Post by timvh on Codesys 3.5.18.60 – Application Loss and Persistent Data Corruption
    
    
       CODESYS Forge
    
    
      talk
    
    (Post)
    
    
      Which device do you use? Does this have persistent memory (e.g. NVRAM) available? Maybe first ask your PLC vendor about the possibilities and how they advice to use persistent variables? If you have no NVRAM available, CODESYS will store the variables in a file when the device gracefully shuts down. But on an abrupt power failure, this is not possible. If you have no NVRAM and you want to use persistent variables, then consider using a UPS. In this case when the power is lost, the UPS can keep the power on the PLC which then can gracefully shut down. Alternatively use the Persistence Manager to store the variable values in a file e.g. only on change. See: https://content.helpme-codesys.com/en/CODESYS%20Application%20Composer/ac_pm_overview.html
    
    Last updated: 2025-08-26
    
    
      
        Post by gseidel on Using an Axis of an Axis Group in Torque Conctrol
    
    
       CODESYS Forge
    
    
      talk
    
    (Post)
    
    
      Hi manuknecht, the axis group currently always writes the axis set torque values. If no dynamic model has been configured for the axis group, then the set torques are written to 0. The solution for your use case is to call SMC_GroupUpdate [0] before you call SMC_SetTorque on the axes. This way, the axis group will write 0 to the set torques in the call to SMC_GroupUpdate(), and SMC_SetTorque then will write the desired set torque. Best regards, Georg [0] https://content.helpme-codesys.com/en/libs/SM3_Robotics/Current/SM3_Robotics/POUs/AdministrativeConfiguration/Computation/SMC_GroupUpdate.html
    
    Last updated: 2025-09-09
    
    
      
        Post by reinholdgaylord on CAA File Handling: "Read only" error
    
    
       CODESYS Forge
    
    
      talk
    
    (Post)
    
    
      Hi, sorry for the late reply. After some investigation, the read-only error was being triggered by a FAT-fs filesystem panic on the kernel end, probably caused by unfinished write/reads causing corruption. I found this thread https://forge.codesys.com/forge/talk/Engineering/thread/e637d252b7/geometry dash lite which seems to give a solution of using SysProcess to send the 'sync' command to the console immediately following a write to prevent issues if power is lost or, in my case, if the unit is harshly power cycled. Indeed this seems to resolve the issue bar the worst possible edge cases. Thank you so much!
    
    Last updated: 2025-09-25
    
    
      
        Post by alexgooi on Licensing info not available.
    
    
       CODESYS Forge
    
    
      talk
    
    (Post)
    
    
      Thank you for the response, The empty softcontainer does not become visible unfortunately, but I think I can get that back to working. I think I'm misunderstanding something. You are pointing to the Softcontainer number and the ticket code, I thought that I needed to fill in the virtual control containers serial code is this a misunderstanding? And if this is indeed the case, how is the link between the server (softcontainer) and the Codesys control docker container made? If I have multiple Codesys docker containers running on the same docker server, how is the correct license distributed to the correct Codesys runtime container?
    
    Last updated: 2025-10-02
    
    
      
        Post by sean-barton on Function block method default arguments
    
    
       CODESYS Forge
    
    
      talk
    
    (Post)
    
    
      I have default arguments specified for function block methods but when calling a method, an error is produced requiring me to supply all the arguments despite there being default values. According to the online documentation, under section "Calling a Method" and subsection "argument passing" of the following link: https://content.helpme-codesys.com/en/CODESYS%20Development%20System/_cds_obj_method.html "Passing an argument for an input ... can be omitted ... for which a default or initial value was specified in the declaration..." I have found this to be the case for all Codesys IDEs I've used, 3.5.11, 3.5.16, 3.5.17, 3.5.19. Am I missing something?
    
    Last updated: 2023-12-21
    
    
      
        Post by macros8 on Translation - How to get text as reference in Frames translated?
    
