Post by expertplas on No connection to opc server from codesys opc client CODESYS Forge talk (Post)
Hello, we have aproblen to connect our CODESYS OPC Client to the OPC Server. We installed the client according the CODESYS manual. We can browse the server and variables can be linked to the PLC. I created a self signed certificate for the CmpOPCUAClent as described. The server has a cerificate also. I copied the certificates to the trusted zone of server and client. But when it comes to data exchange we get an error message. "Communication error in data source OPC UA Library. Error ID : 7001 German : "Kommunikatinsfehler inder Datenquelle OPC UA -Bibiothek. Es wurde kein genauer Fehler angegeben. Fehler ID : 7001" It semms that there is no cerificate exchange. We are working with CODESYS 3.5 SP19 Patch 5. Can anyone here say something about this error or has an idea for a solution? Thanks.
Last updated: 2024-08-19

Post by micik on Reverse bytes in an array CODESYS Forge talk (Post)
Hello, I'm getting the data in Codesys that is an array of 8 bytes. From this array, I need to foram LREAL number, however, because of different endiannes I need to reverse bytes in this array and then copy to a LREAL variable. For this I'm using a loop and it works OK. I wonder if there is a built in function to do this. I have found CAA Memory library but it has functions like reverse bytes in DWORD. But it seems it doesn't have what I need. https://content.helpme-codesys.com/en/libs/CAA%20Memory/Current/CAA_Memory/Reverse-Bit-Swap-ByteWord-order/ReverseBYTEsInDWORD.html What I need is a function to reverse bytes in an 8 byte array, or something similar.
Last updated: 2024-08-22

Post by micik on Reverse bytes in an array CODESYS Forge talk (Post)
Hello, I'm getting the data in Codesys that is an array of 8 bytes. From this array, I need to foram LREAL number, however, because of different endiannes I need to reverse bytes in this array and then copy to a LREAL variable. For this I'm using a loop and it works OK. I wonder if there is a built in function to do this. I have found CAA Memory library but it has functions like reverse bytes in DWORD. But it seems it doesn't have what I need. https://content.helpme-codesys.com/en/libs/CAA%20Memory/Current/CAA_Memory/Reverse-Bit-Swap-ByteWord-order/ReverseBYTEsInDWORD.html What I need is a function to reverse bytes in an 8 byte array, or something similar.
Last updated: 2024-08-22

Post by jonathan1321351 on IO-Link write parameters Ethernet/IP CODESYS Forge talk (Post)
I want to read and write parameters of an IO-Link device using acyclic messages. I have a Cube67+ in Ethernet/IP, connected to an IO-Link master. In the datasheet, I can find the parameters required for the message (Service, Class, Instance, etc.). I see the function block "Set_attribute_single" in the "EthernetIP Services" library, but I'm not sure how to correctly send the index and sub-index for the IO-Link device. The class in the datasheet is 0x80 for the IO-Link Parameter Object, but it’s not present in the CPIClass enum. Is there another function block more suitable for configuring IO-Link devices? (similar to "iol_call" in PROFINET or what’s used in EtherCAT).
Last updated: 2024-09-02

Post by jonathan1321351 on IO-Link read/write parameters Ethernet/IP CODESYS Forge talk (Post)
I want to read and write parameters of an IO-Link device using acyclic messages. I have a Cube67+ in Ethernet/IP, connected to an IO-Link master. In the datasheet, I can find the parameters required for the message (Service, Class, Instance, etc.). I see the function block "Set_attribute_single" in the "EthernetIP Services" library, but I'm not sure how to correctly send the index and sub-index for the IO-Link device. The class in the datasheet is 0x80 for the IO-Link Parameter Object, but it’s not present in the CPIClass enum. Is there another function block more suitable for configuring IO-Link devices? (similar to "iol_call" in PROFINET or what’s used in EtherCAT).
Last updated: 2024-09-04

