Post by testlogic on Sending Sequential Modbus TCP Packets CODESYS Forge talk (Post)
I have a Modbus TCP slave device where I need to do sequential writes to the same register. The register I'm writing to is kind of like a command line, each packet is a command word encoded in Hexadecimal. I am having difficulty implementing this system in CoDeSys 3.5 SP19. I feel like the structure of the program should be something along the lines of (Pseudocode): ModbusTCPSend(Command Register, Command1) ModbusTCPSend(Command Register, Command2) ModbusTCPSend(Command Register, Command3) I have tried to implement this with a rising edge trigger wMot1OPCode := 16#E1; //Stop Motor & Kill Program xMot1SendOP := TRUE; //Send OP on rising edge xMot1SendOP := FALSE; //Reset wMot1OPCode := 16#9E; //Disable Motor xMot1SendOP :=TRUE; //Send OP on rising edge xMot1SendOP := FALSE; //Reset Where "wMot1OPCode" is the IO map for writing to the command register, and "xMot1SendOP" is the rising edge trigger for that modbus channel. However, this doesn't work. The device never responds to the modbus commands. It seems like the trigger variable is switched too quickly for modbus to send the packet. I know the modbus register is working, because I can set the channel to cyclic and the device will respond. However, I can't use this reliably because I need each command to be sent once, in order. Cyclic keeps re-sending the commands and seems like it could miss a command as well if one was sent in-between cycle time. I have also trying using the Application trigger as described by https://faq.codesys.com/pages/viewpage.action?pageId=24510480, but this is also not working for me. See attached picture for my FBD code. This seems like a simple function, I can't tell what I'm doing wrong here. Thanks for the help.
Last updated: 2024-03-06

Post by e13740e on Parameterized Property syntax for array element processing CODESYS Forge talk (Post)
Since parameterized (indexed) properties are not possible, I decided to use architectural approach "Indexing Property Adapter" to achieve the intended goal — avoiding code duplication for validated access to array elements. Essence: Create a Function Block Adapter (FB_PropertyAdapter) that encapsulates the logic for working with a single element of the target array (e.g., with one settings structure). Declare Properties inside the adapter block for accessing each individual field of the data structure. All validation logic is implemented within the Set accessors of these properties. Data Binding via VAR_IN_OUT: The adapter block receives a reference to a specific data element from the global array through its VAR_IN_OUT section, which ensures direct work with the original data without copying. Create an Array of Adapters: In the parent POU (e.g., FB_SettingsManager), an array of these adapter blocks is created — one for each element of the global array that needs to be managed. Initialize Bindings: In a FOR loop, each adapter instance from the array is given a reference to the corresponding data element. Result: This approach allows accessing the data via the index of the adapter array, and then through the property name, which simulates the behavior of an indexed property: MyAdapterArray[Index].MyProperty Thus, the validation and data access logic is written only once inside the adapter block and is then reused multiple times by creating instances of it in an array. This completely solves the problem of code duplication while providing a clean, scalable, and object-oriented architecture compatible with standard CODESYS features. Question closed.
Last updated: 2025-10-19

Post by varshag on Trying to pull Logged In user details and certain other variable values and in turn log to a database CODESYS Forge talk (Post)
Hello All, I am new to Codesys and am trying to create a simple project which would let me log to a 6 column database table. I can use a push button on Visualization to initiate the logging. Column 1:Timestamp Column 2:Full name or Initials of Logged in operator Column 3,4,5,6: Certain variables Any help is highly appreciated. Thank you.
Last updated: 2024-11-07

Post by stuartjr on Disabling forcing of specific variables CODESYS Forge talk (Post)
Is there a way that I can create a variable in a GVL that I can control with logic but a user can not put a force on this variable. I have looked at the access rights but this seems to only limit editing the GVL or POU. This variable will only be assigned a value in one POU but it will be used throughout many other POUs.
Last updated: 2024-03-15

Post by tba123 on Script engine, git checkout, Project Environment CODESYS Forge talk (Post)
Hi, I clone a git repository with VersionUpdateFlags.SilentMode, works fine But now I want to checkout a specific commit (with branch_copy command). When using the branch_copy command there is no VersionUpdateFlags and I get this annoying "Project Environment" prompt, blocking further execution of my script without user input. I already tried something like system.prompt_answers[???] = PromptResult.Cancel but I don´t know the string I need here.. The goal is to have a script that clones a repository and compiles every tag + create compiled libraries.
Last updated: 2024-06-10

