Post by peterned on Programatically restart Codesys OPC UA server?
CODESYS Forge
talk
(Post)
Hi, I'm using a Festo Codesys PLC (CPX-CEC-C1-V3), which is connected to a HMI panel. Both exchange data via OPC UA. Occasionally, the HMI stops displaying data, and looks as if there is no connection. If the HMI stops, the only way to make it work again is to restart the PLC. Restarting HMI has no effect. When the PLC is restarted, HMI starts working normally again. Is it possible to restart the OPC UA server from PLC code? I hope this will make fixing the HMI possible without a PLC restart. Thanks
Last updated: 2024-07-19
Post by thn-power on How to change OPC NodeId IdentifierType
CODESYS Forge
talk
(Post)
Hi Yet another OPC UA question. When setting up a OPC server using "Communcation manager" (Symbol set and information model) in Codesys the NodeId is always given as "opaque" type. At least when browsing using UAExpert. Other standard OPC objects use numeric (or string) identifier, but for some reason my variables seems to get opaque/binary type. See attached photo. How can I change this? I can't see that this is a parameter in the CodesysControl.cfg. Can this be specified in the information model nodeset? And is it possible to specify the exact numeric or string NodeId for each instance? And on a related topic, is there a way to export the OPC server nodeId's with variable name so that it can be imported in a OPC Client? The .xml files in the project folder does not seem to contain the NodeId.
Last updated: 2024-09-20
Post by gediminas on Datasource OPC UA client system failure
CODESYS Forge
talk
(Post)
I am using CODESYS v3.5 SP20 Patch 3 / Control for BeagleboneBlack SL v4.13 and after some time the OPC UA Server crashes. However, Runtime still works without any issues. The events leading up to the OPC server crash are the most suspicious: 1) Mutex deadlock detected - owner thread died, and 2) Runtime received SIGABRT. And it seems very similar with this topic except used versions - issues should be fixed with previous SP's. I can't seem to find any information about these events. Need some pointers in the right direction on how I can fix this problem.
Last updated: 2024-10-25
Post by rafa on MODBUS TCP SERVER DONT AUTO-STARTUP
CODESYS Forge
talk
(Post)
Dear all, I have a project where I have two ModbusTCP communication drivers in the application. It's working normally until a power outage or the installation panel is restarted. As soon as the PLC CPU is restarted, the Ethernet port is OK, but the TCP Server displays an "UNDEFINED" error. I can't reset the error using the diagnostic confirmation or the "mbserver.xConfirmError" bit. I noticed that the error only appears in the "mbserver.byModbusError" memory and the description is "UNDEFINED." The "mbserver.xError" memory doesn't flag an error. When using the warm restart function and then START CPU, the devices return to normal operation. The following demonstration images; The main question is: How can I make devices boot automatically?
Last updated: 2025-07-15
Post by rafa on MODBUS TCP SERVER DON'T AUTOMATIC STARTUP
CODESYS Forge
talk
(Post)
Dear all, I have a project where I have two ModbusTCP communication drivers in the application. It's working normally until a power outage or the installation panel is restarted. As soon as the PLC CPU is restarted, the Ethernet port is OK, but the TCP Server displays an "UNDEFINED" error. I can't reset the error using the diagnostic confirmation or the "mbserver.xConfirmError" bit. I noticed that the error only appears in the "mbserver.byModbusError" memory and the description is "UNDEFINED." The "mbserver.xError" memory doesn't flag an error. When using the warm restart function and then START CPU, the devices return to normal operation. The following demonstration images; The main question is: How can I make devices boot automatically? Um using Codesys Version 3.5.20.30 Patch 3+ My CPU is a Weintek Cmtx Built-int - ( CMT3092x )
Last updated: 2025-07-15
Post by joerg-schneider on SVN: "Include externals" Fehlermeldung
CODESYS Forge
talk
(Post)
Ich habe eine Bibliothek unter Subversion verwaltet und verwende Teile davon in anderen Subversion Projekten mit "Include externals". Wenn man die Bibliothek mit "Copy (Branch/Tag)" kopiert, lässt sich die Kopie nicht mehr mit "Include externals" in anderen Projekten einbinden. Es kommt eine Fehlermeldung, dass ein Pfad nicht gefunden wurde (siehe Anhang). Auch wenn man das Bibliotheksprojekt direkt auf dem SVN Server kopiert (mit Tortoise SVN), kommt die gleiche Fehlermeldung beim Versuch die Kopie mit "Include externals" in anderen Projekten einzubinden. Ich nutze Codesys 3.5.20.60 mit Codesys SVN 4.6.2.0. Wie kann man Projekte auf dem SVN Server so kopieren/verschieben, dass sie später mit "Include externals" in anderen Projekten verwendet werden können?