Post by jacobwago on v3.5 SP19 - Modbus TCP Devices - Channel Limit? CODESYS Forge talk (Post)
Hello, I have experienced the same issue as described above but for the Modbus Serial configurator. Looking for a solution. In v3.5 SP19 Patch 7 the Modbus Serial Master Slave configurator has a "virtual" limit of 10 channels. In v3.5 SP18 Patch 5 this virtual limit does not exist. I can successfully copy back and forth from 18 to 19 with out any build error. However, this is not a good solution for our customers. What is even more confusing is that the IoDrvModbus library is the same version (4.3.0.0) for both SP18 and SP19. Please help in providing a fix to the virtual channel limit of 10 in SP19. Thanks,
Last updated: 2024-09-29

Post by jeroenaero on CodeSys Raspberry pi I2C driver not found CODESYS Forge talk (Post)
Hello, We have a problem with CodeSys on a raspbery pi with an ADS1015 analog to I2C module. It can't find the I2C device on the i2c bus, it says No I2C Driver Found. When we use the RPI terminal we can find the I2C device and read it out. The i2c-1 bus is also accessible from codesys. The device address of the Analog to I2C module is 0x48. Can someone have a look what the problem is? i submitted the screenshots in the attachments. i also include the device description and library.
Last updated: 2024-11-07

Post by dsa28 on OPC UA subscriber not operational CODESYS Forge talk (Post)
Hi, Thanks for the reply. Please note that the information and links provided are related to OPC UA Client/Server. My problem was related to OPC UA Pub/Sub. In the end I have managed to establish OPC UA Pub/Sub communication between Codesys and TwinCAT systems. Keep in mind that OPC UA Pub/Sub example is not provided in the latest library version 1.1.0.0. The user needs to download the previous version to get the example. During the configuration I ended up with some doubts regarding the usage of IEC_ARRAY type in the dataset definition (see attachment). Can you please give more information on how to use this type? Many thanks.
Last updated: 2024-11-29

Post by arcadium on Library ENUM text representation in visualization CODESYS Forge talk (Post)
Hello, Maybe someone could help with this. When I add ENUM to a text field I get the number instead of the text. For my own ENUM variable I have declared and enabled text list value is displayed as text, but I need enum text displayed from softMotion and other internal FB's. In the picture I have one of desired ENUM variable setup, but in the visu I have number, but in the watch window it's text. There is probably some checkbox to tick, but was looking for an hour, can't find a solution. Would apreciate some help
Last updated: 2024-12-24

Post by arcadium on Library ENUM text representation in visualization CODESYS Forge talk (Post)
Hello, Maybe someone could help with this. When I add ENUM to a text field I get the number instead of the text. For my own ENUM variable I have declared and enabled text list value is displayed as text, but I need enum text displayed from softMotion and other internal FB's. In the picture I have one of desired ENUM variable setup, but in the visu I have number, but in the watch window it's text. There is probably some checkbox to tick, but was looking for an hour, can't find a solution. Would apreciate some help
Last updated: 2024-12-24

Post by rossanoparis on Internal Error (ARM): Unsupported conversion! With new version v3.5 SP21 CODESYS Forge talk (Post)
I have updated CODESYS development tool to the version v3.5 SP21 (64bit) The previous version was v3.5.20.40 Compiling an existing application with the new evelopment tool I get the following error. kunbusiodrvrevpibridge, 1.4.1.0 (kunbus gmbh): IoDrvScanModules [IoDrvRevPiBridge](Line 51, Column 1 (Impl)): Internal Error (ARM): Unsupported conversion! This error was not reported in the previous compiler version and is now highlighted in a third-party library, which I cannot change or modify. The error is due to the following conversion: m_udiError := TO_UDINT(excCode); . The excCode variable is a system type, declared as shown below, and should be converted to a UDINT excCode : __SYSTEM.ExceptionCode; m_udiError: UDINT; . I would appreciate it if someone could provide feedback on this issue.
Last updated: 2025-04-15

