Post by hassaank on CODESYS V3+ WAGO PFC200+ MODBUS RTU
CODESYS Forge
talk
(Post)
Hi everyone, Iβm new to CODESYS and Wago devices, and Iβm trying to set up Modbus RTU communication. I have a Wago PFC200 (8110) and a 750-653 RS485 module, and I want to read data from an energy meter using Modbus RTU. Thanks in advance for your help!
Last updated: 2025-03-17
Post by fmon on Modbus TCP client reconnection problem
CODESYS Forge
talk
(Post)
Problem solved The client modbus cycle time was linked to a task at 500ms. Whereas the channel modbus was at 200ms. Certainly problem of packages synchronisation. I let the client modbus cycle time to be handled by itself (See attachement) --> "Use the bus cyle time parameters" (traduce from french) See attachement
Last updated: 2025-03-18
Post by fmon on Modbus : dis- / re-connect cable: modbus does not re-start
CODESYS Forge
talk
(Post)
Problem solved The client modbus cycle time was linked to a task at 500ms. Whereas the channel modbus was at 200ms. Certainly problem of packages synchronisation. I let the client modbus cycle time to be handled by itself (See attachement) --> "Use the bus cyle time parameters" (traduce from french) See attachement
Last updated: 2025-03-18
Post by eschwellinger on Codesys Network driver install for Codesys Control RTE x64
CODESYS Forge
talk
(Post)
Yes, either adding in the CODESYSContro_User.cfg because the driver will no longer appear in the list or type the name from the documentation in the configuration and when the gray check mark appears, the driver is also installed. It is just not selectable anymore.
Last updated: 2025-03-21
Post by kevinm on Programmatically change Tappet on a cam
CODESYS Forge
talk
(Post)
I am considering using a SoftMotion cam and tappets to activate functions on a machine - for example, triggering a pneumatic valve. I need the ability to change the actuation point (tappet "X" location) from the HMI during machine commissioning. Is there a way to change the "X" value of a tappet programmatically?
Last updated: 2025-04-01
Post by imdatatas on Create separate repositories option not working in Codesys Installer
CODESYS Forge
talk
(Post)
Hello Everyone, Create separate repositories option not working in latest Codesys Installer 2.4.0 (Build 3545). It seems like a useful option regarding install the different versions of Codesys IDE on the same computer and keep in isolation from each other, but unfortunately it didn't work. I hope the Codesys team can fix this issue in the next update. Regards, Imdat
Last updated: 2025-04-04
Post by kevinm on Attaching Trace variable to Frame Configuration Variable
CODESYS Forge
talk
(Post)
Is it possible to show a variable from a Frame Configuration in a Trace on that Visualization? I want to pass the FB for an AXIS_REF_ETC_SoE_Standard to the visualization and display live axis data in the visualization. However, I cannot find a way to use a Frame Configuration variable in the Trace Configuration dialog.
Last updated: 2025-04-04
Post by andrej on Creating, using an external Function.
CODESYS Forge
talk
(Post)
Hello, many thanks for your reply. I checked the logs. It seems that dll is not loaded. However other dll such as the Webserver are loaded. Could you tell me what I need to do such that my dll is loaded. (Furthermore I changed the C-Function a bit. I used the M4.exe from the SDK.) Many thanks.
Last updated: 2025-04-23
Post by dnordenberg on BOOL variable in OPC UA and modbus simultaneously
CODESYS Forge
talk
(Post)
How can I have an BOOL variable that is read/write in both modbus TCP server and from OPC UA at the same time? Variables with %MX.n %QX.n addressing which is used for BOOL/coils in modbus server is not allowed in OPC UA symbol list on Schneider M251 controllers. I have already asked on Schneiders forum but there are not a lot of codesys experts over there :( So OPC symbols can't have a address and the modbus TCP server needs a address. So how should I do it then? It seems like an impossible combination. Since I want read/write access from both ways I can't just simply make a second variable and assign it the value of another since it would be a one way assignment. I also tried using VAR_CONFIG which then makes the address syntax %Q or %M in my main variable list and that fools OPC UA Symbol Configuration to allow it and then I add the complete %MX.n address of it in the VAR_CONFIG list. This semi works, I can toggle the BOOL from modbus but the OPC UA symbol seems to be read only. It displays symbol status but nothing happens when I toogle it. I think I need another way to have the variables and symbols pointing to the same bits in memory... My plan B is to write a BOOL array compare FB that saves a history bit from previous cycle and if that does not match current status at next cycle for either the OPC symbol or the modbus variable then it copies the new status over to the other. Maybe ugly but it's like my last alternative. Kind regards David
Last updated: 2025-07-14
Post by timvh on Reading multiple lines from csv file
CODESYS Forge
talk
(Post)
Not sure, but maybe before you enter step 5, set i, lineindex and charIndex to 0. And the buffer variable should have a size bigger than 1 line. Additionally I think you should set bufferstart to 0 before you enter step 5. And in the OSCAT function you always point to the buffer address, but shouldn't this be (buffer + bufferstart)?
Last updated: 2025-07-23
Post by davemansell on control loop library IIR filter
CODESYS Forge
talk
(Post)
Hi there i am experimenting with the IIR filter from the control loop library but have been unable to get it to function no matter what inputs I set I get errorID of wrong_configuration (3). Does someone have a working example that they can share. Best regards Dave
Last updated: 2025-07-29
Post by astrum on OPC UA Information Model Error "Dimensions must be empty"
CODESYS Forge
talk
(Post)
Hello everyone, does anyone know what this error means: Internal Error in code generation for http://opcfoundation.org/UA/DI/: Dimensions must be empty. I use the standard information models from Codesys and haven't even called the Information Model, but my program can't compile. the only thing I did was to insert the Communication Manage.