Post by jgalaska on SMC_Trafo 6DOF Config Error CODESYS Forge talk (Post)
Hello, Recently I was trying to run 6DOF robot in codesys via SMC_Trafo_ArticulatedRobot_6DOF, unfortunately no matter what parameters I tried, it always outputs InvalidConfig Error. I saw the same issue in a topic: https://forge.codesys.com/forge/talk/Motion/thread/16e1f0327f/ But if I understand correctly, the user solved it by developing his own version of this block. I wanted to know if it is a bug in the library (SM3_CNC 4.20.0.0) or am I doing something wrong? Can anyone confirm that they can use the FB without it reporing the Error? Kind regards,
Last updated: 2026-01-21

Post by gerdkoch on Dynamic I/Os Mapping CODESYS Forge talk (Post)
Hi, I assume that you have a Pfc200 G2 or something and work with the original WAGO runtime. Then I would recommend the WagoSysDynamicIoMapping. Here in the example projects there is a PDF file for the library: https://downloadcenter.wago.com/learning-material/details/ll0w3pmdunzvem83g1 There is a global functional component in a GVL of the library. I think it's called DynKbusIoManager or something. The active terminals are registered there. Then there are filter Fb's for e.g. the first clamp with a specific article number. Everything is in the PDF.
Last updated: 2023-08-18

Post by martinlithlith on Relay board / relays for raspberry pi 3 b+ CODESYS Forge talk (Post)
hi! im planning a project on a raspberry with Codesys. For this I'll need a number of relays to control heating and fans, all a max of 24v and about 2a. How would i know if the board / relays i buy will be working with Codesys? Does every hat work or does it need a library/driver? is there a list of drivers/libraries created? as this is a hobby project all tips on a relay board or single boards that works with codesys and not to expensive are very welcome.
Last updated: 2023-09-03

Post by timvh on When Keyboard Key is in Hold, then Webvisu is extreme slow and latent CODESYS Forge talk (Post)
I'm not really sure what you are trying to do, but maybe you are referring to using the CmpCharDevice library? When you "open" the connection to a device, you can pass flags. What helped me is to set the non-blocking flag. I'm not sure if this is what you are referring to, but maybe it helps: dFlags: DINT := CmpCharDevice.ACCESS_MODE.O_RDONLY + DINT#4000; // see details for flags: http://linux.die.net/man/2/open, + DINT#4000 is for non-blocking hDevice := CmpCharDevice.CDOpen(szFilename, dFlags, Result);
Last updated: 2023-09-20

Post by john-martin on Send file from codesys to...... ftp, cloud, etc CODESYS Forge talk (Post)
Hi everybody, I am looking for a solution to send files, for example, to an ftp or a cloud. I can't use oscat library because 64 bit controller are not supported. Therefore, I see that the IIoT library has some functions that might help me to implement this sending process in codesys. Does anyone have any examples of how to do this? I have spent some days with this issue without success. Best regards.
Last updated: 2023-11-02

Post by nathant on Can't open online view of FB instance from code editor, only from Device/POU windows CODESYS Forge talk (Post)
Hello, The title pretty much says it all. When trying to open a FB from the CFC/Ladder/SFC editors while online, the FB does not open in an online view of that specific instance. Instead, it opens an offline view with '???' shown for the value of any variable. This makes debugging extremely cumbersome, as I have to find each FB in the POU window and select the specific instance I am trying to view. Anyone know the cause/solution for this? Thanks.
Last updated: 2023-11-08

Post by fred on Rasperry Control Debian 12 CODESYS Forge talk (Post)
Hi, I have Proxmox running on a Rasperry 4 and have debian 12 ARM installed here. I wanted to install Codesys Control for Raspberry on it. According to the messages, the runtime environment and the gateway were installed successfully, but I can't find a device to downplay a program. The sudo service codesys start command fails. (see image) Does somebody has any idea? Thank you for your help! Greetings Fred
Last updated: 2023-11-22