Post by qkkk on Device Scan CODESYS Forge talk (Post)
Hello all, I have developed a custom I/O driver in CODESYS that communicates via a Unix Domain Socket. In my DeviceDescription.xml, I have set up the following: <scan supported="true"> <scanfbinstance fbname="IOScanDevice"> The goal is to allow the user to scan for connected I/O modules from the CODESYS GUI ("Scan for Devices") and automatically populate the device tree with detected submodules.</scanfbinstance></scan> The function block IOScanDevice is implemented in the driver library and added to the main device's FB instances. However, when I initiate the scan from the GUI, nothing appears to happen the function is not executed. Is there an example project or driver (open source or from CODESYS Forge) that demonstrates a working custom scan implementation?
Last updated: 2025-05-26

Post by fdmartello on Unable to compare projects containing alarm manager 4.5.0.0 CODESYS Forge talk (Post)
Hello. In Codesys version 3.5.19.50 when comparing two projects that have an "Alarm Configuration" obj from the Alarm Manager library vers. 4.5.0.0 the attached error pops up. This originally happened with two projects that I converted from vers. 3.5.17.30 so, thinking it was some conversion issue, I created two clean projects directly in 3.5.19.50 using the Standard Project template and only added the Alarm Configuration objects in them. The result is the same and the only way I found that allowed me to compare them is by deleting the incriminated object in one of the two projects. Has anyone else encountered this issue? Best regards
Last updated: 2024-01-19

Post by mait-tim on Drive communication errors CODESYS Forge talk (Post)
With a machine I'm working with i get a communication error when I'm updating some softstop limits. As soon as I update the code the drives do not want to operate. Using the MC_readStatus I'm receiving errors as soon as i want to start a movement. Using MC_ReadAxisError i see that i receive error 131, no response. With a SMC3_ETC_ReadParameter_CoE i do not recieve any driver errors. Does anyone know how i can figure out what the error is and how to solve it. When i go back to the old software no errors occur. Im working with a legacy machine running a Beijer PLC with some Mitsubishi drives. running on Codesys 3.5 SP10. the runtime version is probably 3.5.3. The drives are all Ethercat Drives (CoE). All using the SM3_drive_ETC libary and the SM3_basic library.
Last updated: 2025-12-22

Post by husarz17 on How change Unity-ID in TCP Modbus Slave CODESYS Forge talk (Post)
My codesys is 3.5.21.30. I am using function ModbusServer from library ModbusTCP_Slave. The reason is that I need share 9000 Holding registers. By standard configuration it is only 4096. fbMbTcpDevice: ModbusTCP_Slave.ModbusServer; fbMbTcpDevice( wPort := 502, pInputData := ADR(awInputReg), pOutputData := ADR(awHoldingReg), uiInputDataSize := 10, uiOutputDataSize := 9000, xEnable := TRUE, tTimeout := 10000, InterfaceName := "eth0", xBusy => xBusy, xError => xError, byClientConnections => byConnections ); Ethernet port is cofigured: Network interface: eth0 IP address: 10.10.22.55 Subnet maskL 255.255.255.0 Default gateway: 0.0.0.0 And it only works when I am reading registers with ID 255 by Modbus Poll. Any other IDs don't work. The actual TCP client device try to read registers with ID 1 and I can't change it... Thanks in advance for your help!
Last updated: 2026-04-01

Post by wbj0t on tool 'update raspberry pi' unavailable CODESYS Forge talk (Post)
Doesnt matter. I have installed sp20 with latest RP 4.13. Same problem. Anyway My large project in RP 4.10 and SP 19 and I need these versions and use same installation programm for Codesys IDE and RP4 package. I did install again, because my SSD broke and now cant update raspberry... I dont know how to translate correctly project to newest version - there are 52769 errors and incompatabilities: after updates libraries anyway some errors still because of devices... I found solution with .deb file from raspberry package - dont need IDE anymore for update raspberry.
Last updated: 2024-09-27

