Post by mubeta on STRUCT AT %MW1000 CODESYS Forge talk (Post)
This is normal and correct since in CoDeSys static addressing of variables uses the IEC method. A LONG tag has the size of 8 bytes, so %ML0 coincides with %MB0 ... %MB7; %ML1000 with %MB8000 ... %MB8007. (Similar reason for word and other formats). Also the reason the compiler won't let you map the structure to a %MW depends on the fact that the individual base elements are manipulated to 64 bits regardless of the smaller size. That said, it makes me strange that you cannot write a parser without making use of static memory allocation.
Last updated: 2024-08-13

Post by timvh on Unable to Connect to Modbus RTU Device CODESYS Forge talk (Post)
If your Control Win is the Modbus "Master" then your configuration should be something like: Modbus_COM (Serial port) - Modbus Master (this is the Control Win SoftPLC actively setting up the communication) - Modbus Slave (this is then your WAGO 750-315) You need to add channels to the Modbus Slave configuration to inform the master which variables to read/write from the Wago module. The way you configured it now, the Control Win is also a slave. PS, don't forget to put the PLC (Control Win) in Run.
Last updated: 2024-09-03

Post by pernockham on Persistence Manager: Config File not found? CODESYS Forge talk (Post)
Trying to utilize the persistence manager, but system do not write to file and do not create the config file. System is a Linux SL, version 4.13.0.0 Problems with persistence/config started when I had other problems to go online, I deleted the config file and the persistent files, but the system will not re-create them. I have tried to remove/re-install the "PersistenceManager"-module, create the folder-structure myself. And also reinstall the linux-runtime but its clearly not working. Any help appreciated.
Last updated: 2024-10-31

Post by durallymax on Access Variable Visu Dialog CODESYS Forge talk (Post)
Is there a way to access the variable in the called dialog? Example: Text Field element with PLC_PRG.myVar as Text variable. OnMouseClick configured to write variable with keypad pop-up. OnValueChanged configured to Execute ST RND(PLC_PRG.myVar,2); Rather than change myVar with each copy of this Text Field, is there a way to access whatever the configured text variable is? Generally try to stay away from ST in visu, but was curious regardless.
Last updated: 2 days ago

Post by mtho on JSON Utilities - JSON file written with invalid structure CODESYS Forge talk (Post)
I'm using the JSON Utilities SL library to write configurations in my program to a file. I'm generating the JSON data using the builder function block and all appears to work correctly. When I write the jsondata to file, I'm finding that some of the JSON elements are not being written in the right location in the file. Rather than writing they keys under the parent object, they get written outside the root JSON object at the end of the file. If I then try to read the file back into the program, I get an invalid_structure error. I don't get any errors when populating the JSON data or when writing the file. I attached an example of the JSON writer output. The problems begin with key P200. Each P200 should go under MBR1 through MBR3. Among the rest of the keys, they are supposed to be under different parent objects. I am using default values for wsLineBreak and encoding.
Last updated: 2024-03-06

Post by francescoc on Custom log CmpLog CODESYS Forge talk (Post)
Hi, I am trying to create a log in my application. Since I cannot find any documentation regarding modifying the codesys configuration file to be able to log in ms, i tried to create a new log via CmpLog.LogCreate. Below is the part of the code where I create the logger and write a test string. In the log tab of codesys I actually see the new log that was created, but it is empty, and in the folder I cannot find any files. I can't find any detailed documentation. Can you guys give me support? Are there any examples? Thank you IF NOT FirstCycle THEN LogName:= 'LOGS/TestLog'; LogOptions.bEnable:= 1; LogOptions.iMaxEntries:= 5000; LogOptions.iMaxFiles:= 100; LogOptions.iMaxFileSize:= 5000; LogOptions.szName:= LogName; LogOptions.uiType:= CmpLog.LogTypes.LT_TIMESTAMP_RTC_HIGHRES; LogOptions.uiFilter:= CmpLog.LogClass.LOG_ALL; LogHandle:= CmpLog.LogCreate(pOptions := ADR(LogOptions), pResult:= ADR(Result)); LogHandle:= CmpLog.LogOpen(pszName:= LogName, pResult:= Result); Component_Manager.CMAddComponent2('TestLogNEW', 16#00000001, ADR(udiCmpIdNEW), 0); CmpLog.LogAdd2(LogHandle, udiCmpIdNEW, CmpLog.LogClass.LOG_INFO, 1, 1, 'Logger started...'); END_IF IF TestWrite THEN TestWrite:= FALSE; CmpLog.LogAdd2(LogHandle, udiCmpIdNEW, CmpLog.LogClass.LOG_INFO, 1, 1, 'Write test'); END_IF
Last updated: 2024-03-16

