Post by paulg on RasPi CAA Serial example - unexpected behavior during debug
CODESYS Forge
talk
(Post)
I've trimmed down the CAA Serial Codesys example to only listen on one port but, when stepping through the Case structure in debug mode, it jumps out of the structure during a specific point in every scan (I'll point it out below after describing the setup and listing the code). I'm using a Pi 4 Model B, and I have an Arduino Nano Every plugged in via USB which is streaming the following serial message at 1 Hz: Time since opening connection: 1 s Time since opening connection: 2 s ...and so on. The Pi shows the Nano at /dev/ttyACM0 so I edited CODESYSControl_User.cfg to read: Linux.Devicefile=/dev/ttyACM The code in my PLC_PRG is (ignore some of the comments, I hadn't deleted them out from the original example): PROGRAM PLC_PRG VAR xStartTest : BOOL:= TRUE; iState : INT; xTestDone : BOOL;(* True, when the test was done succesfully *) (* Settings to communicate with the COM Port *) aCom1Params : ARRAY [1..7] OF COM.PARAMETER; como1 : COM.Open; comc1 : COM.Close; comw1 : COM.Write; comr1 : COM.Read; //sWrite : STRING := 'Test String!'; sRead : STRING(25); szRead : CAA.SIZE; xCom1OpenError : BOOL; xCom1CloseError : BOOL; xCom1WriteError : BOOL; xCom1ReadError : BOOL; END_VAR //This example shows the communication of two COM Ports with each other. //The first one writes a string of characters, which is read by the second one. //After successful execution, the two COM Ports are closed and the test is done. IF xStartTest THEN CASE iState OF 0: //The parameters are set for the COM Port aCom1Params[1].udiParameterId := COM.CAA_Parameter_Constants.udiPort; aCom1Params[1].udiValue := 1; // the correct Port should be adapted aCom1Params[2].udiParameterId := COM.CAA_Parameter_Constants.udiBaudrate; aCom1Params[2].udiValue := 115200; aCom1Params[3].udiParameterId := COM.CAA_Parameter_Constants.udiParity; aCom1Params[3].udiValue := INT_TO_UDINT(COM.PARITY.NONE); aCom1Params[4].udiParameterId := COM.CAA_Parameter_Constants.udiStopBits; aCom1Params[4].udiValue := INT_TO_UDINT(COM.STOPBIT.ONESTOPBIT); aCom1Params[5].udiParameterId := COM.CAA_Parameter_Constants.udiTimeout; aCom1Params[5].udiValue := 0; aCom1Params[6].udiParameterId := COM.CAA_Parameter_Constants.udiByteSize; aCom1Params[6].udiValue := 8; aCom1Params[7].udiParameterId := COM.CAA_Parameter_Constants.udiBinary; aCom1Params[7].udiValue := 0; //The first Port is opened with the given parameters como1(xExecute := TRUE, usiListLength:=SIZEOF(aCom1Params)/SIZEOF(COM.PARAMETER),pParameterList:= ADR(aCom1Params)); IF como1.xError THEN xCom1OpenError := TRUE; iState := 1000; END_IF //After a successful opening, the next state is reached IF como1.xDone THEN iState := 15; END_IF 15: // the reading process is started comr1(xExecute := TRUE,hCom:= como1.hCom, pBuffer:= ADR(sRead), szBuffer:= SIZEOF(sRead)); IF comr1.xError THEN xCom1ReadError := TRUE; END_IF //After completion the size of the written bytes are saved IF comr1.xDone OR comr1.xError THEN szRead := comr1.szSize; iState := 20; END_IF 20: // If everything was successful the ports are closed and the handles are released comc1(xExecute := TRUE,hCom:= como1.hCom); IF comc1.xError THEN xCom1CloseError := TRUE; END_IF IF comc1.xDone OR comc1.xError THEN iState := 25; END_IF 25: // The first port is closed and the used handle released xTestDone := TRUE; xStartTest := FALSE; iState := 0; como1(xExecute := FALSE); comw1(xExecute := FALSE); comc1(xExecute := FALSE); ELSE iState := 0; END_CASE END_IF I realize as I write this that the .udiPort should be 0 and not 1, but that shouldn't be causing the issue I'm seeing. I'm forcing xStartTest:=TRUE every scan so that I can step into each line and observe what's happening. What I see is that the port parameters are set and the port is opened with no errors, but the code jumps out of the case structure to the last line every time it reaches (and I step into) the iState:=15 line (at the end of the iState:=0 block). So every scan cycle it goes through the block for iState=0 and jumps out at the same spot. I'm a little new to PLC programming so I may be misunderstanding the flow, but shouldn't this case structure keep moving down in the same scan? If it only handles one case per scan, why doesn't the value of iState persist? Thanks! Update: I restarted the Codesys control today and I was then able to see an error for como1.eError of "WRONG_PARAMETER". I tried doing some digging and another post made me think I should add another line to CODESYSControl_User.cfg, so I now have: [SysCom] Linux.Devicefile=/dev/ttyACM portnum := COM.SysCom.SYS_COMPORT1 So now when I set .udiPort to 1, I get "NO_ERROR" but I also don't read anything from the port (i.e. szRead = 0 always). If I try setting the port to 0 (which I'm confused about, because I added a COMPORT1 line but the device shows on the Pi as ACM0), I get the "WRONG_PARAMETER" error again. Is there an easier way to troubleshoot the Pi and view what ports the Codesys runtime is actually able to see while the Pi is running?
Last updated: 2024-06-06
Post by rmaas on Strange Behavior on Raspberry Pi
CODESYS Forge
talk
(Post)
Hello, what you are seeing is not strange behavior. The problem is that everyting is happening in the same program cycle. After the variable Stepnumber is changed from 10 to 20 for example then you want the program to wait with the next EQ until the next program cycle. Else every EQ will be be true because in every line the variable Stepnumber is increased. When the program arrives (still in the same cycle) at the line with the timer, the Stepnumber has been increased to 30 in the meantime and the timer will allway be ON because even though the variable is written to 10 in this line in the next cycle it starts with 10 and will be 30 again before reaching the timer in line 8. Not very good at explaining stuff but i hope you get the problem. See screenshot below for an example of one way you could solve this...
Last updated: 2024-06-18
Post by svenkaro on Codesyscontrol.service stoppt nach 30s
CODESYS Forge
talk
(Post)
Wie Du schon vermutet hast, es meint, die Hardware/Firmware sei nicht kompatibel ... ooops... this runtime was built for RASPBERRYPI. Hardware version or firmware version not supported! (-18, 0x00000BB8, 0xFFFFFFFB) Architecture: aarch64 Byte Order: Little Endian CPU(s): 4 On-line CPU(s) list: 0-3 Vendor ID: ARM Model name: Cortex-A72 Model: 3 Thread(s) per core: 1 Core(s) per cluster: 4 Socket(s): - Cluster(s): 1 Stepping: r0p3 CPU(s) scaling MHz: 40% CPU max MHz: 1500.0000 CPU min MHz: 600.0000 BogoMIPS: 108.00 Flags: fp asimd evtstrm crc32 cpuid Caches (sum of all): L1d: 128 KiB (4 instances) L1i: 192 KiB (4 instances) L2: 1 MiB (1 instance) Vulnerabilities: Gather data sampling: Not affected Itlb multihit: Not affected L1tf: Not affected Mds: Not affected Meltdown: Not affected Mmio stale data: Not affected Retbleed: Not affected Spec rstack overflow: Not affected Spec store bypass: Vulnerable Spectre v1: Mitigation; __user pointer sanitization Spectre v2: Vulnerable Srbds: Not affected Tsx async abort: Not affected Allerdings habe ich schon reichlich Firmware versionen getestet.