Post by baltzer on ICertificateVerifier.VerifyCertificate doesn't appear to override an ERR_CERT_HAS_EXPIRED rejection in TCP_Client.Upgrade() CODESYS Forge talk (Post)
Setup: Net Base Services (NBS), TCP_Client + TLSContext, ePurpose := CLIENT_SIDE, connecting to a third-party embedded device (Velux KLF200 home automation gateway) whose factory-installed TLS certificate expired on 2026-07-12 and has no user-facing renewal path. Tested on both CODESYS Control for Raspberry Pi SL (3.5.19.0) and CODESYS Control Win V3 x64, with identical results on both. Goal: Accept the peer's expired certificate via a custom ICertificateVerifier implementation, since the certificate itself can never be replaced. Implementation: FUNCTION_BLOCK FB_MyCertVerifier IMPLEMENTS NBS.ICertificateVerifier VAR udiCallCount : UDINT; aeCurStateLog : ARRAY[0..9] OF NBS.RTS_IEC_RESULT; END_VAR METHOD VerifyCertificate : UDINT VAR_INPUT hCert : NBS.RTS_IEC_HANDLE; eCurState : NBS.RTS_IEC_RESULT; END_VAR IF udiCallCount < 10 THEN aeCurStateLog[udiCallCount] := eCurState; END_IF udiCallCount := udiCallCount + 1; VerifyCertificate := 0; // also tried: VerifyCertificate := eCurState; Wired in via tlsContext.itfCertVerifer := certVerifier at declaration time, alongside itfTLSContext := tlsContext set at TCP_Client's own declaration (per an earlier forum thread here on ensuring inline start-values on FB-typed variables are actually honored when nested one level deep - that fix was needed and worked correctly for getting the handshake to start at all). Observed: - VerifyCertificate is confirmed called exactly once per connection attempt (via the call counter above). - eCurState passed in = 0x709 = ERR_CERT_HAS_EXPIRED - correctly reflecting the actual state of the peer's certificate. - Packet capture confirms the full TLS 1.2 handshake completes correctly at the wire level: ClientHello -> ServerHello -> Certificate -> ServerKeyExchange -> ServerHelloDone -> our ClientKeyExchange/ChangeCipherSpec/Finished -> server's ChangeCipherSpec/Finished. Both sides successfully complete the cryptographic handshake. - Despite this, TCP_Client.Upgrade() subsequently returns NBS.ERROR.CONNECTION_ERROR, and the connection is torn down with a plain TCP FIN (not a TLS alert) roughly 7-8ms after our side ACKs the server's Finished message. - TCP_Client.eErrorID (inherited from LCon) remains NO_ERROR throughout - the failure is only visible via Upgrade()'s return value. - Returning 0 (ERR_OK/ERR_CERT_OK - confirmed via the CmpErrors2 Interfaces documentation that these are literally the same value) makes no difference. - Echoing eCurState back unchanged (on the theory that this callback might work like mbedTLS's native verify callback, where the incoming state is a flags value to be cleared/modified and returned, rather than paired with a separate fixed "accept" sentinel) also makes no difference. - Identical result across udiVerificationMode := 0, 1, and 2. - Importing the peer's certificate into the runtime's trusted certificate store via cert-import trusted makes no difference either. - With itfCertVerifer left at its default (no custom verifier) and udiVerificationMode := 2, the underlying engine sends its own fatal TLS alert (handshake_failure) immediately after receiving the peer's Certificate message - suggesting built-in validation may reject at the record layer independent of whether a custom verifier is even present. Questions: 1. Is there an additional step required for a custom ICertificateVerifier to actually override an ERR_CERT_HAS_EXPIRED (or more generally, any ERR_CERT_*) rejection, or is certificate validation enforced unconditionally for a CLIENT_SIDE TLSContext regardless of what the verifier returns? 2. Is 0/ERR_OK genuinely the correct "accept" return value for VerifyCertificate, or does it expect something else (a specific bit pattern, a different constant, a value that must be computed from hCert itself)? 3. Is there a supported way to connect to a peer presenting a certificate that is both self-signed and expired, short of the peer issuing a new certificate? Happy to share the full packet captures or additional test combinations if useful. Also worth noting for anyone finding this thread later: a maintained Node-RED library for this same device (node-red-contrib-velux-klf200, forked to handle this exact expired-certificate situation) solves it by disabling built-in TLS validation entirely (rejectUnauthorized: false) and doing fingerprint-based pinning by hand after the handshake completes, rather than relying on a validation callback - which may be the more realistic approach here too if ICertificateVerifier genuinely can't override this class of rejection. Thanks in advance /Jørgen Disclosure: most of the CODESYS code and this investigation was developed with the help of Claude (Anthropic's AI assistant) - the state machine design, SLIP/checksum implementation, and debugging methodology (including the packet capture analysis) were worked through in an extended back-and-forth with it. Posting here because we've run out of self-serviceable options and this now looks like it needs input from someone with visibility into NBS's actual implementation.
Last updated: 2026-07-26

