Post by bahrt on Mapping GPIO and adding GPIO configurations
CODESYS Forge
talk
(Post)
Hi I am about to configure ALL GPIOs on a Raspberry Pi 3 model B V1.2. It seems that I have limited understanding of why not all the IO’s become available with the corresponding mapped IO’s – the 'dwInUse' contains mapping of the inputs from GPIO0 to GPIO27. But 'dwInputs' are only showing GPIO0 to GPIO8 and GPIO15 as available inputs. These mentioned inputs work fine You will be able to watch the limited mapped IO activity here: https://drive.google.com/file/d/1zz4PBNBfRZBF2YkiJ2VQxw6L9MBVji7R/view?usp=sharing Can you please bring your best idea on why GPIO09 to GPIO14 and GPIO16 to GPIO27 state are zero in the dwInputs register? Thanks in advance. Best regards Andreas Bahrt
Last updated: 2023-11-16
Post by ewi04 on Recipe Manager - RecipeManCommands, load & write wrong values, Bug?
CODESYS Forge
talk
(Post)
I'm getting closer to the error. The combination of STRUCT and ARRAY probably causes the strange behavior. As soon as the ARRAY is followed by a variable, the problem arises. Examples: X: ARRAY[1..2] OF INT; // okay Y: ARRAY[1..2] OF STRUCT; // problem Z: STRUCT; Z.ArrayOfInt[1]; // okay Z.ArrayOfStruct[1].Variable // problem // *update - array of array also causes the error A: ARRAY[1..2] OF ARRAY[1..4] OF BOOL; // problem I can't be the only one who has this problem. Or? Maybe there is a solution. Anyone? Or is it a bug after all?
Last updated: 2023-11-17
Post by bahrt on Raspberry Pi GPIO mapping
CODESYS Forge
talk
(Post)
Hi I am about to configure ALL GPIOs on a Raspberry Pi 3 model B V1.2. It seems that I have limited understanding of why not all the IO’s become available with the corresponding mapped IO’s – the 'dwInUse' contains mapping of the inputs from GPIO0 to GPIO27. But 'dwInputs' are only showing GPIO0 to GPIO8 and GPIO15 as available inputs. These mentioned inputs work fine You will be able to watch the limited mapped IO activity here: https://drive.google.com/file/d/1zz4PBNBfRZBF2YkiJ2VQxw6L9MBVji7R/view?usp=sharing Can you please bring your best idea on why GPIO09 to GPIO14 and GPIO16 to GPIO27 state are not active (at a fixed zero state) in the dwInputs register? Thanks in advance. Best regards Andreas Bahrt
Last updated: 2023-11-21
Post by felipemsgarcia on Edge Gateway online, but PLC is not online
CODESYS Forge
talk
(Post)
Hello, Up until yesterday (2023/11/20) I was able to connect to the PLC remotely with no issues through Edge Gateway. However, today I can see the Edge Gateway online but I can find the PLC even if I do a network scan. Following the same path as janber0206 @ https://forge.codesys.com/forge/talk/automation_server/thread/e78b11d7e9/, I looked into certificates and found that one of the Trusted publisher certificates has expired earlier today (2023/11/21). Please see image. Questions are: Does it affect the connection to the PLC through Edge Gateway? How do I fix it? Thank you very much in advance!
Last updated: 2023-11-21
Post by captaincookie on SP19 Runtime Zugriff auf lokales Dateisystem
CODESYS Forge
talk
(Post)
Hallo, das konkrete Problem konnte ich seither leider nicht lösen, allerdings habe ich mit SP19 Patch 4 einen Workaround gefunden, der zumindest für meine Anwendung funktioniert: Zunächst besteht das Problem nicht für alle Funktionalitäten gleichermaßen. Die Anzeige einer .bmp oder .tiff-Datei im Visu-Elementtyp Bild beispielsweise funktioniert aus dem lokalen Dateisystem. Die Anzeige von .cnc-Dateien in einer Tabelle dagegen nicht. Allerdings funktioniert das wiederum, wenn der Dateipfad in den Ordner der PLC führt, genannt '_cnc'. In der PLC wird dieser Ordner über den Pfad _cnc/ erreicht. Auch lohnt es sich einen Blick in die PLC Config-Datei zu werfen und ggf. Anpassungen vorzunehmen. Einzelne Einträge definieren Zugriffsrechte und ähnliches. Die beschriebene Lösung ist nicht sonderlich schön und es erklärt das Problem nicht. Vielleicht kann das noch jemand anders beantworten.