Last updated: 2024-06-21
Post by joachimk on Profinet Controller IP-Adresse ändern
CODESYS Forge
talk
(Post)
Die IP-Adresse des Profinet-Controllers soll zur Laufzeit geändert werden. Dabei handelt es sich um eine Anwendung auf einem PC mit einer Standard-Ethernetschittstelle (ControlWinV3+WinPcap). Die Datei "CODESYSControl.cfg" wurde dazu angepasst: .... Adapter.0.Name="Ethernet 4" Adapter.0.EnableSetIpAndMask=1 Die konfigurierte IP-Adresse wird zur Laufzeit an die tatsächliche IP-Adresse der Netzwerkschnittstelle mit dem folgenden Befehl angepasst (die Änderung von 192.168.2.33 auf 192.168.2.34 funktioniert auch): Ethernet.UpdateConfiguredIPSettings(IpAddress:=Ethernet.IPAddress, subnetmask:=Ethernet.Subnetmask, gateway:=Ethernet.GatewayAddress); Der Profinet-Controller geht danach auf Störung und gibt die folgende Fehlermeldung aus: "Controller-Status: currently active IP does not match the controller's configuration" Unter "Ethernet diagnostic information" kann man die geänderte IP-Adresse von 192.168.2.34. Ethernet läuft auch ohne Fehler. Unter "PROFINET IO Driver diagnostic information" -> "IPParameter" sieht man noch die alte (konfigurierte) IP-Adresse 192.168.2.33. Wie kann man die Störung beseitigen? Leider habe ich keine Methode zum Ändern der IP-Adresse auf dem Profinet-Controller gefunden? Reconfiguration des Profinet-Controllers?
Last updated: 2024-06-27
Post by vtec35 on search runtime 4.9.0.0 for pi 3
CODESYS Forge
talk
(Post)
yes but impossible to upload runtime 4.9.0.0 now we have put an image on the sd card with 4.13.0.0, i have 27 error message to this type, and if i test some output not work, et some work ------ Processus de compilation entamé : application : Device.HiddenOnlineConfigModeApp ------- Affecter un type à un code... [ERREUR] conditionneuse_camphre-ssa-05-02-24-V3 maj 241025: C0032: Le type 'Type inconnu : 'ADR(GVL_Io_73f6cbf3_7be8_4500_8421_47e565d899a0_HPS_1.Io_73f6cbf3_7be8_4500_8421_47e565d899a0_HPS_1)'' ne peut pas être converti en type 'POINTER TO IoConfigParameter' [ERREUR] conditionneuse_camphre-ssa-05-02-24-V3 maj 241025: C0077: Type inconnu : 'GVL_Io_73f6cbf3_7be8_4500_8421_47e565d899a0_HPS_1.Io_73f6cbf3_7be8_4500_8421_47e565d899a0_HPS_1' [ERREUR] conditionneuse_camphre-ssa-05-02-24-V3 maj 241025: C0046: Identificateur 'GVL_Io_73f6cbf3_7be8_4500_8421_47e565d899a0_HPS_1' non défini [ERREUR] conditionneuse_camphre-ssa-05-02-24-V3 maj 241025: C0032: Le type 'Type inconnu : 'ADR(GVL_Io_1b6dcc3b_ae11_4288_b9a9_86f9323448d1_HPS_1.Io_1b6dcc3b_ae11_4288_b9a9_86f9323448d1_HPS_1)'' ne peut pas être converti en type 'POINTER TO IoConfigParameter' [ERREUR] conditionneuse_camphre-ssa-05-02-24-V3 maj 241025: C0077: Type inconnu : 'GVL_Io_1b6dcc3b_ae11_4288_b9a9_86f9323448d1_HPS_1.Io_1b6dcc3b_ae11_4288_b9a9_86f9323448d1_HPS_1' [ERREUR] conditionneuse_camphre-ssa-05-02-24-V3 maj 241025: C0046: Identificateur 'GVL_Io_1b6dcc3b_ae11_4288_b9a9_86f9323448d1_HPS_1' non défini [ERREUR] conditionneuse_camphre-ssa-05-02-24-V3 maj 241025: C0032: Le type 'Type inconnu : 'ADR(GVL_Io_5ae6fa5a_c197_4038_9581_03e1650806a0_HPS_4.Io_5ae6fa5a_c197_4038_9581_03e1650806a0_HPS_4)'' ne peut pas être converti en type 'POINTER TO IoConfigParameter' [ERREUR] conditionneuse_camphre-ssa-05-02-24-V3 maj 241025: C0077: Type inconnu : 'GVL_Io_5ae6fa5a_c197_4038_9581_03e1650806a0_HPS_4.Io_5ae6fa5a_c197_4038_9581_03e1650806a0_HPS_4' [ERREUR] conditionneuse_camphre-ssa-05-02-24-V3 maj 241025: C0046: Identificateur 'GVL_Io_5ae6fa5a_c197_4038_9581_03e1650806a0_HPS_4' non défini [ERREUR] conditionneuse_camphre-ssa-05-02-24-V3 maj
Last updated: 2025-10-26
Post by farren on How to stay in a method until something is finished.
CODESYS Forge
talk
(Post)
I know I'm thinking about this wrong -- too many decades of procedural and event-driven programming and only a few months of PLC ST programming...... I've created a visualization with a button that when pushed calls a method. I want the method to take a pressure reading, wait one minute and then take another pressure reading. I'm looking for leaks. I'm using TON for the delay. It seems like what is happening is that the method gets called once and it takes the first reading and starts the TON. But then execution continues, leaves that method call, and the second reading never happens. I can force the method to keep running until the whole thing is done with a While loop, but I understand that is considered BAD in PLC programming. If it push the button again to call the method again, it picks up where it left off and if the timer is complete then it runs the remaining code. How do I keep that method running until it is complete with just one call without using a while loop that ties up the PLC for a minute? Thanks! -Farren
Last updated: 2025-10-31
Post by jonasz on Deploy LicenseServer for Linux SL
CODESYS Forge
talk
(Post)
So here's how: I manually installed the following packages: codemeter-lite_8.30.6885.501_amd64.deb codesyslicenseserver_licenseserver_4.18.0.0_all.deb codesyswbmbase_wbmbase_4.18.0.0_all.deb codesyswbmlicensing_wbmlicensing_4.18.0.0_all.deb Of course, the license server appeared immediately. Trying to install it again using Install in the Deploy tab, the same error appears. Of course, the information that such a server is already installed is also there. Configuring PLC, S_PLC, EDGE, and SAFE_TIMER_PROVIDER went smoothly, and basically everything works. I wrote a simple program for S_PLC. I'm loading the programs into PLC and S_PLC. When loading the program into S_PLC, a message appears stating that there is no connection to the S_PLC controller. Timeout error. Restart the controller, attempt to load, and see the above. After changing the cycle time for S_PLC to 50ms, the problem no longer occurs. My question, besides the difficulty of installation for a new user, is what causes the cycle time for S_PLC to be so long, and how can I fix it?