    
       CODESYS Forge
    
    
      talk
    
    (Post)
    
    
      Hi, thanks for the link. Maybe I create elements in incorrect way. I always use Interface Editor to create variables which are used inside element (see pics). After that I place element in my visu and use Reference property to link variable or set the value. In that case the value of string is not transferred to general text list for translation as I mentioned before. Do I have to all properties which influence behavior of my element create in Frame configuration instead? What´s the difference to the Interface editor? Thanks a lot. M.
    
    Last updated: 2024-01-02
    
    
      
        Post by anderson on function block output
    
    
       CODESYS Forge
    
    
      talk
    
    (Post)
    
    
      I'm trying to make a CNC machine, but I'm having problems because the drive I'm using only has the option of communicating through digital inputs. In this case, I should use the CLP's digital outputs to communicate with it, correct? However, in the function blocks it seems that they are already pre-programmed and I didn't find the pulse output options, for example, so that I could associate a digital output from the PLC to connect this to the drive's pulse input. My question is: is it possible to associate the pulse output of the function block with a digital output of the PLC? and how to do this?
    
    Last updated: 2024-01-05
    
    
      
        Post by mp9876 on Device logon problem following fresh install
    
    
       CODESYS Forge
    
    
      talk
    
    (Post)
    
    
      Yes it had been the case I believe as I have seen that message regarding they were not the same. I had update the device though to match them and that still did not fix the problem. I gotta say I wanted to get out of that situation and attempted a lot of things and then I did two things at the same time that fixed my problem: Wiped the 64 bit version and installed the 32 bit version Installed latest SP20 I wish I knew which one of these actions fixed the problem but now I gotta catch up on this IDE learning; it's been quite a learning experience I have to say! Thank you very much for your time and advice; much appreciated!
    
    Last updated: 2024-03-19
    
    
      
        Post by jonasz on Discontinuity of A/B/C axis movement.
    
    
       CODESYS Forge
    
    
      talk
    
    (Post)
    
    
      Hi, My problem was related to the behavior of the modulo axis, but maybe you will find something useful from what I write. The solution lies in path processing. Codesys offers a G-code analysis tool. Insert a CNC object into the project. The CNC settings object will be added automatically. By inserting appropriate processing modules into the CNC settings object and parameterizing them, you can test the behavior of the axis. When the effect is satisfactory, remember to add the module from CNC settings in the correct order in the processing path. Each CNC machine case is different. You need to spend some time to get your design tailored like an Armani suit. Good luck.
    
    Last updated: 2024-05-09
    
    
      
        Post by paro on Modbus Client Request Not Processed
    
    
       CODESYS Forge
    
    
      talk
    
    (Post)
    
    
      Hi, works in my case if I increase the timeout! to_udint(t#100ms) -> 100 -> 100us.. FUNCTION_BLOCK MODBUS_master_example_ST VAR initDone : BOOL := FALSE; aIPAddress : ARRAY [0..3] OF BYTE := [127,0,0,1]; clientTcp: ModbusFB.ClientTcp; // buffer to read input registers aDataInputRegisters : ARRAY[0..9] OF UINT; // some client requests clientRequestReadInputRegisters: ModbusFB.ClientRequestReadInputRegisters; xExecute: BOOL; uistart: UINT := 100; udiTimeout1: UDINT; END_VAR IF NOT initDone THEN initDone := TRUE; // configure clientTcp clientTcp(aIPaddr:=aIPAddress, uiPort:=502, udiLogOptions := ModbusFB.LoggingOptions.All); // configure clientRequestReadInputRegisters clientRequestReadInputRegisters(rClient:=clientTcp, uiUnitId:=1, udiTimeout:=1000000); // 1sec END_IF // call the client FB's clientTcp(); clientRequestReadInputRegisters(rClient:=clientTcp,xExecute := xExecute AND NOT clientRequestReadInputRegisters.xBusy ,uiStartItem:=uistart, uiQuantity:=3, pData:=ADR(aDataInputRegisters[0]));
    
    Last updated: 2024-05-30
    
    
      
        Post by timo on String nach erlaubten/unerlaubten Zeichen durchsuchen
    
    
       CODESYS Forge
    
    
      talk
    
    (Post)
    