Post by alink on Visu - changing auto-logout time CODESYS Forge talk (Post)
Hello is there a chance to set with a visu input the auto-logout time? At the moment, it is a fix value set in visu-manager. But for individual configurating of passwort policies I create a visu-dialog to set policies and there for an option to set auto-logout-time. But till now, I haven't found a solution. Maybe someone has an idea? Thanks
Last updated: 2023-11-30

Post by mikek10 on Error IoDrvEthernetIP: Connection Failure. (16#1) How to solve CODESYS Forge talk (Post)
Your connection configuration should look something like the attachment. Consuming assembly O->T will be the hex of the assembly you want to reference for output data - I want 102 (DO Data Only) shown in the Wago web page 102 = 16#66. Producing assembly (T->O) is the assembly you require for input data - again shown in the Wago web page - I want 108 (DI Data Only) or 16#6C Then set the number of bytes as per the data in the Wago web page too (both 2 in my case)
Last updated: 2024-07-22

Post by schweizer on Position und Größe optimal anpassen (Container.Height - Visu.Height) funktioniert nicht. CODESYS Forge talk (Post)
Hello forum Does anyone have experience with optimally adjusting the position and size of the visualization elements? For us, the adjustment on the x-axis works in Codesys 3.5 SP20 with (Container.Width - Visu.Width). However, the y-axis is not affected with (Container.Height - Visu.Height). We implemented this according to the example from Codesys "Optimally adjust position and size" and had no success. Thank you very much for your help.
Last updated: 2024-07-29

Post by dantheman on Connecting to SoftPLC Only Works By Turning Off Modbus Ethernet Port CODESYS Forge talk (Post)
I have an IPC with 2 ethernet ports and 1 Wi-Fi. I'm using ModbusTCP with the ethernet port named "enp2s0" connected to my remote I/O. This works fine when testing with Python and also works with CODESYS, but CODESYS is only able to scan for the Linux SoftPLC when I turn off the "enp2s0" interface. In other words, I can't get online with the IDE if I want my ModbusTCP comms to run with CODESYS. I'm using a Linux SoftPLC that has the following entry in CODESYSControl.cfg, hoping that this will allow me to connect with "enp1s0" or "wlp3s0", and leave "enp2s0" for field comms, but this seems to only make the source IP of the ModbusTCP comms to be bound to "enp2s0". That last point is the case only if I don't restart the service, but if I do restart the service after changing the config file, the source IP for the ModbusTCP comms then becomes the one for "enp1s0", which is very confusing to me: [SysSocket] Adapter.0.Name="enp2s0" Adapter.0.EnableSetIpAndMask=1 On the device list, I only have "enp2s0" given as the ethernet device that has the ModbusTCP master & slave beneath it, shown in Screenshot 1. On the IPC, I can ping the ModbusTCP client (remote I/O) from "enp2s0", and I've attached a Wireshark capture of running ModbusTCP from the CODESYS runtime as Screenshot 2, 3 & 4 (again, I can't get online when this is running, I have to turn off "enp2s0" to connect even when it's idle and I don't have an active TCP session with my Python tests). Like I explained above, the source IP is "enp1s0", even though the ethernet device on the project is "enp2s0". I was lucky to catch the red message that showed the source IP that makes sense to me (the one for "enp2s0"), but for some reason that connection was reset and I never saw that packet again. I've also tried this with Auto-reconnect both enabled & disabled, for the ModbusTCP Master device. I also have to turn off "enp1s0" and then turn it on, just so that I can have the ModbusTCP comms running from "enp2s0" (which is not intuitive in any way to me, I'd love some help understanding that phenomenon as well) in the weird manner that I've described above. I would be very appreciative if someone can help me figure out this pickle. I'd love to just connect to CODESYS through my Wi-Fi interface and leave my ethernet ports for field comms.
Last updated: 2024-08-01

Post by gepert on parker servo and position CODESYS Forge talk (Post)
Hello, Thank you for your response. In my application i use ethercat and while work i do not turn off power. After relative move motor is in standstill. As you suggest I suppose that problem is in drive setting but i do not see any option about increase standstill torque. Below i posted some photos from drive setting manager - PSD Servomanager Do you see any settings responsible for standstill torque? thank you
Last updated: 2024-08-05