Post by reinier-geers on License problem gateway CODESYS Forge talk (Post)
The hole setup is made by 3s. So its a comination of one not two. If Epis decide not to support extra licence whats then the funtion of providing an option with a single license ?? So the idee by 3s has a flod. Epis change the system to add the Stick. I send controller inc stick to Epis. On my software i can see the stick. An then you tel me i need a other license to use an license ?? Makes completly no sense. Codesys should be flexible but is not. I tried Delta. But has no HMI and has its own Codesys ?? Why ?? Then i tried Crist. The block there own system by a password. But dont know the password and cant switch it off. At the end the want me to pay for support to solve ther own made problem. So i send it al back. The extra license is adviced by 3s . Now a few month later still no working solution.
Last updated: 2024-05-01

Post by danp1406 on Question about Demo License limitations for Modbus TCP communication and Fieldbus Instances CODESYS Forge talk (Post)
Hello everyone, I am currently working with CODESYS Virtual Control for Linux running in Docker on a Debian virtual machine. I am deploying my application using Deploy Control SL, and in my project I am using the ModbusFB library to implement Modbus TCP communication. My setup is the following: I am trying to establish a Modbus TCP connection between a virtual PLC (CODESYS acting as Modbus TCP Client/Master) and a Siemens S7-1200 PLC acting as a Modbus TCP Server. From the Debian VM, I can successfully ping the S7-1200 and verify that port 502 is open using tools like nc. Network-wise, everything appears to be correct. However, when running the application in CODESYS, I receive messages such as “Demo mode for Modbus/TCP Master started. Will expire and stop!” and socket errors like “ClientSocket.UpdateStatus socket error 111 disconnecting.” The ClientTCP block from the ModbusFB library attempts to connect, but the connection does not remain stable. My main question is whether the CODESYS demo license explicitly limits or interrupts Modbus TCP Master communication. Is it expected that in demo mode the runtime will automatically close sockets after some time or prevent stable Modbus TCP connections? I would like to confirm whether this behavior is normal when using ModbusFB in demo mode, or if I should continue troubleshooting the configuration. Additionally, I would like clarification regarding the “fieldbus instances” mentioned in CODESYS licensing options (for example, 2, 4, or 16 instances). What exactly is considered one fieldbus instance? Does one Modbus TCP Client block count as one instance? Does each active connection to a different device count separately? Do Modbus TCP Master and Server count independently toward the total number of instances? Finally, I would appreciate clarification on any other practical limitations of demo mode when using industrial communication libraries such as ModbusFB. Are there limits on the number of connections, number of requests, or communication duration? I am trying to determine whether demo mode is sufficient for testing a virtual PLC communicating with a Siemens S7-1200 over Modbus TCP, or whether a full license is required even for this kind of validation scenario. Thank you in advance for any guidance.
Last updated: 2026-02-25