Last updated: 2025-07-21
Post by pernockham on Gateway in China - "Gateway not connected"
CODESYS Forge
talk
(Post)
Trying to communicate (from Europe) with/to a unit located in china, the communication seems blocked/stopped. The edge gateway is installed in a linux environment and was possible to link to my Automation server account using the "Automation service tool". However it seems the unit cannot communicate with the Automation server (a Network scan will give the message "Gateway not connected"). (I have tested the eq. setup with units locally which works.) Anyone having experience situation similar to this and if its possible to make this work? Will a VPN be needed possibly? Other tips?
Last updated: 2025-09-04
Post by alexgooi on Licensing info not available.
CODESYS Forge
talk
(Post)
Thank you for the response, The empty softcontainer does not become visible unfortunately, but I think I can get that back to working. I think I'm misunderstanding something. You are pointing to the Softcontainer number and the ticket code, I thought that I needed to fill in the virtual control containers serial code is this a misunderstanding? And if this is indeed the case, how is the link between the server (softcontainer) and the Codesys control docker container made? If I have multiple Codesys docker containers running on the same docker server, how is the correct license distributed to the correct Codesys runtime container?
Last updated: 2025-10-02
Post by kronlundo on Licensing info not available (WAGO PFC200 + Codesys V3)
CODESYS Forge
talk
(Post)
Hi! We're using a WAGO PFC200 for several projects towards the energy sector, and recently upgraded to CODESYS V3. We have the "IEC 60870-5-104 Server" package in a test program, and it works well with the package in DEMO mode. However, when we acquired a license for the "IEC 60870-5-104 Server" package and tried to add the license on the PFC200 through the license manager, we get an error (see attached file). It seems like there is no CmContainer on the device, does anyone have an idea on how to fix this? We've also contacted WAGO on this issue a while back with no feedback yet.
Last updated: 2024-06-10
Post by vformanek on Datasource OPC UA Client error ID:7012
CODESYS Forge
talk
(Post)
Hey, I am facing the same problem. Basically UA Expert and other programs work fine with the login credentials. But codesys can not use them properly. I can see the server login to it manually but when I download the program and run the datasource never runs... Currently I am facing the same Error ID: 7012 and cant get it running properly.
Last updated: 2023-11-21
Post by damian177 on OPC UA Client
CODESYS Forge
talk
(Post)
Hi, Today I ran OPC UA Client Example in 1.1.0.0 version. I opened example visualisation and I tried connected to my OPC UA Server. In first steps looks good but connection was terminate with error OpcUa_BadLicenseLimitsExceeded. I can't test OPC UA Client witohut CODESYS OPC UA Client SL license ? Regards
Last updated: 2024-08-30
Post by domebruce on Which database to use?
CODESYS Forge
talk
(Post)
We have developed a similar application few years ago with .Net and MS Sql Server. The database has about 30 tables, the more bigger tables have 2 or 3 thousands records. We can have multiple threads accessing at the same time to the DB. To garantie the data integrity we need to manage data locks and transactions. Thanks
Last updated: 2025-03-04
Post by programmer on 3.5 P20 hangs - no response
CODESYS Forge
talk
(Post)
hi imdatatas, thanks for your suggestion! I added the process execution to be sure. In the meantime I reïnstall Windows but it dind't help directly. Finally I deleted CodeMeter Runtime Server after Codesys installation. Because this Service was not able to start. And it works (for now) :)!
Last updated: 2025-06-25
Post by wbj0t on one variable signed to modbus tcp server device and modbus serial device
CODESYS Forge
talk
(Post)
Hi. Raspberry pi 4 runtime. Runtime version 4.16, IDE version 3.5.21. Is it possible write new value for variable via modbus tcp or serial devices when both enabled? As I see - not. What can I do? It is terrible restriction.
Last updated: 2025-07-17
Post by stiller on OPC-UA ApplicationUri / ProductUri
CODESYS Forge
talk
(Post)
Thank you for your answer! I'm not sure, but it seems this is not what I am looking for. I attached three pictures. The first one is from the Codesys IDE. I use an Information Model to generate an OPC-UA server. I connected via UA-Expert, and there I see the URIs I would like to change.
