Post by nz-dave on ethercat softmotion axis error CODESYS Forge talk (Post)
Hi all I'm having a little trouble get my axis to work. i can turn them off and on. i can run each servo manually inputting directly to the mapping address. as soon as i try to use any FB's like jog etc my servos wont move and error out. so far I've had error "SMC_ERROR.SMC_DI-POSITIONLAGERROR" and another one about not calling a fb. cheers. in the attachment I have just jogged X_Axis with the MC_JOG FB
Last updated: 2025-03-10

Post by trusty-squire on How can you get the active frame index from a frame CODESYS Forge talk (Post)
If you are switching a frame based on the "Switch Frame Variable", then just use a variable that is accessible to your program to set your active frame. If you're trying to see which is the active visualization, then use the "CurrentVisu" variable. Note you'll need to enable this by checking it on in the Visualization Manager settings. If it's neither of those, you'll need to be more clear on how you're project is set up.
Last updated: 2025-03-11

Post by konstantinoskr on AXIS Rollover CODESYS Forge talk (Post)
The MC_Home or MC_SetPosition requires a programm cycle to be completed. In my application the speed is approximately 120m/min and the programm cycle is 2ms. That means that i will have a 4mm loss on each Trigger of either MC_Home or MC_SetPosition. The best option is to change the value defined in the axis configuration. I tried the SMC_SetMovementType but it only works with the axis standstill or powered off. I need to be able to change it while the axis is moving.
Last updated: 2025-03-12

Post by trusty-squire on AXIS Rollover CODESYS Forge talk (Post)
In that case, the best thing to do might be to track the offset in a separate variable of your logic, then when you provide target positions, make your target position use the tracked offset as below: ActualTargetPosition := (TargetPosition + MyOffset) MOD 360; Although, upon further reflection, you'll still have the same cycle time issues. You might be able to break your code into multiple tasks to reduce the cycle time, or use an Event task to capture the offset position?
Last updated: 2025-03-12

Post by trusty-squire on Ethernet/IP Scanner Exception CODESYS Forge talk (Post)
What is the task configuration? When you are online and look at the task monitor, what does it show? (Put a screenshot here). If the processor is overloaded you'll likely need to increase the cycle interval, disable the watchdog, or change to a cyclic task instead of interval based? Also, You might want to adjust your task priorities so they don't all have the same priority. Just a few thoughts, although looking at the task monitor would help in troubleshooting.
Last updated: 2025-03-12

Post by pistola on Pause Tab Order CODESYS Forge talk (Post)
I'm programming an HMI, and on a settings page I have external buttons allow the operator to tab between various elements to select which one they want to adjust. I then use "Input Configuration" > "OnMouseClick" to select which variable to adjust. The problem is, when adjusting the variable the pointer will move to the other elements within the tab order. Is there a way to pause or prevent the pointer to move to the other elements when a variable is TRUE?
Last updated: 2025-03-17

Post by respl on IFM EXOR Network variable Error CODESYS Forge talk (Post)
We are connected IFM CR711S to Exor EX710. We are exchanging data using network variables. Both devices are configured on same project so no need to use file source. When tested application it works fine. But after 3 months same application not working. We are able to send data from CR711 to EX710 but data from Ex710 to CR711s works only for one scan when we cold reset CR 711S. Can somebody help to find out error.
Last updated: 2025-03-17

Post by atone on Change IO-Link Device Interface connected to a Profinet-Slave at Runtime CODESYS Forge talk (Post)
I need to be able to update (change) the interface of an IO-Link device at runtime. The reason is the connected sensor can be selected at runtime, and some sensors we use have a 2 byte IN interface, others have a 4 byte IN interface, others 16 byte IN, others 16 byte IN/OUT (see attached screenshot). Is it possible at all? When yes, which function should I use? Thank you!
Last updated: 2025-03-18

Post by nz-dave on Ethernet/IP Scanner Exception CODESYS Forge talk (Post)
Hi Trusty-Squire, just seen you post , thanks for the reply. I was out on site the other day as it had done it again and changed a few things like cycle time etc. plc load is only 7% at its highest. I took a few screenshots while i was there to add to this post. its been up for about a week now but seems to happen at random every couple of weeks. fingers crossed!
Last updated: 2025-03-19