Last updated: 2025-11-14
Post by bertus on Can't get SMC_SmoothPath to work
CODESYS Forge
talk
(Post)
Hi Georg, thanks for your time. What is the value of D_ANGLE_TOL? It is set to 0.01. Do you need the assignment bAbort := NOT bDecoder? Does it help to leave it out? This seems to make no difference. Any errors (e.g. SMC_SmoothPath.Error/ErrorID) or PLC log messages? No errors or log messages. What if you comment out SMC_SmoothMerge and SMC_LimtiDynamics, is corner smoothing still not working? Indeed. Is bDecode written from a different task (e.g. visu)? Then I would recommend to assign to a local variable (bDecodeLocal := bDecode) and use that for all FBs. Otherwise, FBs might see different values of bDecode in a single cycle, which will cause problems. It is a local variable, written from a state machine inside this program. But there is new information: During some trial and error, I tried skipping "stage 2: merge short linear segments" (SMC_SmoothMerge). And suddenly it rounds the corners, see attached image. Looking a bit closer, I noticed that (with the original program) after a download (cold start?), it in fact did round the corners, but only once. Ever next cycle in which the NC program was executed, the corners where not rounded. Not sure if there is any relation, but SMC_SmoothMerge is also the only FB which has no bAbort input. Perhaps I need to reset it (or any buffers) by other means?
Last updated: 2025-12-18
Post by bmatlove on Re-create CoE online window in Visu
CODESYS Forge
talk
(Post)
Hello, I am trying to re-create the CoE online window within a Visu for purposes of checking and interacting with device parameters occasionally for maintenance purposes. To minimize reliance on using the IDE for misc interactions. Ideally, I would like to exactly mimic the CoE online window within the IDE. I assume that it uses a few tricks to minimize overhead, such as only polling registers which are within the visual scope, for example. I'm afraid it might be too much to ask for a pre-built drop-in Visu module to exist for this task. Do I have any options aside from manually re-creating all the logic to do this, relying heavily on SdoInfo function blocks? Is there a way for me to reference the device ESI file to shortcut the process of determining how many registers there are and getting the address for each?
Last updated: 2025-12-27
Post by blitz on Can't get SMC_SmoothPath to work
CODESYS Forge
talk
(Post)
This code works well: PROGRAM PLC_PRG VAR execute : BOOL; abort : BOOL; doMDI : BOOL; manualDataInput : STRING(1024) := 'N5 G01 X0.00 Y200.00 N6 G01 X200.00 Y200.00 N7 G01 X200.00 Y0.00 N8 G01 X0.00 Y0.00'; stringStreamArray: ARRAY[0..NUMBER_OF_CHAINS-1] OF SMC_StringStream2 ; i : UDINT; readNCFromStream : SMC_ReadNCFromStream; sentencesFromStringSteam : SMC_GSentenceQueue ; interpreter : SMC_NCInterpreter; interpreterGeoInfoBuffer: ARRAY[1..GEO_INFO_BUFFERS_SIZE] OF SMC_GeoInfo; roundPath : SMC_RoundPath; roundPathGeoInfoBuffer: ARRAY[1..GEO_INFO_BUFFERS_SIZE] OF SMC_GeoInfo; END_VAR VAR CONSTANT MDI_FILE_NAME : STRING := 'MDI.nc'; NUMBER_OF_CHAINS : UDINT := 15; GEO_INFO_BUFFERS_SIZE : DINT := 500; END_VAR readNCFromStream.bExecute := interpreter.bExecute := roundPath.bExecute := execute; readNCFromStream.bAbort := interpreter.bAbort := roundPath.bAbort := abort; IF doMDI THEN stringStreamArray[0].Init(MDI_FILE_NAME); stringStreamArray[0].AppendData(manualDataInput); stringStreamArray[0].SetEndOfData(); i := 0 ; WHILE i < NUMBER_OF_CHAINS DO readNCFromStream.aStream[i] := stringStreamArray[i]; i := i + 1 ; END_WHILE readNCFromStream.bExecute := TRUE; IF readNCFromStream.bBusy THEN ; END_IF END_IF readNCFromStream( fDefaultVel := 10, fDefaultAccel := 10, fDefaultDecel := 10, fDefaultVelFF := 10, fDefaultAccelFF := 10, fDefaultDecelFF := 10, sentences := sentencesFromStringSteam ); interpreter( sentences:= sentencesFromStringSteam, nSizeOutQueue:= SIZEOF(interpreterGeoInfoBuffer), pbyBufferOutQueue:= ADR(interpreterGeoInfoBuffer)); roundPath( poqDataIn := interpreter.poqDataOut, dRadius := , dAngleTol := , nSizeOutQueue := SIZEOF(roundPathGeoInfoBuffer), pbyBufferOutQueue := ADR(roundPathGeoInfoBuffer));
Last updated: 2026-01-09
Post by fredashbolt on Dynamically Update JSON Payload
CODESYS Forge
talk
(Post)
I am trying to generate a JSON payload populated with a value that updates for use with a telemetry system, the payload is to be published by MQTT. I have established the MQTT client and can publish a working JSON payload but I can't get the payload to update as the value (iValue) changes. I am using a timer to trigger the .SetValue function periodically, but the JSON will only give the value as it is when it is first initialized using xFirst IF statement. Any suggestions? Thanks VAR pJsonData : POINTER TO JSON.JSONData := factory.Create(); fb_JBuilder : JSON.JSONBuilder; diRootIndex, diObject1Index : DINT; iValue : INT := 10 ; jsonArrayWriter : JSON.JSONByteArrayWriter; wsJsonData : WSTRING(1000); xFirst : BOOL := TRUE; utf8JsonData : STRING(2000); diTempVal : DINT ; PublishTimer : TON ; END_VAR IF xFirst = TRUE THEN fb_JBuilder ( pJsonData := pJsonData , diRootObj => diRootIndex ) ; diObject1Index := fb_Jbuilder.SetKeyWithObject ( "Device" , diParentIndex := diRootIndex ) ; diTempVal := fb_Jbuilder.SetKeyWithValue ( "Temp" , iValue , diParentIndex := diObject1Index ) ; xFirst := FALSE ; END_IF PublishTimer ( IN := PublishTimer.Q = 0 , PT := T#5S ) ; IF PublishTimer.Q THEN fb_JBuilder.SetValue ( iValue , diTempVal ) ; END_IF jsonArrayWriter( xExecute := PublishTimer.Q , pwData := ADR(wsJsonData), udiSize := SIZEOF(wsJsonData), jsonData := pJsonData^, xAsyncMode := FALSE ) ; JSON.Stu.ConvertUTF16toUTF8( ADR ( wsJsonData ) , ADR ( utf8JsonData ) , SIZEOF ( utf8JsonData ) , bStrictConversion := TRUE ) ;
Last updated: 2026-03-10
Post by konstantin on CAM Motion Recover after STO
CODESYS Forge
talk
(Post)
Hello Mr. Seidel, both the master and the slave axis are modulo. Basically the situation is as follows: One master cycle is 100 units. Slave's modulo length is 2000 units. In the CAM table I defined 10 master cycles on X axis - 1000 units and on the Y axis is the slave - 2000 units. Then depending on the master position 0 to 1000 units the slave's position is plotted on the Y axis - 0 to 2000 units. For example, while the master is executing the 3rd cycle i.e. above 200 units, I trigger the STO function of the slave and it stops. The master executed his cycle but the slave was stopped during the execution. How can I set the slave to continue the CAM sequence from the point where it stopped i.e. third cycle of the master? When I reset the slave error and sync again, everyrhing starts from master's 0 position. Best Regards Konstantin Kolev
Last updated: 2026-02-13
Post by ilya-vah on Table element issues
CODESYS Forge
talk
(Post)
Hello, First post here. I would like to clarify whether the following behavior is known or if it is a bugs. Issue 1 — First row not displayed when using Maximum array index with 1-based arrays Description: When displaying data from an array that is indexed starting from 1 (e.g., ARRAY[1..N]), and the number of displayed rows is limited using the Maximum array index property, the first row of the array is not shown in the visualization. Steps to reproduce: Create an array indexed from 1 (e.g., ARRAY[1..N]). Bind the array to a Table element. Limit the number of displayed rows using the Maximum array index property. Run the visualization. Actual result: The first array element (index 1) is not displayed in the table. Issue 2 — Tooltip string placeholder cannot be bound to string variable from array Description: It is not possible to use a string placeholder in the tooltip that is bound to a string variable from the array. Steps to reproduce: Use a table bound to an array containing string variables. Configure a tooltip using a string placeholder referencing a string field from the array. Run the visualization. Actual result: Tooltip doesn't show any text. A test project demonstrating both issues is attached. Thank you for your time and support.
