I have a pressure sensor that measures 0-600 bar and outputs a 0-5V signal, but my PLC reads analog inputs in the 0-10V range and displays a value of 1024 when 10V is applied. In this case, when the sensor outputs 5V at 600 bar, the PLC shows a value of 512. My working range is 0-350 bar, which means the PLC only uses 298 bits in this range, significantly reducing the resolution. What can I do to achieve better resolution within the 0-350 bar range?
Last updated: 2024-08-23
Post by taqamert on IFM-Sensor ADC READ
CODESYS Forge
talk
(Post)
I have a pressure sensor that measures 0-600 bar and outputs a 0-5V signal, but my PLC reads analog inputs in the 0-10V range and displays a value of 1024 when 10V is applied. In this case, when the sensor outputs 5V at 600 bar, the PLC shows a value of 512. My working range is 0-350 bar, which means the PLC only uses 298 bits in this range, significantly reducing the resolution. What can I do to achieve better resolution within the 0-350 bar range?
Last updated: 2024-08-23
Post by taqamert on IFM-Sensor ADC READ
CODESYS Forge
talk
(Post)
I have a pressure sensor that measures 0-600 bar and outputs a 0-5V signal, but my PLC reads analog inputs in the 0-10V range and displays a value of 1024 when 10V is applied. In this case, when the sensor outputs 5V at 600 bar, the PLC shows a value of 512. My working range is 0-350 bar, which means the PLC only uses 298 bits in this range, significantly reducing the resolution. What can I do to achieve better resolution within the 0-350 bar range?
Last updated: 2024-08-23
Post by timvh on Modbus TCP & RTU with Control for Linux SL
CODESYS Forge
talk
(Post)
It seems you have 2 network interfaces. Did you try eth1? Did you already configure the IP address for this interface in Linux? If yes, then maybe undo this. - or only set eth0 in the Nic configuration without anything else (so no IP address, because this is already set in Linux). For more information about the Nic settings, see (probably already read it?): https://content.helpme-codesys.com/en/CODESYS%20Control/_rtsl_obj_deploy_control_sl_configuration.html PS, if you only want to run CODESYS Control SL, you don't necessarily need the Virtual PLC variant. You could also install and run the CODESYS Control SL Runtime in the Host operating system. This way you should also be able to access the serial port and directly access all ethernet ports. Maybe this is easier?
Last updated: 2024-10-23
Post by xabier on See only variable
CODESYS Forge
talk
(Post)
I have declarated this variable...When i use the variable I see all...I wan see only the variable not all. For example I declarated in GVL_GLOBAL ==> Torque_Mode When I push enter insert in code all rute..GVL_GLOBAL.Torque_MOde...I want see only torque mode...How is possible resolved this problem?? Thanks XABI
Last updated: 2024-03-14
Post by eschwellinger on FILE_OPERATION_DENIED
CODESYS Forge
talk
(Post)
due security reason files could only be accessed in /var/opt/codesys/PlcLogic directory
Last updated: 2023-09-25
Post by h4sanb on Load (or Read) File from PLC
CODESYS Forge
talk
(Post)
I want to download program from existing PLC and upload to new PLC. How to do it?
Last updated: 2024-01-09
Post by corriibme on Read Serial Number of PLC
CODESYS Forge
talk
(Post)
I have recently used this example from @Brine, and it worked. Thanks
Last updated: 2024-05-21
Post by pavanifm on IFM-Sensor ADC READ
CODESYS Forge
talk
(Post)
Hi @taqamert this does not necessary CODESYS issue , seems like hardware issue.
Last updated: 2024-08-26
Post by pavanifm on IFM-Sensor ADC READ
CODESYS Forge
talk
(Post)
Hi @taqamert this does not necessarly CODESYS issue , seems like hardware issue.
Last updated: 2024-08-26
Post by pietrobalint on Persistent variables are not read after initialization
CODESYS Forge
talk
(Post)
I updated to 4.13.0.0 and now it works. Thank you!