Post by duvanmoreno24 on Modbus writing on value change CODESYS Forge talk (Post)
Yes, I tried to do what you put in the first code. However, I have a problem with that and that is that the inputs must be declared with the type. I have many data types running in my code (real, int, uint, bool) and I can't put them in the same function, another thing is that I need to instantiate that function for everything I want to write to the slave. You put a for to 200 but it means that it has to be the same data type and inside the array, but I want to get them individually. I'm struggling to do it in a good and efficient way like wago's E-cockpit does. in the first screenshot you can see, you simply type in value, change the package of things you want to write in value change and it does everything by itself automatically, without comparing any old and new values and even less having the need to activate a bool. , it is perfect.
Last updated: 2024-04-03

Post by abinvest579 on TCP Client CODESYS Forge talk (Post)
Hi All, I am using codesys based plc to read and control magna power DC supply over LXI protocol using SCPI command. To connect device required socket programming for that i am using Net base service library function block TCP_Client to establish connection over TCP/IP , TCP_Write to write SCPI commands and TCP_Read to read data from Magna power DC supply. I have attached screenshot for logic developed. I am able to connect and write commands to device but i not receiving any information from device. For writing Commands i also tried various end of line character like \n,<nl>, A, D, 10, 13, 0x0A, 0x0D but not received any status from device. For testing purpose i am using simple command '*IDN?' to read data. Also if tried to check on hercules software what data actually plc read, first it read correct data after that is read wrong data as see in screen shot. 'Hello World' was correct read and after that Codesys in replaced with 'Codesysorld' that is not correct way. Same issue also appeared for send data. Any one have face same issue how i can read data directly from device correctly and send data please suggest solution on this.</nl>
Last updated: 2024-07-01

Post by ofey on Modbus TCP communication CODESYS Forge talk (Post)
Hi! I tried setting up the PLC I'm working with (Beijer GN-9373) to connect to a modbus master running on a laptop. I have an ethernet connection (via USB-C to ethernet) between the laptop and the controller. I have tried following tutorial on how to set this up. I have added an ethernet device with the IP-address of the PLC. Further I added a ModbusTCP_Slave_Device with default settings. I get the error "Failed to open TCP Port: 1" when I try to go online with the PLC. Earlier I tested the exact same set up with the soft PLC from codesys. I can then read/write values correctly with the Modbus master i have running on the laptop. Hope anybody can help me with this, thanks in advance!
Last updated: 2023-10-06

Post by ewi04 on Recipe Manager - RecipeManCommands, load & write wrong values, Bug? CODESYS Forge talk (Post)
Hallo, I have a strange problem with the recipe manager. ISSUE: When using RecipeManCommands not all values are loaded correctly. Saving a recipe with CreateRecipe(), ReadAndSaveRecipe() or ReadAndSaveRecipeAs() works without any problems. BUT: LoadRecipe(), WriteRecipe() or LoadFromAndWriteRecipe() do not load the data correctly. It is Interesting that we have a different error pattern with LoadRecipe() than with WriteRecipe() or LoadFromAndWriteRecipe(). LoadRecipe() does not load all data and WriteRecipe() or LoadFromAndWriteRecipe() overwrites some data or assigns it incorrectly. And it is also strange that LoadRecipe() writes the values to the PLC. Normally it doesn’t do it. It makes no difference whether the memory type is textual or binary. I have an object consisting of STRUCTs which is inserted in the recipe definition. Environment: Codesys V3.5 SP19 Patch 4 (64Bit), Recipe Management 4.2.0.0 *Add a project (reduced to the problem)
Last updated: 2023-11-15