Last updated: 2026-02-16
Post by risele on Modbus connection via Qronox PCD3 M6893
CODESYS Forge
talk
(Post)
You are welcome. Also note, that it's valid only if you modbus-device use same real/float value representation (IEEE 754). That's true for most of systems. But some devices may have other representation, such as integer + position of the decimal point, for example 123.456 is integer = 123456 and position = 3 Also note, that, ones again, depending on endianess of each system, you may also need to swap not just words, but bytes. TYPE u_Real : UNION rVal:REAL; wVal:ARRAY[0..1] OF WORD; bVal:ARRAY[0..3] OF BYTE; dwVAL:DWORD; //same as previous, may be easier to specify the MB register END_UNION END_TYPE than swapping may be something as VAR A,B,C,D:BYTE; //Bytes of the real value uIn, uOut:u_Real; rVal:REAL; ModbusReg1,ModbusReg2:WORD; END_VAR uIn.rVal:=rVal; uOut.A:=uIn.D; uOut.B:=uIn.C; uOut.C:=uIn.B; uOut.D:=uIn.A; ModbusReg1:=uOut.wVal[0]; ModbusReg1:=uOut.wVal[2]; Or you even need to reorder bits... Ones again, sending float/real values is not defined by Modbus protocol itself, so it is hardware- and software-dependent. The Modbus Poll (and most of modbus tools) have configuration parameters that will properly swap bytes on their side. Ones again, that's very helpful: https://www.scadacore.com/tools/programming-calculators/online-hex-converter/
Last updated: 2026-02-19
Post by risele on Modbus connection via Qronox PCD3 M6893
CODESYS Forge
talk
(Post)
First, if you don't need to change conversion rules in runtime, take a look at "Unit conversion" module (Application -> add object -> UnitConversion). You can specify there biderectional conversion with different units, limits and so on. Second, since MODBUS don't have "real" types but only general 16-bit registers and Real is 32-bit, generally you need a byte-was conversion Real <> two Words. Note, that depending on the devices on both sides, there are two options: Real-> Word1, Word2 or Real-> Word2, Word1, where Word1 is minor register in Modbus register pair and Word2 is major. You can use simple union: TYPE u_Real : UNION rVal:REAL; wVal:ARRAY[0..1] OF WORD; dwVAL:DWORD; //same as previous, may be easier to specify the MB register END_UNION END_TYPE and convert it as following: VAR myUnion:u_Real; rValue_TO_SEND:REAL; rValue_TO_GET:REAL; END_VAR myUnion.rVal:=rValue_TO_SEND; rValue_TO_GET:=myUnion.rVal; Note, that WORD-order should be properly set in MODBUS registers, otherwise you will get strange values. This tool is helpful: https://www.scadacore.com/tools/programming-calculators/online-hex-converter/ Alternative, you can use functions as REAL_TO_DW and DW_TO_REAL from OSCAT_BASIC, for example.
Last updated: 2026-02-19
Post by fpawlak on How to register own component - CMAddComponent() or CMAddComponent2()
CODESYS Forge
talk
(Post)
Hi All, I wonder which way is correct or better? I would like to register my own component in order to use it in CMPLog. I can use CMAddComponent() or CMAddComponent2() to do it. The main difference is whether I provide udiCmpId myself or it will be generated by runtime. But I don't know which way is correct. Please look at those two examples below. I don't know if CMAddComponent2() is newer and then should be used? CMAddComponent() + providing my own udiCmpId //16#FFFF0000 for unknown myVendorId := 16#FFFF0000; myLibId := 1; myComponentId := myVendorId OR CMPID_IecCode OR myLibId; componentHandle := CMAddComponent(pszComponent:= 'myComponent', udiCmpId:= myComponentId, udiVersion:= 1, pResult:= ADR(result)); IF componentHandle <> RTS_INVALID_HANDLE AND result = CmpErrors.Errors.ERR_OK THEN LogAdd2( hLogger:= STD_LOGGER, udiCmpID:= myComponentId, udiClassID:= CmpLog.LogClass.LOG_ERROR, udiErrorID:= 0, udiInfoID:= 0, pszInfo:= 'myComponent regidtered succsefull.' ); ELSE LogAdd2( hLogger:= STD_LOGGER, udiCmpID:= CMPID_CmpMgr, udiClassID:= CmpLog.LogClass.LOG_ERROR, udiErrorID:= 0, udiInfoID:= 0, pszInfo:= 'Error while regidtering myComponent.'); END_IF CMAddComponent2() + udiCmpId generated by runtime componentHandle := CMAddComponent2(pszComponent:= 'myComponent2', udiVersion:= 1, udiCmpId:= ADR(myComponentId), pResult:= ADR(result)); IF componentHandle <> RTS_INVALID_HANDLE AND result = CmpErrors.Errors.ERR_OK THEN LogAdd2( hLogger:= STD_LOGGER, udiCmpID:= myComponentId, udiClassID:= CmpLog.LogClass.LOG_ERROR, udiErrorID:= 0, udiInfoID:= 0, pszInfo:= 'myComponent2 regidtered succsefull.' ); ELSE LogAdd2( hLogger:= STD_LOGGER, udiCmpID:= CMPID_CmpMgr, udiClassID:= CmpLog.LogClass.LOG_ERROR, udiErrorID:= 0, udiInfoID:= 0, pszInfo:= 'Error while regidtering myComponent2.'); END_IF
Last updated: 2026-02-27
Post by egr99 on Modbus TCP Server connection is ESTABLISHED but all holding registers are value 0?