Post by mase on Python script: Launch Codesys, Execute Script, Exit Codesys CODESYS Forge talk (Post)
Hi, sorry I can´t help you with your issue, but I hope you can give me a hint on getting GUID for other objects than POUs. Your code states "Guid("6f9dac99-8de1-4efc-8465-68ac443b7d08")". We can I find the GUID / ObjectIds`? I wasn´t able to get details about the GUID of DataTypes (STRUCT/ENUM,..)m, Functions (FUN), GLOBALS and TYPES. I want to create markdown of all available project elements. Thanks for your help
Last updated: 2024-08-06

Post by pavanifm on Test a manager script (.tsd file{xml document}) not starting from Git CI heedlessly/ without ui CODESYS Forge talk (Post)
'--noUI' option of Command line interface for test manager test script not executing when triggered from CI as well as from Local PC however is it working for execution of python scripts from CLI. can we start codesys test manager scripts from CLI interface without any GUI in background process of windows? i can see simlillar questions asked but no answer yet. otherwise, what is the solution to built test automation framework using Test Manager & GIT CI/CD?
Last updated: 2024-08-07

Post by pavanifm on Test a manager script (.tsd file{xml document}) not starting from Git CI heedlessly/ without ui CODESYS Forge talk (Post)
'--noUI' option of Command line interface for test manager test script not executing when triggered from CI as well as from Local PC however is it working for execution of python scripts from CLI. can we start codesys test manager scripts from CLI interface without any GUI in background process of windows? i can see simlillar questions asked but no answer yet. otherwise, what is the solution to built test automation framework using Test Manager & GIT CI/CD?
Last updated: 2024-08-07

Post by pavanifm on Test a manager script (.tsd file{xml document}) not starting from Git CI heedlessly/ without ui CODESYS Forge talk (Post)
'--noUI' option of Command line interface for test manager test script not executing when triggered from CI as well as from Local PC however is it working for execution of python scripts from CLI. can we start codesys test manager scripts from CLI interface without any GUI in background process of windows? i can see simlillar questions asked but no answer yet. otherwise, what is the solution to built test automation framework using Test Manager & GIT CI/CD?
Last updated: 2024-08-07

Post by pavanifm on Test a manager script (.tsd file{xml document}) not starting from Git CI heedlessly/ without ui CODESYS Forge talk (Post)
'--noUI' option of Command line interface for test manager test script not executing when triggered from CI as well as from Local PC however is it working for execution of python scripts from CLI. can we start codesys test manager scripts from CLI interface without any GUI in background process of windows? i can see simlillar questions asked but no answer yet. otherwise, what is the solution to built test automation framework using Test Manager & GIT CI/CD?
Last updated: 2024-08-07

Post by trusty-squire on How to adapt Codesys Control SL to custom board CODESYS Forge talk (Post)
For general usage, these links might help you out. If you are looking at using I2C interfaces, examples from the Raspberry Pi will probably be useful, even if your board isn't a Raspberry Pi. https://content.helpme-codesys.com/en/CODESYS%20Examples/_ex_rts_serial_com.html https://content.helpme-codesys.com/en/CODESYS%20Examples/_ex_raspberry.html If you're developing your own drivers, I can't help you there, although the link you provided will help. If you drill in deeper, the I2C page for example shows function block and method usage, etc. Good luck!
Last updated: 2024-08-09

Post by shawn-plc on Return value from a tag given a string literal CODESYS Forge talk (Post)
Good afternoon everyone, I am looking for a way to return a value given a string tag path. I put together a pseudo-example to illustrate my use-case and was wondering if anyone in this forum can help. The function fnValueFromTagPath is the function I am looking to either create or use from existing library. I would greatly appreciate it. Please see the attachment for additional detail. -Shawn
Last updated: 2024-08-13

Post by liamb on Converting CANbus to Decimal from signed 2's complement CODESYS Forge talk (Post)
I need to combine two 8 bit CANbus messages to 16 bits signed int then convert to decimal Decimal from signed 2's complement. I've been using the below code to read for new messages, combine them then assign them to a variable What is the best way to do this for from signed 2's complement? fbRxMessage351(Data := RxMessage351Data); IF fbRxMessage351.NewMessage THEN ChargeVoltage := (WORD_TO_REAL((RxMessage351Data[0]) + ((RxMessage351Data[1]) * 256))) * 0.1; END_IF
Last updated: 2024-08-16