODESYS%20Development%20System/_cds_pragma_attribute_instance_path.html
Last updated: 2024-09-30
Post by jeffgamsby on Accessing ModbusTCP addresses from python
CODESYS Forge
talk
(Post)
Hi, I am new to modbusTCP and I am trying to access Input registers from codesys (3.5.SP13). The offset is 16#0000 and I am trying to access Channel 1[24] %IW24 to pull analog values. I am using pyModbusTCP and I need to supply a modbus address and the number of registers to read. What does 16#0000 mean in terms of the actual offset, how do I translate this number plus the channel to access this info via python? Any help would be appreciated, thank you.
Last updated: 2023-09-20
Post by mputaggio on Recipe Manager - RecipeManCommands, load & write wrong values, Bug?
CODESYS Forge
talk
(Post)
Hello, We encountered the same issues on both recipe library versions 4.2.0.0 and the newest 4.3.0.0. The Arrays of structs get saved correctly but loading them restores only some indexes, while others get lost or completely wrong. We have been using the same recipes for the last two years on recipe manager vers. 3.5.17 withoud issues. There also seems to be a different behaviour in vers. 4.3.0.0 but it's still incorrectly loading the recipes. Did you find any workaround or solution? Codesys version used: 3.5.19.50
Last updated: 2023-12-15
Post by rodberna on Library for arrays
CODESYS Forge
talk
(Post)
Hi, I'm creating a program where I need to handle arrays, like: - Declare lenght variable arrays - [array(1..var) of "sometype"]. This is not possible in pure codesys, right? - Know array lenght, min, max, avg values in runtime - append/delete itens in an array - and so on Is there a library know for this in codesys. Is it possible to build our own libraries using some high level language like python or java script?
Last updated: 2024-01-10
Post by wehling-h on PI Input value
CODESYS Forge
talk
(Post)
Hi geoweil, have you tried to save changed values to remanent area or using a VAR RETAIN? After restart you have to initialize Counter with last remanent value. Depending on changes per cycle and the possibilitiy of your control unit to write remanent storage. Otherwise you need a buffering system to ensure save backup of last PI_Counter value. May you could read this Thread to get further help: https://forge.codesys.com/forge/talk/Engineering/thread/31e1c8349e/#bf48
Last updated: 2024-01-12
Post by mejak on Raspberry Pi USB HID RFID Reader - read ID in plc program
CODESYS Forge
talk
(Post)
Hello, I have an RFID reader that is detected as a keyboard. While looking for information, I came across examples using visualization. I would like to read the ID without visualization or external code in python, only in PLC. I found on the forum that you can try reading directly from potru /dev/... https://forge.codesys.com/forge/talk/Runtime/thread/24b3527036/ How to read values directly in codesys? Or maybe there is another solution? Best Regards
Last updated: 2024-01-25
Post by ojz0r on INT_TO_WORD function not working
CODESYS Forge
talk
(Post)
That calculation will not work the way you expect it to. If PumpFillSpeed is limitied to 0-50 then the only whole number would be 50/50 = 1 everything else is 0.0-0.9999... and since you are using word and integer only 50 would work since there is no representation for mantissa in integer values. Declare a temporary real variable and do the calculation and then do a REAL_TO_WORD in the DRV2Speed assignment.
Last updated: 2024-01-26
Post by ofey on two different OPC clients with different privileges
CODESYS Forge
talk
(Post)
Hi! I have usually only connected one OPC client (our system) to an OPC server created in the codesys environment on a PLC. This OPC client has a lot of write privileges. A customer also want OPC access, but I want to restrict his access to only read certain values. Do you know if this is possible inside the single codesys runtime running on a controller?
Last updated: 2024-02-01
Post by sumit on Not able to see input data coming from eip adapter on codesys
CODESYS Forge
talk
(Post)
Hello there, I have an eip adapter running (remotely) that is sending data back to eip scanner (running on codesys). I can send data from scanner (codesys) to the adapter but not getting the data back from the adapter. I have verified the incoming data on wireshark but I don't see this data in the codesys. I have tried local variable mapping and global variable mapping not variable values just stays at 0. Please guide.