Post by r-niedermayer on OPC UA subscriber not operational CODESYS Forge talk (Post)
Hi. As far as projects in "old version"s are concerned, these can be upgraded to newer versions at any time. To do this, the device must be updated accordingly and the copilers and library versions must be adapted. You can find instructions on how to proceed in the online help/FAQ: https://content.helpme-codesys.com/en/CODESYS%20Development%20System/_cds_changing_compiler_version.html https://content.helpme-codesys.com/en/CODESYS%20Development%20System/_cds_cmd_update_device.html See also 4.3.22.4 "How to open an Example Project" within the following pdf for more details on the single steps: https://forge.codesys.com/lib/counit/tickets/_discuss/thread/3e991befbc/ca97/attachment/Public%20FAQ-v13-20240610_075228.pdf Regaring your OPCUA connection state always showing just "DISABLED", without knowing both sides of the assembly in detail, one can only approach the problem theoretically. We can give a chekclist on how to proceed: Fist, please recheck the communication settings in the OPC UA connection function block to ensure that the server URL, endpoint URL, and other settings are correct and match the configuration of the OPC UA server. Verify that the OPC UA server is running and accessible. -You can try to connect to the OPC UA server using a separate client, such as UAExpert, to ensure that the issue is not related to the OPC UA server itself. Test the security settings in the OPC UA connection function block to ensure that the correct security policy and certificate are selected. If you are using a dynamic connection to the OPC UA server, probe that the connection settings are correctly configured and that the OPC UA client is able to establish a connection to the OPC UA server. Also, please loock into the log files for any errors related to the OPC UA connection function block, these should be listet there. The log files may also provide additional information about the issue and help you to further troubleshoot the problem. FYI - Please see https://content.helpme-codesys.com/en/CODESYS%20Communication/_cds_obj_data_source_communication_opc_ua_server.html: Her you can finde the Communication settings via OPC UA Server -> layout Browse Live Server: The client connects to the server and detects the existing variables and types. From Information Model The client reads the data structure (layout) of the OPC UA Server from the information model set here and as a result receives the information about available variables and types. A connection to the server is not required. The list contains the information models installed in the OPC UA Information Model Repository. "Read Connection" Settings from IEC Variable (option set): - The connection settings used by the device are not read here from the dialog, but at runtime from the IEC variable specified here. - For this possibility, please see the Using a Dynamic Connection to an OPC UA Server (https://content.helpme-codesys.com/en/CODESYS%20Communication/_comm_use_dynamic_opc_ua_server_comm_settings.html) The settings for the communication of a Client-data source to an OPC UA Server can also be dynamically configured from the IEC code and can also be changed at runtime. For such a purpose, a structure is available in the DatasourceOpcUAServer library (For a description of the OPC UA Server, there is one included in the standard installation of CODESYS, https://content.helpme-codesys.com/en/CODESYS%20Communication/_cds_encrypt_communication_data_sources_opc_ua_client.html)
Last updated: 2024-11-04

Post by maldus512 on How to adapt Codesys Control SL to custom board CODESYS Forge talk (Post)
Hello everyone, I have been given the task to develop I/O drivers for a custom made, Linux based board to allow for Codesys applications to run and control the hardware. I have successfully installed Codesys Control SL for ARM/Linux and tested it with a simple demo application. Now I should start interfacing the runtime to the actual hardware; I should be able to interact with 2 RS485 serial ports, a few GPIOs and an I2C port, all of which already have the corresponding /dev/ interface in the Linux system. I am having trouble understanding how it should be approached. I have found sporadic references that fail to lead to a really comprehensive documentation. For example: The store page (https://store.codesys.com/en/codesys-control-for-linux-arm-sl-1.html#options) mentions a "runtime package" that should allow "Integration of existing C code" and "Usage of local I/Os", which seems exactly what I need to interact with custom peripherals. I have found no further reference to Codesys-C interpop. The Codesys Help page for the runtime package has a page on the "Development of Drivers" (https://content.helpme-codesys.com/en/CODESYS%20Control/rtsllinuxrbpdriverdevelopment.html) that suggests to either "Implement a function block" or "Implement I/O drivers". Those in turn lead to this page (https://forge.codesys.com/drv/io-drivers/doc/Generic/) which describes briefly an XML schema to describe new devices; unfortunately, it doesn't mention what to do with such a description (i.e. how does the runtime know about it) or how it is in any way connected to the actual hardware. Could anyone give me some pointers? I should also mention I have no prior experience with Codesys, so maybe I'm missing an obvious answer.
Last updated: 2024-08-09