    
      Hallo, Ich bastele gerade an einer möglichst einfachen Möglichkeit mit der ich prüfen kann ob ein String Sonderzeichen enthält. Mein Ansatz ist ein ST FB mit einer Case Schrittkette. Ich vergleiche jedes Zeichen des Strings mit allen Zeichen eines vorher definierten Strings erlaubter Zeichen, der A-Z, a-z und 0-9 enthält und ggf angepasst werden kann, wenn ich weitere Zeichen erlaube. Leider wird meine j Zählervariable nicht richtig ausgeführt. Hat da jemand eine Idee? Oder gibt es eine einfachere Lösung/einen fertigen FB den ich mir anschauen kann? FUNCTION_BLOCK Sonderzeichen_Check VAR_INPUT inputString : STRING; // Zu prüfender String startCheck : BOOL; // Startsignal END_VAR VAR_OUTPUT ok : BOOL; // TRUE, wenn keine ungültigen Zeichen END_VAR VAR i : INT := 1; // Input-String Zähler j : INT := 1; // erlaubte Zeichen Zähler allowedChars: STRING := 'ABCDEFGHIJKLMNOPQRSTUVWXYZabcdefghijklmnopqrstuvwxyz0123456789'; // Erlaubte Zeichen currentChar : STRING[1]; // Aktuelles Zeichen step : INT := 0; // Schritt END_VAR CASE step OF 0: // Warten auf Start IF startCheck THEN step := 10; END_IF 10: // Initialisierungen i := 1; j := 1; ok := TRUE; // Standard: ok step := 20; 20: // Durchgehen des Eingangs-Strings IF i <= LEN(inputString) THEN currentChar := MID(inputString, i, 1); // Aktuelles Zeichen step := 30; ELSE step := 70; // Alle Zeichen ok END_IF 30: // Durchgehen der erlaubten Zeichen IF j <= LEN(allowedChars) THEN step := 40; // Zu Schritt 40 ELSE step := 60; // Ungültiges Zeichen END_IF 40: // Vergleich IF currentChar = MID(allowedChars, j, 1) THEN i := i + 1; // Nächstes Zeichen im Input step := 20; ELSE j := j + 1; // Nächstes erlaubtes Zeichen step := 30; END_IF 60: // Ungültiges Zeichen ok := FALSE; // Setze auf FALSE step := 0; 70: // Alle Zeichen ok step := 0; END_CASE
    
    Last updated: 2025-01-20
    
    
      
        Post by otbeka on CAA File Handling: "Read only" error
    
    
       CODESYS Forge
    
    
      talk
    
    (Post)
    
    
      Hi, On CODESYS V3.5.19.50 I am using the latest 3S File Access library (CAA File & CAA Types) to save and retrieve configuration data from the User Data section of an SD card, via file called config.txt. The application reads the file to memory once upon initialisation, and then the only other operation is overwriting the file with the updated configuration whenever the user changes the settings. An issue is ocurring, seemingly randomly, where the config.txt file, and all surrounding directories, cannot be written to by the unit, returning a READ_ONLY_CAA error upon file open. This sometimes does not clear even after power-cycling the PLC several times, yet checking the file permissions with ls -l shows normal read, write, and execute access. I am wondering if this is caused by the PLC itself or by an issue in my application. I have included my CAA File handler function block (SD_Card_Bin(FB).txt) and any associated types/calls below: TYPE ConfigData : STRUCT Config : ARRAY[0..256] OF STRING(64); NumberOfStrings : UDINT; END_STRUCT END_TYPE TYPE Buffer : STRUCT Data : ARRAY[0..SIZEOF(ConfigData)] OF BYTE; DataLength : UDINT; END_STRUCT END_TYPE A case within my MAIN PRG: mode.WriteConfigDataToFile: VisuElems.CURRENTVISU := 'Screen_Write'; IF xModeHasChanged THEN iErrorCount := 0; iRoute := 0; END_IF CASE iRoute OF 0: inBuffer := ConfigData_To_Buffer(GVL.UnitData); xConfigError := FALSE; xDataConfigured := FALSE; iRoute := 1; 1 : //Read Data from Card SD_Card_Bin.strFileName :=FileName; SD_Card_Bin.iFileOperation := 2; SD_Card_Bin(xExecute :=TRUE, WriteBuffer := inBuffer, xDone =>xDataConfigured, xError=>xConfigError, strErrorCodes=>strError); IF xDataConfigured THEN SD_Card_Bin(xExecute :=FALSE); IF xConfigError THEN iRoute := 32767; ELSE iRoute :=100; END_IF END_IF 100: // The end bCurMode := mode.DisplayProcessVariables; 32767: // Config error iErrorCount := iErrorCount + 1; IF iErrorCount > 2 THEN // Repeats 3 times, if no progress abandons and returns error bCurMode := mode.WriteError; ELSE iRoute := 0; // Try again END_IF END_CASE I'd like to rule out my application as the cause of this bug - help via comments or criticism would be greatly appreciated.
    