Post by atone on Set DeviceID of an IO-Link Sensor at Runtime CODESYS Forge talk (Post)
I need to be able to change (set) the DeviceID of an IO-Link sensor (see DeviceID.png) at runtime. I tried with both ProfinetCommon.PN_PortConfiguration and ProfinetCommon.IOL_PortConfiguration, but I get an error for both when I try to read the port configuration (see PN_PortConfiguration.png). Does one of those FBs is the right one for my purpose? Do I possibly make a mistake when assigning the parameter IOLD_ID/IOLM_ID?
Last updated: 2025-03-19

Post by simone on Preferred way of managing Ip-adress/es for linux (debian) host? CODESYS Forge talk (Post)
Hi pernockham, I think you should ask your device vendor. For some time I used one from an Italian company where they had made a library where you can manage the ip with a function (something like SetIPAddr...), it was based on connmann on linux. From my little experience is better to use the "default" way, so for me is to manage the config file on interfaces or use the ip addr utility
Last updated: 2025-03-24

Post by jbu0105 on Dynamic limits invaild CODESYS Forge talk (Post)
Hello, For my delta robot i wil use the MC_MoveCirvularAbslolute function. Every time that i set the execute of this function has my Axis group a error. Thats is: The dynamic limits for the movement are invalid. What can i do that this error go away? I saw a view funcitons with limit dymanics but i don't now how they work. If i use the function MC_MoveLinearAbsolute than i have no error. Does anyone know how i fix this?
Last updated: 2025-04-04

Post by jbu0105 on Dynamic limits invaild CODESYS Forge talk (Post)
Hello, For my delta robot i wil use the MC_MoveCirvularAbslolute function. Every time that i set the execute of this function has my Axis group a error. Thats is: The dynamic limits for the movement are invalid. What can i do that this error go away? I saw a view funcitons with limit dymanics but i don't now how they work. If i use the function MC_MoveLinearAbsolute than i have no error. Does anyone know how i fix this?
Last updated: 2025-04-04

Post by installwhat on Ethercat and profinet on together CODESYS Forge talk (Post)
I'm curious about the impact of having profinet and Ethercat (specifically softmotion so frame at start of task?) running together. Since it's advised to access the data from the bus task should have both profinet io and ethercat on the same task? Are there any implications around this one should be aware of especially since the frame at task start is just, so far as I'm aware, an ethercat thing? Thanks
Last updated: 2025-04-08

Post by altus22 on RemoteTargetVisu creates Unresolved Reference CODESYS Forge talk (Post)
In order to set the placeholder to empty, open the Library Manager and click on Placeholders in the Library Manager ribbon. If you left click in the library column for CmpEventMgr Implementation, it will show you the available library versions for CmpEventMgr Implementation. To update the runtime, open the Project menu and select Project Environment. That window will show you the current version of CmpUserMgr Implementation and if there is a newer version available in the Recommended column.
Last updated: 2025-04-17

Post by nz-dave on sysfile- transfer file to pc CODESYS Forge talk (Post)
Hi Trying to send csv file to c:\data\xxx.csv Im able to save to plclogic and after doing this https://forge.codesys.com/forge/talk/Runtime/thread/5cac1390b4/ i can now "file transfer" to host pc downloads. but still cant transfer to c:\ im sure i have done this in the past with older versions of the 3.5 ide? just concat the file name as c:\data\My_Filename.csv. any ideas? cheers
Last updated: 2025-04-23

Post by andrej on Creating, using an external Function. CODESYS Forge talk (Post)
Hello all, could you tell me whether I need an additional license in order for v3x64 to execute the DLL? Is there some manual on how to proceed? Other than the rather generic message loading Component failed Lib_XMATH.dll I have no further hints. Many thanks for your feed back. PS: I tried a similar experiment (i.e. generating a native dll for windows and having it executed by the Python VM this worked without an issue).
Last updated: 2025-05-05

Post by sercan on Connecting Parameter 'A' in G-Code to Physical Axis in CNC Project CODESYS Forge talk (Post)
I want to run the following command by linking it to the A-Axis: G01 A45.0 Which TRAFO should I use to do this? SMC_TRAFO_5Axes and SMC_TRAFO_GantryCutter3 function blocks did not work! For example, when SMC_TRAFO_5Axes is used, parameters B and C can be resolved by the transformer. However, parameter A cannot be resolved. Only SMC_Interpolator displays the value of parameter A in the SMC_Interpolator => piSetPosition.dA output. Should I drive this axis with SoftMotion commands (MC_MoveAbsolute etc.)?
Last updated: 2025-05-07