Last updated: 2024-09-04
Post by eschwellinger on Persistent variables are not read after initialization
CODESYS Forge
talk
(Post)
no need to activate application composer. It is part of the licensefree part.
Last updated: 2024-10-11
Post by pietrobalint on Persistent variables are not read after initialization
CODESYS Forge
talk
(Post)
What do you mean it is part of the licensefree part? I attached my error message.
Last updated: 2024-10-20
Post by snhatton on Can't open online view of FB instance from code editor, only from Device/POU windows
CODESYS Forge
talk
(Post)
Good morning, Yes, this is a known bug that has been reported. For now, the only workaround is to open the function block instances from the device tree. Regards, -Shawn
Last updated: 2023-11-08
Post by trycyclepower on How to remove other libraries and keep the only one I have created.
CODESYS Forge
talk
(Post)
I have created my own library inside codesys and when I import it, it has other basic and standard library inside. How do I extract those libraries and keep the only one that I have created? Thanks.
Last updated: 2023-12-18
Post by manuknecht on Specify Input Configuration "OnDialogClosed" Action to only react to certain Dialogs
CODESYS Forge
talk
(Post)
I have a project with several buttons and dialogs. Most of the dialogs are opened using the Open Dialog action of the Input configuration of the buttons. Some dialogs are openend using the FbOpenDialogExtended FB of the Visu Utils library and the FbOpenDialogExtended FB is called in the Execute ST-Code action. I am also using the FileOpenSave dialog from Visu Dialogs which requires an OnDialogClosed action to read out. I realized that the OnDialogClosed action which is meant for the FileOpenSave dialog also triggers if a dialog is closed, which was previously openend using the FbOpenDialogExtended FB. Is there a way to detect which dialog was closed last and specify to which dialogs the OnDialogClosed action reacts?
Last updated: 2023-09-20
Post by trusty-squire on parker servo and position
CODESYS Forge
talk
(Post)
@gepert, When you say "I do not turn off power", are you saying you don't power off the drive, or you don't turn of the MC_POWER function block? I read your statement as you don't kill actual electrical power. MC_POWER should stay enabled. @Gustavo, not related to problem at all, but when you say 1.6 Nm is only enough torque to unscrew a loose bottle cap, I think that's a bit low. A quick mental math I use is 1 Nm is almost the same force as 1kG applied to a 10cm wrench. So 1.6kG applied to a 10cm wrench is still not a huge force, but more than enough to be felt if trying to turn the shaft by hand.
Last updated: 2024-08-06
Post by damian177 on Problem with downloading OPC UA tags by Data Source Manager
CODESYS Forge
talk
(Post)
Hi, In Codesys V3.5 SP20, using Data Source Manager I am trying to connect to the OPC UA server and receive tags from it. The connection is ok, but the Codesys have a problem with downloading Tags group. The window (downloadingTags.jpg in attachement) never stop. After waiting for a while, I disconnect the connection and only the Server group remains downloaded, with OPC UA server diagnostic data (and this is read in Codesys). Of course, I tried connected via another OPC UA client : UaExpert , and everything works as it should, all tags are downloaded (Uaexpert.jpg screen). Has anyone on the forum encountered the OPC UA client configuration in Codesys? Is it possible to manually request the appropriate tags from the OPC server for reading in Codesys?
Last updated: 2024-09-03
Post by timvh on Visuutils FbOpenDialog(Extended) not open Dialog from POUs
CODESYS Forge
talk
(Post)
I had a similar situation recently where this didn't work, but read to the end to see the solution. The reason is that CODESYS only downloads visualisations (dialogs) if they are part of the project or linked to the project. In your case the dialog is not loaded onto the controller. But the solution is pretty simple: Double click on the Visualization Manager in your application. Select the Tab "Visualizations". Here you can see that your dialog is not "checked". Do this manually and load your project on the controller. Then your code should be able to open the dialog, because now it exists on the controller.