    Last updated: 2025-03-19
    
    
      
        Post by open on How to create a stopwatch?
    
    
       CODESYS Forge
    
    
      talk
    
    (Post)
    
    
      Hi @ph0010421, I tried the program the TimeTaken is calculated when stop is triggered. I want the TimeTaken to be continuously calculated and counting when a BOOL variable is true. I tried to program this way: Declaration: PROGRAM PLC_PRG VAR bStartStop: BOOL := FALSE; // Start/Stop button bReset: BOOL := FALSE; // Reset button bRunning: BOOL := FALSE; // Flag indicating whether the stopwatch is running tStartTime: TIME; // Variable to store the start time tElapsedTime: TIME; // Variable to store the elapsed time END_VAR Implementation: // Main program logic IF bReset THEN // Reset button pressed, reset the stopwatch bRunning := FALSE; tElapsedTime := T#0s; ELSIF bStartStop THEN // Start/Stop button pressed, toggle the running state IF bRunning THEN // Stop the stopwatch bRunning := FALSE; ELSE // Start the stopwatch bRunning := TRUE; tStartTime := tElapsedTime; END_IF; END_IF // Update the elapsed time when the stopwatch is running IF bRunning THEN tElapsedTime := tElapsedTime + T#1s; // Adjust the time increment as needed END_IF However counting of the seconds is not accurate. I tried changing the main task cycle time interval to 1000ms. The counting of seconds become slower. (see attached) Please help
    
    Last updated: 2023-12-08
    
    
      
        Post by wbj0t on What the right way to update TCP/COM slave device holding registers
    
    
       CODESYS Forge
    
    
      talk
    
    (Post)
    
    
      Hi all :) I have an plc. This plc has option to be as slave device. There are TCP -> Serial Slave Device and COM -> Serial Slave Device. There are 4096 ModBus holding registers with mark "internal modify" for the both devices above. So, COM Slave has 4096 registers and TCP Slave has 4096 registers. And, finally, I have an ARRAY[0..4095] OF WORD. This array glued with COM Slave and TCP slave. Yes, I need plc's opportunity to be communication both TCP and COM ways for the same registers. For example, the next task structure: * TASK_0: 1. pou_READ_Registers 2. pou_0 3. pou_1 4. ... 5. pou_N 6. pou_WRITE_Registers At the first pou I read registers for the other pous, after job we have sort of state of the plc. At the last pou (6) we write modified registers. It is a good scenario: some one wrote registers for the job, after job we save these (modified) registers. But, what if registers wrote between 1 and 6 pou by operator, for example, at the 3 pou -> the last pou 'pou_WRITE' will rewrite this request from operator. What the right way to work with this logic? Thanks you.
    
    Last updated: 2024-07-01
    
    
      
        Post by ricola on ERROR: CodeMAccess2: Used CmRuntime 2.61.2705.500 is too old
    
    
       CODESYS Forge
    
    
      talk
    
    (Post)
    
    
      hi there , can someone tell me how to deal with this error , please? I use the Linux ARM64SL (4.11) on a bullseye distro and when I want to update or install some package, I have the following reply : pi@NanoPi-R5C:~$ sudo apt upgrade Reading package lists... Done Building dependency tree... Done Reading state information... Done You might want to run 'apt --fix-broken install' to correct these. The following packages have unmet dependencies: ** codesyscontrol : Depends: codemeter but it is not installable or codemeter-lite but it is not installable** E: Unmet dependencies. Try 'apt --fix-broken install' with no packages (or specify a solution). and if I try apt --fix-broken install as suggested, I have a proposal to uninstall codesyscontrol ... :-D so I tried to search if there is some Codesys repo: nothing, then I tried to see if ther was something inside Codesys dev (V3.5.20) and I only found that by reading/requesting my device, i spoted that codemeter was too old . I don't see how to deal with this issue. is there a codemeter.deb somewhere ? thanks in advance for any help.
    