CODESYS Forge
talk
(Post)
Hi there, Read the above description and experienced the same: Reading coil/discrete input/input register/holding register doesn't fill the mapped I/O variable. Any suggestions? Defined (see attachment): - Ethernet (with parameters according to the used Ethernet adapter of my Windows 11 laptop) - -Modbus TCP Client - - -LOGO231 as Modbus TCP Server - - -WS242 as Modbus TCP Server (WaveShare Modbus TCP <-> RTU converter) - - - -WS242_01 as Modbus Server, COM port (slave-id 1 RTU) - - - -WS242_03 idem (slave-id 3 RTU) - - - -WS242_11 idem (slave-id 11 RTU) Writing coil/holding register works from a mapped I/O variable works fine. Verification of Modbus traffic with WireShark: QUERY to and the RESPONSE of all slave-ids are correct Status of all defined is CONNECTED, RESPONSE_SUCCESS, RUNNING etc. Request counters increase with expected frequency. Error counter = 0. (To have all counters works fine I had to change Modbus TCP Client's parameter OptimizationON to FALSE). LOGO231 works fine: values in mapped I/O conform expectation WS242 without Modbus Server, COM port and with defined channels (for only 1 slave-id possible) works fine. PLC Settings: Update I/O while in stop: I see xBusy changing from FALSE to TRUE and vice versa. Always update variables: Enabled 1
Last updated: 2026-04-05
Post by timvh on USB Game Controller with Raspberry Pi
CODESYS Forge
talk
(Post)
I'm not sure it will work, but you could try it with the CmpCharDevice library. You could create a function block that looks something like this: As input for the filename, you have to use your Linux device, e.g.: '/dev/input/event0' '/dev/input/by-path/platform-button@23-event' Off course you must also pass the pointer to the memory where the data can be written to and the size (count in number of bytes) of the buffer. FUNCTION_BLOCK FB_CharDevice VAR_INPUT szFilename: STRING; pbyBuffer : POINTER TO BYTE; udCount : UDINT; END_VAR VAR_OUTPUT iState : INT := 0; nrBytesRead : DINT; END_VAR VAR xInit : BOOL := TRUE; dFlags: DINT := CmpCharDevice.ACCESS_MODE.O_RDONLY + DINT#4000; // see details for flags: http://linux.die.net/man/2/open, + DINT#4000 is for non-blocking hDevice: CmpCharDevice.CmpCharDevice_Implementation.RTS_IEC_HANDLE := -1; Result : CmpCharDevice.CmpCharDevice_Implementation.RTS_IEC_RESULT; END_VAR IF xInit THEN hDevice := CmpCharDevice.CDOpen(szFilename, dFlags ,Result); // if it would not succeed, the result is -1 (Invalid handle) IF hDevice <> 16#FFFFFFFF AND Result = 0 THEN iState := 5; END_IF xInit := FALSE; END_IF IF iState = 5 THEN nrBytesRead := CmpCharDevice.CDRead(hDevice, pbyBuffer, udCount, Result); ELSE nrBytesRead := 0; END_IF Make sure you close the connection properly, maybe by overwriting the default FB_Exit method of the FB: // Clean up device IF hDevice <> 16#FFFFFFFF THEN __TRY CmpCharDevice.CDClose(hDevice,Result); __CATCH ; __ENDTRY iState := 0; END_IF
Last updated: 24 hours ago
Post by hwillems on Ranges, Lambdas, on Fixed arrays of structs
CODESYS Forge
talk
(Post)
I do datastructures and algorithms in Codesys. For example a Struct of Person with thing's like IdNumber, Name, Age etc. as example. Now i do all kind of calculations, filters. So i have this pretty big Fixed Array with Structs. On this struct i want to do simple stuff you can do easily in C++/Python/Rust etc. For example i want to do this: AvererageAge := Average(Peoples.Age); Then it will return the average of all members ages. Or Sort struct on age etc. Or sort on alphabetical Name. Or use Lambda functions to filter/mutate out things like, filter out everybody above 18 years old. Or remove people who it's name start with "A". Currently i have to write my own custom function for example sorting on Age. And make a super specific function based on that particulare datastructure. Here an Example: (*Before calling this FIlter method, set the mNodeFilterSwitch to the desired filter.*) CASE mNodeFilterSelect OF (********************************[ Status Filters ]***********************************) NodeID: FOR x := ACS_OUT_BEGIN TO ACS_OUT_END BY 1 DO FOR y := ACS_IN_BEGIN TO ACS_IN_END BY 1 DO IF marrNode[y].Status.oiNodeID > marrNode[y + 1].Status.oiNodeID THEN mNodeTemp := marrNode[y + 1]; marrNode[y + 1] := marrNode[y]; marrNode[y] := mNodeTemp; END_IF; END_FOR; END_FOR; Started: FOR x := DES_OUT_BEGIN TO DES_OUT_END BY -1 DO FOR y := DES_IN_BEGIN TO DES_IN_END BY -1 DO IF marrNode[y].Status.oxStarted > marrNode[y - 1].Status.oxStarted THEN mNodeTemp := marrNode[y - 1]; marrNode[y - 1] := marrNode[y]; marrNode[y] := mNodeTemp; END_IF; END_FOR; END_FOR; Starting: FOR x := DES_OUT_BEGIN TO DES_OUT_END BY -1 DO FOR y := DES_IN_BEGIN TO DES_IN_END BY -1 DO IF marrNode[y].Status.oxStarting > marrNode[y - 1].Status.oxStarting THEN mNodeTemp := marrNode[y - 1]; marrNode[y - 1] := marrNode[y]; marrNode[y] := mNodeTemp; END_IF; END_FOR; END_FOR; END_CASE; I have like 30+ of these in the enum. Not really DRY code right? These are custom made bubble sort filters in a function. You pass in the Datastructure, and say what function you want. (This is an enum collection of sorting functions) And then the Array with Nodes of Structs gets ordered. Why can't we have Iterators and Lambda's and build in standard functions like regular languages? Also i use bubble sort because it's the easiest to implement because i can't get this to code DRY. Problem with ST (Even the new one with classes) that it's very limited for programming datastructures and algorithms. Yes you still not want dynamic memory and you need to choose the correct algorithm so you know the most extreme edge cases regarding the time it takes to execute the algorithms.(Real-time execution) How are other people dealing with this? Here for example saw some software using an adjusted ST language and having FOR EACH possibility: https://www.fernhillsoftware.com/help/iec-61131/structured-text/st-for-each.html You can then build your own custom Iterator functions. I wish the IEC 61131-3 standard would be more expressive and having more standard modern features, but still keep close to the fact of no dynamics memory and real-time systems.