Post by sercan on Does G75 work when SMC_NCInterpreter is used? CODESYS Forge talk (Post)
When a G75 command is received in a SoftMotion+CNC project, SMC_NCInterpreter does not generate any error commands, but the command does not continue execution! There is information about SMC_NCDecoder in the documentation of the G75 command. Is this command only supported by SMC_NCDecoder? Can the G75 command be used with SMC_NCInterpreter? Forexample: G75 ; RUNNING G01 X$Settings.X$ Y$Settings.Y$ Z$Settings.Z$ ; - G75 ; - G01 X100.0 Y200.0 Z300.0 ; -
Last updated: 2025-05-09

Post by sercan on Does G75 work when SMC_NCInterpreter is used? CODESYS Forge talk (Post)
When a G75 command is received in a SoftMotion+CNC project, SMC_NCInterpreter does not generate any error commands, but the command does not continue execution! There is information about SMC_NCDecoder in the documentation of the G75 command. Is this command only supported by SMC_NCDecoder? Can the G75 command be used with SMC_NCInterpreter? Forexample: G75 ; RUNNING G01 X$Settings.X$ Y$Settings.Y$ Z$Settings.Z$ ; - G75 ; - G01 X100.0 Y200.0 Z300.0 ; -
Last updated: 2025-05-09

Post by sercan on Does G75 work when SMC_NCInterpreter is used? CODESYS Forge talk (Post)
When a G75 command is received in a SoftMotion+CNC project, SMC_NCInterpreter does not generate any error commands, but the command does not continue execution! There is information about SMC_NCDecoder in the documentation of the G75 command. Is this command only supported by SMC_NCDecoder? Can the G75 command be used with SMC_NCInterpreter? Forexample: G75 ; RUNNING G01 X$Settings.X$ Y$Settings.Y$ Z$Settings.Z$ ; - G75 ; - G01 X100.0 Y200.0 Z300.0 ; -
Last updated: 2025-05-09

Post by sercan on Does G75 work when SMC_NCInterpreter is used? CODESYS Forge talk (Post)
When a G75 command is received in a SoftMotion+CNC project, SMC_NCInterpreter does not generate any error commands, but the command does not continue execution! There is information about SMC_NCDecoder in the documentation of the G75 command. Is this command only supported by SMC_NCDecoder? Can the G75 command be used with SMC_NCInterpreter? Forexample: G75 ; RUNNING G01 X$Settings.X$ Y$Settings.Y$ Z$Settings.Z$ ; - G75 ; - G01 X100.0 Y200.0 Z300.0 ; -
Last updated: 2025-05-09

Post by sercan on Does G75 work when SMC_NCInterpreter is used? CODESYS Forge talk (Post)
When a G75 command is received in a SoftMotion+CNC project, SMC_NCInterpreter does not generate any error commands, but the command does not continue execution! There is information about SMC_NCDecoder in the documentation of the G75 command. Is this command only supported by SMC_NCDecoder? Can the G75 command be used with SMC_NCInterpreter? Forexample: G75 ; RUNNING G01 X$Settings.X$ Y$Settings.Y$ Z$Settings.Z$ ; - G75 ; - G01 X100.0 Y200.0 Z300.0 ; -
Last updated: 2025-05-09

Post by glutenaron on Safety drive EL6900 and mitsubishi CODESYS Forge talk (Post)
Hi, Im wokring to get my servo mitsubishi mr-j5-g40-rnj1 working with my safety drive. I have as you can se in the picture Ek1100 koppler and EL6900 as safety plc. My questien is how do i connect the safety_drive to the SM3_Drive_ETC_Mitsubishi_MelServo_J5_Axis1 down below? I get the error ((Logical I/Os]: The logical device 'Safety_Drive' is not mapped to any physical device.)) but how do i map this? regard
Last updated: 2025-05-13

Post by vsgn on Passing properties as VAR_IN_OUT variables. CODESYS Forge talk (Post)
Hi, in my experience, the best options for such a case could be: 1. Pass a FunctionBlock via VAR_IN_OUT, containing all variables, mehods and properties needed for the logic of this graphic element (be aware of implementing correcly both get and set accessor for properties) 2. Pass an Interface via VAR_INPUT, of which you can use obviously only Properties and Methods. This is much more elegant for me. Here, you can just pass directly the instance of a FunctionBlock implementing such Interface as input. Hope you'll find this suggestions useful.
Last updated: 2025-05-13