Post by ewi04 on Recipe Manager - RecipeManCommands, load & write wrong values, Bug? CODESYS Forge talk (Post)
I'm getting closer to the error. The combination of STRUCT and ARRAY probably causes the strange behavior. As soon as the ARRAY is followed by a variable, the problem arises. Examples: X: ARRAY[1..2] OF INT; // okay Y: ARRAY[1..2] OF STRUCT; // problem Z: STRUCT; Z.ArrayOfInt[1]; // okay Z.ArrayOfStruct[1].Variable // problem // *update - array of array also causes the error A: ARRAY[1..2] OF ARRAY[1..4] OF BOOL; // problem I can't be the only one who has this problem. Or? Maybe there is a solution. Anyone? Or is it a bug after all?
Last updated: 2023-11-17

Post by jegerjon on Testing of Codesys program CODESYS Forge talk (Post)
I have a simulation function that toggle xSimActive. I map all IO variables to "IO GVLs" when xSimActive=0. I map IO corresponding SimIO GVL to "IO GVLs" when xSimActive=1. Then I write code for the simulation program that runs when xSimActive=1. Typically increase flow corresponding to pump speed, simulate tankfilling corresponding to flow and so on. I made a FC that require a correct code to activate simulation to avoid unintended activation by service dept. When comissioned remove any possibility to activate simulation. Super when officetesting and supporting service dept. + cheap as it requires no additional equipment, and it is easier to support customer later on in the life cycle as you can test proposed changes without setting up a testlab.
Last updated: 2023-12-07

Post by jegerjon on Testing of Codesys program CODESYS Forge talk (Post)
I have a simulation function that toggle xSimActive. I map all IO variables to "IO GVLs" when xSimActive=0. I map IO corresponding SimIO GVL to "IO GVLs" when xSimActive=1. Then I write code for the simulation program that runs when xSimActive=1. Typically increase flow corresponding to pump speed, simulate tankfilling corresponding to flow and so on. I made a FC that require a correct code to activate simulation to avoid unintended activation by service dept. When comissioned remove any possibility to activate simulation. Super when officetesting and supporting service dept. + cheap as it requires no additional equipment, and it is easier to support customer later on in the life cycle as you can test proposed changes without setting up a testlab.
Last updated: 2023-12-07

Post by ewi04 on Recipe Manager - RecipeManCommands, load & write wrong values, Bug? CODESYS Forge talk (Post)
Hello, according to Codesys, the problem should be solved with version 4.3.0.0. After the update to version 4.3.0.0 I had the problem that the recipes weren’t saved correctly, but loading was okay. Return to the version 4.2.0.0 didn’t change the behavior. Strange… So I uninstalled the update, cleaned the project and built it new. The known behavior of version 4.2.0.0 was back. Update to version 4.3.0.0, clean and build it new, it works. Even with version 4.2.0.0. Strange, but okay. Notice: ManCommands.LoadRecipe() no longer writes into the PLC. Just as it should be. As of now, I can use the new version.
Last updated: 2024-01-05

Post by i-campbell on What does CODESYS expect to do when I get such an error message CODESYS Forge talk (Post)
you need to get the addons that the person that programmed it used. I always store an .installation-config file alongside the project. If you have lost that, then it gets a bit of a headache: I think even with SP18 you can hit yes to open it anyway, and it will suggest which addons it thinks are missing, if you double click the yellow "missing-addons" in the status bar. If you know you have the right addons, you can do a "Save As.." and it will write your current addon list to the file, and you wont get the error next time.
Last updated: 2024-01-08

