Post by ahuckphin on Issues with Modbus Slave with Raspberry Pi
CODESYS Forge
talk
(Post)
I have a DFRobot RS485 temperature & humidity sensor (SEN0438) connected to my Raspberry Pi via a USB to RS485 adapter. I am able to connect and read the sensor data when running a python code locally. However in Codesys, I encounter this error "A bus error has occurred." and "There was no response in time". Could this be because of Modbus Server Channel and Modbus Server Init configuration on my part? Admittedly I am new to Codesys. To get to this stage, I: 1. added some lines to CODESYSControl_User.cfg 2. added "Modbus_COM" in Codesys and set "Serial Port Configuration" under "General" 3. added "Modbus_Master_COM_Port" in Codesys and checked transmission mode is set to "RTU" 4. added "Modbus_Slave_COM_Port" in Codesys and checked server address is set to 1 (also set 1 in my sensor) 5. added 1 channel and 1 init for "Modbus_Slave_COM_Port" under "Modbus Server Channel" and "Modbus Server Init"
Last updated: 2024-07-10
Post by rohitk on CoDeSys libraries for BECKHOFF EL7332/EL7342
CODESYS Forge
talk
(Post)
Hi, step 1 : go to beckhoff website, go to required IO card, go to download option in that, go to XML donlowad and download the file Step2 : Go to codesys software, go to tools - deviceRepository - install that downloaded file.
Last updated: 2023-08-24
Post by lostcontrol on Remote Ethernet/ip Adapter communication with scanner running on codesys
CODESYS Forge
talk
(Post)
is the bus running.? what type of values/IO is the adaptor providing? do you have a map of the data layout? are you actually looking at the right offset?
Last updated: 2023-12-16
Post by matt-s on HMI Pushbutton/Move Instruction
CODESYS Forge
talk
(Post)
I know, that is not the issue though. The issue is the HMI_Blower_Auto_PB variable not changing to false. I do not have the IO modules plugged in yet, that is why there are NaN values for those variables. That should not affect this.
Last updated: 2024-01-25
Post by elektron785 on CAN-Bus in Demo-Version
CODESYS Forge
talk
(Post)
Ja, Gerätebaum ist grün/orange (siehe Bild). IO-Variablen sind gemappt und im Programm verwendet. Ich habe mal noch ein paar Bilder zum Status angehangen.
Last updated: 2024-02-07
Post by timvh on Timeout Error in Modbus Communication with WAGO PFC200 and iEM2050 Meter using 750-652 Module
CODESYS Forge
talk
(Post)
I'm not sure, but maybe you have to configure the 750-652 first with the WAGO-IO-CHECK software to set it in RS485 mode?
Last updated: 2024-02-27
Post by radekkoza on How to use GPIO (and IOT2000 IO-Module) with CODESYS Control for IOT2000 SL ?
CODESYS Forge
talk
(Post)
Hi I have this question I can't find anywhere what pins Di3 and Di4 have all the rest work . I have a 10 input iot2000 card
Last updated: 2024-05-05
Post by radekkoza on How to use GPIO (and IOT2000 IO-Module) with CODESYS Control for IOT2000 SL ?
CODESYS Forge
talk
(Post)
Hi I have this question I can't find anywhere what pins Di3 and Di4 have all the rest work . I have a 10 input iot2000 card
Last updated: 2024-05-05
Post by corriibme on Profinet IO-link master - IODD files
CODESYS Forge
talk
(Post)
I am having the same problem right now. Could you please share more information if you were able to solve the problem?
Last updated: 2024-05-05
Post by radekkoza on How to use GPIO (and IOT2000 IO-Module) with CODESYS Control for IOT2000 SL ?
CODESYS Forge
talk
(Post)
Hi I have this question I can't find anywhere what pins Di3 and Di4 have all the rest work . I have a 10 input iot2000 card
Last updated: 2024-05-05
Post by tgf2024 on Dynamic I/Os Mapping
CODESYS Forge
talk
(Post)
Hi Jinlee, how are you? I have similar application requirements on my project. I have tried dynamic mapping, but the code cannot detect the IO module change when I did hot switch. Do you find the way of how to identify the module change dynamicly? Thanks.