    Last updated: 2024-09-17
    
    
      
        Post by imdatatas on Read "Homed" status from EtherCAT drive
    
    
       CODESYS Forge
    
    
      talk
    
    (Post)
    
    
      Hello, I have experienced such situations with some servo drive devices in the past. The home completion information is reported to the upper controller by the slave drive with the states of the relevant bits in the StatusWord (for example; 6041h Bit10, Bit12 in Home mode). If the states of these bits are correct in terms of number and state but the motor does not actually perform the action; You can contact the slave drive manufacturer. There may be a problem with the device firmware. Another area you can play around with is looking at the settings in the "Advanced configuration" for Softmotion axis on the page the link to below, and trying it out and using the one that works for you. https://content.helpme-codesys.com/en/CODESYS%20SoftMotion/_sm_cmd_add_softmotion_cia402_axis.html A method I recommended worked for a user as in below message. https://forge.codesys.com/forge/talk/Engineering/thread/40bc82454d/ I hope your problem will be solved as soon as possible and by sharing the result here, you will help others to know and overcome it. Good luck. Best regards, Imdat
    
    Last updated: 2025-01-08
    
    
      
        Post by timvh on Device diagnosis ( EtherCAT IO card )
    
    
       CODESYS Forge
    
    
      talk
    
    (Post)
    
    
      You can get the state by just using the name of your node (same name as in device tree): VAR etcState: IoDrvEthercatDriverLib.ETC_SLAVE_STATE; END_VAR etcState := EJ1100.wState; Alternatively, you can iterate through the device tree to get the status of all (Ethercat) nodes. See here an example (no guarantee it works, just give as suggestion): PROGRAM P_IO_State VAR CONSTANT uiMAX_NR_OF_TERMINALS : UINT := 100; END_VAR VAR // general device diagnosis // can only be used when the Device - PLC Settings - Advanced settings - enable diagnosis for devices is enabled // this will add the DED library coupler: DED.INode; terminal: DED.INode; aDeviceState: ARRAY[0..uiMAX_NR_OF_TERMINALS - 1] OF DED.DEVICE_STATE; uiTerminalCount : UINT; uiIndex : UINT; // for each terminal check if it implements device diagnostics xQueryResult: BOOL; itfDevice : DED.IDevice2; xDiagAvailable: BOOL; eError: DED.ERROR; xEverythingOK: BOOL; END_VAR uiTerminalCount := 0; // start at the top of the device tree with the first EtherCAT coupler coupler := EtherCAT_Master.FirstChildNode; WHILE coupler <> 0 DO // for each coupler that is found start at the first terminal terminal := coupler.FirstChildNode; WHILE terminal <> 0 AND uiTerminalCount < uiMAX_NR_OF_TERMINALS - 1 DO // for each terminal that is found get the status through the device diagnosis interface xQueryResult := __QUERYINTERFACE(terminal, itfDevice); IF xQueryResult THEN aDeviceState[uiTerminalCount] := itfDevice.GetDeviceState(xDiagnosisInfoAvailable => xDiagAvailable, eError => eError); uiTerminalCount := uiTerminalCount + 1; END_IF terminal := terminal.NextSiblingNode; END_WHILE coupler := coupler.NextSiblingNode; END_WHILE uiIndex := 0; xEverythingOK := TRUE; WHILE uiIndex < uiTerminalCount DO IF aDeviceState[uiIndex] <> DED.DEVICE_STATE.RUNNING THEN xEverythingOK := FALSE; EXIT; END_IF uiIndex := uiIndex + 1; END_WHILE
    
    Last updated: 2025-02-06
    
    
      