Post by jmfernandes on OpenDir always in error CODESYS Forge talk (Post)
Hello I'm trying to use DirOpen to access a directory where then I can read/list the files inside. But I can't list any files because DirOpen.xError is always true. In eError the message is this: " ERROR_UNKNOWN Local library error ID (0: no error; 5101: time out)**** " I have in the file explorer the path 'C:\CodesysTest\Aluminium' and to make sure I also created in the plc a folder to 'prj/Recipes/Aluminium'. I tried using the different paths, but in both it happens the same thing.Inside the folder Aluminium there is two csv files, that I want to list. I added in the library manager CAA Files and CAA Types. I am using the example of https://content.helpme-codesys.com/en/libs/CAA%20File/Current/Examples.html#directory but not matter what I do, I can't get the list the names of the files. What am I missing?
Last updated: 2024-07-31

Post by chalk on No source code available CODESYS Forge talk (Post)
Hello, This is my first time using Codesys, I am trying to add EtherNetIP communication to a Raspberry PI. I’ve added the EtherNetIP Adapter configured the network setting and added some modules to the pi but when I download the project it generates the following error: “There is no source code available for the object because it is in the compiled library ‘cip object, 4.5.1.0 (3s – smart software solution gmbh)’. Do you want to browse for the original library in order to display the source code? There are 2 errors in the log which are: SOURCEPOSITION App=[Application] area=3, offset=332760 EXCEPTION [Application] occurred: App=[Application], Task=[ENIPAdapterServiceTask] I can’t for the life of me work out how to get around this. I can’t find the source code anywhere or any information regarding this error. I’m using Codesys V3.5 SP19 Patch 3, the version of the Ethernet adapter is 4.5.1.0 and the version of the modules is 4.1.0.0. Any help on this will be greatly appreciated. Thanks
Last updated: 2024-02-02

Post by martinlithlith on Mux I2C CODESYS Forge talk (Post)
Hi! I´ll try to get this thread going again as i´m having simliar problems. Right now i get a red triangle on my connected devices (i´m testing with a BME280 sensor and a PCA9685 resvo driver). The TCA9548 have the green symbol beside it. On the "red" devices i get that the bus is not running. I have tried to either run it using the parent bus cycle setting or creating a new freewheeling task prio 1 but nothing helps. I have compared my settings to the settings from the example from the MUX package and i have read (i think) every thread in forge that could be of interest. EDIT: The ic2detect only shows the mux (70-70) and the servo drive (70-76) so i´ll look in to if i managed to burn the 280-sensor while soldering). Another question regarding the 280 sensor. I have a sensor GY-BM E/P 280 that should record humidity and temperatur. Could this be a problem with the library? Does anyone have an idea of what i might be doing wrong? I have some experience from Codesys but not much so this could be an easy one. All suggestions are welcome. I tried to upload the project archive but it did not work. Should i upload the export or how could i show you my horrible project? Best, Martin
Last updated: 2023-10-22

Post by sanacfu on looking for v2.3 libraries on v3.5.19 CODESYS Forge talk (Post)
Hi all, I'm new to Codesys and Wago but well versed in Rockwell. I've been tasked with upgrading old Wago 750-880 PLCs that run Codesys v2.3. All I was giving is the original PLC program in v2.3 and the currently running machine. I've spec out to what I believe is a suitable upgrade, the PFC100 2ndGen, 750-8111. As I'm rewriting this code on the Codesys I can't find the same library functions blocks for ethernet settings PLC functions. Currently I'm working on code to get/set the PLC ethernet IP address and HMI IP addresses from the HMI screen. One other function I'm looking for is a warm reset function to the PLC. When googling for this stuff I see a lot of code not in ladder logic. Are these functions now not available to implement in ladder logic? Where can I get more information on finding and implementing this functions? Do I have to buy a license from Codesys to use these functions? The PLC I ordered should be arriving in 2-3 weeks.
Last updated: 2024-03-25