Last updated: 2024-09-28
Post by niallel on CamBuilder and first boundary position not zero
CODESYS Forge
talk
(Post)
Hi, I've read the CamBuilder documentation and it shows to use the left boundary of the first segment as SMCB.BoundImplicit(), so that the transition is as smooth as possible. With this it sets X and Y to 0. My first slave position is not 0 (say for example it's 100), so I would set it with SMCB.Bound(0,100). My question is that when the cam goes back to the start (Periodic := TRUE) , will it blend with the last position (360, 100) if I do this? I imagine it will, but the documentation isn't clear as the information in the Periodic Cams only says to set Smooth Transition in the cam properties - but when I'm defining it with code there isn't an option for Smooth Transition to be set. Hope this makes sense? Many thanks,
Last updated: 2024-10-23
Post by mondinmr on Direct Pointers in IOMapping for EtherCAT with IoDrvEthercatLib.ETCSlave_Dia
CODESYS Forge
talk
(Post)
Using SDO, I can read the EtherCAT mappings and offsets from various registers like 0x1c12, 0x1c13, etc. When I obtain registers mapped in the PDOs and various offsets, I could technically access directly to the statusword, controlword, etc., if they are mapped. I have noticed that on IoDrvEthercatLib.ETCSlave_Diag I can find pointers to the input and output buffers. However, although the input buffer can be easily read by referring to what has been obtained from the SDOs, it is not possible to write to the output buffer, as it is overwritten in each cycle by the data from the IOMapping task. Is there a way, knowing an instance of IoDrvEthercatLib.ETCSlave_Diag, to obtain the pointer to the first data in the IOMapping? The offsets are identical to those of the PDOs, but obviously the data is a copy. For me, the cleanest thing would be to access the pointers on IOMapping, for DS402a devices to retrieve the key data and point them to internal references. I need to know this as, having developed our own motion library, I would like to simplify the initial setup by eliminating unnecessary and nonsensical mappings that can lead users to unnecessary errors. In the current version that we have been using for years, we have to map everything manually. I would like to pass only the slave reference to the FB_init constructors and eliminate the mapping.
Last updated: 2024-02-12
Post by julianramirez on ModbusFB write update
CODESYS Forge
talk
(Post)
Hello everyone, I am testing the ModbusFB library tcp server and so far I am able to create holding registers successfully, however, I am trying to identify after each write which registers got updated (i.e. function code, write value). I can even see the var udiNumWriteRequests, which increases with every write. I noticed that there is logging with the LogStatusInfo method. After I call it I am able to read in the console stuff that I want. Nevertheless, this is only available at the logs and is not easy to decode because it consists on several messages, I would like to know if there is a way for me to retrieve this information from the function itself with pointers or if there is any way to copy the logs messages (assuming that I can filter them with the LoggingOptions to only show what I need) inside the runtime code and not in the console. Thanks for your help :)
Last updated: 2024-09-16
Post by gregor on PFC 200 - codesys V3.5
CODESYS Forge
talk
(Post)
As far as I know, only if someone downloaded sourcecode to the PLC.
Last updated: 2023-08-25
Post by derpaul on Official MQTT-Client: MAX_RECEIVE_BUFFER_SIZE_EXCEEDED
CODESYS Forge
talk
(Post)
As for the desciption the max Size is 256MB. But I'm sending only small JSON files nothing more...
Last updated: 2023-09-27
Post by simond on The required device description is not installed..
CODESYS Forge
talk
(Post)
I only get this error on the second instance of the J1939 Manager!
Last updated: 2023-10-03
To search for an exact phrase, put it in quotes. Example: "getting started docs"
To exclude a word or phrase, put a dash in front of it. Example: docs -help
To search on specific fields, use these field names instead of a general text search. You can group with AND
or OR
.