        Post by astutoski on No Motion with SM3_RaspiStepper (GPIO 23/24 Show No Pulses)
    
    
       CODESYS Forge
    
    
      talk
    
    (Post)
    
    
      Hi everyone, I’m completely new to CODESYS and have been teaching myself. And i Want to control an Axis using SM3RaspiStepper. Following the example on the RaspiStepper home page, I set up an axis through a POU and tied the SMC_StartupDrive (Visu) template to my axis instance (sud). Unfortunately, the motor never moves and I don’t see any pulses on the PULSE pin (GPIO 23). Hardware -Raspberry Pi 4 B -Nema 17 stepper motor -A4988 stepper driver (EN pin permanently tied to GND) Software / Runtime -CODESYS 3.5 SP21 Patch 1 – Raspberry Pi runtime (demo) -SoftMotion in demo mode -Package: SM3_RaspiStepper 0.0.0.6 Axis parameters: Pulse pin GPIO 23 Direction pin GPIO 24 Enable pin 0 (unused) Disable pin 0 (unused) Whether I start the axis from the visualization template or through Online Config Mode, the motor never spins. In Online Config Mode I press Power → the state changes from Standstill to Discrete_Motion, but the motor shaft is still locked and no step pulses appear on GPIO 23 (checked with a scope). I can provide screenshots of the Visualization, PLC logs, or wiring pictures if that helps. Any ideas on what I might be missing? Happy to provide screenshots, project files, or scope captures if that helps. Thanks in advance!
    
    Last updated: 2025-06-25
    
    
      
        Post by gseidel on AXIS_REF_SM3 Error Codes?
    
    
       CODESYS Forge
    
    
      talk
    
    (Post)
    
    
      Hi SLUCodesys, dwErrorId is a drive specific error number. The drive documentation should be consulted to interpret it. (Note that you should use MC_ReadAxisError to read this error, see https://content.helpme-codesys.com/en/libs/SM3_Basic/Current/SM3_Basic/POUs/Diagnostics/MC_ReadAxisError.html. Accessing the internal variable will result in outdated values if the acis error is not mapped by PDO and is not recommended in general.) uiDriveInterfaceError holds errors of the SoftMotion driver for the drive. It is also an internal variable, not intended for direct access. It is intended for logging, the PLC log will contain the drive interface error, consisting of this number and an error text. My recommendation for handling axis errors in the CODESYS application: 1) Use MC_ReadStatus on the axis to find out whether it is in state Errorstop 2) If in Errorstop, there are two possibilities: an error reported by the drive (MC_ReadAxisError) or an error of the SoftMotion function blocks (output MC_ReadStatus.FBErrorOccured). 3) If there is no drive error, you can use SMC_ReadFBError https://content.helpme-codesys.com/en/libs/SM3_Basic/Current/SM3_Basic/POUs/Diagnostics/FBError/SMC_ReadFBError.html Best regards, Georg
    
    Last updated: 2025-09-24
    
    
      
        Post by alexgooi on Licensing info not available.
    
    
       CODESYS Forge
    
    
      talk
    
    (Post)
    
    
      Sorry for the question, but I'm not completely getting the idea here, could you be more specific, maybe give an example? I'm now in a state where I don't have a softcontainer on my license server anymore (even after reinstalling from the Codesys-IDE). I tried reaching the webserver of Codemeter but when I do that I get redirected to http://"IP":22352 This is not reachable, afterwards I installed lynx on my Debian machine (command line only). From here I could reach the webserver and toggle the network server setting, but unfortunately this did not help. I also tried to changed the remote read setting to 1 (in the Server.ini file). But after a Codemeter reboot this is overwritten to 0. I have the feeling that it should be much easier to get a license to work, am I missing some checkbox somewhere? Is there a tutorial (or manual) that explains the licensing sequence step by step, because I'm pretty stuck.
    