Post by jtebokkel on Access to the path *** is denied CODESYS Forge talk (Post)
I am also having this issue. It was working fine for the first 2ish months and is now throwing this error. I can just try and go online again a second time and it works. I'm wondering if there is an environmental variable or something that isn't set that is causing it to use an empty path as a temp directory. The empty path will be the location the app is running from which is that path C:\Program Files\CODESYS 3.5.19.50\CODESYS\Common. The permissions don't allow a normal user to write to that directory which causes the error. It also only seems to happen when there are changes or the build has been cleaned.
Last updated: 2024-02-14

Post by mani-i4point0 on Issue with WebVisu on Raspberry PI CODESYS Forge talk (Post)
Hi, I am running Codesys Runtime by purchasing 'Codesys control for raspberry pi MC SL', I am trying to use the Variables from my GVL's. Few of the variables used as a Pushbutton form the Visualization. These 'BOOL' Variable getting unlatched automatically even though there is no write function in the Overall project. All of them are 'Read' functions, at the same time few other BOOL variable behaviors are seems to be fine. I have tried, clean all and download, serval time restarted the hardware. Happy to share any any information. Your input to resolve this issue would be highly appriciated. Version Details: codesyscontrol 4.8.0.0, armhf codesyscontrol based on SDK 3.5.19.0
Last updated: 2024-03-20

Post by struccc on Release SP20 - Changes in behaviour? CODESYS Forge talk (Post)
Dear all, I've just started to migrate some of my ancient projects to SP20. There is one strange error (?) I have noticed so far. In a method call, depending on the circumstances I would like to return reference to an object, or an invalid reference: METHOD Add_EVT_OUT : REFERENCE TO FB_MSG VAR END_VAR IF __ISVALIDREF(refMSG_Entry) THEN Add_EVT_OUT REF= MANAGER.AddMsg_EVT_OUT( refMSG_Entry, _Get_EVT_Message(MSG_EVENT.OUT), _Get_EVT_AddCode(MSG_EVENT.OUT) )^; ELSE Add_EVT_OUT := 0; END_IF So far setting a reference variable to 0, did this. But now, the expression Add_EVT_OUT := 0; gives an error: [ERROR] DB_WTP_370: Add_EVT_ACK MSG_TRIGGER_EXT: C0032: Cannot convert type 'BIT' to type 'REFERENCE TO FB_MSG' Naturally... I can write: Add_EVT_OUT := DWORD#0; But is this the correct way? Is there any constant I could use instead, like "NULL"? Or this is totally wrong and to be avoided?
Last updated: 2024-03-24

Post by david24 on Map in Codesys CODESYS Forge talk (Post)
Hello everyone, I have the task of programming a map. With the help of the visualization element "Table", I have managed to accomplish this. In the Input Configuration, I activated the option: "Write Variables", so that the user can change the values in the map. To test the program, I select the Online Mode (Simulation).There I change the values in the map. When restarting the program in CODESYS, the changes in the map are no longer there. Does anyone know an approach how to save the changes in the map? Thank you for your support Best regards David
Last updated: 2024-04-02

Post by alexgooi on Modbus writing on value change CODESYS Forge talk (Post)
The way I usally tackle this is by syncing only words (then you are able to use the FB above). If you then want to write a Boolean simply type it like this. Value[1].0 := Bool1; Value[1].1 := Bool2; Value[1].2 := Bool3; Uints have the same number of bits than a INT/WORD so these ones will work as well (they are only represented diffrently). A Real will work but you will loose some infomration in the conversion. If you want to keep the information you can convert 2 words to a float with a function (for example with the IEEE-754 standard) . In this way the syncing to the server is very simple and in the Codesys Program you decide what part of the word you want to use.
Last updated: 2024-04-03

Post by tecnocons on Trouble Writing Files to External Paths in CODESYS CODESYS Forge talk (Post)
Hello everyone, I'm encountering an issue in CODESYS regarding writing files to external paths. Despite correctly configuring the placeholder in the CODESYSControl_User.cfg file to allow access to an external folder, CODESYS doesn't seem to write any files, and no errors are reported. The issue on the older versions was absent with no placeholders. I've checked the operating system permissions, and they seem to be in order, but the issue remains. Has anyone faced a similar situation or has any suggestions on how I might resolve this problem? Any help would be greatly appreciated. Thank you in advance for your support. I'm using raspberry PI as a logger. RPI3 Buster Codesys 32bit SL V4.11 Codesys Win64 3.5.20 [SysFile] PlaceholderFilePath.1=/home/pi/scan, $SCAN$
Last updated: 2024-04-09