Last updated: 2023-11-22
Post by orbis-tertius on 3.5 P20 hangs - no response
CODESYS Forge
talk
(Post)
Is there anybody can help me with the same problem? I have to migrate created project in ver.3.5.17.0 32BIT with runtime 4.7.0 to ver.3.5.20.0 64BIT with runtime 4.7.11.0 due to the new license. All the libraries and dependencies are updaded and there are no any errors. The first compilation and loading to the controller is being compleated well. After this being done and if I am forced to change any values or change any code in the current project, another compilation will be freezed. This problem can be solved if pressed Build/cleen or cleen all. There is another method to solve this; if project is loaded with excluded object (Alarm Configuration), repeated compilations will be done well.
Last updated: 2024-06-27
Post by hwopereis on How to use Application Trigger in Modbus TCP Server
CODESYS Forge
talk
(Post)
Hi, I'm currently reading and writing several registers with a Modbus TCP server as a subdevice of a Modbus TCP Client. If I read and write cyclically, there are no issues. The problem is this: I see there is also the option to write by "Application", which I would like to use. However, I don't know With the Modbus RTU client, I see there is a trigger variable, xTrigger, to trigger the writing tasks. However, I can't find any such trigger for the Modbus TCP Client. Does anybody know how to implement the trigger behavior for the Modbus TCP client? In particular, I struggle to find the exact "trigger" variable. I'm running Modbus Client version 4.4.0.0 Thanks in advance!
Last updated: 2024-07-01
Post by mikek10 on HTTP Client TCP Init Error
CODESYS Forge
talk
(Post)
Hi, I tried posting in the discussion for the HTTP Client example but perhaps that is not monitored? I have been using http client successfully for approximately 12 months, however in recent weeks I have begun to get TCP_INIT_ERROR when attempting to communicate. The only resolution seems to be power cycling and then the connection begins to work again for a time. I am not aware of any changes to code or libraries between working ok and now. Cold reset does not resolve, only power cycle. It seems the error from NBS.TCP_Client is 6002 which I think is invalid_addr However the address is the same when working and not working?
Last updated: 2024-07-04
Post by adaml on ScriptEngine - execute "Export -> Bootproject and firmware (SD Card)" from python
CODESYS Forge
talk
(Post)
Hi everybody, recently I was checking how many time consuming manual tasks I can perform with python scripts through ScriptEngine. I have in the project many devices and currently I export bootprojects for them by right clicking on Application, then go Export -> Bootproject and firmware (SD Card) and then point folder where files should be exported. It's fine if project has few devices, but I have some of them with over 30 devices and manual clicking like that is very time consuming. How can I do it with python script? So far I found "create_boot_application" method from Application object (taken by projects.primary.find('Application', True)) but it only generates .app and .crc file instead of full structure to store on SD card (FIRMWARE, USERDATA, SDCARD.INI, Version, Version.txt.sig). Should I use some method to control user interface? Best regards, Adam
Last updated: 2024-07-05
Post by naks on Change IP address from IEC code
CODESYS Forge
talk
(Post)
Hi, I'm working with wago 750-8212 controller. I want to change the IP address of the Ethernet adapter from webvisu. I have read some other threads in this forum and I have tried the following: Added the following text to the config file CODESYSControl.cfg: [SysSocket] Adapter.0.Name="br1" Adapter.0.EnableSetIpAndMask=1 Used the below code : IF xUpdateEthernet THEN Ethernet.Enable := FALSE; Reconfig ( xExecute := TRUE, itfNode := Ethernet, eError => ErrorReconfig, xBusy => xBusy, xDone => xDone, xError => xErrorReconfigure); IF Reconfig.xDone THEN ErrorCode := Ethernet.UpdateConfiguredIPSettings(IpAddress := NewIp, gateway := newGateway, subnetmask := newSubnetmask); END_IF IF Reconfig.xDone OR Reconfig.xError THEN reconfig(xExecute := FALSE); END_IF Ethernet.Enable := TRUE; Reconfig(xExecute := TRUE, itfNode := Ethernet ); END_IF I could change the IP address but when i restart my Controller then the IP address resets to the original, Is there anything I have missed, what else can i try ? Thank you in advance.