    Last updated: 2025-10-01
    
    
      
        Post by nicetuxedo on Can not activate license on Raspberry pi
    
    
       CODESYS Forge
    
    
      talk
    
    (Post)
    
    
      Hello everyone, I'm hoping for some assistance with a license activation issue: a software crash has left my license in a strange state. Here is the sequence of events: I purchased a new license for the Raspberry PI from the official CODESYS web store. I opened the CODESYS and started the online activation process using the ticket number I received. During the activation, the CODESYS software threw an exception and crashed. I was not able to see if the activation completed. After restarting CODESYS, I attempted to run the activation process again with the same ticket number. The License Manager now gives me an error stating that the ticket has already been activated/used. I am now stuck because my installation is not licensed, but the activation server believes my ticket has been consumed. Has anyone encountered this before? Is there a way to have the ticket status reset?
    
    Last updated: 2025-10-08
    
    
      
        Post by mavitia on Application based license problem - Modbus TCP
    
    
       CODESYS Forge
    
    
      talk
    
    (Post)
    
    
      I am running ubuntu on a raspberry pi, and installed an application based license Control Basic M on it, it runs a demo program fine, does not timeout etc. however, when I add a modbus TCP device, I start getting errors: <Entry severity="error" component="CmpApp" user="nobody" timestamp="12/18/2023 3:49:42 PM" infoId="24">Online change denied. Application Application is in exception state!</Entry> <Entry severity="error" component="CmpApp" user="nobody" timestamp="12/18/2023 3:49:42 PM" infoId="68">Download failed: Application=Application</Entry> <Entry severity="exception" component="CmpApp" user="nobody" timestamp="12/18/2023 3:49:41 PM" infoId="0">Application app=Application has invalid license metrics!</Entry> the modbus tcp slave runs, and the counter ticks up, however, when I call the variables on the %IX0.0 in my program, and try to upload the changes, I am getting the error messages which stop the program as far as I understand, the application based, M includes 2 fieldbus instances, but on the other side is fairly new, anything obvious I am missing out here?
    
    Last updated: 2023-12-18
    
    
      
        Post by vipul on Multicast udp
    
    
       CODESYS Forge
    
    
      talk
    
    (Post)
    
    
      Hi, Good afternoon can anybody help me with UDP Multicast code. I am not able to send or recieve data when code is dumped on linux device. Below is my code. Declaration: PROGRAM udp_multicast VAR oneTimeFlag :UINT :=0; state: INT:=0; driver: UDP.UDPDriver; //port : UDP.Port;//moved to GVL src_ipAddr_ud: UDINT; src_ipAddr_st:STRING := '192.168.127.155';//'192.168.1.155';//ipms ip address dst_ipAddr_ud:UDINT; group_ipAddr_st:STRING := '239.1.5.10'; //group_ipAddr_ud:UDINT; result: SysTypes.RTS_IEC_RESULT; //result of recieve function. bind: UDINT; //result of binding. resultCreate:SysTypes.RTS_IEC_RESULT;//result of port creation. timer:BLINK; temFlag :INT:= 0; post:INT :=0; checksumFunc:checksumXor; localStringBuf:STRING[500]; chksum:BYTE; dataBuffer:POINTER TO BYTE; checksumString:ARRAY[0..5] OF BYTE; recvSize:__XINT; errorCode:UDINT; joinGroupErrorCode:UDINT; END_VAR ************8 Implementation: IF oneTimeFlag <> 1 THEN oneTimeFlag:=1; resultCreate := driver.CreatePort(ADR(GVL.port)); src_ipAddr_ud := UDP.IPSTRING_TO_UDINT(sIPAddress:= src_ipAddr_st); GVL.group_ipAddr_ud := UDP.IPSTRING_TO_UDINT(sIpAddress:= group_ipAddr_st); GVL.port.IPAddress := src_ipAddr_ud; GVl.port.ReceivePort:= GVL.src_port;//port on which messages are expected. GVl.port.SendPort := GVL.dest_port; GVl.port.OperatingSystem := 0; //0- any system GVL.port.Socket :=3; //3- socket type is multicast bind := GVL.port.Bind(udiIPAddress:=src_ipAddr_ud,); GVl.port.JoinGroup(udiGroupAddress:= GVL.group_ipAddr_ud,udiInterfaceAddress:= src_ipAddr_ud,eLogCode=>joinGroupErrorCode); END_IF timer(ENABLE:=TRUE,TIMELOW:=T#100MS,TIMEHIGH:=T#100MS); IF timer.OUT = TRUE THEN GVL.port.Send(udiIPTo:=GVL.group_ipAddr_ud,GVL.dest_port,pbyData:=ADR(GVL.writeData),diDataSize:=SIZEOF(GVL.writeData)); ELSE SysMemSet(ADR(GVL.readData[0]),0,SIZEOF(GVL.readData)); result := GVl.port.Receive(ADR(GVL.readData),diDataSize:=SIZEOF(GVL.readData),udiIPFrom=>dst_ipAddr_ud,diRecvSize=>recvSize,eLogCode=>errorCode); SysMemMove(ADR(GVL.readDataBuf[0]),ADR(GVL.readData[0]),SIZEOF(GVL.readData)); END_IF post:=LEN(GVL.readDataBuf);
    