Post by jonasz on Discontinuity of A/B/C axis movement. CODESYS Forge talk (Post)
Hi, My problem was related to the behavior of the modulo axis, but maybe you will find something useful from what I write. The solution lies in path processing. Codesys offers a G-code analysis tool. Insert a CNC object into the project. The CNC settings object will be added automatically. By inserting appropriate processing modules into the CNC settings object and parameterizing them, you can test the behavior of the axis. When the effect is satisfactory, remember to add the module from CNC settings in the correct order in the processing path. Each CNC machine case is different. You need to spend some time to get your design tailored like an Armani suit. Good luck.
Last updated: 2024-05-09

Post by pazderai on CanOpen write issue CODESYS Forge talk (Post)
Thank you for an answer. Unfortunatelly, it doesn't work. The slave needs command byte as follows 0x22. It means expedited transfer where s-bit is not set, therefore data length is not specified. If I use segmented mode by CiA405.SDO_WRITE_DATA it produce command byte as follows 0x21 which is unfortunately supported by the slave and it returns with error 0x05040001 - SDO Abort Code -Client/server command specifier not valid or unknown. I can use CAN API low level to overcome this problem where it is possible to set 0x22 as a command byte, but than I can use user interface to set the communication probably, because I thing that machine expert uses library CiA405.SDO_WRITE for setting the slave. Or am I wrong?
Last updated: 2024-07-16

Post by shrikantp007 on new to codesys help on modbus with ardunio modbus rtu CODESYS Forge talk (Post)
Hello , I am new to codesys ,working with it for just 15-17 days so ,i think i am able to installed it and configure it ,not i want to use ardunio program (smart dustbin ,college project using motor and Ultrasonic Module HC-SR04 and servo motor). i use ardunio program to write code with chatgpt to work ardunio as a modbus rtu as i dont have ethernet or wifi shild ,i wrote program in ariduno but now don have idea what change i have to make in codesys to comunicate as modbus slave it give error with bus error ,where i can get all errors ? Thanks in advance :)
Last updated: 2024-07-21

Post by ofey on EtherCAT fieldbus CODESYS Forge talk (Post)
Hi, everyone! I'm trying to set up a PLC controller and a connection to an EtherCAT slave device in Codesys. I want to create a flexible program that I can upload to multiple controllers with different remote IO connected (same program). On one plant i may have 5 AI-cards and 3 DO-cards, and on another I may have 4 AI-cards and 2 DO-cards. For not needing to maintain several different programs wih different devices defined in the program (one for each set up) I thought that using a remote IO would make it easier having a single program. That way I could refer to different memory addresses instead of predefined slots/channels and IO's, that would give me errors if there was a different IO on the plant than what the program expected. When I tried setting up the etherCAT master, I saw that I had to define the etherCAT slave devices with the different IO'cards for me to be able to refer to the memory addresses in a PRG. Exactly what I was trying to avoid. My setup is something like a program that can handle 16 separate pump controls. In a year maybe 6 plans get deployed, and depending on how large the project is, the number of pumps can vary between 4 and 16. And the managers dont want to have IO's for all 16 pumps on every cabinet, and I dont want to maintain 16 separate projects files in case of updates etc. I thought the best way to tackle this was having a single project that read/write data to the different pump IO's by remote IO (fieldbus ethercat) addresses. And the number of pump controls are activated by an external GUI. If pump 1-6 is activated by the GUI, then the PLC-program tries to read/write input/outputs from predefined addresses for the expected IO's. My test setup is a PFC200 WAGO controller and a EtherCAT fieldbus coupler (750-354) with some IO. I hope I didn't explain this too horrible, and if there is a more easy and elegant solution for this challenge I appreciate a feedback on this.
Last updated: 2024-04-08