Last updated: 2024-08-15
Post by mondinmr on First IO address of a CAADiagDeviceDefault.
CODESYS Forge
talk
(Post)
I have a device CAADiagDeviceDefault: IoConfig_Globals.Axis_A In our library, we perform introspection of the Etc_SlaveDiag. In that case, we have connectors, and by searching for them by address, I can find them in the IO mapping using the offset and size provided by EtherCAT. However, a Lenze i700 drive, instead of placing the IO mapping in the Etc_SlaveDiag device, places it in a sub-device CAADiagDeviceDefault. So, when I perform introspection, I cannot find the IO correspondences. Yet, in the CAADiagDeviceDefault, I do not find the connectors and cannot do the matching. Is there a way with a pointer or reference to a CAADiagDeviceDefault to obtain the address of the first input and the address of the first output? This is because we have our own motion library with many EtherCAT devices that automatically configure the mappings, but I can't manage to do so with the Lenze i700.
Last updated: 2024-08-22
Post by timvh on Readable IO names
CODESYS Forge
talk
(Post)
IF you create an ENUM {attribute 'qualified_only'} {attribute 'strict'} TYPE E_IO : ( FIRST := 0, SECOND := 1 ); END_TYPE You should be able to access the array items like: IOCard_OUTPUT[E_IO.FIRST]
Last updated: 2024-09-28
Post by ton on Beckhoff EK series cannot detect but BK1120 detect
CODESYS Forge
talk
(Post)
Hi, I guess you don't have the right xml file. Download Beckhoff_EtherCAT_BKxxx_MDP.zip from https://download.beckhoff.com/download/configuration-files/io/ethercat/xml-device-description and install these in Device Repository.
Last updated: 2024-11-01
Post by hyys12 on CODESYS 3.5 dicovery of PLC modules
CODESYS Forge
talk
(Post)
I would say that I kind of got an explanation though this document on the WAGO PLC. https://techdocs.wago.com/io-system/750_753/system/en-US/index.html#92248203
Last updated: 2024-12-11
Post by codesysbeginner on Enable and Disable Project IO programmatically
CODESYS Forge
talk
(Post)
@eschwellinger Somehow this code doens't work for me in Codesys V3.5.19. Is this code supposed to work in simulation mode as well?
Last updated: 2025-03-03
Post by libichj on Raspberry Pi: List of available drivers / libraries
CODESYS Forge
talk
(Post)
Is it possible to renew the urls in your post? Especially fo "Arduino UNO IO Device Description and Library"? Thank you for reply.
Last updated: 2025-03-15
Post by atone on Change IO-Link Device Interface connected to a Profinet-Slave at Runtime
CODESYS Forge
talk
(Post)
OK, I figured out that I can simply define all the sensors as 16 bytes IN/OUT, even if they are not all used.
Last updated: 2025-03-19
Post by fabian on v3.5 SP19 - Modbus TCP Devices - Channel Limit?
CODESYS Forge
talk
(Post)
Hi all, Is there an update on this topic? Same problem here, I can not add more than 10 Modbus-Slave channels. Is there a workaround? Many thanks! Fabian Codesys 3.5.19 SP2, Modbus 4.3.0.0, Name: Modbus TCP Slave Hersteller: 3S - Smart Software Solutions GmbH Kategorien: Modbus TCP Slave Typ: 89 ID: 0000 0005 Version: 4.1.0.0 Bestellnummer: - Beschreibung: Ein Geraet, das als Slave für einen Modbus TCP Master konfiguriert ist. Version Konfiguration 3.5.11.0
Last updated: 2023-08-28
Post by rh-pk on v3.5 SP19 - Modbus TCP Devices - Channel Limit?
CODESYS Forge
talk
(Post)
Hello Vincent, I don't have 75 channels but it works for me as described above without any problems. There is also a parameter MAX_MODBUS_CHANNELS in the library parameters for the IoDrvModbusTCP module. The default value there is 100. Perhaps you are reaching the limit there? The value can be adjusted accordingly. I assume that this value is not accepted in the input dialogue and therefore the 'fixed' limit value 10 is used.