Last updated: 2023-08-31
Post by mubeta on Strange problem with the ‘MC_SetPosition’ function
CODESYS Forge
talk
(Post)
How are the servo drives controlled? EtherCAT, step/dir pulses, other? CANOpen, 1 Mb/s, bus load 35%, cycle time 2ms. Another thought is that - if it's step/dir pulse based control - the pulses from the PLC to the drive are getting missed/lost at high frequencies? If that's the case then there would be multiple troubleshooting steps/corrections that could be investigated. Here, it seems to me that we are getting completely off track with the observed problem. You could try to create a simplified program I had already written this elsewhere. The program before being brought into machines was exhaustively tested in SW emulation and the problem did not occur. However, in emulation I was interested in checking other aspects of the process, not this specific one which is for real a correction made necessary after the fact. The part of the program that does this correction with the function mentioned in the topic, came up from its origins, but I didn't know or didn't think it was really useful. A scruple that later turned out to be necessary. However, for now I do not think I will spend any more time on this verification, already lacking any to do my normal. I remain amazed, however, that a function intended to correct the axis position with the motor in motion and that it should not interfere with this, in fact instead changes behavior as the motor speed changes. Mah! When you manually control the motor directly from the servo drive software at the speeds you are calling for, does it move precisely to the target position? The drive and motor have been working fine for about 10 years. In replacing the machine control system, I opted for CoDeSys where before there was something else. But this is not the subject of the problem. What I need to resolve is the fact that a clutch specially placed at a certain point can slip and, therefore, I have the undeniable need to phase the 'prime mover' to the mechanical position of the machine, detected by a cam for each turn, in order to properly stop at its optimum point. Which for now I have ruled out doing. In fact, if I really have to say, since we have now gone brutally OT, I originally thought that this clutch should only come into action in cases of extreme necessity, as happens in most trials. But this one, the way it is made, slips more easily than I could estimate and the servo-controlled 'prime mover,' and the machine, get out of phase, maybe by a little, but frequently, and when the machine work at it's high speed, (in fact all of the time), I can't adjust properly the 'prime mover' position at fly.
Last updated: 2025-01-18
Post by francesco86 on Script python for write in a file Project information
CODESYS Forge
talk
(Post)
Dear all, My python script can read a Codesys project and save in file the different POU, but the problem is that I don't able to read the project info from the obj list. Following of this message there is my python script. Can you help my? Best regards Francesco # encoding:utf-8 # We enable the new python 3 print syntax from __future__ import print_function import os import shutil import time import sys from datetime import datetime print("--- Saving files in the project: ---") print("sys.argv: ", len(sys.argv), " elements:") for arg in sys.argv: print(" - ", arg) if (len(sys.argv)>1): folderExportName = sys.argv[1] print(" folderExportName: ", folderExportName) exportPath = sys.argv[2]+ sys.argv[3]+ "\\"+ sys.argv[1] print(" File path: ", exportPath) # git has_repo=False #save_folder=r'E:\Tmp\ControlPlugins\ControlPlugins\Export' save_folder = exportPath if not os.path.exists(save_folder): os.makedirs(save_folder) else: a=os.listdir(save_folder) for f in a: if not f.startswith("."): sub_path= os.path.join(save_folder,f) if os.path.isdir(sub_path): shutil.rmtree(sub_path) else: os.remove(sub_path) elif f==".git": has_repo=True info={} type_dist={ '792f2eb6-721e-4e64-ba20-bc98351056db':'pm', #property method '2db5746d-d284-4425-9f7f-2663a34b0ebc':'dut', #dut 'adb5cb65-8e1d-4a00-b70a-375ea27582f3':'lib', #lib manager 'f89f7675-27f1-46b3-8abb-b7da8e774ffd':'m', #method no ret '8ac092e5-3128-4e26-9e7e-11016c6684f2':'act', #action '6f9dac99-8de1-4efc-8465-68ac443b7d08':'pou', #pou '6654496c-404d-479a-aad2-8551054e5f1e':'itf', #interface '738bea1e-99bb-4f04-90bb-a7a567e74e3a':'', #folder 'ffbfa93a-b94d-45fc-a329-229860183b1d':'gvl', #global var '5a3b8626-d3e9-4f37-98b5-66420063d91e':'prop', #property '2bef0454-1bd3-412a-ac2c-af0f31dbc40f':'tl', #textlist '63784cbb-9ba0-45e6-9d69-babf3f040511':'gtl', #global textlist '225bfe47-7336-4dbc-9419-4105a7c831fa':'dev', #device 'ae1de277-a207-4a28-9efb-456c06bd52f3':'tc', #task configuration 'f8a58466-d7f6-439f-bbb8-d4600e41d099':'m', #method with ret '261bd6e6-249c-4232-bb6f-84c2fbeef430':'gvl', #gvl_Persistent '98a2708a-9b18-4f31-82ed-a1465b24fa2d':'task', #task '085afe48-c5d8-4ea5-ab0d-b35701fa6009':'progInfo'#project information }; def save(text,path,name,tp): if not tp: tp='' else: tp='.'+tp+'.txt' with open(os.path.join(path,name+tp),'w') as f: f.write(text.encode('utf-8')) def print_tree(treeobj, depth, path): global info #record current Path curpath=path isfolder=False t='' #text tp='' #type # get object name name = treeobj.get_name(False) id = treeobj.type.ToString() if id in type_dist: tp = type_dist[treeobj.type.ToString()] #Print all type of objects #print("--Name: ", tp) else: info[id]=name if treeobj.is_device: deviceid = treeobj.get_device_identification() t = 'type='+str(deviceid.type) +'\nid=' +str(deviceid.id) + '\nver='+ str(deviceid.version) if tp == "progInfo": print("-- There is prog info, ", tp) print("-- It has textual declaration: , ", treeobj.has_textual_declaration) print("-- It has textual implementation: , ", treeobj.has_textual_implementation) print("-- It is folder: , ", treeobj.is_folder) print("-- It is children: , ", treeobj.get_children(False)) print("-- It is children len: , ", len(treeobj.get_children(False))) print("-- It is progInfo type: , ", type(treeobj.ScriptProject)) #for child in treeobj.get_children(False): # print_tree(child, depth+1,curpath) try: if treeobj.is_folder : #system.ui.prompt('folder:'+u, PromptChoice.YesNo, PromptResult.Yes) isfolder=true pass except: pass if treeobj.has_textual_declaration : t=t+'(*#-#-#-#-#-#-#-#-#-#---Declaration---#-#-#-#-#-#-#-#-#-#-#-#-#*)\r\n' a=treeobj.textual_declaration t=t+a.text if treeobj.has_textual_implementation: t=t+'(*#-#-#-#-#-#-#-#-#-#---Implementation---#-#-#-#-#-#-#-#-#-#-#-#-#*)\r\n' a=treeobj.textual_implementation t=t+a.text if treeobj.has_textual_declaration and not treeobj.has_textual_implementation: t=t+'(*#-#-#-#-#-#-#-#-#-#---NOT Implementation visible---#-#-#-#-#-#-#-#-#-#-#-#-#*)\r\n' if treeobj.is_task : exports=[treeobj] projects.primary.export_native(exports,os.path.join(curpath,name+'.task')) if treeobj.is_libman: exports=[treeobj] projects.primary.export_native(exports,os.path.join(curpath,name+'.lib')) if treeobj.is_textlist: treeobj.export(os.path.join(curpath,name+'.tl')) children = treeobj.get_children(False) if children or isfolder: if tp: curpath=os.path.join(curpath,name+'.'+tp) else: curpath=os.path.join(curpath,name) if not os.path.exists(curpath): os.makedirs(curpath) if t: save(t,curpath,name,tp) for child in treeobj.get_children(False): print_tree(child, depth+1,curpath) for obj in projects.primary.get_children(): print_tree(obj,0,save_folder) with open(os.path.join(save_folder,'ExportInfo.txt'),'w') as f: now = datetime.now() infTimeExecution = now.strftime("%Y-%m-%d %H:%M:%S") f.write("Export date and time: "+infTimeExecution + "\r\n" + str(info)) print("--- Script finished. ---") #system.ui.info('save ok') projects.primary.close()