Last updated: 2024-07-08
Post by rcanfield on Code Coverage and Test Manager
CODESYS Forge
talk
(Post)
I am exploring the possibility of measuring test coverage using the Test Manager and Profiler tools. It appears there are some significant limitations. Has anyone been successful trying to use these tools? Here are my observed limitations. Am I misunderstanding anything? * Profiler only works for one "run cycle". Even warm resets will clear the coverage calculations. Thus, all tests would have to manually reset values when complete to prevent contamination to other tests. * It is not possible to see which statements were/weren't executed. One would have to use the flow control tool which cannot be used in conjunction with the Profiler, and must be viewed in realtime. * The profiler control cannot be automated and therefore must be executed through a manual procedure. Thank you!
Last updated: 2024-07-11
Post by rcanfield on Code Coverage and Test Manager
CODESYS Forge
talk
(Post)
I am exploring the possibility of measuring test coverage using the Test Manager and Profiler tools. It appears there are some significant limitations. Has anyone been successful trying to use these tools? Here are my observed limitations. Am I misunderstanding anything? * Profiler only works for one "run cycle". Even warm resets will clear the coverage calculations. Thus, all tests would have to manually reset values when complete to prevent contamination to other tests. * It is not possible to see which statements were/weren't executed. One would have to use the flow control tool which cannot be used in conjunction with the Profiler, and must be viewed in realtime. * The profiler control cannot be automated and therefore must be executed through a manual procedure. Thank you!
Last updated: 2024-07-11
Post by alez on CANopen safety , SRDO error behavior
CODESYS Forge
talk
(Post)
I have a project in which there is a Safety device in CANopen, and the PLC interfaces with it as Master. I would like to understand if it is possible to set the behavior in case one of the SRDOs that I receive from the slave is no longer received. From what I have seen, if the SRDOs are not received, the CANopen safety status becomes "Not in progress" and the mapped variables freeze at the last value detected. I want to understand if it was possible to set the variables connected to the SRDOs to take a default value (e.g. zero) in the event of a CANOpen error during reception.
Last updated: 2024-07-15
Post by pazderai on CanOpen write issue
CODESYS Forge
talk
(Post)
Thank you for an answer. Unfortunatelly, it doesn't work. The slave needs command byte as follows 0x22. It means expedited transfer where s-bit is not set, therefore data length is not specified. If I use segmented mode by CiA405.SDO_WRITE_DATA it produce command byte as follows 0x21 which is unfortunately supported by the slave and it returns with error 0x05040001 - SDO Abort Code -Client/server command specifier not valid or unknown. I can use CAN API low level to overcome this problem where it is possible to set 0x22 as a command byte, but than I can use user interface to set the communication probably, because I thing that machine expert uses library CiA405.SDO_WRITE for setting the slave. Or am I wrong?
Last updated: 2024-07-16
Post by ucconversions on displaying all incoming CAN bus messages
CODESYS Forge
talk
(Post)
Hello Im using CAN API Im receiving CAN messages with no problem. below is my code. METHOD ProcessMessage VAR_IN_OUT ( Incoming message ) Message : CAN.RxMESSAGE; END_VAR VAR i: USINT; END_VAR recvCANid := Message.udiCanID; IF recvCANid = 16#18FF8247 THEN UserVarGlobal.g_countMsg_RPMset := UserVarGlobal.g_countMsg_RPMset + 1; FOR i := 0 TO 7 DO myDataFF82[i] := Message.abyData[i]; END_FOR END_IF but in this way I can only display CAN messages which I know its ID. I want to display all incoming CAN messages for example first incoming CAN message - I assign it into a variable Message1. second incoming CAN message - I assign it into a variable Message2. third incoming CAN message - I assign it into a variable Message3. Can you give me guidance? Thank you BR
Last updated: 2024-07-18
Post by drml on How to implement an interface (IElement)?