Last updated: 2024-04-10
Post by yofi on Configuring an Encoder
CODESYS Forge
talk
(Post)
I have a raspberry pi trying to add encoder to it using that free encoder node. I simply dont understand where the encoder channel A/B suppoded to be mapped when i got to I/O mapping on encoder I get nothing to where to set the channels for the encoder or is there any blocks from a library or how is it that you use an encoder with Codesys it doesn't seem clear at all
Last updated: 2024-05-25
Post by cfam on Codesys Control for PLCnext SL, Bus not running
CODESYS Forge
talk
(Post)
Good day I would appreciate it if you can give me some advice on how to fix my "Bus Not Running Error". I am Using Codesys 3.5 SP20 and Codesys Control PLCnext SL V4.12.0.0. Codesys control was installed on the device and I can log into it but it seems that it does not pick up the PLC or the IO attached (Please see attached Image). The Bus Cycle Task of the AXL F 2152 is set to Main Task and the "Always update Variable" is Enabled on each IO Module. My Main Task interval is set to 100ms and Priority is set to 0. I have tried other options and none seem to work. Your response to this issue will be highly appreciated.
Last updated: 2024-08-12
Post by cfam on Codesys Control for PLCnext SL, Bus not running
CODESYS Forge
talk
(Post)
Good day I would appreciate it if you can give me some advice on how to fix my "Bus Not Running Error". I am Using Codesys 3.5 SP20 and Codesys Control PLCnext SL V4.12.0.0. Codesys control was installed on the device and I can log into it but it seems that it does not pick up the PLC or the IO attached (Please see attached Image). The Bus Cycle Task of the AXL F 2152 is set to Main Task and the "Always update Variable" is Enabled on each IO Module. My Main Task interval is set to 100ms and Priority is set to 0. I have tried other options and none seem to work. Your response to this issue will be highly appreciated.
Last updated: 2024-08-12
Post by shafiq-dsc on Beckhoff EK series cannot detect but BK1120 detect
CODESYS Forge
talk
(Post)
Dear Support, I have i950 wants to connect with Beckhoff EtherCAT coupler BK1120. There are 2 GSD files for BK1120. 1. BK1120 without MDP.(EtherCAT ESI Device Description (XML)) 2. BK1120 with MDP. (EtherCAT BKxxx (MDP) configuration files) When connecting the BK1120 with i950, scanned devices detects BK1120 without MDP from ESI No1 above. But the KL1408 & KL2408 not detect because they have ELxxxx IO type. When manually insert BK1120 with MDP, the KL1xx8 is able to add manually also but the error shows and Install Missing Descriptions appears. The questions; 1. Why the error occurs? 2. Can the i950 connect with KLxxxx IO type or not? Regards, Shafiq
Last updated: 2024-10-25
Post by z3r091 on EtherCATStackLibrary - CmpSysEthernet Unaufgelöste Referenz
CODESYS Forge
talk
(Post)
Guten Morgen, ich habe ein Problem mit dem Lesen von IO Link Geräten. Wir nutzen einen Festo IO-Link Master den ich mittels der Funktionen ETC_ADS_IoLinkRead und ETC_ADS_IoLinkWrite lesen und schreiben möchte. Dazu implementiere ich die Bibliothek EtherCATStackLibrary 4.6.1.0. Hier geht schon das erste Problem los. Diese Bibltiothek möchte eine weitere Bibliothek nutzen, die "CmpSysEthernet". Diese muss ich über die Platzhalter manuell auf "SysEthernet 3.5.19.0" linken. Dann sind erstmal keine Fehler mehr vorhanden und das Projekt lässt sich übersetzen. Beim oder vor dem laden in die (Eckelmann) Steuerung, bekomme ich dann aber Fehler über unaufgelöste Referenzen, über Funktionen aus der SysEthernet Bibliothek (siehe Screenshot). Hat da jemand eine Idee oder Lösung?
Last updated: 2025-01-31