Last updated: 2024-05-10
Post by marek71 on Ambiguous use of name - CO136
CODESYS Forge
talk
(Post)
My PLC is WAGO PFC200 Firmware Revision 26. target After updating WAGO_Devices_and_Libraries with newer Firmware 27, CODESYS wants to update all libraries to new versions. I will only add that I did not update the Firmware in the PLC. After compiling the program, I received the following errors: ------ Build started: Application: Device.Application ------- Typify code... [ERROR] wagosyscom_internal_pfc, 1.0.2.5 (wago): FbSerialInterface_internal: C0136: Ambiguous use of name 'RTS_IEC_HANDLE' [ERROR] wagosyscom_internal_pfc, 1.0.2.5 (wago): FbSerialInterface_internal: C0136: Ambiguous use of name 'RTS_IEC_RESULT' [ERROR] wagosyscom_internal_pfc, 1.0.2.5 (wago): Initialize [FbSerialInterface_internal]: C0032: Cannot convert type 'Unknown type: 'RTS_INVALID_HANDLE'' to type 'POINTER TO BYTE' [ERROR] wagosyscom_internal_pfc, 1.0.2.5 (wago): Initialize [FbSerialInterface_internal]: C0136: Ambiguous use of name 'RTS_INVALID_HANDLE' [ERROR] wagosyscom_internal_pfc, 1.0.2.5 (wago): Initialize [FbSerialInterface_internal]: C0046: Identifier 'RTS_INVALID_HANDLE' not defined [ERROR] wagosyscom_internal_pfc, 1.0.2.5 (wago): comextra_is_tx_empty: C0136: Ambiguous use of name 'RTS_IEC_HANDLE' [ERROR] wagosyscom_internal_pfc, 1.0.2.5 (wago): comextra_get_line_state: C0136: Ambiguous use of name 'RTS_IEC_HANDLE' [ERROR] wagosyscom_internal_pfc, 1.0.2.5 (wago): comextra_is_line_available: C0136: Ambiguous use of name 'RTS_IEC_HANDLE' [ERROR] wagosyscom_internal_pfc, 1.0.2.5 (wago): COMSW_SET_MODE: C0136: Ambiguous use of name 'RTS_IEC_HANDLE' [ERROR] wagosyscom_internal_pfc, 1.0.2.5 (wago): comextra_set_line_state: C0136: Ambiguous use of name 'RTS_IEC_HANDLE' Compile complete -- 10 errors, 0 warnings Build complete -- 10 errors, 0 warnings : No download possible The problem was caused by the WagoSysPlainMem(WAGO) library in the original version 1.5.3.0 after updating to 1.5.3.1. After returning to version 1.5.3.0, the problems disappeared. Probably the version number of this library is responsible for supporting the appropriate Firmware Revision. Can anyone confirm or deny my suspicions?
Last updated: 2024-07-06
Post by mm-sceg on Runtime geht sporadisch in Störung -> RaspiPi4 reagiert nicht mehr
CODESYS Forge
talk
(Post)
Guten Tag, ich hab seit längerem das Problem, dass mein Raspberry Pi4 durch die PLC in Störung geht. Auf dem Raspi läuft eine einfache Software mit OPC UA server, InfluxDB und ein NodeRed-Server. (Und MQTT-Server) Daten werden von der PLC über OPC-UA an NodeRed übergeben. Es kann sein, dass der Raspi 2 Wochen läuft, dann geht die PLC in Stopp. Manchmal nur 2-3 Tage. Ein Neustart über Spannung aus & wieder an schafft Abhilfe. NodeRed wirft extrem viele Fehlermeldungen in kurzer Zeit. Wenn die PLC in Störung ist, kann man sich nicht mal mehr über SSH beim Raspi einloggen. Der Raspi ist aktiv gekühlt und im Normalbetrieb nicht überlastet. Ich hab einige logfiles mit vielen Einträgen die mir nichts sagen, eventuell hat hier jemand eine Idee wie ich dem Problem Herr werden kann :) Der letzte Datenbankeintrag von der SPS war am 11.11.2023 um 5:55:50 Uhr. D.h. danach muss die SPS gestorben sein. Siehe Raspi-Log im Anhang. Das LogFile von Codesys startet leider erst um 11 Uhr, weshalb weiß ich leider nicht. Vielen Dank schonmal
Last updated: 2023-11-11
Post by ewi04 on Recipe Manager - RecipeManCommands, load & write wrong values, Bug?
CODESYS Forge
talk
(Post)
I'm getting closer to the error. The combination of STRUCT and ARRAY probably causes the strange behavior. As soon as the ARRAY is followed by a variable, the problem arises. Examples: X: ARRAY[1..2] OF INT; // okay Y: ARRAY[1..2] OF STRUCT; // problem Z: STRUCT; Z.ArrayOfInt[1]; // okay Z.ArrayOfStruct[1].Variable // problem // *update - array of array also causes the error A: ARRAY[1..2] OF ARRAY[1..4] OF BOOL; // problem I can't be the only one who has this problem. Or? Maybe there is a solution. Anyone? Or is it a bug after all?