CODESYS Forge
talk
(Post)
I'm struggling with the implementation of the IElement interface (in the ElementCollections library), which I will use to create a SortedList. I created a class (FB) "Device" that implements this interface and that has a "Priority" property that I want to use in order to compare the devices in my implementation of the ElementCompareTo method. Unfortunately, the IElement.ElementCompareTo method needs an IElement as an input, which doesn't know about the "Priority" property of "Device". I tried to define the input itfElement as a Device, but then it doesn't want to compile, because the type in the implementation doesn't match the interface.
Last updated: 2024-07-19
Post by toffeebonbon on EL7041-0052 - does it run with EL7041 SoftMotion?
CODESYS Forge
talk
(Post)
I let this project rest for a while and picked it up last week. I have been in contact with the support from beckhoff and got the information that the terminals were identical (communication wise). As the Log of the Axis (not the drive's log) shows the error when trying to write into the register 0x8012 and set the value for an encoder to a value that is the default - at least according to the manual - I was wondering if it is possible to "not write that value" to skip that part? Or am I misunderstanding the way the library communicates with the drive?
Last updated: 2024-07-24
Post by hazarath on How extract JSONElement containing Array data
CODESYS Forge
talk
(Post)
I want to extract each element of an Array. Can someone help me with this. When I use JSONElementToString (part of JSON Utilities SL), I am seeing output as "ARRAY" instead of actual data. Here is the JSON content that I want to read : { "value1Unit": { "units": "M" }, "data": { "stepSize": 300.23, "points": [6,8] } } I would like to read each item of the element "points" i.e. 6 and 8. Here is the code I used, // Reading the content as JSON reader ( xExecute := execute , pwData := ADR ( converted_value ), jsonData := jsonDataStorage ); // Get the JSON Element jsonDataStorage.FindFirstValueByKey( wsKey := fidKeyVar, diStartIndex := searchElem, jsonElement => jsonElement ); JSON.JSONElementToString ( element := jsonElement , wsResult := valueWstring ); The content of the output of valueWstring is shown as "ARRAY" instead of the array items i.e. 6 and 8 Please can someone help me.
Last updated: 2024-07-30
Post by dawidr on Best practices for querying multiple MODBUS devices
CODESYS Forge
talk
(Post)
Hi! What are the best practices for querying multiple Modbus devices? Single PRG or maybe multiple PRG (so basically multiple thread) per each Modbus device. In my current implementation I'm using single PRG and I'm utilizing FbMbMasterMultiQuerySerial and WagoAppPlcModbus.FbDigitalTwinMbSlaveDevice in eCockpit with PFC200. I've the timer with 2 seconds delay there and it was working fine for single device. But now I have three Modbus devices and for two of them I need to run 2/3 queries to get data from all registers. I noticed that the delays for getting the data from the Modbus devices is much bigger right now.
Last updated: 2024-07-31
Post by mubeta on parker servo and position
CODESYS Forge
talk
(Post)
Reading between the lines of what you did not specify, it therefore seems to appear that in the programme, at the end of the movement order, there is an order to remove power and switch off the pulse modulation. if this is the case, it is obvious that the motor then remains free. If the position is to be maintained at the end of the movement, the motor current modulator, which on the PLC side is controlled via the MC_Power method, must not be interrupted. Another possibility is that in the motor drive settings, the standstill torque current is set very low or zero and without position monitoring. You have to check this via the servo motor drive.
Last updated: 2024-08-05
Post by abrarsk on SysCom Library Usage
CODESYS Forge
talk
(Post)
Hello all, I am facing issues with using SysCom library. With SysCom23 library things were simple but since we are migrating to 64bit systems, I am writing a Porting program. With SysCom23, opening the comport was as simple as providing the ComPort no. which returns the Handle as a DWORD. dwHandle:=SysComOpen(Port); But the new library is a bit different. It is asking for 2 input parameters to open the Com Port - Port Number and POINTER to RTS_IEC_RESULT IF hCom = 0 THEN hCom := SysComOpen(ComSettings.sPort, ADR(pResult)); How should I use the RTS_IEC_Result? I can find RTS_IEC-REUSLT under SysType2Interfaces of SysCom library. Also, can someone give me a general understanding of this RTS_IEC_REULT and RTS_IEC_HANDLE, etc.?