Last updated: 2025-08-11
Post by davemansell on explicit cast ENUM to UINT and vice versa
CODESYS Forge
talk
(Post)
This is from sometime ago but below might help someone else; this could be done via POINTERS. Make sure you protect for NULL pointers etc if you take this approach. // DECLARATION myEnumValue : enumMyEnum; u8 : USINT; pmyEnumValue : POINTER TO enumMyEnum; pu8 : POINTER TO USINT; // CODE pu8 := ADR(u8); pmyEnumValue := pu8; myEnumValue := pmyEnumValue^; // dereference the pointer
Last updated: 2025-08-21
Post by davemansell on explicit cast ENUM to UINT and vice versa
CODESYS Forge
talk
(Post)
This is from sometime ago but below might help you could do this via POINTERS. Make sure you protect for NULL pointers etc if you take this approach. // DECLARATION myEnumValue : enumMyEnum; u8 : USINT; pmyEnumValue : POINTER TO enumMyEnum; pu8 : POINTER TO USINT; // CODE pmyEnumValue := pu8; myEnumValue := pmyEnumValue^; // dereference the pointer
Last updated: 2025-08-21
Post by antonz on CoDeSys v3.5: creating libraries for both 32-bit and 64-bit controllers
CODESYS Forge
talk
(Post)
Thanks Tim. I would think it somehow is relevant when creating a compiled library, but that may very well not be the case. If I understand you correctly, then the same compiled library created from my source code would work for both 32 bit as well as 64 bit controllers.
Last updated: 2025-09-01
Post by alexgooi on Execute a .py file with Codesys
CODESYS Forge
talk
(Post)
Hello yann, In the past I have experimented with the execution of Linux commands using Codesys. Maybe this article helps: https://www.linkedin.com/pulse/run-linux-commands-from-codesys-jouke-aalvanger When you are able to execute Linux commands in Codesys, you can run the Python script.
Last updated: 2025-09-03
Post by kporter on Removing <Empty> node in Device Tree
CODESYS Forge
talk
(Post)
I initially created a SoftMotion axis for my EtherCAT CoE drive. I wanted to change it to use SoftMotionLight so I deleted the SM node, which left an <empty> node. I created the SML device, but the <empty> node remains. How can I remove that from the tree? </empty></empty>
Last updated: 2025-09-06
Post by bilalchaudhry33 on IFM Controller CR7XXs
CODESYS Forge
talk
(Post)
HI, I am new to Embedded and telematic field . I am using codesys to program IFM controller and try to communicate two IFM controller over the CAN bus. I need some help and link tu tutorial I have no idea about codesys . I want to do in ST. I am using CAN RAW library from IFM . On following SS there is red triangle on CAN as well.
Last updated: 2025-09-24
Post by mondinmr on What happened to Python?
CODESYS Forge
talk
(Post)
What happened to Python? Iβve just installed version 3.5.21.3 of the CODESYS development environment. Iβm coming from 3.5.19.5. What happened to Python scripting! We rely heavily on it for the automatic generation of thousands of lines of code! It seems absurd to me that such an important feature has been removed!
Last updated: 2025-10-01
Post by rene2 on How can you get the active frame index from a frame
CODESYS Forge
talk
(Post)
I think I struggle with the same issue. I tried the currentVisu variable but this is the active Visualisation. I have a dialog with a frame with frame configuration like in the picture. I would like to use the index te be used to make a button look like it's pressed/selected.
Last updated: 2025-10-14
Post by snhatton on OPC UA: How to change NodeId ?!
CODESYS Forge
talk
(Post)
You can change the node id by adding the following to /etc/CODESYSControl.cfg: [CmpOPCUAProviderIecVarAccess] CustomNodeName=MyPLC123 Then restart the runtime and the new Node name will appear with the connection. I don't know if it's possible to remove the |var| from the name. I hope this helps!
Last updated: 2023-12-11
Post by zatalian on Codesys Control for Raspberry Pi 4.10.0.0 - Raspberry Pi OS > 2023-12-05
CODESYS Forge
talk
(Post)
I tried both 3B en 4. But every time with a lite version. I didn't try the full version of raspberry pi os. Nice to hear you are aware of the problem and trying to fix it. I'll hold on to the image from 2023-10-10 for now.
Last updated: 2023-12-12
Post by nz-dave on Bool turning on in case stament in wrong state?
CODESYS Forge
talk
(Post)
pretty sure its not. ive done a cross reference and only have one write that sets it to true. Only way i can stop it is to remove the function block call from the main pou that is running said case. its got me stumped:/
Last updated: 2023-12-16
Post by preimesbergert on Codesys Control for Raspberry Pi 4.10.0.0 - Raspberry Pi OS > 2023-12-05
CODESYS Forge
talk
(Post)
Same issue here: Raspberry Pi 4 Model B HW 1.5 Regardless of the image (tried 32bit / 64bit version from Raspberry Pi Imager- all the "standard version") and with all tested Codesys Control versions (4.2.0, 4.8.0, 4.10.0) and regardless if single core / multicore / 64 bit variant.
Last updated: 2023-12-21
Post by dhumphries on Execution Order of Function Blocks
CODESYS Forge
talk
(Post)
Function blocks in a SFC are executed left to right, top to bottom, instructions in ST are executed from left to right top to bottom as well. I think you are asking about the execution of POUs although you use the name function block, I believe POUs are executed in the order they are shown under the main task.
Last updated: 2023-12-28