Last updated: 2023-11-17
Post by gilbertamine on Comparing Arrays of structure
CODESYS Forge
talk
(Post)
Hi Everybody, I'm looking for a simple way of comparing two array of a structure. My structure is define like this : TYPE Positions_T : STRUCT PosX: DINT; PosY: DINT; PosZ: DINT; END_STRUCT END_TYPE I have multiples Var : ARRAY [0..220] OF Positions_T, that I need to compare quickly. I don't really want to do a Loop that goes by every 220 points and compare each one of them so I was wondering if there is another way. I came accross the MEM.Compare function, but it require to know the size in Bytes of the memory, and I don't know how to do that... Has anybody an idea on how to do the comparing easily ? Thanks in advance
Last updated: 2024-08-22
Post by peterkcontrols on Copying 2 byte word to output
CODESYS Forge
talk
(Post)
Hello. I am using codesys 3.5. I would like to know if it is possible to set a variable to an output without declaring in. I have defined a STRUCT and within this struct I have a Struct for inputs called I and a struct for outputs called O. I have declared a variable of the type of this Struct, I would like to set or alias the value in this variable to an input/output value of an IO block that has a module on the ethernet tree. Is it possible to copy the contents of %IW0 -> STRUCT.I ? The size of both of these is 2 bytes. I understand that I can declare a variable with the input like Input01 AT %IX0.0 : BOOL; However how can I make STRUCT.I.D00 AT %IX0.0? Is this possible? Thanks
Last updated: 2025-03-03
Post by m83coding on Raspberry Pi Codesys SPI Master
CODESYS Forge
talk
(Post)
Hello, I am trying to control shift registers 74HC596 and 74HC165 via Raspberry PI with SPI interface. So far I did it with a Microcontroller and now I wanna upgrade my Projekt with Raspberry Pi and Codesys Software to be more flexible. I tried to adapt PiFace Function Block to just send or recive a 8 bit via SPI interface of the my Raspberry Pi. With following code (see attached screenshots) * PLC_PRG * PiFaceDigital * PiFaceDigital.write8 * PiFaceDigital.read8 I have a signal at SCK and MOSI pin of the PI, so far so good. But I really struggle with the unterstanding of the code. Is there some detailed description of each line of code? Or is there somebody in the community who can explain each line of code? Or is there a more simple way to send / recive 8 bit via SPI? Manuel
Last updated: 2024-04-23
Post by i-campbell on Official MQTT-Client: MAX_RECEIVE_BUFFER_SIZE_EXCEEDED
CODESYS Forge
talk
(Post)
I can't answer why it's not resetting, but from the description of g_udiMaxReceiveBufferSize, I would guess the sum of sizes of the mqtt packets received in one cycle exceeded this value. So the answer may be to increase that parameter. https://content.helpme-codesys.com/en/libs/MQTT%20Client%20SL/Current/MQTT-Client/Common/Params/MQTTParam.html https://content.helpme-codesys.com/en/CODESYS%20Development%20System/_cds_dlg_library_parameter.html
Last updated: 2023-09-26
Post by leon78 on Codesys 3.5 SP17 Patch 2 CheckBounds (POUs for Implicit Checks)
CODESYS Forge
talk
(Post)
Hello! I use CheckBounds (POUs for Implicit Checks). But I have a problem. I use an array as an VAR_IN_OUT of Function Block. If I try to monitor the array of variable length ([* ]), its does't work. The CheckBounds POU isn't called. If I use the array of fixed lenght ([lower..upper]), the CheckBounds POU is called. Why?
Last updated: 2023-11-14
Post by leon78 on Codesys 3.5 SP17 Patch 2 CheckBounds (POUs for Implicit Checks)
CODESYS Forge
talk
(Post)
Hello! I use CheckBounds (POUs for Implicit Checks). But I have a problem. I use an array as an VAR_IN_OUT of Function Block. If I try to monitor the array of variable length ([* ]), its does't work. The CheckBounds POU isn't called. If I use the array of fixed lenght ([lower..upper]), the CheckBounds POU is called. Why?
Last updated: 2023-11-14
Post by jmfernandes on OpenDir always in error
CODESYS Forge
talk
(Post)
Hello just to give more feedback the error I get is "ERROR_UNKNOWN :represents raw value of 5110" in File.DirOpen. The xDone never gets true, and I never get the listing of files (csv files in this case). In the hDir i get the value of 0 for a DWord!?
Last updated: 2024-07-31