Last updated: 2024-04-30
Post by francesco86 on Script python for write in a file Project information
CODESYS Forge
talk
(Post)
Dear all, My python script can read a Codesys project and save in file the different POU, but the problem is that I don't able to read the project info from the obj list. Following of this message there is my python script. Can you help my? Best regards Francesco # encoding:utf-8 # We enable the new python 3 print syntax from __future__ import print_function import os import shutil import time import sys from datetime import datetime print("--- Saving files in the project: ---") print("sys.argv: ", len(sys.argv), " elements:") for arg in sys.argv: print(" - ", arg) if (len(sys.argv)>1): folderExportName = sys.argv[1] print(" folderExportName: ", folderExportName) exportPath = sys.argv[2]+ sys.argv[3]+ "\\"+ sys.argv[1] print(" File path: ", exportPath) # git has_repo=False #save_folder=r'E:\Tmp\ControlPlugins\ControlPlugins\Export' save_folder = exportPath if not os.path.exists(save_folder): os.makedirs(save_folder) else: a=os.listdir(save_folder) for f in a: if not f.startswith("."): sub_path= os.path.join(save_folder,f) if os.path.isdir(sub_path): shutil.rmtree(sub_path) else: os.remove(sub_path) elif f==".git": has_repo=True info={} type_dist={ '792f2eb6-721e-4e64-ba20-bc98351056db':'pm', #property method '2db5746d-d284-4425-9f7f-2663a34b0ebc':'dut', #dut 'adb5cb65-8e1d-4a00-b70a-375ea27582f3':'lib', #lib manager 'f89f7675-27f1-46b3-8abb-b7da8e774ffd':'m', #method no ret '8ac092e5-3128-4e26-9e7e-11016c6684f2':'act', #action '6f9dac99-8de1-4efc-8465-68ac443b7d08':'pou', #pou '6654496c-404d-479a-aad2-8551054e5f1e':'itf', #interface '738bea1e-99bb-4f04-90bb-a7a567e74e3a':'', #folder 'ffbfa93a-b94d-45fc-a329-229860183b1d':'gvl', #global var '5a3b8626-d3e9-4f37-98b5-66420063d91e':'prop', #property '2bef0454-1bd3-412a-ac2c-af0f31dbc40f':'tl', #textlist '63784cbb-9ba0-45e6-9d69-babf3f040511':'gtl', #global textlist '225bfe47-7336-4dbc-9419-4105a7c831fa':'dev', #device 'ae1de277-a207-4a28-9efb-456c06bd52f3':'tc', #task configuration 'f8a58466-d7f6-439f-bbb8-d4600e41d099':'m', #method with ret '261bd6e6-249c-4232-bb6f-84c2fbeef430':'gvl', #gvl_Persistent '98a2708a-9b18-4f31-82ed-a1465b24fa2d':'task', #task '085afe48-c5d8-4ea5-ab0d-b35701fa6009':'progInfo'#project information }; def save(text,path,name,tp): if not tp: tp='' else: tp='.'+tp+'.txt' with open(os.path.join(path,name+tp),'w') as f: f.write(text.encode('utf-8')) def print_tree(treeobj, depth, path): global info #record current Path curpath=path isfolder=False t='' #text tp='' #type # get object name name = treeobj.get_name(False) id = treeobj.type.ToString() if id in type_dist: tp = type_dist[treeobj.type.ToString()] #Print all type of objects #print("--Name: ", tp) else: info[id]=name if treeobj.is_device: deviceid = treeobj.get_device_identification() t = 'type='+str(deviceid.type) +'\nid=' +str(deviceid.id) + '\nver='+ str(deviceid.version) if tp == "progInfo": print("-- There is prog info, ", tp) print("-- It has textual declaration: , ", treeobj.has_textual_declaration) print("-- It has textual implementation: , ", treeobj.has_textual_implementation) print("-- It is folder: , ", treeobj.is_folder) print("-- It is children: , ", treeobj.get_children(False)) print("-- It is children len: , ", len(treeobj.get_children(False))) print("-- It is progInfo type: , ", type(treeobj.ScriptProject)) #for child in treeobj.get_children(False): # print_tree(child, depth+1,curpath) try: if treeobj.is_folder : #system.ui.prompt('folder:'+u, PromptChoice.YesNo, PromptResult.Yes) isfolder=true pass except: pass if treeobj.has_textual_declaration : t=t+'(*#-#-#-#-#-#-#-#-#-#---Declaration---#-#-#-#-#-#-#-#-#-#-#-#-#*)\r\n' a=treeobj.textual_declaration t=t+a.text if treeobj.has_textual_implementation: t=t+'(*#-#-#-#-#-#-#-#-#-#---Implementation---#-#-#-#-#-#-#-#-#-#-#-#-#*)\r\n' a=treeobj.textual_implementation t=t+a.text if treeobj.has_textual_declaration and not treeobj.has_textual_implementation: t=t+'(*#-#-#-#-#-#-#-#-#-#---NOT Implementation visible---#-#-#-#-#-#-#-#-#-#-#-#-#*)\r\n' if treeobj.is_task : exports=[treeobj] projects.primary.export_native(exports,os.path.join(curpath,name+'.task')) if treeobj.is_libman: exports=[treeobj] projects.primary.export_native(exports,os.path.join(curpath,name+'.lib')) if treeobj.is_textlist: treeobj.export(os.path.join(curpath,name+'.tl')) children = treeobj.get_children(False) if children or isfolder: if tp: curpath=os.path.join(curpath,name+'.'+tp) else: curpath=os.path.join(curpath,name) if not os.path.exists(curpath): os.makedirs(curpath) if t: save(t,curpath,name,tp) for child in treeobj.get_children(False): print_tree(child, depth+1,curpath) for obj in projects.primary.get_children(): print_tree(obj,0,save_folder) with open(os.path.join(save_folder,'ExportInfo.txt'),'w') as f: now = datetime.now() infTimeExecution = now.strftime("%Y-%m-%d %H:%M:%S") f.write("Export date and time: "+infTimeExecution + "\r\n" + str(info)) print("--- Script finished. ---") #system.ui.info('save ok') projects.primary.close()
Last updated: 2024-04-30
Post by alessandro on SysMemCmp SysMemCpy
CODESYS Forge
talk
(Post)