Last updated: 2024-08-05
Post by bernhardw on Probleme mit MC_HALT_SML und MC_STOP_SML
CODESYS Forge
talk
(Post)
Hallo … ich verwende: SoftMotionLight im Positions-Mode Ethercat-Bus Servoverstärker: Metronix BL4104-C . MC_HALT_SML funktioniert nicht zuverlässig (Achse fährt manchmal zu weit oder bis zum Softwareschalter) Ich habe festgestellt, dass intern beim Aufruf von Positions- auf Velocity-Mode umgeschaltet wird - und dann wird wahrscheinlich intern auf Drehzahl 0 abgeregelt. Kennt jemand dieses Problem? – der Wechsel der Betriebsart ja ist nicht verzögerungsfrei! MC_STOP_SML Der Baustein hat keinen Eingangsparameter "Deceleration" Die Achse stoppt und bleibt im Positions-Mode. Aber die Verzögerung ist nicht wie beschrieben: nicht "Objekt 6085h: quick_stop_deceleration" - sondern "Objekt 6084h: profile_deceleration" - aus zuvor aufgerufenem MC_MOVE_ABSOLUTE_SML Ich wäre dankbar für jeden Hinweis Gruß Bernhard
Last updated: 2024-08-05
Post by eguerra on Error in ScriptingEngine Docs - create_pou()
CODESYS Forge
talk
(Post)
In the ScriptingEngine documentation there seems to be an error (or missing information) in the ScriptIecLanguageObjectContainer part ( https://content.helpme-codesys.com/en/ScriptingEngine/ScriptIecLanguageObjectContainer.html#ScriptIecLanguageObjectContainer.ScriptIecLanguageObjectContainer ). The description of the function create_pou() doesn't specify the correct arguments requested, it only says create_pou(type: SpecialPouType) and a script using the documentation definition of the function will raise an error. I tried passing the function arguments similar to the ones specified for the create_dut() function and it seems to work fine: create_pou(name, PouType) , name : str UPDATE: The offline help has the correct definition IExtendedObject<IScriptObject> create_pou( string name, PouType type = PouType.FunctionBlock, Nullable<Guid> language = null, string return_type = null, string base_type = null, string interfaces = null )
Last updated: 2024-08-05
Post by trusty-squire on parker servo and position
CODESYS Forge
talk
(Post)
@gepert, When you say "I do not turn off power", are you saying you don't power off the drive, or you don't turn of the MC_POWER function block? I read your statement as you don't kill actual electrical power. MC_POWER should stay enabled. @Gustavo, not related to problem at all, but when you say 1.6 Nm is only enough torque to unscrew a loose bottle cap, I think that's a bit low. A quick mental math I use is 1 Nm is almost the same force as 1kG applied to a 10cm wrench. So 1.6kG applied to a 10cm wrench is still not a huge force, but more than enough to be felt if trying to turn the shaft by hand.
Last updated: 2024-08-06
Post by alimans on OPC-UA Server, Symbol Set: Raise an error: Object reference not set to an instance of an object.
CODESYS Forge
talk
(Post)
Hi everyone, I just created a very simple library without any code and, added it to my very simple project. after adding this library, I get an error when I try to open "Symbol Set" in "OPC UA Server" in "Communication Manager". Here is the code of my POU in the library: FUNCTION_BLOCK POU VAR eCommand : (CMD_NONE:=0, CMD_RESET:=-1) INT := CMD_NONE; END_VAR Attached is the error that I get. I also noticed that by removing the enumeration variable above (eCommand), I can open the "Symbol Set" again. Anybody has any idea why this error is raised and how could I use enumeration variables without error in "OPC UA Symbol Set"?
Last updated: 2024-08-08