CanOpen Manager - Timeout till _3SCOS.DEVICE_STATE.OPERATIONAL

2020-07-22
2022-02-09
  • neapolitaner - 2020-07-22

    i'm using the CanOpenManager to communicate with my devices (5pcs). Unfortunately the Manager sends a ResetNode to all of my devices without any reason. The time between the ResetNode-cmd is very random -> could be a few minutes to few hours!!?!
    I've made lot's of canbus-traces, can see the ResetNode-cmd by the Manager but can't find any reason for the reset-cmd ...

    -> so my last guess is that there is a intermittet failure on the bus and the manager sends the reset within less than one second!?!

    -> is it possible to modify the timeout of the CanOpenManager that the ResetNode is sent only after a few seconds

    br,
    Andy

     
  • eschwellinger

    eschwellinger - 2020-07-22

    Hi,
    which plc in which version are you using?
    Could you enable CANOPEN_DEBUG as compiler define ( not needed =>3.5SP16
    Then attach the plclogger - maybe the can trace too.

    "Unfortunately the Manager sends a ResetNode to all of my devices without any reason"
    without a reason, the manager certainly doesn't
    There will be a heartbeat error probably?!

    BR
    Edwin

     
  • neapolitaner - 2020-07-22

    i'm using 3.5/SP10 .. i have to stick to that version because the ecu-supplier (TTControl) only supports that version

    "without a reason, the manager certainly doesn't" -> :) i guess so, but i can't really reproduce the issue and depending on my can-traces i can't really naildown any bus-errors or similar.

    my master is producing a heartbeat with 500ms -> upon simulated buserrors the CanOpenManager sends the ResetNode within less than 1sec (guess 1,5*500ms)

    -> how is the hb-timeout in the CanOpen Manager calculated?

    -> so IMHO increasing the errorthreshold/hb-timeout up to 3sec would probably fix my sporadic buserrors(missing node-hb)?!

    -> should i set asymetric hb-times (master=500ms, nodes=100ms)?

    a restart of the can-nodes is very 'bad' in our application therefore i'm looking for a more forgiving behaviour of the CanOpenManager

     

    Last edit: neapolitaner 2020-07-22
    • jenslindruo - 2022-02-09

      Hi neapolitaner
      Did you ever find a solution to this problem? I am currently facing a similar situation.

       
    • jenslindruo - 2022-02-09

      Hi neapolitaner
      Did you ever find a solution to this problem? I am currently facing a similar situation.

       
    • jenslindruo - 2022-02-09

      Hi neapolitaner
      Did you ever find a solution to this problem? I am currently facing a similar situation.

       
    • jenslindruo - 2022-02-09

      Hi neapolitaner
      Did you ever find a solution to this problem? I am currently facing a similar situation.

       
  • neapolitaner1 - 2022-02-09

    hi,

    finally i found the issue ... on my CAN-bus there are several CanOpen and J1939 devices. To keep the busload as low as possible i set the CanOpen PDO's to different interval-times. Therefore every few minutes/hours (depending on the chosen timings) all PDO's need to get handled at the same time.

    This "spike" in bus-load and especially cpu-load required way too much processing-time and exceeded the cycletime of the CPU.

    means: i've chosen 10ms as minimum CPU taskcycle
    during "spike": the CPU taskcycle-time took up to 14ms and probably messed up the internal timing/statemachine of the CanOpenManager

    solution: i've set the CPU-taskcycle-time to 20ms and since that modification everthing is fine!

    br,
    Andy

     