Last updated: 2024-02-29
Post by dominggus on Recipe Manager - RecipeManCommands, load & write wrong values, Bug?
CODESYS Forge
talk
(Post)
I still have the same problem even when updating to CODESYS Recipes 4.3.0.0. My scenario: I'm trying to save/load an array of structs using the Visu: - Execute Command > "SaveRecipeAs" works properly - Execute Command > "LoadWriteRecipe" works not entirely: the structs of array[6] and array[7] should have been empty but were duplicates of array[4] and array[5]... the struct contains 26 variables and the array's length is 30.. Maybe there is a upper limit on recipe variable count?
Last updated: 2024-03-02
Post by ewi04 on Recipe Manager - RecipeManCommands, load & write wrong values, Bug?
CODESYS Forge
talk
(Post)
It's good that you've found a workaround. But it's bad that you need one. The array length auf my struct is 16. My struct also contains other arrays of structs. It contains a total of 1716 variables. I have tested saving and loading extensively under version 4.3.0.0. It looks good. I couldn’t find any problems. Maybe it helps to reinstall the update (see previous post). Otherwise you could try my test project (first post). This should work with version 4.3.0.0.
Last updated: 2024-03-04
Post by k4zz on Continuous Build Server
CODESYS Forge
talk
(Post)
Hallo Martin, Thank you so much for the Code example. It works really fine for .porject Types. However, I encountered a challenge when attempting to apply it to .library Types. I also tried the option to "Perform static analysis automatically after compilation" # get Project values myProject = projects.primary # Creates an active application app = myProject.active_application # build Application and run static code analysis app.generate_code() Could you please offer any insights into why this might be occurring?
Last updated: 2024-03-15
Post by k4zz on Statisch Code Analyse ausführen via Python
CODESYS Forge
talk
(Post)
Derzeit arbeite ich daran, statische Codeanalyse in unsere (CI/CD)-Pipeline zu integrieren. Konkret habe ich die statische Codeanalyse erfolgreich für .project-Typen durchgeführt, und sie funktioniert einwandfrei. Allerdings habe ich Schwierigkeiten bei der Ausführung derselben für .library-Typen festgestellt. Hierbei habe ich zwei Methoden ausprobiert: system.commands["staticanalysis", "run"].execute() # get Project values myProject = projects.primary # Creates an active application app = myProject.active_application # build Application and run static code analysis app.generate_code()
Last updated: 2024-03-18
Post by k4zz on Scripting static code analysis
CODESYS Forge
talk
(Post)
Currently, I am working on integrating static code analysis into our CI/CD pipeline. Specifically, I have successfully performed static code analysis for .project types, and it works flawlessly. However, I have encountered difficulties in executing the same for .library types. In this regard, I have tried two methods: system.commands["staticanalysis", "run"].execute() # get Project values myProject = projects.primary # Creates an active application app = myProject.active_application # build Application and run static code analysis app.generate_code() your help is greatly appreciated.
Last updated: 2024-03-18
Post by mimodia1 on I do not have any reedings in RUN MODE from MPU6050........
CODESYS Forge
talk
(Post)
Good morning, mecke96. Exactly the same thing happens to me, although I have not done the part of executing a .py file. It only reads the temperature and the counter, but the other values are zero as in your image "no readings". I have tested the MPU6050 device on an Arduino and it works. Could you tell me if you solved it?
Last updated: 2024-03-29
Post by valenting on Problem with Licenced Software Metrics
CODESYS Forge
talk
(Post)
Hi, I tried with another project, using codesys SP20 with the latest visualization installed, I can install the application on my device but it doesn't work I get an exception "invalid license metrics" and the app won't run See attached the metrics in project and allowed by license, and the logs What am I supposed to do ? Everything is in the newest version and the values are lower than allowed and nothing works...
Last updated: 2024-04-26