    Last updated: 2024-01-14
    
    
      
        Post by umdee on Error when monitoring LAD programs
    
    
       CODESYS Forge
    
    
      talk
    
    (Post)
    
    
      System Information from the computer being used: OS Name Microsoft Windows 11 Pro Version 10.0.22631 Build 22631 Other OS Description Not Available OS Manufacturer Microsoft Corporation System Manufacturer Dell Inc. System Model Latitude 5500 System Type x64-based PC System SKU 08B9 Processor Intel(R) Core(TM) i7-8665U CPU @ 1.90GHz, 2112 Mhz, 4 Core(s), 8 Logical Processor(s) BIOS Version/Date Dell Inc. 1.3.11, 6/11/2019 SMBIOS Version 3.2 Embedded Controller Version 255.255 BIOS Mode UEFI BaseBoard Manufacturer Dell Inc. BaseBoard Product 0M14W7 BaseBoard Version A00 Platform Role Mobile Secure Boot State On PCR7 Configuration Elevation Required to View Windows Directory C:\WINDOWS System Directory C:\WINDOWS\system32 Boot Device \Device\HarddiskVolume1 Locale United States Hardware Abstraction Layer Version = "10.0.22621.2506" User Name CARDASSIA-IX\Engineer Time Zone Eastern Daylight Time Installed Physical Memory (RAM) 16.0 GB Total Physical Memory 15.8 GB Available Physical Memory 4.67 GB Total Virtual Memory 18.5 GB Available Virtual Memory 2.52 GB Page File Space 2.63 GB Page File C:\pagefile.sys Kernel DMA Protection Off Virtualization-based security Not enabled Windows Defender Application Control policy Enforced Windows Defender Application Control user mode policy Off Device Encryption Support Elevation Required to View Hyper-V - VM Monitor Mode Extensions Yes Hyper-V - Second Level Address Translation Extensions Yes Hyper-V - Virtualization Enabled in Firmware Yes Hyper-V - Data Execution Protection Yes
    
    Last updated: 2024-03-19
    
    
      
        Post by salvadegianluca on How to use TON inside an FB that is instanced within a Visu page
    
    
       CODESYS Forge
    
    
      talk
    
    (Post)
    
    
      Hi everyone; I'm building a project in which the drag of the mouse over some controls (or the click event) changes the background color of the control items; this change of color is made with an FB that assignes a color code to the background with MUX command based on the value of an enumerator, this part is perfectly working but, when I'm using a touchpanel instead of a web visu (controlled by a mouse) I get into some issues as it seems that the touch operations are not triggering the MouseEnter and MouseLeave properties as it's done with the mouse.... For this reason I'm trying to add a TON to my FB and, if the enum that changes color remains at the same state for more then 3s I'm automatically resetting it to it's "0" so the item gets back the not selected color. Anyhow it looks like the TON function from library is not working in these FB that are instanced in the various visualizations, as instead they do if I create some instances within the POUS. Anyone has ideas of how to make them work?
    
    Last updated: 2024-04-15
    
To search for an exact phrase, put it in quotes.  Example: "getting started docs"
To exclude a word or phrase, put a dash in front of it.  Example: docs -help
To search on specific fields, use these field names instead of a general text search.  You can group with AND or OR.