VAR Data1:ARRAY[1..10] OF SINT ; Data2:ARRAY[1..10] OF SINT ; Data3:ARRAY[1..10] OF SINT ; Data4:ARRAY[1..10] OF SINT ; ex_1 : BOOL ; ex_2 : BOOL ; enable : BOOL :=0 ; END_VAR // PROGRAM // The scope of this example is compare and copy the values of two ARRAY only if some value is different using SysMemCmp and SysMemCpy. // In this 2 example we don't use a FOR cicle for do this, and pBuffer1 and pBuffer2 is just a pointer to ARRAY. See details in Library util.SysMem of Codesys // The compare funcion util.SysMem.SysMemCmp is bidirectional if Data1 chanege respect Data2 ex_1 go to 1 and if Data2 change respect Data1 also // but the copy function util.SysMem.SysMemCpy work only from source ARRAY pSrc:=ADR(Data1) to destination ARRAY pDest:=ADR(Data2) // Example 1 Full ARRAY compare and copy // This compare 2 different equal ARRAY and if there is some difference ex_1 go to 1 and if you give enable he copy Data1 in Data2 ex_1 := TO_BOOL(util.SysMem.SysMemCmp(pBuffer1:=ADR(Data1), pBuffer2:=ADR(Data2), udiCount:=SIZEOF(Data1))); IF ex_1 AND enable THEN util.SysMem.SysMemCpy(pDest:=ADR(Data2), pSrc:=ADR(Data1), udiCount:=SIZEOF(Data1)); END_IF // Example 2 Only selected area of the ARRAY compare and copy // This compare 2 different equal ARRAY starting from position number [3] for 4 byte in this case start at position [3] and finish at position number [6] // and if there is some difference only in area [3..6] of the ARRAY ex_2 go to 1 if you give enalbe he copy Data3[3..6] in Data4[3..6] // if something change in other array position[0..2] or [7..10] are ingnored ex_2 := TO_BOOL(util.SysMem.SysMemCmp(pBuffer1:=ADR(Data3[3]), pBuffer2:=ADR(Data4[3]), udiCount:=4)); IF ex_2 AND enable THEN util.SysMem.SysMemCpy(pDest:=ADR(Data4[3]), pSrc:=ADR(Data3[3]), udiCount:=4); END_IF // Attention udiCount input is intended in <byte> in the example 1 I pass to udiCount:=SIZEOF(Data1) for compare and copy the intere ARRAY and // SIZEOF pass the size of intere ARRAY in byte to the function input, in this 2 examples I used variable type SINT each one occupie 1 byte and one position in the ARRAY // and in the example 2 I pass udiCount:=4 for compare and copy only 4 position of Data3/4[3..6] if you want to extend this example and use it for an ARRAY OF WORD // remember that each WORD will occupe 2 byte (16 bit) and you will have to pass udiCount:=SIZEOF(Data1) if you need to compare intere ARRAY example 1 // but need udiCount:=(42) for the example 2 because need to compare and copy 4 word each occupie 2 byte (16 bit). // For REAL (32 bit) need udiCount:=SIZEOF(44) for LREAL or (64 bit) need udiCount:=SIZEOF(416) // a good rule is calculate the dimension of the ARRAY in byte without empty space at the end, multiple of data type number for variable bigger then 8 bit // Example : If you want to create an ARRAY for 5 REAL (32 bit) each occupie 4 byte the correct size is ARRAY[0..19] OF REAL 54=20 position. // NOTE : In the example the position of compare function util.SysMem.SysMemCmp is first and the copy function util.SysMem.SysMemCpy inside the IF is after // in one cycle of the program the two array is compared and if there is some difference and enable are copied. // If you move util.SysMem.SysMemCmp after the IF cycle he will copare the ARRAY in the current cycle but the copy of the value will do in the next cycle.</byte>
Last updated: 2025-10-24
Post by ryandmg on Web Client (HMI) Disconnects from Webvisu (Weidmuller u-OS)
CODESYS Forge
talk
(Post)
Hey Everyone, I'm having a bit of a struggle finding settings that will reliably maintain a connection between the webvisu and a touchscreen client. Every so often the HMI disconnects and will perpetually display the red spinning arrow with the "Error Happened, Will resume automatically" text. Power cycling the HMI to force a reconnect will re-establish comms. It seems to happen during periods of inactivity if that's a clue. From what I've gathered so far this seems to have something to do with the webvisu update rate, buffer size as well as the visu task scan rate. We first tried the default settings as follows: Webvisu Update Rate: 200 ms Webvisu Buffer Size: 50,000 Visu Task Scan Rate: 100 ms Priority 31 Other Tasks for Reference: Main Task Scan Rate: 100 ms Priority 1 Alarm Manager Scan Rate: 50 ms Priority 31 Ethercat Task: 4 ms Priority 1 This would disconnect some what regularly. We then made the following changes to try and stabilize: Webvisu Update Rate: 150 ms Webvisu Buffer Size: 75,000 Visu Task Scan Rate: 75 ms Kept other tasks the same. This seems to disconnect even more frequently. Also for reference the network is very small and only consists of the PLC, a small switch and the HMI. We're also not controlling frames from outside the visu program itself. The frame changes are all done natively. Any suggestions to get this to stop disconnecting? Oh and whatever the issue is the log does not record it. Figured I would ask here before opening a ticket. Thanks in advance for your help!
Last updated: 2023-09-06
Post by fefefede on Get the numer of day
CODESYS Forge
talk
(Post)
Hello i tro to create a program to turn on or off the air condition in relationship temperature and numer of day. I can't get the number of day. I try this after installing SysTime library but this not work and have this error on debug ------ Build started: Application: Device.Sim.Device.Application ------- Typify code... Generate code... [ERROR] giorno_accensione_aria: PLC_PRG Device: PLC Logic: Application: C0032: Cannot convert type 'Unknown type: 'SysTimeCore(TRUE)'' to type 'TIME' [ERROR] giorno_accensione_aria: PLC_PRG Device: PLC Logic: Application: C0035: Program name, function or function block instance expected instead of 'SysTimeCore' [ERROR] giorno_accensione_aria: PLC_PRG Device: PLC Logic: Application: C0032: Cannot convert type 'Unknown type: 'DayOfWeek(CurrentTime)'' to type 'INT' [ERROR] giorno_accensione_aria: PLC_PRG Device: PLC Logic: Application: C0035: Program name, function or function block instance expected instead of 'DayOfWeek' [INFORMATION] giorno_accensione_aria: PLC_PRG Device: PLC Logic: Application: C0181: Related position Build complete -- 4 errors, 0 warnings : No download possible PROGRAM PLC_PRG VAR Temperatura: UDINT; AriaCondizionata: BOOL := FALSE; CurrentDayOfWeek: INT; //Variabile Giorno CurrentTime: TIME; GiornoDellaSettimana: INT; DayOfWeek: INT; END_VAR CurrentTime := SysTimeCore(TRUE); // Ottieni l'ora corrente CurrentDayOfWeek := DayOfWeek(CurrentTime); CASE GiornoDellaSettimana OF 1: // Azioni per Lunedì 2: // Martedì se più 10° accend altrimenti spegni IF Temperatura >= 10 THEN AriaCondizionata := TRUE; ELSE AriaCondizionata := FALSE; END_IF 3: // Mercoledì se più di 50° accendi altrimenti spegni IF Temperatura >=50 THEN AriaCondizionata := TRUE; ELSE AriaCondizionata := FALSE; END_IF 4: // Giovedì se più di 40° accendi altrimenti spegni IF Temperatura >=40 THEN AriaCondizionata := TRUE; ELSE AriaCondizionata := FALSE; END_IF 5: // Venerdì se più di 50° accendi altrimenti spegni IF Temperatura >=50 THEN AriaCondizionata := TRUE; ELSE AriaCondizionata := FALSE; END_IF 6: // Sabato se più di 25° accendi altrimenti spegni IF Temperatura >=25 THEN AriaCondizionata := TRUE; ELSE AriaCondizionata := FALSE; END_IF 7: // Domenica sempre spenta AriaCondizionata := FALSE; END_CASE
Last updated: 2023-09-14
To search for an exact phrase, put it in quotes. Example: "getting started docs"
To exclude a word or phrase, put a dash in front of it. Example: docs -help
To search on specific fields, use these field names instead of a general text search. You can group with AND or OR.